768.0. "EMU...overtemperature" by GIDDAY::CALLAGHAN (If it works dont fix it) Wed Feb 12 1997 18:55

    I have a site with SWXRC-05 raid controllers (in a CSS custom cabinet)
    that is having the Environmental Monitor Unit (EMU) detecting an
    overtemperature condition.
    
    I have had the customer measure the air temp outside the cabinet at 25C
    and internally at 31C. This configuration is running in an open office
    environment.
    
    My understanding is that the SWXRC controllers had an envoronmental
    temp spec of +18C to +24C, and was intended for operaion in a Class A
    computer room environment.
    
    My question is: At what temperature does the EMU activate its overtemp
    		    alarm?
    
    Armed with this information I can then state to the customer the
    internal temperature that the SWXCR is reaching, and then push back
    onto them to address the problems of air cooling for this
    configuration.
    
    Thanks
    Patrick Callaghan
T.RTitleUserPersonal
Name
DateLines
768.1OvertempJULIET::SMITH_PThu Feb 13 1997 19:099
    On Page 7-18 of the SWXRC-04 manual -Part #EK-SMCS1-UG.
    
    	Section 7.8.3 - Error - Temperature Light (Amber) On (See Figure
    			7-6) The Shelf temperature is above the recommended
    			operating temperature of 35C(95F).  The blowers run 
    			at high speed.  If the shelf teperature rises over 
    			50C(122F) The subsystem shuts down.
    
    Paul