3765.0. "Recording on alarm rules fails" by BACHUS::FOLENS () Fri Sep 18 1992 09:53

    I'm trying to start recording on a alarm rule. When I start it,
    it tells me the record is successfull created. But when I do
    a show recording, its telling me its active but the number of
    successfull polls=0 and the number of failed polls=1 with the the last poll
    failure reason = "MCC specialized exception code: 385".
    Should recording work on alarm rules? I could find it back in the doc.
    
    -Geert-
T.RTitleUserPersonal
Name
DateLines
3765.1works on Ultrix but not on VMSTOOK::SHMUYLOVICHFri Sep 18 1992 13:4128
> last poll failure reason ="MCC specialized exception code: 385".

	According to the data dictionary it tells "The rule ... was not
	enabled, and therefore has no counters".


>    Should recording work on alarm rules? 

	You can record alarm rules on Ultrix but not on VMS.

	The Alarms FM performs polling operations in itself (not in the
    background process like the Historian) and stores all runtime information
    about rules in memory. 

	On Ultrix each FM is running as a separate process and therefore
    when the Historian background process issues a "Show....rule..." directive
    it comes to the same Alarms process which is performing polling operations
    (assuming that both these processes are running under the same uid).

	On VMS each instance of MCC uses its own copy of FM so one Alarms FM
    "does not see" rules enabled by another Alarms FM.

	You can see this behavior if you invoke two MCCs, enable Alarms rule
    from one of them, and issue a "Show ... rule.." directive from another.