291.0. "Electrical, Wiring, etc" by DRAGON::SCHIFF () Tue Sep 16 1986 01:16

The following incident happened to my house last week.  Any thoughts, comments,
or advice would be greatly appreciated.

Background:                            

Sewer construction is being done in the street in front of my house.  Since the
street foundation is mostly ledge, blasting is being done with dynamite
charges. Standard procedure has been for the construction company to disconnect
the water service to the homes across the street from me, blast, and then
reconnect the water service.  Water service is not being disconnected on my
side of the street since the water main is located on my side.  The water
service pipe also serves as the electric ground for my house (and I assume
the same is true for everyone else's service pipe). 

The electric company's transformer is located on a pole in front of my house.
                
My house has 200 amp service and electric heat.  There were no previous
electric problems that I am aware of.  The electric dryer is 220 by itself
on a 220 volt circuit.  However, when the dryer starts up, the lights in
the house dim slightly for a second or two.  When the electric heat is turned
on, no change is noticed.


What Happened:

Wednesday night I discovered that the following no longer worked:

         Two electric garage door openers (the motor mechanism)
         One TV 
         One VCR
         One Battery Charger
         Two cable TV boxes
         One DF03
         One transformer from my alarm system.

The VCR and DF03 needed fuses replaced.  The TV's fuses are fine but the
machine is dead;  there does not appear to be any "meltdown" inside the TV.  I
can't find a fuse in the garage door openers.  With the exception of one cable
box, all the components are fairly close to each other but at least three
circuits are involved; one cable box, VCR, and TV are plugged into the same wall
outlet.  The wall outlets are fine and no circuit breakers were tripped
at the the main or any other (e.g. electric water heater) service panel.

Thursday morning:

Speaking to the construction people, I discovered that when they had
reconnected my across-the-street neighbor's water service the previous day, the
person making the connection received a shock and there was an electric arc or
spark. Although I don't know for certain, this is probably when my appliances
were damaged. 

The electric company came by and while they were checking my ground connection
to my water pipe, the house experienced a severe brownout. This was at the same
time as the construction people once again disconnected my neighbor's water
service.  This brownout lasted about 3 minutes and was significant enough that
I had to disconnect my refrigerator for the duration, since it was really
laboring.   My neighbor's water pipe was reconnected about an hour later (well
after the brownout had ended) but there were no sparks or electric currents
present at that time. 

At one point, the electric company was checking the connections at my electric
meter and noticed that a small auxiliary box mounted there to provide
additional 220 service to one room in my house was "reading 190 across one leg
and 0 across the other".  This reading was not reproducible when it was tried
later. This circuit leads into a service panel in a room under my garage and
was supposed to drive an electric heater; however the service panel in the room
under the garage has been turned off for the five years I have lived here. 

The electric company can find nothing wrong and no appliances were damaged at
any of my neighbors homes (including the one across the street).  I was also
the only house to experience the brownout. 

Current Status:

No one knows what happened or if it will happen again as the sewer construction
proceeds down the street.   I unplug anything with transistors and/or outlet
mounted stepdown transformers before the construction starts each morning and
plug it back in at night.  The electric company has promised to place recording
meters at my service panel.  Everyone seems concerned (especially the
construction workers since they are setting off the dynamite charges will
electrical current), but no one has an answer.   

The electric company did express some concern that the lights dimmed briefly
when a dehumidifier in the room under the garage cycled on.  They claimed that
I was close enough to their transformer that this should not have occurred.
They think that the connection from the street to my meter (which is mounted on
a pole on my property about 75 feet from the street) may be deteriorating.  I
always thought that a dehumidifier drew significant current during startup;
however, if the dryer is on a separate 220 circuit, should it cause the
lights to dim on start-up? 
                                                                         

Question:

Has anyone ever experienced anything like this?  Where do I proceed from
here?  

    
mike
T.RTitleUserPersonal
Name
DateLines
291.1Check the neutral coming into your houseSOFCAD::KNIGHTDave KnightTue Sep 16 1986 11:107
    I had a problem like that many years ago.  It turned out that the
    neutral line was open at the service feed somewhere.  Thus many
    appliances had 220 across them and many had 0.  This kind of situation
    is extremely dangerous (fire hazard, etc. etc.).  If you have an
    open neutral and your ground connection is VERY good, nothing much
    happens.  If the ground is bad or becomes bad, things go to hell
    in a handbasket fast.
291.2Neighbor's Short?USFHSL::PIEPERWed Sep 17 1986 15:3524
    I just thought I'd throw a few comments out to maybe draw some
    discussion about this one...
    
    My first reaction to this one is to think that the problem is really
    at your neighbors house (the one whose water line was disconnected
    when you had your problems).  There is no reason that I can think
    of that there should be a potential difference between his water
    line and the water main (the shock the workman got and the sparks
    when reconnecting). My theory is that the neighbor's water line
    is shorted to a hot wire somewhere in his house. This of course
    is not a "dead short" but probably a nick in a wire causing a 
    high resistance connection. Since ground and neutral are tied together
    in the service panel, their ground and neutral being tied to a hot
    lead essentially ties your ground and neutral to the same hot lead
    (giving you a zero reading on one side and 190 on the other)because
    your ground is tied to their ground via the water lines.
    
    just a couple of questions:
    
    Are there any more houses that are serviced from the same transformer
    that you are?
    Did anyone else have any electronic stuff get damaged?
    
    Joe
291.3Sounds FamiliarMAXWEL::BROSNIHANBRIANWed Sep 17 1986 16:167
       We are also having some water work done on our street. Last
    week our neighbors had the fire dept. there because they smelt
    smoke and the lights were flickering. After invesigating,  the
    Mass. electric company said that the water dept.  disconnected
    their ground wire from the water meter which caused an electrical
    surge. From what they told me... a few of thier wires got fried
    and the water dept. is liable.
291.4PROBLEM SOLVED!DRAGON::SCHIFFFri Sep 19 1986 00:5268
The problem has been solved (I hope)!  (.1) had the answer.

The electric company came by my house yesterday morning to install recording
meters on my main service panel.  While they were there, they checked the main
circuit breaker box and discovered that the neutral connection was very loose.
This service panel had supposedly been "checked" by the town electrician and an
electrician I had called. 

The electric company also checked the connections at my meter and decided that
the neutral there was also bad.  This had been discovered the first time they
were at my house and said it probably was not the cause of the problem but I
should have my electrician fix it.  My electrician looked at it but had to
order the appropriate parts so he did not fix it.  (The wire is aluminum, going
into the box, and the wire exiting from the box and going into my house is
copper. The wires are joined in the meter box with a device which clamps each
piece and serves as a connection.  The correct procedure is to apply a special
paste (Penetrox?) on the wires to prevent corrosion.  This was not done 17 years
ago when the house was built.) 

The electric company removed both wires from the very corroded clamp and the
wire hidden under the clamp was in very poor condition.  They cleaned the wires
with a stiff metal brush and then created a fairly solid, but temporary, jump
between them.  The jump apparently violates electrical codes for permanent
connections but they are allowed to make them for emergencies.  They are also
not supposed to fix any connections belonging to the customer (rather the
customer's electrician is supposed to do this under their direction); however
this can be waved in an emergency if the customer is willing to assume any
liability (which I was).  I still have to get my electrician to make a
permanent connection with the proper clamp. 

We went back into my house and started the dryer which no longer caused the
lights to dim on start-up.  They explained to me that the dimming was
previously caused by the dryer motor (at 110) rather than the dryer heater
resistance (at 220). The "definitive" test they suggested is to run the washing
machine in spin cycle; this worked fine with no lights dimming.  They came back
this morning to remove their recording meters and everything appeared fine.
                 

In summary, I have probably had this problem for the five years I lived in the
house.  The dynamite blasts for the sewer construction most likely caused
vibrations that made a loose connection(s) much worse.  As I understand it, the
grounding load is supposed to be distributed 50-50 between the neutral at the
service panel and the water pipe ground;  my corroded/loose neutral connections
threw this into a very unbalanced (20-80?) state.  Since I was the only
one in the neighborhood to suffer any damage, the disconnection-reconnection
of my neighbor's ground appears to have further upset this condition but
did not harm his appliances (his lights don't dim so his neutral is probably
fine).  Note:  dimming lights don't automatically mean you have a poor neutral,
it is also a function of the service rating and distance from the transformer.
Since I have 200 amp service and the transformer is in front of my house,
dimming lights did, in fact, indicate a problem.

The connection at my circuit breakers is something I could check every couple
of years; however, how often do you remove your electric meter to check
the connections there?  This problem would not be recognized until you ran into
a problem like mine, or worse yet, a fire.

I also feel that the electric company really did a super job in helping me.
The connections behind the meter and at my service panel are legally my
responsibility, not theirs.  They could have just diagnosed a potential
problem and come back after I had fixed it.  

I think I'll log off and plug in the rest of my appliances.  Ready Kilowatt
and Mr. Light Bulb are my friends, once again! 

mike


291.5Wiring a three-way switchDSTAR::SMICKVan SmickFri Oct 24 1986 11:1624
    I have a basic electrical question.
                              
    What is the proper way to wire a light when I want two switches able to
    control it? I know this is frequently done -- for instance at the
    top and bottom of a stairway. You can turn on the light at the bottom
    and turn it off at the top, etc.              
               
               
                              ------------
    --------                  |  light   |          --------     
    |switch|                  |__________|          |swtich|           
    --------                                        --------        
                                                         
                                                    
    ---------                                       
    | power |                                       
    | panel |                                       
    --------                                        

I have done simple wiring before, but this one eludes me!
    
    Thanks for the help.
    
    VCS
291.6LATOUR::KILGOREWild BillFri Oct 24 1986 11:3528
                               14/3
       ,----------------------------------------------.
       |                      ------------            |
    --------                  |  light   |          --------     
    |switch| 3-way            |__________|          |swtich| 3-way          
    --------                        |               --------        
       |                            `-----------------'                    
       | - 14/2                              14/2              
    ---------                                       
    | power |                                       
    | panel |                                       
    --------                                        

    The logic looks like this:

    |     14/2    |          14/3           |             14/2

    white---------*-------------------------*--------------------------*----.
                                                                            |
                                                                          load
                  ,-*--------black-------*-.                                |
    black------*-'                          `-*--------black-----------*----'
                    *---------red--------*

    The light is on. If either of the two switches is moved to the red wire,
    the circuit is broken. To relight the light, either that switch must be
    moved back to the black, or the other switch moved to the red.
291.7Here It IsSTAR::SWISTJim Swist ZKO1-1/D42 381-1264Fri Oct 24 1986 11:3612
    
                                o-----(Black)--o
    Power  (Black)-----------o                    o-----(black)---LIGHT
                                o------(Red)---o
           (White)------------------------------------------------FIXT
    
    (Tough to draw switches).  You need single pole double throw switches.
    
    The left end of the left-hand switch, and the right end of the
    right-hand switch as shown above go to the terminal labeled "COMMON"
    on each switch.    
                       
291.8LATOUR::KILGOREWild BillFri Oct 24 1986 12:0724
    You can also add more switches, as shown below:

    white---*--------------------------*-------------------------*---------
                (B)                (A)   (C)
         (A) ,-*--------black-------*-. ,-*--------black-------*
    black-*-'   (C)                (B) X (D)                      ,-*--black
               *---------red--------*-' `-*---------red--------*-'

           3-way                     4-way                      3-way

    The "3-way" and "4-way" should probably be translated into "3-pole"
    and "4-pole". A nornal light switch has two poles, which are either
    connected or not. A 3-way (3-pole) switch has three connections, and the
    input connection (A) is always connected to one of the output connections
    (B or C). The 4-way (4-pole) has four connections; in one position, the
    connections are (A-D) and (B-C), and in the other position, the connections
    are (A-C) and (B-D).

    More 4-way switches can be added to the above circuit, as long as they are
    between the 3-ways. I've used the three-switch setup, with the first switch
    at the bottom of the stairs, the second at the top, and the third at the
    other end of the upstairs hallway - I have yet to see a situation that calls
    for more than three.
    
291.9THANKS!DSTAR::SMICKVan SmickFri Oct 24 1986 12:193
    Thanks for the information. I'm all set now!
    
    VCS
291.10Helpful BookOOLA::OUELLETTERoland, you've lost your towel!Fri Oct 24 1986 16:207
Mass Hardware in Acton carries a wonderful little book with all
the wiring help you could ever want.  It's called something like
"Electrical wiring for Home and Farm Simplified".  The book
claims to conform to the latest national wiring standards and is
in it's 37th edition.  For $2.95 you can't go wrong...

R.
291.114-Pole... 'I'll order it for you if...'NETCOM::HARRISMark Jay Harris, Term Srvr Mktg MgrFri Oct 24 1986 20:126
    The real question is FINDING 4-POLE switches!!! Try it. I have yet
    to
    find a retailer that carries it IN STOCK!
    
    Mark
    
291.12REGENT::GETTYSBob Gettys N1BRMSun Oct 26 1986 00:564
                That's the sort of thing that you go to your local
        electrical supply house for.
                
                /s/     Bob
291.13Go to an elec. supplierDRUID::CHACEMon Oct 27 1986 15:424
     Spag's has (had) four pole switches, as so does Maynard Supply
    on Rt.62.
    					Kenny
    
291.14OOLA::OUELLETTERoland, you've lost your towel!Mon Oct 27 1986 15:466
re: .5

The book's title is "Wiring Simplified".
It's in its 37th edition.

R.
291.154-pole switches at Spag's still.CLOUD::SHIRRONStephen F. Shirron, 223-3198Mon Oct 27 1986 16:582
    I bought a 4-pole switch at Spag's last week ($6.50 or so).  I had
    to ask at the Electrical Department (they kept them in the back).
291.16There's lots of variationsBEING::WEISSTrade freedom for security-lose bothTue Oct 28 1986 10:5829
By the way, for ease of wiring, you always need a 14-3 wire between the two 
switches, but you can run the power into either switch box or the light box, 
and if you run the power into a switch box you can run the 14-2 wire to the 
light from either switch box.  For example, if you run the power to the light:

   Switch							 Switch
 +-------+		     		  		       +--------+
 |	 |		     	White	 		       |        |
 |     o-+-----------------------------------------------------+-o      |
 |  o    |                       Red                           |    o   |
 |  |  o-+-----------------------------------------------------+-o  |   |
 |  |    |			Black			       |    |   |
 |  |  ,-+-----------------------------------------------------+----'   |
 |  |  | |						       |        |
 +--+--+-+		      +---------+		       +--------+
    |  | 	Black	      |         | Black
    |  `----------------------+---------+-------- Power in
    `-------------------------+---,  ,--+-------- 
		White	      |   |  |  | White
			      +---+--+--+
				  |  |
				 Light

With a few minutes and a piece of paper it's easy to figure out the other 
variations.  Also, note that if you are using 14-3 wire, the circuit should 
only be a 15 amp circuit (which most lighting circuits are).  If it's on a 20 
amp circuit, you should use 12 guage wire.

Paul
291.17Variation: light between switchesNOVA::PALPaul LemaireTue Oct 28 1986 13:0815
Here's the variation for the author's problem (light between the switches).
'W/tape'  means White wire with a band of black electrician's tape at both
ends (to signal that this is a 'hot' wire)



                 B
    B        o----------------------------------------------o
----------o      R                                             o-----|
             o----------------------------------------------o        |
    W            W                              W/tape               |
-------------o-------------------|   |-------------------------------|
                                 |   |
                               W |   | B
                                 light
291.18Dim Wit?WFOVX3::CRABTREEThu Oct 30 1986 10:216
    
    Now the next question is: "Where do you add a dimmer to any of the
    above circuits and do they have 3-way dimmers?"
    
    John
    
291.19HELP! ...The story continues.DSTAR::SMICKVan SmickThu Oct 30 1986 10:3920
As the author of .0:
    
    Thanks for all the help on the wiring. I put in the 14-3 and the
    swtiches -- and it works!
    
    PROBLEM:                                          
                                                      
    Even though I put the fluorescent lights on a separate circuit, they
    dim when other appliances in the house come on. Why?
                                                      
    This is a 2 year old house. Originally, the basement had standard
    incandescent lights on a circuit with the freezer and other appliances.
    These lights (as well as others which may or may not have been on the
    same circuit) dimmed when some of the appliances started. So, I ran a
    new circuit -- complete with a new 15amp circuit breaker to make sure
    the new fluorescent lights would not dim. But they do. 
                                                         
                           Any ideas on what is wrong?   
                                                         
    
291.20VINO::KILGOREWild BillThu Oct 30 1986 11:046
    re .13
    
    Yes, 3-way dimmers are available, in most department stores (and
    surely Spag's). You put a single dimmer at either end of the
    run of switches. Unfortunately, you can only control the brightness
    from that end.
291.21FURILO::JOHNSONPeter JohnsonThu Oct 30 1986 11:4119
Just a piece of info for those of you who have to control/dim lights from
several locations for convenience.  I use BSR x10 modules in my house and
with control consoles located in strategic locations I can control circuits
anywhere in the house.  Its especially nice at night in a multi-story
house to hit the all-off button and all my lights go off - or in an emergency
you can hit all on and all the lights come on.  The original reason I got them
was so my wife could turn the outside floods on from the upstairs master
bedroom.  Now were addicted - we can control the whole house from anywhere.
Additionally I have a timer module so I can have any ligths come on at
any time for security or other reasons - like coming home to a house with
some lights on when you drive home in the dark.

As for dimming.  Putting devices on a separate service is not necessarily
going to eliminate such a problem.  It depends on what your house wiring
and service back at the box looks like.  When a large appliance goes
on (one with motors) a large surge current can and does cause a momentary
voltage drop coming into the house.  This voltage drop can and does get
reflected on house branch circuits especially if the devices on these
circuits are very voltage sensitive.
291.22MORE INFO?DSTAR::SMICKVan SmickThu Oct 30 1986 11:5220
    RE: -.1
    
>    It depends on what your house wiring and service back at the box
>    looks like.  
    
Can you elaborate on this? This is a new house and I assumed it had
adequate service.    
    
>    This voltage drop can and does get reflected on house branch circuits 
>    especially if the devices on these circuits are very voltage sensitive.


1. Are fluorescent light fixtures "very voltage sensitive"?
2. Are lights on a dimmer switch which have been turned down to a low output
   level "very voltage sensitive"?

    
    Do you know of any "cure" for the situation?
    
                       Thanks, VCS
291.23Source for BSR-106910::GINGERThu Oct 30 1986 14:2313
    re .16- the BSR system 10
    
    I agree they are a real great gadget. I didnt buy one because they
    were a bit expensive. Last year DAK- a catalog company that sells
    electronic stuff was selling the controller for $9.90, plus a couple
    bucks shipping. They had the simple controller and the fancy
    programmable timer controller and several of the optional device
    controllers all at similar savings. I just got a catalog from them
    a couple weeks ago and noted they still had them listed. Unfortunately
    I threw the catalog out so I cant give you an exact address or current
    price.
    
    
291.24Juice lost in sauce!NETCOM::HARRISMark Jay Harris, Term Srvr Mktg MgrThu Oct 30 1986 14:3120
    If you are having a dimming effect on one circuit when an appliance
    on a TOTALLY different circuit is switched on... then you have
    feeder problems.
    
    	1. Check overall box loading. If you approach the box limit
    		for appliances ACTUALLY in use, then you ned more 
    		AMPS from the street. (Not usually the case as boxes
    		are typically calculated properly by a good electrician.)
    		If you DO NEED more amps from the street... look out!
    		the power company gets real picky about what they can
    		and can not do, and what it will cost YOU to upgrade!
    

    	2. Have a qualified electrician check the MAIN feeder connections.
    		If you have a dimming effect, power is being lost
    		somewhere. If the connections are faulty, the actual
    		joint will take some power (and heat up in the process!)
    
    mark
    
291.25I wish the programming was easierZEPPO::SULLIVANSpontaneity has a time and placeThu Oct 30 1986 16:509
    
    Let me add to the recommendations for the BSR units. I use them
    to control several lights/appliances in my house. They are getting
    cheaper too. BTW, Radio Shack and Sears sell them under their brand
    names. Usually one of them is having a sale (plus DAK). Sears seems
    to be the only one who makes a three way wall switch unit.
    
    							Mark
    
291.26Voltage Sensitive Lights....SAVAGE::LOCKRIDGEThu Oct 30 1986 17:3517
    RE: .17
    >    1. Are fluorescent light fixtures "very voltage sensitive"?
           
    I have several (like six or seven) fluorescent lights in my shop,
    a few of which were VERY cheap ones ($9.00 each or something like that).
    Those lights are VERY VOLTAGE SENSITIVE. The better lights (in the
    range of $20 each) do not show the problem nearly as much.  My drill
    press and band saw are on the light circuit as they have lights
    on them I always forget to turn off.  Everytime I start the drill
    press, the cheap light just about go out - well, a slight exaggeration,
    but they do dim quite a lot.  The good ones hardly blink.  It probably
    depends on the quality of the ballast used.  I also have on in my
    organ that is "All solid state", which I guess means that it doesn't
    have a ballast in it and it hums like hell. A little 60hz noise
    I can deal with but this too much!
    
    -Bob 
291.27FURILO::JOHNSONPeter JohnsonThu Oct 30 1986 19:2517
    
>    It depends on what your house wiring and service back at the box
>    looks like.  
    
> Can you elaborate on this? This is a new house and I assumed it had
> adequate service.    
    
I suppose I should ask exactly what is going on which causes your lights
to dim.  Large motor devices (like well pumps) draw large surge currents
momentarily so a voltage drop can be seen especially if you are at the
end of the line from where the power source is for your house (power
source being the reduction tranformer).  To give an example an RA disk
drive can suck 36 amps at 120 volts.  Usually the dimming would/should
be very momentary.  What's the service into your house, how far from
distribution tranformer?

-peter
291.28THE SITUATIONDSTAR::SMICKVan SmickFri Oct 31 1986 10:5931
    RE: -1
    
    The service is 100amp, and I do not know how far I am from a
    distribution transformer. I am not in a development, nor at the
    end of a street, so I would guess that there is a transformer within
    a reasonable distance.
    
    As for what is going on, the lights have done a momentary dimming when:
                                                  
   1 This morning I know that the furnace was on (FHA-oil) as well as
     the water heater (Elect).                    
                                                  
   2 Last night I know that the furnace and hot water heater were off,
     and the refrigerator kicked in.
             
   3 Night before last (furnance & water heater off) when the large
     upright freezer kicked in the lights dimmed momentarily and then 
     flickered for several minutes.
    
    
    Based on all the information I have received thus far, I would guess
    that the problem is caused by: 

    a. The cheapness of my lights (Channel $10)
    b. The 100amp service my house was wired with
    
   Any other thoughts?
    
    Thanks
    VCS                            
     
291.29RENKO::JOHNSONPeter JohnsonFri Oct 31 1986 11:3424
>    a. The cheapness of my lights (Channel $10)
    
>   Any other thoughts?

Forget the flourescents for the moment.  What do the incandescents show.
If you can hang an incandescent off the same circuit this will give a
much more reliable indication (visually) of what's happening.  The light
from the incandescent will reflect better the volatage fluctuation.  If it
dims momentarily (we're talking less than 1/2 second here - and the dimming
is just) then I should think this would be ok.  If its much longer or much
dimmer then the service box, feed and branch circuits bear a little closer
inspection.  Closer inspection means looking at the mechanical connections
making sure everything is tight can clean.  How old are the circuit breakers?
Maybe one is old and is not giving good connection.  Turn them on and off
several times to cause contact wiping.  Next step would be to look at
actual current draw and voltages.  This would require an amp probe and
voltmeter.  

-peter

    
     

291.30Check the drops across the connections/breakers.NETCOM::HARRISMark Jay Harris, Term Srvr Mktg MgrFri Oct 31 1986 12:1129
    I too say forget the 'cheapness' of the lights. That should NOT
    be an issue.
    
    One trick I learned is as follows: (This MUST be done with caution)
    
    Using a standard AC voltmeter, press one probe into the main feeder
    line. (there should be 3 wires coming into your house which produce
    basically two separate 'legs' for your breaker box.)
    Determine which appliances turning on cause the problem and find
    the breaker that is supplying it.
    Press firmly one voltmeter probe into the FEEDER lead at the TOP
    of the first connection to the box. (Wire is probably 1/2" in diameter
    so look for that on the TOP of the box. Press into WIRE not after
    connection point!)
    Press the other probe into the BREAKER screw connection feeding
    the leg in question.
    If the appliance kicks on, you should see VERY little voltage
    present if everything is ok. (actually ideally ZERO, but in reality
    a breaker will take a few volts in the element within it)
    
    IF THE VOLTAGE IS ANYTHING MORE THAN A FEW VOLTS... check connections,
    check breakers, check wires that have been nicked, etc.
    
    
    Mark
    
    (BE CAUTIOUS IF YOU DO THIS!!! LOTSA AMPS IN THAT BOX!)
    
    
291.31Two More CentsFSTVAX::HARDENFri Oct 31 1986 16:2128
    Your problem sounds very familiar to me. I had the flickering lights
    problem for quite some time before isolating it. I suspected the
    power company was causing it due to the time of day I noticed it,
    early AM. I thought maybe they were throwing some big switches or
    something as the demand increased.
    
    I checked with some neighbors as to whether they were experiencing
    any of this, of course they weren't, so then I got real curious
    and worried about my electric service.
    
    I isolated the problem by waiting until the flickering came up again
    and went down to the service panel, took off the cover and just
    looked and listened.
    
    What I found was the connection from the main to the circuits was
    loose on one leg and the flickering lights was caused by the arcing
    across the on again off again gap. 
    
    The solution was simple, VERY CAREFULLY, WITH ONE HAND IN YOUR POCKET,
    WEARING RUBBER SOLED SHOES, reach in with a screw drive and tighten
    the screw.
    
    Loose electrical connections can/will cause fires. God knows how
    long this problem existed in my house, it's 40 years old.
    
    Careful and happy hunting,
    
    -boB
291.32Basic wiring questionsAMULET::FARRINGTONstatistically anomalousMon Nov 17 1986 12:2327
    A new (Cape-style) house with unfinished 2nd floor & basement...
    
    I am about to embark on wiring the upstairs.  My thought was to
    use 12/2 wiring for plugs/lights.  However, when I examined the
    wiring left by the builder for the connections to the power box
    (in basement) he used 14/2.
    
    	Question - which alternative is recommended ?
    
    		1. continue 14/2 usage.
    		2. install at junction/connection 12/2.
    		3. reroute 12/2 to the box in basement.
    
    Also, I had hoped to run a separate circuit to the bathroom but
    only two circuits are terminated to the 2nd floor.  Should I -
    
    		1. connect ground-fault plug to the 1st floor plug,
    		   or install a second circuit.
    		2. split the bathroom between the two circuits.
    		3. is it worth the effort to drop a third line to the
    		   power box.
    
    Any input would be appreciated; I'm not very confident in this area...
    
    Dwight
 
    
291.33VINO::KILGOREWild BillMon Nov 17 1986 12:4322
    Two circuits are enough for the upstairs of a normal-sized cape,
    and 14/2 is sufficient, unless you're planning to put a shop or
    a 5-kw. ham transmitter up there.
    
    Put the bathroom at the end of one circuit. Place a GFCI/outlet
    unit in the first box, then wire the rest of the bathroom (including
    light and switch) from the LOAD side of the unit. That way, the
    entire bathroom is protected, and only the bathroom.
    
    Use the two circuits so that if one trips, you can still find your
    way to the stairs with light from the other (eg, you might want
    to supply the hallway light from one circuit, and put an outlet
    in the hallway from the other circuit, into which you can plug a
    night/emergency light).
    
    To keep voltage drops to a minimum, use the screw connections on
    the sides of outlets, and not the slip-in connections on the back.
    
    For more home wiring hints, see "Home Wiring Simplified" (or something
    like that, available in electrical dept. at Spag's), or hardcover
    books from Readers Digest and Home and Garden, available at libraries
    and book stores.
291.34It depends on the amperage of the circuitBEING::WEISSTrade freedom for security-lose bothMon Nov 17 1986 12:549
In general, 14 gauge wire is used for 15 amp circuits and 12 gauge wire is used 
for 20 amp circuits.  If by any chance the 14/2 wire is attached to a 20 amp 
breaker, you should probably change the breaker to 15 amp, since I believe that 
it's a fire hazard to send 20 amps through 15 gauge wire.

Which you decide to use depends on the size of the circuit, but whichever way 
you go, match the wire to the breaker.

Paul
291.35ULTRA::PRIBORSKYTony PriborskyMon Nov 17 1986 13:3723
    First, .-1 is right:   the 14-gauge wire is for 15-amp max.   If
    you continue from the drop your builder left you with 12 gauge,
    think of the 14 gauge as a fuse (that is, don't do it).   The maximum
    capacity of the circuit is the smallest capacity item on it - that
    is normally the circuit breaker.   If you run a 20-amp breaker,
    to 14-gauge wire, and then continue with 12 gauge wire, you've got
    a 15 amp circuit, and a good chance of a fire.   DON'T DO IT.  
    It may also be against code (the code generally "makes sense" and
    this doesn't make sense.)
    
    The recommendation about the GFCI is also correct.   You can get
    the GFCI outlets at almost any hardware store, and I'm sure Spags
    has them too.   If you have a dedicated breaker in your panel, and
    you can "find" that circuit, then there is ample capacity to handle
    one more bathroom (those circuits handle the kitchen (most likely
    some but not all, probably the ones around the kitchen counter) and
    the other bath.   If you can't locate the circuit from upstairs
    (I couldn't, it was too far away), the outlet-style ones will be
    enough.   Also, my inspector exempted the bathroom lights from the
    GFCI protection.   Also note that connecting the convenience outlet
    on a medicine cabinet is against the code.   They are generally
    two-wire outlets and thus can't be connected to the GFCI to give
    the right protection.
291.36ULTRA::PRIBORSKYTony PriborskyMon Nov 17 1986 13:3910
    Another recommendation:   Do get a permit and have it inspected.
    I had to have my inspection before I put up ANY insulation - all
    wires must be visible.   And, use insulated staples.   The books
    mentioned earlier describe the maximum number of wires you can have
    in any single outlet box or junction box - adhere to them.   Make
    sure you don't cross your hot/ground (keep the black wire connected
    to the black wire throughout) as the final inspection (hot wire
    test) will insure that the polarity is correct on all outlets. 
    They will also test the GFCI, and you must tell the inspector what
    outlets are on the load side of any outlet-type GFCI  protector.
291.37Avoid GFCI circuit breakersALEX::CONNAlex Conn, ZKOMon Nov 17 1986 13:447
    Another point: Do *not* use a GFCI circuit breaker at the box. 
    My electrician says they are expensive, often fail to work right
    out of the box, and are not worth the trouble.  Use the outlet type--
    they only cost $10-15 and can be used to protect a number of outlets
    in a chain.
    
    Alex
291.38price questionEXODUS::SEGERthis space intentionally left blankMon Nov 17 1986 13:505
Are you sure on that $10-$15 price tag?  I bought one at Spags 5 years 
ago for $20 and felt like I got a bargain because everywhere else wanted 
over $30!  Have prices on something finally come down?

-mark
291.39VINO::KILGOREWild BillMon Nov 17 1986 14:2721
    
    re .6
    
    Yes, GFCI outlet devices have come down quite a bit in price. The
    one I bought at Spag's eight years ago cost me $27, and now I can
    find them for $10 on sale in department stores (even Sears stocks
    them at $16). They are a much better buy than the panel GFCI breakers,
    and seem to be much less prone to lightning suicide.
    
    re .3
    
    Assuming that the electrician knew his job, there is a 15-amp breaker
    at the other end of each 14/2 wire that he ran to the second floor.
    Extending the circuit with 12/2 does not violate any code in that
    case, as the circuit is still protected in accordance with its
    weakest link. For long-haul circuits, it sometimes makes sense to
    use a heavier wire than minimum to decrease line voltage drop. However,
    I would not classify a normal circuit in a two story house as long
    haul, and in any event running 12/2 for the second half would not
    gain enough in reduced line loss to justify the cost in materials
    and decreased wire counts in the boxes.
291.40??? on .1 and quick connectsSWTPEA::COUTUREMon Nov 17 1986 15:0411
    	I have a question about something that was mentioned in .1.
    
    	Is it better to attach the wire to the sides of the outlet,
    instead of the quick connects? If so, Why and What are the benefits?
    
    	I've always used the quick connects and not have have any problems
    but maybe I should start using the sides. I guess quick connect
    = Easier + Me taking the easy route..
    
    				Thanks
    
291.41Use the screw terminalsBEING::WEISSTrade freedom for security-lose bothMon Nov 17 1986 16:1923
The problem with the quick connects is that the point of contact to the wire is 
quite small.  There are (I think) two metal plates angled together like a V, 
and the wire slips between them, with the V preventing the wire from being 
pulled back out.  The only point of contact is where these plates hit the wire, 
and that's usually with only an edge of the plate:

			\ \   | |   / /
			 \ \  | |  / /
			  \ \ | | / /
			   \ \| |/ /
			    \/| |\/
			      |_|

This is at least an order of magnitude smaller than the contact area of a screw 
terminal.  I know of at least one case where the connection in a quick connect 
has failed altogether.  If you think of a large circuit, the current must go 
through a series of these to get to the last outlet, and this can cause a 
significant voltage drop.  It might not be much of a loss to use the quick 
connects on the last outlet, but terminating outlets are easy to wire anyway.

It takes a little longer, but I always use the screw terminals.

Paul
291.42VINO::KILGOREWild BillMon Nov 17 1986 16:463
    
    .9 was on the money. I have traced a multitude of wiring problems
    to use of the slip-in connects (not in MY house, of course ;-).
291.43OOLA::OUELLETTERoland, you've lost your towel!Mon Nov 17 1986 19:399
re: quick connection stories

I had 2 intermittent open circuits because of them.  I think that
quick connections exist so that contractors don't have to pay
electricians to do the job right.

__Never__ use quick connections with Aluminum wire!!!

R.
291.44While you are still planning ...PAXVAX::NAYLORMark E. NaylorTue Nov 18 1986 01:068
    While you are in the planning stages for the wiring, you may
    want to plan for a future room air conditioner.  If there is a 
    window where you think you may install an air conditioner, you
    may want to run a separate circuit to an outlet below that window
    so that the AC will have its own circuit.
    
    Mark
    
291.45AL wire and screws...SAVAGE::LOCKRIDGETue Nov 18 1986 18:0116
    RE: .11
    
>   __Never__ use quick connections with Aluminum wire!!!

    This may be true with fixture for CU wire (which should NEVER be used
    with AL wire anyway), but AL fixtures have just that type of
    connections - to keep constant pressure on the wire. The problem with
    AL wire is that as it oxidizes, it gets smaller in diameter.  With a
    screw connection, this can lead to a loose and hence dangerous
    connection.  The 'quick type connection' keeps constant pressure on the
    wire as it gradually gets (minutely) smaller. 
    
    Just thought you'd like to know.
    
    -Bob
                                                 
291.46More free adviceNOVA::PALPaul LemaireTue Nov 18 1986 20:4533
    The same electrician who told me never to use quick-connects also
    told me to avoid wiring through outlets.  That is instead of using
    the receptacle to splice the circuit like so:


          -----------------------      ---------------------------
            S              _____ \    / _____                        
            o             / __  \_@__@_/ __  \         to other      
            u             |    o            o|          outlets      
            r             \ --  /-@--@-\ --  /                       
            c              ----- /    \ -----
            e                   /      \
          ---------------------/        \------------------------

    Do it this way:

                                splice
          ----------------------\---------------------------------
            S              _____ \      _____                        
            o             / __  \_@__@_/ __  \          to other
            u             |    o            o|           outlets
            r             \ --  /-@--@-\ --  /
            c              ----- /      -----
            e                   /
          ---------------------/---------------------------------

    The reasons are:
	- If ANY screw works loose in the wire-thru method, you get problems
	  all the way down the line (no, the gremlins don't loosen them,
	  you do when you're wallpapering or whatever).

	- Those little break-off bars between the screws don't have to
	  carry the current for the whole circuit.
291.47More more free adviceCADZOO::HARDINGThu Nov 20 1986 16:2418
    SInce I just had my final inspection done on my wiring heres
    my two cents worth. On several of my outlets I used a type
    that you could insert from the back then by tighting the
    screw on the side the wire was clamped to the outlet. It
    met code but the inspector wasn't pleased. The reason was
    that there was more bending of the wire when the outlet
    was pushed into the box when it was inserted from the back 
    then when put on the screw on the side. 
    
    Adding a little thought to that one could see that with straight
    push in there could be more pressure put on the contact points
    causing the wire to pull out. The other is that if one did
    not push the wire in far enough or the wire started pulling
    out there will be some bare wire showing. This could cause
    a intermitten short.
    
    dave
    
291.48On wriring socketsDSSDEV::REINIGAugust G. ReinigSat Dec 06 1986 18:0424
    re .14
    
    First, I find your drawing a little confusing.  What do you mean
    be source.  Wouldn't it be better to label it like so?
    
    
               black                            black
          -----------------------      ---------------------------
                           _____ \    / _____                        
                          / __  \_@__@_/ __  \                       
                          |    o            o|                       
                          \ --  /-@--@-\ --  /                       
                           ----- /    \ -----
               white            /      \        white
          ---------------------/        \------------------------
    
    Is thre any reason to go through the house and make the changes
    in the wiring your friend suggested?  Finally, should the splice
    go to of the live screws on the outlet or is the power drop over
    one of the tabs inconsequential and it's only when power passes
    through several tabs that the loss becomes noticeable.
    
                                                August G. Reinig

291.49Didn't know there was such a thingSUPER::MATTHEWSDon't panicSat Dec 06 1986 18:305
    Is there any way to tell whether an existing panel breaker has a
    GFCI? 

    					Val 
    					(also doing bathroom wiring)
291.50Without a GFCI label, assume it's notALEX::CONNAlex Conn, ZKOSun Dec 07 1986 01:485
I believe the panel breakers have the same test feature as the outlets 
(you're supposed to push test once a month to see if the ground fault 
portion is working properly).  I believe that the affected outlets 
would be labeled as well.  GFCI breakers are rare in most houses.  Due 
to cost and reliability, most builders opt for the single-outlet types.
291.51GF breakersRINGO::FINGERHUTSun Dec 07 1986 20:512
	I have a GFCI breaker.  It's as you described.
    
291.88Wiring for a motorBCSE::SPT_LEPAGEMon Dec 08 1986 16:0011
    I've recently 'liberated' a motor from a dishwasher we replaced.
     I'd like to use this motor for something, since it does work OK.
    (I'll probably get something like a belt sander or lathe from AMT,
    they sell their tools without motors).  Anyway, this motor was wired
    to a 110V line, and has 4 wires coming from it - black, white, yellow,
    and red.  My question, for you electrical types, is how would I
    wire this up to a standard 3-prong plug so I can use it?  Thanks
    in advance for any help.
    
    -Mark LePage
    
291.89If its not at least 1/4 HP forget it.15476::HARDINGMon Dec 08 1986 18:005
    Before you decide to use it for anything check out the HP of the
    motor. A lot of diskwasher motors are less then 1/4 HP. If it
    is, junk it. Its not worth using. Also some of them are two speed.
    
    dave
291.90Just a thought...JOET::JOETThu Dec 11 1986 10:584
    Most (all?) dishwasher motors are bi-directional.  One direction pumps
    the water through the spray arms, the other pumps it out the drain. 
    
    -joet
291.91Oh yea, the h/p ratingBCSE::SPT_LEPAGEThu Dec 11 1986 11:226
    The point in .1 (horespower rating) is one I had forgotten about.
    I took a look at it last night, but can't find any h/p rating on
    the plate with the other standard info.  The motor will certainly
    need to produce 1/2 h/p or more, so maybe this 'project' isn't worth
    it.  An underpowered tool probably wouldn't be much good.
    
291.98Wire through kitchen vent, and cut studMIZZEN::DEMERSChris DeMers WorksystemsWed Feb 11 1987 10:5714
    The saga continues.  After some good replies to my questions on
    kitchen subfloors, etc. I am well on my way to a new kitchen.  As
    part of the "package", the installer is putting in the exhaust vent
    from the stove to the outside.  When he got to the wall he encountered
    a stud (just about dead center) and a wire.  Jogging around the
    stud would have been difficult because of lack of room, so he cut
    it.  I guess I can live without one stud.  Anyway, the wire is a
    different story.  He notched the end of one of the vent pieces and
    slid it over the wire. Now I have a wire running through the exhaust
    vent.  Is this legal?  Will the wire deteriorate?  Should a conduit
    surround the wire as it passes through?
    
    
    Chris
291.99Doesn't sound too goodLIONEL::BRETSCHNEIDECrazy Hawaiian DTN 289-1604Wed Feb 11 1987 11:238
    I had the same problem, except that I AM doing it myself.  I boxed
    in the area which will contain the vent and rerouted the wire. 
    I can't see how it would or could be legal to have the wire run
    through the vent area.  There should at least be a grommet over
    the wire at each edge of the vent to protect it from chafing on
    the edge of the sheet metal.  (Just my $.02 worth)
    
    bb
291.100VINO::KILGOREWild BillWed Feb 11 1987 11:409
    I wonder it it's breaking some obscure code? When wiring is
    specifically installed in ductwork (using the ductwork as a convenient
    wiring route), the wire must be encased in a metal conduit, or it
    must be certified as low-smoke-creating (in case it starts to burn).
    Certainly the spirit of the code is not being violated in ypur case
    (since the duct only vents to the outside) but you may be inviting a
    future technicality hangup.
    
    The point about possible chafing is also well taken.
291.101Geez, what some jerks will doBEING::WEISSTrade freedom for security-lose bothWed Feb 11 1987 12:4311
In this case, who cares about code?  It is certainly not unheard of to have all 
the grease that accumulates in the vent catch fire.  That's why they have to be 
metal.  Aside from the fact that such a fire would quickly remove any 
insulation from the wires, it can also escape into the wall cavity through the 
hole that the jerk cut in the vent.  It's plain unsafe, code or not.

Tell him, in no uncertain terms, that his solution is completely unacceptable, 
that he has to buy a new vent to replace the one he cut, and he has to either 
move the vent or the wire.

Paul
291.102common sense leads automatically to codeAMULET::YELINEKWed Feb 11 1987 13:231
    Have to agree.....
291.103Your insurance adjuster won't like it...after the fireSEESAW::PILANTL. Mark PilantWed Feb 11 1987 14:1522
    The National Electrical Code has a good deal to say about wires
    passing through hazardous and harsh environments.  (I would certainly
    consider an oven/range vent to be a harsh environment.)  To comply
    with the current code, it is usually necessary to use special cable
    and/or supply conduit for the cable to run in.
    
    From your description of what was done, I would say that the work
    was in violation of the electrical code.  (It might also be useful
    to indicate who did this, so that other of us will know to stay
    clear.)
    
    I would also second the suggestion that you get the installer to
    fix the problem correctly.  You should probably also consider
    with-holding payment until this problem is fixed.  IT IS MOST CERTAINLY
    A DANGEROUS SITUATION.
    
    - Mark
    
    BTW:  I had the pleasure of reading through all 600 some odd pages
    of the 1984 code (1987 version isn't out yet) when I installed a
    new service panel in my house.  (I went from a 100 amp fuse panel
    to a 200 amp breaker panel.)
291.104CAD::VANNOYWed Feb 11 1987 15:248
    
    
    	    I agree.  Common sense should tell you, you are
    	asking for trouble.  I usually do my own work when
    	possible, simply because I sleep better at night know-
    	ing it's done right.  In your case, I wouldn't get
    	much sleep!
    					/Derrick
291.105VIDEO::DCLDavid LarrickWed Feb 11 1987 15:4615
I agree with the preceding replies; the installation as stands doesn't 
sound safe, and almost certainly doesn't meet code.  If you need a specific 
code reference, ask for it here and we code-hounds can have a race!

If your contractor doesn't want to fix it, get the town building inspector 
and/or wiring inspector involved.

Of course, depending on how your contract is worded, you may have to pay 
some extra money to have the wire re-routed properly.  The question is 
whether the contractor should have reasonably expected to find a wire with 
insufficient slack in that wall; it may be a judgement call.

But one reason to pay a pro is so he can take this type of risk, and so 
you're sure everything is done safely and to code.  Don't settle for 
anything less.
291.106Never time to do it right, always time...MIZZEN::DEMERSChris DeMers WorksystemsWed Feb 11 1987 16:0222
    Well, all's well that...
    
    I confronted the installer and told him that the installation was
    sleazeball.  He agreed and we worked on a solution.  No hard feelings
    although I wish he would have filled me in before he made a decision.
    
    We traced the wire and found that it serviced the washer/dryer.
    What's strange is that the wire is dedicated (I did an exhaustive
    test of all plugs/switches in the house) yet runs up to the second
    floor, down through the kitchen wall into the basement and mounts
    on the foundation wall.  After we convinced ourselves that this
    was strange and that the line was indeed dedicated, we clipped the
    wire.  I'll run a new one downstairs on the floor joists.
    
    This is why I like to do things myself.  Unfortunately things like
    family, work, time constraints and lack of experience force me to depend on
    "professionals".  I do go home every night though, look over the
    work and say "Is that the way I would have done it?"
    
    Thanks for your replies.
    
    Chris
291.1071987 NECPAXVAX::NAYLORMark E. NaylorWed Feb 11 1987 23:189
    re: .5
    
    The 1987 NEC is out; I have a copy at home.  As mentioned in a
    previous note, the cost is around $37.  However, I found that it
    is available in loose-leaf for $24.50.
    
    
    Mark
    
291.108Are fluorescents a fire hazard with old wiring?HAZEL::THOMASNo <ESC> from realityMon Mar 02 1987 13:4917
After installing a fluorescent light fixture in my kitchen, I noticed a warning
on the box just as I was throwing it away. It essentially says:

WARNING - DANGER OF FIRE.  Most homes built before 1985 have wiring rated at
60 degrees C. Consult qualified electrician before installing.

Needless to say, my house is older than that. If there is a real problem,
selling these units for installation in existing homes is ludicrous. 
There does not appear to be any temperature marking on the house wiring.
I have since seen other fluorescent fixtures for sale with the same warning
on the box. 

What's going on here? Are these things really a fire hazard or are the warnings
the result of an over zealous consumer protection agency run by Ralph Nader? 


- Rich
291.109CACHE::WHALENWhy is common sense so uncommon?Mon Mar 02 1987 14:3412
291.110VINO::KILGOREWild BillMon Mar 02 1987 15:2524
291.111Flame seal insulation...ZENSNI::HOETue Mar 03 1987 01:418
    wild bill's answer is correct. The wire insulation now requires
    the higher temperature. Fiberglas or teflon insulated falls under
    the newer code. The fix is to be sure that all wiring *within the
    fixture* have the higher temperature rating 90 degree C (which is
    almost at boiling temperature).
    
    /cal, an ex electrician who found wiring was too shocking.
    
291.771Cleaning up the electrical system of an older houseMORMPS::WINSTONJeff Winston (Hudson, MA)Tue Mar 10 1987 21:1229
We are moving into a place which may need some electrical work - I'm 
looking for opinions on what does/doesn't NEED to be fixed, and what 
can be done by a DIY'er as opposed to a licensed electrician.  The 
situation is:

House is 26 years old.  Has old style fuses (round screw-in, large 
'automobile' type), appears prior owner did some DIY work in the 
fusebox.  ALL outlets are 2-prong.  No outlets in bathrooms (excepting 
1 in the light fixture over the mirror, in SOME bathrooms).  
Fusebox has 100A coming in, but only 60A service.  (Note: my wife uses 
1300W hair dryer in the bathroom, and we want to add central A/C)

The EE in me says that the 'RIGHT' things to do are:

	1) replace/update fusebox, put in 100A service and breakers.
	2) put new service to bathrooms, with GFI
	3) put 3 prong outlets everywhere.

Is this all luxury, or a good idea (it does cost $$)?

We also want to:

	4) put ceiling fixture boxes in 5 rooms
	5) hang a fan from the cathedral ceiling in the living room (can I do 
	   this with ZIP cord?)
	6) (maybe) wire external spotlights over garage, out back, etc
	
Is this DIY or 'electrician' stuff?
				thanx	/j
291.772consider 200 ampsCLUSTA::MATTHESWed Mar 11 1987 07:3210
    You might consider putting in 200 amp service if you are going to
    re-wire.  The incremental cost is insignificant compared to wanting
    to do it later when you get the  arc welder for the garage or some
    such.  The key word here is RE-WIRE.  To go from 2 prong to 3 prong
    outlets may mean rewiring the entire house from 2 wire to 3.  Can
    be  done but fishing wires through existing construction can be
    painful and the least time consuming.
    
    If you don't put in 200 amp service consider an oversize panel (i.e.
    200 amp box) and use a 100 amp main breaker.  Change is then minimal.
291.773Have integrity yourself firstCLUSTA::MATTHESWed Mar 11 1987 07:4421
    Just re-read the original note.  In Mass.  90 per cent of what you
    want to do MUST be done by licensed electrician.  If you have the
    knowledge or can get a friend to help, you could have an electrician
    do the main panel and all the hookups.  See if you can strike a
    deal with him (or her) that you fish all the wiring.  Most electricians
    would be willing to do this I expect cause it's a real pain in the
    whatsis.  It's also very time consuming therefore $$$$$$.  You gots
    to talk nice though.  I once heard of a guy who told the electrician
    that he'd hook up the main panel after the electrician had strung
    all the wires figuring he'd save himself a day's labor fee.  What
    the heck all the wires are just dangling there waiting to be dressed
    and just 'plugged' into the panel.  Well talk to a frien whose wired
    houses and he'll tell you that wiring the house is the dog work
    and hooking up the panel is the 'gravy'.  Well I don't know how
    the guy was stupid enough to turn his back on the electrician, msut
    have been picking up his tools or something but when he went to
    hook up the panel there were no longer any labels on any of the
    wires and most if not all were just a tad SHORT.
    
    Moral, when you make a deal with the contractor make an honest one.
    What the heck, you expect him to have integrity. 
291.774WiringVIDEO::FINGERHUTWed Mar 11 1987 11:2111
>        Just re-read the original note.  In Mass.  90 per cent of what you
>    want to do MUST be done by licensed electrician. 

    You can do your own wiring in Mass.  You don't need a licensed
    electrician for any of it.
    
    If your town requires you to have a licensed electrician take out
    the electrical permit, then that's probably because your town's
    wiring inspector is a licensed electrician and is doing this as
    a favor to all the electricians in your area.  What town is this?
    
291.775more infoZEN::WINSTONJeff Winston (Hudson, MA)Wed Mar 11 1987 13:149
Thanks for all the good comments so far......some additional info

I had an electrician look at the job, he tells me that the 3rd wire is 
available at all the outlets, just need new sockets.

The town is Sudbury, MA

Extra question:  What do you suppose an electrician should charge for 
all this, his pre-estimate guess was $1000 - $1500
291.776You TOO???THE780::CHANGTheFaceOfADragonFlyIsNothingButEyes!Wed Mar 11 1987 16:3930
    
    GOSH!  Your original note sounds EXACTLY like what we are facing.
    Our house is 34 years old, 60amp service, no grounded outlets, old
    fabric wrapped wiring, etc...
    
    The estimates that one electrician gave us (another is coming tonight):
    
    Upgrade from 60amp to 100  -- $700
    Upgrade from 60amp to 150  -- $870
    Upgrade from 60amp to 200  -- $1100  <-- We're thinking about putting
                                             in a hottub.  (Oh by the
                                             way we are in California,
                                             Bay Area.)
    
    To ground an existing outlet -- $60 each  <-- We aren't fortunate enough
                                                  to have the third wire there.
    
    To "clean-up" (work done by the previous owner not to code) -- $200
    
    Install bathroom GFI outlets -- $100 each
    
    Install bathroom fan -- $250 (depending on which fan we choose to
                                  use).
    
    My husband also wants to do some of the work himself.  He wants
    to rewire the whole house!  I don't think it's necessary.  I sure
    will be interested in the future replys to this note.
    
    -Gina
    
291.777BEING::WEISSTrade freedom for security-lose bothWed Mar 11 1987 17:2313
291.778AUTHOR::WELLCOMESteveWed Mar 11 1987 17:3611
    Ditto on .6 .  If you have a specific location where a grounded
    outlet makes sense (the garage, maybe) think about getting that
    done.  But the whole house? Not worth the money or trouble.
    A GFI in the bathroom is nice, but the slightest bit of common
    sense (don't stand in the shower while you unplug the heater with
    wet hands) is just as good.  I might upgrade the service entrance 
    to 100 amps with breakers (200 amp if you have or plan on getting
    LOTS of appliances) and let it go at that.  The wiring you have is 
    probably perfectly safe, as is.  If/when you discover a real need
    for additional circuits or grounding, get that done.  
    
291.779check your code firstCOBRA::DUTHIEWed Mar 11 1987 19:5112
    When I checked on changing my house in Littleton, Ma. from 60 to
    100 amps, I was told that the code required that the entire house
    be brought up to current code standards if the main service equipment
    was changed.  Are you prepared to re-do the entire house to current
    code?  (your code may vary... check with the town.)
    
    Also, to change an outlet to a GFI is only about a $10 part (on
    sale) and isn't much different than just replacing an outlet.  Of
    course, the GFI requires a grounded circuit to the box it is going
    into.
    
    Jim D.
291.780BTWMORMPS::WINSTONJeff Winston (Hudson, MA)Wed Mar 11 1987 20:271
BTW: Mass codes require all new outlets in bathrooms to be GFI
291.781VIDEO::DCLDavid LarrickWed Mar 11 1987 20:4066
re .4, Sudbury:  I heard a rumor that Sudbury is one of the most
restrictive towns around, and requires ALL electrical work to be done by a
licensed electrician.  Note that this is a rumor only; please double-check 
before you base any decisions on this information!

The Maynard wiring inspector told me that legally I wasn't supposed to do 
any electrical work, but that he realized I would probably do it whether he 
approved or not, so he might as well issue me a permit and perform 
inspections.  I said "Yes, sir!", and didn't ask him to quote chapter and
verse. 

re .0:

I agree with the other replies:  it doesn't sound like any of your proposed 
work is critically necessary.  Do fuses blow often?  Do the lights dim when 
you plug in the iron?

You're extremely lucky to have grounded wiring in place.  Is it in good 
condition?

Start by making a circuit map of the house.  Find out which circuit serves 
each outlet, fixture, and appliance.  You can determine a lot by tracing
the wires through the basement, but verify your work by disconnecting the
circuits one-by-one.  Then figure the normal and worst-case wattage load
for each circuit. 

If there are unused circuits (fuse sockets) in the fuse panel, or if the
existing circuits have excess capacity, you may not need a new panel. 
There's nothing inherently inferior or unsafe about fuses; they're just
less convenient than circuit breakers. 

> 1300W hair dryer in the bathroom, and we want to add central A/C

A dedicated circuit with GCFI will handle this hair dryer just fine.
Consider gas A/C?

>	1) replace/update fusebox, put in 100A service and breakers.
>	2) put new service to bathrooms, with GFI
>	3) put 3 prong outlets everywhere.
>
>Is this all luxury, or a good idea (it does cost $$)?

Except to power the A/C, about which I know nothing (I'm originally from
the Washington, DC area; New England summers still don't seem hot to me), 
sounds like luxury.  Given that you have grounded wiring, 3-prong outlets
are easy and DIY if you're reasonably careful, but I'd still install
3-prong only where specifically needed.

>	4) put ceiling fixture boxes in 5 rooms

Now you're talking ceiling demolition/repair or serious fishing or both.  
Unless, of course, there's an unfinished attic above.  If you want wall
switch too, see the first sentence.

>	5) hang a fan from the cathedral ceiling in the living room (can I do 
>	   this with ZIP cord?)

I'm not sure what you're talking about, but zip cord doesn't sound kosher.  
A ceiling fan needs strong mechanical support, usually a metal rod through 
which the wiring runs.

>	6) (maybe) wire external spotlights over garage, out back, etc

Worthwhile, probably DIY, perhaps top priority for all this stuff.  Parts
suitable for outdoor use are relatively expensive, and you may again be
looking at some serious fishing and/or demolition/repair.
291.782Nooooooo problem in SudburyDRUID::CHACEThu Mar 12 1987 13:180
291.783only kidding folksKELVIN::RPALMERHalf a bubble off plumbMon Mar 16 1987 16:199
291.784Do you attach grounding tab on adapters?WMEATH::KEVINTue Mar 17 1987 12:535
    re .12   I agree with you that it should have been done right; however,
    when was the last time you attached the wire pigtail or tab from
    a 3 - 2 adapter to the center screw on the outlet?  (if the outlet
    box isn't grounded, even doing that doesn't give you a grounded
    outlet)  
291.785What's the alternative?WELFAR::PGRANSEWICZTue Mar 17 1987 15:4915
    RE: .12
    
    I am doing exactly that in my house.  First, the old 2 prong outlets
    have been painted over (why do people do this???) and second, a
    lot of the outlets are just worn out and don't hold the plug like
    they should.  Oh, and third, do they sell 2 prong outlets anymore?
    I can't recall seeing any.  I've got plenty to do already, so rewiring
    the entire house just doesn't come close to the top of the list.

    I know this is the "right" way but I just can't see it.  Should
    I label the outlets "NOT GROUNDED".  As a previous note suggested,
    I'm not sure I really need grounded outlets except in the kitchen
    and bath (which I intend to re-wire).
    
    Phil
291.786No easy solution...BEING::WEISSTrade freedom for security-lose bothTue Mar 17 1987 17:0817
>    Should I label the outlets "NOT GROUNDED"?

A rhetorical question, I assume. Who wants to have little labels on every 
outlet?  What I suppose you could do, if you were really worried about it, would
be to buy a length of 1/8" metal rod, cut off a bunch of 1/2" pieces, and shove 
them into the ground plug holes.  That would prevent anyone from inserting a 
3-prong plug, and it doesn't detract from the look of it.  Of course, if you 
sell the house, the poor sap who buys it won't know anything about it until he 
tries to use a 3-prong plug.  Due to Murphy's law, this person will not have a 
3-to-2 prong adapter, and this will occur at 10:05 on a Friday evening when he
absolutely needs to use this tool to finish some job on the guest room, and 
relatives are coming first thing in the morning.  Still, I suppose it's better 
than letting him plug it in thinking it's grounded and getting a nasty 
surprise.  But I can just see the reply to note 147: "You'll never believe what 
the jerk who owned my house did! ...."

Paul
291.787No ground?DRUID::CHACETue Mar 17 1987 17:4013
      Are you sure there is no connection to the ground of the fuse box?
    If you have armored cable (BX) then the outer metal jacket should
    make a connection between the fuse box and the outlet box. If you
    have Romex it should have a ground wire that is connected to the
    fuse box and the outlet box. I suppose there may be some very old
    wiring that is 2 conductor with absolutly no ground, but this should
    be very rare. Knob-and-Tubing wiring does not have any ground, but you
    would only find this in VERY old houses (75+ years).
    
     If you have armored cable, a simple pigtail from the new outlet
    to a screw in the outlet box should give you the ground you need.
    
    					Kenny
291.788How many wires do you haveKELVIN::RPALMERHalf a bubble off plumbTue Mar 17 1987 18:018
    
    	There IS stuff called two wire romex.  It isn't armored cable
    and contains no ground wire.  It is vintage 1930's.  My house is 
    full of the stuff (except in my shiny new kitchen :^) ).  Yes I 
    also have knob and tube wiring, except I've replaced the knobs with 
    junction boxes.  The stuff still looks and works fine, so I'm in
    no hurry to replace it.  History of wiring tours will be given upon
    request. 
291.7893D::GINGERWed Mar 18 1987 01:545
    Two wire Romex is not at all rare. It was the only kind in use
    from sometime in the 30's until I think late 50's or maybe even
    the 60's. Even in the 60's two wire was still being used in some
    cases.            
    
291.7902 prong REPLACEMENT outletsHEADS::OSBORNSally's VAXNotes Vanity PlateWed Mar 18 1987 14:318
Re: .14

In Massachusetts, you can buy and use two-prong outlets only as
replacements for existing non-grounded service.  So, yes, remove
your painted and worn outlets and install unpainted equivalents. 

Hmm ... why is the paint stuck so tightly while the lamp won't
stay plugged in due to gravity? 
291.791Electrics observationsBPOV09::SJOHNSONSteveWed Mar 18 1987 15:3347
    
    Upon doing some rewiring in my 65 year old 2-family I also found
    some electrocution kits. :^)   (3rd terminal not grounded)
    
    An easy way to check to see if the 3rd terminal is grounded is to
    put a voltage checker(light) between ground and one of the other terminals.
    
    I woundn't bother to replace all your 2 prongers with 3's either,
    execpt maybe the kitchen (fridge, microwave, or any number of
    modern appliances). I would say that mine are about half and half
    right now.
    
    I'm planning in putting in an outdoor outlet too, I'll get plenty
    of use out of it, mostly when trimming the hedges. Also for electric
    starting snow blowers, or any other work outside needing a power
    tool.                                   
    
    I guess the previous owner strung an extension cord out a window.
    Not for me!  You might want to also.
                
    The wiring schematics for older houses will be quite strange too,
    as was mine.  You'll probably find that each room has one of it's
    outlets tied together on one circuit.  In other words you may have
    to unscrew 2 or 3 fuses to completely shut down power to a room.
    When they upgraded the electrical system, they didn't bother to
    consolidate one room on one circuit, just added wiring to what was
    already there.  Nothing wrong with this, just a little inconvenient
    until you've generated the schematic for your house.
                                                                   
    My unit has a 100 amp service, which serves my needs fine.  The rental
    unit has a 60 amp service, but is only using 30 amps of it, there
    are two empty fuse sockets in the fuse panel.  I plan on tapping
    these to add some outlets to the rental.  They've blown a fuse once,
    when they had their hair curler on at the same time as they pushed
    down on the toaster.  (that's what they said)  I put a slo-blo fuse
    in there and haven't had a problem since.  But this is an indication that
    the electrical system in the rental needs some upgrading.
    I feel that 60 amp is good enough for an apartment but for an entire
    house, maybe not.
    
    Steve
    
    
    Back in the horse and buggy days each room
    was lucky if there was one outlet in it, and some times the whole
    house ran off two 20 amp fuses!  There weren't too may appliances
    on the market then
291.792My mess.WELFAR::PGRANSEWICZWed Mar 18 1987 16:4720
    The "original" wiring in my house (built around 1950) is all 2 wire,
    non-shielded romex (cloth covered).  I'm pretty sure this includes
    all kitchen, bathroom and exterior lighting circuits.  Some new wiring
    was added in the basement for what used to be an apartment.  This is 
    3-wore romex.  There must be at least 6-7 sub-panels clustered around
    the main panel (there's one there somewhere).  I'm pretty sure it's
    60-amp service.
    
    I'm planning on upgrading the service to 100-amp and replacing the
    thousands of fused, subpanels with breakers.  When I redo the bathroom
    and kitchen, I'll run new, GFI 12-2 circuits.
    
    Is there anything else I should consider doing?  My detached garage
    is fed from a single line run from the house.  Should there be any
    special considerations for this circuit?  Has anybody out there
    actually replaced their 2-wire romex with 3-wire throughout
    the house?  Is it difficult?  Is it worth it?  I'm pretty close
    to re-wiring the whole house anyway.

    Phil
291.793USMRM2::CBUSKYThu Mar 19 1987 11:435
    Outlets in the garage (as well as outside) should be GFI protected
    as well. You don't want to zap your self when to step in a puddle
    while you're using the electric buffer on your car! :-)
    
    Charly
291.794No fishing permit required...JOET::JOETSat Mar 21 1987 02:3515
    re: .21
    
    I've redone a few circuits in my house from 2-wire to 2-wire w/ground.
    Since you don't have to "fish", it's really less than half the work
    of adding a new outlet in old construction. 
    
    You have to twist and tape the old and the new together and basically
    just pull the old stuff out. Make sure that it's solid wire and not
    going through a junction box somewhere.  
    
    A little detective work and it'll be OK. 

    -joet
    
    P.S. 14 gauge pulls a hell of a lot easier than 12.
291.795pulling stapled wireCLUSTA::MATTHESSat Mar 21 1987 08:239
    re .23
    
    That's great unless the old wiring is stapled to the studs like
    it is in mine.  You 'throw away' the old and put in new.  I'm told
    that this is code in my area to do this (Nashua, NH circa 1969).
    
    Fortunately I'm only making some minor changes, nothing major.
    It just goes against the grain to know that wire is lurking in the
    walls going to waste.
291.796Taylor's Rent-A-Gorilla...JOET::JOETMon Mar 23 1987 12:528
    re: .24
    
>    That's great unless the old wiring is stapled to the studs like it is
>    in mine.
 
    Pull REAL hard?
    
    -joet
291.118Wiring Circuit PLan QuestionFRSBEE::PAGLIARULOThu Mar 26 1987 15:5529
	I'm bringing power out to a new porch via a circuit that now powers one
upstairs bathroom outlet.  I plan on putting a GFI in the bathroom and then
running 14-2 from there to the porch outlets and lights i.e

	 L--|--|
	 ---|--|--o-----------------o-----------
	|   |  |_______________________  	|
	|   |  |		       | 	|
	|   |  L-----\ 	PORCH	       L 	|
	0   / /	      \			       /0
	|  / /	       \     _________________/	|
	| | /		\   /			|
	 -s-s--------------o--------------------------------------------
	|		Bath. Outlet					|
	|			HOUSE					|

There will be two legs coming off the bathroom outlet box.  One leg will go to
the GFI and from there to the first outlet on the right and then continue
around to power all the other outlets.  The other leg will go to the inside 
porch lights and associated switch leg.  Off the left light I want to bring 
power to some outside lights and put those on a separate switch.

Before I go through and do all this I want to make sure there is nothing wrong 
with my circuit plan.  So, can any of you electrical types that are more 
familiar with wiring then I am see anything wrong?  

Thanks,

George
291.119Wiring changesSEESAW::PILANTL. Mark PilantFri Mar 27 1987 13:5514
    It is generally a good idea to have at least one light on a separate
    circuit.  Having everything on one circuit has the potential for
    creating a dangerous situation.  If you should happen to trip a
    breaker/blow a fuse, you could be left in the dark; which will give
    you lots to bang into.
    
    Also, you might run into a problem with the size of the wire currently
    serving the bathroom.  I would not be at all surprised to find it
    as 14-2.  Supplying another room off that could lead to problem.
    
    A general rule that I use when running new circuits is to use nothing
    smaller than 12-2 for outlets, and usually 14-2 for lights.
    
    - Mark
291.120BEING::WEISSTrade freedom for security-lose bothFri Mar 27 1987 14:040
291.797Too simple to be legal?CADSYS::BURDICKEd Burdick HLO2-2/G13, dtn 225-5051Fri Mar 27 1987 17:158
Would it be legal to just run a new ground wire through whatever route was
convenient?  I don't have this problem, because my house is only 6 years old,
but in reading this stuff, it dawned on me that replacing all the wiring seems
like a lot of work compared to just running a ground wire.  Dropping a 14
guage single wire (bare or insulated) from the attic or into the basement
might be an easy spot upgrade if it ran to a legal ground.  Since the wire
is sitting at ground, it would be pretty hard to make it dangerous.  
Or is this a no no for some reason?
291.798VIDEO::DCLDavid LarrickTue Mar 31 1987 13:3433
> < Note 873.14 by WELFAR::PGRANSEWICZ >
>
>    I know this is the "right" way but I just can't see it.  Should
>    I label the outlets "NOT GROUNDED".  As a previous note suggested,
>    I'm not sure I really need grounded outlets except in the kitchen
>    and bath (which I intend to re-wire).

A nit, but an important one:  according to code and modern practice, you 
not only need grounded outlets in kitchens and baths (and basement, and 
outdoors), but those grounded outlets also need GFCI protection.

>    ...do they sell 2 prong outlets anymore?
>    I can't recall seeing any.  

They're hard to come by new.  They should be readily available from 
renovation and rewiring projects, though.


re .-1

> Would it be legal to just run a new ground wire through whatever route was
> convenient?  

The code has some specific requirements for supporting and insulating
single conductors, but I can't remember if they apply to the ground wire.  
On the one hand, what you're proposing is weird and nonstandard, and 
therefore not a good idea; on the other hand, if it does improve the safety
of your wiring, and you probably wouldn't have gone to the trouble of a 
more drastic safety improvement, then it's better than nothing.

Note that you need to connect all of the ground wires to the service panel, 
rather than finding a convenient water pipe or other local ground.  I'm not 
sure exactly what "ground loops" are, but I know they're bad!
291.799from NEC 1987...REMEDY::KOPECne1gTue Mar 31 1987 15:0438
    ok, let's see what the NEC has to say about all this...
    
    Do you only need grounded outlets in the bath and kitchen?

    	210-7(a)  Receptacles installed on 15- and 20- ampere branch 
    	circuits shall be of the grounding type.
    	  Exception: Nongrounding-type receptacles installed in
    	accordance with 210-7(d), Exception.

    Can you leave them ungrounded?
    
    	210-7(b)  Receptacles and cord connectors having grounding 
    	contacts shall be effectively grounded.
    	  Exception: Ground-fault circuit-interrupter replacement
    	receptacles installed as permitted by section 210-7(d),
    	Exception.
        
    so, what do I replace my two-conductor outlets with?    
    
    	210-7(d)  Grounding-type receptacles shall be used as replacements
    	for existing nongrounding types and shall be connected to a
    	grounding conductor installed in accordance with [210-7] (c)
    	above.
    	  Exception: Where a grounding means does not exist in the 
    	receptacle enclosure either a nongrounding or ground-fault
    	circuit-interrupter type of receptacle shall be used. A
    	grounding conductor shall not be connected from the
    	ground-fault circuit-interrupter type receptacle to any outlet
    	supplied from the ground-fault circuit-interrupter type 
    	receptacle.

    [this "shall not be connected", I believe, deals with wire-
    through GFI connections downstream..]
    
    ...tek
    
    
    
291.137Simple (?) Wiring ProblemBOOKIE::WIEGLERFri Apr 03 1987 13:0922
    I recently moved into a new (actually 7 year old) house.  The wiring
    is interesting because almost every light is controlled from 2
    switches, for convenience I suppose.  The previous owners took their
    dining room celing fixture with them and I want to hook up my new
    one.  I have installed numerous celing lights in the past and have
    never had any problems until now.  The dining room light is controlled
    by 2 switches; one is a dimmer and the other is a regular on/off
    switch.  The ceiling box has three sets of wires feeding into it.
    Each set of wires has a black, white, and a copper ground.  The
    3 copper grounds are all twisted together, but all the other wires
    were just left hanging.  The fixture that I want to install has
    2 wires, 1 black and 1 white.  HERE IS THE PROBLEM: I tried to install
    the fixture by connecting all the white wires together (the 3 from
    the ceiling box and the one from the fixture), and then connecting
    all the black wires together.  I left the ground wires twisted together
    and tucked them up into the box. The result is that the circuit
    breaker switches off the first time I use the wall switch.
    
    WHAT AM I DOING WRONG???   GAWD, I FEEL SO STUPID!!!
    
    The wife really wants this light working this weekend, so any help
    would be greatly appreciated.
291.138Insulate the connections?HEADS::OSBORNSally's VAXNotes Vanity PlateFri Apr 03 1987 13:296
You did cover each connection?  With the wire nut?  With 
the black electrical tape?  

If the wires were just twisted together and jammed into the box, 
they could short against each other and even against the box 
itself.  (We have been there!)
291.139VINO::KILGOREWild BillFri Apr 03 1987 13:4637
    
    The first thing to do is disconnect the wires you connected, get paper
    and pencil, pull out the switches in question, and try to make a
    diagram of the circuit. An AC voltmeter or circuit testing light will
    help in this endeavor. An alternative would be to ask the previous owner.
    
    No red wires, eh? Guess the installer didn't go the normal route,
    using 14/3 cable to provide the extra conductor needed for such
    a circuit.
    
    Two normal variations of the circuit are shown below. (The switches
    can be either dimmers or toggle - circuit is still the same.)
    
             switch           switch            light
               ,*-----red------*.
    black----*'                  `*----black-----*
                *----black-----*                  \
                                                  / (load)
    white-----*-----------------*----------------*

    
             switch           light            switch
               ,*-----red-------*----------------*.
    black----*'                                    `*-.
                *----black------*----------------*    |
                                                      |
    white-----*---------------*   *-------------------'
                               \ /
                              (load)

    I can't come up with a variation, using an extra 14/2 to replace
    the red conductor from the 14/3, that puts three cables in the light
    box. Perhaps the results of your circuit testing will help.
    
    You shouldn't feel stupid - the problem is that you're not placing
    the blame on the correct party (see the ever popular "Why did they
    ever do that?" note in this conference).
291.140It's a remote switchBEING::WEISSTrade freedom for security-lose bothFri Apr 03 1987 14:2066
I bet I know what is going on.  You have three two-conductor wires coming into
the light box.  One is the power coming in from the circuit box.  Another is 
the power going out, continuing on to another light on the same circuit.  And 
the third is going out to the remote switches.  There is a 3-conductor wire 
connecting one switch with the other.  That means that one of the switch boxes 
has the other end of the two conductor wire going out from the light and the 
three conductor wire going to the other switch, and the other switch box has 
just the three conductor wire.  A diagram will probably help:

			+---------------+
		Black	|		|  Black
Power in   -------------+---         ---+----------  Power out
from		White	|		|  White     to other 
Panel	   -------------+---	     ---+----------  lights
			|      | |	|
			+------+-+------+
			      W| |B
			       | |
			   +---+-+---+		+---------+
			   |   | |   |  Black	|	  |
			   |   | +---+----------+-------+ |
			   |   |     |  Red	|	| |
			   |   |  ---+----------+---\   | |
			   |   +-    |  White	|    ---+ |
			   |     \---+----------+---	  |
			   |         |		|	  |
			   +---------+		+---------+

Thus it makes sense that the breaker trips when you hit the switch, because you 
are directly connecting the black and white wires.  What you want to do is 
this:  First, wire all three of the black wires together, but don't include the 
black wire from the light, just the three black wires coming in.  By doing 
that, you connect the power in with the power out, and you provide power to thw 
switch.  Next figure out which of the three wires is the one going to the 
switch.  It might help to find out which of the switch boxes has the wire 
coming in.  Then, connect the white wires of the OTHER two wires with the white 
wire of the light.  Again here, you're connecting power in with power out, and
you're tying in the neutral end of the light with the circuit.  All you should 
have left at this point is the white wire from the switch and the black wire on 
the light.  Hook these together, and you're done.  

BTW, you might be able to tell which is the switch if the white wire has a 
piece of black electrical tape wrapped around it, which indicates that it is 
really carrying current.  If it's not there, you might do that yourself to save 
a future light-changer the same problem you're having.

When you're done, the wiring should look like this:  (* is a connection)

			      Light
			       | |
			      W| |B
			+------+-+------+
		Black	|      |  \	|  Black
Power in   -------------+--------*------+----------  Power out
from		White	|      | |/	|  White     to other 
Panel	   -------------+------*-|------+----------  lights
			|       /|	|
			+------+-+------+
			      W| |B
			       | |
			      Switch


Good Luck!

Paul
291.141I bet thats it!TRACTR::DOWNSFri Apr 03 1987 14:406
    Nice job .3, I second this solution! If fact that is exactly how
    I wired all of my three way ceiling lights. 
    
    Boy isn't this file great! Anyone out there know what next wednesday's
    Mass. megabucks ticket sequence will be?
    
291.142One thing to trySTAR::SWISTJim Swist ZKO1-1/D42 381-1264Fri Apr 03 1987 15:548
    .3 seems likely, but a simple verification is in order.  Since there
    is an outfeed to some other part of the circuit, then if all wires
    are left unconnected, and the circuit breaker is turned on, them
    there will be at least one other fixture or outlet which is not
    working (probably need the light in question, but maybe anywhere!).
    
    This would be simple to test before proceding with .3
    
291.143yes but.......MRMFG1::C_DENOPOULOSFri Apr 03 1987 16:0010
    Not so fast .4, .3 may be right but in an appartment I was in I
    had the same situation as .0.  There was no 14/3 wire anywhere.
    If the downstairs switch was off, the upstaris did nothing.  If
    the downstaris switch was on, then you could turn the light off
    and on again from upstairs.  Needless to say, this was a royal pain.If
    an electrition did your wiring, then you probably have what .3 had
    shown.  If the previous owner did, then who knows!!
    
    Chris D.
    
291.121VIDEO::DCLDavid LarrickFri Apr 03 1987 17:5225
Existing 14/2 wire shouldn't be a problem as long as you don't plan to run 
a radial arm saw on the porch - or, for that matter, to vaccuum the porch
while running a hair dryer in the bathroom. 

If you do plug in anything on the porch that's likely to trip the GFI, 
walking around into the bathroom to reset it could be a pain, especially in 
the dark.  You might consider a second GFI on the porch itself.  If the 
porch is weathertight, you don't NEED GFI protection on the porch at all.

You mention adding two legs to the existing bathroom outlet box.  Adding
additional wires to an existing box can cause you to exceed the Code-
specified maximum wire count for the box size.  These calculations are
certainly detailed, but straightforward once you get the hang of them. 
Code considerations aside, trying to work with too many wires crammed into
too small a box is unpleasant work, and increases the likelihood of a
short. 

The GFIs I've installed are quite large, and take up most of the space in 
the box.  You may need to replace the existing bathroom box with a larger 
(i.e. deeper) one just to fit the GFI in.

One last parting shot:  "a circuit that now powers one upstairs bathroom 
outlet" doesn't strike me as a typical configuration, especially for
pre-GFI construction.  I'd double-check to make sure the circuit really 
does serve just that bathroom.
291.122What is and What Shall BeFRSBEE::PAGLIARULOFri Apr 03 1987 19:2021
	When I traced all my house circuits last winter I taped a sheet of 
paper on the box that said what each fuse runs.  When I looked at the 
bathroom fuse again I realized that that fuse doesn't run only the 
bathroom just yet.  Right now it also runs the washer, the gas drier, the 
dishwasher, and one kitchen counter outlet!  When I wrote the base note I guess
I was thinking of what would be on that circuit when I got all the stuff off
that doesn't belong there.  This is the same circuit that had a 30 amp fuse in 
the box when we moved in.

	After re-evaluating the situation I've decided to run a separate circuit
for the porch.  The GFI will be the first oulet on the this circuit.  It's this
circuit that will power the bathroom.  As I originaly planned, the washer and 
drier will get their own circuit as well as the dishwasher.  The kitchen 
outlet that was on the dishwasher/drier/bathroom/clothes washer circuit will 
be wired to one of the other kitchen circuits.

Thanks for all the help.

Oh yeah, one more thing.  For a circuit with a clothes washer and gas drier 
is it best to use 14-2 or 12-2

291.123SEESAW::PILANTL. Mark PilantFri Apr 03 1987 20:053
    One person's opinion:  I'd use the 12-2.
    
    - Mark
291.124VIDEO::DCLDavid LarrickFri Apr 03 1987 20:388
I used 12/3, two opposite-phase 20A circuits in a single cable, to power 
the washer and gas dryer separately.  Arguably overkill, and 20A isn't 
enough if somebody wants an electric dryer there; but I still like it that 
way.

Separate, dedicated circuit for dishwasher too.  I think Code requires it 
that way, since the dishwasher is built in and hard-wired.  The clothing 
applicances are plug-connected, so the rules aren't as strict.
291.112Cross your fingers and hope.CAD::GREENBERGSteve HLO2-2/H13 225-6105Fri Apr 03 1987 20:519
I ran into similar problems with an electric radiant cove heater.  I didn't
find the electrical supply stores around here too helpful in telling me what
the thermal rating was for the wire they were selling me.  I put some wire in
boiling water and it didn't seem to affect the insulation at all.

So far, I have been through one heating season with the heaters installed and
didn't have any problem.

/Steve
291.125HmmmTALLIS::SAMARASAdvanced Vax Engineering LTNSat Apr 04 1987 21:188
re: .6
    
    Isn't your neutral connection carrying twice as much as it should?
    If you can pull 40A from your box with your configuration, isn't
    all of the return current flowing through 1 wire????
           
    just wonderin',
    ...bill
291.126VIDEO::DCLDavid LarrickSun Apr 05 1987 19:029
>    Isn't your neutral connection carrying twice as much as it should?

No, that's the beauty of it.  Since the two circuits are opposite in phase, 
they cancel rather than adding.

"Worst case" is when one circuit is drawing 20A and the other zero:  the
neutral carries 20A, i.e. normal.  When both circuits are drawing something, 
the neutral carries their difference, and when they match, the neutral
actually carries zero! 
291.127VIDEO::DCLDavid LarrickSun Apr 05 1987 19:092
P.S. This technique is perfectly legal, and is described in some detail in 
the Code under the name of "3-wire circuits".
291.128Not an optionALIEN::WEISSTrade freedom for security-lose bothMon Apr 06 1987 11:185
As mentioned before, the size wire you use is not an option if it's a 20A 
circuit.  You HAVE to use 12 gauge wire.  You can only use 14 gauge if the 
circuit is 15A.

Paul
291.129a questionTALLIS::SAMARASAdvanced Vax Engineering LTNMon Apr 06 1987 13:165
    What's the likelyhood of getting away with a washer and a fridge
    on the same 20A 12-2 circuit?  I don't have anymore room in my panel,
    and they don't make "double" breakers for Cutler Hammer (yet).
    
    ...bill
291.130CSSE32::NICHOLSHERBMon Apr 06 1987 15:302
    A dish washer and clothes washer cannot hack the same 12-2 20A circuit
    in our house.    
291.131VIDEO::DCLDavid LarrickTue Apr 07 1987 12:4020
>    What's the likelyhood of getting away with a washer and a fridge
>    on the same 20A 12-2 circuit?

I don't think code has any objection to this arrangement as such, although 
I wouldn't recommend it.

You're pretty likely to trip the breaker when both appliances demand high 
power at the same time.  But that's likely to be when you're in the house 
and awake, and you can go reset it.  Annoying, but not disastrous.

If you're in the habit of leaving the washer running when you go to bed, 
plan to wake up to a warm refrigerator once in awhile.

Better would be to put the washer on a circuit with lights and infrequently-
used outlets, and put the fridge with kitchen outlets.  (Code requires two
circuits dedicated to kitchen outlets, but the fridge may be on one of these). 

Be sure to read the rating plates on both appliances before you decide 
anything.  If you report those ratings here, you might get more free 
advice...
291.132A Possibly Dumb QuestionFRSBEE::PAGLIARULOTue Apr 07 1987 13:293
	When you're running wires between studs that will also have 
fiberglass insulation between them do you put the wires behind or in
front of the fiberglass?  Does it matter?  
291.133Don't do itSTAR::SWISTJim Swist ZKO1-1/D42 381-1264Tue Apr 07 1987 15:1220
    Ahh, a catch-22 of wiring.  Wiring run horizontally has to pass
    through holes which must be more-or-less centered in the stud. 
    Otherwise you run the risk of nail penetration, plus cuts close
    to or on the edge will weaken the studs.

    However this forces you to compress the insulation either behind
    or in front of the wire.  The electrical code doesn't care, but
    neither is a great idea from an insulating effectiveness point of
    view.
    
    You will notice most professional electricians in new houses solve
    this problem by not doing it.  Wiring on walls to be insulated will
    run up from the floor below or down from the attic directly along
    the studs, even if this means using a lot more wire.  In fact you
    will usually see this even on interior walls, since it's a matter
    of habit.
    
    If this is a basement wall you are finishing, it is legal (and
    saves a lot of drilling) to run the wiring between the back of the
    studs and the concrete wall, if you have space there.
291.134VINO::KILGOREWild BillTue Apr 07 1987 15:256
    re .14:
    
    You could slit the fiberglas batt (but no the facing) where it will
    intersect the wire, to allow it to wrap around the wire without
    comperssing.

291.144Simple (?) Wiring Problem - Part 2BOOKIE::WIEGLERThu Apr 09 1987 13:4245
    Thanks to all of you who responded to my wiring problems described
    in note 966.  Unfortunately, none of them worked.  Rather than restate
    the problem, I'll just continue where I left off in that note. 
    I spent 2 1/2 hours last night climbing the ladder, wiring the light
    fixture, going down to the basement, turning the circuit back on,
    going upstairs to check the light, finding it still wasn't right,
    and then doing it all over again with a different wiring arrangement.
    I labelled all the wires to keep track of all the different
    combinations.  There are 3 sets of wires coming into the ceiling
    box.  I labelled the black ones A, B, & C and the white ones 1,
    2, & 3.  The kitchen ceiling light also comes from the same circuit,
    so, I believe my dining room box is also a junction box leading
    to the kitchen light.  The explanation given by Paul Weiss in note
    966.3 makes a lot of sense (thanks Paul) and, yes, there is a red
    wire running between the 2 wall switches in the dining room, but
    not to the ceiling box.  However, I tried connecting it up Paul's
    way and it still didn't work. I connected all 3 black wires together.
    Then I connected 1 white wire to the black wire from the light,
    and the other 2 white wires to the white wire from the light.  I
    tried this in all 3 possible combinations, but the dining room light
    never lit.  I also tried another suggestion which
    was to  connect 2 black wires together, 2 white wires together,
    and the remaining black and white wires to the light.  I tried this
    in all 9 possible combinations and I got the following results:
    1. The kitchen light worked, dining room light didn't
    2. The kitchen light was out, but the dining room lit (although the
    dining room switches didn't turn it off, but the kitchen switch
    would dim the dining room light)
    3. Nothing would light 
    
    I'm sure this sounds confusing; I could draw a picture of the wiring
    and all the possible combinations I tried, but probably couldn't
    do it clearly on the screen. If anyone loves the trill of a challenge
    and lives in Manchester, NH, I'm sure I could stock my fridge with
    beer and have a LIGHT-WIRING PARTY this weekend. 
    
    Now, I know that the previous owner had a working light in that
    room, and I guess the next step is that I'll call him up and see
    if he can help, but I suspect he's not too knowledgeable about such
    things.  I am certainly open to any suggestions.  The last thing
    I want to do is to PAY an electrician to come over and sort it out,
    but if I get desperate enough....
    
    
                                         
291.145If at first you don't suceed...YODA::BARANSKI1's &amp; 0's, what could be simpler!?Thu Apr 09 1987 15:139
The solution!



Rip out all the wires, leaving a wire or string or twine or rope between
the switches and lights to allow you to pull new wires through, and wire
it up in a way that you understand it!

Jim.
291.146start at the beginning...WHO::SHOREYThu Apr 09 1987 16:3324
    are you getting power to the box?  i would think that the first
    thing to do would be to hang all three black wires and all three
    white wires out of the box, turn on your circuit breaker, and find
    out which pair, if any, is live.  if you don't have a test light,
    now is the time to spring for the $1.29 and get one.
    
    once you have a live pair, one of the other pairs should go to the
    kitchen circuit.  connect your live pair to one pair (you may turn
    off the circuit breaker when doing this) and try the kitchen light.
    if it doesn't work, connect your live pair to the other pair and
    try the kitchen again.  
    
    once you get the kitchen going, connect the black wire from the
    remaining pair to the two blacks, connect the white wire from the
    remaining pair to the black wire of your new dining room light,
    and connect the white wire from the dining room light to the two
    whites.
    
    if this doesn't work, you need a new lightbulb or switch!
    
    good luck, and let us know how you make out.  i'd love to stop by,
    but i'm busy with my own home_work this weekend.
    
    brian (225-7285)
291.147We'll get it yetBEING::WEISSTrade freedom for security-lose bothThu Apr 09 1987 16:4333
More questions:

You say: "The kitchen ceiling light also comes from the same circuit,
so, I believe my dining room box is also a junction box leading
to the kitchen light."  Does this mean that if you don't connect any wires, the 
kitchen light won't work?

Other than the 3-conductor wire running between the two dining room switches,
there should be just one 2-conductor wire going to just one of those switches.
Are there any other wires in those switch boxes?

Does the kitchen light have 1 or two switches?  You said that the kitchen 
switch would dim the dining room light.  Do you mean that the kitchen switch is 
a dimmer switch and it controlled the dining room light?  Or is it a regular 
switch, and would dim the dining room light when turned on?

How many wires come into the kitchen light and switch boxes?


If we can't figure it out from your description, there's another way to find 
out what's going on.  Go spend $2 on a cheap voltage tester.  Now separate all 
the wires in the box, and go turn on the breaker.  *Carefully* try the tester 
between each black wire and the ground wires until you find the hot wire.  Now 
you'll at least know where the power is coming in from.  Now open up both 
switch boxes, plus the switches and light in the kitchen (don't forget to mark 
which wires go where in these boxes - you don't want to make the situation 
worse :^)), and get all the wires separated and loose in those boxes.  Connect 
the known hot wire in the dining room box with another black wire, then go turn 
the power on again, and check the other boxes to see where that wire went to.
You can keep doing this until you've identified where all the wires are going,
and then you ought to be able to figure out how to wire it.

Paul
291.148Reply .4 continuedBOOKIE::WIEGLERThu Apr 09 1987 19:077
    SOMEHOW THE END OF .4 GOT CUT OFF.  Here's the rest:
    ...and wire it according to the suggestion in .2.
    If it still doesn't work, I may try replacing the switch and dimmer
    and hope that they are the cause of my misery.  
    
    I am open to all suggestions until the weekend.  Then I'll go home
    and try them all.  I'll report back to you on Monday.
291.149BEING::WEISSTrade freedom for security-lose bothThu Apr 09 1987 20:139
You want to try .4 again?  From my terminal, it all got cut off.

Is your kitchen light a flourescent?  If so, then maybe when you turned on the
kitchen light and it dimmed the dining room but did not turn on the kitchen, 
perhaps it did turn on the kitchen, but the flourescent would not work with the 
lower voltage.  That would help in figuring it out, because it would mean you 
had the two lights in series.

Paul
291.150Here are some more factsBOOKIE::WIEGLERThu Apr 09 1987 20:3831
    I guess .4 got screwed up so let me enter it again here:
    
    Re questions from .3 and .6:
    
    The kitchen has 2 light switches (neither is a dimmer).  When I
    said that the kitchen switch dimmed the dining room light, I meant
    just that.  I couldn't turn off the dining room light, but flipping
    the kitchen switch dimmed the dining room light. (Pretty wierd,
    huh?)
    
    The kitchen light is not a florescent; it is a track light.
                                                       
    I believe that if I leave all the wires in the dining room box
    unattached, then the kitchen light will not work (it won't have
    power).  I haven't actually tried it, but I will.
    
    There are only the 3 sets of wires going into the dining room box.
     No other wires feed into it.
    
    The suggestion made in .2 is basically the same as made by Paul
    in 966.3.  I do believe that it is the correct way, but for some
    reason it did not work.  I will get a line tester, identify the
    power wires, identify the wires to the kitchen light, and wire
    it according to the suggestion in .2.  If it still doesn't work,
    I may try replacing the switch and dimmer and hope that they are
    the cause of my misery.
    
    I am open to all suggestions until the weekend.  Then I'll go home
    and try them all.  I'll report back to you on Monday.
    
                                                         
291.151Look at a book on wiringBEANCT::VANCLEAVEThu Apr 09 1987 21:469
With a 3-way switch is important to know where the switch is in relation
    to the power feed and the lights.   Try looking at the TIME-LIFE
    Basic Electricity Book, but be careful, it doesn't show all the
    possibilities for this kind of wiring.  If you diagram your circuit
    and it looks like the one in the book, you're probably ok.  By the
    way, a wiring diagram of your whole house will be invaluable later
    on when you want to add more circuits or check a fuse.
    
    Dave Van Cleave
291.152Dimmers die like thatCADSE::MCCARTHYExcellent, more than a match for poor Enterprise.Thu Apr 09 1987 21:4711
    Dimmers have a habbit of kicking the bucket if the circut they are
    attached to trips a breaker.  If the wiring was incorrect the first
    time you turned the switch on, you may have killed the dimmer.
    
    	One of the previous replies said that one of your switches for
    the dinning room must have a 14-2 AND a 14-3(red) wire.  Wire the
    box as stated in note 966.3 and then use a single pole switch between
    the 14-2 in the switch box.  Have you tried this?
    
    Still pretend I'm an electrician every Saturday,
    Brian Mac
291.153Bad dimmer = interesting possibilityBOOKIE::WIEGLERFri Apr 10 1987 14:0110
    Thank you Brian Mac (.9).  If my dimmer blew when I tripped the
    circuit, that would explain a lot.  How about if I remove the dimmmer
    switch and just connect the wires together (the ones that ran to
    the dimmer switch) as a means of bypassing the switch?  Then I could
    test out the circuit without the dimmer in the way.  Does that make
    sense?  What do I do with the red wire that leads into the dimmer
    box?                                                    
    
    Boy, this is great.  I almost look forward to tackling the wiring
    tonight.  
291.154What to do with redVIDEO::DCLDavid LarrickFri Apr 10 1987 15:0526
> What do I do with the red wire that leads into the dimmer box?
    
Here's how a simple 3-way switched circuit looks:

          white
     -------------------------------------------------+
power                                                 |
     ----+           black                          LIGHT
         |      /----------------\                    |
         +-----/                  \-------------------+
          black  ----------------     black
                     red

So, if you want to replace one of the switches with a hard-wired connection 
for testing purposes, you have two options:

1. Wire black to black, ignore the red.  Don't connect that leg to the
   circuit at all.  The other switch will turn the light on when it 
   connects to the black leg, off when it connects to the red leg.

2. Wire black to both red and black.  Thus both legs are always hot.  The 
   other switch will turn on the light no matter which way it's switched.

Option 1 is most useful for most purposes, including yours.  Option 2 is 
useful for such applications as determining whether the red wire has 
continuity, or determining whether the other switch is working properly.
291.155Use 3 way as single poleCADSE::MCCARTHYExcellent, more than a match for poor Enterprise.Mon Apr 13 1987 11:379
    You can use a 3-way switch as a single pole switch.  There are three
    points on the 3-way, one of them is usually a copper color, this
    is the point.  By taking the wire that is coming from the celling
    box to the switch (the 14-2) and connecting one of them (white or
    black) to the point terminal and the other to either of the remaining
    two terminals you have a single pole switch.
    
    Brian mac

291.156A HAPPY ENDINGBOOKIE::WIEGLERMon Apr 13 1987 14:1333
    Well, here's the final chapter of my story.  I went home on Friday
    and did the following:
    
    I removed the dimmer switch and wired that box to complete
    the circuit without the switch.           
    
    Then I used a circuit tester (bought it Friday afternnon at a hardware
    store for $1.89) to determine which of the wires coming into the
    ceiling box carried power. 
    
    I connected the power wires to another set of wires in the ceiling
    box to determine which wires led to the kitchen ceiling light.
    I then labelled all the wires.
    
    The remaining set of wires going into the ceiling box obviously
    went to the wall switches.  I then wiring the light according to
    the recommendations in notes 992.2, 992.3 and 966.3 and IT WORKED!!
    I then danced a little euphoric jig around the house.  Apparently,
    the dimmer blew when I tripped the circuit breaker in an earlier
    wiring attempt (a possibility suggested in note 992.9) so that even
    when I did have it wired correctly, it wouldn't work.
                                                                    
    I installed a new dimmer switch on Saturday and now everything works
    great.  Thanks to everyone who responded with suggestions.  This
    notes file is the greatest.
    
    I do have one more question.  When I dim the light, it hums.  I
    have had this occur with other dimmed lights in the past.  Is this
    something you learn to live with, or can it be cured?  It's not
    terribly loud, but it is noticeable.
    
    THANKS AGAIN FOR ALL THE HELP!
                                  
291.157Alls well that ends wellBEING::WEISSTrade freedom for security-lose bothMon Apr 13 1987 16:3933
Hooray!!

Glad it worked out.  Just goes to show once again that the SUM of the 
experience of the people in this file is amazing.  I chanced to be the first 
person to suggest the correct wiring, but I never would have suspected that 
wiring it incorrectly before would have busted the dimmer.  Wonderful!  Y'learn
sumpin' new ever day.

As to the dimmer, the reason it humms is that the dimmer does not lower the 
amplitude of the entire alternating current sine wave, it just clips the wave 
at a certain amplitude, so instead of a nice clean sine wave you get something 
that looks like this:


   ___________________                               ___________________
  /                   \                             /                   \
 /                     \                           /                     \
/                       \                         /                       \
                         \                       /
                          \                     /               
                           \___________________/


All those jerky transitions make the filament hum.  I imagine it takes a bit 
off the life of the bulb, also, but I don't know.

I heard somewhere that if you put a 3-way bulb in the socket, it won't hum, but 
I've never tried it.  Supposedly something about the way the filament is held 
in a three way bulb keeps it from humming.  Let us know if you try it and it 
works.

Paul

291.158PEANO::GLASERSteve Glaser DTN 226-7646 LKG1-2/A19Mon Apr 13 1987 17:2516
    If a 3-way doesn't help the humming lamp problem, you might try
    either long life lamps (designed for places that are hard to get
    to so you don't want to do it very often) or tough lampss (designed
    for being mishandled as in trouble lights, etc.).
    
    The humming is coming from the filament vibrating.  The tough lamp
    has many more filament supports.  Both lamps have thicker than normal
    filaments.  These lamps are more expensive and may not put out as
    much light.
    
    If you can't use these lamp (say you need decorator lamps), there
    are dimmers available that don't cause the humming problems.  They
    are much more expensive and usually can't fit in an outlet box but
    they are available.
    
    Steveg
291.159I'll try some other bulbsBOOKIE::WIEGLERMon Apr 13 1987 18:027
    Interesting information about why the humming occurs.  The light
    fixture we have looks sort of like an upside down glass bowl (with
    ridges in the glass) suspended from a brass chain.  Because the
    bowl part is clear we have always used a clear bulb in it.  It gives
    off a beautiful glow (especially when dimmed) but I'll try some
    other bulbs, just for the heck of it.  Thanks again. 
    
291.160Hot Hummer Horrifies HomeownerERLANG::BDBrian D. HandspickerMon Apr 13 1987 18:2410
    Why would the dimmer itself hum?  My electricians just finished
    installing dimmers for the front hall and living room recessed
    lights.  The dimmers are side-by-side.  The hall dimmer controls
    three fixtures without humming.  The living room dimmer controls
    9 fixtures (@ 25 watts per fixture) and hums and heats.
    
    Is this normal?  Is this simply the result of the heavy load 
    or the result of miswiring?
    
    bd
291.161hot dimmersWHO::SHOREYMon Apr 13 1987 19:0421
    9x25 = 225, which seems to be a lot of watts for a dimmer.  i think
    that the average dimmer is meant to handle one 100 - 150 watt bulb.
    
    you can overload a dimmer quickly by shorting out the wires, in
    which case it fails quickly (as we have found out here) or you can
    overload it slowly, in which case it fails slowly.
    
    find a dimmer that is meant to handle 225 watts and replace yours
    immediately, if not sooner.  a hot box in a wall is a fire waiting
    to happen.
    
    on dimmers in general - i believe that the more you dim the lights
    the more energy is absorbed by the dimmer = more heat dissipated.
    they have always scared me, because i have felt very hot walls
    when they fail.  perhaps newer dimmers are more reliable, but if
    it were me i'd still try to come as close as possible with the proper
    wattage light bulb, then only dim the lights as little as possible.
    
    correct me if i'm wrong.
    
    brian
291.162225 is not too much.STAR::SWISTJim Swist ZKO1-1/D42 381-1264Mon Apr 13 1987 19:2819
    Re .18
    
    Most ordinary elcheapo dimmers are rated at 500-600 watts.  So 225
    should be no problem; however, the humming/buzzing problems will
    increase with a larger load.
    
    Re: Earlier replies.
    
    It's not my experience that sending square waves through a filament
    shortens the life - if it does, then it's more than offset by the
    lengthening of life due to lower voltage.

    Actually, I find the more annoying problem is that the damn harmonics
    from those square waves radiate around the house wiring and introduce
    buzz into radios, particularly AM.
    
    Jim
    
    
291.163most timmers chop time, not voltagePEANO::GLASERSteve Glaser DTN 226-7646 LKG1-2/A19Mon Apr 13 1987 19:5036
    Most of the dimmers out there work by cutting the sine wave apart in
    time, not voltage. 
    
    In other words (or pictures):
    
             |\
             | \
             |  \
             |   \
             |    \
             |     \
    _________|      \_________       ____________
                             |      /
                             |     /
                             |    /
                             |   /
                             |  /
                             | /
                             |/
    
    Where the vertical lines move based on what position you have the
    control at.  The vertical pulse contains all sorts of high frequency
    components.  The interference you get in radios, stereos, etc. is
    due to tha appearance of this pulse of RF 120 times a second.
    
    The good (expensive) dimmers do things to moderate the rise time of
    this pulse.  This cuts down on the RF noise, makes the filaments last
    longer, and helps with humming problems in filaments and dimmers.
    [actually now that the FCC has tightened up the rules on EMI, it may be
    that all dimmers do this to some extent.] 
    
    Note that the dimmer is just acting as a switch (turning the bulb
    off and on 120 times a second).  It is not absorbing any energy
    as was implied in an earlier reply.
    
    Steveg
291.164filter.....NEXUS::GORTMAKERTue Apr 14 1987 02:058
    You can cut some of the interference by installing a .05mfd
    ceramic disk capacitor between hot and gound and neutral and ground.
    I tried this due to problems with lines on the tv caused by the
    dimmer. Worked fine the 1st time. Besure to properly insulate the
    leads on the cap with old (wire)insulation scraps and tape.
    
    -j
    
291.165Maybe they don't know the words??TALLIS::SAMARASAdvanced Vax Engineering LTNTue Apr 14 1987 13:4820
    A humming dimmer is not usually a sign that anything is wrong. It
    turns out that the semiconductor device in the dimmer that is doing the
    switching actually vibrates slightly! This happens 'cause it's
    switching 2 or 3 AMPS, 120 times a second. It generates a little
    EMF (for you EE types). BTW, the most noise
    (electrical and audible) occurs at about the mid brightness setting. 
    
    The semiconductor device gets a little warm from all this switching, so
    its mounted (riveted) to a heat sink to keep it cool.  Usually this is
    just the case of the dimmer. Some high power dimmers have "fins" on the
    front of them to help remove the heat. If the vibrating semiconductor
    device is a little bit loose, or if your dimmer is not fastened into
    your electrical box tightly, the sound could be louder. I'd suspect
    that a plastic box would make less noise (I'm guessing). 
    
    The speed control in an electric drill works the same way.  They
    "buzz" or hum at slow speeds too.
                  
    
    ...bill
291.113??? about wattage in fluorescent fixturesCHAPLN::ROSENTHALOut to break Murphy's Law!Tue Apr 14 1987 15:3014
    
    I bought a beautiful kitchen light fixture from the Lightolier
    catalog for my new house.  The fixture required 2 40-watt lamps.
    After having it installed, I've found it MUCH too bright and
    harsh in my kitchen (I can't remember the type of lamps I
    chose, whether they were soft white, or cool white, or whatever).
    
    Can I change the 40-watt lamps to something dimmer, as I would
    with a regular fixture, or must I use only 40-watt?
    
    Thanks.
    
    Donna_who_didn't_do_enough_homework_and_now_needs_sunglasses!
    
291.166CLOVAX::MARESTue Apr 14 1987 15:5917
    RE: .17
    
    Does     ME   =   ME   ?????   
             yl
              e
              c
              t
              r
              i
              c
              i
              a
              n
               
    
    Randy
    
291.114No, But...YODA::BARANSKI1's &amp; 0's, what could be simpler!?Tue Apr 14 1987 16:4210
The problem with fluorescent fixtures is that the amount of light they produce
is directly proportionate to their size, or to be exact, their surface area. So,
no, you can't just change to a lower wattage 'bulb'. 

However, the above assumes that all other things are equal...  There are
a number of different 'bulbs' that put out different light at the same
wattage...  You could replace the cover with a smoked cover to dim the light...
etc...

Jim.
291.115A couple more ideasVIDEO::DCLDavid LarrickTue Apr 14 1987 19:1011
> (I can't remember the type of lamps I
> chose, whether they were soft white, or cool white, or whatever).
    
The tube should say, right on it.  Most common, cheapest, and most likely
is cool white.  Perhaps what you're reacting to is not the level of light
so much as its harsh, garish quality; if so, switching to soft white or
warm white might well do the trick.


Simplest solution:  just remove one of the tubes.  It may not look very
good, but it'll be less light. 
291.167Know my LimitationsERLANG::BDBrian D. HandspickerTue Apr 14 1987 22:0913
    Re: .17 - .22 
    Thank you all for easing my fears.  I will rest much
    easier now.  
    
    Re: .23
    This time around I had enough rewiring to warrant hiring
    a real electrician.  I'll putter.  I'll run wire.  But
    I won't rewire an entire condominum unit while I and 14
    other people live in the building.  One screw-up and all
    of us are without light and heat.  I let a pro handle
    this one.
    
    
291.116NEXUS::GORTMAKERWed Apr 15 1987 00:4014
    You can also purchase the GE watt-mizer lamps they do have a somewhat
    lower lumen output over standard cool white lamps. I belive the
    wattage for the watt-mizer lamps is 34 -vs- 40 watts.
    Not a big savings but... I would sugggest the warm white or day
    light lamps. I use them in every lixture i have and prefer them
    for the reduced harshness and how they make colors appear.
    BTW-they do run 5-10% higher in price.
    
    -jerry
    P.s. Any lighting store worth its name should be able to demo
    the various bulbs for you. GE makes about 20 types of 40 watt
    lamps all different colors,ect. Get a cataloge for more info.
    
    
291.168Help with Wiring (lighting)FDCV19::CUMMINGSTue Apr 21 1987 13:330
291.169VINO::KILGOREWild BillWed Apr 22 1987 14:2713
    
    Use whatever routing is more convenient (less cable, less cutting,
    fewest cables per box, etc). Three-wire cabling is not neccessary for
    what you have in mind.
    
    Do you really need a 20-amp circuit? How big are these lights? A
    15-amp circuit will handle 10 150-watt lamps with a capacity margin
    of 17% (120v.*15a.=1800w., 10*150w.=1500w., 1500w./1800w.=83%).
    And 14ga. wire is so much easier to work with than 12ga. (not to
    mention somewhat less expensive).
    
    I would also check the capacity of the dimmers - most are rated
    in the 300-600w. range. Make sure they can handle the proposed load.
291.170125% of continuous load..REMEDY::KOPECEschew Obfuscation!Wed Apr 22 1987 15:049
    re: is 20 amp circuit really needed:
    
    Normal (code) calculation is  125% of the permanently connected
    continuous load.. the continuous load for recess lighting is the
    RATING of the fixture. so, if you use 8 fixtures rated at 150W,
    the answer is yes, you can get away with 15 amps. 10 fixtures wouldn't
    work (16.3 amps min.)
    
    ...tek
291.117Gro-Lux?Q::ROSENBAUMRich Rosenbaum;mail-&gt;Boehm::RosenbaumTue Apr 28 1987 17:4012
    re .7
    Romoving one of the lamps will probably prevent the other from working.
    
    
    You might try using one "Gro-lux"  or "Plant-Gro" bulb.  These are
    fairly reddish, and have a much lower light output than standard
    bulbs.  You proably would not like two bulbs of this type, tho.
    
    I would try one Gro-Lux and one Warm white.  The Gro-Lux type are
    expensive, though - about $10 for 1 4'.
    
    __Rich
291.181Voltage drop in old wiringTALLIS::SAMARASAdvanced Vax Engineering LTNTue Apr 28 1987 19:3227
    I've been renovating an old house and have run into an electrical
    problem.  It seems that there is an excessive voltage drop from any of
    the existing outlets.  Lighting is OK, but whenever a high current
    device is used, the lights dim alot. A "smart" device like a microwave
    oven, sometimes causes the oven to shut off since it "knows" when the
    voltage gets too low. The VCR gets wierd too, when all of the lights
    are on. (I haven't measured yet, but it MUST be a 20 or 30 volt drop to
    do that)!! 
    
    There are some new (<1yr) circuits that are fine. The existing stuff is
    classic 1940 BX two wire, with the shield used as the safety ground.
    I took the breaker panel apart and everything looked nice and tight.
    
    My question is:  Is this old BX stuff inherently high resistance
    wire?  Was copper rare during the war or something??  So far, I'm
    hoping to find a junction box with a loose connection, but I can't
    find one.  I tightened all of the outlet screws (they were already
    pretty tight), but I couldn't see anything funny.  
    
    I'm starting to wonder if the BX wire is high resistance stuff.
    There is a pretty long run of wire up to the second floor. I'm not
    too happy about dissipating all of that power in my wires.
    
    Any info is appreciated,
    ...bill_who_doesn't_like_old_wiring_anyway
    
    
291.182VIDEO::DCLDavid LarrickTue Apr 28 1987 20:3022
First of all, it may just be that your house is under-powered, or that your 
circuits are poorly configured.  Make a circuit list/diagram of the house, 
listing all loads by circuit.  You may be surprised at the current some of 
your circuits are drawing!

Failing that, it sounds like dirt and corrosion where the existing wires
are connected to the existing outlets, rather than deterioration of the
cables themselves.  You'd do well to get a voltmeter and measure the
voltage at every point where you can get at it, i.e. at each outlet along
each circuit.  That procedure would help you pinpoint which outlets (and
maybe cables) are in the worst shape, and where your corrective efforts
should begin. 

The Old House Journal had an article a few years back with useful 
information about debugging old wiring.  One technique involves shutting
off all circuits but one, unplugging all loads on that one remaining 
circuit, and then checking the electric meter.  If the meter moves at all 
over a period of an hour or so, you've got a slow current leak in that 
circuit somewhere.

All of the above problems are potentially quite serious.  As you mention,
the "missing" power is being dissipated as heat somewhere in the house. 
291.183Check your fusistors.TALLIS::KOCHKevin Koch LTN1-2/B17 DTN226-6274Wed Apr 29 1987 11:564
     A much more common cause of dimming when the fridge turns on (or 
whatever) is old fuses that have developed a resistance.  Electricians 
call them fusistors.  Try replacing your main fuses.  It worked for 
me.
291.184AUTHOR::WELLCOMESteveWed Apr 29 1987 13:516
    Corrosion on the terminals in the outlets, maybe?  Or low pressure
    on the plug terminals when one is plugged in?  
    Does the plug heat up on a current-drawing appliance when you plug 
    it in?  If so, changing the outlets might help.  Or maybe run an
    ignition file into the outlet slots (power off first!!!) to clean 
    the contacts?
291.185check neutral linesWHO::SHOREYWed Apr 29 1987 22:0511
    check to make sure that they didn't ground the neutral wire when
    they did the original wire.
    
    if neutral is grounded and something is drawing current, ground
    potential can actually go up.  when ground is above ground (!!!???)
    that is like a voltage drop.
    
    i know it sounds screwy, but it really happened in a place where
    i used to work.  they were having voltage drop problems when lots
    of things were on and found that the ground inside the building
    was about 10v higher than the ground outside.  this too is dangerous...
291.171LITTLE ADVICEANOVAX::GUYDISHThu Apr 30 1987 12:5711
    BEING AN ELECTRICIAN FOR A FEW YEARS, MAYBE I CAN HELP WITH ONE
    SUGGESTION.
    
    14 GAUGE WIRE WILL BE PLENTY BIG ENOUGH FIRST OFF  AND WHEN YOU
    RUN THE WIRE, GO TO THE SWITCH FIRST AND THE TO THE LIGHT THE REASON
    BEING THAT MOST RECESSED LIGHTS HAVE VERY LIMITED SPACE IN THEIR
    JUNCTION BOXES AND THE LESS CONNECTIONS AND WIRE NUTS IN THE BOX,THE
    BETTER AND SAFER
    
    
    JOE
291.186good ideasTALLIS::SAMARASAdvanced Vax Engineering LTNThu Apr 30 1987 18:0411
    Thanks for the ideas so far.  I'm going to check this out this weekend.
    BTW, there have been some recent new circuits added to the building
    that are absolutely fine. I doubt if there is a problem with the
    service entering the building. Also, the sevice box was recently
    upgraded to all breakers, so there aren't any fuse panels left. There's
    just something funnie going on with the "old" BX stuff.  The idea about
    ground currents in .4 sounds feasible. I'll get out the "OLD" VTVM and
    do some measuring. 
    
    thanks so far,
    ...bill
291.198HELP WITH WIRING!VENOM::WATERSThe Legend of the LakesFri May 01 1987 13:5222
    I have a wiring question!  I think I have the right idea in mind
    but when it comes to electricity I'd like to make sure!
    I have one heavy duty cord coming off my bench...when plugged
    in, it turns my fluorescent lights on and makes the outlets to
    my work bench LIVE!  I want to put a switch in so I don't have to
    plug in the cord...just hit the switch..and BINGO!  Now the outlet
    that I plug into is mounted right beside the main power boc to the
    house!  I've mounted the switch box right above this outlet!  When
    I took the outlet apart last night and found that there is only
    a black and white wire coming out of the main box into the outlet!
    Where is the ground?  Shouldn't it be grounded to the outlet box
    it self?  Could someone just walk me through this..
    
    I have one cord with three wires coming off the bench..
    I have the outlet pulled apart and disconnected from the two B/W
    wires coming out of the main box...
    The switch box is mounted just above the outlet..What do I do????
    
    The power is turned off..I'm stupid...NOT CRAZY!
    							John
    
    
291.199A possibilityARGUS::CURTISDick 'Aristotle' CurtisFri May 01 1987 14:2221
    I've seen instances where the ground wire was wrapped around the
    last inch of outer cable insulation in a tight wrap. This just
    happens to be the place where the clamping device in the top (or
    bottom) of the box holds the cable firmly in place;  the effect
    is to make a good connection between the ground wire and the box.
    
    You can determine whether this is the case by loosening the screw
    on the clamp and (carefully!) pull the cable out about an inch or
    so.
    
    Oh, by the way... (getting set to be beaten about the head and
    shoulders here)...
    
    I was thinking of adding a couple of outlets to a room here, and
    the outlets have ONE ground screw.  The ground wire in my 12-2 looks
    rather large for putting two wires on the single screw;  is it
    legitimate (i.e., according to the Electrical Code) to put one wire
    on the screw, and do this wrapping jazz with the other?
    
    Dick
    
291.200conduit?WHO::SHOREYFri May 01 1987 14:5010
    is the outlet connected to the box with conduit?
    
    perhaps that is the ground?
    
    
    also, do you want to run your entire workbench through the switch,
    or just the lights?  you might be better off to leave the bench
    as it is and wire a separate circuit for the lights.
    
    brian
291.201IT IS CONDUIT!VENOM::WATERSThe Legend of the LakesFri May 01 1987 15:2410
    Brian, I'd like to run everything into the switch!  I was going
    to run the lights into the regular cellar lights that turn on when
    the switch at the top of the stairs is turned on!  I don't want
    my shop lights coming on everytime the kids take a bag of rubbish
    down!  And I am putting the switch where it can't be reached!  Even
    though the kids have been told never to go near my power tools..you
    never know what a kid will do!I like the idea that the bench and
    machinery is dead when the switch is off!  There is conduit coming
    from the main box to the outlet!  Is that my ground?   And if so
    how do I ground the switch box?
291.202BEING::WEISSTrade freedom for security-lose bothFri May 01 1987 17:290
291.203Some answersVIDEO::DCLDavid LarrickFri May 01 1987 17:5749
Nice guess on the conduit, .2.

re .0 and .3:  Yes, the conduit is your ground, and a good one too, 
assuming all clamps are properly installed.

The idea is to ground both the box and the device (outlet, switch, etc.). 
An old technique was to ground the box (perhaps by conduit clamps or by 
the wrapping technique .1 mentions), then assume the ground is properly 
transmitted to the device by its mounting screws.  Modern Code and modern
practice require that the device be grounded too, by running a ground wire
(usually bare, sometimes green-insulated) to the device's grounding screw. 

In your case, you can assume that the existing box is properly grounded by
the conduit and its clamp.  There should be a (bare or green) wire running
from a screw driven into the box itself to the device's ground screw; if
there isn't one, you should probably install one.  To propogate that ground
to another (new) box, connect the ground wire of your Romex to another
screw driven into the existing box.  Use a proper Romex clamp, too. Even
better (but more difficult), use conduit. 

N.B.  If there are any plastic boxes (as opposed to metal ones) involved, 
the answers are different, since there's not much point to grounding a 
plastic box.

re .1:  

>    ...is it
>    legitimate (i.e., according to the Electrical Code) to put one wire
>    on the screw, and do this wrapping jazz with the other?

The "wrapping jazz" must have been legit once - my father taught me to do
it that way - but it's a no-no now.  Note that your scheme would transmit
the ground for the outlet, plus that for any boxes downstream, through the
outlet's mounting screws - risky, especially for #12 wire. 

As you seem to recognize, the Code NEVER allows multiple wires under a
single screw, so that's not an answer either.

You're supposed to run a bare wire from the device's ground screw, another
from the box's ground screw, and connect both to the ground wire(s) coming
in from outside the box. 

Special topless wire nuts exist that allow you to connect two wires 
together, but pass the end of one or both wires on through to attach to
screws.  Crimp lugs are even better for this purpose. 

If there's only one cable coming into the box, it's also possible to loop
the ground wire around the box's ground screw and end the same wire at the
device's ground screw. 
291.204IS THIS THE RIGHT WAY?VENOM::WATERSThe Legend of the LakesFri May 01 1987 18:5312
    So...this is how I'll do it! 
    First I'll run the wire coming from my bench to the switch, then
    I'll put the w-on one side and b-on the other and screw the g-to
    the back of the box.  I'm then going to run a short cord running
    out of the switch box to the outlet box making the connections to
    both the switch and the plug and making a good connection of the
    ground wire from box to box the grounding of the outlet box will
    be cared over to the switch by making the connection to both boxes!
    RIGHT??????!!!!  
    When I do this tonight I don't want any electricity getting me to
    excited!!!!!!!!!!!!
    
291.205VIDEO::DCLDavid LarrickFri May 01 1987 20:3252
Maybe yes, maybe no; I can't tell for sure.  A couple of questions arise 
from your description:

>    First I'll run the wire coming from my bench to the switch, then
>    I'll put the w-on one side and b-on the other and screw the g-to
>    the back of the box.

Well...what type of "wire" is it?  If it's an extension cord (even a heavy-
duty one), you really shouldn't wire it permanently to anything.  You might 
prefer to install a switch-controlled outlet into which you can plug your
"wire", or even re-wire the existing outlet so it's controlled by the 
switch.

Alternatively, if the existing "wire" is Romex that you've attached a plug
to, your existing installation is illegal (but you'll be fixing that).  The
point is that extension cords and permanent wiring are different things,
made of different materials, intended for different purposes, and mixing
them causes problems. 

I don't understand how you plan to wire the switch.  What's usually done is
to switch the hot (black) side of the circuit, and run the common (white)
side straight through the switch box, unswitched. 

..."to the back of the box":  on the INSIDE of the box, right?

>    I'm then going to run a short cord running
>    out of the switch box to the outlet box making the connections to
>    both the switch and the plug and making a good connection of the
>    ground wire from box to box 

The "short cord" must be Romex or other official house-wiring cable of the 
proper gauge, NOT a hacked-up extension cord. 

Your description of grounding both boxes seems OK.

Be sure you NEVER put two wires under the same screw.  In a situation where 
you'd like to do so, you should connect those two wires to each other and 
to a short jumper wire, using a wire nut.  Then attach the other end of the
(single) jumper wire with the screw. 

>    the grounding of the outlet box will
>    be cared over to the switch by making the connection to both boxes!

I don't understand this description at all.  You haven't said anything 
about the grounding screws on the devices (outlet and switch) themselves.

I can't tell whether you understand how to do the job or not - maybe you
just didn't write very precisely.  But I would strongly suggest that you
get a book about wiring (the Time-Life one is probably about right for this
job), and read and understand it thoroughly before you proceed.  Too much
is at stake here to fool around, and your NOTEing friends won't be down in 
the basement watching you!
291.206Ask a silly question, get material for 3 more...ARGUS::CURTISDick 'Aristotle' CurtisMon May 04 1987 00:2835
    .5:
>The "wrapping jazz" must have been legit once - my father taught me to do
>it that way - but it's a no-no now.  Note that your scheme would transmit
>the ground for the outlet, plus that for any boxes downstream, through the
>outlet's mounting screws - risky, especially for #12 wire. 
 
    Oh good.  Guess who showed me that trick?  But I don't understand
    your objection.  I have a 20A duplex outlet made by Leveton here.
    At top and bottom are the little metal tabs with captive screws
    that bolt the outlet into the box.  Turning it over reveals that
    the two metal tabs are part of a metal strip that runs the length
    of the outlet, and  the metal strip has a wing on the side into
    which the ground screw is mounted.  So, unless the mounting screws
    have some sort of nonconductive finish, they too will be electrically
    grounded.  But then again, if the box is grounded, the screws will
    be too, so what's the difference?  (Besides which, I thought I stated
    that this would involve the cable clamp in the back of the box,
    whose screw would effectively be a ground screw for the box -- oh,
    come to think of it, there's TWO such screws in the box, perhaps
    using one of them would be legitimate?)
    
    
>You're supposed to run a bare wire from the device's ground screw, another
>from the box's ground screw, and connect both to the ground wire(s) coming
>in from outside the box. 

>Special topless wire nuts exist that allow you to connect two wires 
>together, but pass the end of one or both wires on through to attach to
>screws.  Crimp lugs are even better for this purpose. 

    Sigh.  Does Spag's carry these topless wire nuts?  Or these crimp
    lugs?  (Are these vanilla looking things, or multi-wire wombats?)
    
    Dick
    
291.207VIDEO::DCLDavid LarrickMon May 04 1987 02:3327
Please understand that I was describing the Code (as I remember it from a
big project several months ago, and as the Maynard wiring inspector
enforced it), not my personal opinion. 

My interpretation is that the Code wants to separate the functions of
mechanical support and electrial/ground continuity.  The idea, I guess, is
that the mechanical support (clamps, mounting screws, etc.) can fail or be
taken apart without loss of ground protection.  So even though you have two 
mounting screws that happen to provide adequate ground, they don't count 
for Code purposes; you still need a separate electrical ground path that 
doesn't serve any mechanical function.

Note that the above is my guess; the Code tells you what to do, not why.

For me, the Code's ratio of worthwhile stuff to foolishness is high enough 
that I don't bother trying to justify each rule.  I just do what it says, 
especially if there are likely to be inspectors, other electricians, or 
other owners involved.

    
>    Sigh.  Does Spag's carry these topless wire nuts?  Or these crimp
>    lugs?  (Are these vanilla looking things, or multi-wire wombats?)
    
Sorry, I don't know.  Crimp lugs are pretty widely available (auto parts 
stores and even K-Mart, I think).  I was lucky enough to receive a Buchanon 
crimping tool as a present, so once I found a source for their special 
lugs, I was all set - used very few wire nuts.
291.208COBRA::DUTHIEMon May 04 1987 14:5036
    Well, I hope you didn't try it yet.  If you hook the white wire
    to one side of the switch, and the black wire to the other side
    of the switch, you will blow your fuse/circuit breaker as soon as
    you turn the switch on (if your lucky).  You need to put the black
    wire from your work bench to one side of the switch, and a black
    wire from the other side of the switch to your power supply.  The
    white wire should pass unbroken through the box where the switch
    is, and run directly to the power supply.  Your idea to use a plug
    between the switch and the original outlet sounds OK, but probably
    not to code.  What you are doing is basically using an extension
    cord that has an on/off switch in it.  What I would do is...
      Put a short piece of conduit between the new switch box and the
    old outlet box.  You can buy an offset nipple (is that the right
    name?) that is about 3" long with about a 1" offset and is threaded
    at both ends.  This will ground your new box.  Run the black wire
    from the outlet strip to one side of the switch.  Run a black wire
    from the other side of the switch to the black wire on the original
    outlet.  There should be two screws on each side of the original
    outlet, this new wire goes to the unused screw next to the black
    wire.  Run the white wire from the outlet strip directly to the
    screw next to the white wire on the original outlet.  Run the green
    or bare wire from the outlet strip to a screw in the back of the
    switch box.
    
    ____ 
       |  black       black                          1 is the fuse box
       |----------, ,----------,                     2 is the old outlet
       |        |----|       |----|                  3 is the new switch
     1 |        |--2-|       |--3-|  black
       |----------' '---,      '------------->
       |     white      |                      to work bench>
       |                '-------------------->
    ---|                             white
                                             (plus green wire to ground)    

    Jim D.    
291.209switched outlet?WHY::SHOREYMon May 04 1987 19:3318
    i like the suggestion in .10.  there is one other way, those of
    you who know the CODE correct me if i'm wrong...
    
    you can wire the switch before the outlet, therefore making a
    switched outlet.  you could leave the extension cord you have
    going to your bench, and use the switch to turn it on and off.
    i'm pretty sure it's ok to have a switched outlet.
    
    if you have tools on your bench that draw lots of power, make sure
    you get a heavy duty switch.  overloading a switch can melt the
    contacts together, and someday you might think you're turning the
    power off but it'll still be on.
    
    if you don't fully understand what you're doing, read up on it or
    find somebody to help.  when houses burn due to faulty wiring
    claims don't get paid.
    
    brian
291.210Spag's, strikes again.WELFAR::PGRANSEWICZMon May 04 1987 20:476
    RE: .8
    
    Yes, Spags has both the wire nuts and crimp lugs.  In the electrical
    dept., first find the wire nuts in the bins.  Now do a 180 degree
    turn and you'll see the crimp lugs on the top shelf.
    
291.211I would avoid a switched outlet by a workbenchCADSE::MCCARTHYExcellent, more than a match for poor Enterprise.Mon May 04 1987 22:5411
    >    if you have tools on your bench that draw lots of power, make sure
    > you get a heavy duty switch.  overloading a switch can melt the
    > contacts together, and someday you might think you're turning the
    > power off but it'll still be on.

	I would not run ANY power tool off a switched outlet (well maybe
    a hand drill) but I know I would not like to be around when the
    contacts start to melt!
    
    mac
    
291.212VIDEO::DCLDavid LarrickTue May 05 1987 12:4810
>	I would not run ANY power tool off a switched outlet (well maybe
>    a hand drill) but I know I would not like to be around when the
>    contacts start to melt!
    
Unnecessary paranoia.  If the ratings of the switch, outlet, and wire are 
all greater than that of the power tool in question, all will be well.  If
the power tool's rating exceeds that of the outlet and/or wire, you're in 
trouble whether there's a switch in the circuit or not.

It's just a question of using the proper materials for the job.
291.187please clarifyTALLIS::SAMARASAdvanced Vax Engineering LTNTue May 05 1987 14:2515
    RE: .4

    >check to make sure that they didn't ground the neutral wire when
    >they did the original wire.
    >
    >if neutral is grounded and something is drawing current, ground
    >potential can actually go up.  when ground is above ground (!!!???)
    >that is like a voltage drop.
    
    How can a grounded neutral cause a problem?  If it's grounded at
    the receptical (white to GND), then there would be an additional
    return path (I think).  At the service panel, isn't neutral tied
    to ground there anyway??
    
    ..bill
291.213Maybe unnecessary, but ratings are not my only reasonCADSE::MCCARTHYExcellent, more than a match for poor Enterprise.Tue May 05 1987 14:3117
    
	There is one more reason I never use a switced outlet.  Have you
    ever been drilling a hole with Milwalkee right-angle drill and had
    the power shut off and back on quickly?  That sucker has alot of
    torque.  The drill stops, you say "What the....." and loosen your
    grip (still holding the trigger)  BAM the power returns and it starts
    doing a twist! (Never use the trigger lock by the way!).  You then
    here in the distance "No Bobby, the other switch."
    
    	When you work under unknown conditions (kids in area, or at a
    customers house) I try to reduce risk so I make sure that I am using a
    constant feed outlet and tell the people to send the kids out to
    play.
    
    	By the way, if the drill stops now, I let go of it QUICK!
    
    mac  
291.188One point (only)CADSE::MCCARTHYExcellent, more than a match for poor Enterprise.Tue May 05 1987 14:358
    By code, the neutral and ground wires are only supposed to be "common"
    (connected) at one point.  That point is usually in the breaker
    panel.
    
    I am not sure if it would cause a voltage drop but the neutral side
    of a circut can carry a load (voltage).
    
    mac
291.189Ground is for safety, not for any current!DRUID::CHACETue May 05 1987 14:3810
     The reason is that ground in this case would be carrying current
    which it is never supposed to do except in a fault condition. The
    ground in house wiring is supposed to be a redundant safety and
    not a paralleled conductor. If there is any current flow in the
    ground then there will be a voltage on the wire due to normal
    resistance. This may or may not cause problems with equipment that
    uses ground as a reference. It definitely could cause problems at
    other outlets if you had an open neutral in the circuit in question.
    
    					Kenny
291.214I'm all set!VENOM::WATERSThe Legend of the LakesTue May 05 1987 17:5634
Well, thanks for all your suggestions!  I had the scare of my life!

I wired it the way I described and ....boom!  I knocked the whole house

out!  I am presently in the process of buying the duplex I live in so

instead of messing with it anymore I called the landlord and explained

what I did and that I had no power in the house.  He said I probablly 

had to reset the breaker for the whole house that was located in the 

basement on the other side!  He said not to mess with it and he would have

his electician come over to wire it up!  Its all set now..works great!

He put a seperate breaker in the box for the bench..the bench wire which is

14 gage wire runs to the switch and then a piece of heavy duty solid wire

runs from the switch box to the outlet box!  It looks o.k.!  That wire from

my bench comes out of one of the long black bars with five plug outlets.

I never use more than one power tool at a time and the switch installed will

never be on when I'm not in the workshop working.  I think I'm all set!

Thanks for all your help and concerns.  I learned a good lesson..handyman

or not...when it comes to electricity you better know what your doing!!


							John
291.215Electrical questions - BostonNEPTUN::BERKSONMon Jun 08 1987 17:4623
    A few questions about wiring. This ifor the third floor of a 3 family
    house with the breaker box in the basement. It is in Boston and
    I'd like the answers to conform to the National and Massachusetts
    code.
    
    1. Does the 1987 code require GFCI's in the kitchen?
    
    2. Does the code require two separate small appliance circuits in
    the kitchen? Of what capacity?
    
    3. My impression was that these two circuits are required and that
    they must/should be GFCI's. Since these circuits are sometimes run
    via a three conductor cable, how is the GFCI incorporated? I assume
    a standard GFCI wouldn't work here.
    
    4. A dishwasher and disposal will be wired on separate breakers
    in the basement. Is there any requirement for there to be an additional
    switch for them in the unit?
    
    Thanks.
    
        mitch  
        
291.216JOET::JOETMon Jun 08 1987 18:195
    Not to sound like a broken record, but check with the building
    inspector.  Since he (she?) has the final say, it only makes sense
    to see what he's looking for.
    
    -joet
291.217Would rather not ask the inspectorNEPTUN::BERKSONMon Jun 08 1987 19:125
    Only licensed electricians can do electrical work in Boston. I am
    looking for answers which can be had without asking the building
    inspector. 
    
      mitch
291.218BPOV09::SJOHNSONHill Street Station...Mon Jun 08 1987 20:304
    
    you can pick up the NEC code book at bookstores for about 25 bucks,
    if you'd like something official to use as a guideline.  
    
291.219Where?DELNI::OSTROMAndy Ostrom Networks Mktg. 272-7132Mon Jun 08 1987 20:398
re: .3

    Anyone know of a bookstore that HAS the 1987 code.  I've been looking and 
can't find it anywhere...


			Andy Ostrom

291.220VIDEO::DCLDavid LarrickMon Jun 08 1987 22:1142
Disclaimers:  the following is my opinion only, and I don't know if Boston
has electrical code provisions of its own, in general or specifically for
rental property. 

>    1. Does the 1987 code require GFCI's in the kitchen?

Yes, for outlets that are within some defined distance (six feet?) of the sink.
    
>    2. Does the code require two separate small appliance circuits in
>    the kitchen? Of what capacity?

Yes, at least two, 20A each.  Note that a refrigerator is a "small 
appliance" for purposes of this rule.
    
>    3. My impression was that these two circuits are required and that
>    they must/should be GFCI's. Since these circuits are sometimes run
>    via a three conductor cable, how is the GFCI incorporated? I assume
>    a standard GFCI wouldn't work here.

Subtle distinction:  the requirement is that the OUTLETS (and, as we've 
seen above, only certain outlets) be protected by GFCI - not necessarily
the entire circuit.  So one option is to run 3-wire cable to all of the
outlets that don't require GFCI, than use normal 2-wire cable (perhaps
tapped off of a 3-wire circuit) for the outlets near the sink. 
    
You may certainly have GFCI on the entire circuit, either via a 
service-panel-mounted GFCI breaker, or via a GFCI outlet in the first box 
on the circuit.  The problem, as you've noticed, is that the available GFCI 
packaging doesn't lend itself to 3-wire circuits.  Anybody know about 
clever GFCI packaging that's more accomodating (or is there an inherent
restriction that I haven't thought of)?

>    4. A dishwasher and disposal will be wired on separate breakers
>    in the basement. Is there any requirement for there to be an additional
>    switch for them in the unit?

I've never heard of a dishwasher or a disposal that didn't have some sort
of switch associated with it, so maybe I don't understand your question. 
    

re .4, where to find 1987 code:  I don't know for sure, but I would think
that electrical supply houses would be a better bet than bookstores. 
291.2211987 NEC code book @ Ralph PillSEESAW::PILANTL. Mark PilantTue Jun 09 1987 01:248
    RE: .4
    
    	Last time I was in, Ralph Pill in Nashua had a large stack of
    	1987 NEC code books.  They also had a smaller stack of 1984
    	code books.  I'm not sure of the price, but a phone call would
    	correct that.
    
    - Mark
291.222no gfi for three wire cktsREGENT::GETTYSBob Gettys N1BRMTue Jun 09 1987 12:0610
                It would be difficult (if not impossible) to construct a
        gfi that would work on a 3 wire circuit (two hots and a neutral)
        because of the way in which a gfi works. A gfi senses an
        imbalance of current between the hot lead and the neutral lead.
        In a three wire circuit, the only time that the current is
        guaranteed to be balanced between hot and neutral is when only
        one side is in use. ANY current drawn on the opposite side WILL
        cause the neutral current to be different from the hot current!
                
                /s/     Bob
291.224MA code book, outlet type GFIsVIDEO::GOODRICHGerry GoodrichTue Jun 09 1987 12:5523
    You don't really want the NEC, Mass has a somewhat stricter
    version.  I am not sure about the present, but you should
    be able to find where to purchase a Mass version by calling
    state agencies in Boston.  The Mass version was just the
    NEC book with a prefix of requirements unique to Mass such
    as using insulated staples.

    As to 3 wire & GFI's - the only purpose is to save wire.
    If you are running 3 circuits (2 utility & dishwasher) just
    put the outlets near the sink on the single circuit. Or you
    can just run 3 single circuits.
    
    Another approach would be to run the 3 wire circuit to the
    kitchen with conventional breakers.  Wire one circuit to
    the first GFI protected outlet and use a outlet type GFI.
    Additional protected outlets may be wired from the outlet
    GFI.
    
    If you find the source for the MA code book it might be handy
    to post it in a seperate note.

    - gerry
291.225CRETE::FLANNERYTue Jun 09 1987 18:033
    Walden Books at Searstown Mall in Leominster had them
    last month.  Might still.
    
291.226gfi circuit breaker in mainMORMPS::WINSTONJeff Winston (Hudson, MA)Tue Jun 09 1987 21:124
interesting thing about GFIs - I just had an electrician put them in 
all 3 bathrooms - instead of putting $30 gfi's in each one, he put in 
regular outlets, and put them all on a dedicated line with a 'gfi 
fuse' in the fusebox - new idea?
291.227NEXUS::GORTMAKERthe GortWed Jun 10 1987 01:1910
    re.11
    No, they have been around for along time...some disagree on the
    protection they offer. Square-d is a popular vendor for these type
    of GFI's but they only work in Sq-d panels federal pacific makes
    them for thier panels.
    Anyone out there care to expand on why the panel GFI's are
    not used as often?
    
    -jerry
    
291.229VINO::KILGOREWild BillWed Jun 10 1987 12:0514
    Assuming we're talking about a GFCI panel breaker, as opposed to
    a GFCI outlet:
    
    o  The breaker is VERY expensive ($65 retail, $40 if you have an
       electrician friend). The outlet can be had for $10 on sale at
       retail outlets.
    
    o  The breaker seems to be much more sensitive to surges (lightning
       strikes, etc; I have heard of many breakers destroyed by
       near strikes, but the outlets seem to come out ok.)
    
    o  The breaker is more suitable for new construction, when you have
       some control over the wire routing. The outlet can be popped in
       anywhere it's needed, as an afterthought.
291.230Had 'em... Don't like 'em!USMRM2::CBUSKYWed Jun 10 1987 13:1717
    I had a GFI/breaker in the panel for the bathroom and it it/was a royal
    pain in the A**. It had a habit of tripping randomly in the middle of
    the night, usually 2-3 times a month with NO set pattern, ie only in
    electrical storms or wet nights. I replaced the breaker once to no
    avail. 
    
    We would discover that it had been tripped usually in the morning after
    a shower while trying to plug in a razor or hair dryer. Then it was
    either a trip to the basement or a loud cry to some else in the house,
    "WOULD SOMEBODY PLEASE GO DOWNSTAIRS AND RESET THE G*D* CIRCUT
    BREAKER." 
    
    I've since rewired and replaced the bathroom outlet with the more
    common GFI/outlet. It has never tripped but if/when it ever does the
    reset button is right there. 

    Charly
291.231Where to get the various electrical code booksISBG::POWELLReed Powell - LCG Marketing - 297-4261Wed Jun 10 1987 14:0522
   
    To get the NEC code call the NFPA at 800-344-3555.  As I've said
    in other notes, this is good reading for sleep-less nights, but
    for the '87 code they got smart and sell their own version of "What
    we meant when we wrote this document" as Audel's and others have
    been doing for years.  Get that version (includes the straight text,
    but with explanatory notes, etc., like a lot of the Tax books do).
    
    For the Mass addendum (it's not a seperate book, just a couple of
    pieces of paper mimeographed), call the State Bookstore in boston,
    and they will tell you the order number, and you can send them the
    $$ - they are quick also (NEC takes credit cards).  Or you can go
    pickup the Mass stuff yourself (better like climbing hills!).
    
    Does the City of Boston have their own?  You say that in Boston
    a licensed electrician is required.  That means Bostons has different
    requirements than Mass, which does not require that (FOR YOUR OWN
    SINGLE FAMILY RESIDENCE). If Boston already has one screwey trist,
    better check with the city (call the inspector and hand him a line
    - he cannot trace the call!) they may have others (GFCIs needed
    for alarm clocks, toaster ovens, and portable jackhammers).
    
291.232Forget breaker-box GFIsALEX::CONNAlex Conn, ZKOWed Jun 10 1987 14:2917
RE: Main box GFIs

When replacing our service after it was ripped out by the hurricane last
year, I asked my electrician about breaker-box GFIs.  He flatly stated
that he would not put them in.  They often fail right out of the carton
or shortly thereafter and only result in dissatisfied customers and
return trips for him.  And they're expensive.  If you're in love with
having a GFI at the main box control a whole circuit, wire an outlet GFI
next to the main box and connect the whole circuit in question to the
protected side (make sure the GFI outlet is rated appropriately; some
are rated for 20 amps, others are only for 15). 

[Actually, the elecrician when pressed *would* put a breaker-box GFI 
in, but the price he felt he would have to charge was approaching the 
cost of the panel!]

Alex
291.233ULTRA::PRIBORSKYTony PriborskyThu Jun 11 1987 13:446
    Re: GFCI on a 3-wire/2-circuit setup:
    
    I'm absolutely positive that the data sheet with the Leviton that
    I put in recently contained explicit instructions for such a setup.
    This GFCI is the one that has screw terminals for all connections
    instead of the usual braided wire that you use with twist-locks.
291.234GFCI breakerVIDEO::FINGERHUTFri Jun 12 1987 12:478
    This is a different GFCI question:
    
    I have a GFCI breaker.  Yesterday it tripped, and now I can't get
    it to reset.  When I move it all the way to the OFF position, it
    doesn't stay there, but goes back to the center.  It will stay in
    the ON position, but there's no power to the circuit.  
    Is it dead?
    
291.235Hidden ResetSWSNOD::RPGDOCDennis (the Menace) Ahern 223-5882Fri Jun 12 1987 19:494
    I've sometimes seen cover plates that cover over the reset button on
    the front of a GFI outlet.  Unscrew the cover plate (if it's one of
    those outdoor outlets with a hinged cover) and press RESET. 
    
291.236GFI'sVIDEO::FINGERHUTFri Jun 12 1987 20:0117
>        I've sometimes seen cover plates that cover over the reset button on
>    the front of a GFI outlet.  Unscrew the cover plate (if it's one of
>    those outdoor outlets with a hinged cover) and press RESET. 

    I know what you're talking about, but no, that's not what I have.
    I have a GFI breaker, not a GFI outlet.  
    What's the test button do on the breaker anyway?  On mine, it doesn't
    do anything.  Is it supposed to trip the breaker?
    
    I assume the breaker is broken.  BTW, that's the second one I've
    gone through.  I'll be replacing it with GFI outlets (I have 2
    outlets each running directly off the breaker, so I assume
    I need 2 GFI outlets?)
    
    Now I know why GFI breakers aren't used much..... While it was
    working, it tripped very often.
    
291.237VIDEO::DCLDavid LarrickSun Jun 14 1987 02:2320
re .21

>    I'll be replacing [a GFI breaker] with GFI outlets (I have 2
>    outlets each running directly off the breaker, so I assume
>    I need 2 GFI outlets?)
    
If you really do have two separate cables running directly from the service 
panel to the two outlets, then yes, you need two GFI outlets (barring some 
re-wiring).  

But if the cables run from the service panel to the first outlet, and then 
from the first outlet to the second outlet, then you only need one GFI 
outlet, to be installed in place of the existing first outlet.

It is possible (and common) to wire a GFI outlet so that "downstream"
outlets are GFI-protected.  It is also possible to wire it so that
downstream outlets are NOT protected - although it makes sense to protect
downstream outlets whether you're required to or not, unless you have some
overwhelming reason for not doing so.  Instructions for both styles of
wiring should come with the GFI outlet. 
291.239GFI breakerVIDEO::FINGERHUTTue Jun 16 1987 15:2316
>    BTW was the breaker ever exposed to the weather, perhaps as part of a 
>temporary service; or a leak during construction?  Did it get itself
>cycled on a regular basis?  Can you tell us the brand?    

    It was never exposed to the weather or used as temporary service.
    BTW:  The one I did use in my temorary hookup also broke after a
    couple months.
    
>    Did it get itself cycled on a regular basis?
 
    What?
    
>    Can you tell us the brand?
    
    Bryant.
           
291.240Preventive maintenance for breakersVIDEO::DCLDavid LarrickTue Jun 16 1987 17:337
>>    Did it get itself cycled on a regular basis?
 
>    What?

Yup, breakers last longer (and are more likely to be re-settable when they 
trip) if they're manually switched off and on periodically.  A couple of 
times a year is plenty.
291.241Mass Electric Code at State Book Store.DELNI::OSTROMAndy Ostrom Networks Mktg. 272-7132Tue Jun 16 1987 21:1717
I stopped by the State Book Store the other day.  They no longer publish the 
"entire" Electrical Code, but just the changes for Mass.  It cost a whopping 
$1.25 (might have been $.75, can't remember).  I'd be glad to make some copies 
for folks -- or if there's enough interest maybe two or three of us could 
divvy it up and type it in.  Then we could put the parts together and add it 
as a note -- it should remain current till 1990.

They also sell lots of other books including a cut-down version of the state 
Building Code with only sections 1 and 21.  These apply to one and two family 
dwellings.  The cost was $7.00 and it came in its own loose leaf binder.


			Andy Ostrom

BTW -- Good luck getting them on the phone -- I tried 3 or 4 times a day for
	a week.

291.190WILD WIRINGTALLIS::SAMARASAdvanced Vax Engineering LTNTue Jun 30 1987 13:2924
It's been a while, but I finally got this electrical problem solved.  
Initially, the problem was excessive voltage drops.  After some 
investigation, I found 3 outlets with NO ground continuity, and 2 with 
backwards polarity. At this point I got suspicious that the previous owner 
did something stupid.  Sure enough, after 2 whole Saturdays of tracing 
circuits, and running up and down to the basement 300 times turning power 
off and on, I found the problems. It seems that the previous owner lowered 
the kitchen ceiling a few years back. Since there was a light fixture in 
that ceiling, he just ran an extension wire from the old ceiling fixture 
to the new lowered one. Pretty stupid: reverse polarity, no ground, wire 
size too small, loose conections, bare wires.  I'm just real happpy I 
found it.  Luckily, the "old box" was directly above the new one, so I 
only had to enlarge the existing opening slightly to do my handy work.
I installed a complete new box at the "new" ceiling level.  All of the 
wiring in that area now terminates in this new box. I'm happy, everything 
works right, and I can use my u-wave in the kitchen!
BTW, I still get a 10V drop in this circuit, but at 10Amps and 200 ft of 
wire, 1 ohm ain't too bad.

I guess the previous owner was proud of his wiring.  After all it worked 
didn't it?  :'))


..bill
291.191Nice workVIDEO::DCLDavid LarrickTue Jun 30 1987 13:458
Congratulations, and thanks for reporting back to us.

A helper and a pair of walkie-talkies or intercoms are indispensable for 
that type of work.

Then again, maybe the  l - o - n - g  walk to and from the breaker box 
makes us take enough time to think over the problem thoroughly, encourages
us to make every test count. 
291.242Horizontal T&G boards over electrical boxes?STAR::SWISTJim Swist ZKO1-1/D42 381-1264Mon Jul 13 1987 17:1523
    I hate writing new notes (2nd one today) but this
    electrical/woodworking combo question seems to be new.
    
    How do you install horizontal tongue-and-groove boards over electrical
    boxes?  This one has me baffled - the 1x8 boards have about a 3/4"
    tongue.  If I cut out the hole exactly where the box is, then I
    can't lower the board onto the one below it because the box is in
    the way, and that's the only way you put t&g boards on. If I elongate
    the hole by 3/4" such that I can press it over the box rim and clear the
    tongue below it before lowering it in place, then the hole is too
    big to seat the ears of the outlet/switch nicely against the finish
    wood (it's also pretty close to being exposed under the switchplate.
    
    I have the same problem even if I straddle the box over a joint
    (upper piece is OK, but lower piece has the same problem).
    
    I suppose I could put the boxes in after the fact (use old-work
    boxes with ears), but I'd sure like to do all my rough wiring first.
    
    Is there some standard solution to this problem?
    
    Jim
    
291.243Installing T&G around electrical boxesSEESAW::PILANTL. Mark PilantMon Jul 13 1987 17:518
    One thing that I have done to install T&G over electrical boxes
    is to cut out the desired size opening, then back bevel the edge
    parallel to the tongue (or groove as the case may be).  There is
    usually enough give in the tongue & groove to allow then to engage
    while still keeping the exposed surface gap to a minimum.  I usually
    use about a 15 or 20 degree angle for the bevel.
    
    - Mark
291.244T&G boards over outletsVIDEO::FINGERHUTMon Jul 13 1987 18:216
    I had the same problem.
    I cut my bottom board to just the right width so that there was
    a T&G joint where all my outlets were.  If 2 boards meet at the height of
    the boxes, you don't have the problem.
    
   
291.245splicing wires in ceilings?REMEDY::KOPECHow did I get myself into this??Thu Jul 23 1987 14:4921
    In order to install some skylights, I need to move a couple
    of wires out of the way.. unfortunately, the wires themselves are
    too short to be routed any way other than the current routing.
    
    So, I have a couple of choices:
    
    1.) replace the wires from source to destination. This would be
    a bear to do; I'd have to remove and rewire 6 nailed-to-the-studs
    boxes (some double-gang), snake wires through walls with blocks
    in them, etc... 
    
    2.) stick some junction boxes up in the rafters and splice. Sounds
    rational, but it seems to be a technical violation of the Code
    (junction boxes must be accessible without removing any of the
    building, 370-19).  
    
    I can't believe that Joe Contractor would go through all the hassle
    of (1). Do people really do (2) and nobody cares, or is there a
    special method of splicing in concealed spaces?

    ...tek
291.246Access panelVIDEO::DCLDavid LarrickThu Jul 23 1987 15:205
One possibility is to put the splice boxes behind an access panel.  If you'll 
be putting fancy trim boards around the indoor skylight opening, make one of
those trim boards removable, and hide the boxes behind that.  Or, if you'll 
have a light shaft through the attic, you can put the access panel up in a
side wall of the light shaft. 
291.247$8 coversVIDEO::GOODRICHGerry GoodrichMon Jul 27 1987 14:4716
    I mounted a smoke detector over my junction box, it looks
    like it belongs there. I didn't need another smoke detector
    but it solved the cosmetic problem.
    
    This situation may need two splice boxes, two smoke detectors
    might look a bit silly, any chance you can have a removable
    piece of trim somewhere?  In the spirit of the code, a stranger
    should be able to find it.
    
    Once I did cheat and covered a splice. I soldered the wires
    and  carefully insulated them.  This was as close as I could
    get to an "unspliced" joint.
    
    - gerry
    
291.248exTALLIS::SAMARASAdvanced Vax Engineering LTNMon Jul 27 1987 18:0311
I recently remodeled a bathroom, and part of the renovation was alot of 
rewiring. The electrician said that I'd have to have access to the old box 
in the ceiling. I wasn't too pleased about having an access cover in the 
middle of my new ceiling, but I went along with it.

Anyhow, a few weeks ago I discovered a wierd wiring problem left over 
from the previous owner/hacker.  After tracing wires all over the place, I 
*needed* to get at the bathroom connection to test the circuit.

I was VERY tempted to bury that box; luckily I didn't.  It doesn't bother 
me much any more....
291.249Splices? We don't need no steenking splices!JOET::JOETTue Jul 28 1987 14:153
    You could always pull another wire of the proper length.
    
    -joet
291.250the code is for standard constructionNRADM2::MITCHELLgeorge..ya snooze - ya loseWed Jul 29 1987 15:178
    
    	Add the length of wire needed to get them out of the way,
    	add the necessary boxes to house the splices, solder the 
    	connections and use "wire nuts" on top, tape them if you wish
    	and bury them....no problem. Re-running new wiring is out
    	of the question. you'd be tearing the house down to do it.
    
    				___GM___
291.251this hurts my psyche, but...REMEDY::KOPECJoe Isuzu for President!Wed Jul 29 1987 15:4416
>      	and bury them....no problem. Re-running new wiring is out
>    	of the question. you'd be tearing the house down to do it.

    yes, this is exactly the problem; I'd have a few days of sheetrock
    work if I wanted to run new wires; the wires are stapled (so I can't
    pull a new wire through with the old one), and the walls have blocks
    in them, so I can't snake... plus, the boxes are all new-work boxes
    that won't come out without a fight (read: rip and patch sheetrock).
    
    I guess I don't feel too bad about doing a concealed splice; it's
    not a junction (where I might need to get into test some part of
    the circuit), it's just a striaght-thru splice.. 
    
    time to close my eyes....
    
    ...tek
291.252AUTHOR::WELLCOMESteveWed Jul 29 1987 17:095
    HOWEVER:
    
    No matter HOW you do it, an inaccessible splice is against the code.
    
    If you still go ahead and make one, at least put it in a box.
291.253PHENIX::CONNELLHa..I'd like to meet his tailor..Wed Jul 29 1987 18:2111
>    HOWEVER:
>    No matter HOW you do it, an inaccessible splice is against the code.
    
ALSO:

	Should (God forbid) you have a fire, and the splice be (or even
suspected to be) the cause, your insurance could be negated.

	Is it worth the risk?

						--Mike
291.254More creative solutionsVIDEO::DCLDavid LarrickThu Jul 30 1987 12:5232
I'm surprised that none of the preceding suggestions was practical.  Here
are a couple more, mostly obvious ones, mostly inspired by Gerry's smoke 
detector.  Sometimes you gotta do what you gotta do, but I urge you to
think hard one last time about alternatives. 

1. Attach a lamp to the workbox, either recessed or hung from the ceiling.

2. A track light power feed.  You don't need to install the track light;
   having the power feed there makes it look like there used to be track
   lighting, or like you're planning for future track lighting.

3. Just a duplex outlet.  Good conversation piece.  Explain that it's for 
   Christmas lighting, or for your roof heat cables.  (Doesn't have to be 
   true...).

4. Don't put a switch up there.  Code calls for switches to be within some 
   distance from the floor, something like seven feet.

5. There exist blank box covers that are meant to be unobtrusive in
   ceilings, to cover up now-unused boxes or as placeholders for future 
   lamps etc.  The ones I've seen are round and white.

6. Use a regular blank box cover, carefully install it flush with the 
   ceiling, and paint over it.

It sounds like whatever you do will be near the new skylight.  Thus it's 
more likely than your average electrical work to be exposed to water
problems, and to structural weirdness as your skylight framing settles 
under load.  And if you bury this work on the roof side of the attic 
insulation, it'll also be exposed to more temperature variation (and, 
again, moisture) than usual.  My point is that, if I HAD to bury a box 
someplace, this is not the location I would choose.
291.255ALUMINUM WIRING QUESTIONSVRTMP1::SMICKVan C. SmickTue Aug 25 1987 22:3421
    Since there is no note on aluminum wiring, I'll start one.
                                                 
    I have read several notes on the hazards of using aluminum (AL) wiring
    in the house. I have not seen anything on AL wires on lamps, appliances
    etc.                                                    
                                                            
    SPECIFICS:                                              
                                                            
    I have a clear glass lamp and I want to use the "clear" decorative
    wiring sold in many hardware stores. After purchasing it and cutting 
    it to size, I suddenly noticed that the wire is AL. The light 
    socket has screw connections (one copper, one AL), and the plug
    I used is the clip on plug -- which has brass connections.
             
    QUESTIONS
    
    Is there any danger in using AL wire?
    Is there any danger in mixing the copper of the light socket and
    plug with the AL wire? If so, are there AL light sockets and plugs?
    
    
291.256STAR::GOLDSTEINAndy Goldstein, VMS DevelopmentTue Aug 25 1987 23:105
Are you sure the wire is AL? Never heard of aluminum wire being used
in light gauge cord. I'll bet it's tinned or plated copper. Strip some
insulation and scrape the wire with a knife a while. If it turns reddish
it's copper. If it's real soft and stays silvery white, it's AL and I'd
throw it out and get some clear insulation copper wire from Radio Shack.
291.257DICKNS::WELLCOMESteveWed Aug 26 1987 22:452
    I'll also bet on the tinned copper.  Virtually certain.  99.99999%.
    
291.258YEP -- All that glitters is not goldDSTAR::SMICKVan C. SmickThu Aug 27 1987 11:401
    You were right. Thanks I can sleep easy now.
291.172More wiring help pleaseRECKON::GONYEOMon Aug 31 1987 14:4115
I have a situation similar to that described in .0 but I really dont
want to run the power to the switch first (as recommended in .3).  The
switch is on a finished wall and there is only one wire going to it now.

My question:  what is the correct wiring configuration?

      Power                                                       Dimmer
      Source  ==================================================  Switch
                    ||             ||              ||
                    ||             ||              ||
                |-------|       |-------|       |-------|
                | Light |       | Light |       | Light |	
                |-------|       |-------|       |-------|

	Thanks.   Jim
291.173simple series hookupTOOK::CAHILLJim CahillMon Aug 31 1987 16:5030
    I don't understand your comment about "... there is only one wire
    going to it now."  I'm assuming you mean one cable, containing three
    wires (black for hot, white for neutral, and bare copper for the
    ground).
    
    If the wiring is indeed as shown in your diagram, wire each light
    up like this (for simpicity, the grounds are not shown; they should
    be connected together, as well as to each junction/switch box):
    
                             (junction box)
                      +------------------------------+
    >>>===============|------------------------------|===============>>>
     (power in from   |\    (white neutral wire)    /|   (power out to
      source or pre-  | \                          / |    next light or
      vious light)    |  \    (black hot wire)    /  |    dimmer switch)
                      |   \_________    _________/   |
                      |             |   |            |
                      +-------------|---|------------+
                                    |   |
                                <out to light>
    
    At the dimmer switch, just connect the two leads of the switch to
    the black and white wires.  If the switch has screws instead of
    leads, the black wire goes to the brass screw while the white wire
    goes to the silver-colored screw.
    
    P.S.  I'm assuming your switch can handle the load of the three
    lights... you should not!
    
    Jim
291.174Yes, I know....TOOK::CAHILLJim CahillMon Aug 31 1987 16:588
    Obviously, the disadvantage of this wiring circuit is that if one
    lamp burns out, they all go out (since the blown bulb breaks the
    looped circuit to the other two).  Because you don't want to or
    can't run the power to the switch first, this is the price you have
    to pay.  Since there's only three lamps on the switch, it shouldn't
    take too long to find the burned out bulb.
    
    Jim
291.175Smells badTALLIS::SAMARASAdvanced Vax Engineering LTNMon Aug 31 1987 17:469
Can you run power to the "last" light box first?  Then you could connect 
the switch and power the remaining lights from right to left (per your diagram).


I'd avoid series lighting at ALL costs.  I'd go to the dentist before I'd 
do a series wire.  Besides, each light will be 1/3 as bright.


...bill
291.176a small piece of 14-3 would be required...3D::WHITERandy White, Doncha love old homes...Mon Aug 31 1987 18:3736
RE:1047.4 

>I have a situation similar to that described in .0 but I really dont
>want to run the power to the switch first (as recommended in .3).  The
>switch is on a finished wall and there is only one wire going to it now.

	Jim
		I assume that what you currently  have is this.

      Power   -------------------------------------------------- Dimmer
      Source  ---------------------- --------------------------- Switch
                                   | |              
                                   | |              
                                |-------|
                                | Light |	
                                |-------|

	If you don't want to rerun the entire leg but can get at the middle
	section you could wire it thusly (grounds not shown for clarity):

           14-2                                          14-2
         Existing              New 14-3                Existing       Dimmer
             <--|                                      |-->           Switch
                                       BLK
   Line   BLK ---x-------------------------------------x-------- BLK Line
  Neutral WHT -----x---------------x----------------             
                   |               |   WHT         | 
                   | --------------|-x-------------|-x---------- WHT Load
                   | |             | | RED         | | 
                   | |             | |             | |
                   | |             | |             | |
                |-------|       |-------|       |-------|
                | Light |       | Light |       | Light |	
                |-------|       |-------|       |-------|

	Good Luck
291.177RECKON::GONYEOTue Sep 01 1987 15:5226
Thanks to all that responded.  Re .8, one clarification question.  Which
WHT wire (the neutral or the load) goes to which wire (WHT or BLK) on
the lights?

           14-2                                          14-2
         Existing              New 14-3                Existing       Dimmer
             <--|                                      |-->           Switch
                                       BLK
   Line   BLK ---x-------------------------------------x-------- BLK Line
  Neutral WHT -----x---------------x----------------             
                   |               |   WHT         | 
                   | --------------|-x-------------|-x---------- WHT Load
                   | |             | | RED         | | 
                   | |             | |             | |
                   | |             | |             | |
                |-------|       |-------|       |-------|
                | Light |       | Light |       | Light |	
                |-------|       |-------|       |-------|

Re: .7, could you explain why you do not like this type of wiring?  I
do not understand why each light would be 1/3 as bright.

Re: .5 - .8, all assumptions are correct.

	Thanks.  Jim

291.178clarifications ...3D::WHITERandy White, Doncha love old homes...Tue Sep 01 1987 16:1938
RE:1047.9 

	Hi Jim,

> Re .8, one clarification question.  Which WHT wire (the neutral or the load)
> goes to which wire (WHT or BLK) on the lights? 

           14-2                                          14-2
         Existing              New 14-3                Existing       Dimmer
             <--|                                      |-->           Switch
                                       BLK
   Line   BLK ---x-------------------------------------x-------- BLK Line
  Neutral WHT -----x---------------x----------------             
                   |               |      WHT      | 
                   | x-------------|-x-------------|-x---------- WHT Load
                   | |     RED     | |    RED      | |            ^  
                   | |             | |             | |           /   
                   | |             | |             | |        This wire should
               WHT | | BLK     WHT | | BLK     WHT | | BLK    have black tape
                |-------|       |-------|       |-------|     wrapped around 
                | Light |       | Light |       | Light |     the white plastic
                |-------|       |-------|       |-------|     to indicate it
                                                              is a hot line.

>Re: .7, could you explain why you do not like this type of wiring?  I
>do not understand why each light would be 1/3 as bright.

	.7 illustrates a series connection of lights, like the old christmas
	strings.  In a series connection with equal loads the total available
	voltage will be proportionately divided against the loads.  In the
	illustration shown 1/3 or approx. 40 volts.  The current in this
	configuration will be the same for all loads.

	In the illustration above the lights are wired in parallel though 
	each will have its own current draw, they will all have the same
	voltage across the load.

	Hope this helps - Randy
291.179LOOKS good now!TALLIS::SAMARASAdvanced Vax Engineering LTNTue Sep 01 1987 22:365
RE:.5 and RE:.6 assume series wiring which isn't cool.   The last 
reccomendation is a parallel connection wich is fine (that's what I'd 
do).  Each light has a direct shot to the power line.

...bill
291.180forget series, go with parallelTOOK::CAHILLJim CahillWed Sep 02 1987 13:476
    Re .11
    
    Yup, I agree....  Although a little more complicated, it does avoid
    the problems with series wiring.
    
    Jim
291.265Confused Ground or Grounds for Confusion...SAWDST::PAQUETTEColonial Computing NutWed Nov 25 1987 14:2119
  I'm confused about electical grounding!  

  I have an OLD house that has a NEW 100A service.  The feed in has the ground
  wire attached to the "GROUND BAR" like what I expect.  Some of the house 
  circuits are TWO wire with NOGROUND and others are THREE wire.  On the
  THREE WIRE circuits the BLACK (hot) is connected to the circuit breaker but 
  the WHITE and BARE wire are attached to the same point on the BAR??

  Is this some MICKEY_MOUSE wiring setup or what??

  I want to splice some THREE wire onto a TWO wire circuit running out of a
  light fixture.  What do I attach the ground wire to??  The WHITE ??

  If I didn't have to face snaking wire around/throught 10" beams,  I'd
  rewire the whole thing from scratch with THREE wire but....

  Can anyone shed light on what's going on here....

						-=Dennis
291.266separate but equal paths to groundCIMNET::LUNGERDave Lunger, 291-7797, MET-1/K2Wed Nov 25 1987 14:3813
What you see is correct.  The three wire circuit gnds connect to the same point
electrically in your panel.  The idea though, is that at the other end
of the circuit the white or neutral wire is your normal path to ground...
there will be current in this wire.  The ground wire is a separate (but
basically equal) path to ground for things like chassis, metal parts on
appliances that get handled, etc. This does not carry current.  If there
should be a short, the ground wire will safely carry the current to ground.

I believe that GFCI's somehow use this to work... ie: if current goes thru
the ground wire, the circuit trips and/or if current in white wire does
not equal current in black circuit trips... I'm not sure of this, but it
works something along those lines...

291.267Be CarefulCASSAN::OLSONC. JOHN OLSON DTN: 297-5344Wed Nov 25 1987 14:4714
    The tying of the White(AC low) to the Bare Ground wire is common
    in three wire house wiring.  They are trying to make them at the
    same Power Reference Point.
    
    As for connecting or tapping power from a light fixture, be careful.
    If the Black(AC High/Hot) is being switched, then you could have
    a Amperage problem for the circuit that you are trying to create.
    The switch can be your weak link for the circuit.  Always verify
    your source when tapping into another box.
    
    What are you trying to power off this light fixture??
    
    
    		John
291.268grounds for confusionYODA::BARANSKIToo Many Masters...Wed Nov 25 1987 15:0363
I've always been confused about electrical service grounding... and I'm supposed
to be an electrical engineer! :-)

The way I understand it, there's this here wire with you on one end, and the
electrical company on the other end.  There may also be God only knows howmany
transformers on the wire between you and the electrical company, but I'm
confused enough as it is, so I'll skip that part.

Anyway, you have this here wire from the electrical company, and it's *hot*,
electrically speaking.  Now there's a couple of other wires that come into your
house from the electrical company, but basically they are there so that you
think that you are getting more for your money from the electrical company and
electricians.  

Only one of the extra wires has any meaning, it's the opposite phase of the
*hot* wire from the electrical company.  I think it's the electrons the
electrical company sold you last month, or something.  This wire is for when the
electrical company wants to sell you more electricity, and rather then replace
the wire you already have with a bigger one, they give you two wires, and charge
you twices as much by selling you the electrons twice.

One of the other extra wires simply goes out to your telephone pole, and goes
into the ground, in other words, it's grounded.  Ah Ha! you say, that's where
the ground is, right?  Wrong!  There's a half dozen or so grounds, and this is
only the first one. Again, these extra grounds are to make you feel like you are
getting your money's worth.  All these grounds go into the ground, and a bunch
of wires tied to a common point all have the same voltage, right?

So then you have two or three or more (I'll forget about the other wires if you
will) wires coming into your house.  Now they start putting colors on the wires
to confuse you.  They call one wire "white", and one wire "black". The "white"
is supposed to be the *hot* one, but that doesn't mean anything at this point,
because you can get the blue spark fairy to come forth from either one of them,
so just forget about that distinction. 

Usually close to where your wire come into your house, there is a fuse or
breaker box.  Here they add another wire, and call *it* ground, too.  This wire
usually doesn't have any insulation put on it; the electricians save money this
way, and immediately pass the savings on to their bank accounts.   This wire
also goes into the ground, so I suppose they have a good reason for calling it a
ground, but what did they do to that perfectly good ground that they had? Nobody
knows, all I can tell you is that it's ruined, forever, and ever.

Now you have three of four or more wires (see above...) that you run all over
your house.  Now the electrical code is written by electricians, for
electricians, to make money...  that is why the code says that you have to have
an outlet every six feet of wall.  Sheeash, you'd think they never heard of
extension cords.

Eventually, all these wires go to a box in the wall that you can stick a plug
into (or your fingers) to get electricity out of the wall.  And this plug goes
to a cord that goes to a transformer, and a power supply, and there is another
entirely unassociated ground on the other side of the power supply. This is my
home territory, where I went to school, where the electrons and grounds behave
as the laws of nature and God intended them to.   

But wait... there's three more grounds here: ground, chassis ground, and
floating ground!!!  AAAAAARRRRRGGGGHHHHhhhhh...... <silence> <except for a few
whimpers> 

Jim.


291.269DICKNS::WELLCOMESteve Wellcome (Maynard)Wed Nov 25 1987 15:4920
Re: .3
>to confuse you.  They call one wire "white", and one wire "black". The "white"
>is supposed to be the *hot* one, but that doesn't mean anything at this point,

    NO!  The **BLACK** wire is hot, the ***WHITE*** is neutral.  
    
    Re: .0
    
    Yes, the neutral and ground get tied together at the service entrance,
    AND AT THAT POINT **ONLY**!!!  Do NOT connect them together anyplace
    else.  You cannot ground boxes, outlets, etc. on your 2-wire circuits.
    According to code, for a 2-wire circuit with no separate ground
    wire available, you're supposed to use only 2-prong sockets (without
    the hole for the grounding prong on a 3-prong plug).  That's to
    keep somebody from thinking an applicance with a 3-prong plug is
    grounded just because he plugged it into a 3-prong outlet.  If you
    want a grounded outlet on a circuit that is currently 2-wire, you'll
    have to run a new line from the service entrance and rewire that
    circuit.
    
291.270Ground is ground the world around ???TOOK::ARNWed Nov 25 1987 15:598
    
    I'm glad someone came out of the closet. I was always embarrassed
    that I was an Electrical Engineer and could not explain it either.
    I'm convinced it's a secret and they tell you when you get your
    electrical license or something.
    
    Tim
    
291.271DICKNS::WELLCOMESteve Wellcome (Maynard)Wed Nov 25 1987 16:0729
    Re: .0 again
    
    You shouldn't splice 3-wire onto a 2-wire circuit, because you can't
    ground it properly.  Either go all the way back to the service
    entrance with 3-wire, or extend the 2-wire circuit with 2-wire.
    You can probably use 3-wire and just clip the ground wire short
    so it's obvious that it's not to be used, but I'm not sure about
    that.
    
    Is the present wiring BX (armored cable)?  If so, the metal armor
    may be grounded.  HOWEVER, it may not be an acceptable ground
    according to the code.  If it's BX and IF it has an internal metal
    strip inserted inside the sheathing (like a wire, only it's sort
    of flat), then you can use the sheathing as a grounding path.  If
    there is no metal strip, then the sheathing is not acceptable as
    a grounding path and you must treat the circuit as a 2-wire circuit.

    Assuming the metal strip is there, you should be able to connect
    the ground wire of your 3-wire cable to the junction box where you
    are making the splice and continue from there.  However, I am a
    little hazy on the details here, and that may not be correct.
    
    To explain things a bit further, BX cable, by itself, has a relatively
    high resistance.  It's steel, which is not all that great a conductor
    compared to copper, and the spiral construction doesn't provide
    a very good ground path exept around and around and around and
    around...the spiral.  Hence the inserted metal strip; it runs linearlly
    inside the armor sheathing and provides a ground path of acceptably
    low resistance and good reliability.
291.272I have seen the light....SAWDST::PAQUETTEColonial Computing NutWed Nov 25 1987 16:2416
	WOW!!! Thanks for the plentify and rapid response!

  There is TWO wire running from the panel to a "pull_chain" light fixture.
  A piece of BX cable is spliced to the two-wire coming into the light and
  runs to another "pull_chain" light fixture in another room.

  I want to replace the OLD fixtures (can't find globes to fit them) with
  NEW pull_chain fixtures and since there are only two lights on the entire
  20A circuit, I'd like to tap off the line and add 4 outlets (2 in each room)

  I think I'll use three-wire for the outlets and tape up the ground for now.
  After the holiday crunch, I'll go back and feed new wire from the panel...


						-=Dennis
291.273Is the box big enough?VIDEO::DCLDavid LarrickWed Nov 25 1987 16:516
When you "tap off the line", be sure the box from which you do so is big
enough to hold the additional wires and wire nuts.  Cramming too many
things into too small a box is difficult, dangerous, and contrary to Code. 

I trust your "20A circuit" uses 12-ga. wire in addition to having a 20A 
breaker.
291.274what the power company gives youTOOK::CAHILLJim CahillWed Nov 25 1987 16:5360
    The difference between grounds (chassis, equipment, safety, etc.)
    may be confusing, but what it boils down to is this:  there should
    be only one point in an electrical system where all the grounds are
    brought together and joined.  This avoids something known as ground
    loops.
    
    First, what the wires are....  Most houses have three wires coming
    off the pole:  two insulated wires and a bare wire.  They usually
    appeared to be all twisted together, but in some localities may
    be seperated.  Older houses that do not have 220 volt service have
    only one insulated and one bare wire; the reason why will hopefully
    become apparent after reading the following.  If you measured the
    voltage on the bare wire by putting your meter between it and "ground",
    it should read close to if not 0 volts.  The other two wires contain
    110 volts measured relative to the bare wire (meter probes placed one
    on the bare wire and one on either of the two other wires).  However,
    a meter placed between the two insulated wires will read 220 volts.
    This is because the voltage is constantly switching back and forth
    between positive and negative phases; when one wire is at +110v, the
    other is exactly 180 degrees out of phase, or -110v.  Remember the
    old sine wave??
    
    These three lines are brought through the meter and into a circuit
    or fuse box.  The bare wire gets connected to a copper bar containing
    many connection points, while the two "hot" wires go through a double
    (a.k.a. ganged) main breaker.  Notice that the bare wire does not
    get interrupted by a breaker; this is an important safety feature!!
    Once through the main breakers, the two hot lines feed both single
    110v circuits and larger capicity 220v circuits.
    
    The larger circuits that feed electric dryers, hot water heaters,
    and stoves contain both a red and a black wire (along with one or
    two others:  a white and possibly a bare).  The black wire gets
    attached to one of the two insulated feeds from the power company,
    while the red wire goes to the other insulated feed.  The smaller
    110v circuits contain only a black wire, in addition to the white
    and bare wires.  This can go to either of the above two feeds, but
    the system as a whole should balance the load drawn from each feed
    as closely as possible (it makes the power company very happy by
    causing less wear and tear on their equipment!).
    
    Every electrical circuit contains a white wire.  These get connected
    to the bar containing the bare feed wire.  If the circuit also has
    a bare grounding wire, that too gets connected to this bar.  This
    bar is also attached to a good ground point, either a cold water
    pipe coming into the house, a grounding rod driven several feet into
    the ground, or a cable that's buried along the foundation.
    
    In the simple case where's there's only one fuse/breaker box, the
    white and the bare wires are tied together and grounded.  It gets
    more complicated when there are multiple fuse/breaker boxes.  In
    this case, the white and bare wires should not be joined together
    in the secondary distribution boxes, but attached to seperate bars
    that are isolated from each other.  But that's another story.
    
    I hope this clears up the confusion about what the lines coming
    from the power company provide you.  Sorry if this has been boring
    for any other power distribution junkies!
    
    Jim
291.275fingers engaged before brain....TOOK::CAHILLJim CahillWed Nov 25 1987 16:599
>    two others:  a white and possibly a bare).  The black wire gets
>    attached to one of the two insulated feeds from the power company,
>    while the red wire goes to the other insulated feed.
    
    Least anyone misunderstand what I wrote in .9, the red and black
    wires must go through a double breaker (and the main breaker) before
    they connect to the main power company's feeds.

    Jim
291.276Like water pressure?AKOV75::CRAMERWed Nov 25 1987 18:1538
    re: .9
    
    	I understand, I think, what you, and others have said, I have
    just one question left concerning the original scenario.
    What is the problem with connecting the ground and neutral (white)
    wires to the neutral wire of the existing 2 wire circuit?
    It seems that the net effect will be the same.
    

    				       +-- junction box
				       V    
 neutral bar in box - old white ooooooo+oooooooooo new white - fixture
   					\________________ ground
    
    
	versus a complete three wire circuit
    
        
 neutral bar in box -oooooooooooooooooooooooo new white - fixture
		     \_______________________ ground
    
    With your comment on "ground loops" I can only assume that in the
    former circuit the electricity which should go all the way from
    the fixture, at the end, to the neutral bar (and thence to ground?)
    will "loop" back TOWARD the fixture from the connection at the
    junction box, probably because the resistence on the old white
    wire is higher than the new white or new ground, depending on which
    wire (white or ground) is carrying the current.
    And the reason that this doesn't happen in the three wire circuit
    is that the neutral bar (aka ground) is the path of LEAST resistence.
    
    
    Or am I totally lost?
    
    Alan who had an electrician wire the new range outlet
    
    
    
291.277Do it right, it's more painful to do it overARGUS::CURTISDick 'Aristotle' CurtisFri Nov 27 1987 02:2518
    .8:
    
    If I read the code synopsis book correctly, the minimum acceptable
    box for an outlet with 2 12-3 cables (i.e., a daisy-chained set
    of boxes) will be the size that's about 3 1/2 inches deep
    (approximately the depth of a planed 2 x 4 -- we ran into a bit
    of hassle with the screws going a little beyond the 2 x 4, and hitting
    foundation).  It was an annoyance to discover that I'd bought
    about 8 boxes that were too shallow, but at least the ones of the
    correct size allow you to fold the wires and push them and the outlet
    in without being a Hercules.
    
    If you're getting the boxes at Spag's, look for the deeper of the
    two sizes of metal boxes (don't know what the measurements are for
    the plastic ones, which I thought I saw recently).
    
    Dick
    
291.278Richter's near Nashua??FREDW::MATTHESFri Nov 27 1987 10:224
    I've seen the book 'Richter's'  touted here and elsewhere in this
    file.
    
    Anyone know where I can obtain a copy near Nashua N.H. ??
291.279grounding.MRMFG1::J_BORZUMATOMon Nov 30 1987 13:2610
    dennis, your 100a service hook is fine. its wired correctly.
    you should also find a ground going to the incoming water line.
    or perhaps a ground rod. (make sure one of them is there)
    we're in the same boat when it comes to old houses. mine
    is 100 yrs +????. i have the old "knob and tube" in some places.
    my wifes uncle is an electrician, he tells me the knob and tube
    is good wiring and to leave it alone, or replace it.
    in your last question are you saying you are looking at a light
    fixture that has only one wire????
    jim
291.280DICKNS::WELLCOMESteve Wellcome (Maynard)Mon Nov 30 1987 13:5911
    Re: .11
    >It seems that the net effect will be the same.
    
    Yes, it does, doesn't it?  However, doing what you suggest is
    absolutely positively NOT permitted by the electrical code.
    The problem is "ground loops" as you suggest.  I'm somewhat vague
    about the exact details of the phenomenon, but I seem to recall
    a note in this file someplace that did an excellent job of explaining
    ground loops and why they are A Bad Thing To Have.  
    Do it right, do it according to code; that's what separates competent
    do-it-yourselfers from house butcher do-yourself-iners.
291.281So what is a ground loop? :-)YODA::BARANSKIToo Many Masters...Mon Nov 30 1987 20:020
291.282better Nate than lever?REMEDY::KOPECHuh?Thu Dec 03 1987 18:0225
    The reason you can't just connect the white and bare conductors
    together is that the voltage drops along the white wire will get
    connected to the case of the washing machine that's sitting in a
    puddle in your basement (or the case of that electric drill, etc...)
    the "equipment grounding conductor" is kept separate to keep these
    voltages in line...
    
    (as he scratches the back of his brain) The rules for outlets on
    2-wire circuits are:
    
    a.) Can't add a new, non-grounding (2-prong) outlet. 
    b.) existing non-grounding outlets are to be replaced with
        grounding (3-prong) types unless there is no way to provide
        the ground (see the BX-discussion a few replies back..)
        (you can install a GFCI, but you can't extend a new ground
        from it.)
    c.) NEVER, EVER install a grounding outlet without a proper
        ground. This is serious stuff, here... people have been killed
        by violations of this rule.

    houses with 2-wire circuits are not fun, unless you are an electrician;
    then they pay for your kid's education.
    
    ...tek
    
291.967Plastic vs Metal boxesNETMAN::SEGERthis space intentionally left blankMon Dec 07 1987 17:3510
I'm surprised this wasn't listed already, unless it's buried under some 
unrelated topic as much of this stuff is...

Is there any general opinions about metal vs. plastic boxes?  It seems that in
almost any new construction I see that everyone uses plastic, yet SPAGS only
carries metal.  In fact, one can get plastic boxes virtually anywhere cheaped
than the metal boxes at Spags.  My thought is if plastic is better than metal,
why would Spags even bother carrying the metal?

-mark
291.966NOT at the FISH & TACKLE counterCHART::CBUSKYMon Dec 07 1987 18:2919
    SPAG'S DOES carry the plastic! But you do have to look for them, they
    are hidden, believe it or not, in the ELECTRICAL DEPARTMENT. 
    
    They have a trash barrell FULL of the single boxes in the back row near
    the door bells. They list for $.33, the same as I've seen in other
    stores, but at least they're not MORE. The doubles are in the same row
    as some of the metal work boxes (middle row). I don't remember the
    prices of them or the availibility of the triple boxes. 
    
    I prefer the plastic boxes for new work in the single size. 
    
    The double and especially the triple are too flimsy for my liking. My
    experience with the triple has been when you mount the box on the stud,
    the box does not remain square but rather takes on a trapazodal shape.
    The switches and the switch plate then are mounted on a slant and look
    like S#%T. I'll stick with the metal boxes for the few places that
    require more than a single.
    
    Charly
291.9653D::BOOTHStephen BoothTue Dec 08 1987 10:169
    
    	Plastic boxes suck, they are brittle and snap very easy and
    I have never seen a pro use one ! If you screw them down too tight
    or you nail them in too hard or you tighten the cable clamp too
    much and SNAPPPPPPPPPPPPPPPPPP!
    
    	-Steve-
    
291.296Two appliances on one 220V circuit with toggle switch?GLIVET::RECKARDJon Reckard 264-7710Mon Dec 21 1987 11:337
    Can two 220 appliances (range, dryer, (is a dishwasher 220?)) share one
circuit?  The arrangement I have in mind would put a toggle switch of some
kind in the loop, enabling one appliance and disabling the other.  (This
is in a full-circuit-breaker-box-type-house.  And I'm not including any
baseboard heat in the loop.)
    It shouldn't be too hard to plan certain non-meal times to use the
dryer - just flick the switch.
291.297CHART::CBUSKYMon Dec 21 1987 12:2217
    
    
    
    
                               ??? WHY ???
    
    

    
    
    Even if there aren't or weren't any code restrictions it is generally a
    not a good idea to do something that is too far from what most people
    would consider normal. Future owners (and who ever does the laundry and
    cooking in your house) will curse you 'till the day you die and then
    some. 

    Charly
291.298shared 220vNSSG::FEINSMITHMon Dec 21 1987 12:238
    Considering that the dryer would have a 30 amp or 40 amp connector,
    you're talking quite a large switch(a transfer switch would do the
    job quite well, but be rather expensive). A big question would be
    the electrical code in your area. Unless the two locations are near
    each other, you may be better off running two separate circuits,
    once the cost of everything is considered.
    
    Eric
291.299ULTRA::PRIBORSKYTony PriborskyMon Dec 21 1987 12:254
    Someone with the code book handy could comment, but I think these
    heavy appliance circuits must be DEDICATED (that is my recollection
    of reading the code at the library).   DEDICATED means NOT SHARED,
    so you can't do it...
291.300There's gotta be another wayVIDEO::DCLDavid LarrickMon Dec 21 1987 12:367
I agree with the other replies - your proposed scheme is inconvenient, requires 
an expensive switch, and is probably contrary to Code.  There are likely to be 
better ways to share capacity and free up breaker-box slots.

But if you're still considering this option, check with your local wiring
inspector _before_ buying the materials or investing substantial planning time.
291.301BSS::HOEThe Rockies lets you come higher.Mon Dec 21 1987 14:2911
    Not all 220VAC appliances are the same. A/C compressors are 220V
    only while stoves and dryers uses the neutral for the 110V timer
    and lights.
    
    Though some places allows for aluminium wires, get the copper if
    you can afford the copper. I had thought about using the 220V line
    to the A/C from the old stove plug since I converted over to gas
    stove. The cost of the connectors and stuff made running the line
    from the C/B box more feesible.
    
    /cal
291.302Not a real good ideaWORDS::DUKEMon Dec 21 1987 15:158
    The dryer has a 30 amp. plug and the range has a 50 amp.  Feeding
    the 30 amp. receptacle with a 50 amp. breaker is a code violation.
    Feed the 50 amp. w/ a 30 amp. breaker and you risk tripping the
    breaker if all of the range units are on.  Not a real good idea
    at best.  Run two separate circuits.  You will be much happier in
    the long run.
    
    
291.303horse into a camel??AIMHI::BERNARDMon Dec 21 1987 16:2314
    This little project you have conjured up is really turning a horse
    into a camel.
    
    -1 is absolutely right, you are violating basic wiring rules, and
    the standard electrical code (for MA I'm sure).
    
    It will take less time, effort and money to just run 2 separate
    lines. Otherwise, you will need a switch, heavy duty relay for the
    poser, indicator lights, have to run wire to the receptacles anyway.
    
    Enough said
    
    JMB
    
291.304Let me try againGLIVET::RECKARDJon Reckard 264-7710Tue Dec 22 1987 11:1414
    Well!  I didn't expect to get my head bit off!
    Just kidding.  These responses comprise a perfect example of the benefit
of Home_work.  Thanks.  Now, just one more peep, and I'll be quiet.
    We have a 3-family house and inadequate wiring (I mentioned our full circuit
box, I neglected to mention its capacity - 100 amps! - that handles 3 range
circuits, 1 dryer circuit, and one room's electric baseboard, with only two
tripped circuits in 4 1/2 years - one of my first projects was separating two
ranges that shared 1 circuit!).  Before we inherited a dryer, one of our tenants
started using the one dryer hookup, in a central hallway.  OK with us.  And then
I started wondering why couldn't we share the one circuit.
    So, adding another circuit is out (unless we add another 100 amps - $$$$).
Sharing a 50-amp device with a 30-amp (or whatever) isn't a factor.  And, I'll
check out the dedicated aspect with the town/state codes (NH).
    One reply listed 4 or 5 things I'd need, even if it was legal.  More info?
291.305don't be a fool!!!AIMHI::BERNARDTue Dec 29 1987 16:3032
    
    I've run into many situations like yours and all of them have scared
    the daylights out of me. I was looking at a house once and the owners
    had an air conditioner attached to small extension cord. I mentioned
    the potential hazard to the owner and they laughed. I was going
    to show them how the cord would crack from heat, but when I touched
    it, ALL of the insulation fell off in my hand, there was a big spark
    and the owner almost fainted.
    
    I know you mentioned that $$$$ was an issue, but 100  amps for 3
    families is VERY dangerous. You should get quotes from local
    electricians for running 100 amp services for each appartment and
    then have a detailed inspection done of the wiring. For me it's
    more than $$$$, but's it piece of mind and the safety of my family
    and possesions that's important. Electrical fires are very common,
    expecially when heating and old or inadequate wiring are involved.
    
    I wouldn't use "only 2 tripped breakers in 4 1/2 years" as a comfort
    indicator. What you may have is damaged insulation on the wire that
    was sharing 2 ranges. The ranges themselves won't last as long.
    Sort of like working in a brownout all the time. The service cable
    should be checked. I'll bet it's warm most of the time. Circuit
    breakers are supposed to be toggled every 3 months or so to be sure
    that they will operate. Do you do that???? Most folks don't.
    
    In short, your initial question didn't even begin to discuss your
    real problem. You should fix that before you are reparing fire damage!!
    
    Sorry for any harsh statements, but I've seen situations like yours
    turn into tradegies.
    
    JMB
291.306PARITY::GALLAGHERMon Jan 04 1988 14:2014
    
    I agree with all of the replies; you really need to install dedicated
    services for each unit, and size your ciruits correctly.
    
    The only thing that might be marginally acceptable (and despite
    this, I believe that what I'm going to tell you is against code
    regs) is if you had a piece of baseboard heat requiring a 20 amp
    230 circuit, as well as something such as say an air conditioning
    unit.  If you could safely assume that you'd not use either at the
    same time -- such as the heat and the AC together, then you could
    safely do it.  However, I have this situation in my house, and I
    have 2 separate circuits.  The wire and the breakers are cheap enough,
    so I'd certainly encourage you not to compromise your property and
    safety.  Do it correctly and you won't have to fix it later.
291.316Grounding a 2-wire Circuit?DECWET::MCWILLIAMSBrian @ DECwest, 206.865.8837Tue Feb 16 1988 22:4128
    I'm doing some minor kitchen remodeling (counters, lights, paint,
    etc.) and I'm contemplating adding another outlet to my new
    counter space when I take the old counter out.  Adding this outlet
    will involve extending from one of two existing outlets. 

    Presently, there exists one outlet already on the counter.  It
    uses old, 2-wire (ungrounded) wire and shares a 20 amp breaker
    with the kitchen overhead light and 4 living room receptacles. 

    On an adjacent wall is another outlet, on 12 (14?) ga. 3-wire by
    itself on a 20 amp breaker.  Very virtuous looking. 

THE QUESTION:

    1. Is it safe/acceptable to add a ground wire to a 3-prong outlet
    and ground the receptacle directly to plumbing (under the sink)? 

    This way, I could extend the old 2-wire outlet and put in grounded
    3-way receptacle without going through the hassle involved in
    extending from the existing grounded supply on the adjacent wall
    outlet. 

    Thanks for your help, 

    -Brian 


 
291.317NO!AKOV88::CRAMERWed Feb 17 1988 11:0814
    I'm not an electrician, but, from perusing this file and talking
    to folks who know about such things the answer is a resounding NO!
    You should not run a 3 wire from a two wire, in fact it is not
    up to code and, therefore, illegal.
    
    Find out if that grounded outlet on the 20A breaker is 12 or 14
    ga. wire, 'cause if it is 14 then the breaker is too big for the
    wire and unsafe, also.
    
    If I were you I'd have a qualified electrician look at your wiring
    given that the house is old and has obviously had some additional
    electrical work done.
    
    Alan
291.318NO!FANTUM::BUPPWed Feb 17 1988 12:006
    It's interesting how much trouble that can cause if the pipe is
    ever replaced with plastic.....
    
    (However, I have done something similar to get a ground-fault
    interrupter installed. Don't do as I do, do as I say....)
    
291.319Highly illegalSTAR::SWISTJim Swist ZKO1-1/D42 381-1264Wed Feb 17 1988 12:277
    The real reason is that the Nat'l electrical code requires that
    all grounds for circuits emanating from a given main panel be
    connected to physical ground at one and only one point.  This is
    to eliminate any possibility of ground loops - a dangerous phenomenon
    caused by potential differences between two different grounds due
    to leakages, imperfect conductivity of pipes/earth/etc.
    
291.320There's another thing to look out forPSTJTT::TABEREunuchs are a trademark of AT&amp;TWed Feb 17 1988 13:1116
I suppose enough people have told you that you shouldn't ground to a 
pipe by now.  There's another potential problem in your message though: 
The Code now requires that the outlets in your kitchen be separate from 
the lighting cicuit. (Makes sense -- kitchens are filled with dangerous 
things, and if you just popped a breaker 'cause the mixer cord is 
frayed, you don't want to stumble around in the dark.)  I believe it's 
ok for the light to be tied in to the living room circuit, but not the 
kitchen outlet.

This isn't a problem in your present situation, because your old wiring 
is "grandfathered" in under the new code, but if you go to make changes, 
you may be required to bring  the whole kitchen into compliance.  It 
would be a good idea to voluntarily make the change anyway while you're 
snaking the wire over from your modern outlet. :-)

					>>>==>PStJTT
291.321Maybe it IS grounded ...ERLANG::BLACKWed Feb 17 1988 14:3645
    In my "old" (1955) house in Seattle, I had the same problem: two
    prog outlets in the kitchen, and I wanted to add another outlet
    and GFCI.  I had already fiddled the wires from the new outlet down
    to the basement, and was prepared to run a new grounding wire back
    to the panel.
    
    However, when I finally managed to rip out the metal box that housed
    the existing outlet, I found that it WAS grounded.  The grounding
    wire had been installed before the sheetrock, and was attached to
    a screw on the OUTSIDE of the box.  So, the box WAS grounded, although
    I couldn't tell from the inside.
    
    If you have a metal box, you may find the same thing.  Get out your
    test lamp and see if the box is grounded.  If so, rip it out, bring
    that grounding wire through the knockout, and you are home.
    
    Now for my problem:
    
     >> The Code now requires that the outlets in your kitchen be separate
     >> from the lighting cicuit.

    Oh dear!  My kitchen has a main light and a small one over the sink.
    They used to be on the same circuit, but I recently re-wired the
    one over the sink so that it is on a different circuit from the
    main light, but on the same circuit as an outlet.  I did this (without
    a permit, of course) for two reasons:
                                
    (1) When I turn off the main light circuit, to work on the living room
    or the breakfast room, or something else, it is nice to have at
    least the small light over the sink still work.
    
    (2) I wanted to use a pair of three-way switches on the light by
    the sink, instead of the existing single switch.  Normally that
    would mean running three-core cable to replace the two core, which
    means ripping out the outlet box, which typically means major repairs
    to the wall.   However, this switch shared the box with an outlet,
    so by using the power supply to the outlet the feed the common side
    of the switch, I was able to avoid all that.
    
    My question:  have I broken the new code?  (Which code introduced
    this requirement?)  Or is it OK as long as ONE light is on a separate
    circuit?
    
    	Andrew
    
291.323I'm legitDECWET::MCWILLIAMSBrian @ DECwest, 206.865.8837Wed Feb 17 1988 15:5114
Well, against my nature, I broke down and decided to do the project the right
way ... 

I added a new circuit.  This required using up my last breaker in the panel,
cutting a hole in the wall for wire-snaking, as well as removing a baseboard so
I could sneak the wire behind it. 

But hey, I'm glad I did it.  According to code, you're supposed to have
two (2) "small appliance" circuits in a kitchen, separate from the lighting
circuit.  That's what I've got now.

-Brian


291.324Stupid question?CSSE32::NICHOLSHERBFri Feb 19 1988 01:016
    is there any danger in replacing 2 prong outlets with 3 prong outlets?
    Maybe another way of asking the question is: What uses are there
    for 3 prong outlets that are dangerous when there are only 2 wires
    backing up the 3 prongs?
    Just bought a bunch at Spags for 60c and have installed several.
    
291.325QUARK::LIONELWe all live in a yellow subroutineFri Feb 19 1988 02:126
    Re: .8
    
    The danger is if you use an appliance which, for safe operation,
    requires the ground pin to be grounded, and something goes wrong...
    
    				Steve
291.326DICKNS::WELLCOMESteve Wellcome (Maynard)Fri Feb 19 1988 11:587
    The basic problem is, if you put in an ungrounded 3-prong outlet,
    the outlet is not telling the truth.  It's lying to whoever plugs
    a 3-prong plug into it.  
    I can see one danger.  You hire a contractor.  He plugs his 3-wire
    extension cord into one of your outlets, runs the cord outside,
    plugs his 3-wire saw into it, pulls the switch, and promptly gets
    zapped.  He sues you.  
291.327More infoCSSE32::NICHOLSHERBFri Feb 19 1988 13:507
    Thnx for help .10,.11
    Called around and discovered that two prong outlets are not made
    anymore, are not stocked, and are apparently out of code (in Mass)
    One store suggested that a 3 prong outlet can be properly grounded
    simply by running appropriate-guage-wire from the ground screw in
    the outlet to the back of the junction box. Does that make the outlet
    "3-prong-safe"?
291.328Is the junction box grounded?ULTRA::BUTCHARTFri Feb 19 1988 14:2910
re .11

Only if the junction box itself has been properly grounded.  If I remember
correctly, one type of system uses the metal of the electrical conduit that
the wires run through as the ground.  (Might be an out-of-date or state
memory though.)  This works fine as long as all the junction boxes are
properly connected directly to the conduit and nobody has broken the path
in subsequent renovations.

/Dave
291.329VIDEO::DCLDavid LarrickFri Feb 19 1988 15:0126
.11>    Called around and discovered that two prong outlets are not made
.11>    anymore, are not stocked, and are apparently out of code (in Mass)

They won't be easy to find, but they are in fact _required_ by Code when
the box isn't properly grounded.  This should only be true when replacing a
defective 2-prong outlet - if you're installing a new box or running a new
cable, it must be properly grounded, and then you must use a 3-prong outlet. 

Maybe your fellow NOTErs will have enough 2-prongers lying around for you. 
I know I have at least one you can have. 


.11>    One store suggested that a 3 prong outlet can be properly grounded
.11>    simply by running appropriate-guage-wire from the ground screw in
.11>    the outlet to the back of the junction box. Does that make the outlet
.11>    "3-prong-safe"?

As .12 indicated, this advice is correct only if the box itself is properly 
grounded - a dangerous assumption.  If the box were properly grounded, you'd 
most likely already have a 3-prong outlet there!

_Never_ get this type of advice from a store.  The people behind the counter 
and answering the phones may know their stock (often they don't even know 
that), but they don't know the Code.  If they knew the Code, they'd be out 
working as electricians and making lots more money. 
291.330Sure its only two wire?AKOV75::CRAMERFri Feb 19 1988 15:0912
	What kind of cable do you have? My house had two pronged outlets
    also and, unless you looked carefully, 2 wire cable to match.
    BUT, they took the ground wire and wrapped it neatly around the
    cable under the cable clamp (holds the cable to the box) grounding
    the box. I could then run a pigtail to the box for my new three
    prong outlets.
    
    	Alan
    
    PS I may still have some two prongs you can have, if necessary.
       I'll let them go REAL cheap ;^)
    
291.331Source for 2-prong outletsNEBR::HARRISONBob Harrison, CIM EngineeringFri Feb 19 1988 15:540
291.332please, take my outletsTOOK::CAHILLJim CahillFri Feb 19 1988 16:1020
    I have about 20 million two-prong outlets, free for the taking
    (In fact, I might pay someone to take them out of my sight!).
    This is due to the replacement of 90% of the existing outlets in
    my house with 3-prongers.  And, yes... the new outlets are indeed
    grounded.  The existing wiring has the ground wire brought out
    of the outlet box and attached with a neat little spade lug to
    a screw on the outside (i.e., inaccessible within the wall!) of
    the box.
    
.12> Only if the junction box itself has been properly grounded.  If I remember
.12> correctly, one type of system uses the metal of the electrical conduit that
.12> the wires run through as the ground.  (Might be an out-of-date or state
.12> memory though.)  This works fine as long as all the junction boxes are
.12> properly connected directly to the conduit and nobody has broken the path
.12> in subsequent renovations.
    
    You're probably thinking of armored cable, more commonly known by
    a trade name:  BX cable.  Your last point is an important one!
    
    Jim
291.333Can't use BX shield as ground.TALLIS::KOCHKevin Koch LTN1-2/B17 DTN226-6274Fri Feb 19 1988 16:1811
     There have been other notes stating that two-wire BX cannot be used 
to ground a three prong outlet.  The metal shield is not considered a good 
enough conductor back to ground.  

     Yet another earlier note stated that you can put a GFCI on your 
two-wire-plus-BX circuit.

     I have some 12-2 and 14-2 romex with a much smaller diameter ground 
wire.  How can it be legal to use this to ground the third prong?  If the 
third wire is smaller, how can it carry the full load in a hard fault?

291.334CSSE32::NICHOLSHERBFri Feb 19 1988 16:235
    thnx for good analysis and advice guys. Will try to determine if
    in fact the wiring is 3 wire. (House was built c. 1954)
    
    
    			herb
291.335HPSMEG::LUKOWSKII lost my A$$ in the '87 CRASH!Fri Feb 19 1988 16:3126
>They won't be easy to find, but they are in fact _required_ by Code when
>the box isn't properly grounded. 
    Richter and Schwan's (sp?) Wiring Simplified calls this out.
    
>Maybe your fellow NOTErs will have enough 2-prongers lying around for you. 
    True.
    
      I replaced all of the two-prong recepticles in my house with
    grounded ones. I saved the ones that appear to be in reasonable enough 
    shape to be used again and meant to put in a note offering them to
    anyone that needed them for the reason stated above.  I believe I have 
    at least a dozen left (maybe more).  If anyone needs some/all, let
    me know. No warranty/liability is expressed or implied. 
     
    
>				If the box were properly grounded, you'd 
>most likely already have a 3-prong outlet there!

      I think it really depends on when the house was wired. My house
    was built in '55 and ALL of the boxes are properly grounded (or
    at least were when they were installed) yet none of the recepticles
    were the grounded type.  I don't understand this but then again, I 
    don't know what the code was thirty years ago. 
    
    -Jim
    
291.336DICKNS::WELLCOMESteve Wellcome (Maynard)Fri Feb 19 1988 16:3212
    BX armor can be used as a ground *IF* it has a bonding strip
    running along inside it.  This is just a thin metal ribbon, running
    inside the armor but outside the wire bundle.  The armor, by itself,
    isn't considered a suitable ground because the spiral-to-spiral 
    connection isn't very secure, and the only path that has any reliablity
    is around and around and around and around and around and around...
    following the spiral, which ends up being too high a resistance.
    The bonding strip gives a straight-line path, and makes it acceptable.
    (Or so the theory goes).
    The bonding strip ought to be bent over the end of the BX armor
    and clamped under the cable clamp; and don't forget the anti-chafe
    bushing.
291.337BINKLY::WINSTONJeff Winston (Hudson, MA)Sat Feb 20 1988 03:292
NHD hardware (and I think some true value stores) sell 2 prong outlets

291.338DICKNS::WELLCOMESteve Wellcome (Maynard)Mon Feb 22 1988 12:406
    Re: .19
    Yes, that seems to have been the code at one time.  My parents' 
    house was built around 1953 and it has grounded boxes with 2-prong 
    receptacles.  I guess the theory was that if a fault developed 
    in the box and a hot wire touched the box it would blow a fuse, 
    not just sit there ready to zap somebody.
291.339Smaller ground wire?VIDEO::DCLDavid LarrickMon Feb 22 1988 14:1220
.17>     I have some 12-2 and 14-2 romex with a much smaller diameter ground 
.17> wire.  How can it be legal to use this to ground the third prong?  If the 
.17> third wire is smaller, how can it carry the full load in a hard fault?

The ground wire does indeed carry the full load in a hard fault, but 
_not_for_very_long_ - just long enough to trip the breaker.  At the power 
levels 12-2 is used for, it takes a while for the resistance of the smaller 
ground wire to generate enough heat to be dangerous.

But the Romex I've used has a ground wire of about the same size as the
other conductors (I think).  Is yours some special-purpose product?   Does
it have "Type NM" printed or stamped on the outer jacket?  ("Type NM", for
"non-metallic", is the Code's name; "Romex" is one brand, and the universal
trade name.) 

Not to be insulting, but just covering all the bases:  you're comparing the 
ground wire's size with the conductor _inside_ the white and black 
insulation, right?  Of course the "black and white wires" are bigger than 
the bare one when you include the insulation!
291.340AUTHOR::WELLCOMESteve Wellcome (Maynard)Mon Feb 22 1988 15:447
    re: .23 etc.
    Yes, I think the ground wire can, by code, be one size smaller than
    the other wires, so with 12-gauge insulated wires you can have a
    14-gauge ground.  (At least this used to be true - haven't checked
    the latest book.)  I saw, some time ago, some NM wire in which 
    this was done; most of what I've seen has the ground the same size
    as the others though.
291.341Used to be that wayCADSE::MCCARTHYCADSE Environment GroupMon Feb 22 1988 20:056
    A while ago (10+ years) there was ROMEX around with a smaller ground
    wire.  When they started to produce it with same size ground, they
    advertised it as "14-2 Romex with full size ground".  I think it
    would be hard to buy some now though.
    
    bjm
291.342nopeSOFCAD::KNIGHTDave KnightTue Feb 23 1988 10:021
    The '87 code does NOT allow a smaller ground anymore.
291.307Conversion between 220V plug types possible???SUSHI::KMACDONALDGot any ICE you need climbed?Tue Mar 01 1988 12:3319
Well, I have a question on a similar-but-dissimilar topic as .0. My 
situation is that I'm living in a townhouse now, which has 220V service
in the bsmt. with a plug that looks sorts like:

   L
  \ /

and I'm thinking of buying a planer, also 220 (230?) V which seems to 
come with a plug shaped like:

   o
  _ _

As I don't want to rewire this townhouse, which I'll only be in for a 
few more months, is it possible and/or SAFE (!!!) to somehow make up an
extension/conversion cord to allow the planer to plug into the dryer 
circuit, or are these types of circuits incompatible???

                                                   ken
291.308Do itALIEN::WEISSTrade freedom for security-lose bothTue Mar 01 1988 13:2415
I think it should be fine to make a short conversion cord.  The only difference
in the two plugs is amperage.  Luckily, the planer is lower amperage than the
outlet - it would clearly be unsafe to do the conversion if it were the other
way around.  The planer plug is a 20A plug, I'm not sure the exact amperage of
the outlet, but it's at least 30A, maybe as much as 50A.  Make sure you use
wire rated for at least 20A for the cord, and that there is only one outlet on
the cord - if there were two outlets, the cord would have to be rated for the
amperage of the wall outlet since it could take more than 20A. 

At first I wasn't sure about the safety of putting the lower amperage planer
on the high amperage line, but then I thought about 18 guage stranded lamp 
cords being safely plugged into 20A circuits, and that convinced me it would be 
fine.

Paul
291.343No lights on 2 Kitchen Appliance CircuitsERLANG::BLACKTue Mar 01 1988 13:4117
    I thought that I would answer the question that I asked in .5, since
    no-one else has!  
    
    I bought a new Richter and Schwann (no, I don't have the real code)
    and they are quite explicit:  the kitchen must have two 20A circuits
    for appliances.  These circuits MAY also serve the dinning room,
    breakfast room and pantry, , but MUST serve the kitchen.   They
    MAY have an electric clock recepticle, but MAY NOT have ANY LIGHTS.
    The refrigerator MAY use one of these circuits.
    
    So, I disqualified one of my circuits from this provision when I
    connected the supplimentary light to it.   BUT it turns out that
    the refrigerator is on its own 20A circuit, so I DO still have the
    two circuits required by the Code.
    
    	Andrew
    
291.309Use Pigtail, make extension cordERLANG::BLACKTue Mar 01 1988 14:1314
    Go to the hardware store and buy a "PIgtrail" for a dryer -- about
    three feet of flexible cord with the 30A dryer plug molded on the
    end.  Then put a handybox (one of theose metal boxes with rounded
    corners) on the other end, with a cable clamp -- you may hev to
    enlarge the knockout to get the cord into the box.  Put a 20A socket
    into the box, and connect the wires.
    
    Voila -  one extension lead.  Should cost you ~ $15

    I've never seen the 30A plugs on sale other than connected to the
    pigtail, but I bet DEC has a source for them!
    
    	Andrew
    
291.310Don't touch those ... ******** ZAP ********SUSHI::KMACDONALDGot any ICE you need climbed?Tue Mar 01 1988 16:045
Thanks, folks! I may get this thing flying, after all. If I make up the 
rig Andrew suggested, which wire goes where? I suspect that wiring the 
plug improperly could be exciting....

                                              ken
291.311Manuals, manuals...11508::CURTISDick 'Aristotle' CurtisTue Mar 01 1988 18:077
    .14:
    
    Some wiring books (Richter & Schwann?) may describe the proper way
    to wire various plugs.  Come to think of it, the code might, too.
    
    Dick
    
291.312ALIEN::WEISSTrade freedom for security-lose bothTue Mar 01 1988 18:288
Wiring's pretty simple.  In the cord from the plug, there'll be three wires.  
One of them will either be bare (no insulation) or will have green insulation.  
This is the ground.  On the outlet, there will be three screws - one will be 
in a distinctly different place from the other two and should be green.  
Connect the ground wire to this screw, and the two other wires to the other 
screws.

Paul
291.313NEXUS::GORTMAKERthe GortWed Mar 02 1988 00:027
    Wouldent it be a good idea to change the breaker in trhe panel too?
    Seems a 20-30 amp device on a 50 amp feeder could be a tad dangerous
    at least to the planer. It would have to draw 50 amps before tripping
    the breaker. Or am I missing something?
    
    -j
    
291.314ALIEN::WEISSTrade freedom for security-lose bothWed Mar 02 1988 11:2713
>    Wouldent it be a good idea to change the breaker in trhe panel too?
>    Seems a 20-30 amp device on a 50 amp feeder could be a tad dangerous
>    at least to the planer. It would have to draw 50 amps before tripping
>    the breaker. Or am I missing something?
    
I thought that at first too, but then I thought of what would happen to, say, a 
clock radio if it really drew all 20 amps that it's circuit would allow.  POOF!
I guess the point is that it's common practice to have devices with far less 
capacity than the circuit.  Think of wiring a shop such that you could run more 
than one machine on one circuit - you'd make that circuit 40 amps or so, yet 
none of the machines would draw that much.

Paul
291.315NEC ends at the outlet, sortaSTAR::SWISTJim Swist ZKO1-1/D42 381-1264Wed Mar 02 1988 11:5816
    re: Last couple.
    
    The purpose of the panel breaker is to protect the building and
    its internal wiring.   If a plugged-in device wishes to protect
    itself it may do so by a breaker on the device rated at the device
    current (seen on many motors, good stereo equipment, etc).  But
    it's not required on the device by the NEC.
    
    Failure modes of a device where it draws enough current to become
    a hazard but not enough to trip the breaker are considered rare
    enough that the NEC doesn't worry about it.  The underwriter's lab
    has some say in this matter when they UL approve a device - one
    of their criteria is the implications of various kinds of failures.
    
     
    
291.259Another AL-CU connection questionACUTE::MCKINLEYWed Mar 30 1988 22:4613
    I have a similar question.  I was hooking up the power for a dishwasher
    (Sears) and found what seems to be aluminum wiring.  I am hooking 14
    guage solid copper wire to 14-16 gauge stranded aluminum (appearing)
    wire.    The wire appears to be a solid silvery color, i.e. I look at
    the end and there is no copper color seen.  I guess that this is AL,
    not clad CU.  I'm using copper wire nuts for the connection.  Is there
    any problem with this?  BTW, the dishwasher runs on 110VAC.

    As a more general question, when is there a problem using AL and CU?
    The instructions for the dishwasher warn about hooking "stranded copper
    wire to solid aluminum wire," exactly the opposite of what I have.

    ---Phil
291.260NEXUS::GORTMAKERthe GortThu Mar 31 1988 01:087
    re-.1 the wire nuts should be rated as AL/CU anything less could/will
    be a problem later it is also against code. BTW-most wire nuts are
    rated for both but be 100% sure before using them I dont think you
    want a fire later on.
    
    -j
     
291.261Use an anti-oxidantSEESAW::PILANTL. Mark PilantThu Mar 31 1988 13:365
    I would also consider using a dab of anti-oxidant before using the
    wire nut.  I usually goes by the name NOALOX, or some such thing.
    (I don't have my bottle in front of me.)
    
    - Mark
291.262Thanks ACUTE::MCKINLEYThu Mar 31 1988 16:298
Re: -.1,-.2

    Thanks for the tips, I'll check the wire nuts to see that they are
    rated correctly and look around for the anti-oxidant.

    Anyone want to tackle the general AL-CU question?

    ---Phil
291.344GFCI to replace 2-prong?QUARK::LIONELWe all live in a yellow subroutineFri Apr 08 1988 15:546
    The latest Popular Science has an article suggesting the use of
    a GFCI outlet to replace a 2-prong outlet, in the absence of a ground
    wire.  They claimed that this gave some protection against leaks to
    ground, but I am very dubious about this.  Anyone else care to comment?
    
    				Steve
291.263VINO::KILGOREWild BillFri Apr 08 1988 17:136
    re .7:
    
    I thought it had something to do with the comparitively large
    expansion/contraction that AL goes through as normal currents
    generate heat, which over time can cause a bad connection, extreme
    heat and fire.
291.345ground current - with no ground?!DRUID::CHACEFri Apr 08 1988 19:302
     If it's really a two-wire circuit it will need a ground installed
    before it can have fault current through it.!
291.346Ground is NOT necessaryCURIE::DISHMANFri Apr 08 1988 20:1019
    
    I've been successful installing GFCI's in two-wire circuits. 

    According to an electrical consultant (actually, an instructor), GFCI's
    work by comparing the current in both sides of the circuit.  Any
    mismatch triggers them to shut off.  A ground is not required.
    For some reason, "code" doesn't allow installation of outlets beyond the
    ungrounded GFCI. 

    Assuming this is correct, it substantiates the information in .28, and
    provides a measure of protection to ungrounded, two-wire circuits. 

    Further evidence for the lack of a ground requirement is that it works.
    I've installed GFCI's in all exterior locations, some fed only by knob
    and tube wiring.  I intentionally shorted one to ground (via a long
    wire) and, yes, it cut out as hoped. 
 
-Bruce                                  
    
291.264The why of itREGENT::GETTYSBob Gettys N1BRM 223-6897Mon Apr 11 1988 12:2218
                Aluminum and copper have different rates of expansion
        and contraction. This causes any connection between them to
        eventually work loose. Once it is slightly loose, heat starts to
        build up in the joint causing more loosening. And on and on it
        goes until the resistance is high enough to cause enough heat to
        be generated to cause a problem, like a fire.
                
                The electrical devices (outlets, etc.) which are marked
        as aluminum usable use an alloy for their terminals which has a
        close enough coefficient of expansion to aluminum so that the
        loosening doesn't occur (assuming proper installation). The
        NoAlOx (or other preparations) also reduces the problem by
        keeping the aluminum from oxidizing and provides a conductive
        path to reduce the resistance in the joint. Less resistance
        means less heat;  thus less expansion and contraction; thus less
        problems.
                
                /s/     Bob
291.347Yes, but....AMUSE::QUIMBYMon Apr 11 1988 14:166
    From a theoretical point of view, .30 is right -- the GFCI will
    fulfill its ground-fault function without a grounding conductor.
    
    However, the GFCI outlets ceom with three-hole outlets, and it is
    probably not acceptable to have what appears to be a grounded outlet
    when the ground is not connected.
291.348QUARK::LIONELWe all live in a yellow subroutineMon Apr 11 1988 19:2112
    I went back and looked at the PS article.  It stated that the "code"
    (they had a citation which I don't recall) explicitly allows for
    a GFCI to replace a two-prong outlet.  Says nothing about the
    unconnected ground pin.  However, the article goes on to say that
    you CAN do a feed-through with this method, contradicting what an
    earlier reply here said.
    
    I agree that a GFCI is better than nothing, but I would be inclined to
    fill in the ground pin with something (silicone sealant?) rather than
    allow the possibility of someone depending on that being a ground.
    
    					Steve
291.283Outlet ground tied to commonVIDEO::DCLDavid LarrickMon Apr 25 1988 14:3453
291.284Advise and WithdrawBIMINI::SCHNEIDERDennis SchneiderMon Apr 25 1988 15:3019
David,

1. Given the description, I'd suspect that Neutral and Safety ground have
   been bonded elsewhere in the wiring.

   I've NEVER seen anyone intentionally strap safety ground to neutral in
   in outlet box. One wonders why they bothered to clamp the safety
   grounds together.....

2. As far as the ethics/law are concerned, I'd have told my neighbor that
   you believed there was a genuine hazard there and let the neighbor
   take whatever decisions fell out of that.

   Given you were likely not looking at the only instance of crossed
   neutral/safety ground, genuinely correcting the hazard would have
   been lots of work.

Dennis

291.374Need advice on old wiringTOLKIN::ROMANOIt works better if you plug it inThu May 19 1988 12:5620
    This note is also in REAL_ESTATE.
    
    I'm interested in buying a 118 year old Victorian in Hudson.  The
    building seems to be very stable and in good shape.  It's about
    2700 square feet of living space.  One sticking point for me is
    that over 50% of it still runs on the ancient "ceramic" insulated
    wiring from the vintage 20's.  The other half has been upgraded
    to the metal-sheathed wiring (mental coil) and modern wiring.  My
    question is how dangerous in the old wiring.  The amount that it
    will cost to replace is going to be a strong indicator on the price
    we are willing to pay for the house.  Any rough estimates on
    replacement costs for the old wiring... does it need to be done
    right away.  We would like to run a couple of air conditioners in
    some of the floors to branch wiring may be necessary.
    
    
    Thanks for the information,
    
    
    -Don-
291.375DICKNS::WELLCOMESteve Wellcome (Maynard)Thu May 19 1988 13:444
    The official name for that kind of wiring is "knob and tube."  
    It's basically safe.  I wouldn't worry about it.  You'll want 
    to replace it someday, but don't panic in the meantime.  After 
    all, it's been there for a long time already with no problem.
291.376more..TOLKIN::ROMANOIt works better if you plug it inThu May 19 1988 13:579
    I'll admit that I'm a little concerned about the hazards of it.
    I'm more concerned whether it will be able to meet our needs.  I
    couple of air conditioners will need to be used... can this wiring
    handle it.  If we do want to change it (a lot of people have), any
    ideas on cost estimates... we just want to know what we're up against.
    
    Thanx,
    
    Don
291.377As long as they work ...CIMNET::HARRISONBob Harrison, CIM EngineeringThu May 19 1988 13:582
    I still have two circuits (out of 17 )that are knob and tube in
    my 1917 vintage house. No problems ...
291.378SPGOPS::FLANNERYThu May 19 1988 14:4912
    More important that what kind of wiring it is, check what's
    on each circuit and see how many outlets are in the rooms for
    the air conditioners.  We have a lot of this wiring and the
    only problem have is that many of the rooms only have one
    outlet.  If you want to run an AC off it could present a
    problem.
    
    As for cost to replace, if you don't want to rip out the walls
    and/or ceilings, its very labor intensive.  Took us 8 hours to
    snake a new line into the kitchen.  To pay someone could get
    very expensive.
    
291.379Knob and Tube OK, but modify to meet needsTOOK::ARNTim Arn LKG2-2/BB9 226-7572Thu May 19 1988 15:4018
    The wiring itself is probably OK if noone has seriously overloaded
    it in the past creating problems. The problem is that you probably
    have a 60 amp service running only 4 - 15 amp circuits throughout
    the house. All of the lights for a lot of rooms could be on the
    same circuit. Now you want to take two air conditioners which draw
    about 30 amps when the compressor kicks in, and put it on the existing
    wiring. From experience let me tell you, buy about 10 boxes of slow
    blow fuses and have them ready. What I did to solve the problem
    was to add a circuit breaker box capable of adding 8 new circuits.
    Then, you can string a seperate line to each place you want a air
    conditioner or a grounded outlet for hooking up you home computer.
    There is nothing wrong with knob and tube wiring, except that it
    does not provide a ground at outlets. Mine is still in excellent
    shape and is 65 years old. I can't imagine that the previous owner
    hasn't added another box! Hasn't the kitchen been remodeled?
    
    Tim
    
291.380HEYDEN::BBARRYThu May 19 1988 15:538
I do not know MA electrical codes very well, but doesn't the 50% rule 
kick in when he adds the additional circuits.  The 50% rule says that if 
more than 50% of the current electrical capacity is remodeled, upgraded or 
added to then the entire system must be upgraded to current code levels.
I know this was the case in Arizona.  

Brian

291.381Do it right!!!AIMHI::BERNARDThu May 19 1988 16:3839
    
    Knob and tube was the best way to wire in the "old" days. Those
    days also saw lots and lots of house fires started by faulty electical
    systems. The major problem with K&T is that there is no ground,
    or third wire back to the fuse box to open the circuit in the event
    of a short. I've heard of cases and actually ran into one where the 
    old wiring became frayed inside the box, and everytime something was 
    plugged in, a spark came out. The fuse never blew.
    
    With today's ever increasing dependence on elecrticity, the last
    place to scrimp is in the wiring. 
    
    A previous note made a good suggestion to upgrade the service. I know 
    the MA code doesn't allow K&T wiring to run into a new box. Most
    electricians run new wiring to the first junction box and connect
    there. I personally have made every effort to replace all K&T that
    can be reached without major work.
    
    For your A/C's, I would run dedicated circuits. They tend be be
    real noisy (electically) so you may get interferrence on appliances
    or blinking lights if they share circuits.
    
    While you're at this project, don't forget to install electric smoke
    detectors that are connected together on all floors. I got cheap
    at my mothers house and a careless tenant nearly caused a disaster.
    I'm installing them this weekend!!.
    
    As for costs, you can usually count on not exceeding $100 per device.
    A device would be a plug, light etc.. This sounds like a lot, but
    as a previous noter discussed, it can take lots of time for old work
    wiring. Get several estimates and references, and make sure that
    the inspector does more than a walk through inspection.
    
    Sorry for the long note for a simple question, but I've seen too
    many bad things happen due to faulty wiring.
    
    good luck
    
    JMB
291.382RAMBLR::MORONEYThe purpose of diplomacy is to prolong a crisisFri May 20 1988 00:386
FWIW:

Until very recently (a couple months ago) there were knob-and-tube circuits in
use in the Mill, carrying 550 volts.

-Mike
291.383lots of work or $$ for new.27958::DONNELLYTake my advice- Don't listen to meFri May 20 1988 04:0626
As stated, the knob and tube is probably ok especially if not overloaded.  
The trick here is not over loading it.  Unscrew one fuse and go see what 
goes out, you can find out the extent of the circuits like this.  Most knob 
and tube is 14 ga. wire, that means 15 amps max.  Hardly suitable for ac. 
What I would suggest is putting in new wiring to handle everything except
ceiling lights and some switches to run them.  The rational is that light
bulbs will not overload the wire and those fixtures are usually the
toughest to get to. 

Adding the new wiring is very expensive if done right.  I rewired my
complete house like this and it took me a year.  The house is only 1200 sq.
ft. (ok, I didn't work on it 24 hours a day).  I called in an electrician 
to run the huge 200 amp cable, put up the meter socket, and hook them up to 
the wire from the street and my new panel.  This took all of 4 hours and 
cost about $500.  If I had paid for the whole job it would have run over 
$5000 I'm sure (lots of outlets and circuits).

Another thing to consider is, are the walls accessable to run wires?  I ran 
one 3-wire to the attic and then everything top down for the 2nd floor.  
This was ok but still lots of work.  I've seen lots of surface conduit in 
old victorians; gets the job done but doesn't look too great.

I guess there's no simple answer for you.  Just don't put in bigger fuses, 
the 15 amp ones will blow if they're supposed to.

Craig
291.384More than 15 Amperes?ERLANG::BLACKFri May 20 1988 22:198
    I think that 14 guage wire in knob and tube can safely carry more
    than 15 amps.  14 guage NM cable can carry 15 amps, but knob and
    tube can safely get hotter than NM cable with paper and plastic
    in direct contact with the wires.
    
    However, voltage drop may certainly be a problem with 14 guage.
    
    
291.385RAMBLR::MORONEYThe purpose of diplomacy is to prolong a crisisSat May 21 1988 01:4010
re .10:

Open wire *is* rated at a higher current capacity than cable (a wire table I
have rates #14 as able to take 32A continuously as a single, bare open-air
wire), *BUT* try explaining that to your insurance company should your house
burn down and they find 20A fuses for #14 knob-and-tube wiring, even if it
wasn't at fault!  Run #14 gauge with 15A breakers/fuses and use its "open-ness"
as a safety factor to make up for its obsolencence, if you keep any of it.

-Mike
291.386Electric wire thru several 2 x 4's ?HPSTEK::CURRANWed May 25 1988 20:2014
    
    My husband is currently wiring up a new addition.  There are
    several places in the room where we need to go thru about 4-5
    2 x 4's, which is about 6-7.5".   Last night my husband was
    drilling thru the middle of one of these and broke our new
    drill,  because of the 16" distance he needs to start with
    a small drill then put a larger one in the hole and attach
    the drill to it.  Seems the larger drill wasn't tightened enough
    and it damaged the holders.  Is there an easier way to do this ?
    Could the 2 x 4's be notched and then covered with metal to
    still meet code ?  What would be the easiest way to notch them ?
    
    thanks
    Karen Curran
291.387Notches and groovesVIDEO::DCLDavid LarrickWed May 25 1988 21:0820
Yes, the Code allows you to install wiring in notches or grooves and then 
cover them with metal plates to protect them from nails and other damage.

It goes into some detail about how thick the metal plates need to be.  I
was going crazy looking for material that would meet these specs until my
wiring inspector let me in on the secret:  just use the box sides that are 
left over when you disassemble boxes to gang them.

I used a router to cut a groove along some framing lumber.  Repeated passes
with a circular saw (with its blade set to the proper depth of cut) might
be faster for cutting notches.  Actually, just cut the notch top and bottom
with the saw, then hit between the cuts with a hammer; a good-sized plug
should pop right out.  Neatness doesn't count much, as long as you leave
something sound enough to attach the metal plates to. 

Don't notch so deeply that you weaken the structure, especially in multiple 
adjacent boards.  And don't count on the metal plates for any structural
help; their purpose is to protect the wiring from nails, not to hold the
house up.  If you go deeper than, say, 1/3 of the board's width, you should
be drilling holes, not cutting notches. 
291.388SMURF::WALLACELife's a beach, then you dive!Wed May 25 1988 21:0814
    	4-5 2x4's sounds like a supporting post for a beam or a header
    which would make me leary of notching it.  There are two things
    you might do.
    
    	1. Notch the 2x4's and then replace the notched out section
    	with a piece or wood so that the strength of the post is not
    	impaired.  (If in fact it is a supporting post of some kind)
    
    	2. There are 90 degree drill attachments that are sold for just
    	this purpose.  It allows you to get into tight places.  The
    	unit goes into the drill chuck like a regular bit, then forms
    	a tight 90, into which you insert the drill bit.
    
    	3. Rent a 90 degree drill.
291.389Anther way to wireFRSBEE::DEROSAbecause a mind is a terrible thingThu May 26 1988 12:3610
    Another way I've seen wiring done is instead of drilling or notching
    2x4's, run the wire up into the attic or the space above the ceiling
    and then back down to where ever and then up again and so on. This
    uses more wire but you don't have to drill so many holes and the
    holes you have to drill, you can get at. The good thing about this
    is if you want to cut a hole in the walls for something the wires
    aren't in the way..
    
    BD  
291.390trouble drilling??AIMHI::BERNARDThu May 26 1988 16:5920
    
    At the risk of sounding out of line, if he can't get holes drilled
    in 2x4's, are you sure he should be wiring the house???
    
    I can't imagine why he can't drill a 3/4" hole in studs with a regular
    drill set-up. And why can't the smaller drill go through all of
    them? Is he pushing too hard, or not pulling the drill out occasionaly
    to clear the saw dust? Or is the bit dull?
    
    The previous suggestions of using a 90 degree drill, or going to
    the attic or basement are excellent alternatives. Most electricials
    I've worked with over the years use notching as a last resort. For
    one thing, if you don't also notch for the plate, it will make the
    sheet rock bulge in that spot. Not much granted, but it will show.
    Also some inspectors are real tough on the depth of the notch. Why
    risk having to add more support.
    
    good luck
    
    JMB
291.92Fried Motor anyone ?TOOK::ARNTim Arn LKG2-2/BB9 226-7572Thu May 26 1988 17:407
    Does anyone know where you can buy spools of varnish coated copper
    wire for rewinding motors? I've called every electrical supply place
    and motor repair shop but noone sells the wire. I'm in N.H., Mass.
    
    Thanks
    Tim
    
291.391won't fit !!FREDW::MATTHESThu May 26 1988 17:598
    The problem is that you don't have the normally 14-1/2" between
    studs when you encounter 3, 4, or 5 of them together.
    
    The regular drill setup won't fit.
    
    He's probably having a problem because he's going at an angle and
    then trying to straighten out once in the stud pocket.  This would
    put undue sideways pressures on the drill and bit.
291.392Use Spade bit, series of extendersERLANG::BLACKThu May 26 1988 18:1119
    I've found a spade bit is better for these jobs than an auger bit.
    Because the shank is smaller than the head, to some extent one CAn
    straighen out the hole.
          
    You can get 6", 12" and 18" bit extenders for the Irwin spade bits.
    Drill the first 6" with the bit, add a 6" extender and drill the
    next 6", remove and add the 12" extender, etc.
    
    The first 6" could be a slightly larger diameter, too.
    
    If all else fails, how about removing the stud adjacent to the 6"
    pillar, drilling the hole, and putting the adjacent stud back.                                             

    Notching should be OK too.  The nail plates to cover the notch cost
    a quarter each at Ralph Pill's.  (I have 10 or so such plates if
    you want 'em -- I ended up drilling holes instead!)
    
    	Andrew
     
291.93VAXWRK::INGRAMLarry IngramThu May 26 1988 19:426
	The wire is called "magnet wire". What gauge are you looking for?
	the thinner stuff can usally be purchased from electronic supply
	houses, not electrical. You could also look in the yellow pages
	under wire-insulated or wire products.

Larry
291.393Just get a long auger bitHPSVAX::POWELLReed Powell HPS MarketingFri May 27 1988 00:2726
    Notching is certainly a last resort - lots more work to get it flush
    with the 2x so the sheetrocking is not a problem.  Code says you
    can notch up to 1/3 of the width, fyi.
    
    I disagree on the spade vs auger point.  What I did when I started
    my wiring, after trying a spade bit a couple of times, was to go
    out and get a 5/8" x 18" auger bit (costs around $15 at Spags).
    I never regretted it.  Especially for going through multiple 2xs
    in one swipe - the auger would have been a pain in the a**.  The
    auger pulls itself in nicely. 
    
    If the combined depth of the 2xs is real deep, then you end up hitting
    it from each side, pointed towards the outside wall (making a sort
    of V), and then either pushing the wire through, or maybe having
    to fish it through, depending on how well you got the two holes
    lined up.  I never had to do that though - but then I used 2x6s
    and that gave me the necessary additional depth.  
    
    I doubt if this is a supporting post or anything.  Probably is either
    at the corner of an inside partition wall, and the extra 2x are
    there to both give nailing surfaces for the wallboard on all sides
    and to give a solid surface for the partition to be nailed into,
    or else an inside corner along the outside wall, again to give added
    nailing surfaces for the wallboard.  
    
    
291.94Motor still fried,getting well doneTOOK::ARNTim Arn LKG2-2/BB9 226-7572Fri May 27 1988 13:538
    I'm looking for 20 gauge. Somebody I called yesterday also suggested
    an electronic supply house. Do you know of any good ones off of
    495? I didn't look under wire in the yellow pages either. I'll check
    it out.
    
    Thanks
    Tim
    
291.95A couple of places to tryVAXWRK::INGRAMLarry IngramFri May 27 1988 14:3014
>    Do you know of any good ones off of 495? I didn't look under wire in the
>    yellow pages either. I'll check it out.
    

	You could try Active electronics in Westboro. It's on Flanders Rd.,
	about 1/2 mile west on Rt. 9 from 495. Phone is 366-9684 or 366-
	8899. Also, You-Do-It Electronics just off Highland Ave. in Needham.
	That is just off Rt. 128 though.

	Radio shack sells the stuff too, but the thickest they have is 22
	gauge.

Larry    

291.394HPSTEK::CURRANFri May 27 1988 17:4225
    
    
    Wow,  I really pleased to see so many responses.  
    The 2 x 4's are for supporting beams and headers on either side
    of 8' windows.  Going to the attic was an alternative and we did
    do that in the areas we could.  On the end wall this was not possible.
    He is most capable of doing the work, you must admit that after
    working a 10 hour day, and then working around the house anyone
    is likely to have their patience tried.  
    
    What we did was bought a 1/2" drill, the one we had was 3/8"
    and we bought the Irwin spade bits with the extenders.  He's
    going to give that a shot this weekend.  
    He was using just regular drills to begin with.
    The auger bit sounds like a good idea,  We missed that at Spags
    yesterday, are they where the other drill bits are ?  On the main
    isle ?
    
    I was looking thru the Sears catalog and the have a right angle
    attachment for $7.99, perhaps we'll try that with the auger bit.
    
    thanks for the help
    Karen
    
    
291.395Using spade drill bitsSEESAW::PILANTL. Mark PilantFri May 27 1988 19:0612
    On comment on the extensions: make sure the set screw is TIGHT.
    There is nothing worse than having the set screw loosen up leaving
    the spade bit still on the hole.  (I had this happen when I was
    drilling through 2 4x4s and 1 2x4 nailed together.)  Also, remember
    to pull the bit out frequently to let the wood chips out.  Otherwise
    the bit may bind up in the hole.
    
    If I has it to do over again, I would not have used the short (6")
    spade bits.  I would have located one of the longer auger bits or
    an 'electricians' long (18"-24") twist drill of the right diameter.
    
    - Mark
291.396I use drill extensions only because I'm too cheap to use the right toolSTAR::SWISTJim Swist ZKO3-4/U14 381-1264Fri May 27 1988 19:557
    Mark's point is well taken.  Extension bits are inexpensive but
    don't really work all that well.  The problem is that they have
    to serve the function of the drill chuck but in a space equal to
    the smallest spade bit they support (3/8" to 1/2" typically).
    Allen-head setscrews just don't cut it given the torque generated
    by drilling through 5 2*4's or whatever.  If you can get it tight
    enough, you'll probably strip the setscrews or your wrench.
291.96NEXUS::GORTMAKERthe GortSat May 28 1988 01:477
    An electronic supply house should carry it. Belden is one brand
    Carol Cable is another you may have to special order to get a spool
    with enough footage to wind a motor depending on gauge most of the
    spools I have seen were only 100-200' for 20-32 ga. sizes.
    
    -j
     
291.397BPOV08::SJOHNSONI've found my Victorian at last!!!Fri Jun 03 1988 16:2917
re. < Note 2328.10 by STAR::SWIST "Jim Swist ZKO3-4/U14 381-1264" >
>    Mark's point is well taken.  Extension bits are inexpensive but
>    don't really work all that well.  The problem is that they have
>    to serve the function of the drill chuck but in a space equal to
>    the smallest spade bit they support (3/8" to 1/2" typically).
>    Allen-head setscrews just don't cut it given the torque generated
>    by drilling through 5 2*4's or whatever.  If you can get it tight
>    enough, you'll probably strip the setscrews or your wrench.
>

                  I did just that recently, the allen head set screws 
                  stripped, and I went out and bought a longer extension
                  at Sears.  Same thing though, after I use it 15 or 20 times
                  the screws will strip again I would say.

Steve

291.401Dead Electric Outlets - HELP!BLURB::WIEGLERMon Jun 06 1988 13:3426
One evening last week we had a thunder storm.  Although we didn't lose power, 
our lights did flicker a few times.  The following morning 3 electic 
outlets in our house were dead.  I don't know if the storm had anything 
to do with it or not, but I thought it was worth mentioning.

The three dead outlets are all in bathrooms (one outlet in each 
bathroom).  The outlets are NOT GFI outlets. They are regular outlets, 
just like everywhere else in the house (the house is 10 years old and 
the only GFI outlet is in the garage).  

I checked the cicuit breakers and they are all ON.  I even flipped them 
all off, and then on again, just to be sure.  I used a line tester and 
confirmed that there is power at each of the circuit breakers 
themselves.  I also used the line tester at the outlets (removed the 
cover plates and tested at the screw terminals on the outlets) and found 
that there is no power at any of the outlets.  That is, there doesn't 
seem to be power leading in to any of the outlets.  As far as I can 
tell, there doesn't seem to be anything on this circuit except for these 
three outlets (one of which is used for the washing machine).

What do I do now?  I'm looking for suggestions.

Obviously, I could call in an electrician, but I usually try to handle 
these kinds of problems myself if I can.  However, when I run out of 
ideas, I will call an electrician (anyone know a good one in Manchester, 
NH?)
291.402Just have to trace circuitsNSSG::FEINSMITHMon Jun 06 1988 13:547
    Its a pain, but you'll need to trace the circuit from the breaker
    to the first outlet. You may find a junction box somewhere in between
    tat first outlet and the panel which has a very high resistance.
    Its a nuisance job, but its probably the only way to find the problem.
    
    Eric
    
291.403It still may be that other GFI!TRACTR::DOWNSMon Jun 06 1988 14:187
    Did you check the GFI that you mentioned in the garage. The garage
    GFI may control the three outlets in all the baths. With one GFI
    oulet you can easily protect a number of outlets that follow the
    GFI in the same circuit. Otherwise you have to start tracing the
    circuit as mentioned in .1
    
    Good Luck!
291.404Ck for Panel GFINSSG::FEINSMITHMon Jun 06 1988 14:386
    In ref to .2, the house I had in NY had all the bathrooms and the
    one outside outlet on the same GFI (in panel box), so that's probably
    a good shot. 
    
    Eric
    
291.405This could be easier that I thoughtBLURB::WIEGLERMon Jun 06 1988 17:324
    Thanks a lot.
    I'll check that GFI tonight.  That sounds like a very likely suspect.
    I didn't realize that one GFI would protect the other outlets on
    the same circuit. I'll post the result tomorrow.
291.406GFI in panel box?BLURB::WIEGLERMon Jun 06 1988 17:354
    One more thing....
    RE: .3
    You said you had a GFI in the panel box.   What exactly would that
    look like?  None of my circuit breakers look unusual.
291.407Make a listVIDEO::DCLDavid LarrickMon Jun 06 1988 17:457
Not to pick on .0, but this episode underscores the importance of having an
accurate electrical map of your house - a list of every electrical outlet,
light, and appliance in the house, what circuit they're on, how much current 
they draw, and ideally how the cabling runs. 

Making this list while things are working properly is infinitely easier than 
trying to figure it out after something fails.
291.408REGENT::MERSEREAUMon Jun 06 1988 17:517
    RE: -.1
    
    > Making this list while things are working properly is infinitely 
    > easier than trying to figure it out after something fails.

    For those of you that normally have a properly working system :^}
    
291.398Basic grounding questionsLABC::FRIEDMANMon Jun 06 1988 23:4314
    A basic house wiring question:
    
    The green wire is the ground.  I connect this to the recepticle
    green screw and also to each metal outlet box?  The more connections
    to metal conduits and boxes, etc. the better?  My reasoning would
    be that if a bare hot wire would touch any of the metal then a
    short circuit would develop and the circuit breaker will trip.
    Otherwise a piece of metal could be electrified and if some
    poor grounded soul touched it they would be shocked.  Is this
    principle correct: all metal that could come in contact with
    an electrified wire is best off grounded?
    
    
291.399Other uses also.CLOSUS::HOEColorado's the place to be.Tue Jun 07 1988 03:379
    There are other needs for grounding; your terminal at home or your
    PC might generate RFI or radio frequency noise that radiates to
    tvs and radios. Grounding reduces the RFI.
    
    Lightening strikes dissipates better if the ground is within a grid
    (cage). multiple ground paths are used to lessen the effect of the
    lightening. 
    
    cal hoe
291.409You folks are so smart!DOODAH::WIEGLERTue Jun 07 1988 12:377
    I went home last night and checked the GFI outlet in the garage
    and, sure enough, the button was out.  The electrical storm must
    have tripped it.  I hadn't relaized that it was on the same circuit
    as my bathrooms, but when I reset the GFI, all the outlets came
    alive again.
    
    Thanks again.  
291.410how to trace the wireMSEE::CHENGTue Jun 07 1988 12:395
    re: .6
    YES, I agree it's one of those things that homeowner SHOULD do.
    Now the question. What method do you use to trace how the system
    is wired. i.e. to find out where the 1st outlet, 2nd,... etc., without
    tearing down the wall.
291.400VIDEO::DCLDavid LarrickTue Jun 07 1988 13:0813
Your reasoning in .0 is good.  But there's more to it than that; electricians 
and safety experts have built up a significant body of knowledge over the 
years on grounding and related electrical subjects. 

This body of knowledge is contained in the National Electrical Code.  It calls 
out the techniques and materials that should be used to achieve safe grounding 
in a variety of circumstances. 

Thought experiments such as the one in .0 are valuable for understanding why 
the Code says what it does; but when it comes to doing the work, don't try to 
derive your techniques from first principles.  Get a copy of the Code and/or 
the various commercial guides to it (as recommended elsewhere in this
conference), and follow it. 
291.411VIDEO::DCLDavid LarrickTue Jun 07 1988 16:5425
I thought I remembered existing discussions of circuit-tracing techniques 
in this conference, but I can't find them.  Can anybody help?

The first step is to make the list of what outlets, lights, applicances,
etc. are on which circuits.  This list will give you many clues in tracing
the cabling. 

Any cable paths that are exposed in the basement or attic are relatively 
easy, although time-consuming and error-prone, to trace.  A flashlight, a 
helper, and lots of patience are necessary.

If there's a GFCI in the circuit, tripping it will tell you which outlets 
are downstream and which are upstream.

It's more work, but you can use the same technique with any electrical box, 
by opening it up and disconnecting the wires that go downstream.  You need 
to use appropriate safety techniques, of course, and be prepared to repair 
any wiring you might break, especially in very old work.

A thorough job of cable tracing is sufficiently painful that it's probably
reasonable to put it off until you have a problem - although it may be more
difficult then.  The indispensable thing to have is the list of what's on
which circuit, and that's relatively easy to make - even enjoyable if you
make it a family project.  The cabling information is a useful-but-optional
adjunct to that list. 
291.412Don't believe every thing you read LDP::BURKHARTWed Jun 08 1988 17:5824
    	Funny this should come up now. Last night I was working on some
    wiring in my basement & garage for auto door openers and shop lights.
    Well, I've been lazy and never di a check of what circuits were
    connected with what. I figured it was pretty simple as the house
    is only 3 years old and all the breakers labeled. So i figure I
    can safely add 2 outlets for door openers & 2 fluorescent light
    fictures to 3 basement & garage lights 75W; 3 smoke detectors; 1
    300W spot light; and 1 15amp GFI outlet. All this on a 15 amp circuit.
    	Now the fun part; I turn off the circuit to work in the switch
    box and while the power is off I decide to take a break and move
    the sprinkler in the front yard. I go up stairs and start to head
    out the front door but stop first to turn on the front entry way
    lights. Guess what? No lights. Turns out in addition to the above
    the outside front 2 lights (2 x 60W) and front foyer chandelier
    (8 x 40W or 50W) are also on the same circuit. Does not leave much
    on the 15 amp circuit for that 1 outlet I have in the garage for 
    plugging in the powertools.
    	Good thig I'm adding additional dedicated outlet for powertools.
    
    			...Dave
    
    	Who will be checking every outlet and light this week.
    
    
291.413I don't trust lables anymore.TOLKIN::GUERRADUMP THE DUKEWed Jun 08 1988 20:3911
    I don't believe everything I read either. My house is 3 years old
    and I bought it with an unfinished second floor. There were two
    pairs of wires going up to the second floor, two for heat and two
    for lighting/outlets. The ends were dangling in the cellar marked
    as north or south sides. When I was finishing the electrical installation
    I figured I could electrify the side I was done with (north) so
    I proceded to connect the lighting wire to the panel. Much to my 
    surprise, when I flipped the breaker on I heard a pop and the breaker 
    tripped. The wires on the south side shorted since they were touching 
    the junction box. It looks like the electrician that did the original 
    wiring didn't know north from south. 
291.414Wiring an OLD house (no ground).DCC::JAERVINENPeace thru superior firepowerThu Jun 23 1988 12:4541
    I finally have bought this old (>200 years) house in Chianti
    (that's in Italy for those of you who don't drink wine).
    
    The existing electrical wiring seems to be at least as old, if not
    from Roman times...
    
    To be frank, seeing the system would cause any US/German/Scandinavian
    inspector to die of heart attack (or be electrocuted) immediately.
    Nevertheless, ENEL, the State Energy company, connected power without
    a whisper...
    
    Basically, in Italy, they bring a two-wire (single phase) system
    into the house (live and neutral). But neutral isn't necessarily
    quite neutral (this is a rural area and the xformer may be quite
    far away) and you are not supposed to ground the neutral at the entry
    to the house as would be done here (in Germany) [and in US].
    
    In fact, there's no ground whatsoever in the house. Despite that,
    the person who did the wiring used only 3-prong outlets, just leaving
    the center (ground) unconnected (probably just to enable him/her
    to connect grounded devices easily to any outlet).
    
    So eventually I would like to provide a ground in the system
    before it grounds me. I think I should also use GFI's extensively.
    
    I know how things are wired in Germany (I am an EE) but I have never
    encountered a system like this. I'd be grateful for any ideas to
    make a safe & simple wiring, as well as advice on any pitfalls.
    
    There's a steel water pipe going from the house to a well about
    1000 ft away (in fairly wet soil) which should provide a fair ground.
    On the other hand, I keep thinking that there's no great need for
    a ground if everything is protected by sensitive GFIs... (remember
    that there's no code this installation has to conform to - just
    has to be reasonably safe). This might be a problem with things
    like the water heater which may have some leakage here and there
    and make the GFI trip even when no real fault exists. Same thing
    might apply to some other appliances.
    
    Any ideas?
    
291.415BEING::WEISSTrade freedom for security-lose bothThu Jun 23 1988 13:1117
>             -< true ground could develop voltage in your neutral >-

From what I understood of what he said, there already IS current in the 
'neutral'.  If he connected the ground to it, then if he plugged a grounded 
plug of, say, a power drill into a socket, it would charge the case of the 
drill, which is probably a bad idea.  :^)

I think he's planning on creating a 'ground' for the ground of the plugs that 
is separate from the neutral.  Different from wiring here in the states, but it 
doesn't sound like a bad idea to me.  The case of the drill would be connected 
to true ground, which is what you want anyway.  Course I'm no EE, so I'll defer 
to the greater wisdom of nearly anyone, but it seemed like you had missed a 
significant piece of what he'd said.

I agree, though, that I'd use GFIs wherever I could.

Paul
291.416DCC::JAERVINENPeace thru superior firepowerThu Jun 23 1988 14:1324
    re .1,.2: .2 is right - as I said in .0 you are not supposed to
    connect neutral and the (yet non-existing) ground together - because
    the 'neutral' may not be quite neutral. When I measured the difference
    between neutral and the water pipe was just about 2 volts - but
    if one of the vineyards hanging on the same 220 volt (three phase)
    line switches on a big machine, it might well be mich higher.
    
    Also, if the power company's neutral breaks somewhere between the
    transformer and my house, and I connect neutral to ground, then
    everybody's power (after my house) would flow through my ground...
    
    In the normal German (and US as far as I know) system all the neutral
    and ground wires coming from the outlets are connected at one single
    point (the fusebox) and nowhere else, the same point being connected to
    a separate ground in the house (about 600 ft of flat galvanized steel
    strip is usually used here, buried around the house) and of course the
    neutral brought in by the power company.
    
    There's a tendency to use very sensitive (10 mA) GFI's here in
    Germany for special purposes though these are not yet approved by
    VDE. These should offer quite perfect protection for humans (and
    animals) in all circumstances, but may be too sensitive for some
    purposes.
    
291.418Here's a pointer for youCALVA::WOLINSKIuCoder sans FrontieresThu Jun 23 1988 15:2413
    
    
      The wiring system in Italy sounds alot like the French one. 
    You might try contacting John Simpson in Valbonne he was the
    European Area environmental specialist for a long time and is
    extremely knowledgeable in all of the European power systems.
    Just say I pointed you in his direction and I'm sure he'll help
    out if he can. I know he could be easily bribed with a few bottles
    of good Chianti.  :-)
    
    
      -mike          
    
291.419Hey Maybe Try This!TRACTR::DOWNSThu Jun 23 1988 16:219
    I'm no electrician but I have done alittle wiring in my day. Why
    can't you just drive a normal copper grounding rod into the ground
    (usually 6 to 8 feet long) and connect a ground wire, connected
    to a common bar and ground all wiring to that, If your going to
    rewire the old place anyway. 
    
    P.S. I always thought tha inorder for a GFI circuit to work
    effectively, you have to have a good ground system already intact
    inorder to connect the GFI circuit breaker too????
291.420MTWAIN::WELLCOMESteve Wellcome (Maynard)Thu Jun 23 1988 16:2813
    The fact that neutral floats with respect to ground seems to me
    to be basically irrelevant to the way you want to do the wiring.
    Except at the main service panel (and ***ONLY*** at the main
    service panel), here in the U.S. the neutral is kept strictly
    separate from ground.  I'd think that you would want to do the
    same thing, except with the added premise that the neutral/ground 
    connection point for you is "somewhere else", outside your house, 
    and you have nothing at all to do with it, even at the main
    service panel.  Just keep neutral/ground separate everywhere.
    
    I think your idea of using the water pipe going to the well for
    your ground is good.  It ought to work just fine.  

291.421DCC::JAERVINENPeace thru superior firepowerFri Jun 24 1988 09:074
    re .6: A normal GFI doesn't rely on ground for its operation, it
    trips based on the difference in current in neutral and live
    (I think this has been discussed extensively elsewhere in this file).
    
291.422Not as complex as it seems at firstREGENT::GETTYSBob Gettys N1BRM 223-6897Fri Jun 24 1988 12:1717
                I think that the way you want think about this situation
        is to consider that the two wires which enter the house are both
        hot (think 220volt line here in US with only 220volt equipment
        hung from it - thus no neutral needed). Now it becomes obvious
        what to do. Wire up the ground to all the desired outlets and
        appliances, but NEVER connect it to either of the two "hot"
        wires coming into the house. 
                
                As for GFI's - use them anywhere that you would normaly
        use one (and they do sense on the difference between the two
        power carrying conductors) and forget about it otherwise.
        Remember that ground is there to keep the case of an appliance
        at a potential that would be safe for you to touch when you are
        grounded. It performs no other function at an appliance
        connection point.
                
                /s/     Bob
291.423PSTJTT::TABERTouch-sensitive software engineeringFri Jun 24 1988 13:1511
So I went back to Richter & Schwan and looked it up.  What I said about 
sub-panels was in error, and I've removed it from the file to avoid 
confusion to others.  (However, what I said IS the way the subpanel in 
my house is wired... more work to do, I guess.)

However, there was reason behind my madness, and it's this; if the 
neutral is developing voltage with respect to a local ground, then
equipment that uses ground for a reference will have problems.  There's
more to grounding than saftey, these days. 

					>>>==>PStJTT
291.439Should aluminum house wiring be replaced?CLT::DOUCETTEJoanne ShaughnessyWed Aug 03 1988 13:1811
    My husband and I are in the process of buying a house, and we
    just had it inspected and they found aluminum wiring throughout
    the house.  The house is 17 years old.  The inspector recommended
    that we have the branch circuitry changed to copper, and that
    rewiring was not neccessary.  
    
    Has anyone had any experience with this?  Is this procedure 
    satisfactory, and any idea what it costs?  
    
    thanks for any advice!
    -Joanne
291.440not an expert but...NAC::N_MORINWed Aug 03 1988 13:368
    I am not an expert but I seem to remember that aluminum wire was
    found to cause fires if not installed properly. I think the wire
    became loose after a period of time. Special procedures had to be
    followed to install aluminum properly. Notice that aluminum wire
    is not used in houses anymore. It may be in your best interest to
    consult with an electrician. Maybe you can use wire replacing as
    a bargaining chip to reduce the price. It is supposed to be a buyers
    market. Good luck.
291.441BEING::WEISSTrade freedom for security-lose bothWed Aug 03 1988 13:585
See also note 1450 for some discussion of aluminum wiring.  I left this note 
here to address the issue of whether the wiring should be replaced and if so 
how to go about it and how much it would cost.

Paul [Moderator]
291.442SMURF::WALLACELife's a beach, then you dive!Wed Aug 03 1988 15:179
    
    	RE: 0
    
    	I don't think it's necessary to replace the wire but you should
    	have an electrician check it out.  There is a "goop" used for
    	aluminum wiring to keep it from corroding and loosening as .1
    	suggested.  Although aluminum wire is no longer used in general
    	house wiring, 14-2, 12-2, the service entrance cables and most
    	other big stuff, is still all aluminum.
291.443should be no problems MPGS::PARTAINChuck Partain, KA1MWPWed Aug 03 1988 17:0414
    
    the goop is called no-al-ox.
    It is a cleaner/deoxidizing compound that keeps the aluminum from 
    becomming oxidized on the terminals. I have had NO problems for 12
    years except I have taken off the mains ands cleaned them with this
    stuff.
    ---------------------------- I DO NOT----------------------------
    recommend anyone but an experienced electrician doing this as the
    volts/amps are enough to ruin your day.
    ------------------------------------------------------------------
    
    If it has to be done at all.
    
    chuck
291.444POOL::HAMMONDCharlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684Thu Aug 04 1988 18:4215
>< Note 2520.3 by SMURF::WALLACE "Life's a beach, then you dive!" >
>
>                            ...the service entrance cables and most
>    	other big stuff, is still all aluminum.
      
      Service  Entrance  Cables  are  the ones from the meter box to the
      main breaker box, if I recall the code definitions. Or do you mean
      the  wires  from the transformer on the pole to the meter box?  In
      either case I thing your wrong. I know from first hand observation
      that  ALL  the  wires in my meter box are copper.  I think this is
      general practice.  The 'extra care' required for  Aluiminum  isn't
      worth it.
      
      However  on  the transmission line side of that transformer on the
      pole you're almost sure to find Aluminum.  
291.445HPSMEG::LUKOWSKINat'l apathy week &amp; nobody cares!Thu Aug 04 1988 19:2413
      It may depend on which electric company you are serviced by or
    whatever the electrician felt comfortable with.  I asked the electrical
    inspector about the aluminum wire at my house which is all of the
    wire from the pole to the breaker box.  He said that it is getting
    very uncommon to use copper wire for this cable since it costs so
    much more.  I'm guessing but I believe the numbers were something
    to the effect of $1.10/ft for aluminum and $3.50/ft for copper.
    I know that at least part of the wire to my cooking range is aluminum
    but I think it is only the ground wire.  As was said before, aluminum
    wire has been determined to be safe WHEN INSTALLED PROPERLY. 

    
    -Jim
291.446SMURF::WALLACELife's a beach, then you dive!Thu Aug 04 1988 20:178
    
    
    	Price is the key.  I have Aluminum entrance service cable from
    	the pole transformer to the meter box, and from the meter box
    	to the service circuit box.  All the wires from the service
    	to the house (individual circuits) are copper.  When you get
    	to #4 and larger wire sizes, I think you'll find aluminum to
    	be more popular. (cheaper)
291.447Aluminum just has to be used properlyFREDW::MATTHESThu Aug 04 1988 20:2421
    re last couple
    
    Right - WHEN INSTALLED PROPERLY.
    
    All the fame (on infame) that AL wire has received has been because
    it was used to wire houses and the Al just pushed into the Cu sockets
    on outlets.  Oxidation, expansion, contraction - high resistance
    connection - heat - fire.
    
    I recently installed a subpanel in the garage as well as changed
    over from 100 to 200 amp service.  The cable from the street is
    Al and the cable I used for the subpanel ~75 feet is Al.  The Al
    is at least 2 sizes larger the Cu I would have needed but is one-third
    the cost.  The 75' Al cable cost me $93.00.  I forget exactly what
    the quote was on the Cu but I know I nearly fainted.
    
    Then I got educated on how to install and work with Aluminum.  The
    problem was when they used it to wire houses, the electricians treated
    it the same as they did copper.  You can't do that.  And as long
    as you treat it properly, it's just as safe as copper.  And a hell
    of a lot cheaper.
291.448branch circuits and fixturesRETORT::GOODRICHTaking a long vacationFri Aug 05 1988 14:1617
    AL branch wires have 2 problems;
    
    In the 60s they were installed without proper treatment and
    with fixtures not suited for AL.
    
    The wires break easily if bent too many times.
    
    New branch wires can be very expensive to install, somewhat
    dependent upon the house construction.
    
    I would suggest checking all fixtures to ensure that they
    are suited and treated for AL wire. Be very careful not to
    bend the wires too many times - they will break.
    
    This may be a job for an electrician.
    
    - gerry
291.449POOL::HAMMONDCharlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684Fri Aug 05 1988 17:4225
      Continuing a theme from -.1 ...
      
      Yes,  if  aluminum wiring is installed correctly -- meaning proper
      wiring devices and proper installation techniques, which are  BOTH
      DIFFERENNT  from  whats  used with copper wire -- then it is safe.
      But will it stay that way?  Aluminum becomes  brittle  and  breaks
      easily when it is bent repeatedly and/or sharply. I've never lived
      in a home in which switches/outlest/light  fixtures  haven't  been
      changed  from  time to time, either to replace worn out devices or
      to modernize.  The simple act of disconnecting aluminum  wire  and
      reconnecting  it to a new device is usually more than the wire can
      safely tolerate.  In theory you should be able to do this  without
      significant  flexing  of  the  wire.   In pratice it is just about
      impossible.
      
      I  worked  for ALCOA for a while after I got out of college.  They
      had  (surprise!)   aluminum  wiring  and  whenever  they  replaced
      anything  they cut the wire back and butt spliced a new piece onto
      the end, just to avoid this problem.
      
      The  price argument is valid for heavier gages of wire, expecially
      since these tend to be 're-worked' less often.   As  for  aluminun
      anwhere  inside  the  breaker box, well, I might make some limited
      exceptions, but I think it is trouble looking for a place to happen.
      
291.466questions on rewiring motors for 220STEREO::COUTUREGary Couture - Govt. Syst. Group - Merrimack NHMon Oct 24 1988 16:4115
I am in the process of wiring my new workshop and would like to include 
some 220 circuits so I can run my larger tools on 220.  Can someone give me a 
quick lesson in whats involved in changing a motor to 220 and wiring for it?

- I plan to run 12/3 and use a 20 Amp breaker with probably only 2 boxes to a 
    breaker.

- I have not looked at the motors closely but I think the re-wiring diagrams 
   are on them.  But  do i need to replace the electrical cord?? 

- what type of outlet and plug do i need?


thanx

291.467Ck youer instruction bookletNSSG::FEINSMITHMon Oct 24 1988 18:508
    Check the instructions for the given tool. Many large power tools
    can be wired for either 110 or 220v. The type of plug/outlet is
    dependent on how much the unit draws and any local codes. A 220v/15A
    plug is different from a 20A plug, and even within the same current
    ratings, can be multiple styles (ie straight plug in, twist lock,
    etc).
    
    Eric
291.470Do you mean 12/3 wg or 12/2wg?GWYNED::MCCABETue Oct 25 1988 14:415
    By the way, most 220v tools do not need a neutral, unless you have
    a 100v lighting fixture. 12/2 wg should be fine, tape the white
    wire red in the outlet box and breaker panel.
    
    						Chris
291.365Send me the $63 and I will do it for you!OASS::B_RAMSEYBruce RamseyMon Oct 31 1988 22:3313
    My dad had the same problem in his house - his wife wanted the couch
    in the middle of the room with the lamp next to it.  He took a knife
    and made a slit in the carpet, drilled a whole thru the flooring
    big enough to fit a plug thru and then wired an outlet in the joist
    in the basement.  He stuck the plug thru the slit in the carpet,
    thru the hole in the floor and plugged it into the new outlet. 
    
    There is no cover plate at $63 and dog would have to be a REALLY
    good aim to be able to make it in the slit in the carpet and into
    the outlet on the joist.  You could move the outlet 6-10 inches
    away from the whole in the floor just as long as the cord from the
    lamp would go the distance.
   
291.366Don't try this at home, kidsHANNAH::DCLDavid LarrickTue Nov 01 1988 15:473
    .12 is, of course, in violation of the National Electrical Code.  I
    hope that the insulation on the lamp cord is in good shape, and that
    somebody inspects it frequently.
291.367BEING::WEISSTrade freedom for security-lose bothTue Nov 01 1988 16:5612
>    .12 is, of course, in violation of the National Electrical Code.  I
>    hope that the insulation on the lamp cord is in good shape, and that
>    somebody inspects it frequently.

Could you elaborate, Dave?  I know that it's a no-no to run a cord under a 
carpet, becuase of the wear of people walking on it and grinding dirt into the
insulation.  But if the hole in the floor were clean and smooth with no
projections that could damage the insulation, it seems like the outlet-in-the-
joists solution would work safely.  But I don't really know the electric code. 
Why is this dangerous and outlawed? 

Paul
291.368MTWAIN::WELLCOMESteve Wellcome (Maynard)Tue Nov 01 1988 16:595
    Re: .13
    
    Can you quote chapter and verse of what part of the code it violates?
    It seems as though it's one of those things that *ought* to be in
    violation of the code, but I'm not sure it is.
291.369No Code book here, but I'll work on it...HANNAH::DCLDavid LarrickTue Nov 01 1988 19:339
    re .14, .15:  I don't have my Code book handy, but I'll look it up and
    post the information when I get a chance.  The issue is probably that
    only permanent wiring may be run through structural members (such as
    floors), and lamp cord with a plug on the end is scarcely permanent
    wiring.
    
    It also makes sense to plug an appliance into an outlet that's located
    in the same room as the appliance, so you can unplug it conveniently
    and safely if it develops a short.
291.370STROKR::DEHAHNWed Nov 02 1988 13:508
    
    I'm with DCL, it's against Code. Temporary wiring can't be installed
    under carpeting. And any permanent receptacle must be surrounded
    with non combustable material. Thus you need an honest-to-goodness
    floor receptacle. It's your insurance loss.
    
    CdH
    
291.371MTWAIN::WELLCOMESteve Wellcome (Maynard)Wed Nov 02 1988 14:007
    The permanent receptacle down in the basement on the beam is
    certainly legal; it's in a legit box.  I'm not sure if lamp
    cords, etc. are classed as as "temporary wiring"; I thought temporary
    wiring was what you would do at a construction site, etc. until
    the real wiring was in: Romex tied together with wire nuts
    and dangling off nails driven into ceiling joists, etc.  The "under 
    the carpet" restriction might apply, but this is "through", not "under".
291.372The last word...maybe!GWYNED::MCCABEWed Nov 02 1988 16:2311
    The real problem here is there is a receptacle in the floor, ie
    the female cord cap. In my 1984 code book, 370-17 (b) on floor
    boxes, it states "boxes listed specifically for this application
    shal be used for receptacles located in the floor". The only
    exception is for show windows. You can not run lamp cord, SJ cable
    etc, through a wall or floor legally, only conduit, NM cable, BX,
    etc. Article 480-8 on flexible cords states " Flexible cords shall
    not be used (2) where run through holes in walls, ceilings or floors.
                                                     
    
    						Chris
291.373MTWAIN::WELLCOMESteve Wellcome (Maynard)Thu Nov 03 1988 11:542
    480-8 is it!  It's illegal.  Thanks for hunting that up.
    
291.471POOL::HAMMONDCharlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684Fri Nov 04 1988 17:1321
      1)  Check  the  directions that came with them motor/tool.  If you
      don't have  instructions  for  converting  vrom  110  to  220  you
      probably  can't  do  it.   i.e. the motor has to be designed to be
      convertable -- not all motors are.
      
      2) re .3 
          
>          Hopefully  you  mean *1* box to a breaker, this is 230V right?
>          Check the NEC, you are allowed  to  do  multiple  boxes  to  a
>          breaker only as an exception around 120V circuits, this is not
>          generally allowed.  
          
      Could  you be more specific, please?  I ask because I have two 230
      volt outlets and two 110 volt duplex outlets wired to a single  20
      amp  breaker in my "shop" (read "back of garrage").  Since all the
      wiring devices are rated for 20 amps (I think the 230 volt outlets
      are actually rate higher) I don't see any way I could overload the
      circuit without tripping the breaker (which I could probably do if
      I  plugged  in  and  ran enough stuff at the same time, but then I
      could also do that on a 110 volt circuit).  I also don't  see  any
      other hazzard.  What's the purpose of this code requirement?
291.472MILVAX::HOTue Nov 08 1988 20:3310
    re .5
    
    A 230 volt outlet wired to a single 20 amp breaker?  Is this possible?
    
    I thought two adjacent breakers ganged together were needed to get
    230 volts.  Otherwise the circuit is being fed by only one of the
    two hot legs in the panel.
    
    - gene
         
291.285why 110V not 240V ?GIDDAY::GILLARDEyeless in GazaWed Nov 09 1988 02:0322
Re: .9
>    The larger circuits that feed electric dryers, hot water heaters,
>    and stoves contain both a red and a black wire (along with one or
>    two others:  a white and possibly a bare).  The black wire gets
>    attached to one of the two insulated feeds from the power company,
>    while the red wire goes to the other insulated feed.  The smaller
>    110v circuits contain only a black wire, in addition to the white
>    and bare wires.  This can go to either of the above two feeds, but
>    the system as a whole should balance the load drawn from each feed
>    as closely as possible (it makes the power company very happy by
>    causing less wear and tear on their equipment!).

I've been meaning to ask this question for twelve months, and I'd better
ask it now bacause I'm going next week.

Pity an ignorant lad. Why do US domestic electrics use 110 V and have all
this damned tinkering around with load balancing and the like ?  Anyone
know why 240 V was not chosen as in most of the rest of the world ?

Just _very_ curious

Henry Gillard - TSC Sydney
291.473WILKIE::THOMSWed Nov 09 1988 11:0825
>< Note 2744.6 by MILVAX::HO >
>
>
>    re .5
>    
>    A 230 volt outlet wired to a single 20 amp breaker?  Is this possible?
>    
>    I thought two adjacent breakers ganged together were needed to get
>    230 volts.  Otherwise the circuit is being fed by only one of the
>    two hot legs in the panel.
>    
>    - gene
         
The two hot leg "busses" alternate down the panel on both sides.

Any double pole breaker inserted in the panel will attach to both legs.
				


			A	B
			B	A
			A	B
			B	A
		
Ross
291.474MTWAIN::WELLCOMESteve Wellcome (Maynard)Wed Nov 09 1988 12:142
    I assume by "single 20-amp breaker" the author must mean one double breaker.
    
291.286MTWAIN::WELLCOMESteve Wellcome (Maynard)Wed Nov 09 1988 12:196
    I suppose because for most domestic use, 240 volts is much more
    than is necessary; who needs 240 volts to run an electric shaver
    or a fan?  120 volts is presumably less dangerous in the case of
    accident, too.
    
    My guess.
291.287As explained to me by a power xmission guy...BOSTON::SWISTJim Swist BXO 224-1699Wed Nov 09 1988 12:4532
    re: .-1 
    There isn't enough safety difference between 120 and 240 for that to be
    an issue.


    The answer to your question is historical.
    
    It goes back to finding the right balance in the simple equation
    W = E*I.   What you need to run electrical things is power (measured
    in watts) - theoretically the volts and amps are irrelevant as long
    as when multiplied together they yield the power you need.  Practically
    speaking, too low a voltage will require too high a current - this
    is inefficient to transmit, requires huge transformers, expensive
    heavy wire, and heat buildup/fire problems if connections get loose.
    Too high a voltage can break down insulation easily, and is difficult
    to switch without expensive devices.
    
    I believe the history is that 120V was arrived at in the early days of
    power transmission planning as the best balance in the above equation
    (some old systems (USA as well as foreign) are still 120V).  What
    wasn't figured in the equation was the demand for electricity - no one
    figured it would find as many applications as it did.  Doubling the
    voltage was a fairly cheap solution to this problem since the
    insulation and switching problems are really not much worse at 240 than
    120.  The alternative of keeping the voltage the same and doubling the
    current would have meant rewiring a large percentage of users and
    transmission facilities. 
    
    That's the story as I understand it.  Upward compatibity, inertia,
    and history are all responsible for having both 110 and 240 devices
    as well as entire systems.
    
291.288WOODRO::THOMSWed Nov 09 1988 12:4617
>< Note 1742.21 by MTWAIN::WELLCOME "Steve Wellcome (Maynard)" >
>
>
>    I suppose because for most domestic use, 240 volts is much more
>    than is necessary; who needs 240 volts to run an electric shaver
>    or a fan?  120 volts is presumably less dangerous in the case of
>    accident, too.
>    
>    My guess.


I was always told in school etc., that 120v became an industry U.S. standard
at the turn of the century and stuck. Too costly to change.  Actually the
higher voltage appliances would be more efficient, motors lighter, less windings
and all that good stuff.


291.289BEING::WEISSTrade freedom for security-lose bothWed Nov 09 1988 12:530
291.290CRAIG::YANKESWed Nov 09 1988 17:185
    
    	Besides, when has the US ever worried about being standard?  Don't
    we still speak in terms of those silly inches and yards?? :-)
    
    								-c
291.475CHALK::HAMMONDCharlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684Fri Nov 11 1988 17:4923
>                      <<< Note 2744.7 by WILKIE::THOMS >>>
>
>The two hot leg "busses" alternate down the panel on both sides.

      I  believe that this is always, or almost always, the case for the
      type of breaker box you have in mind.  However,  there  are  other
      kinds! 
      
      I have a six position breaker box in my garage.  The breakers run
      across the box. The phases follow a pattern something like this: 
      
                  A B B A A B
      
      (This may not be exactly right since I don't have the box in front
      of me to look at, but the point is as follows.)  Obviously  it  is
      physically  possible to put a two-pole breaker in two positions in
      which both poles will  contact  the  same  phase.   It  is  highly
      unlikely  that there is any goo reason to do this; it would almost
      certainly violate the code prohibition of conductors  in  parallel
      (or  whatever).   This  box  is  clearly  labeled indicating where
      two-pole breakers may and may not be used.
      
      So...  Check your box before you plug in two pole breakers.
291.291CURIE::BBARRYFri Nov 11 1988 17:575
<    	Besides, when has the US ever worried about being standard?  Don't
<    we still speak in terms of those silly inches and yards?? :-)

	Inches/feet/miles is better then inches/feet/ kilometers they use in 
	Canada.:-)
291.476Double check please!WOODRO::THOMSFri Nov 11 1988 19:045
RE:9   Hmmm, Never run across a panel as you've described. Double check
the panel when you get a chance. If it is as you described, might be an old
panel, but the layout still doesn't make sense.

Ross
291.477POOL::HAMMONDCharlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684Mon Nov 14 1988 18:0930
>                      <<< Note 2744.10 by WOODRO::THOMS >>>
>                           -< Double check please! >-
>
>RE:9   Hmmm, Never run across a panel as you've described. Double check
>the panel when you get a chance. If it is as you described, might be an old
>panel, but the layout still doesn't make sense.

      No need to double check; I know the insides of it. It was used for
      our temporary electric service when our house was built.  I  saved
      it  when  the permanent electric was connected and installed it in
      our garage.  At that time I had it all apart to install a separate
      ground buss and to de-ground the neutral buss.  At that time I saw
      the actual shape  of  the  power  busses.   I'll  try  to  draw  a
      reasonable facsimile below.
     
              .-------------------------------. 
              |                            (A)|     (A),(B)--Place where 
              |  .----------.        .--------'             phases A & B 
              |  |.--------.|        |.--.               connect to buss      
              |**|| **  ** || **  ** ||**|                               
          =====1====2====3====4====5====6=====    ==== -- Bar onto which 
              `--'|        |`--------'|  |               breakers attach 
         .--------'        `----------'  |                               
         |(B)                            |        ** --   Point at which
         `-------------------------------'         breakers contact buss
      
      NOTE:  Neutral and (separate) Ground Buses not shown.  There is no
      "Main" breaker as this is a distribution panel.  (Its fed  from  a
      breaker  in  the  main  panel.  This may not be real accurate; the
      point is the SHAPE of the phase buses.
291.478What vendor?WOODRO::THOMSMon Nov 14 1988 18:286
Again, I've never seen a panel as you've described, doesn't mean that there 
aren't any. I've been a part time Master electrician for the past 14 years
and have seen a few odd ball panels. Who is the vendor of this particular
panel?

Ross
291.479MISFIT::DEEPThis NOTE's for you! Mon Nov 14 1988 19:208
re: .-1 Interesting!

On thing I notice is that if you want to put double breakers in the box,
you are ok as long as you put the double breakers in first, and single
breakers in last.  3 double breakers can be accomodated.   Weird, but 
functional.

Bob
291.480POOL::HAMMONDCharlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684Tue Nov 15 1988 13:2310
      RE .12, .13 
      
      I'll  try  to remember to check the brand/model on the box tonight
      and post it here.  If you'd like to come by in Bedfore NH and  see
      it  your welcome.  I assume its a perfectly standard box -- I went
      into Seamans Supply (sp?)  and asked for a temporary  service  and
      this is what they gave me.
      
      Meanwhile back at .5 -- can you answer the question there?
      (under 2)
291.481Check your loadWOODRO::THOMSTue Nov 15 1988 15:3038
>< Note 2744.14 by POOL::HAMMOND "Charlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684" >
>
>
>      RE .12, .13 
>      
>      I'll  try  to remember to check the brand/model on the box tonight
>      and post it here.  If you'd like to come by in Bedfore NH and  see
>      it  your welcome.  I assume its a perfectly standard box -- I went
>      into Seamans Supply (sp?)  and asked for a temporary  service  and
>      this is what they gave me.
>      
>      Meanwhile back at .5 -- can you answer the question there?
>      (under 2)



I think the question was (correct me if I'm wrong): Is it o.k. to have multiple
outlets on a 240v brach circuit?  The NEC says: Article 210-4 Multiwire
branch circuits (C) Line to Neutral Load. Multiwire branch circuits shall supply
only line to neutral load.

Exception No 1: A multiwire branch circuit that supplies only one utilization
equipment.

Exception No 2: Where all ungrounded conductors of the multiwire branch circuit
are opened simultaneously by the branch circuit overcurrent device.


Exception #2  is the key exception for your example. If you have the circuit 
protected by the proper size overcurrent device (circuit breaker) and when
the breaker trips it opens all ungrounded wires (hot), you're o.k..
However, I would be concerned on what load you're placing on that circuit!
Article 430-25 and 210-22 state you must calculate the first (largest) motor 
load (if over 1/8hp) at 125% full load current plus the sum of the other loads.
I bet that circuit you're using isn't up to the task of handling all of the
"possible" load. < It must be rated for the sum possible load!

Ross
291.482circuit protectionWILKIE::THOMSTue Nov 15 1988 16:1920
>< Note 2744.5 by POOL::HAMMOND "Charlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684" >
>          
>      Could  you be more specific, please?  I ask because I have two 230
>      volt outlets and two 110 volt duplex outlets wired to a single  20
>      amp  breaker in my "shop" (read "back of garrage").  Since all the
>      wiring devices are rated for 20 amps (I think the 230 volt outlets
>      are actually rate higher) I don't see any way I could overload the
>      circuit without tripping the breaker (which I could probably do if
>      I  plugged  in  and  ran enough stuff at the same time, but then I
>      could also do that on a 110 volt circuit).  I also don't  see  any
>      other hazzard.  What's the purpose of this code requirement?



You have the attitude that many home electricians have: Hey if I smoke the
wiring by placing too heavy a load on the circuit the breaker will protect me!
You should wire a circuit so the breaker will "never" have to trip due to
overload!

Ross
291.483POOL::HAMMONDCharlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684Tue Nov 15 1988 19:4525
>                      <<< Note 2744.16 by WILKIE::THOMS >>>
>
>You have the attitude that many home electricians have: Hey if I smoke the
>wiring by placing too heavy a load on the circuit the breaker will protect me!
>You should wire a circuit so the breaker will "never" have to trip due to
>overload!

      Re:  above -- Your admonishment is properly taken, but unneeded. I
      DON'T have that attitude. I was trying to understand what might be
      wrong with the way my shop is wired.  I didn't intend my (possibly
      poor choice of) wording to imply undue reliance on a breaker.
      
      Re:   .15 -- Thanks for the information.  O.K. Both conductors are
      controlled by one, two-pole 20 amp  breaker,  so  the  circuit  is
      within code in that regard.  Now as to the load -- nothing is hard
      wired into this circuit; it has 2-240v outlets and  2-120v  duplex
      outlets.  Some place I have information as to how to rate the 120v
      outlets; how do I rate the 240's?  
      
      My gut feeling is that I'm well within the limits. Reality is that
      the heaviest simultaneous load I  place  on  the  circuit  is  the
      radial arm saw plus a dust collecting shop vac.  (The 120v outlets
      are there for lesser tools, not  used  simultaneously.   But  that
      doesn't  mean  that some one, some day... After there are 2 of the
      240v outlets!  
291.484Sorry, But...MAMIE::THOMSTue Nov 15 1988 22:1730
>      
>      Re:   .15 -- Thanks for the information.  O.K. Both conductors are
>      controlled by one, two-pole 20 amp  breaker,  so  the  circuit  is
>      within code in that regard.  Now as to the load -- nothing is hard
>      wired into this circuit; it has 2-240v outlets and  2-120v  duplex
>      outlets.  Some place I have information as to how to rate the 120v
>      outlets; how do I rate the 240's?  
>      
>      My gut feeling is that I'm well within the limits. Reality is that
>      the heaviest simultaneous load I  place  on  the  circuit  is  the
>      radial arm saw plus a dust collecting shop vac.  (The 120v outlets
>      are there for lesser tools, not  used  simultaneously.   But  that
>      doesn't  mean  that some one, some day... After there are 2 of the
>      240v outlets!  


O.k., Let me put in my last two cents about your shop circuit!
I believe it's in violation of code due to the fact there is
the potential to overload this circuit. In real life, if you have the skill
and the knowledge to do proper wiring methods (good connections, properly
stripped wire, etc.), your circuit will probably never cause you a 
problem. However, what if you sell your house to a person that wants to
hook up his 2hp table saw, 3 hp compressor, a drill press and a shop
heater to this circuit? Let's also suppose that the 20 amp breaker fails
to trip at ~ 20 amps. (believe me this happens!)
Personally, I would stick with exception #1 that I quoted out of the NEC.
This recommends one multiwire circuit to one device/load.


Ross
291.485POOL::HAMMONDCharlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684Wed Nov 16 1988 16:4926
>                      <<< Note 2744.18 by MAMIE::THOMS >>>
>                               -< Sorry, But... >-
>
>O.k., Let me put in my last two cents about your shop circuit!
>I believe it's in violation of code due to the fact there is
>the potential to overload this circuit. ...

      I appreciate your opinion and I may in fact change this circuit.  

      On  the other hand you may have knowledge that you aren't sharing.
      I'm quite certain that "potential to overload" is not a cause  for
      any code violation. If it were, every circuit with an outlet on it
      would be in violation!  (Let alone circuites with muliple,  duplex
      outlets!)

      What  I have is a circuit that I'm certain is quite safe the way I
      use it.  I also don't think that this circuit presents any greater
      danger  than any of the other, clearly "code legal" circuits in my
      house. I had thought it met code requirements, but an earlier note
      raised a question about this.  
            
      In a previous reply I asked specifically HOW the code requires you
      to calculate the load froma 240v outlet.  By adding 2x the  result
      of  this  calculation  plus the load for the 2 110v duplex outlets
      I'll know if it meets code or not. Isn't this the correct thing to
      do?
291.486Send mail if you want to continue this argument!WILKIE::THOMSWed Nov 16 1988 17:4758
>< Note 2744.19 by POOL::HAMMOND "Charlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684" >
>
>      I appreciate your opinion and I may in fact change this circuit.  
>
>      On  the other hand you may have knowledge that you aren't sharing.
>      I'm quite certain that "potential to overload" is not a cause  for
>      any code violation. If it were, every circuit with an outlet on it

You're dead wrong! Home circuits are certainly designed "not" to be overloaded!
Why do you think the code requires (2) 20 amp circuits in the Kitchen, (where
the potential to overload is the greatest in a home). Also, don't confuse
living space with shop area, two totally different areas.


>      would be in violation!  (Let alone circuites with muliple,  duplex
>      outlets!)
>
>      What  I have is a circuit that I'm certain is quite safe the way I
>      use it.  I also don't think that this circuit presents any greater
>      danger  than any of the other, clearly "code legal" circuits in my
>      house. I had thought it met code requirements, but an earlier note
>      raised a question about this.
  
 I'm glad you don't wire houses for living. If you wire a problem in, at least
it will be yours.
           
>      In a previous reply I asked specifically HOW the code requires you
>      to calculate the load froma 240v outlet.  By adding 2x the  result
>      of  this  calculation  plus the load for the 2 110v duplex outlets
>      I'll know if it meets code or not. Isn't this the correct thing to
>      do?

I believe I told you how to calculate the load on your shop circuit in one of 
my previous replies. There is no formula like X # of amps/outlet (like there is 
for living space, 120v circuits). Mulitwire cicuits are sized to the "load".
BTW, I bet any good electrical inspector would fail your circuit due to the
reasons I stated in earlier replies. (I'll re-state : "the potential to overload
the circuit you've described is too great").

Let's suppose you have a  3hp compressor, a 2hp saw, a 1000 watt heater and a
3/4 hp drill press attached.

3hp x 746w /240 x 1.25 = 11.7 amps

2hp x 746w /240        =  6.2

3/4 x 746w /120        =  4.7

     1000w /120	       =  8.3    (Portable, not fixed)
------------------------------
			 30.9 amps

This example is basically the equipment I have in my shop.
My table saw is wired 120v. Each piece has it's own dedicated circuit with
the exception of the portable heater which is rarely used.


Ross
291.487WRONG!MISFIT::DEEPThis NOTE's for you! Wed Nov 16 1988 18:5024

Typical home circuit, with the potential to plug 8 items in...(4 duplex
outlets)...

OK... I plug in my 1500 watt heater, my 1200 watt hair dryer... (that's 2)

Now, I plug in 6 more heaters  (because I ran out of oil) ...  My wiring
is to code, and I've just exceeded the limit.  Of course the breaker 
trips (if its working...whens the last time you toggled your breakers?)

What .-2 was trying to say is that it IS POSSIBLE to exceed the limits on 
the normal BY THE CODE circuits.  

Of course, the above senario is extremely stupid, but it proves the point.

I ran a dedicated 220v circuit for my table saw, and I have two outlets...
one in the garage and one in the cellar.  The only thing I own that is
220 is the saw, and it can't be on both outlets at the same time.
When I move, I'll pull one of the outlets and take it with me.  If that's
against the codes then the codes are wrong, and I'm not going to worry
about it.

Bob
291.488I'm glad it's your houseSTROKR::DEHAHNWed Nov 16 1988 19:066
    
    You should have a seperate circuit for your garage, preferably a
    subpanel.
    
    CdH
    
291.489MAMIE::THOMSWed Nov 16 1988 19:0843
>< Note 2744.21 by MISFIT::DEEP "This NOTE's for you! " >
>                                  -< WRONG! >-
>
>
>
>Typical home circuit, with the potential to plug 8 items in...(4 duplex
>outlets)...
>
>OK... I plug in my 1500 watt heater, my 1200 watt hair dryer... (that's 2)
>
>Now, I plug in 6 more heaters  (because I ran out of oil) ...  My wiring
>is to code, and I've just exceeded the limit.  Of course the breaker 
>trips (if its working...whens the last time you toggled your breakers?)

Come on give me a break! The code is written to cover most "normal" situations.
Your scenario is absurd.



>What .-2 was trying to say is that it IS POSSIBLE to exceed the limits on 
>the normal BY THE CODE circuits.  

Yeah and the code is written to make the possible overload conditions minimal!


>Of course, the above senario is extremely stupid, but it proves the point.

The only point you've proven is wiring should be left to professionals that
are licensed by the State.

>I ran a dedicated 220v circuit for my table saw, and I have two outlets...
>one in the garage and one in the cellar.  The only thing I own that is
>220 is the saw, and it can't be on both outlets at the same time.
<When I move, I'll pull one of the outlets and take it with me.  If that's
>against the codes then the codes are wrong, and I'm not going to worry
>about it.
>
>Bob

Why tell me, why don't you write to the NEC and convince them that you know more
about correct/safe wiring procedure than they do and the code should be changed.

Ross
291.490Let's lighten upRGB::SEILERLarry SeilerWed Nov 16 1988 21:2324
re .1-:  The point here is that, for 110V circuits, the code does **not**
prevent overloads, it just tries to make them unlikely.  Lots of people
pop their circuit breakers, so it isn't fair to say that the code prevents
overloads in all "normal" situations.

The rules for 220V circuits are apparently must more restrictive, but even
they do not seem to totally prevent the possibility of an overload.

So I'd say that, while following the code is important, understanding
the reasons behind the code rules is even more important.  That's what 
this note used to be about.  I'd guess that none of us have houses that 
are 100% code compliant (I've found really awful examples in my house),
so it is important to understand which things are really bad (eg, I've taped
over my outlet with hot and neutral reversed until I fix it) and which 
aren't as serious (eg, .-2 shouldn't have two 220V outlets on one breaker, 
but so long as only one is used at a time, it can be fixed later).


Now, back to business.  I'd like to know if one should test circuit
breakers.  If so, how?  Is physically flipping them enough?  How can
I be sure that my 15A breaker is really going to trip if I one day
accidentally put 20A through it?  

	Larry
291.491I give up!WILKIE::THOMSWed Nov 16 1988 21:5852
>< Note 2744.24 by RGB::SEILER "Larry Seiler" >
>                             -< Let's lighten up >->
>
>re .1-:  The point here is that, for 110V circuits, the code does **not**
>prevent overloads, it just tries to make them unlikely.  Lots of people
>pop their circuit breakers, so it isn't fair to say that the code prevents
>overloads in all "normal" situations.

I agree to the point that it is always possible to overload a circuit. But
if a circuit is wired to code, an overload is "not" a normal occurrence. A
homeowner would have to do something really stupid! 

>The rules for 220V circuits are apparently must more restrictive, but even
>they do not seem to totally prevent the possibility of an overload.
>
>So I'd say that, while following the code is important, understanding
>the reasons behind the code rules is even more important.  That's what 
>this note used to be about.  I'd guess that none of us have houses that 
>are 100% code compliant (I've found really awful examples in my house),

I wired my Nashua home in 1982. I had three electrical inspections by an
inspector that overruled the code to be more stringent in certain circuits.
My home passed 100%, no calls. Some of the really awful examples you've
found in your house probably came about from some past homeowner doing
his own wiring. I know and have seen/repaired some truly unbelievable
wiring jobs.


>so it is important to understand which things are really bad (eg, I've taped
>over my outlet with hot and neutral reversed until I fix it) and which 
>aren't as serious (eg, .-2 shouldn't have two 220V outlets on one breaker, 
>but so long as only one is used at a time, it can be fixed later).

That's o.k. if this homeowner wants to run a circuit (in his own house)
in this manner. But don't tell me the code is wrong because (in this case) the 
homeoowner is either unable or unwilling to do a proper job.

>Now, back to business.  I'd like to know if one should test circuit
>breakers.  If so, how?  Is physically flipping them enough?  How can
>I be sure that my 15A breaker is really going to trip if I one day
>accidentally put 20A through it?  

>	Larry

No, flipping the breakers will tell liitle about the breaker. Sometimes a
breaker will go bad and not be able to be reset.  (Safe failure).
The only way to test your breakers would be to pull them from the circuit
and set up some kind of test load. Not really feasable.
Again, the key to a safe circuit is to set it up so it's not normally
in an overload condition. 

Ross
291.493MISFIT::DEEPThis NOTE's for you! Thu Nov 17 1988 12:3047
Well!  Since my intent was to draw a little heat away from the guy everyone
was beating up on for a simple question, I guess I was successful!  8-)


>>(eg, .-2 shouldn't have two 220V outlets on one breaker, 
>>but so long as only one is used at a time, it can be fixed later).
>That's o.k. if this homeowner wants to run a circuit (in his own house)
>in this manner. But don't tell me the code is wrong because (in this case) the 
>homeoowner is either unable or unwilling to do a proper job.

First of all, lets remember why the code is there in the first place.  It's
to establish a safe set of standards for electricians to use to keep them
from getting sued when your house burns down.  It's extra protection for
the insurance companies, because if they can prove your house was not wired
to code, they can get out of paying you.

The code is not BIBLE and is not practical for all occurances.  In some it is
inadequate (for my peace of mind) and for others, overkill.   I have no problem
sleeping at night with a circuit that runs from my panel in the garage to the 
workshop in the cellar, with two 220v outlets on it, knowing that only one
can be used at a time.  I wouldn't leave it that way for the next guy who might
own two 220v tools.  The code says that I am in violation, and I say that the 
code was not written to take into account a person who only owns one 220v 
device, and wants to use it in two possible places.   I am neither unable
nor unwilling to do a proper job... I have!  It just isn't according to the
code, which is not designed for this particular occurance.   Thats called
making an intellegent decision, and people are still allowed to do that
once in a while, regardless of the insurance companies, and lawyers, and
inspectors, and I resent the implication that I am an accident waiting to 
happen, simply because I use some common sense.

Dismantle SOAPBOX  (according to code, of course)  8-)

Now then:

>No, flipping the breakers will tell liitle about the breaker. Sometimes a
>breaker will go bad and not be able to be reset.  (Safe failure).

Right, but flipping the breaker WILL tell you if its frozen closed... the most
common failure, usually due to corrosion from high humidity or the elements.
The feel of the breaker as it is toggled can also tell you if it may be
gunking up...(that's a technical term!) 8-)

Now then...  what does ALL this have to do with rewiring 220v motors? 8^)

Bob
291.494MAMIE::THOMSThu Nov 17 1988 13:0573
>< Note 2744.27 by MISFIT::DEEP "This NOTE's for you! " >
>
>
>
>Well!  Since my intent was to draw a little heat away from the guy everyone
>was beating up on for a simple question, I guess I was successful!  8-)


No Bob, I don't feel we were beating up on anyone. It was a disagreement and
I certainly hope no feelings were hurt. However, I was asked about a particular
circuit and I gave my thoughts. I'm open to any argument about safe wiring and
don't profess to know all of the answers. I did work as an Apprentice 
electrician, took many hours of classroom on wiring and passed the State exam
to become a Journeyman electrician, than later Master electrician. But then
again, I currently don't work electrical problems daily or even weekly.



>First of all, lets remember why the code is there in the first place.  It's
>to establish a safe set of standards for electricians to use to keep them
>from getting sued when your house burns down.  It's extra protection for
>the insurance companies, because if they can prove your house was not wired
>to code, they can get out of paying you.
>
>The code is not BIBLE and is not practical for all occurances.  In some it is
>inadequate (for my peace of mind) and for others, overkill.   I have no problem


The NEC is the Bible for safe wiring. If you want to disregard it in your own
wiring, that's your call.


>sleeping at night with a circuit that runs from my panel in the garage to the 
>workshop in the cellar, with two 220v outlets on it, knowing that only one
>can be used at a time.  I wouldn't leave it that way for the next guy who might
>own two 220v tools.  The code says that I am in violation, and I say that the 
>code was not written to take into account a person who only owns one 220v 
>device, and wants to use it in two possible places.   I am neither unable
>nor unwilling to do a proper job... I have!  It just isn't according to the
>code, which is not designed for this particular occurance.   Thats called
>making an intellegent decision, and people are still allowed to do that
>once in a while, regardless of the insurance companies, and lawyers, and
>inspectors, and I resent the implication that I am an accident waiting to 
>happen, simply because I use some common sense.
>
>Dismantle SOAPBOX  (according to code, of course)  8-)

Again, If you want to disregard the code, fine. Just make sure you don't tell
the Municipality you live in about it.

>Now then:


>Right, but flipping the breaker WILL tell you if its frozen closed... the most
>common failure, usually due to corrosion from high humidity or the elements.
>The feel of the breaker as it is toggled can also tell you if it may be
>gunking up...(that's a technical term!) 8-)
>
>Now then...  what does ALL this have to do with rewiring 220v motors? 8^)

>Bob


Like I said, flipping the breakers will tell you little about their condition.
One of my college professor's once did a lab experiment for our class. He 
randomly picked new breakers and tested them at the rated capacity. If I
remember correctly approx. 10% didn't trip anywhere near their ratings.
This professor was an old time electrical engineer that used to design
many electrical components for Westinghouse, very knowlegable in electrical
equipment.


Ross
291.495Sizing conductors for motors etc.WOODRO::BERKNERTom Berkner 264-7942 MK01Fri Nov 18 1988 19:3444
    Last night as a way to waste an evening, I looked up the multiple
    receptical problem in the NEC 1987 edition.
    
    In article 210-19 it says:
    GENERAL.  Branch-circuit conductors shall have an ampacity not less
    than the maximun load to be served.  In addition, conductors of
    multioutlet branch circuits supplying receptacles for cord- and
    plug-connected portable loads shall have an ampacity of not less
    than the rating of the branch circuit. ...
    (FPN):See Part B of Article 430 for minimum rating of motor
    branch-circuits ....
    220-3.  Computation of Branch Circuits. ...
    (c)Other loads -- all Occupancies.
    (2)Outlet for motor load      See Sections 430-22,-24 and 440.
    (5)*Other outlets      180 volt-amperes per outlet
    For receptacle outlets, eachj single or multiple receptacle shall
    be considered at not less the 180 volt-amperes.        
    
    [Basically this says to figur 180VA (1.5amps) per outlet regardless
    of whether it has 1, 2, 4 or more recepticals included + add the
    motor loads as determined in article 430. -tom]
    
    Article 430.24 says:
    
    CONCUCTORS SUPPLYING SEVERAL MOTORS.  Conductors supplying two or
    mote motors shall have an ampacity equal to the sum of the full-load
    current rating of all the motors plus 25 percent of the highest
    rated motor in the group.
     
    Where one or motors of the group are used on
    short-time, intermitent, periodic, or varying duty, the ampacity
    of the conductors shall be computed as follows:
    
    (1)Determine th needed amprere rating for each motor used for other
    than continuous duty from Table 430-22(a) Exception. [table says
    use 90% of nameplate current rating -tom]
    
    (2)[pertains to continuous duty -tom]
    
    (3)Multiply the largest single motor ampere rating determined from
    (1) or (2) above by 1.25.  Add all other motor ampere ratings from
    (1) and (2) above and select the conductor ampacity for this total
    ampere rating.
                                   
291.496MAMIE::THOMSMon Nov 21 1988 11:3483
>< Note 2744.29 by WOODRO::BERKNER "Tom Berkner 264-7942 MK01" >
>                     -< Sizing conductors for motors etc. >-
>
>    Last night as a way to waste an evening, I looked up the multiple
>    receptical problem in the NEC 1987 edition.
>    
>    In article 210-19 it says:
>    GENERAL.  Branch-circuit conductors shall have an ampacity not less
>    than the maximun load to be served.  In addition, conductors of
>    multioutlet branch circuits supplying receptacles for cord- and
>    plug-connected portable loads shall have an ampacity of not less
>    than the rating of the branch circuit. ...
>    (FPN):See Part B of Article 430 for minimum rating of motor
>    branch-circuits ....
>    220-3.  Computation of Branch Circuits. ...
>    (c)Other loads -- all Occupancies.
>    (2)Outlet for motor load      See Sections 430-22,-24 and 440.
>    (5)*Other outlets      180 volt-amperes per outlet
>    For receptacle outlets, eachj single or multiple receptacle shall
>    be considered at not less the 180 volt-amperes.        
>    
>    [Basically this says to figur 180VA (1.5amps) per outlet regardless
>    of whether it has 1, 2, 4 or more recepticals included + add the
>    motor loads as determined in article 430. -tom]
 
You're correct in this statement for normal household branch circuits, with
the exception you didn't point out: small appliance branch circuits (kitchen).
However, for the shop question 220.3 (c)  (1) Outlet for a specific appliance
or other load except for a motor load................. ampere rating of
appliance ot load served. 

		and.
(2) Outlet for a motor load................ See Sections 430-22 and 430-24 and 
Article 440.

These are the pertinent passages. The 180 volt-amp calculation is for
"occupancies" (branch circuits).




   
>    Article 430.24 says:
>    
>    CONCUCTORS SUPPLYING SEVERAL MOTORS.  Conductors supplying two or
>    mote motors shall have an ampacity equal to the sum of the full-load
>    current rating of all the motors plus 25 percent of the highest
>    rated motor in the group.
>     
>    Where one or motors of the group are used on
>    short-time, intermitent, periodic, or varying duty, the ampacity
>    of the conductors shall be computed as follows:
>    
>    (1)Determine th needed amprere rating for each motor used for other
>    than continuous duty from Table 430-22(a) Exception. [table says
>    use 90% of nameplate current rating -tom]


Say what??? "Any motor applications shall be considered as continuous duty 
unless the nature of the apparatus it drives is such that the motor will
not operate continuously with load under any condition of use." (fine print
on the bottom of 430-22(a)).

I say Exception No. 1: Conductors for a motor used for short time, intermittent,
periodic, or varying duty shall have an ampacity not less than the percentage
of the motor nameplate current rating shown in Table 430-22 (a)
Exception unless the authority having jurisdiction grants special permission
for conductors of smaller size. 

Try Varing duty, continuous rated motor! 
    
>    (2)[pertains to continuous duty -tom]
>    
>    (3)Multiply the largest single motor ampere rating determined from
>    (1) or (2) above by 1.25.  Add all other motor ampere ratings from
>    (1) and (2) above and select the conductor ampacity for this total
>    ampere rating.
                                   

Agreed, I stated this before.

Ross

291.497MAMIE::THOMSMon Nov 21 1988 12:5920
I just re-read my last reply (hastily written) and I don't think I gave
enough information. What I wanted to say is the 180 volt/amp branch circuit
calculation is for occupancies, such as living rooms, bed rooms, etc. 
Shop loads are a different story, see last note for pertinent articles in the
code. 
Tom, The chart you were using, 430-22 (a) is an exception chart for motors
that see varying duty such as elevators, welders, conveyors, etc. Depending
on the application, these motors are either lightly used, intermittent, light
loads or "hammered" on or off with a full load. That's why the charts there.
The lightly loaded, lightly used motors would be rated at less than the full 
load current and the on/off heavily loaded motors are rated at a high 
percentage.
Tom, if you wanted to try and use that particular chart for a shop application
such as a table saw, the Varying Duty, Continuous rated motor would apply. This
is an overkill for a normal shop circuit and a continuous duty motor.
The motors we were discussing are Continuous Duty and should be rated at 125%
full load current. If multiple motors are on the same circuit, the first/largest
motor is rated at 125% and the next at 100%.

Ross
291.498POOL::HAMMONDCharlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684Mon Nov 21 1988 19:2627
      In reading the last few replies I could conclude that every outlet
      in my shop should be on a separate breaker,  and  that  even  this
      would be illegal since some yo-yo could plug an overload into that
      outlet. Of course that's absurd and of course I don't think anyone
      intended  that  message.  (But what difference does it make if set
      the saw for 120 vs 220 and plug it in????)
      
      Which  comes  back  to  the question I tried to ask at least twice
      before and which I'll now re-word, perhaps better:
          
          In  a home, 120v outlets are rated at 1.5 amps for purposes of
          determining the load on a circuit. What load factor applies in
          a "shop" for 120v and 220v circuits which are not dedicated to
          specific equipment?  
          
          The  implicit  question  here  is  something like "what is the
          difference between what I have and just pluging the  saw  (set
          for 120v) into any of the outlets in my home?
      
      If  there's  an answer to this in previous replies I can't pick it
      out.
      
      BTW  using  1.5  amps  per  120v  outlet and 225% of the nameplate
      amperage (figuring a possible second device of  the  same  rating)
      from  my  saw  my  circuit  is loaded to ~18-19 amps, which surely
      sounds O.K. to me for a 20 amp circuit.  (I did  this  at  home  a
      couple days ago and don't have the actual figures in front of me.)
291.499Someone else pleaseWILKIE::THOMSMon Nov 21 1988 21:1745
>< Note 2744.32 by POOL::HAMMOND "Charlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684" >
>
>
>      In reading the last few replies I could conclude that every outlet
>      in my shop should be on a separate breaker,  and  that  even  this
 
Listen, you've about got it! Basically you should have separate circuits
for your heavier loads. How many diy out there have plugged in a good size
table saw to a regular 15 amp branch circuit and tripped the breaker when
starting the saw or ripping some thick wet wood? I have and I bet many
have done the same. I recommend running separate circuits to your more
or less fixed equipment (table saw, compressor, drill press, mig welder etc.)
I definitely like to have my 240v circuits, separate.

>     would be illegal since some yo-yo could plug an overload into that
>      outlet. Of course that's absurd and of course I don't think anyone
>      intended  that  message.  (But what difference does it make if set
>      the saw for 120 vs 220 and plug it in????)
>      
>      Which  comes  back  to  the question I tried to ask at least twice
>      before and which I'll now re-word, perhaps better:
>          
>          In  a home, 120v outlets are rated at 1.5 amps for purposes of
>          determining the load on a circuit. What load factor applies in
>         a "shop" for 120v and 220v circuits which are not dedicated to
>          specific equipment?  
>          
>          The  implicit  question  here  is  something like "what is the
>          difference between what I have and just pluging the  saw  (set
>          for 120v) into any of the outlets in my home?
>      
>      If  there's  an answer to this in previous replies I can't pick it
>      out.
>      
>      BTW  using  1.5  amps  per  120v  outlet and 225% of the nameplate
>      amperage (figuring a possible second device of  the  same  rating)
>      from  my  saw  my  circuit  is loaded to ~18-19 amps, which surely
>      sounds O.K. to me for a 20 amp circuit.  (I did  this  at  home  a
>      couple days ago and don't have the actual figures in front of me.)


Geez Charlie, I don't know how else to tell you. I've quoted code, I've come 
flat out and told you in the plain English. I give up, anyone else want to try?

Ross
291.501How can we make this better?POOL::HAMMONDCharlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684Tue Nov 22 1988 19:1357
>                      <<< Note 2744.33 by WILKIE::THOMS >>>
> 
>I definitely like to have my 240v circuits, separate.

      Beleive it or not, this was apparent from your various replies.

      O.K.  'nuff  o'  this.  Lets talk for a moment about some possible
      ways to make this situation better.  
      
      The  garrage has a six position breaker box which is fed from a 50
      amp breaker in the main breaker box.  At present these are used as
      follows:   Position 1 -- inside lights in the garrage and enclosed
      breezway. Position 2 -- outslide lights. Position 3 & 4 -- the now
      infamous  shop  circuit.   Position 5 -- garrage door openers (2).
      Position 6 -- outlets in the garrage and breezway  (excluding  the
      "shop").   All of these are 20 amp circuits.
      
      Running  additional  circuits  from the main box is not reasonable
      because most of the wiring is inside a wall.  Installing a  larger
      breaker  box in the garrage is not reasonable for the same reason,
      but adding a second box in the garrage may be reasonable. (see D &
      E) 
          
      Here's some ideas in order of difficulty -- easiest first.
      
      (A)  I  could  easily  eliminate one of the two 240v outlets.  Any
      future 240V tools would have to take turns.
      
      (B)  I  could  move  the  4 110v outlets (2 duplex outlets) to the
      circuit which is now used only for the garrage door  openers  (two
      garrage  doors).   I don't like this idea because (1) simultaneous
      use of both garrage doors and some tools could  possibly  overload
      the  circuit,  and  (2)  I like to be able to turn off the garrage
      door openers independently -- like when I have  something  leaning
      on them.  
      
      (C) I could run #10 wire and upgrade the entire circuit to 30 amps.
      
      (D) I could run #10 wire to the shop and install a new breaker box
      with a 20 amp 240v and 2 15amp 110v circuits. This would mean that
      a shop distribution panel would be attached to a 30 amp circuit in
      the garage distribution panel which is, in turn, attached  to  the
      main breaker box.  Would this be legal?  (I'm not certain that I'm
      using the terms "distribution panel" and "breaker  box"  according
      to any NEC definition here.)

      (E)  I could continue the 50 amp feed from the main breaker box on
      to a second box in the  garrage  and  use  this  to  feed  several
      seperate  circuits  to the shop.  There's enough space next to the
      current box for another small (4-6  position)  box.   (This  might
      actually be easier than (D) because I could probably still use the
      existing circuit for the 240V outlet(s).  

      I'll appreciate any and all comments on these ideas.

      ...and  since  I  won't  see your replies till after Thanksgiving,
      have a happy Thansgiving.
291.502My 2 cents worthWILKIE::THOMSWed Nov 23 1988 11:3339
>< Note 2744.35 by POOL::HAMMOND "Charlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684" >
>                       -< How can we make this better? >-
>
>>                      <<< Note 2744.33 by WILKIE::THOMS >>>
>> 
>>I definitely like to have my 240v circuits, separate.
>
>      Beleive it or not, this was apparent from your various replies.
>
>      O.K.  'nuff  o'  this.  Lets talk for a moment about some possible
>      ways to make this situation better.  
>      
>      The  garrage has a six position breaker box which is fed from a 50
>      amp breaker in the main breaker box.  At present these are used as
>      follows:   Position 1 -- inside lights in the garrage and enclosed
>      breezway. Position 2 -- outslide lights. Position 3 & 4 -- the now
>      infamous  shop  circuit.   Position 5 -- garrage door openers (2).
>      Position 6 -- outlets in the garrage and breezway  (excluding  the
>      "shop").   All of these are 20 amp circuits.
 
O.k., Here's what I would do: If you're currently only running (1) 240v tool,
wire in (1) appropriate amperage outlet using position 3 & 4. Combine circuits
1 & 2 to one breaker  (#1), Run a new 20 amp circuit off of postion #2 with
(2) duplex outlets in convenient locations. If you add another 240v piece of
equipment, calculate the the "new" load on circuit #3 & 4 and if acceptable,
add a second outlet. 

This is the easiest and safest way to redistribute the loads as I see it. 
However, You might be able to do something with the lighting and breezeway
circuits. I don't know the area size or number of outlets, number of
outside lights, etc.
Another option might be running a new breezeway circuit from the main service
and in doing this, freeing up sub panel space and allowing you to add another
240v circuit in the future.


     

Ross
291.503combine and dedicateMAMIE::BUTTONfeet on ground,head in twilight zoneMon Nov 28 1988 13:265
    Combining the 120v circuits is the way to go.  Getting the right
    conbination so that overhead lights stay on if receptacles pop is
    the tricky part.  Dedicate your high load 240v circuits.
    
    					paul b
291.504PEEK::HAMMONDCharlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684Wed Nov 30 1988 13:2914
      RE: .36 & .37 -- Thanks.
      
      After  thinking  about this over turkey, etc., I realized that the
      "key" is to combine the 2 lighting circuits to free up a  position
      for  a  dedicated  120v  outlet  circuit in the "shop".  I'll also
      remove one of th 240v outlets.
      
      What  is/are  your  opinion(s)  on  those  breakers  which put two
      circuits on one position in the box?  I was thinking about  useing
      one  of these for the two lighting circuits.  I think they only go
      to 15 amps max, but thats no problem -- although wired for 20 amps
      (as are all circuits in my house) neither of the lighting circuits
      would even come close to 15 amps.  (i.e they'd  easily  fit  on  a
      combined 20 amp circuite.)
291.505Rathole alarmHANNAH::DCLDavid LarrickWed Nov 30 1988 14:2710
               <<< Note 2744.39 by HANNAH::DCL "David Larrick" >>>
                               -< Rathole alarm >-

.38 set off my rathole alarm - rather belatedly for this topic!  The double
breaker that fits in a single slot is a subject of sufficient general
interest, and sufficiently unrelated to "rewiring motors for 220", that
I've started a new topic in 2846.  Please, let's continue this particular
tangent there.

			DCL with moderator hat on
291.506DISABLING ELECTRIC WIRESWMOIS::C_GIROUARDWed Dec 28 1988 11:4214
    I've looked, but have not been able to find anything in the file.
    I am in the process of refinishing my foyer. The contractor put
    a small (independently controlled) electric baseboard heater there.
    I will be doing some wain's coating (sp?) there. Since I have never
    used the heater in its trhee year existence I want the thing out!
    
    The question is can I just cap the wires with wire nuts. Does it
    get more complicated if the heater is on a circuit with other things
    that I can't disable. 
    
    Any suggestions on the best course of action. I want to do the easiest
    and safest thing!
    
    Chip
291.507STROKR::DEHAHNWed Dec 28 1988 12:2223
    
    Forget about the easiest or safest way, you should do it by the
    Code. That way you're covered if there's a fire.
    
    Remove the power to the circuit by the switch or overcurrent device.
    Then remove the wires from the heater. Trace the wires back to the
    junction box they originated from. Disconnect and remove the wires
    from the jbox that go to the heater. Then all you have is a wire
    that's disconnected at both ends. If the power for the heater
    originates in it's own circuit in the panel, then you have to
    disconnect main power, pull the breaker, and replace it with a blank
    breaker cover.
    
    If you plan to use the heater, or that circuit, in the future, then
    you can remove the wires to the heater, and install a junction box
    in the area. Install the wires in the jbox with the proper hardware,
    wire nut the ends (a little tape over the nuts won't hurt), and
    close up the box with the proper cover.
    
    Both ways are safe and should be legal in your area.
    
    CdH
    
291.508ALTERNATIVEWMOIS::C_GIROUARDWed Dec 28 1988 16:194
    Thanks. Maybe I will put an outlet there as an alternative as there
    isn't one now.
    
    Chip
291.509is it 110 or 220?NSSG::FEINSMITHI'm the NRAWed Dec 28 1988 16:595
    Just make sure if the feed is 110v or 220v before installing an
    outlet (hint-usually a 220 feed uses black and red wires for the
    hot).
    
    Eric
291.510THANKSWMOIS::C_GIROUARDThu Dec 29 1988 10:003
    Will do and thanks.
    
    Chip
291.511Three wires for split outletPOLAR::PENNYFor the Benefit of Mr. KiteThu Jan 05 1989 19:2120
    I don't know about the States, but here in Canada you can't take
    a two wire 220 volt feed and split it into two 110 volt lines *without*
    a white neutral(sp?) wire. 
    
    Heaters are usually 220 volt, two wire. (Two conductors (red/black)
    and a bare ground wire). Otherwise you'd be drawing twice the power 
    (current) through the line. (Read WIRE HEAT and breaker load -
    you can only load your breaker to 80% of its rating. (Canada again)).
    You would need a *large* breaker 30 : 40 Amp instead of 15 : 20
    Amp. Now, split receptacles are allowed (usually manditory (X3)
    for kitchen counter outlets). You need a three wire feed
    (black/red/white) with a bare ground. Black and red are HOT lines,
    white is neutral. The black and red wires go on the brass colored
    terminals of the outlet, (AFTER BREAKING OFF THE TAB THAT CONNECTS
    THE BRASS COLORED SCREWS "PLATE" TOGETHER!). You'll see it sort of 
    between the screws. The white wire is secured to the silver colored 
    screws, without breaking the tab on that side. Ground (bare) goes 
    to the green ground screw on the outlet.
    
    IF A SPLIT OUTLET IS NOT INSTALLED THIS WAY, IT IS ILLEGAL. 
291.512TRITON::CONNELLDown on Toidy-toid 'n Toid AvenueFri Jan 06 1989 11:3611
>< Note 2897.5 by POLAR::PENNY "For the Benefit of Mr. Kite" >
>    I don't know about the States, but here in Canada you can't take
>    a two wire 220 volt feed and split it into two 110 volt lines *without*
>    a white neutral(sp?) wire. 

	Wouldn't it be easier to just swap the double pole breaker in the box 
 to a single pole, 20 amp one?  (then put a blank cover over the exposed 
 opening that remains).  Assuming that there is no other 220v device on
 the circuit, this would allow the use of a standard 110v outlet.

							--Mike
291.351MYVAX::DIAMONDNo brag, Just fact.Wed Jan 11 1989 16:4321
    
    I looked through keywords and did a dir/title and couldn't find
    anything that is exactly what I want so instead of starting a new
    note, I figured this was as good a place as any.
    
    Does anyone know if I can get or where I can get a double switch,
    one of which is a dimmer switch??? Places like Grossmans dosn't carry
    anything like it.
    
                         -----
                         |   |
    	                 | > |    <------ Switch (normal)
    	                 |   |
                         -----
                         |   |
    	                 | > |    <------ Switch (dimmer)
    	                 |   |
                         -----

    
    Mike    
291.352VINO::GRANSEWICZWhich way to Tahiti?Wed Jan 11 1989 17:2110
    
    I've never seen such a beast.  I've seen the double regular switch
    only.  I think dimmer switches are usually considerably larger than
    a regular switch and it may be physically impossible to have such
    an arrangement.  If one does exist, it'll probably cost $100 since
    its probably a very demand item.
    
    Good luck with the search.
    
    Phil
291.353Gerry Rig it, so to speakAKOV13::FULTZED FULTZWed Jan 11 1989 17:257
    Have you thought of putting a regular and a dimmer switch together
    yourself?  You would need the appropriately sized box and may have
    trouble finding a switch cover to fit, but it would probably be
    cheaper than trying to find a combination switch.
    
    Ed..
    
291.354VINO::KILGOREWild Bill -- DECintact EngineeringWed Jan 11 1989 18:237
    If you have to fit everything into a single box, I think your out
    of luck. Dimmers can dissipate considerable heat (depending on the
    load), and I doubt anyone has crammed two of those toasters into
    the space of a single box.
    
    If you can use a double box, a normal double switch cover will work
    with both rotary and the newer up-n-down dimmers
291.355put them side by side ??\FREDW::MATTHEShalf a bubble off plumbWed Jan 11 1989 18:243
    Do they have to be one above the other ???
    
    Side by side is a piece of cake.
291.356tried and could not find it (2 months ago)CADSE::MCCARTHYIllegitimi Non CarborundumWed Jan 11 1989 20:468
	When I was working on a job in the south shore area the home owner
	changed her mind several times on what she wanted to be switched,
	dimmed, outlet etc.  We ended up trying to find the device in 
	question and after trying three different elect. supply houses 
	we gave up.  Each one said "the don't make it".  We knew it was
	a long shot anyway.

	bjm
291.357Oh WellMYVAX::DIAMONDNo brag, Just fact.Wed Jan 11 1989 21:2710
    
    Side by side is what I was trying to stay away from. The switch
    is located in the bathroom surrounded by tile. To put another switch
    in I'd have to cut the tile, not an easy task and at the some time
    make it look nice. I had never heard of that kind of switch either,
    but then again, I'm not an EE or electrician. It was a long shot
    I have to admit, but it was worth a try. Looks like I'll have to
    cut the tile.
    
    Mike
291.358combination dimmer and regular switchVIDEO::FINGERHUTWed Jan 11 1989 22:434
    Maybe there's a way you can re-configure a rotary dial dimmer switch
    so that turning the dial dims one light, and pushing the rotary
    dial turns the second light on or off.
    
291.359a device that is close in functionCADSE::MCCARTHYIllegitimi Non CarborundumThu Jan 12 1989 09:0814
	Reply .24 got me thinking of a single gang device that the
	Casablanka (sp??) (the Calf. ceiling fan company) make to control
	BOTH the fan and the light kit on it.  It look very much like a
	dimmer but it has two knobs (similar to a car radio).  One is a
	three position unit for the fan the other is a push-on/off, turn
	to dim control for the light kit on the fan.  Depending on how
	the motor speed control portion handles the voltage it may be 
	possible to get a three position dimmer and a full range dimmer 
	into a single gang box.  
		I don't know if this would work.  This device does exist
	and is UL listed.
    
	bjm
291.360VINO::KILGOREWild Bill -- DECintact EngineeringThu Jan 12 1989 10:395
    re .24:
    
    I'll bet the three-position control is just a rotary switch to turn
    on the different windings of a three-speed fan, and would not provide
    a dimming effect.
291.361I've seen those...they should work ok.MISFIT::DEEPBring out yer dead...(clang!)Thu Jan 12 1989 12:486
If re: .25 is correct, than it would probably work for Mike's application.

.23 is a good idea, but of course, it would be against the code.  8^)

Bob
291.362Don't know what code would say about this one.LYCEUM::CURTISDick &quot;Aristotle&quot; CurtisThu Jan 12 1989 16:4010
    .23, .26:
    
    Perhaps what .23 has in mind is something like what you see for car
    headlights, or the reverse of a common car radio control:  the knob
    rotates, and at one stop it also throws a switch, with a second switch
    controlled by push/pull on the knob.
    
    No, I haven't seen such a beast.  Sorry!
    
    Dick
291.363double switch w/dimmerBAGELS::MONDOUThu Jan 12 1989 18:1310
    re: 1729.16 , request for a double switch w/dimmer
    
    I replied directly to the author but thought I would also enter
    the info here in case anyone else is looking for the same switch.
    
    I have seen a switch of this type in an electrical store in
    New Hampshire, near the Pheasant Lane mall.   I don't remember
    the name of the store or the manufacturer of the switch, but if
    anyone is interested, contact me and I'll find out the next time
    I am in the area.
291.364MYVAX::DIAMONDNo brag, Just fact.Fri Jan 13 1989 18:5621
    
    re .28
    
    Well I went to that store at lunch (happened to be in the area)
    and they don't have the switch. Maybe they did at one time but not
    now.
    
    As for the other switch some of you are talking about, I saw something
    like that at Builders Square. One was a three position fan and the
    other was a full dimmer for a light. Now my question is will this
    work in my situation. What I need the switch for is to hook up a
    exhaust fan for my mother's house. She has one switch there right
    now that is a dimmer which controls the light. Every exhaust fan
    I've looked at says to only hook it up to a timer switch or a standard
    on/off switch - nothing about being able to use a variable control
    switch. Does anyone know if these fans can be used with a variable
    control switch???? When I installed the fan on my woodburning stove
    the directions warned me from using it with a variable control switch.
    Are these fans built the same way????
    
    Mike
291.513Wire Color CountsPOLAR::PENNYFor the Benefit of Mr. KiteMon Jan 23 1989 20:156
    RE: .6
    
    You would still have the wire coloring to contend with. In Canada,
    you may do what you mentioned, IF, you properly color code the wires.
    In effect, put white tape over the red wire where it enters the
    "outlet" box AND the main panel. 	dep
291.424"3-wire" circuitVINO::GRANSEWICZWhich way to Tahiti?Thu Mar 16 1989 19:0816
    
    I'll ask this here since my house is reasonably old, has several
    2 wire circuits and the question isn't worth a brand new note.
    
    I'll be replacing my 7 fuse boxes with a breaker panel soon and
    have come across some wiring I'll need help with.  I have what I
    believe is called a "3-wire" circuit.  It's basically a 220 line
    but it's not used as 240.  It's used as 2 110 circuits.  
    
    My questions are:
    
    Is this a common practice today?
    
    What type of breaker should be used for this beast?  2 singles
    or 1 double?
    
291.425xrefHANNAH::DCLDavid LarrickThu Mar 16 1989 20:433
    I know there are multiple existing discussions of 3-wire circuits
    someplace in this conference, but the only one I could find was in
    topic 931, beginning at reply 6.
291.4263-wire connection at service panelVINO::GRANSEWICZWhich way to Tahiti?Fri Mar 17 1989 12:307
    
    RE: .12
    
    Thanks for pointing to 931 but it doesn't address my main question
    which is how is a 3-wire circuit connected in the service panel?
    Do I use 2 singles, a double or doesn't it matter?
    
291.427MAMIE::THOMSRoss - 264-6457Fri Mar 17 1989 12:5014
>< Note 2412.11 by VINO::GRANSEWICZ "Which way to Tahiti?" >
                             -< "3-wire" circuit >-

    
 >    have come across some wiring I'll need help with.  I have what I
 >   believe is called a "3-wire" circuit.  It's basically a 220 line
 >   but it's not used as 240.  It's used as 2 110 circuits.  
    
 
In older homes it used to be common practice to snake /3 romex (to the attic)
and use it for two circuits, sharing a common neutral. If this is the case
in your scheme, use two separate breakers.

Ross
291.428See the Code for 3-wire rulesHANNAH::DCLDavid LarrickFri Mar 17 1989 13:4319
    The Code has some specific provisions regarding 3-wire circuits, and I
    would suggest that you read and heed them.  Under some circumstances
    you do need to use a double breaker (two breakers in a double-size
    package, with their handles mechanically connected together so they
    turn off together).
    
    I think the rule is something like:
    
    - If the two circuits are both present in any outlet box or switch box,
      they must be connected by a double breaker
    
    - If the two circuits split apart in a workbox (and so are never both
      present in any outlet box or switch box), they may be connected by 
      single breakers
    
    The idea is to avoid the situation where someone wants to work on an
    outlet, switches off a breaker that appears to turn off that outlet,
    and gets shocked anyway by the other circuit in the outlet box. 
    Presumably people expect this sort of thing in work boxes.
291.429NSSG::FEINSMITHI'm the NRAFri Mar 17 1989 13:5426
    One thing to remmeber is to have each of the hots attached to a
    different leg of the 220 feed into the panel (different bussbar).
    The reason for this is that there is only one neutral, and as long
    as the two hots are out of phase with each other, the neutral won't
    be overloaded. Normally, with full size breakers, the bussbar the
    breaker attaches to will alternate on each side top to bottom:



                           A  B              
                           |------- (breaker)
                              |---- (breaker)
                           |-------     .
                              |----     .
                           |-------     .
                              |----     .
  
    However, on panels that support the half size breakers, two adjacent
    breakers can be attached to the same bussbar and cause problems.
    
    Eric                          
                               
                            
    
    
    
291.430VINO::GRANSEWICZWhich way to Tahiti?Fri Mar 17 1989 18:4214
    
    Alright!  Now we're getting somewhere.  As far as I can tell, the
    2 circuits are only in the ceiling light where they then split off.
    
    Richter's also got into the whys of putting the different legs of
    the circuit on different legs of the bussbar.  I don't believe it's
    connected that way now though.  I got a typical 4 circuit fuse box
    with the 2 large pullout cartridges above.  If the numbering of
    the fuses is 1, 2, 3, 4 then the legs were connected to 3 & 4. 
    This sounds like it was connected wrong but what are the consequences
    of this situation?  Everything has been working properly with no
    blown fuses.
    
    
291.431Be careful here - some things are not obviousREGENT::GETTYSBob Gettys N1BRM 235-8285Fri Mar 17 1989 19:3114
291.432it's probably wrong.TFH::DONNELLYTake my advice- Don't listen to meSat Mar 18 1989 01:2227
>    Richter's also got into the whys of putting the different legs of
>    the circuit on different legs of the bussbar.  I don't believe it's
>    connected that way now though.  I got a typical 4 circuit fuse box
>    with the 2 large pullout cartridges above.  If the numbering of
>    the fuses is 1, 2, 3, 4 then the legs were connected to 3 & 4. 
>    This sounds like it was connected wrong but what are the consequences
>    of this situation?  Everything has been working properly with no
>    blown fuses.

if I was you i'd double check this out.  the consequences are fire.  ok, so 
it's working so far.  with breakers not popping and safety factors you 
simply have not loaded things up enough to melt plastic.  but basically, if 
3 & 4 are on the same leg, you have two separate circuits, both with a 
15 (20?) amp fuse, pushing up to 30 (35, 40?) amps back through the same 
single nuetral wire.  take the cover plate off the box.  behind you can 
trace the wires from the big cartridge fuses to the plug fuses.  if one 
cartridge fuse leads to both fuses of your 3-wire circuit, it's wrong.  
just switch one of them with one of the circuits coming from 1 or 2.  i 
suppose it's possible for one cartridge to feed fuses 1 & 3, and the other 
2 & 4, so do check.
    
craig

btw, it's times like this when it's helpful to have found out what runs off 
what fuses.  then you can understand why the load has been low enough to 
not cause problems so far.  like the air conditioner was on one circuit and 
the furnace was on the other.  :^)
291.433"Outlet" <> outletHANNAH::DCLDavid LarrickSat Mar 18 1989 17:4714
.17>    Alright!  Now we're getting somewhere.  As far as I can tell, the
.17>    2 circuits are only in the ceiling light where they then split off.
    
A nit, but perhaps an important one:  the term "outlet", as used in the
Code (and in .15) includes lighting fixtures as well as receptacles for
plugs.  So if the circuits split in a box that also has a ceiling light
attached to it, that box is technically an outlet box.  To conform to Code,
the two circuits must be on the same double breaker.

I don't know whether the equivalent of a double breaker exists in fuse
technology.

But if the two hot wires are indeed on the same leg, you've got bigger
problems than technical Code violations.  Please check this out right away.
291.434VINO::GRANSEWICZWhich way to Tahiti?Mon Mar 20 1989 13:3917
    
    Thanks for all the help and info.
    
    Well, the 7 old fuse boxes are history and I now have a 100 amp
    breaker panel for my main service panel!
    
    I currently have the 3-wire circuit on 2, single pole 15 amp breakers
    and they are on seperate legs.  Do 15 amp double poe breakers exist?
    I don't recall seeing them on the list at Spag's so maybe they are
    not a common item.
    
    Another question:    
    I replaced the BX wire to the furnace with Romex.  Hell, it was
    a short run and while I was having sooo much fun ripping out wires
    ;-) I figured I do it.  Does the wiring to the furnace have to be
    in conduit?  If it does, then how much it (same area protected by
    firecode sheetrock?)?  
291.435Furnace wiringVINO::GRANSEWICZWhich way to Tahiti?Wed Mar 22 1989 14:5213
    
    Let me explain the situation in more detail:
    
    The old power source to the furnace was BX cable which went in above
    the firecode sheetrock to the thermal switch right above the furnace.
    However, the cable exited the sheetrock through a 1" square hole.
    To me, the fire protection offered by the sheetrock appears to be
    compromised.  Should I instead run the power feed through EMT conduit
    to the thermal switch and seal up the 1" hole?  The wire to the
    shutoff upstairs is also just stapled to the firecode sheetrock.
    I would think that that wire should also be in conduit.  Or am I
    going overboard here?
    
291.292what about extending 2 wire on non-outlet circuitsREGENT::POWERSTue Apr 18 1989 17:2220
I have an extend-the-2-wire grounding question that is skirted over
here and in 1980.* and 1992.*.
My brother has a 50/60-ish year old house, two wire circuits, some knob 
and tube, some BX (also one legged, that is, 110 only).
I've been helping him out by adding outside lighting fixtures for him.
One was a motion detecting yard light, the other a new porch light.

The Question:  What should one do with the grounding wire in the new boxes
and fixtures?  I had been clamping them together and to the boxes, hoping
for local integrity.  Of course, there is no safety ground for this
local circuit to connect to, so am I compounding the problem by connecting
boxes together?  Some boxes are, of course, switches (with metal boxes
and covers) so safety is a consideration.  Should I actively AVOID wiring
the bare wire to the fixtures so shorts at the fixture will NOT propagate
to other areas of the circuit?  Of course, I know better than to connect
ground and neutral.  (That's the one message conference members here continue
to beat into one another's heads!  Rightfully so, since it's so hard
to justify it on simple first principles.)

- tom powers]
291.293WILKIE::THOMSRoss - 264-6457Tue Apr 18 1989 18:3025
RE:-1 The code says: 250-50 (exception) For replacement of nongrounding-type
receptacles with grounding-type receptacles and for branch-circuit extentions
						    ^^^^^^^^^^^^^^^^^^^^^^^^^ 	
only in existing installations that do not have an equipment grounding conductor
in the branch circuit, the grounding conductor of a grounding-type receptacle 
outlet shall be permitted to be grounded to a water pipe which is bonded in
accordance with Section 250-80(a). 
Also take a look at Article 210-7, (c) and (d).
210-7 (d) (exception): Where a grounding means does not exist in the receptacle
enclosure either a nongrounding or a ground-fault circuit-interrupter type
of receptacle shall be used. A  grounding conductor shall not be connected from
the ground-fault circuit-interrupter receptacle to any outlet supplied from
the ground-fault circuit-interrupter-type receptacle.





"Don't wire in a grounding type device on a ungrounded system!" It's o.k.
to use a non-grounding device or add a ground. But don't provide false security
of an apparent grounding-type device.



Ross
291.294WOODRO::THOMSRoss - 264-6457Tue Apr 18 1989 19:3511
RE:27  		I re-read your note and assume you're not connecting any
receptacles to your extension. However the rule still applies, keep
the circuit two wire or upgrade to a true 3 wire with a grounding conductor.
If you connect your extension like a 3 wire, what would keep some future
unsuspecting homeowner from adding a grounding type receptacle on that 
particular branch? Also by staying 2 wire, (assuming the upgrade to three wire 
isn't practical), if you should have a short to metal,
at least the short would be isolated from the rest of the circuit.


Ross
291.295WOODRO::THOMSRoss - 264-6457Tue Apr 18 1989 20:048
Also...  read article 250-33. Other Conductor Enclosures. Exeception No. 1:
Metal enclosures for conductors added to existing installations of open wire,
knob-and-tube wiring, and nonmetallic-sheathed cable, which do not provide an
equipment ground, if in runs of ***less than 25 ft*** (7.62 m), if free from
				^^^^^^^^^^^^^^^^^^^^^
probable contact with ground, grounded metal, metal lath, or other conductive 
material, and if guarded against contact by persons shall not be required to 
be grounded.
291.514Need a "Banana" (inductive amplifier)MISFIT::DEEPSet hidden by moderatorMon Jun 12 1989 13:3519
Back in the dark ages of Data Communication, before the world got smart
and started using Ethernet, we used to use a device for tracing particular
cables out of a bundle.

I think it was some for of inductive amplifier.  You would connect a tone
generator (supplied as part of the set) on the ends of the wire, and then
trace along walls, cable troughs, etc., listening for the tone with the 
receiver end (jokingly called the "banana" because of its yellow color and
shape).   You could detect the tone without touching the cable...as much
as 1/2 foot away. 

WARNING!   USE ONLY ON UNLOADED (READ DISCONNECTED FROM BREAKER PANEL)
WIRES!

Your local telecomm people will probably have one... maybe you could borrow
it.  They still live in the dark ages!  8^)

Bob
291.515OASS::B_RAMSEYBeautiful Plumage the Norweigen BlueMon Jun 12 1989 17:306
    If you have access to the attic or cellar above and below the wall,
    look for wires coming and going.  You can often get a feel for the
    location of wires by where they enter/exit the wall and by looking
    at what electrical services are provided on the wall(lights, swithes,
    outlets, etc.)
  
291.516BEING::MCCULLEYRSX ProMon Jun 12 1989 17:5212
    re .3 - I have access to either attic or cellar, but not both, since
    the situations are on the first and second floors of my two-story
    home.  In fact the particular cases that most concern me both concern
    what my educated guess thinks/hopes might be horizontal runs involving
    outlets, switches and lights in a fairly small area of the room(s).
    
    The item described in .1 sounds like it's close to what I want,
    it's probably the same principal as .2 except using the 60-Hz field
    instead of coupling an induced tone into the cable.  Anybody able
    to give me a lead on the sort of gizmo described in .1?
    
    Thanks!
291.517Ask a good metal-detector hobbyist!POLAR::MACDONALDMon Jun 12 1989 20:129
    Find someone who has a metal detector for locating coins and metal
    underground and ask them to find a buried wire for you. Nothing
    pleases these hobbyists more than a challenge like this; a good 
    operator will be able to do the job within minutes, distinguishing
    between wires, nails, and outlet boxes.
    
    Every respectable neighbourhood has at least one.
    
    Bernie
291.518NEXUS::GORTMAKERWhatsa Gort?Tue Jun 13 1989 08:416
    Carol cable used to market a device used for locating wireing hidden
    in walls. It worked very much like a stud sensor except it picked
    up the 60hz and used it to create a signal(audible). Sorry I forget
    the name.
    
    -j
291.519Tracing is not that hardKACIE::POWELLReed Powell HPS MarketingTue Jun 13 1989 13:2911
    You will probaby have more luck tracing the wiring from the attic than
    you think - when houses are wired, horizontal runs are usually rare -
    vertical runs are a lot easier and faster, so that is what they do in
    most cases.   Orienting yourself is the hardest part (ie, sitting in
    the attic saying "what the &*@ am I above?), but all that really takes
    is having someone on the floor below tapping on the ceiling, or
    listening to your tapping.
    
    I was doing exactly waht you are, and this worked out fine in my case.
    
    
291.520Wire tracing methodsRGB::SEILERLarry SeilerTue Jun 13 1989 14:0534
If you have access to both the attic and the cellar, it should be
possible to figure out a lot of it even without metal detectors.
Here's a couple rules that I discovered in the two houses in which
I have traced wires -- I appreciate knowing if they are more general.

1)  First step, of course, is to find out which outlets are on which
breakers.  Then apply the following steps to each breaker individually.

2)  Look for outlets (on the same breaker) in similar positions on 
different floors.  It's a good bet that the wire runs vertically.

3)  Look for outlets (on the same breaker) around the walls in the
same room, or on opposite sides of the same wall.  If you can't
find the wire running between them in the basement or attic, it
probably runs inside the wall, at the level of the outlets.

4)  Outlets added after initial construction will be wired more
obscurely, but they're easier to find, since they almost certainly
go directly up into the attic (from the second floor) or directly
down into the basement (from the ground floor).  You may have to
dig in the insulation to find them all.

5)  Another simple trick is to take the covers off the outlets to
see whether the outlet is at the end of a run, or whether there
are wires both in and out -- or maybe 3 or more wires.  Note that
a wire out of a box could go to a light, instead of to another outlet.

6)  If you find a junction box (or outlet with multiple wires) 
and you can't figure out which branch heads for the breaker box, 
disconnect it and see which wires/outlets you've just disabled.
And be careful of those bare wires when you turn the breaker back on.

	Enjoy,
	Larry
291.521induction pick-upSICVAX::SCHEIBELU can Teach A new dog UL TRIXTue Jun 13 1989 18:1410
    Besides the methods in .8 something I have had moderate succes with is
    using an amplifier and a telephone pickup coil. (available at rat-snack
    for about 15 bucks) plug a load into the outlet like a light bulb hold
    the coil to the wall and listen in the amplifier's speaker for the 60
    cycle hum. This works sometimes it has a lot to do with the composition
    of the wall and how close the wire runs to the surface.
    
       Good luck,
      Bill
    
291.522Modern vs. historical wiring techniquesHANNAH::DCLDavid LarrickWed Jun 14 1989 15:4022
    .7>  when houses are wired, horizontal runs are usually rare -
    .7>  vertical runs are a lot easier and faster, so that is what they do in
    .7>  most cases. 
    
    Depends on the age of the house.  Modern wiring is done .7's way.  Back
    when labor (even skilled labor) was cheap and wire was expensive, it was 
    more common to go to the trouble of drilling through lots of framing
    members to save a few feet of wire.  So the older the house, the more
    likely you are to find runs through walls, diagonal runs through
    joists, etc.
    
    To the excellent list in .8, I would add:  consider the framing
    complexity of windows, doors, bays, stairwells, etc.  Such things
    require substantial pieces of lumber (headers, sills, cripples, etc.),
    which limit the possible routes that wiring can take to get from one
    place to another.  It also helps to know the history of any additions
    and/or electrical upgrades to the house.
    
    This won't help you much now, but:  whenever you open up a wall, take
    photographs of its innards before you close it up again - and leave the
    photos behind when you sell the house.  They're invaluable for answering 
    questions about framing, plumbing, wiring, insulation...
291.523Draper make oneIOSG::CARLINDick Carlin IOSGFri Jun 16 1989 09:0314
    Sorry about the late reply but there is indeed such a gadget. I have
    just bought one for $15 made by Draper (do they distribute in the US?).
    
    It detects wires, pipes etc. I wanted to locate the wires for a servant
    bell system. These (the wires, not the servants) are buried in the
    walls, running through lead conduits.
    
    It also detects ac power, flowing or not.
    
    I'm very impressed with it, hope you can find one over there.
    
    Cheers
    
    Dick
291.524impressed, you say?TLE::THORSTENSENThu Jun 22 1989 16:214
    Is it just a metal detector? Will it also work as a stud finder?
    
    The stud finder I have is useless... maybe the Draper product would
    solve multiple 'finding' pproblems.
291.525Very impressedIOSG::CARLINDick Carlin IOSGFri Jun 23 1989 16:4511
    Sorry, it's pretty versatile but locating studs is something it won't
    do. It's a metal/field detector.
    
    Right next to it in the shop was a stud detector made by Black and
    Decker. Is that the one you've got? - in which case I'll bear your
    negative recommendation in mind. I was tempted to buy it to avoid
    having to poke piano wire through the walls to locate studs.
    
    Dick
    
    
291.526Yes, Metal detectors will workFRIEZE::MEANEYJIMMon Jun 26 1989 19:0519
291.527May help....VICKI::DODIERTue Jun 27 1989 17:1214
    	You should be able to get a good idea of where a run is by looking
    at where the wire enters the room from the cellar/attic AND turning
    off breakers and seeing what outlets/lights went off. This will
    also tell you how much is on the line already so you can decide
    if you want to use it or not.
    
    	Secondly, you should be able to remove the cover and the
    switch/outlet (and if your real lucky the box itself), which will give
    you an idea of where the wire is coming from/going to.

    	Ray
    
    BTW - If your adding/changing wiring in a bathroom keep in mind that you 
    need a ground fault breaker or outlet.
291.528Cheap RadioCURIE::BBARRYTue Aug 01 1989 19:2620
	You can buy electric wire finders.  They essentially amount to SCR 
	circuit to generate pulses and a amplitute modulator hooked upto a 
	speaker to detect the pulses.  You can easily do the samething with 
	a lightbulb, dimmer switch and cheap transistor radio.  Plug the 
	light in through the dimmer and pass the transistor radio in the 
	general vacinity of the wire.  As you get closer to the wire the 
	clicking becomes louder.  

	The transistor radio picks up the magnetic field created by the
	change in current in the wire.  The magnetic field is proportional to 
	the change in current, so the SCR is used to quickly pull the 
	current to zero.  Sometimes just the normal 60Hz AC is adequate to 
	generate a detectable pulse.

	I have some Radio Shack books at home that show how to build everything
	that is needed.  I'll draw the circuit in here when I get a chance.
	It probably is nothing more then aa triac and a few pots to adjust 
	sensitivity.

	Brian
291.529Frozen screws in Electrical boxPOWDAH::PEREZThu Aug 10 1989 18:1911
    Does anybody out there know how I can loosen the screws that 
    hold the white/ground wires to the busbar in a circuit breaker
    box.  They all seem to be frozen in place.  
    What I am trying to do is add another circuit in my house, 
    (remodeling the ole kitchen) and most of the existing screws
    are stuck.  Also it seems like a good time to remove the old
    circuits from the panel.

    adTHANKSvance

    Dick -
291.530CLOSUS::HOESammy sit! Dad needs a breath!Fri Aug 11 1989 15:498
Dick,

After turning off the main braker, try squirting some penetrating
oil into the screws. Most of the time, the screws are gulled in
position. Sometimes, an over zealous electrician may have
stripped or cross threaded the screws.

Cal
291.531VLNVAX::HEDERSTEDTT.B.S.Fri Aug 11 1989 16:006
    
     Try a hand impact tool with the CORRECT size screwdriver blade. This
    has always worked for me. Sometimes a little heat applied will help
    to break the bond between the screw and the bonding bar.
    
    			Wayne
291.532More queries!POWDAH::PEREZMon Aug 14 1989 13:1216
re: .1
    Thanks Cal.
    I'll try the oil.  (Probably in combination with Wayne's reply.)

re: .2
    Thanks Wayne.
    Will a small "tap" on the end of a screwdriver suffice in the absence 
    of a hand impact tool?
    How does one apply heat to a particular screw safely?    
    
Question:
    What is the white stuff around the bar?  My suspicions are similar to
    the white stuff around my car battery.  Is this safe?  At least as the
    house is concern?

Dick - :-)
291.533An answer, and another questionTOKLAS::FELDMANWeek 5: insulation and inspectionMon Aug 14 1989 17:1126
    re: .3
    
    While a small tap on a screwdriver may help, and probably won't hurt,
    it's not the same as a hand impact tool.  A hand impact tool is design
    to convert the linear energy of the hammer blow into rotational energy. 
    You hold the tool tightly in the direction you want the screw to turn,
    and hit it with a hammer.  An internal wedge transmits the force of the
    blow into turning force on the tool's bit.  It sounds like a reasonable
    idea in this case, so long as you don't get carried away.  Remember,
    only some of the force is converted to rotational; the rest is the same
    as a solid hammer blow against the screw.
    
    Along the same lines:
    
    Is there an easy way to remove a plastic clamp from the service box?  I
    want to remove the cables that were left from our electric heaters when
    we converted to oil.  The wedge holding the cable in the clamp is
    positioned facing a neighboring clamp, so there's no room to simply
    pull out the wedge, and I'm not sure I could get it out, anyway.  The
    clamp is in the back row, making it difficult to get in there with
    pliers, to hold down the latches and pull the clamp out.  I'm perfectly
    willing to destroy the clamp and replace it with a metal one, but I'm
    not sure if there's an easy way to do that without electrocuting
    myself.
    
       Gary
291.534DeOxDYO780::SCHAFERBrad - back in Ohio.Mon Aug 14 1989 18:4922
RE: .3 (oxidization)

    Probably not a problem (read: dangerous) ... but to avoid that in the
    future, use some DeOx (elec conn lubricant) - the stuff is designed
    primarily for split-bolt wire unions, but works well on breakers
    and panel screws.

RE: .4 (to destroy or not to destroy)

    What kind of clamp, and what size wire?  Clip mounting or threaded with
    a nut?  If the former, I'd destroy it.  If the latter, the nut should
    be 'toothed' - you can use a screwdriver/hammer to get the thing to
    come out.  Either way, a good pair of diagonals can be used to cut the
    screws that secure the wire pinch - UNLESS the screws are on the inside
    of the box.  In that case, shoot the electrician. 8-)

    An aside - given the nature of the oil market (and assuming that the
    wire is in decent shape), you might be better off putting the loose end
    of the old wire in a box and cap it off.  You might want to use it
    again.

-b
291.535TOKLAS::FELDMANWeek 5: insulation and inspectionMon Aug 14 1989 19:0915
    re: .5
    
    It's a plastic clamp that's clip mounted.  It looks as though you push
    it in from the outside, and it locks in place.  Similarly, once the
    cables are inside the clamp, it looks like you push a plastic wedge in
    from the side to hold the cable, and the wedge locks in place.  In
    other words, the whole thing seems to be designed to be
    permanent/non-reusable.
    
    I will dead-end the old heater wires in a separate box, just for
    posterity.  I just want to get the wires out of the service box, to
    make things neater for when we finish wiring the addition, and to avoid
    having to punch another knockout.
    
       Gary
291.536WD-40 might be safer than oil?VMSDEV::HAMMONDCharlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684Thu Aug 17 1989 19:287
      I'm  not  sure  I  like  the idea of spreading oil around inside a
      cirucit breaker box.  I suspect it could have a detrimental effect
      if  it  got on/in the breakers themselves.  I'd use WD-40 instead.
      Its safe for use on electical stuff.
      
      If you DO use oil, keep it to a minimum only where neded. (i.e. on
      the neutral or ground bus.)  Wipe it off when done.
291.537VLNVAX::HEDERSTEDTT.B.S.Fri Aug 18 1989 16:108
     I use a BIG soldering iron to get the heat on the bar. Works for me!
    
    I am not big on the idea of oil in a breaker box. WD-40 or a electrial
    contact cleaner are better ideas!   If possible,highly recommened!,kill
    the juice to the panel before you start to work on the bus bar.
    
    
    			Wayne
291.538Part of a circuit showing only 80VCECV03::SADLERAsk a glass of water!Mon Oct 09 1989 14:2938
    A neighbour of mine called last night with a problem which he thought
    I'd be able to help with, but it beats me... can someone help?
    
    He's installing a bathroom fan, and has tapped into a cable in the
    roof, and connected the fan across it as shown in the diagram below.
    The fan doesn't run and putting a meter across the terminals at
    the fan shows 80 volts. What's wrong?
    
    


                -------o-------- black
	               |   
                       |
                -------(-----o-- white
                       |     |
                       |     |
                       |     |
                  ------     -------
                  |                |
                  |                |
                  |                |  --
                switch            fan   80 v across here
                  |                |  --
                  |                |
                  |                |
                  ------------------


    All suggestions gratefully received, I'm a recent 'import' from
    the UK and I don't understand this 120v system very well.
    
    Thanks,
    
    Andy
    
    
291.539Bad connection is my guessMOOV00::S_JOHNSONPark Ave in Beautiful WorcesterMon Oct 09 1989 14:5031

                -------o-------- black    --
	               |                     Whats voltage here??
                       |                  --
                -------(-----o-- white
                       |     |
                       |     |
                       |     |
                  ------     -------
                  |                |
                  |                |
                  |                |  --
                switch            fan   80 v across here
                  |                |  --
                  |                |
                  |                |
                  ------------------


    See if you have 120 at the source; if so, then either the wiring is bad,
    (maybe a bad connection) or the switch or fan is bad.  Try removing them
    from the circuit one at at time (bypass them with a jumper) to see if
    the 120 comes back.  

    My guess is a bad connection or bad switch; the fan itself wouldn't cause 
    a voltage drop like that, the fuse would blow due to overcurrent.  Double
    check all conections.  You're using wirenuts for connections, aren't you? 

     Steve       

291.540Tapped the wrong cableWJO::MARCHETTIMama said there'd be days like this.Mon Oct 09 1989 14:5333
    
    The other 40v is across some other load.
    
    It appears that your neighbor tapped into a switch cable.  I've added
    to your drawing to illustrate what is going on.  As long as the switch
    is open, the fan will be in series with whatever load the switch is
    meant to control (probably a light fixture).  If you close that switch,
    the fan won't work at all, and there will be 0 volts across it.
    
    I suspect that this wouldn't work in the UK either. 8^)
    
    Bob
    
    P.S. Does your neighbor do his own plumbing too?
                                                           black
               ----------o-------- black---------- load ------
	       |         |                        
              swtch      |                                    source
               |         |                                 white
                ---------(-----o-- white ---------------------
                         |     |
                         |     |
                         |     |
                    ------     -------
                    |                |
                    |                |
                    |                |  --
                  switch            fan   80 v across here
                    |                |  --
                    |                |
                    |                |
                    ------------------
    
291.5412 volts for you, 1 for me, ...ASD::DIGRAZIATue Oct 10 1989 19:4733

	I agree with .2, though load is probably "downstream" of
	"swtch", and downstream of the white tap:

               ----------o-------- black----------------------
	       |         |                        
              swtch      |                                    source
               |         |                                      
                ---------(-----o-- white ---------load--------
                         |     |               
                         |     |
                         |     |
                    ------     -------
                    |                |
                    |                |
                    |                |  --
                  switch            fan   80 v across here
                    |                |  --
                    |                |
                    |                |
                    ------------------
    

	Let's see, 40V is 1/2 of 80V, so the load is about 1/2 the
	resistance of the fan.  Very crudely, it's about double the 
	fan's wattage (or is it 4 times the fan's wattage?  Hmmm...).  
	So some device with twice (or four times) the fan's wattage is
	under suspicion.  (If the fan isn't turning at 80V, does it make
	sense to estimate resistance/impedance for a stopped motor, versus
	some unknown load?)

	Regards, Robert.
291.542Don't get zapped!!!OPUS::CLEMENCETue Oct 17 1989 02:5935

				WARNING

	You are assuming that the white lead is netural or unswitched.
Take the enhancment to the drawing below. This would be to code for mass.


               ----------o-------- black-----------+        +--white---
	       |         |                         +--load--+
              swtch      |                                      source
               |         |                                      
                ---------(-----o-- white --------------o-------black---
                         |     |                       ^
                         |     |                       wirenut
                         |     |
                    ------     -------
                    |                |
                    |                |
                    |                |  --
                  switch            fan   80 v across here
                    |                |  --
                    |                |
                    |                |
                    ------------------
    

	Your assumption of the load value is twice the wattage. To
find the switch that it is connected into..... you should place the meter
across the fan and turn on the fan switch. You should then try switching other
switches in the house and observe for voltage changes.

	Be carefull that you don't get zapped....

Bill
291.192Resistance of wire?ULTRA::WITTENBERGSecure Systems for Insecure PeopleTue Nov 07 1989 15:117
    Does anyone  have  a table showing resitance of wire (ohms/ft) for
    various  gauges?  Since  some of what I'm doing is low voltage and
    low  current, I'd appreciate numbers for wire from 10 to 20 gauge.
    At  this  point even a few values would help. Please state whether
    the resistance is for one or both legs of the circuit.  Thanks.

--David
291.193Here are a fewVINO::DZIEDZICTue Nov 07 1989 17:198
    Assuming copper (!) wire, this is the resistance in Ohms per
    1000 feet.  If you have two legs then sum them (i.e., a 20
    foot run of 2-wire cable is 40 feet as far as voltage drop
    is concerned).
    
    #10: 0.9989		#12: 1.588	#14: 2.525
    #16: 4.016		#18: 6.385	#20: 10.15
    
291.194ULTRA::WITTENBERGSecure Systems for Insecure PeopleWed Nov 08 1989 21:366
    Thanks for the information. The bicycle light system I just bought
    uses 22ga. copper for a 5 ft. run carrying 1 amp. (at 6 volts). So
    about 2% of the power goes into the wires. I'm going to upgrade it
    probably to 16 ga.

--David
291.195not saying you shouln't make the change, though.NOVA::FISHERPat PendingThu Nov 09 1989 07:407
    re:.14:  Your bike lighting system uses 22 ga strand wire doesn't it?
    The numbers in .13 are for solid.  I think someone told me a long time
    ago that strand wire has the same resistance as the next higher guage
    of solid wire so the 22 ga strand is about the same as 20 ga solid.
    -- Until you get a bunch of strands broken :-).
    
    ed
291.196ULTRA::WITTENBERGSecure Systems for Insecure PeopleThu Nov 09 1989 13:205
    Yup, they  use speaker wire. It's stranded wire. Even if I use the
    resistance  for  20  ga., I'm still loosing over 1%, and batteries
    are a lot heavier than the wiring, so it's worth conserving power.

--David
291.197divergence from "home owner topic"NOVA::FISHERPat PendingThu Nov 09 1989 17:194
    I reduce the voltage drop by shortening the distance from the battery
    to the light.  1 ft is good but it means putting a cage up front.
    
    ed
291.737Sizing wirenutsREGENT::MOZERH.C.C. ;-)Thu Nov 30 1989 11:5117
    
    I did a DIR/TITLE="wirenut" and didn't find anything, therefore
    this new NOTE.  If there is something somewhere else, please
    point me to it and/or move this note there.  Thanks!
    
    I have a question regarding wirenut sizes/capabilities.
    
    I need to be able to connect 2 #10 and 2 #14 solid copper conductors
    together inside a junction box.  All I have seen (and currently
    have a box of) are red "large" wirenuts.  The box says they are
    capable of 2 #10 and 1 #16 or #18 and 2 #10's alone are tough to
    "wrap"..
    
    Does anyone know if a larger one is made and, if so, where in the
    Central MA area I can get some (preferably 6 or so)?
    
    				Joe
291.738WILKIE::THOMSRoss @285-3151Thu Nov 30 1989 13:276
>< Note 3617.0 by REGENT::MOZER "H.C.C. ;-)" >
>                              -< Sizing wirenuts >-

Go to an electrical supply outlet that carries "Ideal" wirenuts and
buy the grey colored.
Ross
291.739CIMNET::LUNGERDave Lunger, 291-7797, MET-1/K2Thu Nov 30 1989 13:578
another possibility since you already have reds; and greys are a car-ride
away....

use 2 wire nuts to connect them, putting 2 #10's on one, and 2 #14's on
the other, and connect them with another length of #14, leaving you with
2 #10's and 1 #14 on one, and 3 #14's on the other. The latter may be
a yellow connector (check box; i'm not sure). You could also use a #12
as the short length between the wirenuts.
291.740Great info, thanks!!REGENT::MOZERH.C.C. ;-)Thu Nov 30 1989 16:146
    
    Thanks for the responses!!  Definitely gives me way(s) to do it!
    
    I will let you know which way I do it and how it works out!
    
    				Joe
291.741How big is the box?TALLIS::KOCHKevin Koch LTN1-2/H09 DTN226-6274Fri Dec 01 1989 12:156
>use 2 wire nuts to connect them, putting 2 #10's on one, and 2 #14's on
>the other, and connect them with another length of #14, leaving you with
>2 #10's and 1 #14 on one, and 3 #14's on the other. 

     This will work but will have a drastic effect on the number of 'wires' 
in the box.  You've added two more wire nuts and an extra piece of wire.
291.742It's a 4" incherREGENT::MOZERH.C.C. ;-)Fri Dec 01 1989 14:527
    
    Right now it's a 4" square box, but I've already decided that I
    NEED to get a 4" one with front and back open to double the depth
    of the box based on a single 4" square one got filled last night
    with 4 "red" wirenuts joining 2 pcs. of #10/3 with ground.
    
    				Joe
291.743Two-Piece wire nuts.POLAR::MACDONALDMon Dec 04 1989 15:5916
    There are wire nuts available which can easily handle several larger
    wires, and the space they occupy is about 1/2 bigger than the 
    larger standard wire nuts you are probably using.
    
    These larger ones come in two pieces, an inside brass hollow cylinder
    (sleeve-like) which can have an opening of about 1/4 inch into which
    you slip the wires to be joined (no twisting); they are held inside 
    this cylinder by a large flat set-screw in the side wall. The 
    set-screw is tightened and clamps the wires.
    
    This brass cylinder, with the wires clamped inside, has one end
    threaded over which you screw the plastic insulator completing the
    junction. It really does not look different than the standard twist-
    the-wire-and-screw-on-the-nut type. Any good electrical supplier should
    have them, but you probably won't find them at the local hardware.
    
291.744Sounds a bit shaky to me, unless its ground.JAZZ::WHITERandy White, Doncha love old homes...Thu Dec 07 1989 15:5514
RE:< Note 3617.2 by CIMNET::LUNGER "Dave Lunger, 291-7797, MET-1/K2" >

>use 2 wire nuts to connect them, putting 2 #10's on one, and 2 #14's on
>the other, and connect them with another length of #14, leaving you with
>2 #10's and 1 #14 on one, and 3 #14's on the other. The latter may be
>a yellow connector (check box; i'm not sure). You could also use a #12
>as the short length between the wirenuts.

	Huh, depends on what your doing, but I'm not sure this is code.
	I'd go with the larger wire nuts or insulated splices.  But if you
	do use this method be sure that you keep the 10's together in one
	wire nut because of ampacity.

							- Randy
291.924Surge/Spike ProtectionSOLAR1::FERREIRAThu Jan 11 1990 10:5818
Mr. Moderator,  I have looked thru the other notes listed under 1111.34/.35.36
and didn't find anything for surge/spike protection.  If I've overlooked a
better place for this note please feel free to redirect.

I have a new home therefore new electrical system.  When I arrived home
yesterday I found that we had experienced a 2 hr. power failure sometime
during the day.  The resulting damage consisted of tripping (2) GFI panel
circuits, a remote control ceiling fan, an electric garage door opener and
one of the PC boards in our new TV.  I will be calling Mass Electric to voice
my concerns and losses.  What I would like to do is protect my home from a
reoccurance of same.  I do not have any lightning protection nor surge/spike
protection in the house, I didn't think either would be necessary.  I know
hind-sight is 20-20  :-).....  Anyway, does anyone know what, where how I can
protect my; house from this sort of loss/disruption in the future..
We are located in Westford Ma with power supplied by Mass Electric. 200A 
service and it's all circuit breakers.  

Thanks in advance   Frank
291.925Not your average power outage!!POLAR::MACDONALDThu Jan 11 1990 11:2920
    Sounds like you had more than a simple power outage, the results you
    describe are serious - I had the same symptoms when I had lightning
    hit my underground telephone cable.
    
    I would lodge a serious complaint with the local Power Co. that you
    experienced a major surge or transient which caused the described
    damage, and first ask them to identify what happened (something of
    this magnitude should have been known). Since you are in a new house
    assume it may happen again, you may be on a power network with major 
    industrial loading - which can cause this type of disruption; I could 
    be wrong but it is worth asking about.
    
    With regard to some form of protection, the standard hardware variety
    "surge eliminator" or "noise reducer" probably would not do the job;
    these are designed for reducing noise and such from appliances that
    otherwise would interfere with you TV. To do the job properly, your
    incoming power line should be monitored for disruptions and then the
    protective device sized accordingly. A good Power Co. could provide 
    some assistance/guidance regarding this.
    
291.926QUARK::LIONELFree advice is worth every centThu Jan 11 1990 14:237
You can buy a voltage surge protector from DEC through the Employee Purchase
Plan - I think it works out to under $100.  This is wired into your breaker
box and protects the whole house.  I know several people who have done this,
and the DEC unit provides a lot more protection than the individual outlet
types.

			Steve
291.927Thanks and Specific questionsSOLAR1::FERREIRAThu Jan 11 1990 14:406
Thanks Steve,
	Do you happen to know how I can contact one of them and ask some
	installation specifics?

Frank

291.928QUARK::LIONELFree advice is worth every centThu Jan 11 1990 19:217
Re: .3

You won't get any installation help from DEC!  I suggest asking in
ELECTRO_HOBBY.  Or send mail to Vernon Miller (OPAMP::VMILLER) - I 
know he's done this.

				Steve
291.929plus 2 months to get fixedDEMING::TADRYFri Jan 12 1990 16:5517
    The same thing happen to me in Sterling, Home of Sterling Flicker and
    Flash, a tree limb fell on one of the main feeder lines during a 
    snow storm. Why was the limb that close to a feeder.... Anyway, 2
    T.V. sets, Stanley Garage door opener (The Sears was fine) VCR
    and 1 GFI bit the dust. Metropolitan covered the claim, I had to
    pay the deductable. They only pay to a certain point then they 
    have to review it, I think it was $700.00 worth of repair and I 
    came close. Check with your insurance co. I found out they would
    have paid to have the garage door opener and my large tv removed for
    the repair, no big deal. I didn't know my GFI was bad until it started
    tripping once a day then more frequently. If you suspect their bad, 
    have them replaced. I wasn't the only one who had damage and we got
    no satisfaction from the power company. I put surge protectors on 
    all the outlets that had equipment that was damage due to the surge.
    
    Good Luck,
    Ray
291.745Light Dimmer Switch & Ground ConnectionsCSC32::S_JOHNSONLifetime Member of Aye Phelta ThiMon Jan 29 1990 13:0812
This might have been mentioned elsewhere, but I could not find it anywhere.

I replaced a dimmer switch on our house.  When I took the old one off, I 
noticed there were three wires coming out of the switch.  The new one did not 
have the three wires so I just hooked up the black and white wires to the ones 
coming out of the box.  I don't remember doing anything to the bare ground 
wire.  Should I have?  The box is plastic and the house is fairly new (8 yrs 
old).

Thanks for any and all replies.

scott
291.7463-way/2-way selection?REGENT::POWERSTue Jan 30 1990 12:004
I'd guess that you had a three-way dimmer in the box and you replaced it with
a two way.  It sounds like your installation is a single switch installation,
so the third wire on the old dimmer can float, as long as it it taped so
it won't short to something.
291.747One more time for meCSC32::S_JOHNSONLifetime Member of Aye Phelta ThiWed Jan 31 1990 16:1110
    Does that mean, it is ok to leave the bare ground wire not attached to
    anything?  The bare ground wire I'm referring to is coming out of the
    box.  The old switch had  metal plate on it that dimmed the lights if
    you kept your finger on it after awhile.  The new switch has a dial on
    it that you turn to dim the lights.
    
    Should I tape the bare ground wire coming out of the box or just leave
    it hanging?
    
    scott
291.748grounded frameNYEM1::MILBERGBarry MilbergThu Feb 01 1990 01:587
    The last dimmer I bought (a GE) mentioned in the instructions that if
    the old switch was grounded (with a bare wire to the green screw) that
    you should ground the frame of the dimmer by attaching the bare wire to
    the front (metal) frame.
    
    	-Barry-
    
291.749Intended for nonmetallic boxesSHRFAC::BOUDREAUThu Feb 08 1990 05:1810
    	The reason that there is a ground wire coming out of the dimmer
    is if it is installed in a nonmetallic box, all exposed metal parts
    of the dimmer must be grounded. To do this you should tie it to
    the branch circuit ground in the box. If you have a metal box and
    the dimmer is mounted on a metal plate, (most are) and the metal
    plate will be mounted to the box the disregard the ground wire coming
    out of the dimmer.

    
    				CB
291.750Ground connectionsCSCMA::LEMIEUXThu Feb 08 1990 13:0717
    
    	Always connect the ground wire coming from the dimmer to, 1)
    the ground wire run with the other circuit conducters, 2) if the
    box is a metal box connect the groung wire to a ground screw that
    is then screwed into the metal box. As long as the metal box is
    properly grounded.
     
    	If you don't do the above you are depending on the mounting 
    screws for the ground connection, which is not allowed by NEC, also 
    if you were to remove the switch from the box with the power on for 
    trouble-shooting purposes, the switch would no longer be grounded 
    which would allow the metal parts of the switch to possibly become live....
    I think you can see what the results would be....
    
    
    
    	
291.751DEFINE QUALIFIED_PERSON NOT::EVERYONESHRFAC::BOUDREAUFri Feb 09 1990 04:1938
   RE-1
    
    	There may be some confusion on this topic. Are we talking about
    Grounding type receptacles, or general purpose snap switches 
    (dimmers)?? 
    
    	First of all the NEC requires that metal enclosures for switches to be
    grounded. (380-12) However it does NOT require the YOKE (strap) of the
    switch to be bonded other than the mechanical connection to the
    grounded box (yes the mounting screws are an approved method, in fact
    you can use the mounting screws to ground a receptacle when there is
    direct metal contact to the yoke of the receptacle). Now remember, the
    ground of the receptacle is going to serve some type of portable or
    cord connected equipment, and therefore should have excellent
    integrity. However, the yoke of a switch is *really* only grounding the
    strap and at worst the metal face plate. Remember that the face plate
    is only held on by the 6-32 screws and you are depending on them to
    provide an adequate ground. The only way that the yoke of the switch
    could become energize is 1) faulty wiring, 2) a wire coming off of the
    device (see #1), or as you had stated 3) a QUALIFIED person working on
    it. Now if this *qualified* person should work on this device while
    energized, he/she is aware of the hazards involved (art #100), and if
    they are uncomfortable with this situation they should shut that
    circuit down. 
    	
    
   	 The intention of the green wire coming out of the dimmer, was to ground
    the yoke (strap) of the switch when mounted in a nonmetallic box. The
    same goes for the green screw on some snap switches. They are only
    required when the switch enclosure is not grounded (nonmetallic). 

    
    	If you are not satisfied with this information I ask you to print
    the article #'s that support your theory. Remember an inspector
    cannot reject your work unless he/she can point out the *violation*
    in the code.
    
    				   CB
291.752Clarification of .5CSCMA::LEMIEUXTue Feb 13 1990 13:1411
    Hi,
    
    	RE.6
    
    		After a quick review of what I wrote in .5 I agree
    with what you have pointed out in .6. I was thinking non-metallic
    boxes but not writing what I was thinking. :')
    
    	Sorry for any confusion caused by my reply.
                                                  
    Paul L.
291.753leave this space blankSHRFAC::BOUDREAUWed Feb 14 1990 02:555
    No problem.
    
    	That's why we all use NOTES, for discussion.
    
    				CB
291.52Knob/Tube to Romex Connection?MFGMEM::S_JOHNSONSay it, don't spray it!Thu Feb 15 1990 15:1023
  I need to connect some new romex wiring to an existing 2 wire (knob and tube)
 circuit.  The romex, will be 14-2 with ground.  If the old wiring was easily
 accessible, I'd rip it all out and replace it.  But it goes between the
 1st and 2nd floors, and I don't want to rip the floor up to replace the wiring,
 which does not necessarily need replacing.

  I must connect these two types of wire in a junction box, of course.

  The question is:  What tyoe of junction box must be used?  The two wire system
 wires are enclosed in a (somewhat) flexible tube, presumably to protect against
 mechanical damage.  This needs to enter the junction box and meet code, and
 be connected to the romex.

  Is there special junction box for this application?

  Then what do I do with the ground wire on the romex?  Just ground the box?


   Thanks

   Steve

291.754Log Home WiringDNEAST::DEE_ERICTue Feb 20 1990 11:1318
    If you have ever wired a log home, perhaps you can advise me.....

    	How do you wire the outside walls of a log home?  

    	Do you do the same pre-planning that a post and beam requires, and 
    avoid outside wall wiring where ever possible?  

    	Do you wire the outside walls by installing the boxes in the logs, and 
    lead the wires between the logs.  Do you route out the logs and provide
    a path for the wires?

    	If so, is there a danger of pinching a wire or driving a spike through 
    the wires?

    	Any information you can share or lead me to will be appreciated.

    Eric
291.755I did itTOOK::SWISTJim Swist LKG2-2/T2 DTN 226-7102Tue Feb 20 1990 15:0526
    I wired a log home from top to bottom.
    
    1) First of all you AVOID wiring in the outside walls where possible. 
    You may have to get an electrical inspector to agree, for example, that
    an outlet on an interior wall 6" from an exterior wall is just as good
    as an outlet on an exterior wall 6" from the same interior wall.
    
    2) Yes, you have to preplan outside wall wiring and drill each course
    of logs as the walls go up.  A (serious) router with a (serious) bit is
    needed to make box openings unless you have years to do it with a
    drill/chisel or other such means.
    
    3) Outlets near the floor are relatively tolerable to deal with.  Ones
    higher up like light switches or kitchen counter outlets are the pits. 
    The wire has to pass through many courses of logs and it always seems
    to catch on something no matter how well the access hole is lined up
    and cleaned out.
    
    4) For places where appearance is not a consideration, think about
    using wiremold or some on-wall wiring system (if you think wiremold
    is attractive, think about using it on ALL outside walls :-).  I
    did this where the through-log wiring would have been ridiculous.  It's
    also the ONLY alternative for after-the-fact wiring on outside walls.
    
    I love my log home and most of building it was great fun; however, I
    would have to say that wiring the outside walls was NOT fun.
291.756Some suggestionsVMSDEV::HAMMONDCharlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684Tue Feb 20 1990 19:3430
      For outlets around the exterior perimeter I offer two suggestions:
      
      1) Put the outlets in the floor -- run the wires between the floor
      and the ceiling of the floor below.
      
      2) Use an extra large/thick "baseboard" to create a wiring raceway
      around the perimeter.
      
      For  switches  and  lamps mounted in/on the perimeter wall you can
      often build a vertical wiring raceway that ends up  looking  much
      like  a  post.   Alternately,  put  the  lamps  and switches in/on
      interior partition walls near where they intersect  the  perimeter
      walls. 
      
      *THE*  key  to  wiring  in  a  log home or a post and beam home is
      advance planning.  In a conventionally framed  home  (i.e.  "2-by"
      construction)  you  don't  need  to  think about wiring until the
      house is fully framed.  Wire can be run through the wall  cavities
      before installing insulation and sheetrock. But in a log home or a
      post and beam home the wiring has to be planned in advance so that
      wire can be run during construction.
      
      If  you're  not doing the work yourself -- maybe even if you are --
      you might want to look at different electricians till you find one
      who  has  wired  this type of building.  Better to profit from his
      experience that to pay for the learning experience of someone  who
      has never done this type of job.
      
      Also  --  Is it a "kit home"?  If so the kit supplier probably has
      information including mistakes to watch out for.
291.757SUSHI::LOG_HOMESOASS::RAMSEY_BPut the wet stuff on the red stuffTue Feb 20 1990 20:234
    You might also want to post this in SUSHI::LOG_HOMES.  That conference
    caters to all aspects of Log Home building and maintenance.  
    
    Hit keypad 7 to add SUSHI::LOG_HOMES to your notebook.
291.758Planning is EVERYTHINGSHRFAC::BOUDREAUThu Feb 22 1990 02:5812
    	I have wired a log home before. If you have proper planning,
    it really isn't all that bad. Make sure that you bore your holes
    using an auger bit (the home I was involved with the homeowner used
    a flat bit and the chips fell into the next lower course). Also
    clean your holes after *every* drilling. With proper planning you
    can place your receptacles and switches where you want them. I feel
    that in the long run you will appreciate the added convenience of
    having your receptacles and switches where they *should* be and not
    where they were easy to install.

    
    				Cary
291.759Planning sounds like the answerDNEAST::DEE_ERICThu Feb 22 1990 12:0620
    Re: all

    Thanks for the good replies - I'm in the planning stage right now, and
    will do my own construction when I've finally decided upon what I want. 
    I have plans for a house that I like, but haven't decided on stick, log,
    or post & beam, so I'm weighing all the alternatives.  I'm leaning to log
    or post & beam.
    	
    Pre-planning sounds like a must - so I'll give that part more
    consideration.  I like the idea of wide baseboards, wiring in floors 
    or upright support logs(posts).  The prospect of boring long holes to 
    get fixtures/outlets where I want them seems like a reasonable place 
    to put some extra energy.

    I'll search the LOG HOME conference too, and cross post the request if
    the subject has not been covered yet.  

    I appreciate all the ideas,
    Eric 
291.760DICKNS::WELLCOMESteve Wellcome (Maynard)Fri Mar 02 1990 14:073
    Comment: aren't in-the-floor outlets against code now?  Even if
    they aren't, I'd avoid them.  They fill up with crud, and there's
    no way to get it out if a vacuum cleaner doesn't work.
291.863Looking for hi-tech switchesNITMOI::PESENTIOnly messages can be draggedMon Mar 05 1990 23:0114
    Does anyone know of any "hi-tech" switch/dimmer suppliers.  I've seen
    the Stanley remote control set ups, but I'm looking for something that
    is more flexible than that.
    
    I would like to have multi point dimmer control (>2 points) for some
    lighting.  Also, it would be nice to have a lot of switches at a given
    point without them taking up too much room.
    
    I've checked a couple of lighting stores, and they seem to go for
    lo-tech traditional switches.  Should I be investigating electrical
    supply stores?  Or U Do It Electronics?  Or what?
    
    
    							-JP
291.864QUARK::LIONELFree advice is worth every centTue Mar 06 1990 14:058
Try the ATSE::X-10 conference for info on the BSR X-10 system.  The Stanley
Lightmaker system is just a tiny subset of X-10 (but isn't compatible with
other X-10 devices).  There's a lot more out there.

If you have a recent DAK catalog, look at the descriptions of the X-10
devices there.

			Steve
291.865Low voltage switching?EUCLID::PAULHUSChris @ MLO6B-2/T13 dtn 223-6871Wed Mar 07 1990 18:0520
    	An in-between (between traditional switches and the X-10 systems)
    is low-voltage (24V) switching of relays. I just ordered half a grand's
    worth yesterday. You come off your panel right into a relay cabinet.
    Each relay can be connected to any number of switches. Relays are
    available with pilot light contacts for remote switches with pilot
    lights. Two switches can be put into a standard outlet box (that would
    normally hold one switch, or a duplex outlet). There are high narrow
    switch plates that hold up to three switches and you can put 3 or 4
    switches in a double-width box.	
    some rough prices: relays $20 to $28 each 
                       switches 5 to 10 each
    		       cabinet with transformer, rectifier, relay mounts
    			about $150
    These are available from GE.  Source in E. Mass is G.E. Supply in
    Woburn. 
    	Obviously, you don't want to use these when you don't need multiple
    switches separated by long distances (3-way stuff works fine, thank
    you).  But, if you have some situations with 3 or more switching
    locations, some over 100' from the device, I think this is the way to
    go.  - Chris
291.866Radio ShackVMSDEV::HAMMONDCharlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684Wed Mar 07 1990 19:201
      RADIO SHACK sells X-10 type controls.  They frequently have sales.
291.53Knob&tube to Romex, or Romex to knob&tube?HANNAH::DCLDavid LarrickWed Mar 07 1990 20:4822
I've used regular boxes for this application.  The "somewhat flexible" sleeve 
fits nicely in both types of Romex clamps (integral and external).

Re ground:  if you're replacing knob and tube starting from the service panel,
and re-attaching an old knob and tube run to the new run of Romex, then you're 
fine just to ground the junction box - the knob and tube won't be grounded, but
it's no worse off than it was before.  

But if you're tapping a new Romex run off of an existing knob and tube run,
then your new Romex run won't have a ground.  Your options in this case, it
seems to me, are:

1. Use ungrounded Romex, ungrounded outlets, etc.  The Code makes an exception
   to its usual grounding requirements in cases like this, but the materials may
   be hard to come by.

2. String a ground wire from your service panel to your junction box.  
   Logically, you're converting the knob and tube run into a grounded circuit.

3. String a ground wire from a conveniently-located grounded circuit.  Not as 
   good as the other options because of potential ground loops and crosstalk, 
   but better than nothing.  (Electrical junkies please confirm this opinion!)
291.54VMSDEV::HAMMONDCharlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684Thu Mar 08 1990 19:1622
>2. String a ground wire from your service panel to your junction box.  
>   Logically, you're converting the knob and tube run into a grounded circuit.
>
>3. String a ground wire from a conveniently-located grounded circuit.  Not as 
>   good as the other options because of potential ground loops and crosstalk, 
>   but better than nothing.  (Electrical junkies please confirm this opinion!)

      My  reading  leads  me  to  believe  that  there are problems with
      running a seperate ground wire.  I have been told that a  seperate
      ground  wire  will NOT be accepted in new work; it must be part of
      the cable the contains the neutral and hot wires. I think that the
      problem  is  that  there  is  no  other  way  to  be sure -- well,
      reasonably sure -- that you will have a good ground  and  that  it
      will  stay  good.  Of course, a grounded type outlet iln which the
      ground prong is NOT properly grounded is  a  disaster  waiting  to
      happen. 
      
      My advice?  Run an entierly new, properly grounded circuit.  don't
      attempt to add a ground to an existing circuit.
      
      Another  good  piece  of  advice  is  to  check  with  a  licensed
      electrician or with a building inspector.
291.55One is needed, more are ACCEPTABLEGENRAL::HUNTERfrom SUNNY Colorado, WayneTue Mar 13 1990 18:0119
    	Take this as COLORADO code and might be different back your way:

    	A separate ground wire MAY be run to EACH circuit IF it returns to
    the grounding stud in the breaker panel.  This separate ground must run
    NEAR TO or with the existing wire for safety purposes.  If the wire is
    inside a conduit, a separate ground wire MUST also be enclosed WITHIN
    the conduit.  The conduit itself is NOT adequate for grounding
    purposes.  

    	As a sidelight to the above statement of facts, you MAY run as many
    ground leads as you wish as long as you have ONE continuous grounding
    wire attaching to the ground lug of the breaker panel.  For VERY HIGH
    FREQUENCY equipment, it is ADVANTAGEOUS to run a GROUNDED GRID for the
    equipment and keep the ground impedance LOW.  So, in this type of stated
    case, you will have one ground wire (LONG) inside the conduit or in the
    vicinity of the original wire in ADDITION to an entire grid of wide,
    flat, LARGE bars or etc. to drain the high frequency signals.  The
    single wire meets the code of providing a grounding path for safety, and
    the grid grounds the radio frequency.
291.56question on dryer plug styleDRIVE::HANAMHike with a HuskyTue Apr 17 1990 21:1225
    A basic question -

    I have an electric clothes dryer that is marked 3 wire, 120/240 60
    cycle.

    And an outlet that is marked 125/250.

    Are these compatible? The dryer plug is slightly different than the
    outlet; like this -

    outlet		dryer

    \   /		\   /

      |                   |
                         -+ (like a backwards L)


    I'm hoping that a new cord on the dryer will save me a call to an
    electrician, but don't want to change anything that would be
    dangerous.
    
    Thanks for your advice and experience.
    
    Mike
291.57220, 221 whatever it takesOASS::RAMSEY_BPut the wet stuff on the red stuffTue Apr 17 1990 21:3511
    One configuration is for a Dryer and the other is for an electric
    range/stove.  You can change the pigtail (the cord on the appl.) or you
    can change the outlet.  Check the rating of the fuse before using the
    applicance on that outlet.  You probably only need a 30 amp fuse for a
    dryer and a 50 amp for a range.  Check the documentation with your
    dryer.  Don't change the fuse from 30 to 50 unless the wire is rated
    for that load.  It is ok to go from 50 to 30.
    
    Either someone switched the pigtail on your appl. or the outlet was
    used for a different appl.
    
291.58DRYER OUTLET INFOCSCMA::LEMIEUXTue Apr 17 1990 22:0440
    
    	Amperage rating is the key to your question.
          
    	All appliances have an amperage rating and need to be fed by
    a circuit that is suitable for that appliance. You need to determine
    what the amperage draw for you dryer is an then determine which
    receptacle applies in your situation. That information can be found
    on the nameplate attached to the appliance where you found the voltage
    rating.
    	
        The appliance cord with the backwards L at the bottom may be
    the correct configuration for the dryer, if it was designed to be run 
    on a 30 amp 120/240 circuit. The receptacle with this configuration is 
    known as a NEMA 10-30R and is rated at 30 amps at 120/240 volts.
    
    	The other receptacle you have drawn is known as a NEMA 10-20R
    or a NEMA 10-50R depending which side the larger blade socket is
    located on. They are rated at 20 amps and 50 amps in that order.
    at 120/250 volts.
     
        In either case, the receptacle that is currently installed is
    probably not the correct one for the purpose. I would consider 
    having someone look at it if you are not comfortable with trying to 
    determine if the wire size is adequate, and if it is fused correctly 
    for the wire and dryer ampacities. 
      
    	None of the above would be correct if this dryer outlet were
    being fed from a sub-panel in either a multitenant building or
    a mobile home. These types of installations would require a 4 wire
    receptacle that has a seperate ground wire and associated blade
    socket. You would then have to have a 4 wire appliance cord to match
    this. The type of receptacle that would satisfy this requirement
    would be a NEMA 14-30R.
             
    	I hope this helps you out,
    
    	PL
    	   
    
       		
291.59DRIVE::HANAMHike with a HuskyWed Apr 18 1990 15:505
    
    thanks to both of you for your detailed replies. I've called an
    electrician friend and he'll be coming over to look at things. 
    
    thanks, and i'm happy i didn't just swap cords.
291.761FSTTOO::BEANAttila the Hun was a LIBERAL!Thu Apr 19 1990 17:0816
    My wife and I will start building our NorthEastern Log Homes kit later
    this summer.  Wiring is a big concern I have.  The NELH homes I have
    seen use door jams for channels for some of the light switch and
    exterior wiring.
    
    I though of "in-floor" outlets, too.  Commonly used in computer rooms,
    etc.  I don't think there are restrictions against them.  Cleaning can
    be a problem if they are in a traffic area...but, removal and
    maintenance is easy.  Problelm with them is carpeting.  They are a pain
    in the A#* if you have to put carpet around them.  
    
    Our kit dealer suggested cutting the box hole into the second tier of
    logs (that'd put the bottom of the outlet about 12 inches above floor). 
    That way you only drill two logs for each outlet.  
    
    tony
291.762NITMOI::PESENTIOnly messages can be draggedFri Apr 20 1990 11:538
My old roomie did a lot of research before buying her log home.  The one she 
bought uses a wood stove for heat, with an electric backup.  All of her outlets
are built into the electric baseboards.  If you are not going to have electric
heat, you could set up some wooden baseboard enclosures, and run all your wiring
thru them.  For wall wiring, it depends a lot on the finish for your walls. 
Rounded, chinked logs would be difficult.  However, her home uses a lot of 
surface type wiring, except instead of metal channels, they are wooden, to match
the walls and ceilings.  Looks nice, and is barely noticeable.
291.763Timber-frame/stress skin wiring & plumbingSEESAW::PILANTL. Mark Pilant, VMS SecurityFri Apr 20 1990 17:0612
    You might also want to check out Tedd Benson's book "The Timber-Frame
    Home" and the June/July 1988 (number 47) issue of Fine homebuilding.
    
    These two primarily deal with wiring and plumbing in timber-frame homes
    and stress skin panels, but there are probably some ideas you could
    use.
    
    Another thought would be to check with Jim Swist (a fellow HOME_WORK
    noter).  He fairly recently finished a log home he was building.  He
    could probably give you some good hints and gotchas.
    
    - Mark
291.60Outlet near chimney?SALEM::PAGLIARULO_GMon May 07 1990 11:2712
    	I need to move an outlet.  The most convenient place to move
    it to (for use - not wiring) is in the wall that contains the chimney.
    the chimney is only used for the gas water heater and furnace and
    I'm talking about an outlet on the second floor.  Now, intuition
    tells me that there's no way that this is allowed in "THE CODE"
    but I figured I'd ask.
    
    Can I do it?
    
    Thanks,
    
    George
291.465QUARK::LIONELFree advice is worth every centTue May 22 1990 15:3014
I am having the same problem.  My house is 24 years old and most of the
wiring has some sort of fabric outer insulation.  I haven't yet looked to
see if it has a temperature rating printed on it.

I called an electrical distributor and asked about a sort of heat shield as
was described in .5.  I was told that these did not exist in the US, and that
my only choice was to rewire the box with newer wire.  Sigh.  I can't find
anything in the NEC either that would allow a heat shield.

Actually, there was one alternative - use lower wattage bulbs.  The fixtures
I have use two 40W bulbs.  In some cases, two 25s would be ok, but elsewhere
no.  Augh....

				Steve
291.61what made this outlet short?LEZAH::QUIRIYChristineMon Jun 25 1990 18:1727
    Here's my story: I just moved into an apartment.  I made the mistake
    of looking behind/under the stove, saw how filthy the floor was and 
    decided to wash it.  

    The outlet for the stove is mounted on the floor along the wall.  
    Instead of using the mop for this area, I got down on my hands and 
    knees and used a sponge and was very careful not to slosh water at 
    the outlet.  However, the tile that the outlet "sits" on was loose 
    -- or it loosened when the water hit it/seeped under.  After the 
    floor was dry, I plugged in the stove.  After a little while (a 
    minute? a half minute?) I heard zzzzt!  After a lot of unproductive 
    running around, I unplugged the plug and when I did that, there was 
    more zzzzzt-ing and a small whisp of smoke.  (I was sure the house 
    was going to go...)

    This happened Friday and the stove's still unplugged, though I did
    turn the main breaker back on (couldn't find a separate breaker for 
    the stove).  Is it OK to plug the stove back in, or could there be
    a problem here?  I can't say for certain that NO water got into the 
    prong-slots, but I doubt it.  This house is OLD, it's had 4 owners
    in the last 9 years, and I've not yet been impressed that the 
    current owner is the conscientous sort.  

    Thanks,

    Christine
291.62What I'd doRGB::SEILERLarry SeilerMon Jun 25 1990 21:0516
If it were me, I'd unscrew the outlet cover (with the power to it turned
off, of course) and look inside.  If I saw any blackened insulation, I
would close the cover again and call the owner to let him know (as nicely
but firmly as possible) that he's got to get an electrician out on an
emergency basis because the stove isn't safe to operate.  If he gives
trouble about that, I would *immediately* call the town hall and ask who
I could talk to about a landlord who doesn't provide an operable stove
or safe wiring.  

After what you described, If I opened the box and didn't see any blackened 
insulation, I'd be very surprized!  I'm also surprized that it took that
long for the arcing to start.  Could the cord to the stove, or something
inside the stove, possibly have been wet?

	Luck,
	Larry
291.63Old aluminum wiring?SSDEVO::JACKSONJames P. JacksonMon Jun 25 1990 21:1723
291.64Get owner involved nowDDIF::MCCARTHYComing to you from Pink Flamingo LandTue Jun 26 1990 10:426
    An apartment?  I would suggest leaving it alone, call the landlord and
    tell him/her to come down right away.  Most likey they do not want the
    place to burn down.  Even if they are the "slum loards" type, all you
    have to do is threaten him with the health department or city housing
    authority (if such exists).  If in MA, I don't think you can rent an
    apartment without a working stove.
291.764Orange outlets and Hospital wiring?MEIS::FONSECAI heard it through the Grapevine...Tue Jun 26 1990 19:5819
I was in the General Doroit Auditorium in the mill yesterday,
and noticed the the outlets installed at desk level in the arena
for members of the audience were colored orange.  Each outlet also had
a small inverted green triangle symbol.

What did this indicate?  GFCI or spike protection?

A related question:

How are hospitals wired?  I was on a hospital tour recently, and noticed that
many of the outlets were colored or had tiny symbols attatched.
I suspect that for certain applications in a hospital, it doesn't
matter if a circuit is starting to overload, you want that lif-support
system to keep running.  How do they deal with this?

Thanks,
-Dave
(Want to make sure that intensive care addition to my house is wired correctly
:-)
291.765NOTIME::SACKSGerald Sacks ZKO2-3/N30 DTN:381-2085Tue Jun 26 1990 20:583
I would guess that in a hospital, only certain outlets are hooked up to
emergency power.  When the generator kicks in, you don't really need the
TVs to work.
291.766QUARK::LIONELFree advice is worth every centTue Jun 26 1990 21:024
The green dot or triangle indicates a special grounding requirement.  I'd 
have to look at the NEC to see what it is.  You should too.

			Steve
291.767VLNVAX::HEDERSTEDTT.B.S.Wed Jun 27 1990 00:1610
     The green sticker means the outlet has a "safty" ground. The normal
    ground in your house socket attaches to the ground prong of the outlet
    and the metal box (if you have a metal box) the outlet resides in.The
    Hospital has two seperate ground wires.One for the ground prong of the
    outlet and the other attaches to the metal box and frame of the outlet 
    It is a added safty feature. Hospital's have their own special spec on
    wiring and its own grade of electrical parts.
    
    
    		Wayne
291.65LEZAH::QUIRIYChristineWed Jun 27 1990 02:139
    
    re: .39-.41
    
    Thanks for all the replies!  I haven't lived in an (old) apartment for 
    10 years and am relearning how to react in this sort of "emergency".
    
    The outlet (and wiring to it) will be replaced tomorrow.
    
    CQ
291.768Isolated ground for computersCSCMA::LEMIEUXWed Jun 27 1990 12:4517
    
    	Hi,
    
    		What you have seen there is an "ISOLATED GROUND"
    receptacle. Designated by the green triangle on the face of the
    device. It is used to supply an isolated ground to a computer load
    to minimize the possibility of the introduction of noise etc into
    the computer. 
    
    	The Hospital grade wiring devices will have a green circle on
    the face and serve a completely different purpose than the "IG"
    types for computer loads.
                  
    	Did this help any?
    
    	PL
    
291.769more informationRAMBLR::MORONEYHow do you get this car out of second gear?Wed Jun 27 1990 16:1310
The new computer wiring of the Mill is "clean" power.  The computer recepticles
are fed off a separate breaker panel that has a separate feed from the other
loads.  Lights and normal outlets have their own breaker panel separate from
the computer loads. 

I don't know if the "isolated ground" is simply from being separate feeds back
to the feed that supplies the breaker panels (and maybe further, I don't know)
or if they're grounded in some special way.

-Mike
291.770The code...HDLITE::FLEURYWed Jun 27 1990 16:3360
    RE: a few
    
    The following is from the 1987 NEC book.
    
    Article 517 covers health care facilities which includes in-home care.
    
    517-11. Grounding of Recepticles and Fixed Electrical Equipment.
    	In areas used for patient care, the grounding terminals of all
    recepticles and all noncurrent-carrying conductive surfaces of fixed
    electrical equipment likely to become energized that are subject to
    personal contact, operating at over 100 volts, shall be grounded by an
    insulated copper conductor.  The grounding conductor shall be sized
    according to Table 250-95 and installed in metal reaceways with the
    branch-circuit conductors supplying these recepticles or fixed
    equipment.
    
    	Exception No. 1:  Metal recaeways are not required where Type MC
    cable, Type MI cable, or Type AC cable with an insulated grounding
    conductor is used.
    
    	Exception No. 2:  Metal faceplates shall be permitted to be
    grounded by means of a metal mounting screw(s) securing the faceplate
    to a grounded outlet box or grounded wiring device.
    
    	Exception No. 3:  An equipment grounding conductor enclosed in the
    sheath of a nonmetallic-sheathed cable assembly installed in accordance
    with the limitations of Sections 336-2, 336-3, and 336-4 sdhall be
    permitted to be used in accordance with Parts C and D of this article.
    
    517-13. Recepticles with Insulated Grounding Terminals.
    	Recepticles with insulated grounding terminals as permitted in
    Section 250-74, Exception No. 4, shall be identified; such
    identification shall be visible after installation.
    
    	(FPN): Care is important in specifying such a system with
    recepticle insulated grounds since the grounding impedance is
    controlled only be the grounding wires and does not benefit
    functionally from any parallel grounding paths.
    
    ================================================
    
    250-74. Connecting Recepticle Grounding Terminal to Box.
    	An equipment bonding jumper shall be used to connect the grounding
    terminal of a grounding-type recepticle to a grounded box.
    
    	Exception No. 4: Where required for the reduction of electrical
    noise (electromagnetic interference) on the grounding circuit, a
    receptical in which the grounding terminal is purposely insulated from
    the recepticle mounting means shall be permitted.  The recepticle
    grounding terminal shall be grounded by an insulated equipment
    grounding conductor run with the circuit conductors.  This grounding
    conductor shall be permitted to pass through one or more panelboards
    without connection to the panelboard grounding terminal as permitted in
    Section 384-27, Exception No. 1, so as to terminate directly at an
    equipment grounding conductor terminal of the applicable derived system
    or service.
    
    (FPN): Use of an isolated equipment grounding conductor does not
    relieve the requirement for grounding the raceway system and outlet
    box.
291.450How much more for all coper everywhere?SNDPIT::SMITHSmoking -&gt; global warming! :+)Wed Aug 08 1990 02:107
    If you are building a new home, is it worth starting out with copper
    wire everywhere (including the feed from the road)?  I know aluminum is
    cheaper for the main feed and any runs to subpanels (and I'm
    considering several subpanels), but how much more can copper cost when
    you are starting from scratch?
    
    Willie
291.451CSC32::GORTMAKERwhatsa Gort?Wed Aug 08 1990 03:267
By the time you spend the extra time and money buying recipticles and switches
rated for Cu/Al the copper would be cheaper. Al is best used for the service
drop and copper for the rest. I worked in a electrical supply warehouse before
joining DEC and the smallest aluminum wire we carried was 2/0 a tad overrated
for a 20A outlet.

-j
291.452Go with Copper, AL is just not worth itHNDYMN::MCCARTHYWhat will I do when the day is 1.5 hr longer?Wed Aug 08 1990 10:299
    I don't think you can use AL for anything under 30A runs (dryer).  Back
    in the late 60's/ early 70's (I think that was the time frame) there
    was AL Romex available in 12/14 guage.  I never installed it but had to
    play with it in a few junction boxes.  You had to be very careful not
    to nick the wire because a few twists after the nick and it would break
    off.  Never mind the fact that it could not handle the load, it was
    just a bitch to work with.
    
    bjm
291.453What about the drop from the street?SNDPIT::SMITHSmoking -&gt; global warming! :+)Wed Aug 08 1990 12:097
    OK, is it worth paying extra for copper from the street as well, or can
    you 'assume' (and we know what happens when you assume boys and girls,
    you burn your house down) that an aluminum drop is OK and is properly
    done?  The only alumimum feeds I've seen have had some of the strands
    cut off to allow them to fit into their clamps... :+{
    
    Willie
291.454Aluminum OK for feeds.HDLITE::FLEURYWed Aug 08 1990 15:257
    re: .-1
    
    For the extra cost (probably > 2X), I would say that copper for the
    feed is not worth it.  As long as there is NO-Ox on the junctions at
    the meter socket and panel, you shouldn't have a problem.
    
    Dan
291.455Cost more to run.ISLNDS::CALCAGNIA.F.F.A.Thu Aug 16 1990 16:469
    
    Is aluminum still legal in MASS?  I thought due to all the problems
    in the 60's it wasn't.
    
    However I do know that it costs a lot more to have Aluminum wiring
    in a house vs copper, something to do with resistance.
    
    Cal.
    
291.456Only for the big stuff, I don't think they make 12/2 RX in ALEVETPU::MCCARTHYSorry Mike but I'm leaving.Fri Aug 17 1990 00:4415
>>    Is aluminum still legal in MASS?  I thought due to all the problems
>>    in the 60's it wasn't.

	Yes it is, but only for large item like ranges, service entrances
and maybe dryers.

>>    However I do know that it costs a lot more to have Aluminum wiring
>>    in a house vs copper, something to do with resistance.

	Al cost more?  I don't think so, not with the price of copper. 
Given a one-to-one price per foot for same gauge wire, AL would cost more
because you are required to oversize the AL wire for the breaker it is on. 
Ie if you could get away with #12 copper, you would have to use #10 AL. 


291.457resistance of Al and CuRGB::SEILERLarry SeilerFri Aug 17 1990 01:2419
>>    However I do know that it costs a lot more to have Aluminum wiring
>>    in a house vs copper, something to do with resistance.

I presume that you mean Al has a higher resistance than copper (true),
and hence you get more voltage drop with aluminum than with copper, 
thus losing electrical energy to heating up your wires.

Well, I don't think so.  I believe that the codes required larger
conductors for Al house wiring than for copper house wiring, thus
equalizing the resistance per length.  That's certainly the case for
service conductors.  You can get a copper service conductor if you want
to, but copper costs maybe 3 times as much at the same allowed amperage.

Of course, if connections between the aluminum house wiring and the
receptacles loosen, that raises the resistance and wastes energy.
Eventually, that can cause a fire, which will definately cost more!

	Enjoy,
	Larry
291.458Actually.ISLNDS::CALCAGNIA.F.F.A.Fri Aug 24 1990 16:5113
    
    Re 18.
    
    That's correct.  Aluminum does have more resistance.
    
    I've lived in houses with Aluminum wiring throughout, and moved
    to a copper wired house.  Same heat same number of appliances and
    fixtures, well the new house had more lights.
    
    The Copper wired house cost me less to run.
    
    Cal
    
291.800Is rewiring needed here?OAXCEL::KAUFMANNA Great Cloud of WitnessesWed Aug 29 1990 16:4921
    I'm a novice at electrical work, and was wondering if anyone could
    help me out.
    
    I have an older home in Sudbury.  It was built in 1936, originally
    as a vacation cottage for Walthamites who spent their summers in
    the country.
    
    Over the years, the house has been added on to, and it is now best
    described as a modified Cape, 3 BRs, 1 bath.
    
    My question concerns the wiring: almost all the lights in our home
    flicker.  We have circuit breakers, but the wiring appears to be
    old -- it's wrapped in cloth.
    
    Do we need to replace the wiring?  If so, will it need to be done
    by an electrician?  How long (in terms of days) does rewiring take?
    How much 'damage' is done to walls and ceilings during rewiring?
    
    Any comments are appreciated.
    
    Bo
291.801Get some books and videosULTRA::SEKURSKIWed Aug 29 1990 18:2421
    
    
    
    	In my town your not even suppossed to pull the wire if your not 
    	an electrician.
    
    	I'm in the process of adding on a family room and did the wiring
    	myself. My uncle is an electrician and he checked my work then I 
    	had the inspector approve everything.
    
    	It's suprisingly easy but *very* time consuming if your a novice.
    
    	I found the Time Life books very helpful along with the books you
    	find at Grossmans. I couldn't have done any of the work without
    	the hometime videos also. It's really nice to stop and rewind then 
    	play again a demonstration you didn't quite catch the first time.
    
    						Mike
    						----
    
    	P.S. I could of done without the 5 minute Chevy commerial....
291.802MFGMEM::S_JOHNSONChicagoThu Aug 30 1990 16:0516
  I've added 8 circuits to my 94 year old house, and am in the process of
adding 3 more for a new 3/4 bath/laundry room  I'm installing on the 1st 
floor off the kitchen.  The books you mentioned are good, "Sunset" books
are good also.

  But my best "practical" wiring experience came from completely wiring our
kitchen, with 6 circuits, with the help of my father in law who is
a master electrician.    Techniques on drawing out your wiring
plans, in what order to run the wires to which devices, rough wiring 
installation, finish wiring techniques,, etc. Also consult your wiring
inspector for wiring tips.  Even though the one in Upton, MA is a stickler,
he's very helpful in helping you to do the job right, and informing you
of these little tricks, that probably won't be found in books.

steve
291.459KAOFS::S_BROOKIt's time for a summertime dreamTue Sep 18 1990 13:0723
    The type of wire would not affect the cost of electricity in your
    house.  If anything the possible higher resistance joints of Al would
    actually LOWER the amount of electricity used.
    
    The Power Equation tells you this ...
    
    P = V**2
        ----
         R
    
    V remains constant @ 117 (nominal) therefore ...
    Increasing the resistance in the circuit will lower the total power
    used.
    
    What will happen is that the appliance will use less power (because the
    voltage across its terminals has been reduced) and the remaining
    slightly reduced power will be dissipated in the terminals, junctions
    etc.
    
    Therefore, if your copper wired house uses less total electricity, then
    there is definitely some other reason for it.
    
    Stuart
291.460Ai wiring is not going to save electricityOPUS::CLEMENCEThu Sep 20 1990 12:0833
RE:. 20

	I am sorry to tell you this, but, AI wiring will not LOWER
    the cost of power used. In fact it would likely increase it.

	Most electic devices will draw more electricity at a lower
    voltage than it would at its proper voltage. They operate at a lower
    efficiency. Also for devices with motors, the life of the moter would
    be shortened.
  
>    V remains constant @ 117 (nominal) therefore ...
>    Increasing the resistance in the circuit will lower the total power
>    used.

	This would hold true if most appliances reistance would remain the
    same at the same voltage. Take a 100 watt light bulb. Its resistance
    at 1 volt is about .5 ohms, but at full voltage it is about 145 ohms.
    
>    What will happen is that the appliance will use less power (because the
>    voltage across its terminals has been reduced) and the remaining
>    slightly reduced power will be dissipated in the terminals, junctions
>    etc.

	This statement is correct that the remaining power will be dissipated
    in the terminals, juctions. The power dissipated is HEAT! A fire hazzard. 
    
>    Therefore, if your copper wired house uses less total electricity, then
>    there is definitely some other reason for it.

	The reason is simple. Your appliances work at best efficiency with
	full power going to them. I.E. Less electricity.
    
    Bill
291.461KAOFS::S_BROOKOriginality = Undetected PlagiarismFri Sep 28 1990 21:0548
>	I am sorry to tell you this, but, AI wiring will not LOWER
>    the cost of power used. In fact it would likely increase it.

    I have a very hard time believing this (and currently live in an
    Aluminium wired house)
    
>	Most electric devices will draw more electricity at a lower
>    voltage than it would at its proper voltage. They operate at a lower
>    efficiency. Also for devices with motors, the life of the moter would
>    be shortened.
  
    Not necessarily true, not necessarily true and not necessarily true to
    each of the 3 points in this paragraph.  The first is explained below.
    The second is a nonsense ... an electric heater for example will
    dissipate all the power it consumes ... it may not dissipate 1500 watts
    anymore, but it will still be 100% efficient.  The third is not
    necessarily true either ... unless the load is close to the maximum
    power rating of the motor, at which point you'll get an increase in
    its power factor.
    
>	This would hold true if most appliances reistance would remain the
>    same at the same voltage. Take a 100 watt light bulb. Its resistance
>    at 1 volt is about .5 ohms, but at full voltage it is about 145 ohms.
    
    Light bulbs in particular work on a very non-linear temperature vs
    resistance scale, and the major part of that non-linearity occurs
    before the bulb lights.  Once the bulb lights, the resistance increases
    dramatically and the difference in resistance between a 117V bulb
    operating at 100 V vs 120 V is almost negligible.
    
    Most other electrical devices do not have this non-linearity.
    
    Aluminium wiring when the proper size is used and the joints are made
    correctly will introduce negligible power drop.  So, even accounting
    for a few joints with increased resistancce, and a few devices with
    lower resistance, the overall net effect should be negligible.
    
>    in the terminals, juctions. The power dissipated is HEAT! A fire hazzard. 
    
    That is why Aluminium wiring has been eliminated, and why it is
    recommended that you ensure that all Al junctions are tight and
    the fittings are CU/AL rated.  But, don't be alarmist, otherwise
    Al would not be used for main feeds ... that's high current, and
    a slight increase in resistance on any connection due to oxidation
    could be an instant brown-out.
    
    Stuart
    
291.462RAMBLR::MORONEYShhh... Mad Scientist at work...Sat Sep 29 1990 00:1425
re .22:

There are a few cases where high resistance in the feed can cause higher
power consumption.  Consider the case of a 100% efficient electric water
heater.  To produce a certain amount of hot water, it must consume a
certain amount of power.  Now if there's higher resistance in the feed,
the voltage at the water heater is reduced.  Therefore, to produce the
same amount of hot water, it must stay "on" longer.  You use more electricity
since you use the amount of electricity the water heater uses (same in both
cases) PLUS the amount heating the wires (the resistance in the feed)

This does not hold true for things that stay on a certain length of time
regardless of the applied voltage, such as light bulbs.

I believe light bulbs are pretty close to being a constant current load
when in the range where they give off light (that is, their resistance
is approximately proportional to the voltage)

_If properly installed_ (and connections are good) the resistance of the
wires should be independant of whether aluminum or copper is used.  This
is because a larger wire size is used to compensate for the higher resistivity
of aluminum.  Ever wonder why the aluminum feed in the main breaker box is so
huge?

-Mike
291.463KAOFS::S_BROOKOriginality = Undetected PlagiarismMon Oct 01 1990 13:2836
>There are a few cases where high resistance in the feed can cause higher
>power consumption.  Consider the case of a 100% efficient electric water
>heater.  To produce a certain amount of hot water, it must consume a
>certain amount of power.  Now if there's higher resistance in the feed,
>the voltage at the water heater is reduced.  Therefore, to produce the
>same amount of hot water, it must stay "on" longer.  You use more electricity
>since you use the amount of electricity the water heater uses (same in both
>cases) PLUS the amount heating the wires (the resistance in the feed)
    
    OK, I'll buy this argument ... but ... during the 8 heating months, the
    excess heat is going into your house, reducing your overall heating
    bill slightly.  During the 4 cooling months, it is increasing your
    cooling bill.  Overall difference ... negligible.
    
    Having been involved with stage lighting and prolonging the life of
    the expensive projector bulbs they use (and the dimmers), I was
    concerned about this, and what I found was that the resistance of
    a light bulb increases dramatically from cold until it starts to
    give off "white" light, at which point it increases only slightly
    to normal working temperature.
    
    Anyway, after all this discussion, a noticeable difference in power
    consumption would have to be explained in other ways ...
    
    for example our furnace blower fan in our current house stays on
    distinctly longer to extract more heat from the furnace which increases
    consumption.  A single degree difference in heating level can produce
    a noticebale difference in consumption, especially with electric heat.
    
    There are too many variables in the heating / cooling system (like
    weather, inaccurate thermostats, different comfort levels between
    two houses etc) which could have a big impact on electricity
    consumption to accurately say that there was a difference due to
    Al rather than Cu wire.
    
    Stuart
291.464RAMBLR::MORONEYShhh... Mad Scientist at work...Mon Oct 01 1990 14:3719
re .24:

>    OK, I'll buy this argument ... but ... during the 8 heating months, the
>    excess heat is going into your house, reducing your overall heating
>    bill slightly.  During the 4 cooling months, it is increasing your
>    cooling bill.  Overall difference ... negligible.

Don't forget that electricity is more expensive than gas or oil, so if you have
a non-electric house, a large increase in the electric bill will be offset by
a smaller decrease in gas/oil usage.

Actually, if there's enough resistance in the wires to make a difference in
the heating bill, your house will have burnt down anyway...

I don't believe that resistance of Al wiring would make a difference in the
resistance in the circuit, since a 20A branch circuit would be wired with
12 gauge copper or 10 gauge aluminum, which both have about the same resistance.

-Mike
291.66whats enough?SNAX::HURWITZTue Oct 16 1990 23:5425
    Basic question...
    
    What rating wire should be calculated to use x amount of wattage on x
    amount of amps?
    
    (for instance)  The cords that my track lighting came with are 18 gauge
    which I thought wouldn't handle the 8  75watt lights total on the
    3 track sections.  The cord (18 gauge) says right on it that it can
    handle no more than 1675 watts!  Ya right.  I want to hardwire this
    track light series with romex to a wall dimmer and want to make sure
    there is room for the other mistery outlets on this circut.  (I know
    that one was sent to an outlet in the bathroom by the previous owner.)
    
    Whats the best easy-read wiring book?   Whats the best way to calculate
    how much room is left on a circut with it still being safe?  (i.e.
    if 14-2 romex is used and there is a 15 amp breaker and the total
    wattage is only 600 watts then this uses about 7 amps at 120 volts.)
    Right? So is this "half" safe?  I would assume so.  I would not assume
    revving my car to the red line was safe though, but would assume that
    half way to the red line would be normal usage.  So is half way to the
    total rated AMPs of the circut normal use?  I do plan on checking/finding
    the other outlets from this circut (some how).
    
    do I know what I'm even asking?
    Steve....................................................................
291.67ODIXIE::RAMSEYTake this job and Love it!Wed Oct 17 1990 12:2610
    Well it depends...
    
    There are several charts in the NEC handbook which address this issue. 
    It depends on the number of outlets how you determine the usage.  For
    instance, if you only have 1 outlet on a circuit, figure 100% usage. 
    If two outlets 90%, 4 outlets 80% usage, etc.  This is from memory so
    don't go with these numbers.
    
    Check out the NEC handbook at your local library for real specific
    details.
291.68what else is on the circuit?BPOV06::RIDGETrouble w/you is the trouble w/meWed Oct 17 1990 15:1913
    re. -2
    I am not an electrician. Here is what I would do to plan what I needed.
    A 15 amp circuit of 120 volts gives a total of 1800 watts available. 
    (apms x volts = watts) For safety, and I think required by code, you
    plan on 80% maximum useage. So that leaves you with 1440 watts.
    (1800 x .8)
    
    Then it is important to find out what else is already on this circuit. 
    You need to know what is on the circuit to be able to tell how much
    light the track lighting can be allowed to add to the circuit. 
    
    I believe that 14-2 wire is used in 15 amp applications and 12-2 wire
    is used for 20 amp applications.
291.69VMSDEV::HAMMONDCharlie Hammond -- ZKO3-04/S23 -- dtn 381-2684Wed Oct 17 1990 19:2415
re: << Note 574.43 by SNAX::HURWITZ >>>

>    What rating wire should be calculated ...
 
      Just  so  that  you  understand, the size wire to use in hardwired
      installations is not based directly on the load  on  the  curcyut,
      but on the size of the breaker that protects that circuit. Yes, of
      coures, the breaker has to be heavy enough for the load, and maybe
      thats  really  what you asking.  But please understand that if you
      have a 20amp breaker then you must use # 12 wire or heavier (#  14
      or  heavier  for  15 amps), and this is true even if you only load
      the circuit with 1 or 2 amps.
      
      Different  rules apply for the wire sizes that are used in plug-in
      lamps and small appliances.
291.70TLE::FELDMANLarix decidua, var. decifyWed Oct 17 1990 20:2411
re: .43

Are you saying 8 75 watt bulbs on each of three sections, for a total of 24
bulbs?  That's a lot of track lighting, which deserves a dedicated 20 amp 
circuit if you insist on putting it all on one circuit.  

If you mean there are only 8 bulbs total, then that's only 600 watts total, or
5 amps.  I don't know the numbers by heart, but I'd imagine an 18 gauge wire
can handle 5 amps (on a plug; don't use 18 gauge for a hardwired installation).

   Gary
291.71only 8 bulbs total and one more questionSNAX::HURWITZWed Oct 17 1990 23:5951
    These are the 2 things that I'm planning to do.
    
    a.  go to the library and try to find that NEC code book.  Hopefully
        its not too hard to understand.
    
    b.  The circut is a 15 amp circut so I will use 14-2 wire to hardwire
        the 3 tracks in series and then to the wall dimmer:
    
    /-----T R A C K-------------------------------\ 
    |                                     ^       |
    | <-14/2  ^                           |---->  |
    |         | 2 heads here             14/2     |
    T                                             T
    R                                             R
    A  <----4 heads here     2 heads here  ---->  A
    C                                             C
    K                                             K
                                                  \\-----down wall to
                                                        dimmer here
    
    
     Total heads = 8.  Total watts if using 75 watt bulbs = 600 = 5 amps
     out of a 15 amp line.  Plenty of light and plenty of "room" for the
     other outlets.  BTW of the 8 outlets in the room only 3 are used now.
     I just have some figuring to do on the amps used by the other stuff on
     that line and I have to find the other paths this line takes in the
     house.
    
     One more question....... (I really could use a good basic wiring book)
    
     
     What does it mean when you say wire in series?   I assume that I
    should wire the tracks as follows:
    
    
from    -hot-(black)--------*terminal-on-track*---------------  
track#1      14/2 wire                                         to track#2
        -white--------------*terminal-on-track*----------------
    
    and so on to form a loop.  Is this in series?  Or is the following in
    series? :
    
                            *-terminal-on-track-*
                            |  _________________|
                            | |
  from   -hot-(black)-------* *--------------------------------- to track#2
  track#1
         -white----------------------------------------------------------
    
    
    Steve...................................................................
291.72RAMBLR::MORONEYShhh... Mad Scientist at work...Thu Oct 18 1990 00:2414
I don't really follow your series/parallel diagrams, but you wire 120V
electrical in parallel.  This means for something like the tracklights,
connect all the black wires together, and connect all the white wires together.
I'd guess for lighting tracks they may not be marked to black and white,
call one rail black and the other white.

Be sure you know what you're doing before wiring, you don't want to burn
your house down.

Possible "gotcha" with the dimmer:  many dimmers can handle only 300 watts or
so.  Be sure to get one large enough (be sure to allow for the time when
someone replaces the bulbs with higher wattage bulbs, too)

-Mike
291.73Not a big enough circuit?ULTRA::WITTENBERGSecure Systems for Insecure PeopleThu Oct 18 1990 14:238
    Check the  code  book  carefully. I think you're going to have too
    many  outlets on that circuit. If memory serves, you have to count
    each  outlet  as 1.5 amps, so you've got 12 amps in outlets, and 5
    amps  in your lights puts you over the max. allowed. Also, if they
    are  considered  "continuous duty" you are allowed even less power
    draw per circuit.

--David
291.74TLE::FELDMANLarix decidua, var. decifyThu Oct 18 1990 15:3011
If you're looking for basic reading, don't bother with the code book.  It reads
like a cross between legalese and a software spec, written by a committee for
which clarity was never considered a priority.

In addition to the usual Time-Life, Sunset, and similar books, there's a very
good basic wiring book available at Spag's and sources.  I've forgotten the
name, but I learned about it by reading other notes in this conference, so I'm
sure you could find it by doing some searching.  It's a thin (1/4 to 1/2 inch)
medium sized (6 by 8 or 7 by 9) book that sells for $5 or less.

   Gary
291.75you need a basic wiring bookBPOV02::RIDGETrouble w/you is the trouble w/meThu Oct 18 1990 15:3932
    		Series vs Parallell I do not know but:
    
re .48       Provided these are the same track-light, not two diferent
    	     units.
                            _______________________
                            | _________________    |
from    -hot-(black)--------*|terminal on track|   |______________  
track#1      14/2 wire       |                 |                 to track#2
        -white--------------*|terminal op track|   ----------------
                            ||_________________|   |
                            |______________________|
             
    	 OR: I would preferr to show it using your second diag with one
    	     minor change:
    
    
                            *-terminal-on-track-*
                            |  _________________|
                            | |
  from   -hot-(black)-------*->--------------------------------- to track#2
  track#1                     |
         -white---------------*-------------------------------------------
    
             So, as someone already stated, all white wires are connected,
             and all black wires are connected.
    
    	     (the > in the diagram means that there is no connection at
    	     that point)
    
    hope this helps
    Steve
                   
291.76thats it!SNAX::HURWITZThu Oct 18 1990 23:2911
    re -1
    
    Thats exactly what I was asking and what I needed to know.
    Maybe by next year this time I'll be replying with the answers instead
    of the questions.
    
    Thanks all.
    
    Steve.........(off to Spags to find that wiring book and a 800 watt
                   dimmer if one exsists.) 
               
291.930possible solution?CSOA1::MCCULLOUGHMon Oct 22 1990 19:4221
    My inlaws are currently renovating an older house they bought. The
    house is about 20-25 yrs old. They hired a licensed electrician to come
    in and do some rewiring including the installation of a new service
    entrance in the garage. Since new wiring was also being run from the
    pole, the electrician put the new service on the  back wall of the
    garage while the new wires came in the front. No problem.
    
    Then the inspector comes to inspect the wiring. Says they have to
    remove the already installed wiring in the garage and install a FUSE
    box  where the wires enter the garage, and then rerun the wires to the
    service box. The inspector said that this fuse box was to protect the
    service box, with main breakers etc. from a power surge, so that in the
    event of a surge the fuses would protect the breakers.
    
    I'm not sure if this inspector is for real or if there is a new code
    requiring the additional fuse box.
    
    Any ideas?
    
    Mike
    
291.931Sound like you need disconnectCSCMA::LEMIEUXMon Oct 22 1990 22:1331
    
    
    	I am not sure if I completely understand what you are saying
    but I'll give it a try....Do the wires coming from the utility
    enter the front of the building? and continue on to the rear of
    the building through the interior walls to the breaker panel in
    the rear? Does this sound like the scenerio?
     
    	If so there must be a disconnect switch that is either
    fused or breaker type where the wire enters the building interior
    in the front. You cannot have unprotected service entrance wires
    running around inside the building.
    
    From that point on the cable from the disconnect switch to the panel 
    will have to contain the phase conductors, a neutral and the ground 
    because the breaker panel at the rear of the building is now a sub-panel.
    The neutral to ground bond will have to be in the disconnect switch.
    along with the grounding conductor to the cold water pipe and the
    ground rod. There must not be a neutral to ground bond in the
    sub-panel.
    	
    	As for the inspector using surge protection as the reason for
    fuses, I think he was probably just mixing terms and meant that
    the wires running in the building must be protected for over current.
    
        As I stated I was not completely sure of what you were really
    asking so if you could post a little diagram here we might be able
    to help you out a little better.
    
    Paul L
    
291.932Not all that unusualSTAR::DZIEDZICTue Oct 23 1990 10:206
    Sounds like my (new) neighbor's (new) house.  Their service
    drop is on the front corner of the garage, but their panel
    is near the middle of the basement (garage at basement level).
    They have a service disconnect switch right inside the garage
    where the feed from the meter enters the garage, and a standard
    panel in the basement.
291.933Cutoff required if more than 5' from meter.HDLITE::FLEURYTue Oct 23 1990 10:5612
    RE: .7
    
    The code requires a cutoff switch as described in .8 whenever the main
    panel is farther than 5' from the meter.  This cutoff can be either a
    breaker or knife switch designed for this.  Usually, you will see a
    breaker in this type of application.
    
    Once this is done, the main cutoff becomes the "main" panel and the
    other panel is wired like a sub-panel.  The connection should be made
    with SER cable (3-wires w/g) rather than SEU (2-wires w/g).
    
    Dan
291.934clear as mudCSOA1::MCCULLOUGHTue Oct 23 1990 12:2728
    Maybe there is some logic here.
    
    The new wires entering the building are coming in the front while the
    breaker box is in the back, distance of about 20 feet. I can see that
    without a switch, fuse or breaker box where the wires enter the house
    they would be unprotected to the breaker box. So this makes sense now.
    
    If the breaker box was installed close to the point of entry it would
    have been a different story.
    
                                ceiling
     wires|_________________________________________________________|
    ======|=======================================================--|
    entry | ^                                                     | |
    point | |_ wants fuse box here                                | |
          |                                     new breaker box   --|
          |                                                         |
                                                                    |
          front of garage                                back of garage
    
    
    
    Mike
    
    
    
    
    
291.935RE: .7 "Licensed"?MVDS02::LOCKRIDGEArtificial InsanityTue Oct 23 1990 15:2712
    re: .7

>   My inlaws are currently renovating an older house they bought. The
>   house is about 20-25 yrs old. They hired a licensed electrician to come
                                               ^^^^^^^^
    Gee, being licensed assured that the electrician was up-to-date with
    the codes, huh.  One would expect that a licensed electrician would be
    required to keep current, or isn't that a requirement after obtaining 
    the license?  (This is both a facetious and at the same time serious
    question).

    -Bob
291.936works as advertisedCLUSTA::GLANTZMike 227-4299 @TAY Littleton MATue Oct 23 1990 15:415
  Yes, they're required to take refresher courses (a certain number of
  hours, I forget exactly how much). These cover mainly changes and
  additions to the code. If you're interested and live in the Greater
  Maynard area, the Asabet Valley Regional Vocational School in Marlboro
  offers these courses.
291.937FYICSCMA::LEMIEUXTue Oct 23 1990 16:4722
    
    	All that is required to renew your electrical licensce is 15 hours 
    continueing education for every new code release...which equates to 
    15 hours every three years. It is probably not enough but that is
    the way it is today in all of the New England states. 
    
    		The diagram you posted as I requested does indeed explain
    your situation and my solution/explaination along with the other
    ones posted here are correct. This installation needs a disconnect
    at the point of entry and the correct style cable running to the
    sub-panel.
    
    	As this situation shows, as with any profession there are those
    who know what they are doing and those that do not. It's funny that
    the only ones who get written about are the ones who do not, which
    tends to make it appear that there are a lot more electricians who
    don't know what they are doing than there are that do. 
           
    	Signed,
    
    	An electrician
    
291.938VMSDEV::HAMMONDCharlie Hammond -- ZKO3-04/S23 -- dtn 381-2684Tue Oct 23 1990 18:1610
      The  requirement  that  the service entrance cutoff must be "near"
      the point where the service enters the building is not new.   This
      was  a  requirement  six years ago when we build our house and had
      then been on the books  long  enough  to  make  it  into  consumer
      oriented  wiring books.  I don't recall that "near" was defined as
      five feet or left to the inspector's discretion, so  the  "5  foot
      rule" may be relatively new.  
      
      But I agree that a "licensed" electrician should have known better
      than to expect to get away with a 20 foot run.
291.939No distance specified in NECCSCMA::LEMIEUXTue Oct 23 1990 19:4112
    
    Charlie is correct, there is no footage specified by the NEC. Refer
    to Article 230-70 (a). which explains where the disconnecting means
    shall be placed. It must be placed either outside the building
    structure or inside nearest the point of entrance of the service
    conductors. 
    		If you have a copy of the NEC "handbook" it even
    goes on to explain that NEC does not dictate the distance, but leaves
    it up to the local authority having jurisdiction to specify a distance
    if they want to.
                                              
    
291.940What kind of problems does an outside disconnect invite?VAXADA::G::MORRISGreg MorrisTue Oct 23 1990 22:2712
I will be building a house and was planning on structuring the basement so
I could eventually create a large finished room down there.  A lot of finished 
basements I've seen have some sort of funny little door in the finished wall 
to hide the main breaker panel.  I was hoping to avoid this by locating the
main panel in the portion of the basement that will be left unfinished.
It is unlikely that location will be "near" the meter.  

Having a cutoff inside would require some sort of access door in the finished
wall which kind of defeats the purpose of locating the main panel far away in 
the first place.  I haven't seen a cutoff on the outside of a house.  How 
unusual is that?  Any other way to solve this problem?
291.941Here are just a few optionsWMOIS::BOUDREAU_CWed Oct 24 1990 01:0222
    RE-1
    
    	It is possible to buy meter sockets with Main breakers in them.
    This is most common on multiple gang sockets, but they are available in
    single gang configurations.  You could also install a main disconnect
    outside in a seperate encloser. There is a drawback however, they
    connot be locked in the on position, and must be readily assable. This
    means that they are open to tampering by strangers, or anyone who wants
    to. This may prove to create a much worse situation.
    
    	The only other option you have, is to run the conductors from the
    meter socket to the panel on the OUTSIDE of the house. This could be an
    eyesore if done incorrectly. However, with a little imagination it can
    be very inconsipuous.
    
    	Why not go all the way and go under ground, with the meter socket
    away from the house. The bottom line here is HOW MUCH DO YOU WANT TO
    SPEND??? 
    
    	Just my $0.025
    
    			CB
291.942outside is normal in some placesREGENT::GETTYSBob Gettys N1BRM 235-8285Wed Oct 24 1990 12:4210
                Interesting side note - My aunt and uncle live in
        Arkansas and where they live, it is REQUIRED that the main
        cutoff be outside at the meter and ACCESSABLE. The rationale is
        for the fire department to be able to cut the power to the house
        quickly and safely in case of fire. Their breaker panel is
        located in a closet (actually the washer and dryer are there
        also) just off the kitchen in the center of the house.
                
                /s/     Bob
291.943Outside disconnects commonCSCMA::LEMIEUXWed Oct 24 1990 13:4412
    
    		Some areas in Colorado also use outside disconnects
    and panelboards. I worked in the Breckenridge/Frisco area of Colorado
    in the late 70's early 80's and we installed many panelboards and
    disconnects outside without any problems at all when done correctly. 
    
    	I think the only time that locking the disconnect is a problem
    is a multi-tennant situation. If it is your own home you can lock
    anything you want as far as the code is concerned. As for locking
    breakers in the on position, it does not affect their operation
    they will still trip as required. If the disconnect were fused
    it still would not be a problem.                                    
291.944Found the paragraph about lockingCSCMA::LEMIEUXWed Oct 24 1990 14:2110
    
    
    	In addition to my previous reply I found the only reference
    to locking a service entrance overcurrent device. It is ART. 230
    -92 in the NEC. But as I said before multi tennant situations differ.
    
    	It say's as long as the branch circuits on the load side are
    in an accessible location, and are of lower ampacity than the service
    entrance over current device you can lock the service over current
    device.
291.945Common Practice in AtlantaODIXIE::RAMSEYTake this job and Love it!Wed Oct 24 1990 18:5922
    We had our service upgraded from 60 to 150 about 18 months ago.  The
    meter is outside and there is a ~15ft run inside the house before it
    reaches the main fuse panel.  The local inspector required that there
    be a shutoff located outside between the meter and the fuse panel.  The
    meter had to be moved anyway because it was located inside the car port
    and the offended various safety rules.  The new meter box is about 24
    inches tall.  The meter itself is located near the top half and the
    bottom half has a hinged cover.  Under the cover is a main breaker
    switch.  The hinged cover has a slot which fits over a eye shaped
    protrusion so that the cover can be locked.  Aparently very common with
    new construction.
    
    As to the fire department actually using it to shutoff the power...
    As a member of a the local fire department, I can say that our
    departments policy is that we are fire fighters, not electricans.  We
    do not turn off any electricity, we have to wait for the power company. 
    This is a safety caution from the viewpoint of they know better how to
    handle electrical problems, and the process of flipping off a fuse can
    cause small arcs at other terminals and fuses inside the structure. 
    Any gas leak and you have just created a means to ignite it.  But none
    of this has anything do to with the topic at hand :^)
    
291.946SERVICE DISCONNECTWMOIS::BOUDREAU_CWed Oct 24 1990 20:4027
    RE 21,22

    	Locking the main disconnect. The article that you mentioned had to
    do with the "over current protection". We are talking about the SERVICE
    DISCONNECT. Art 230-70a states, "LOCATION. The service disconnecting
    means shall be installed at a readily accessible location either
    outside of a building or structure, or inside nearest the point of
    entrance of the service conductors." 

    	By definition (see art 100), Accessible means "Admitting close
    approach: not guarded by LOCKED doors, elevation or other EFFECTIVE
    means."

    	Readily Accessible means, "Capable of being reached quickly for
    operation, renewal, or inspections, without requiring those to whom
    ready access is requisite to climb over or remove obstacles or to
    resort to portable ladders, chairs, ect.."


    	My conclusion is as I stated before, that the SERVICE DISCONNECT
    cannot be locked in the on position. Breaker locks must be removed in
    order to OPEN the circuit. As you stated, the breaker will still trip
    internally, when locked in the on position. But the locks (effective
    means) must be removed to disconnect the service.


    				CB
291.947Many interpretations of NECCSCMA::LEMIEUXThu Oct 25 1990 12:5624
    
    
    RE .23
    
    		A perfect example of why no 2 individuals involved in
    this trade can agree on a particular article in NEC....it usually
    can be twisted any way that you want it to be. In the end, if the
    local inspector lets you lock the disconnect, it's OK to do so
    by code although it is probably not the best thing to do.
    
    	I was pointing out another option or way of interpreting the
    particular rules pertaining to the situation in the original question
    and not trying say that my interpretation was the only one that
    is viable. Sorry if I came across that way. I have been in this
    business too long to think that my interpretation is the only correct
    one. When performing this type of work you interpret the code
    according to the training and past experience you have and adjust
    accordingly when you encounter an inspector who differs from your
    point of view, within reason. Obviously if the inspector is having
    me do something that is a blatant safety problem I would certainly
    question his method.  
                         
    
    
291.77I apologize if I'm teaching my grandmother...LYCEUM::CURTISDick &quot;Aristotle&quot; CurtisThu Oct 25 1990 14:2147
    .52 has two circuits which are both wired in parallel;  the only
    difference is how they were sketched.
    
    .48 has one parallel circuit, followed by one series circuit.
    
    Parallel is what you want.  If you were to wire the lights in series,
    they would be (a) be very dim, (you could say that they were dividing
    between them the 120 volts that each should have), and (b) if one
    burned out or was removed, it would break the circuit and none would
    light.
    
    To make it somewhat more obvious:
    
    
    -hot----------------+---------------+---------------+---------------+
                     	|		|		|		|
                        |		|		|		|
    			@		@		@		@
                        |		|		|		|
                        |		|		|		|
    -white--------------+---------------+---------------+---------------+
    
    In a parallel circuit, each light (@) or other load gets the full
    voltage applied to the circuit, and the total current is the sum of
    the current consumed by each load.
    
    
    
    -hot----------------@---------------@---------------@---------------@-+
                         		 		 		  |
                         		 		 		  |
    -white----------------------------------------------------------------+
    
    In a series circuit, the voltage is "shared" by the various loads, and
    none is actually getting the full voltage.  In this case, if the four 
    lights were all the same wattage, they'd each be using 1/4 the voltage;
    your 75 watt bulbs would look mighty dim.
    
    There may be some application for this kind of thing when you are
    wiring a house, but I don't know of any.
    
    
    Don't forget that the switch goes in the "hot" side of the circuit; 
    dimmers will normally have instructions that you can follow.
    
    
    Dick
291.948SALEM::LAYTONThu Oct 25 1990 15:486
    If the goal is to shut the power off to the house, and the meter is
    outside, wouldn't it be easiest to simply break the plastic Electric
    company seal, and yank the meter?   You could lock the main disconnect,
    inside or out.
    
    Carl (definitely not a firefighter or electrician or wiring inspector).
291.949QUARK::LIONELFree advice is worth every centThu Oct 25 1990 16:4111
Re: .25

Yanking the meter creates an incredible electrocution hazard, as you
have the main feed unprotected and exposed.  When a meter is pulled, it
is replaced by an insulating glass plate.


With an outside disconnect, I'd be worried about someone coming along and
maliciously disconnecting power to the house.

					Steve
291.950Pulling meter NOT recomendedWMOIS::BOUDREAU_CThu Oct 25 1990 21:199
    
    RE-1

    	I agree, also the meter is not an approved disconnecting method. It
    is used as such in emergency situations. A problem does arise if the
    meter is pulled under a heavy load. This could cause one to draw an
    arc, which could "jump" across the LINE side of the meter. This is the
    most serious possible situation. The result could be disastrous. For
    this reason, a MAIN disconnect is required. 
291.951no twisting hereWMOIS::BOUDREAU_CThu Oct 25 1990 21:5418
    RE 24

    	I agree the not all interpretations of the code are the same.
    However, I try to interpret it as it was intended, and not necessarily
    as it can make my job easier. If the main disconnect was intended to be
    able to be locked in the ON position, it would be stated (as it was
    stated that the over current protection devise can be locked on). Since
    it is not stated, I would conclude that it not an option. This theory
    is backed up by the phrase, "readily accessible". 
    
    	As an electrician, you must know that if you give inaccurate, or
    poor advice, you could be found liable if some one gets injured by
    following the advice as given them. I know that I am not willing to
    risk neither my master's, nor journeyman's licenses. Thus, I give
    advice as I see fit, and as a lawyer may interpret the code. Anyone
    else can do as they please.
    
    				CB
291.867in-line dimmer switch ?MSEE::CHENGFri Mar 01 1991 14:376
    I bought a crystal table lamp last night. The lamp comes with one of
    those cheapo in-line switch on the power cord. I would like to replace
    it with a dimmer-switch. Is thare a in-line dimmer-switch out in the
    market ? Where can I find it ?
    
    
291.868MSESU::HOPKINSGive PEACE a chanceFri Mar 01 1991 16:284
    I just bought an extention cord with an in-line dimmer switch.  I'm not
    sure if that's what you're looking for.  It's made by G.E. and I bought
    it at K-Mart.
    
291.869QUARK::LIONELFree advice is worth every centFri Mar 01 1991 16:404
    You can get inline dimmers that hook in just like an inline
    switch.  Check most any place that sells electrical supplies.
    
    			Steve
291.870or Wolfer'sENABLE::GLANTZMike 227-4299 DECtp TAY Littleton MAFri Mar 01 1991 16:426
  You can also find a wide selection of high-quality stuff like this (if
  K-mart's GE isn't good enough) at any good lighting store. One which
  comes to mind as having an excellent selection is Wolfer's in (I
  think) Brighton. They have some really incredible lighting control
  stuff -- the sort of stuff you see advertised in Architectural Digest
  and installed in $5-million homes.
291.871Try Somerville Lumber3149::YEEFri Mar 01 1991 21:316
    I bought a couple at Somerville Lumber...works well.  Made by GE, I
    think, clamps in-line with the cord.  It has a slide on the side and
    comes in dark brown.  There is also a cheaper switch (2 position
    rotary)...  available also at Somerville lumber.
    
    Ed
291.543Electrical code violation - report it?STAR::DZIEDZICFri Mar 08 1991 11:2428
291.544Newly built houseSTAR::DZIEDZICFri Mar 08 1991 14:132
    BTW, to clarify, the house in .0 is newly built, so I'm quite sure
    the crockery was done by the electrician used by the builder.
291.545FLOWER::HILDEBRANTI'm the NRAFri Mar 08 1991 14:334
    I would report it....the "electrican" could cause future harm to others
    and should be stopped.
    
    Marc H.
291.546KOALA::DIAMONDNo brag, Just fact.Fri Mar 08 1991 16:306
    
    I'd also report, but it probably won't do any good. The local building
    inspector would have to take part of the blame also. He was supose to
    inspect the house!!!
    
    Mike
291.547VMSDEV::HAMMONDCharlie Hammond -- ZKO3-04/S23 -- dtn 381-2684Fri Mar 08 1991 17:5912
      Whether  or  not  to report the violation is pretty much up to you
      and how you feel about such things.  It might be  more  bother  to
      report  it  than  its  worth,  or you might think its an important
      thing. 
      
      On  the other hand you should get this fixed.  Having a box broken
      open to make room for more wires than allowed is  not  a  marginal
      violation  -- its a real danger.  Fixing it right may mean cutting
      the wall open to install a large/deepr  box.   That  means  $s  to
      re-drywall, re-plaster, re-paint, etc.  The builder should do this
      at no charge to you.  And if the builder is reputable he may  just
      decide not to deal with this electrician again.
291.548Makes my skin crawl.XK120::SHURSKYStuntman for Wile E. Coyote.Fri Mar 08 1991 18:184
Oooooh, just think of all the things this guy did in your walls you haven't 
found yet!  I couldn't resist.

Stan
291.549Builder first, inspector secondWMOIS::BOUDREAU_CFri Mar 08 1991 18:5413
    	I would contact the builder and ask/request that the problem be
    fixed. Also tell him that you will not pay to fix something that was
    wrong in the first place. 

    	You said that you were doing some work there with a permit. I would
    mention it to the wire inspector (if he will be coming) and see what he
    says. Sometimes we (electricians) get inspections before we really
    should (not quite finished but close enough). This is common practice
    if you are a local (your reputation has allot to do with it). However,
    this situation can change if you start doing shabby or unacceptable
    work.

    	Cary
291.558What type of wire inside conduit?JUPITR::DICKFri Mar 08 1991 23:5112
    Looks like I will be wiring my shop using conduit, since it runs
    outside of the walls it will give me the option of easy electrical
    relocation as the shop takes shape. I won't have to snake wires through
    the walls and insulation. 
    
    The question is what kind of wire to use in the conduit ?? I see both
    solid and stranded copper that appear to meet code. What are the pros
    and cons of each ? 
    
    Harold Dick 
    
    JUPITR::DICK
291.559A few pros and consSTAR::DZIEDZICSat Mar 09 1991 17:1017
    Solid wire is typically stiffer than stranded wire for a given
    size, but the stranded wire has a slightly larger cross-sectional
    area.  Stranded wire is often easier to pull through long runs of
    conduit.
    
    Other than solid/stranded, another factor in conduit wiring is the
    wire type.  The NEC allows more type THHN/THWN wires in a given
    size of conduit than type T/TW wires.  That can make a difference
    in what size conduit you use.  You'll have to get the complete dope
    from tables in the NEC, but as an example, with 1/2-inch conduit,
    and number 14 wires, the code allows 9 T/TW wires, or 13 THHN/THWN
    wires.
    
    Making connections at devices (switches/receptacles) is a little
    harder using stranded wire.  Some inspectors don't like it for this
    reason.  (A good reason to check with your local inspector first.)
    
291.560the pull is easier, the final connection is more workDDIF::MCCARTHYWell Norm, lets go take a look.Sun Mar 10 1991 14:0313
>>    Making connections at devices (switches/receptacles) is a little
>>    harder using stranded wire.  Some inspectors don't like it for this
>>    reason.  (A good reason to check with your local inspector first.)

I also thought that you had to use spade type crimp-on ends making the
connections to non-SPEC grade devices (switches, recep..) (ie stranded wire
under a screw is not allowed).

Pulling stranded wire through is A GREAT DEAL easier especally if you have any
bends to pull through.


Brian
291.550Inspector stopped by todaySTAR::DZIEDZICTue Mar 12 1991 16:1914
    The inspector stopped by today for my rough electrical inspection
    and looked at the box.  He was a little pissed the electician
    didn't replace the box when he broke the side (the couple of
    extra wires in the box didn't bother him too much).  He thought
    that perhaps a single pole switch was originally installed at
    that point, and that he flagged that as a violation; apparently
    there is a change in the 1990 code requiring switches at all
    entrances and exits to a (room? basement?).  (We got off on a
    tangent and I didn't get the exact details of the code change;
    perhaps someone else might be able to elaborate on it.)
    
    He suggested I call the electrician and tell him to fix it; if
    the guy gives me any guff I should call the inspector back and
    he'll "politely remind him" to fix it.
291.551HPSTEK::MONACOTue Mar 12 1991 16:2212
    If this is a Newly constructed house in Mass you may have some legal
    clout. I belive but I'm not positive that Contractors/builders are
    required to fix problems for a period of one year. 
    
    We are on our third home and I have dealt with a number of contractors
    and tradesmen. I have had good luck with them fixing problems that have
    occured or were discovered after several months. 
    
    Check with your builder first and by all means DOCUMENT all conversations
    and letters to be on the safe side.
    
    Don
291.552its your moneyELWOOD::DYMONWed Mar 13 1991 09:495
    Look at it this way.  Your paying for it.  You might as
    well get it done right.  You wouldnt buy a new car with
    one flat tire now would you?????????????
    
    JD
291.561pulling and bendsWORDS::DUKEThu Mar 14 1991 10:5620
>       Pulling stranded wire through is A GREAT DEAL easier
>   especally if you have any bends to pull through.


        There are restrictions in NEC on the number of bends
    between pull/junction boxes.  Unless things have changed
    recently, the limit it 360 degrees of bends.  Sounds like a
    lot of bends, but it adds up fast when you consider all of
    the little offsets and saddles to get around things.  The
    closer one gets to the max number of conductors the harder it
    is to pull regardless of the number of bends.

        If you have never worked with EMT or other conduit, be
    prepared to make a few pieces of spaghetti.  Once you get the
    hang of it, it is almost fun.


    Peter Duke

291.562that hard ??FREDW::MATTHEShalf a bubble off plumbFri Mar 15 1991 11:496
    
    Do you mean making spaghetti by pulling the insulation off the wires ??
    
    By the way, what about the use of soap or vaseline ??
    
    -f
291.563I thought the code said no to soap/vasline.EVETPU::IMPINK::mccarthyWell Norm, lets go take a look.Fri Mar 15 1991 14:114
I think soap and vaseline are against code.  There is a product out
there that is UL approved.

Brian
291.564Not wire damageWORDS::DUKEFri Mar 15 1991 15:1328
    
>   Do you mean making spaghetti by pulling the insulation off
>   the wires ??

        No, not damage to the wires.  I was thinking of my first
    attempt at bending EMT and how easy it was to make things
    like offset (especially at boxes) go in the wrong direction.
    For a shop or garage, it sure beats all that drilling.  Makes
    adding a new circuit in the future MUCH easier unless the
    pipe is full.

        If you happen to be in Merrimack or near by, I have 1/2
    and 3/4 inch benders you are welcome use.

        I spoke with one of the contract electricians here (MKO).
    He stated that many inspectors require crimp lugs on stranded
    wire for devices that have only screw connections.  If the
    conductors are passing through a box, another alternative is
    to wire nut in taps of solid wire for connection to the
    device.  This type of arrangement is generally prefered to
    using the bond strap (between screws) on the device.  This
    also avoids opening the circuit to replace the device.  More
    important in commmercial than residential.



    Peter Duke

291.565Wire LubeESDNI4::FARRELLBlack Pearl Express Trucking, LTD.Mon Mar 18 1991 12:4115
<<< Note 4158.5 by EVETPU::IMPINK::mccarthy "Well Norm, lets go take a look." >>>
                -< I thought the code said no to soap/vasline. >-

I think soap and vaseline are against code.  There is a product out
there that is UL approved.

Brian

> Most Electrical Supply houses carry "Wire Lube".  Comes in a 1qt bottle
>and resembles a grayish paste.
>
>Runs about $5 - $7 a bottle
>
>/Joe

291.566"Duck Butter...."RAVEN1::GHOOPERParrotheads Make Great Lovers!Tue Mar 19 1991 02:175
    There is a product that is used. It is commonly called "soap" by a lot
    of electricians, but it is not actually soap. We used to call it "duck
    butter".  Can't remember the actual brand name.
    
    	-Hoop-
291.567real slippery stuffEVETPU::MCCARTHYWell Norm, lets go take a look.Tue Mar 19 1991 02:216
We used to call it lube, and usually had the color of Mellow-Yellow.  We
usually only used it for underground services and if you got it on your hands
you might has well take five minutes off and clean your hands because you can't
get a grip on ANYTHING!

bjm
291.568IDEAL wire pulling lubeCSCMA::LEMIEUXTue Mar 19 1991 11:3311
    
    	Hi,
    
    		A brand that comes to mind is made by IDEAL, wire pulling
    lubricant. You can buy it in a can like paint or a squeeze bottle.
    It's cheap and save lots of labor and avoids lots of damage to the
    wire and to the conduit if the conduit is PVC. 
    
    	I have a name for it also....but I can't use it here :') 
    
    	Paul
291.553Code change?FDCV06::MARINOWed Mar 20 1991 18:269
    Can someone clarify the 1990 code change about switches to entrances
    and exits.  We just built a new house, and there is now switch next
    to the door leading to the bulkhead, sort of confused me.  
    
    Also, is a requirement to have circuit breaker outlets in bathrooms,
    or can they use any type of outlet.
    
    thx! :^)
    
291.569Can you flare the end for several inches, by a small amount?LYCEUM::CURTISDick &quot;Aristotle&quot; CurtisWed Mar 20 1991 19:259
    I've a question about working the conduit.
    
    I have a mechanical, not electrical, application for which I thought
    that the conduit would be fine;  alas, the inside diameter is small by
    a very small amount.  Is it possible to make 1/2" conduit expand, by
    a small amount, for a length of 4 or 3 inches?  Or is it either
    impossible, or a dicey thing that's likely to spoil the stock?
    
    Dick
291.570RAVEN1::GHOOPERYou help me more by not giving in..Thu Mar 21 1991 09:013
    They sell conduit stretchers at the same place as they do grid squares. 
    
    	-Hoop-
291.554Depends on what you have around...HNDYMN::MCCARTHYWell Norm, lets go take a look.Thu Mar 21 1991 09:5212
>>    Also, is a requirement to have circuit breaker outlets in bathrooms,
>>    or can they use any type of outlet.

	May I assume you mean GFI protected outlets?  If so, Yes.  There are
several ways of doing this, a GFI receptacle or a "normal" receptacle provided
that it is GFI protected.  The second part can be done by having the receptacle
wired into the "load" side of a GFI receptacle. someplace else in the house or it
can be on a GFI breaker.  If you have more than one bathroom it is common that
one will have a GFI receptacle and the second will be wired to the load side of
this, hence protecting it.

Brian
291.571Don't suppose anyone would be willing to lend one for a night...LYCEUM::CURTISDick &quot;Aristotle&quot; CurtisThu Mar 21 1991 13:133
    Great!  Would you know if they're expensive?
    
    Dick
291.572NOTIME::SACKSGerald Sacks ZKO2-3/N30 DTN:381-2085Thu Mar 21 1991 13:271
What's a grid square?
291.555GFIFDCV07::MARINOThu Mar 21 1991 18:066
    RE .11
    
    We have 1 1/2 baths the upstairs has a "GFI" breaker, (the kind
    with the reset button/test button.  But the downstairs bathroom
    only has what looks like a regular outlet.
    
291.556Test it to see if it is protected.XK120::SHURSKY&lt;DETOUR&gt; Easy Street under repair.Thu Mar 21 1991 18:539
The one with the regular outlet may be protected by the other GFI outlet (refer
to .11).  To test it, press the "TEST" button the GFI outlet, run down stairs
and plug something into the other outlet.  If the something works then that GFI 
is not protecting the downstairs outlet.  Try this with any other GFI outlets
in the house.  If none of the GFI outlets disables the downstairs bath outlet,
then I wouldn't use the hair dryer while standing in a puddle of water in the
downstairs bath.  %-{

Stan
291.573Ever been 'Snipe' hunting?RAVEN1::GHOOPERYou help me more by not giving in..Mon Mar 25 1991 05:0910
    RE: -1
    
    	A "conduit stretcher" is an old gag that is played on new
    electricians' helpers and "grid squares" is an old gag played on new
    recruits right out of boot-camp. 
    
    	"......go fetch me a box of 'grid squares', Private, and don't come
    back with out 'em....." 
    
    	-Hoop-
291.574WMOIS::VAINEThe Silver BulletMon Mar 25 1991 10:314
    you get those things the same place you get right and left ground
    straps.......
    
    lynn
291.575SALEM::LAYTONMon Mar 25 1991 12:543
    ...and fetch me a bucket of steam...
    
    ...from the sea locker...
291.576KENT::KENTPeter Kent - SASE, 223-1933Mon Mar 25 1991 15:311
    ...and clean the contacts on the SCRs.
291.577Abrasives might serve me -- and .12 obviously has a source...LYCEUM::CURTISDick &quot;Aristotle&quot; CurtisMon Mar 25 1991 16:278
291.578Likewise ... '.. relative bearing grease ..'AHIKER::EARLYBob Early, Digital ServicesMon Mar 25 1991 16:4211
    During a stint at an Environmental Research and Survey Company, we
    were "on the river" near Albany, NY with "in situ" (in place) water
    direction and speed meters, and the diving supervisor sent the
    conract technician for a can of "relative bearing grease" ...
    
    Would probably work as well during an Orienteering Meet..
    
    Bob
    
    
291.579Sorry, son, fresh out...try the hanger across the fieldULTNIX::taberBitingly cold. Extra Dry. Straight up with a twist.Tue Mar 26 1991 11:274
...20 yards of flight line....a bucket of propwash (rotorwash if you
work on helicopters)...

brings back memories.
291.580RAVEN1::GHOOPERYou helped me more by not givin' in..Wed Mar 27 1991 01:459
    RE: .16
    
    	Ha! I haven't heard that in a long time!
    
    RE: .19
    
    	Watch it, buddy!  :-)
    
    	-Hoop-
291.581Water HammerMEIS::TOWNSENDErik S. Townsend (DTN) 247-2436Wed Mar 27 1991 12:2412
A typical scenario in a volunteer firefighter-candidate's oral exam:

Examiner:	"Let's see, on Engine #5, which compartment is the Water
		Hammer stored in, and what is it used for?"

Usual Ans:	"Uh, I think its in the left rear compartment and its
		used uh, I think to blow water through a door..."

(For the uninitiated, Water Hammer is not a device but an undesirable
phenomenon which can destroy a pump if proper action is not taken)

ET
291.582bit bucketsPCOJCT::MILBERGI was a DCC - 3 jobs ago!Wed Mar 27 1991 20:519
    Surprised that with all us kumpooter types, no one has mentioned the
    infamous
    
    		"bit bucket"
    
    which - in the days of paper tape or card puches - DID exist!
    
    	-Barry_who_is_old_enough_to_remember_and_young_enough_to_remember-
    
291.583My sides hurt!EPOCH::JOHNSONIf we build it, they will come.Wed Mar 27 1991 23:266
Does this discussion have anything to do with when we used to send guys back
aft on a carrier for a 'bucket of steam' or 'twenty feet of chow line' or a
dozen 'relative bearings'?

How about left- and right-headed nails (not to mention ceiling- and
corner-nails)?
291.584Don't forget the wind shiftersSEESAW::PILANTL. Mark Pilant, VMS SecurityThu Mar 28 1991 00:004
    How about the infamous left and right handed wind shifters.  These
    are great for directing smoke from a campfire.
    
    - Mark
291.585QUARK::LIONELFree advice is worth every centThu Mar 28 1991 12:253
    Or the classic left-handed monkey wrench.
    
    		Steve
291.586polka-dot paintCLOSET::VAXUUM::T_PARMENTERBrain thieves!Thu Mar 28 1991 12:261
skyhook
291.587old swabbies neverBTOVT::CACCIA_Sthe REAL steveThu Mar 28 1991 14:062
    aboard a carrier you would also have needed a pad-eye swab.
    
291.588The way this note is going,.... seems appropriate.MARX::SULLIVANWe have met the enemy, and they is us!Thu Mar 28 1991 15:357


	Has anyone found the best price for an air shredder now that Spags
doesn't carry them anymore.

						:-)
291.589ULTNIX::taberBitingly cold. Extra Dry. Straight up with a twist.Thu Mar 28 1991 15:512
Wadda mean they don't carry them anymore?  They're right next to the
conduit stretchers, by the flight line over by the left-hand ground straps...
291.590:-)NOVA::FISHERIt's SpringMon Apr 01 1991 14:404
    Well, now that we can't get any work done 'cause nobody can find the
    necessary equipment, let's all go on a snipe hunt....
    
    ed
291.591how short?NOVA::FISHERIt's SpringMon Apr 01 1991 14:413
    Anybody got a diagram of a short circuit?
    
    ed
291.592Oh those werethe daysCSDNET::DICASTROQuantity time!Mon Apr 01 1991 19:045
    And of course, no Saturday at the garage would be complete without
    sending the apprentice to the juck yard/parts store for a VW radiator.
    
    
    
291.593Oh NO!! - not the air shredder!!FREDW::SYSTEMhalf a bubble off plumbTue Apr 02 1991 13:216
    
    I kneeeeew someone would mention an air shredder.  Frankly, I'm
    suprised that it's not a code requirement that the air in the conduit
    has to be shredded in order to pass inspection.
    
    How does the inspector do that without it all leaking out ??
291.594the jokes on you......CSC32::J_KALINOWSKIForget NAM?....NEVER!Wed Apr 03 1991 15:0015
    
        RE:  .27
    
          LEFT and RIGHT hand monkey wrenches DO exist as well as
    crescent wrenches. I have both kinds and they have both been
    around for about 70 years.
    
         Either one of the left handed wrenchs will have left hand
    threads so that the natural motion of thumb and index finger
    OF THE LEFT HAND will accomplish the same task (opening or closing
    the jaws) as a right hand wrench would do. If you shop at "REAL"
    plumbing supply stores or auto parts stores they can show you both
    kinds. You don,t find real tools at K-MART.
    
    -john
291.595Don't forget Metric!CSCMA::DENCEThu Apr 04 1991 15:021
    YEP!  And they ALL come in metric sizes!!!
291.596That reminds me of a story.....AUNTB::SIMONFri Apr 05 1991 13:003
    in those days of propwash...you could also be sent for a buffer
    amplifier to make the buffer run better when buffing the barracks
    floor....
291.557resolution?ULTRA::WITTENBERGSecure Systems for Insecure PeopleFri May 17 1991 19:526
    So, did the electrician fix it? 

    Also, did  you  talk  to  the  builder  to  let  him know what the
    electrician did?

--David
291.597Line for 60amp circuitDATABS::ROYALThu Jun 06 1991 18:2212
    
    I need to extend a dedicated 60 amp circuit (2 30amp breakers) for my 
    dryer.   I need to extend the line about 6 feet (hence move the existing
    recepticle with it).   What I'm planning on doing is simply using a 4" 
    metal junction box and 6 feet or so of new wire to run from the junction 
    box to where I want the dryer recepticle to reside.   My problem is that
    I don't know what kind of wire to buy and I can't find any indication
    on the existing line.
    
    Thanks in advance.
    
                      -- Phil 
291.598CSC32::GORTMAKERWhatsa Gort?Fri Jun 07 1991 03:184
    The wire is probably either 10/3G or 8/3G the 10/3g is a flat cable
    the 8/3g will be round. Hope this helps you identify what you have.
    
    -j
291.599I may have some.SMURF::PINARDFri Jun 07 1991 11:564
    10-3 +G doesn't have to be flat...
    I'll check this weekend to see if I have a small piece hanging
    around...
    Jean
291.600220v 30ampDATABS::ROYALFri Jun 07 1991 13:216
    
    Thanks.   Ya, what I hadn't realized is that this line is really a 220
    volt 30 amp line, hence 2 30amp breakers are needed.   I have some 10-3
    plus ground wire hanging around.
    
                  -- Phil
291.601Cu or Al wire?CXCAD::RSMITHRandy Smith, CX01-1/Q11, DTN 522-6712Wed Jun 12 1991 13:5112
     I realize this message is after the fact, but there are a couple of 
     points which may not be clear to everyone.  Yes, 10 gauge is rated at 
     30 amps for both Cu and Al.  However, there are different rules for 
     dealing with Cu and Al splices.  Cu-Cu splices are made with a wire nut.
     Al-Al splices are made with a wire nut and an anti-oxidizing compound.  
     I don't have my NEC (National Electrical Code) book handy, but I believe 
     Cu-Al splices with a wire nut are not allowed.  It wasn't clear in the 
     original message whether Cu or Al wire was being used.

               -- Randy
    
291.602Table 310-16 WMOIS::BOUDREAU_CWed Jun 12 1991 20:026
    	#10 AL may be rated for 30 amps. But if you look at the obelisk
    note you will see that the over current protection shall not exceed 25
    amperes.

    	CB

291.603It's a double breaker, not two singlesPOLAR::PENNYFind me in my field of grassWed Jun 12 1991 20:5212
    Re: .3
    This is a 220 Volt, 30 Amp line, but the "two" breakers should be "ganged"
    together at the toggle. (The thing you flip when a breaker trips.) This
    is a double breaker, usually riveted together on the body portion. 
    There should be a steel rod going through both toggles and held in with
    a small circlip at each outside edge. This is for safety. ie: When one
    "hot" side trips, it mechanically pulls the other hot side off in
    conjunction. So, if it trips, it's FULLY tripped off on both busses.
    (Red AND Black). 8/3 wire should be used as you're driving a motor, a
    resistance heating element, (and a timer). The farther from the main
    panel you are, wire guage goes up. 8/3 is sufficient in most homes
    unless your run is around 80 or so feet.     dep
291.604note 9, table 310-16CXCAD::RSMITHRandy SmithThu Jun 13 1991 13:5110
    Re: .5

    Yes, Al #10 is initially rated at 25 Amps.  But, NEC also says:
    "Where the standard ratings and settings of overcurrent devices do not
    correspond with the ratings and settings allowed for conductors, the 
    next higher standard rating and setting shall be permitted."
    Since 25 Amp 2 pole breakers are not made and the closest breaker is 
    30 Amp, then Al #10 can be upgraded to 30 Amp capacity.

                  -- Randy
291.605FLOWER::HILDEBRANTI'm the NRAThu Jun 13 1991 15:494
    Well....I know what the table says,but,I would go with the "lower"
    standard rating,not the "higher". Al and Cu just are not the same.
    
    Marc H.
291.606"I don't have one in the truck" is NO excuse!!WMOIS::BOUDREAU_CThu Jun 13 1991 20:037
    Randy,

    	Just because one doesn't carry a 2 pole 25 amp breaker doesn't mean
    that it isn't available. They are available. Most electrical
    manufactures make them. Not all wholesalers stock them.

    	CB
291.78LEZAH::KILFOYEFri Jun 14 1991 12:2416
    
    This may have been answered before, but...  I would like to convert an
    existing two prong receptacle to a three-prong grounded receptacle. 
    The problem is that wire running from the box is older two-wire romex
    cable with no third ground wire.  Is it okay for me to simply ground
    the receptacle by installing a ground wire from the receptacle to the
    metal outlet box?  I'm not planning on running new cable from the
    circuit breaker box to the outlet, so that's out.  If I can't do it
    this way, should I just stay with the ungrounded two-prong receptacle?
    I also need to install an ceiling fan and I plan to wire it with a
    wall switch to a receptable. Once again, there is no third wire at the
    receptacle.  
    
    Thanks,
    
    Chuck
291.79Already hereODIXIE::RAMSEYPut the Environment FirstFri Jun 14 1991 12:323
    See note 3637 for information about 2-prong to 3 prong upgrade.  Last
    count had over 45 replies.
    
291.607CXCAD::RSMITHRandy SmithTue Jun 18 1991 14:155
   Re - 9

   Oops...my mistake.  
   
         -- Randy
291.608Rough estimate for electrical workKAHALA::PALUBINSKASMon Jul 01 1991 14:135
    Need to have approximately 6 electrical wall plugs, 3 ceiling light 
    fixtures and an 8 foot electric baseboard heater installed in basement.
    Could someone give me some type of estimate which I should expect to
    pay ?  Thanks Janet.
    
291.609More information neededSASE::DUKEWed Jul 10 1991 10:3423
>   Need to have approximately 6 electrical wall plugs, 3 ceiling
>   light fixtures and an 8 foot electric baseboard heater
>   installed in basement.  Could someone give me some type of
>   estimate which I should expect to pay ?  Thanks Janet.
    

        Not much to go on here.  Is the area finished ie dry
    wall, trim, paint, etc?  If it is, the job is considerably
    more difficult and takes much more time and care.  Is there
    space for new circuits in the existing electrical panel?  How
    large is the area?  How far to the electrical panel?  All
    three lights on one switch or individual switches?  Three way
    switches?  Is this a DYI job?  Lots of this things to be
    considered before anyone could make much of a guess.

        Not trying to rain on the parade, but more information is
    needed.


    Regards,
    Peter Duke

291.610QUARK::LIONELFree advice is worth every centWed Jul 10 1991 12:545
Why not call in an electrician (or three) and ask for an estimate?  They're
free.  There are too many variables to account for without actually seeing
the job to be done.

				Steve
291.611EVMS::PAULKM::WEISSTrade freedom for security-lose bothWed Jul 17 1991 11:215
At the request of the author, I moved the note about buying the fixer-upper and
its replies to note 634, which is titled "Should we buy this fixer-upper?"

Paul
[Moderator]
291.613How do I know wiring is 20 amp v.s. 15 amp? NODEX::BRASSMon Jul 22 1991 16:0911
Hi,
	I am having trouble running my air conditioner in the upstairs 
of my house(condo/townhouse). The upstairs runs on a 15 amp fuse and the 
ac draws a lot of power sometimes and blows the fuse. My downstairs runs
on a 20 amp fuse, and I am considering useing a long extension cord or 
something to run the ac off the downstairs. How do I know the downstairs wiring
is 20 amp and the previous owner did not just put a 20 amp fuse in place of
a 15. Is it normal to have the upstairs wired 15 amp and the downstairs 20 amp
I would think they would be the same. Also if anyone has any ideas about the 
ac problem they would also be apreciated, the ac is a sears 10,500 btu.
		Bob
291.614Don't do it!ELWOOD::LANEMon Jul 22 1991 16:489
15 amp circuits are wired with 14 gauge wire; 20 amp circuits use 12 gauge.

Do _NOT_ run your air conditioner using a long extension cord. It's an
excellent way to burn your house down. There are a lot of reasons why
this won't work and shouldn't be done. The first that comes to mind is
the generally poor connectors the extension cords use. They overheat
under heavy loads.

Mickey.
291.615QUARK::LIONELFree advice is worth every centMon Jul 22 1991 16:498
Don't do it.  The long extension cord can't handle the power draw.

Anyway, to answer your question, you'd have to look at the size of wire
used for the circuit.  If it's 14-guage, it's a 15-amp maximum circuit.
If it's 12-guage, 20 amps is allowed.  You may be able to see the size
stamped on the sheath of the cable as it enters the fuse box.

				Steve
291.616GIAMEM::S_JOHNSONBan all gunsMon Jul 22 1991 17:158
If it's a 15 amp circuit and the AC keeps blowing fuses, try a 15 amp 
slo-blo fuse.  They're designed to withstand the tempoarary surge in current
when a motor kicks in (in your case, the AC's compressor)

My Panasonic 8000 BTU does the same thing, when plugged into a 15 amp 110 volt
circuit.

Steve
291.617What does NEC say about wire size within circuitsSEURAT::NEWMANChuck Newman, 297-5499, MRO4-1/H16, Pole J13Mon Jul 22 1991 17:3325
291.618Extension cord idea is out :-(NODEX::BRASSMon Jul 22 1991 17:4010
Thats a bummer about the extension, I thought those big long orange extensions 
were suppose to be able to handle a lot of power, but I am NOT going to take the 
chance with my house. 

I tried the slow blow fuse idea last year and still blew the fuse. Do they
have different types of slow blow fuses, maybe some slower than others?
For now I run the ac through a power strip with its own 15 amp circuit breaker
that saves on fuses and trips down stairs to change them :-)

		Bob
291.619FSDB45::FEINSMITHPolitically Incorrect And Proud Of ItMon Jul 22 1991 17:4916
    RE: .4, the SMALLEST guarge wiring in a run is what the fuse/cb is
    sized to. Generally, the inspectors will not OK a mixture of wire and
    of you had a 12/14/12 which was protected by a 20 A fuse, its plain
    dangerous and illegal.
    
    RE: .5, perhaps you have something on that circuit besides the A.C.
    I don't know what your 8000 BTU machine draws, but a 9500 in my shop is
    rated 12 amps. First see what else in on the circuit. If nothing is on
    it, you might want to check the connections at each outlet on the
    string. Often, electricians use the push in terminals at the outlets.
    These may loosen with time, causing a voltage drop. You also might want
    to meter the circuit with the a/c compressor kicks in, to see what the
    voltage drop is. A final possibility is a defect in the a/c itself
    causing it to draw too much current.
    
    Eric
291.620QUARK::LIONELFree advice is worth every centMon Jul 22 1991 18:099
My bedroom AC unit is 8000BTU and it is on a 15A circuit.  The lights dim
when the compressor kicks in, but I've only blown the fuse once and
I think I had some other things going on that circuit. Still, at 8 amps or
more, you're better off if you can put it on a legitimate 20A circuit.

Another thing you might try is the screw-in circuit breakers that
replace the fuse.  They seem to be more tolerant of surges.

			Steve
291.621Put in a dedicated circuitVMSDEV::HAMMONDCharlie Hammond -- ZKO3-04/S23 -- dtn 381-2684Mon Jul 22 1991 18:588
      The  best thing to do is to install a dedicated, 20Amp circuit for
      your air conditioner.  The most difficult part of this is  finding
      a  way to get the wire from the fuse or circuit breaker box to the
      location of the air conditioner.  If you'd be  willing  to  run  a
      small  conduit  up  the outside of the building even this would be
      fairly easy.  An experienced electrician should be able to do this
      in  two  or  three  hours  maximum.   (Of  course,  there could be
      difficulties that I'm not anticipating.)
291.622CHIEFF::MACNEALruck `n' rollMon Jul 22 1991 19:163
    Have they stopped selling those heavy gray extension cords designed for
    appliance useage?  Finding one long enough to go to the first floor
    might be a problem.
291.623QUARK::LIONELFree advice is worth every centMon Jul 22 1991 19:256
Re: .9

They still sell them, but they tend to be 3 feet long.  I have seen
14-gauge 50-foot cords, but I would not recommend running an AC from one.

		Steve
291.624while we're on the subject of a dedicated circut...SNAX::HURWITZMon Jul 22 1991 23:197
    Anyone have a guess as to how much a dedicated circut/outlet for an
    8amp AC would cost to have put in.  The main box in the basement is
    probably 25' from where the line would enter the floor above.  Looks
    like it would be easy but I don't have the know how to wire it into the
    big box?
    
    Steve.......
291.625It isn't enough for wiring to be safe when installedRGB::SEILERLarry SeilerTue Jul 23 1991 16:1220
I've heard it said that one should *never* use 12-gauge wire on a 15amp
circuit, for precisely the reason cited in .4.  Someone (including the
original installer) can come along years later, see a 15A fuse/breaker
attached to 12 gauge wire, and conclude that it's safe to upgrade to a
20A fuse/breaker, not knowing (or unable to discover) that there's a 
piece of 14 gauge wire hidden in a wall somewhere in the circuit.

We tend to concentrate on the problem of installing wiring that is safe.
A far tougher problem is installing wiring that will *stay* safe through
decades of use and modification.  Part of staying safe is doing things in 
such a way that it's easy to tell whether one is doing the right thing.  
Consistency, such as using consistent wiring sizes, helps a lot.  

Of course, it would be long-term safe to use a 15A breaker if *all* of the 
wiring on the circuit is 12 gauge.  But in that case, why not just use a 
20A breaker?  And if the reason to use 12 gauge is because of voltage drop 
in a big house, it might be a better solution to put in a subpanel.

	Enjoy,
	Larry
291.626KAOFS::S_BROOKThe U word makes me c-sick!Tue Jul 23 1991 20:279
    On the other hand, my training tells me that if a circuit is
    installed with a 15A breaker, then it should remain that way,
    even with 12 ga wire, because there is something in that circuit
    with a 15 amp rating.  Only if I can trace the entire circuit and
    be satisfied that it qualifies for 20A should the breaker be
    upgraded.  It would make far more sense if the codes were written
    that way instead of the more illogically restrictive way they are now.
    
    Stuart
291.860220V/120V lines with 3-wire SE cableLANDO::DROBNERVAX 6000-500 Systems EngineeringThu Sep 05 1991 14:1339
This topic seems to be a appropriate place for this; 

I am looking for some advice on specific code requirements -

I am doing some bathroom remodeling (new window, tile floor, etc) and 
adding a whole house attic fan.  

I need to get power to the fan (120V at 8Amps steady on high).

I have a unused piece of wire that currently runs from the circuit breaker
box located in the basement to the bathroom upstairs.  This wire is currently
not USED - it is not connected in the CB box and ends in a junction box in
the bath.  This wire is 6/2 with a bare GND, AL, SE (service entrance cable).
Now you may think that this is pretty strange!! - It was going to be used to
power a sauna heater in the bathroom which was never installed.

So what I would like to do is add another piece of wire from the junction
box in the bath up to the attic.

Now come the questions - 

1) Do I run this as 240V line from CB box - and in the attic add a sub-panel
   and pull 120V off of one side.

	I think I can NOT do this since I only have 2 Hots and a GND, I
	am missing the neutral wire.  (SE cable is 3 wire - to do this I
	would need 4 wire cable - 2 Hots, 1 neutral, and GND.

2) Do I run this as a 120V line from CB box - (on a 20AMP breaker)?

	Need to mark the end of the cable to white from black or red
	that is in the CB box.

3) If I do run this as a 120V line can I change the wire size at the junction
   box in the bathroom to 12 gauge (with appropriate AL-CU cable connectors).

	I think this is also NOT allowed.

Thanks/Howard
291.861not aluminum!!!SALISH::ROBERTS_JOLife IS fair in the Pacific NW.Fri Sep 06 1991 12:1013
    When you use the term AL do you mean you have aluminum wire?  If so, I
    would try to get power from somewhere else.  The aluminum expands and
    contracts and over time has a loose connection with more resistance
    creating heat and poor connections and more resistance and more heat
    and...get the picture?  It can burn you.
    
    If you do use it, just get some white tape to put on the red wire.  Now
    you have a black - hot, white - neutral, and bare - ground. If you must
    splice to make the wire reach, better use more aluminum. And make sure
    you have a good tight connection - and check it in a year or so and
    tighten it up again.  If you connect copper with the aluminum, buy some
    good insurance.  
    
291.862WLDBIL::KILGOREDigital had it Then!Fri Sep 06 1991 13:156
    
    re .25:
    
    You should stop at point 1. With no neutral, there's no acceptable
    way to tap 120 off the feed.
    
291.349Change two prong to three prong outletsNODEX::BRASSTue Nov 12 1991 14:085
HI,
	I want to change my outlets, I have the old two prong and they have
a ground wire connected to the box. Can I just connect the ground to the outlet?
		Thanks
		Bob
291.350BGTWIN::dehahnNinety eight...don't be lateTue Nov 12 1991 16:148
No.

You must bond the box, ground wire, and ground terminal on the outlet together 
using a wire nut. The metal box will have a tapped hole which you can use for
its ground lead.

CdH
291.627So I WAS right...JUNCO::CASSIDYMission: Repair with care.Sat Jan 04 1992 02:2911
	    All this talk about "black tape on the white wire" got me to
	believing my electrical shop teachers had misguided me.  They 
	never mentioned this because we always used Romex and were in-
	deed following code.  My intention was not to cause people to
	lash out in response for my 'supposed' misinformation.
	    Many thanks to those who helped clarify this... and prove
	me right.  ;^)

					Tim

291.1021What size circuit?NICCTR::MILLSFri Jan 24 1992 02:1140
    This is the closest note I've seen on the subject I'm interested in.
    I've done ton's of DIY wiring and I'm pretty proud and pretty sure I've
    done it right. I've had the same problem as the base note and I think
    it was good advise.
    
    My problem is this. I'm trying to install a large backup electric
    heater for a oil furnace that is not always dependable. I wanted to
    stick with something that was under 20amps if possible. Because of
    cost. I Looked through one brochure and they seemed to go from #14 wire
    recommended to #10 (and skipped #12). But that made sense since no AMP
    ratings were in the 12-18 amp range. Another brochure listed a portable
    that pulled 16.67amps @240v that specfied the 20 amp outlet (the kind with
    one blade that goes across but 240v) but did not specify wire gauge.
    
    I also found another brochure that listed a 16.67 amp unit. I figured
    that this was a magic number (as high a powered unit you can fit on a
    20 amp circuit). I'm getting their keep reading :-). Finally I decided
    on a unit that listed it at 16.67 amps and recommened #10 wire. I
    assumed the #10 was a misprint (in brochure) and when I received the
    unit the specs say #10 wire but do not specify how many amps (except in
    brochure, maybe 16.67 was a misprint?).
    
    I've always assumed (for both 120v or 240v 2 wire or 3 wire) that
    
    #14 for 15amp circuits
    #12 for 20amp circuits
    #10 for 30amp circuits
    
    If it draws 16.67 (@240v) why do they spec #10 wire. If you had to wire
    a 240 16.67amp load circuit what wire do think would be needed? I've
    always used 10-3 for 30amp!! 240v dryers. I don't think it's to handle a
    surge since heating elements come up smooth and the motor is very
    small. Should I use 10-2 and 30amp breaker or 12-2 and 20amp breaker. I
    also had to buy contact relays (for low voltage control) which are
    pretty expensive for higher amperage (20 going to 30). I beleive there
    is a rule that says your load should not exceed ~85% (not sure on
    exact number) of a circuit. 16.67 amps comes out to 83% of 20amps. So
    20 amps seems to make sense. But using #10-2 on 20amp breaker doesn't
    make sense to me. The unit is 4000watts @240v which can be coverted to
    amps but I forget how.
291.1022#10 vs. #12RGB::SEILERLarry SeilerFri Jan 24 1992 15:5725
My best understanding is:

    You don't need to use #10 wire to a 20A outlet.

    So if it can plug into a 20A outlet, you can use #12 wire.

    But heater loads are supposed to be only 80% of max rating.

    So if it really draws >16A, why does it have a 20A plug?

My guess would be that #10 is recommended because it will have less
voltage drop than #12 -- and for >16A of current, that's a consideration.

However, I just got my garage inspected, and all of my electric baseboard
heaters use #12 wire.  Of course, none of the circuits exceed 16A, which
is about 15 feet of baseboard heater.  I'm thinking of putting 16' of
heater on some of the circuits, but that isn't the way I've got it set
up now.  I'll only turn them on when I'm working out there in the winter,
and that's not going to be very often.

	Luck,
	Larry

PS -- Watts divided by Volts equals Amps:  4000/240 = 16.67A.  Of course,
the line voltage may be more or less than 240V...
291.1023So 80% is the numberNICCTR::MILLSSun Jan 26 1992 03:2120
    Thanks for your excellent reply.
    
    When you say "voltage drop is a consideration" do you mean efficientcy
    or danger.
    
    The number 80 something always stuck in my head. So you say it's 80,
    Is that code? Hmmmm 80% applys to just heaters?
    
    I called the manufacturer and they said #10 and 20 amp breaker.
    I called an electric supply house and asked them what I needed #12 and 20amp
    I called mass electric and they asked an electrician and said #12 and 20amp
    
    I was going to go with #12 until I read your reply and stated the 80%
    figure. I guess I'm right on the edge and different people have
    different opinions. Another reason why I don't like using #10 is it
    "labels" the line as 30amp. In 10 years when I'm gone somebody will
    probably try to plug a dryer in it.
    
    Does the 80% apply to the wire or breaker or both? In other words
    should I use 25-30amp breaker since I exceed 80% of 20amps.
291.102416 is a "magic" numberREGENT::GETTYSBob Gettys N1BRM 235-8285Sun Jan 26 1992 15:0231
                The radio club that I belong to just had some new wiring
        added for a linear (power amp) at the town CD headquarters and
        the job of deciding exactely what to do and babysitting the
        electrician while it was done fell to me. What we ended up with
        is three long 20 amp 120v circuits running from the emergency
        generators main panel back to the room. The electrician had some
        interesting info - some of which I knew without knowing I did -
        some nice to know. One piece was the 16 amps as the max steady
        load on a 20 amp circuit. The other was using #10 for a long run
        on a 20 amp circuit (these runs were about 150 feet!). Something
        else - one of the circuits was outfitted for a twist lock
        recptacle which is a 30 amp receptacle. This became legal
        because of the use of #10 wire which is the minimum for a 30 amp
        circuit. (We wanted the circuit to be dedicated and unusable for
        anything else!) The only 20 amp item on the circuit is the
        breaker itself. (Dictated by the fact that there wasn't a 30 amp
        one available - old and non-standard boxes cause problems!)
                
                In the process of doing this - it was discovered that
        the current wiring to the CD rooms was done incorrectly. I'm
        sure we all know the trick of running a pair of 120v circuits
        with three wires (two hots and a neutral) by using the opposite
        sides of the distibution (the current in the neutral will be
        the current drawn by one side minus the current drawn by the
        other). This had been wired that way but the hots were BOTH
        taken from the same side of the distribution! Now if the two
        circuits had full current drawn the neutral would be carrying
        TWICE its rated current!!! And this was supposedly installed by
        competent electricians!!!!!!
                
                /s/     Bob
291.1025some of them just don't check....TLE::MCCARTHYDECTPUSun Jan 26 1992 16:0616
>>        other). This had been wired that way but the hots were BOTH
>>        taken from the same side of the distribution! Now if the two

was most likly caused by:

>>        one available - old and non-standard boxes cause problems!)

It was most likly assumed that every-other spot was on a different leg of the
220 service.  When dealing with older boxes that assumption is not always true.
Fuse style panels led themselves to this type of error very easily.  The old
Federal Pacific had SEVERAL different styles of plug in modules, you had to
make sure were were on different legs of the service.

bjm


291.628Electrified plumbingCUPMK::PHILBROOKCustomer Publications ConsultingTue Jan 28 1992 18:3723
    I'm experiencing what I believe to be a very unique problem, that's why
    I started a new note.
    
    As of this morning we seem to have an electrified tub faucet. We have a
    Symmons Temptrol unit and the lever that controls the tub/shower flow
    is electrified when the water is on and I'm standing in the tub. When
    the water is off, no problem. When the water is on and I'm not standing 
    in the tub, no problem.
    
    I'm not talking a simple case of static electricity build-up here, this
    thing is truly electrified -- serious voltage! I'm not the least bit
    handy and know nothing about electricity short of it being the stuff
    that makes lights go on. I've checked the water pipes in the basement
    and behind the tub wall and there are no electrical wires touching the
    pipes.
    
    Last night the motor in our furnace blew. They oil company came by and
    replaced the motor but that's the extent of recent electrical work --
    with the exception of the installation of a new water heater back on
    November 12th. Any ideas? I'm shocked!
    
    Thanks,
    Mike
291.629FLOWER::HILDEBRANTI'm the NRATue Jan 28 1992 18:586
    Any idea of the voltage present?  Do you have a VOM to measure, say
    from the water to ground?
    
    Maybe a problem in the water heater with a defective element?
    
    Marc H.
291.630CUPMK::PHILBROOKCustomer Publications ConsultingTue Jan 28 1992 19:019
    No, no idea -- I don't have a voltage meter.
    
    If it's the water heater, why is the problem only with the tub and not
    the bathroom and kitchen sinks?
    
    Is this a job for a plumber or an electrician?
    
    Thanks,
    Mike
291.631CSC32::S_MAUFEhottub and chains weatherTue Jan 28 1992 19:058
    
    perhaps you have a leak to ground and the other sinks etc are connected
    via plastic pipe?
    
    I'd put a meter on the electrified spot and start pulling the plugs of
    appliances until the electric goes away.
    
    Simon
291.632CUPMK::PHILBROOKCustomer Publications ConsultingTue Jan 28 1992 19:449
    I called the water company and they suggested it was a grounding
    problem. Next I called an electrician and they suggested a grounding
    problem as well. They also suggested that the motor going on my furnace
    may have been linked to this problem (the furnace is only 6 years old
    so it's unlikely the motor would burn out that soon).
    
    At $45/hour, an electrician is on his way. Oy vey!
    
    Mike
291.633RAMBLR::MORONEYIs the electric chair UL approved?Tue Jan 28 1992 20:386
I'd guess a grounding problem as well, or an open neutral.

Question:  Do your lights dim when a major appliance (fridge, furnace) kicks
in?  Do any lights get _brighter_ when a major appliance kicks in?

-Mike
291.634Just curious.WMOIS::BOUDREAU_CTue Jan 28 1992 22:075
    RE.4

    	At $45/HR did you get one electrician or one electrician and an
    apprentice??

291.635solvedCUPMK::PHILBROOKCustomer Publications ConsultingTue Jan 28 1992 22:1022
    Well, $67.00 later, the mystery is solved.
    
    It was a grounding problem. A rather bizzarre turn of events, however.
    Turns out the furnace, which the former owners of the house had
    installed 7 years ago, was never grounded. The copper pipe supplying
    the oil feed to the furnace runs under the cement basement floor over
    to the oil tank. The oil tank's filler pipe was touching the sewer pipe
    which in turn was feeding back to the bathtub's drain pipe. As a result
    of the furnace being ungrounded, and the whole system coming in contact
    with the water pipes, the copper drain pipe on the tub was charged with 
    120 volts! The electrician said that if there weren't as much PVC on
    the tub's assembly as there is, we could likely have been electrocuted!
    
    So, the problem was patched by installing a grounding clip and copper
    wire between the copper water pipe and the copper waste pipe on the
    tub.
    
    Now we have to prepare to shell out major bucks to have the service
    upgraded to 100 amps and have everything in the house grounded. 
    
    Thanks for all the tips.
    Mike
291.636CUPMK::PHILBROOKCustomer Publications ConsultingTue Jan 28 1992 22:114
>Question:  Do your lights dim when a major appliance (fridge, furnace) kicks
>in?  Do any lights get _brighter_ when a major appliance kicks in?
    
    Yup.
291.637CUPMK::PHILBROOKCustomer Publications ConsultingTue Jan 28 1992 22:139
    >    	At $45/HR did you get one electrician or one electrician and an
    >apprentice??
    
    It was one guy -- it was quoted at $45 because it was technically after
    hours. He ended up charging me $60 for 90 minutes work plus about $7 for 
    parts. 90% of the time he spent here was just investigating and trying
    to track down the problem.
    
    Mike
291.638had the same problemRAMBLR::MORONEYIs the electric chair UL approved?Tue Jan 28 1992 22:2419
re .8:

>>Question:  Do your lights dim when a major appliance (fridge, furnace) kicks
>>in?  Do any lights get _brighter_ when a major appliance kicks in?
>    
>    Yup.

It looks like you have an open neutral.  The neutral wire is supposed to carry
the difference in current between the hot legs back to the pole transformer.
If the neutral line is open (broken) the current flows through whatever
ground it finds through the ground to the ground stake at the pole transformer.

The "good" news is, depending on where the break is, it might be the electric
company's problem and they'll fix it for nothing.

I'm suprised the electricians didn't spot this.  The ground clamp just treats
a symptom, you still have a problem.

-Mike
291.639KAOFS::S_BROOKWed Jan 29 1992 12:5213
    There is definitely still a problem that has now been masked.  An
    open ground on something like the furnace should NOT have made the
    furnace electrically hot.  The ground is there for safety to take
    fault currents to ground instead of through you!  Yes there are
    some induced charges possible on the furnace, but not sufficient to
    give you a shock.
    
    Now there is a fault current running permanently to ground and which
    you are possibly paying for.  A lifted neutral may or may not cause
    the problems you experienced.  It sounds like this electrician did
    half a job.
    
    Stuart
291.6406602::MACNEALruck `n' rollWed Jan 29 1992 13:115
291.641CUPMK::PHILBROOKCustomer Publications ConsultingWed Jan 29 1992 13:2029
    >It looks like you have an open neutral.  The neutral wire is supposed to 
    
    The electrician mentioned that we have only a grounded neutral, but
    nothing else. He also remarked that he was hoping it was a PSNH problem
    so that I wouldn't have to pay anything, but apparently it was not. The
    thing that disturbed me was he had to call to the main office to check
    on something twice -- seems he didn't quite know how to take care of the
    problem himself...
    
    >The "good" news is, depending on where the break is, it might be the 
    >electric company's problem and they'll fix it for nothing.
    
    So should I call PSNH? What do I tell them? I don't speak electricity
    very fluently...
    
    >I'm suprised the electricians didn't spot this.  The ground clamp just 
    >treats a symptom, you still have a problem.
    
    Yes, he said it was just a patch and that we really needed to ground
    the furnace and the rest of the house. He could have grounded the
    furnace for me but he didn't have the right size wire in the truck! So
    he went on his merry way. Am I still dealing with a potential problem
    here that could be risky and dangerous?
    
    This was Stellos Electric, by the way, a rather reputable firm in the
    Nashua area. Although, the guy was pretty young and a little cautious.
    
    Thanks for all the help.
    Mike
291.642CUPMK::PHILBROOKCustomer Publications ConsultingWed Jan 29 1992 13:216
    >    If you're going for the upgrade, spend a little more and go to 200
    >amps.
    
    Isn't this overkill for a 5-room ranch? (No garage, either).
    
    Mike
291.643CUPMK::PHILBROOKCustomer Publications ConsultingWed Jan 29 1992 13:2414
    >    Now there is a fault current running permanently to ground and which
    >you are possibly paying for.  
    
    What do you mean I'm paying for a ground? 
    
    >A lifted neutral may or may not cause the problems you experienced.  
    >It sounds like this electrician did half a job.
    
    So, should I call the main office back and argue? I have no concept of
    what he might have done right and what he might have done wrong, or
    what he should have done instead.
    
    Thanks,
    Mike
291.6446602::MACNEALruck `n' rollWed Jan 29 1992 13:4716
291.645CUPMK::PHILBROOKCustomer Publications ConsultingWed Jan 29 1992 14:0117
    >    Depends on what kind of toys you're running.  If you have a workshop
    >with table saws and the like, a kitchen with a microwave oven and small
    >appliances, an airconditioner or two, TV/stereo/VCR/etc., electric
    >dryer, electric hot water heater, electric stove, the power
    
    With the exception of the workshop power tools, we have all that stuff.
    
    >I opted for the 200 amp service when I upgraded mine from 60 amps.  My
    
    Can you give me a ballpark for the cost of doing this? I have no
    concept of what this might cost. Is it closer to $1000 or $5000?
    
    Maybe we would be better off with 200. Thanks for giving me something
    to think about.
    
    Mike
    
291.646KAOFS::S_BROOKWed Jan 29 1992 14:3219
    re .15
    
    What I meant was that if there is a leakage fault somewhere that 
    electrified the metalwork of your furnace and through other contacts, 
    your waste stack, there was negligible current flowing.  Now that it 
    has been grounded, there is likely a current flowing to ground that
    is consuming power that you'll be paying for.
    
    If the problem really is a floating neutral then this is not the same,
    but on the other hand, I would not normally expect the difference
    between neutral and ground even with a floating neutral to be
    sufficient to give you a shock -- a tingle yes, a shock no.  In this
    case though, you wouldn't be paying for leaked power.
    
    Unfortunately, if you have a house with ungrounded wiring, the only
    way to ensure safety and fix problems like this is to get the house
    rewired.   Mega $ I'm afraid!
    
    Stuart
291.647RAMBLR::MORONEYIs the electric chair UL approved?Wed Jan 29 1992 14:3937
re .13:

>    >The "good" news is, depending on where the break is, it might be the 
>    >electric company's problem and they'll fix it for nothing.
>    
>    So should I call PSNH? What do I tell them? I don't speak electricity
>    very fluently...

Tell them that you believe the neutral feed to your house may be broken,
or you have an open neutral, describe how lights get dim and others get
brighter when the refrigerator kicks in, describe the "shocking" experience
in the tub, tell them you had an electrician over and what he did and you
don't think he actually fixed the problem.  I don't know what PSNH will do
if they determine the problem is not with their wiring, nor do I know exactly
where their responsibility ends (probably "their" side of the meter box).
    
You may want to look at the electrical feed to your house.  You may not be
able to spot anything but then again it might be something obvious, a broken
wire.  Look where the wires attach to your house, look where it attaches to
the pole.  If you have the type of wire where there are 2 black wires wrapped
around an aluminum bare wire, look at the connections to the bare wire.

>    nothing else. He also remarked that he was hoping it was a PSNH problem
>    so that I wouldn't have to pay anything, but apparently it was not.

If he found the problem, he should have either fixed it then, or at least told
you what and where the exact problem is and tried to schedule a fix if he
didn't have the wiring/parts, or called PSNH if he determined it was PSNH's
problem.

While you need a good ground, you really need to get the neutral fixed.

You could always bite the bullet and get the service upgrade now, since when
the feed to your house, the meter, service entrance feed and fusebox are
replaced, the problem will be fixed since it's in there somewhere.

-Mike
291.648KAOFS::S_BROOKWed Jan 29 1992 14:4212
    Having read back through these notes, since the problem was the
    connection through the pipes to the bath waste from the furnace, and
    the furnace was recently worked on AND the problem appears to have
    started with the replacement of the furnace motor ... 
    
    I would say quite categorically that there is something wrong with
    either the furnace motor, or its installation.  A floating neutral
    should not ever put 120 Volts between local neutral and ground, except
    in nearly no load conditions ... ie no electrical appliances working.
    And if it did, you'd likely be blowing electrical equipment like crazy.
    
    Stuart
291.649KEYBDS::HASTINGSWed Jan 29 1992 15:0244
    I'd suggest popping into an electrical supply or good hardware store. 
    You can pick up a socket tester. This is a device with three prongs and
    three lights that you plug into an electrical outlet. Depending on the
    condition of the socket different lights will light up. This is a very
    fast and easy way to check your house electric system.
    
    If my house had bad grounds, as this device will tell you, I would be
    concerned about the saftey of anyone operating any device plugged into
    any of the defective sockets. BTW this device goes for around $5.
    
    Getting Technical - 
    
    (I am NOT an electrician - treat the following accordingly!)
    
    There shoud be three wires in your house electric system. One is the
    hot wire and supplies the electricity, the other two are Neutral and
    Ground. The Neutral is sort of a return path for the electricity and is
    grounded by the power company. The Ground wire is a wire literally to
    the ground at your house. This is often accomplished by driving a
    copper stake into the ground next to your house (usually near the power
    meter) and attaching the house ground to it.
    	There is an important difference between Neutral and Ground.
    Despite the fact that they are both "grounded" they are grounded in
    different places. This can cause a potential difference between them.
    As a safety measure most appliances and tools have their outermost
    cases and parts connected to Ground. This way no matter what happens
    inside the appliance/tool you won't get zapped.
    	if an appliance is not grounded properly, ie: someone breaks off
    that pesky third prong, you might get a potential difference between
    the case of the appliance and a true ground. We once had a refirgerator
    that did this. If you touched the metal trim on the refrigerator whil
    touching the stainless steel sink you would get a bit of a tingle. The
    best I can describe this is that the metal felt "fuzzy" is you stroked
    it lightly. This condition was caused by a "ground loop", of difference
    between the Neutral onthe refrigerator and Ground that natrually
    existed in the copper pipe plumbed sink.
    
    To sum this all up:
    	The hot wire is there to provide you electricity
    	Neutral is there to complete the circuit.
    	Ground is there to protect you.
    
    
                                                     Mark
291.6506602::MACNEALruck `n' rollWed Jan 29 1992 15:074
291.651RAMBLR::MORONEYIs the electric chair UL approved?Wed Jan 29 1992 15:0729
re .20:

>    I would say quite categorically that there is something wrong with
>    either the furnace motor, or its installation.  A floating neutral
>    should not ever put 120 Volts between local neutral and ground, except
>    in nearly no load conditions ... ie no electrical appliances working.
>    And if it did, you'd likely be blowing electrical equipment like crazy.

Not necessarily.  It may be that the old furnace was grounded better than
the new one, replacing it revealed the problem.  By grounded I mean the
ground wire to the box *and* a ground to earth (through the water pipes?).

If you have an open neutral and a bad ground you *will* see a voltage between
neutral and ground.  It won't be 120 volts but it can be noticeable.
My own case is a good example.  I had an open neutral (in the box), and
I noticed some serious blinking when the furnace kicked in.  Investigation
showed a 10-15 volt spike between neutral and a water pipe when the furnace
kicked in.  But the neutral was grounded directly to a water pipe, supposedly.
Connecting a temporary wire to a good ground and running it along the "ground"
wire revealed sparks!.  It turns out that from moisture and carrying current
for nn years caused the ground clamp to corrode where it attached to the pipe,
and if I had almost everything in the house off, except a 120 volt heater, a
piece of corroded wire at the clamp would glow red!!  In this case the current
path for almost 15 amps was from hot through the heater, to neutral back to the
box, through the ground wire to clamp to water pipe.

Needless to say, I took care of this.

-Mike
291.652KEYBDS::HASTINGSWed Jan 29 1992 16:2828
    re: .22
    Yes, older homes do not have the ground wire. That is why I said
    *should* instead of "would". You will be much safer to get rewired. But
    how much safer depends on the appliances that you are using. Many have
    plastic housings, (hair dryers, some electric tools, etc...) and pose a
    minimal risk. You can further reduce your risk by doing common sense
    things like not standing in water when you use and electrical
    appliance.
    
    One other risk of 2-wire houses is to your electronics. If you have
    been wise enough to buy a surge/spike protector for your computer of
    whatever, the protection will be eliminated if the ground is not there.
    
    	Since one furnace motor burned out prematurely I would be concerned
    that it would happen again until the real problem was solved. If your
    Neutral is floating and the motor is completing it's circuit through
    the ground, you may have a resultant low voltage condition on the
    motor, as well as other appliances in the house. This condition may not
    be severe enough to prevent "normal" operation, but it will drastically
    shorten the life of electric motors.
    	Fortunately this is easy to check. Simply place a meter on the
    input electrical lines to the furnace motor and verify the proper
    operating voltage there. If this condition that I have suggested here
    is present, instead of seeing an A/C voltage of 110-120v you might see
    90v or so.
    
    					Mark
    
291.653KEYBDS::HASTINGSWed Jan 29 1992 16:307
    after I entered my last reply I realized that I had left one other
    thing out.
    
    A bad Neutral might also cause and *over* voltage on your electrical
    equipment. (Also not good!)
    
    
291.654CUPMK::PHILBROOKCustomer Publications ConsultingWed Jan 29 1992 18:0438
    I spoke with PSNH who advised I call back Stellos and chat with a
    Supervisor. I did and he assured me that everything was done properly
    and safely and he's offered to have the city inspector come out to look
    things over and put my mind at ease. Apparently the electrician who
    came to my house last night is one of Stellos' top foremen. He said
    the neutral in the house is properly grounded. Of course, my lack of
    education in the arena of electricity leads me to misinterpret things
    and after the feedback I got here and what PSNH told me, I've been
    quite concerned. But I now feel a lot better.
    
    Before he has the inspector come out, however, he's going to talk with
    the guy who did the work and make sure everything's looking good. I
    obviously want to be sure the entire system is safe, but I don't want a
    city inspector condemning my house, either. 
    
    He told me we should upgrade to 150 amps and that will cost somewhere
    around $800.00 excluding any extras like installing additional outlets
    and fixtures and grounding appliances which may not already be
    grounded. So, we're going to start saving our pennies.
    
    The one thing the supervisor felt should be done that they will come
    back out to do is to ground the furnace to the electrical box. Once
    that's done, he feels everything will be perfectly safe. We're
    operating under the assumption, for the time being, that all the major
    appliances are properly grounded because the former owners had the
    kitchen remodeled 6 or 7 years ago and would have had to get all the
    new appliances hooked up properly and inspected. Considering that we
    have an electric water heater, electric dryer, dishwasher,
    refrigerator, furnace, and so on, there's got to be 220 in the house
    and it has to be properly wired. 
    
    Thank you very much to all who helped me here and offline. I appreciate
    all the time you all took to coach me on this. I hope to be back here
    one day soon giving advice to others about upgrading electrical
    service!
    
    Cheers,
    Mike                            
291.655VERGA::WELLCOMESteve Wellcome (Maynard)Wed Jan 29 1992 18:267
    Don't bother with 150 amps - go to 200.  The incremental cost should
    be minimal.  A 150 amp service entrance is an oddball - hardly
    anybody uses it.  A friend of mine installed one in his house, and
    has ever since wondered why he chose it over the more standard 200.  
    (Not that a 150 amp service entrance will be any problem, if you
    choose it, but I can't think of any compelling reason why you'd
    want to.)
291.656MANTHN::EDDPress END or pay! {argh}Wed Jan 29 1992 18:285
    You may want to shop that service upgrade gig around to a few
    electricians. I've recently obtained estimates for a service upgrade
    ranging from $350 to $550...
    
    Edd
291.657Miswired furnace motor?HDECAD::THOMASStop, look and listenWed Jan 29 1992 18:475
    Seems to me the oil company miswired the motor when they replaced it.
    I'd bet they connected one side of the motor to furnace ground instead
    of the neutral return wire.
    
    Everything was fine 'till they changed the motor, right?
291.658KAOFS::S_BROOKWed Jan 29 1992 19:1521
    re .29
    
    Exactly my point.
    
    Also a floating neutral would have given a small voltage ground to
    neutral not the 120V that the electrician implied!
    
    If the electrician reckons the neutral is NOT floating, then there
    is definitely something wrong with your furnace motor!
    
    Even on an ungrounded piece of electrical equipment, you should not
    get more than a stray electromagnetically induced charge.  That would
    dissipate the moment the electricial tried to measure it.  If there
    was a voltage on the furnace / bathtub, there is something wrong
    with the furnace.
    
    Simple
    
    Stuart
    
    
291.659CUPMK::PHILBROOKCustomer Publications ConsultingWed Jan 29 1992 19:1916
    >    Seems to me the oil company miswired the motor when they replaced it.
    >I'd bet they connected one side of the motor to furnace ground instead
    >of the neutral return wire.
    
    That's a possibility. The electrician checked all the furnace wiring,
    however, and aside from the furnace not being grounded, he said
    everything was fine.
    
    >Everything was fine 'till they changed the motor, right?
    
    True. I'm going to ask the electrician if there's a possibility the
    motor was installed improperly and if so I'll go back to the oil
    company and get them to pay the electrician's bill!
    
    Thanks,
    Mike
291.660exKAOFS::S_BROOKWed Jan 29 1992 19:202
    Or maybe it was a faulty motor ...
    
291.661CUPMK::PHILBROOKCustomer Publications ConsultingWed Jan 29 1992 19:2111
    >    You may want to shop that service upgrade gig around to a few
    >electricians. I've recently obtained estimates for a service upgrade
    >ranging from $350 to $550...
    
    Are those reputable, licensed electrician's estimates? The last thing I
    need is to get an amateur in here, save a few bucks, and end up with a
    sub-standard job. After what we've been through this week, I'd be more
    comfortable paying top price for top quality.
    
    Thanks,
    Mike 
291.662MANTHN::EDDPress END or pay! {argh}Wed Jan 29 1992 19:255
    > licensed, reputable...?
    
    Yep.
    
    Edd
291.663Don't assume anything6602::MACNEALruck `n' rollWed Jan 29 1992 19:4614
291.6646602::MACNEALruck `n' rollWed Jan 29 1992 19:486
291.665kindaNICCTR::MILLSWed Jan 29 1992 20:088
    Polarized plugs are not to prevent housing from being hot. Neither side
    should go to the housing (just ground if it's 3 wire) and nothing if
    it's 2 wire. It is however safer for lamps and such because the hot
    will be switched instead of neutral and thereby prevent a jolt when
    changing a bulb (no hot socket).
    
    I think polarized plugs take care of interference (or other) problems in
    electronic equipment also.
291.666Another zapNICCTR::MILLSWed Jan 29 1992 20:3126
    Note, there are to many replies to this note and I don't have
    time to read them all. But.
    
    I had a related problem recently. My wife said she was getting a jolt
    from a switch box. I kinda ignored it thinking it was static. But she
    persisted. So I checked it out. I put a load (coil type) tester on it
    (between ground mount plate of each switch) and got nothing but the
    neon bulb in the tester did flash. I touched each switch and got zapped
    (sorta line a phone wire zap). I put my multi meter on it (essentually
    no load) and got 82volts !!!. So I took the box apart and low a behold
    the "certified" electrian wired both grounds from the two leads coming
    in independently to each switch ground !!!. All grounds should be tied
    together otherwise you can get a potential between grounds. Even
    moisture can case a hot lead to leak to the ground wire. If it's truely
    ground it will sink it. The leak (where ever it was) was so small it
    could supply enough volts to jolt you but no real current (could not
    drive the load tester). Connecting the ALL grounds together in several
    boxes fixed alot of mysterous jolts and strange ground fault trips.
    
    P.S. I think every circuit in a house should have ground fault.
         The ground fault was trying to tell me something before my
         wife got zapped. It would also catch a lot (certainly not all)
    	 of wiring errors that even certified electrians make.
    
    I'm pretty sure this reply will keep this HOT note alive for another day or
    two :-).
291.6676602::MACNEALruck `n' rollWed Jan 29 1992 20:489
291.1026SOLVIT::THOMSRoss 285-3151Thu Jan 30 1992 11:4510


Read N.E.C. Article 424-3. It states that electric space heating equipment 
should be on a circuit rated for 125% of the heater rating.

4000 watts / 240v * 1.25 = 20.8 amps    Hence the 30 amp circuit.


Ross
291.668KAOFS::S_BROOKThu Jan 30 1992 14:5816
    re .36
    
    Not quite ... Polarised plugs were introduced to ensure in general
    becaused most appliances only switch one conductor, that the
    "hot" lead is switched, and in the case of lamps, that moreover,
    the hot wire connects to the button on the bulb base rather than
    the screw thread.  The housings of appliances are never never never
    connected electrically to anything except ground, or in the case of
    electronic equipment, the chassis while not grounded is capacitively
    connected to neutral where you then may develop a very small voltage
    with negligible power.
    
    Housings are never connected directly to either of the two "power"
    conductors ... live or neutral.
    
    Stuart
291.669polarize does not make housing saferNICCTR::MILLSThu Jan 30 1992 17:324
    Right .-1. That's what I meant by a hot socket when changing a bulb.
    Re: .-2 polarizing the plug would NOT prevent the housing from getting
    hot if the insulation wore away. The only thing that would help insure
    that to not happen is a 3 wire with ground going to housing.
291.968Ahhh someone with the book !!!NICCTR::MILLSThu Jan 30 1992 18:1011
    
    Thankyou for looking that up :-). I'm convince to use #10 wire. But...
    
    Do they differentiate the "Wire" from the "Breaker" or is it implied
    that the entire circuit (wire and breaker) be of the rating. This is
    what stumped me. The manuafacturer said 30 amp wire (#10) but 20 amp
    breaker. What I'm worried about is that if the heater malfunctions
    (shorts) and it's on a 30 amp breaker that wiring and controls within
    the heater get fried.
    
    Thanks again...
291.670You still have a problem to fixJVAX::JOHNSONWed Feb 19 1992 15:5632
    I also think the guy concerned about the furnace was right.
    The electrician measured 120 volts at the plumbing - this is
    not just a bad or elevated neutral problem.
    Grounding the drain to the water pipes solves the shock problem
    - everything in the shower is at the same voltage.  However, the
    current you felt in the shower is now flowing directly to ground.
    
    The power going to the furnace should not connect to the frame of
    the furnace.  It should be totally insulated from the furnace frame.
    Since the furnace frame and the associated piping was made live,
    there is something wrong with this insulation.  The proper way to
    diagnose this is to disconnect the furnace circuit (both phase and
    neutral) somewhere between the furnace and the main panel, and to
    test for this leakage path using a megger or hypot tester.  Working
    his way through the loads (burner, igniter, thermostat transformer,
    circulating pump) the electrician should be able to finally find the fault. 
    My guess it is with the circulator or its wiring, which was replaced
    at the same time the problem arose.

    Until the problem is resolved, there will continue to be a risk
    to those working on or near the furnace (since it still is not grounded
    except through contact with the sewer line.  There is also the
    potential for the leakage current to overheat the faulty connection
    resulting in a fire risk (although proper wiring according to the
    code and UL listing of the pump should prevent it from propagating).

    The clearing of the fault and the grounding of the furnace should
    be a separate consideration from that of replacing the main panel.
    It seems you need the electrician again, but he should fix the source
    of the problem, not just apply a bandaid.

    Bob
291.803Can DIY replace fuse box with CB panel ?MSEE::CHENGFri Apr 17 1992 15:1424
    I am planning to upgrade the electrical system in my house. The house
    is a 2-family house. Each unit has a 60A fuse box and most outlets are
    2 wire ( no ground ). This is what I plan to do :
    
    	. change the fuse box to circuit breaker, 100A each
    	. update the service from 60A to 100A each, this may mean bring in
    	  200A service to the house and split them halp for each apartment.
    	. re-wire just a few outlet to accomodate air conditioning and power
    	  hungry appliance, but not re-wire the whole house
    	. finish basement and completely re-wire the basement.
    
    I want to do this in three stages. The first stage is changing the two fuse
    boxs to circuit breaker. My brother-in-law is a licence electrician in
    New York City and he is currently out of work. He's kind enough to
    offer free help to install the new circuit breaker panels. My question
    is, is it legal for a DIY ( actually in this case a out of state
    license electrician ) to install the CB panel ? Do I have to
    acknowledge the city about this ? Do I need to get a permit for doing
    this ?
    
    Once this is done, I then will hire a MASS electrician to bring in new
    ( higher ) 200A service. And the other stuff I plan to do.
    
    
291.804QUARK::LIONELFree advice is worth every centFri Apr 17 1992 16:305
Call your community's electrical inspector and ask.  You will probably
have to get a permit for the work, and will almost certainly have to have it
inspected afterward.

			Steve
291.805its not yours to touch - pull a permitTLE::MCCARTHYHe's the Other Brian this monthFri Apr 17 1992 17:1610
In most cities / towns in MA, for electrical work, they do not care who does
the work as long as it is done to code (or there interpretation of the code
and a permit is pulled).

When he goes to install the new panels, he will have to pull the electrical
meter - since that is the property of the electric company that services your
house, you better pull a permit.  They can get VERY nasty when that little
plastic tag has been tampered with.

Brian J.
291.806GIAMEM::S_JOHNSONFri Apr 17 1992 17:399
re     <<< Note 873.57 by TLE::MCCARTHY "He's the Other Brian this month" >>>

>They can get VERY nasty when that little
>plastic tag has been tampered with.

   Just curious, what are the repurcussions of doing this, have you seen them
   first hand?

SJ
291.807Only Mass lic elect. is allow to doMSEE4::CHENGFri Apr 17 1992 17:4719
    
    Just finished talking to the electrical inspector in Medford ( that's
    where I live ). The following was what he told me :
    
    . ONLY Mass licensed electrician is allowed to do the work ( change to 
      CB panel ). Since my in-law is lisc in NY not in Ma, he can't do the
      work.
    
    . this job requires a permit from the city
    
    . the eletrician will have to notify the electrical company before the
      work is started
    
    . city elect inspector will inspect the work after it is done
    
    They sure don't allow you to save some money by DIY even if you know 
    what you're doing but without the license ( Mass license I should say ).
    
    
291.808MANTHN::EDDReal programs in DCL? .NOT.!Fri Apr 17 1992 18:2610
    re: first hand knowledge of missing meter tag...
    
    I've seen what they do, and it's not pretty.
    
    They come to your house, even while you're NOT THERE, and they...
    
    
      ...put on a new tag!
    
    Edd
291.809Hmm, I did electrical work without a problem...HDLITE::FLEURYSat Apr 18 1992 14:1715
    RE: .59 ( I think)
    
    I hate to correct an inspector, but...  I believe you asked the wrong
    question.  As the homeowner, you are allowed to do any electrical work
    you want ON YOUR OWN HOME.  I suspect that you mentioned that you would
    be assisted by a NY licensed electrician.  That makes a difference. 
    You are no longer doing the work yourself, therefore you need a permit
    and license for the work.
    
    I have done electrical work in both NH and Ma without a problem given
    that I contact the local inspector first with the plans and contact the
    electic company BEFORE I do the work.  I have not had any problems at
    all.
    
    Dan
291.810NOTIME::SACKSGerald Sacks ZKO2-3/N30 DTN:381-2085Mon Apr 20 1992 14:245
re .61:

In MA, the rules vary from town to town.  For instance, in Boston, you can't
do electrical work on your own house (unless you're a licensed electrician,
of course).
291.811KAOFS::S_BROOKMon Apr 20 1992 15:4915
    The assumption was also there that an out of state licensed electrician
    was helping and therefore "being paid" ... If you are paying someone to
    help, then he must therefore be locally licensed.  Never mind North
    American free trade, it appears that free trade doesn't exist between
    states of the U.S. or Canadian provinces.
    
    Also, in many areas, if you as a householder, pull a permit to do
    electrical work or plumbing (which I understand you cannot do in Mass
    anyway), you must do the work yourself.  NO ASSISTANTS.  That way if
    there are problems, you as householder cannot shirk your responsibility
    by saying ... "Joe Blow did that bit ... I'll sue him".  Licensed
    electricians have insurance to cover this; your neighbour or friend
    doesn't.
    
    Stuart
291.812Local code differsELWOOD::DYMONWed Apr 22 1992 19:4111
    
    Ahhhh, better check with you local on how they work things.  I did
    most my inside work without a permit.  The service needed a permit 
    requiring a license number and the Electrican had to have insurance.
    Seeing we pulled the meter,(100A to 200A), the local had to call 
    in a "D" number to the E co., because after the blue tag on the 
    meter came a turn off power move.
    
    Nothing is ever cheep or short and simple.....
    
    JD
291.813and he was only doing LITTLE stuffTLE::MCCARTHYOver 50 copies soldThu Apr 23 1992 11:508
In MA, if you are doing eletrical work for someone, you have to show the owner
proof of insurance OR they have to sign a paper that releases liability.  This
law was passed about two years ago.  When you go to pull the permit you have to
show the town/city the proof of insurance or the letter from the person you are
doing the work for.  For a one-man electrical business, the insurance was
running somewhere around 7-11 hundred dollars a year.

bjm
291.814RGB::SEILERLarry SeilerFri Apr 24 1992 17:2914
Mass law allows homeowners to do their own electrical work, if they pull
a permit.  Some towns have more restrictive rules, but mine doesn't.  I
don't see that it is necessary to tell the inspector whether I had friends
help me do my own electrical work (though I'd tell him if he asked -- and
he's no dummy, I'm sure he knows).  However, I take full responsibility
for all DIY work done on my house.  If I'm not prepared to take that
responsibility, I hire someone to do the job -- I'm paying both for their
work and for their insurance coverage.  I suggest that you not accept
help with a DIY project unless you intend to end the project understanding
just what was done and why -- which is actually the way I like to approach
everything that is done to my house.

	Enjoy,
	Larry
291.817multiple recepticles, 1 fuseMILPND::BENHAMThu May 21 1992 12:3617
    I rent an older apartment that was built evidently when they didn't
    thing electricity was going to take off.  Most rooms have only one
    electrical outlet in it and some don't have any.  The whole upstairs
    and cellar seem to be on one circuit and the whole down stair (living
    room, dining room and kitchen) seem to be on another.  
    
    Here is my problem.  In my bedroom I have a clock radio that I like
    to set for one hour when I'm falling asleep.  In my daughters room
    which is back to back with my room she has a fan.  When she puts
    the fan on I get nothing but static over the radio and you can't
    listen to it.  From what I have been told all the electricity going
    into the apartment from the street is being used, so that I can't
    put a new outlet leading to a new fuse in. (I hope that made sense)
    Anyone have any suggestions or know of any product that could help?
    
    Thanks  
    Carole
291.818WLDBIL::KILGORE...57 channels, and nothin' on...Thu May 21 1992 13:269
    
    1) Better electronics stores will carry an intereference filter that you
       can plug into the wall outlet, then plug your radio into it. Might be
       worth a try...
    
    2) Pull rank!
    
    This wouldn't perchance be an AM station, would it?
    
291.819MILPND::BENHAMThu May 21 1992 15:575
    ref -1
    
    2) it's hard to pull rank when it's hot out.
    
    and yes it is an AM station.
291.820VERGA::WELLCOMESteve Wellcome PKO3-1/D30Thu May 21 1992 16:088
    Quite likely the problem is not the house wiring, the problem may
    be the fan itself.  It may be broadcasting RF interference, in
    which case a well-grounded copper screen cage around the fan would
    help.  Lots of other people no doubt know much more about that stuff
    than I do though.
    
    One quick thing to try: turn the radio (or fan) plug over in the
    outlet and see if that helps any.
291.821KEYBDS::HASTINGSThu May 21 1992 16:463
    another thing to try. Move either the fan or the radio or both to
    opposite sides of their rooms. Put as much distance between them as
    possible. Is this a fairly old fan? A newer one may create less static.
291.822WLDBIL::KILGORE...57 channels, and nothin' on...Thu May 21 1992 21:137
    
    With an AM station, you're probably picking up the noise through the
    antenna, so an interference filter on the plug might not do too much
    good.
    
    AM is much-much-much more prone to noise of this type than FM.
    
291.823RAMBLR::MORONEYIs the electric chair UL approved?Thu May 21 1992 21:5111
AM radios pick up lots of noise through the power line as well.  MAYBE a power
filter on the line cord of the fan, radio or both may help, maybe not
(especially if the AM station is weak)  I think Radio Shack has a clip-on
ferrite thingy that may help.  I'm not sure if they're good enough for
AM suppression.  If you try them, install the one on the fan as close to the
motor as possible.

Try a different fan, one with an induction (brushless) motor, these shouldn't
cause interference.

-Mike
291.815INNA::STJOHNWed Jul 22 1992 12:294
  You can do the work yourself if and only if it is your residence.  Multi-family
(which in your case it is a 2 family, whether or not you live there) you must
have a Mass licensed person.  No options or questions permited.  Key is
  Multi-family.
291.816INNA::STJOHNWed Jul 22 1992 12:294
  You can do the work yourself if and only if it is your residence.  Multi-family
(which in your case it is a 2 family, whether or not you live there) you must
have a Mass licensed person.  No options or questions permited.  Key is
  Multi-family.
291.671Electrical Problem..AIDEV::HOLLANDTue Aug 18 1992 13:4815
	I need some advice...


	I have a track lighting, with 3 spot lights on it, and a 
	dimmer to adjust light, The dimmer is the rotary type, with
	push on/off.

	The problem is that if the light has been on, if you touch the
	dimmer switch plate, its hot..

	any clue what this could be?


	Ken Holland
291.672QUARK::LIONELFree advice is worth every centTue Aug 18 1992 14:154
This is normal, though it may be your lamps draw more current than the dimmer
is rated for.

			Steve
291.673How warm is it?MANTHN::EDDNimis capsicumTue Aug 18 1992 15:454
    Agreed. The energy that would have gone to the lights is disappated
    as heat. 
    
    Edd
291.674QUARK::LIONELFree advice is worth every centTue Aug 18 1992 15:5313
Re: .2

Well, not really.  Most dimmers use a switching triac that alters the duty cycle
of the current going to the lamp; this is more efficient (and also works better)
than putting a variable resistor in series.  There are some losses involved,
though, and this can make a dimmer warm.  Most inexpensive dimmers are rated
for 600W, though I would feel uncomfortable about pushing them that high.  You
can get heavy duty dimmers rated for 1000W or more.

If a dimmer is getting hot to the touch, I would say that it is either
defective or underrated for the use.

			Steve
291.675AIDEV::HOLLANDTue Aug 18 1992 17:394

	Its hot to touch! I was worried about a potential fire
	hazard. I think I'll replace it with a 1000w dimmer
291.676Pull all but one bulb...still hot?RESYNC::D_SMITHTue Aug 18 1992 18:195
    Or reduce bulb wattage, then turn your dimmer up to achieve th same
    intesity.
    
    Dave'
    
291.677TUXEDO::YANKESTue Aug 18 1992 20:4110
    
    	Wait, *3* spot lights are exceeding the capacity of a (presumed to
    be...) 600w dimmer?  I have track lights and went for the largest sized
    bulbs the heads were rated for -- and that was only 75 watts per.  If
    you're really exceeding 200 watts per bulb, I sure hope you are using a
    different kind of track light head than we have... ;-)  I suspect that
    you just have a faulty dimmer switch.
    
    							-craig
                                         
291.678Electical Outlets Needed.DEMON::RHODAN::DIROCCOMon Sep 28 1992 17:1214
    Hi,
    
    Moderator, please move this note if there is a better spot for
    it....
    
    Electric outlets, or lack of them in my old house is presenting
    a problem.  How difficult is it to add more outlets?  Is ripping
    holes in the wall and snaking wires as bad as it sounds??? Argh.
    
    Any experience out there with this type of thing?  I would
    appreciate some thoughts on this.
    
    Thanks,
    Deb
291.679VERGA::WELLCOMESteve Wellcome PKO3-1/D30Mon Sep 28 1992 17:2712
    >>							     Is ripping
    >> holes in the wall and snaking wires as bad as it sounds??? 
    
    Yes.
    
    Every job like this is unique, there is no way to tell ahead of
    time what you are going to run into.  There are some other notes
    in here somewhere, I'm sure, that talk about techniques for
    fishing wires, etc.  Ingenuity and a devious mind help a lot.
    An unfinished attic directly above or an unfinished cellar
    directly below help a lot too.
    
291.680MANTHN::EDDPlease turn out the lights...Mon Sep 28 1992 18:215
    ...and adding outlets may only change the problem.
    
    Make sure your circuits will support the anticipated load.
    
    Edd
291.681At what expense???ROULET::CASSIDYAspiring conservationistTue Sep 29 1992 03:1413
>  Is ripping holes in the wall and snaking wires as bad as it sounds??? Argh.
    
>    Any experience out there with this type of thing?  I would
>    appreciate some thoughts on this.

	    I think in some situations it's far better to call in a 
	professional.  An electrician would cost you some bucks but
	would also know what needs to be done... and then deal with
	all the headaches involved.  Not that I always listen to my
	own good advice.

					Tim

291.682get a stud finderTOOLS::COLLIS::JACKSONAll peoples on earth will be blessed through youTue Sep 29 1992 12:3619
Usually difficult.

I just added two more electrical outlets; one in the
garage and one in the kitchen.  Garage was simple, kitchen
was a royal pain (had to take out a lot of tile, rip out
the plaster board, drill several holes, run a wire all the
way to the fuse box (did not go off an existing run but
added a new run) and then have to repair everything which
included ordering new tile (since some tile broke).  

Personally, I would not choose to hire it out because I'm
sure it would cost a ton of money.  The simple job (in the
garage) I would not hire out because it's easy and rewarding.

One thing I can see, between this and the soap dish in the
bathtub which came out, I'm learning how to tile and grout
expertly.  :-)

Collis
291.683WLDBIL::KILGOREBill -- 227-4319Tue Sep 29 1992 12:434
    
    Look on it as an opportunity to become intimately acquainted with the
    construction details of your home...
    
291.684Frustrating but very rewardingDUSTER::MCDONOUGHTue Sep 29 1992 16:3023
    I did this in my house and some areas were more difficult than others. 
    My house was build around 1860 and is a two story two family.  For the
    first floor, for each new circuit, I ran a wire from the box to the
    first outlet through the basement.  I popped off the baseboard (6 inch)
    and then ran the wires to the next outlet(s) along the baseboard.  I
    most areas I was able to fish the wire behind grooves in the 2x4's. 
    Those I couldnt fish behind, I drilled through.
    
    The second floor, I used a snake to go from the attic to the basement
    and then pulled up lines.  This was not a fun task so I left a string
    in place incase I ever have to do it again.  I then fished down to
    where the first outlet of the circuit was to go.  From there, I went
    around the baseboard to the next outlet.  I some places I hit
    stops in the walls and changed where the first outlet went.
    
    I only had to do it this way in 2 rooms since we were remodeling the
    entire house and all the other rooms we had gutted to the studs, but
    just doing it for those 2 rooms made me appreciate new contruction!
    
    When the frustration factor got too high, usually with the lights on
    the first floor, I just banged holes and patched them with plaster later.
    
    Good luck...Rhonda
291.685Go slowlyKAYAK::GROSSOPrevent &amp; Prepare or Repent &amp; RepairTue Sep 29 1992 17:2946
These replies were great!  Gosh this note brought back memories.  I've
completely rewired two 100 year old homes and these replies captured the
spirit of the effort.  I have a few points I'll add.

If you opt for an electrician, decide what work you really need the electrician
to do.  I was lucky for on both my homes, the circuit box and feed had been
upgraded, so I could just run the wires.  A large part of the job does involve
electrical work.  If you want the electrician to connect the wires to the
box, that's 10 minutes of work.  Mounting the box and snaking the wire through
the house without destroying wallpaper/tiles/plaster/etc can take up to 3 hours
for one outlet.  Consider doing that yourself if you're at all handy.  
Essentially hire the electrician to do only what you can't.  

If you opt to let an electrician do the whole job, then be sure you're hiring
one who respects/loves old homes. I've seen some horrible things done in
an effort to save time.  A half hour of smashing holes to save three hours of
snaking that leaves 8+++ hours of repair/patch/repaint/repapering.

There are plenty of fine books with lots of hints, tricks and pointers as to
how to get wires through a house.  In retrospect, I guess it must have been
fun cause I did it twice.  You do get very intimate with the house and learn
lots of its secrets.  If you're really going to upgrade the wiring and put 
new outlets on all the walls, then you may consider what I did.  I ran a feed
to the attic with a subpanel and then wired the second floor down from there.
That saved lots of wire and hassle dragging each wire back down to the basement
and also makes it trivial if I ever divide the house into a two family.

Looking back I think I wish I'd had a better idea of all that was in store for 
the house.  I painstakingly snaked wires to get outlets exactly where I 
wanted them and then two years later lifted floor boards as part of a heating
system upgrade that would have made rewiring trivial.  Planning ahead is hard
but can save lots of effort.  

One last bit of advice.  Try to live in an old house for a while before jumping
in and "fixing".  I read this advice in an old house book and its wonderful
advice.  Actually, the author suggests a year.  Live in the house for all its
seasons before you do anything.  Those big old drafty windows which you hate
all winter, make the house the nicest on the block in the summer.  That tree
blocking your view might give shade where you'll really appreciate it.  And
remember, people have lived there a 100 years without the improvements you
think the house needs, maybe you can too.  But by living with it first, you'll
be doing only the improvements the house really needs, and might be able to
coordinate them to your financial advantage. 

-Bob

291.686Updated service...DEMON::RHODAN::DIROCCOTue Sep 29 1992 17:4925
    Snifff...snif...that last reply almost brought a tear to my eye! 
    
    My house was build somewhere between 1832 and 1850, the historical
    society is a little fuzzy on the dates, but it is obviously 'ol-d'.
    Fortunaley, the electical has been updated by a previous owner, so
    adding outlets or switches would basically be just a matter of 
    snaking and wiring, and patching some holes.
    
    I think adding a sub panel in the attic is a good idea, something
    my husband and I didn't think of.  I do think the panel in the
    cellar is becoming pretty full.  
    
    Living in the house for a year is a good suggestion, we have been
    there for 7 months.  Next year we are leaning heavily on re-doing
    the heat system for the house, so it may be better to wait on some
    of this stuff, but I think we may be able to add an outlet or two
    in our bedroom, (which has 1 outlet in the entire room), because I
    am going to put up new wallpaper.  The walls are in good shape though,
    so no need to tear them down.  I guess we'll survive if all of you
    did.  
    
    .7 mentioned some good books on doing this, any titles??
    
    Thanks,
    Deb
291.687SITBUL::ALINSKASTue Sep 29 1992 18:007
I always wondered what people ment when they said "snake a wire". In the 
past I always used a 10 gauge aluminum wire which I thought worked fine.
The last wiring job I did, I bought an electrician's snake. This is like the
best tool ever invented. I needed to snake wire in an outside wall stuffed 
with insulation. The aluminum wire did not work at all. Not even close!
With the snake it took a few seconds. The snake went right where I wanted
it. THis is definitelt a tool to have if you plan on doing somw wiring!
291.688The "yellow book"SSDEVO::JACKSONJim JacksonTue Sep 29 1992 18:014
I find the Reader's Digest "yellow book" to be an excellent source of ideas.
There's a section on how to run wires.  I don't recall the exact title,
something like "The Readers Digest Do-It-Yourself Guide".  There's also a
"blue book", a Fix-It-Yourself Guide.
291.689It's lots of fun!!!ESKIMO::CASSIDYAspiring conservationistWed Sep 30 1992 03:588

	    Snaking wires is an art form.  A good electrician can do some
	amazing things with one.  I've gotten my hands dirty and have had 
	some success with snakes, but only due to stubborn persistance.
	If you opt to do your own electrical work, get ready for a trying
	experience.  
						Tim
291.690JUPITR::HILDEBRANTI'm the NRAWed Sep 30 1992 11:017
    One idea....learn about the construction technique used for your
    home. If post and beam...study pictures about the method before
    you start.
    
    If its balloon framing or Western framing, learn about that method too.
    
    Marc H.
291.80RAMBLR::MORONEYIs the electric chair UL approved?Thu Oct 22 1992 17:045
What is the formula for the size box needed for wiring?  Or to put it another
way, what size box would I need for a junction box for 5 14/2+ground Romex
lines?

-Mike
291.81STAR::DZIEDZICFri Oct 23 1992 23:3212
    Number 14 wires require 2.0 cubic inches per wire; number 12
    wires require 2.25 cubic inches per wire.  The last time I
    read the NEC, you counted ALL grounding wires as ONE wire
    (I believe this may have changed recently?); you count each
    "device" (switch/outlet/etc.) mounted inside the box as ONE
    wire.  There are lots of twists regarding wires which run
    "through" a box (as in conduit wiring).
    
    IF the "all grounding wires count as ONE" rule is still valid,
    you'd have (5*2)+1 wires (11), times 2.0 cubic inches per,
    for a total of 22 cubic inches.  Most boxes these days have
    the cubic inch capacity stamped inside.
291.82QUARK::LIONELFree advice is worth every centFri Oct 23 1992 23:513
    The 1990 NEC still counts all grounding conductors as one.
    
    			Steve
291.83BIG box...LUDWIG::CASSIDYAspiring conservationistMon Oct 26 1992 01:255
	    Don't know where you're at, but Mass. code counts all grounds
	individually (=15 #14 wires).  Or so I was recently told by a
	friend who's an electrician.  Can't help with the correct box
	size.
					Tim
291.84VERGA::WELLCOMETrickled down upon long enoughMon Oct 26 1992 10:413
    ...and isn't there something about each cable clamp counting as a wire?
    
    
291.85HelpJUPITR::HILDEBRANTI'm the NRAMon Oct 26 1992 12:065
    In the installation book for a hot air gas furnace, it states that the
    wire bringing power to the furnace should be "type T wire or
    equivalent". What is that? 
    
    Marc H.
291.86Adding Outlets for garage door openersROULET::HUIWed Oct 28 1992 15:4634
I am planning to add a couple of outlets in the ceiling of my garage to operate
2 new garage door openers. I have 2 line coming into the garage (One for
outside lights and One for the garage lights and 2 existing Outlets (See
Below).


                             [ ] <--Outside Outlet
     S= Light Switches        |
        inside the            |
        Familty Room         [ ] <--Inside Outlet
                              |
                              |
        S-------------+       |
        S-----------+ |       |       0 = Ceiling Lights
                    | |       |
                    | |       |
                    | +-------O--------------O
                    |
                    |        { }            { }    
                    |        
                    |
                    |
                    |                   { } = New Outlets location
                    |
                    |                   X = Outdoor Lights
                    X-------------------------------------X


My Question is where should I wire the new outlets from for the garage door
openers? Do I have to bring in a new line (I have a 200 A Panel)? Can I just
tie it into the light fixture? What do I have to watch out for to complete this
job. This just look to ease for me to paid a certified electrician or should I?

Dave
291.87VMSDEV::HAMMONDCharlie Hammond -- ZKO3-04/S23 -- dtn 381-2684Tue Nov 03 1992 18:3635
>I am planning to add a couple of outlets in the ceiling of my garage to operate
>2 new garage door openers. I have 2 line coming into the garage (One for
>outside lights and One for the garage lights and 2 existing Outlets (See
>Below).
...
>My Question is where should I wire the new outlets from for the garage door
>openers? Do I have to bring in a new line (I have a 200 A Panel)? Can I just
>tie it into the light fixture? What do I have to watch out for to complete this
>job. This just look to ease for me to paid a certified electrician or should I?

      How much power do the openers take? Since you *WILL* -- not often,
      perhaps, but sometimes -- run both at once  you  need  to  have  a
      heavy  enough  supply  to  do  this  safely.   If  you  have other
      lights/outlets on the same line, it will have to be  heavy  enough
      to  handle  both openers AND all the other lights/outlets.  If you
      have access to the panel and there is space for another breaker it
      is  almost  certainly a good idea to run a separate line for these
      openers. This also makes it easy to switch them off when you go on
      vacation  nor  anytime you want to be sure the doors don't open or
      close.  (Much easier than unplugging!)

      As  for  "what  to  watch  out  for"  -- you have to watch out for
      everything that  a  certified  electrician  would  look  out  for.
      Without  seeing  your  garage,  it seems like this is a very easy,
      straight forward job.  On the other hand, if you don't know how to
      tell  apart  the ground, neutral and hot wires, perhaps you should
      think twice.
            
      If  you  aren't certain of the code requirements and the "how to",
      spend the $ for a pro.  If the panel is in the garage and the wire
      can  be  run on the surface this is about a 1 hour job -- probably
      less that $50, as a guess.  If the pannel is somewher else, or  if
      wires  have  to be fished through the walls, it might run to twice
      that much.  (Caution! I haven't hired an electrician in some time,
      so these $ could be off.)
291.874Making outlets stick outMR4DEC::BMCWILLIAMSImprovise if you have to ...Wed Nov 04 1992 12:5711
Anyone know of any tricks for making electrical wall receptacles (outlets)
stikck out of their boxes farther so the faceplate fits better?  

I just moved about 8 outlets in my kitchen and seem to have set some of the
boxes in a little too deep.  It's too late the move the boxes (sheetrock is
up), but can I, say, add washers behind the mounting screws to make the outlet
stick out farther?

Or am I the only person ever to set a receptacle in too deep? ;-)

Brian
291.875Use the EarsJUPITR::HILDEBRANTI'm the NRAWed Nov 04 1992 13:076
    The mounting "ears" on the duplex outlet will reference the actual
    surface, not the box. In this way, the outlet will be flush to the
    wall. Have you kept the ears on? They can be removed if you want the
    outlet to be flush to the box instead.
    
    Marc H.
291.876MR4DEC::BMCWILLIAMSImprovise if you have to ...Wed Nov 04 1992 13:184
RE. .1:

Some jerk (me) must have cut the openings in the wallboard too big, so the
"ears" evidently don't touch the wall ... :-(
291.877NOTIME::SACKSGerald Sacks ZKO2-3/N30 DTN:381-2085Wed Nov 04 1992 13:291
Use small washers under the screws.  Or stick bits of cardboard there.
291.878feature on some boxesDAVE::MITTONToken rings happenWed Nov 04 1992 15:0420
    This be moot, depending on your actual boxes, but...
    
    some metal box types allow you to move the box in/out relative to
    their mounting tabs.   Look for a screw head in the obvious place.
    
    Crude ASCII drawing follows:
    
    
    	  |
    	  L-|-
    	+---|---+
    	|   ^	|
    	|	|
    	|	|
    	|	|
    	+---|---+
    	  --|-
    	  |
    
    	FWIW: Dave.
291.879QUARK::LIONELFree advice is worth every centWed Nov 04 1992 15:156
You can buy plastic spacers designed to solve just this problem.  I've seen
them at home supply stores.  And no, you're not the only one to do this!

You can also get box extenders, but they won't work in all cases.

				Steve
291.880some other optionsEVETPU::MCCARTHYbut I kept rolling off the couchThu Nov 05 1992 09:1715
Don't use cardboard - if things, for some reason, get hot in there, cardboard
is flammable.

Somewhere in this conference someone mentioned using the 49 cent cheap plastic
boxes and slicing off the front inch or so.  This gives you the added value of
still having the side terminals covered.

The tabs that bend off on the upper and lower corners of the outlet make good
spacers - and it sounds like in your case they aren't doing what they should -
holding the box against the wall.
                     
Creating a "spring" by coiling 14g wire around an small screwdriver or the tip
of needle-nose pliers.

bjm
291.881I use air...RANGER::PESENTIOnly messages can be draggedThu Nov 05 1992 10:324
All I do is loosen the outlet mounting screws, then tighten the faceplate 
screw to pull the outlet forward.  Works great.  The outlet IS a bit spongy
(gives a little) as you plug stuff in, but I've never had any problems cracking
the faceplate.
291.882it happened to me....WFOV12::KOEHLERPersonal_NameThu Nov 05 1992 11:484
    re last few. Acrtually you should have the outlet tight inside the 
    box. Otherwise the wiring might loosen and cause a short.
    
    Jim
291.883SPEZKO::LEMIEUXThu Nov 05 1992 17:1941
Hi,

   There is a little more to this subject than just securing the outlet
   to keep it from being pushed in or loose fitting. 

   The NEC requires that the box if installed in noncumbustible materials 
   (gypsum board,plaster etc.) have the front edge of the box  be no 
   further back from the finished surface than 1/4". If its installed in  
   cumbustible materials (wood paneling, wainscoting, etc) then the front 
   edge of the box must be installed flush with the finished surface.
   (this applies to boxes in walls or ceilings)

	See Art 370-10 


   The method that I have used to satisfy  this rule and the inspectors 
   is to use the sheetmetal "add-a-depth" rings. These sit on the finished 
   surface but extend back into the existing box and surround the device 
   your trying to secure. Some even come with longer screws so that you 
   don't have to but them seperately. They are designed for the purpose.
   They may even come in plastic these days but I haven't seen them myself.
	
   If your afraid of possible shorts aginst the sheetmetal simply wrap
   some elec. tape around the receptacle so that the termination screws
   are covered. (You'll see this done a lot on jobs that were done with
   metal boxes especially in commercial work.)

   Try any well stocked electrical supply, they should have them.

   Another related NEC article requires that the plaster surrounding the 
   box have no gaps greater than 1/8" at the edge of the box....You should
   see the discussions this one causes when the inspector tells the 
   electrician to fix the plaster around the boxes or he won't pass the 
   job. Of course the plasterers are nowhere to be found at this point in 
   the job :') 

	See art 370-11

	Later

	Paul
291.976HummmmmLANDO::OBRIENGive it a TRITue Dec 01 1992 20:4316
    Hi,
    
    	I just installed a 3-way dimmer switch and noticed that there is a
    slight humming noise at the bulbs(75w reflective type).  I did not
    notice the noise w/ the regular on/off switch.
    
    Is this the filament in the bulb(cheap bulbs?) or possibly a bad/cheap 
    3-way dimmer?  I can get the brand name if that would help.
    
    thank you
    	
    regds,
    	John
    
    p.s.  If this is discussed elsewhere, sorry for the duplication and
          could you point me to the right note?
291.9771111.35 = 3217...LUDWIG::CASSIDYAspiring conservationistWed Dec 02 1992 03:2610
	John,

	    Note 1111 contains a directory for all the notes in this con-
	ference.  Typing DIR 1111.* will allow you to scan the directory
	easily.  Note 3217 has information pertaining to your situation.
 	    Buying a higher quality dimmer could reduce, or even eliminate
	the buzzing noisee.  Or you could turn on a radio to drown it out.
	8^)
					Tim

291.691Surface-Run Wiring?ASD::DICKEYThu Dec 17 1992 15:0719
    
    Does anyone have experience with surface mounted wiring (e.g., conduit
    or raceways)?  I have some Knob & Tube wiring in the ceilings of my
    house which my insurance company wants me to replace.
    
    Running new wiring through the walls/ceilings seems to be impossible
    without putting holes in the walls/ceilings.  I'm disinclined to do
    that since this space is currently occupied by a renter.  Eventually,
    (when the renter moves out) I would like to redo the interior and
    I expect to rewire correctly at that time, so the surface-run wiring
    would be somewhat temporary (though these tenants aren't likely to
    move out in the next couple of years, at least).  For this reason
    I'm looking for a cost-effective alternative.
    
    I hope to run the wiring myself and only bring in the electrician to
    hook up the new wiring to the panel.
    
    Any suggestions or insights would be appreciated,
    Rich
291.692do it right the first time.ELWOOD::DYMONThu Dec 17 1992 15:448
    
    You might want to do it a room at a time.....  It would say
    you from doing it twice...
    
    Heck, its only a renter...wire up a bunch of new boxes and give
    them 100 extention cords!!!  :):):):)
    
    Sparky
291.693VERGA::WELLCOMESteve Wellcome PKO3-1/D30Thu Dec 17 1992 16:498
    If you use Wiremold (brand) surface-mount wiring, you may be amazed
    at how much the stuff costs.  You may decide that doing the job
    that way, only to discard it later when you do it "right," is
    too much a waste of money.
    
    What does your insurance company have against knob-and-tube wiring?
    My understanding is that it's very safe, albeit unsigtly and without
    a separate ground wire.
291.694Conservative Insurance Co.ASD::DICKEYThu Dec 17 1992 19:4525
    
    My insurance company is very conservative (which is generally fine
    by me as it means lower premiums).
    
    My home inspector said that as long as the knob & tube was accesible
    so it could periodically (e.g., annually) inspected, he didn't feel
    there was a problem.  This implies that if hidden, he would feel it
    is a problem.
    
    When the inspection was done, my understanding was that the only
    knob & tube was exposed (in the basement).  I was told that the
    upstairs was re-wired.  I had the electrician in to replace the
    exposed wiring (as required by my insurance company), and while he
    was doing this discovered that most of the upstairs had been
    rewired, but not 4 of the overhead light fixtures (in one area of
    the first floor).  The electrician replace everything he could get
    at easily, but I'm left with the problem of the wiring in the
    ceiling.
    
    Now that I think of it, the two lights on the back porch could
    just be done with BX or Conduit on the surface.  This would only
    leave two overhead lights for which a more expensive solution is
    needed.
    
    Rich
291.952One fixture, 2 circuits. Legal?MSD05::ORRMon Mar 15 1993 18:4637





      The closest I could find to this question is #4076, but I
thought this specific situation different enough to enter separately.
If covered eleswhere, please point me to it.

Question #1.
      I'm installing a new bathroom ceiling fixture which has 4
separate functions (light/heat/exhaust/night light) and says it
demands a separate 20A circuit. The fixture itself has knockouts for 4
separate #14 cables, one for each function, that come from a cluster
of 4 switches to be mounted on the wall (fed by the 20A line). That's
easy enough but I'd really rather tie the "light" section of this
fixture into another existing circuit that controls the vanity lights.
Electrically that's easy. I'll just take the proper cable that enters the
fixture and run it to the vanity circuit. But is that legal? That
would leave one physical light fixture fed by two separate breakers.
If you didn't know that, you could turn one off (the vanity circuit,
for example) and leave the rest of the fixture live, possibly
resulting in a maintenance hazard.

Question #2.
      Along the same lines, even if I wanted to wire that fixture in
the more conventional way, could I still place the control switches
(which are on their own 20A circuit) in the same box cluster as the
switches controlling the rest of the bathroom? Again, we have a
cluster of wall mounted boxes (in this case 3 wide) being fed by two
separate circuits. Kill one and the cluster still has power - another
possible maintenance hazard.


      Are either of these situations legal (here in Mass.)?.....
                                                               
291.953ASD::DICKEYMon Mar 15 1993 18:567
    
    I don't know about the code, but a book I have that describes
    this type of wiring strongly suggests that the handles for
    the two circuit breakers in question be tied together (giving
    the effect of a double breaker).
    
    Rich
291.954Yep, thought of that.....MSD05::ORRMon Mar 15 1993 19:5017





      The problem is that the existing wiring to the rest of the bath
is all #14 and deeply buried within the walls etc. So one of the
breakers would have to be 15A and the other 20A. I'm sure I could
fabricate or steal such a bar from other dual breakers, but then I
thought I'd have to physically tie the two breaker bodies together
just like they do on standard dual units. That's a lot harder and
presents a replacement problem down the road for whoever owns the
place when one of these breakers die. I know that I could rewire the
whole bath with #12 wire, but that's a time consumer that I'd hoped to
avoid.

291.955Looks familiar...LANDO::OBRIENGive it a TRIWed Mar 17 1993 20:3830
    This is bizarre.  Practically the same situation happened to me this
    weekend.  In our bathroom, we previously had a LIGHT in the tub, and a
    FAN/HEATER outside the tub.  We put in a skylight, which got rid of the
    ceiling supporting the FAN/HEATER, so I decided to put a 3-funtion unit
    inside the tub; FAN/LIGHT/NIGHTLIGHT.
    
    The original FAN/HEATER was on one circuit, the LIGHT on another.  I
    said, OK, I'll use the pre-existing switches so that:
    
    LIGHT = LIGHT
    FAN   = FAN
    HEAT  = NIGHTLIGHT
    
    Hooked up all the switchboxes, and all that was left was the
    FAN/LIGHT/NIGHTLIGHT unit.  Well, they designed the LIGHT/NIGHTLIGHT
    (in the unit), such that they had the same COMMON/RETURN(...BUMMER...)
    and the FAN had a different COMMON/RETURN wire.
    
    So, I could NOT hook it up like planned since my initial desire was to
    have the LIGHT and NIGHTLIGHT on different circuits.  From what I
    understand, you can NOT have one return for two different circuits!
    
    So, I guess you have to see how your unit is designed.  You may already
    know all the above stuff....  I don't know if there is any code saying
    that it MUST be on the same circuit(unless the unit happens to only
    have one common wire).
    
    
    regds,
    	John
291.956if you think about it - it DOES make sense20438::MCCARTHYbut I kept rolling off the couchThu Mar 18 1993 09:5619
>>                                                          From what I
>>    understand, you can NOT have one return for two different circuits!

Did that surprise you?  

Doesn't it make sense?  You could end up having 2 appliances drawing 20 amps (-
the 15%) on different 20A (110) circuts "returning" on a single 12g wire - 
this means that 12g wire is taking 40A worth of load (assuming of course that
the two circuts are on the same leg of the 220 service). Can you say overheat?
I knew you could :-)

My mention of "the same leg of the 220 service" is the exception to using the
same common line.  You can run two 110 circuts in a 12-3 or 14-3 RX (gee is
that a trademark???) as long at the two circuts are on different legs of the 
220 service.  Because AC is a "wave" each leg "peaks" at a different time
and this means that the most current that will ever be drawn at a single time 
is at the apex of either leg - and the other leg is at zero at that time.

bjm
291.957TOOK::SWISTJim Swist LKG2-2/T2 DTN 226-7102Thu Mar 18 1993 12:025
    Electricity 101.
    
    Kirchoff's current law:  The current in a loop is the same anywhere in
    the loop.   It does not get "used up" by passing through a load.
    
291.958LANDO::OBRIENGive it a TRIThu Mar 18 1993 12:2116
*>>                                                          From what I
*>>    understand, you can NOT have one return for two different circuits!
*
*Did that surprise you?  
    
    
    No, not at all.  That's why I was bummed out when I saw the config of
    the fan/light/nightlight wiring....
    
>My mention of "the same leg of the 220 service" is the exception to using the
>same common line.  You can run two 110 circuts in a 12-3 or 14-3 RX (gee is
>that a trademark???) as long at the two circuts are on different legs of the 
    
    
    That's interesting, and I think I picture what you're saying but how can
    you tell if they're on different legs w/out a scope?
291.959I guess I won't chance it....MSD05::ORRThu Mar 18 1993 12:4110
    RE: .3

You may be in worse shape than I. At least my fixture has the provisions for 
completely different cables into each of the functions. 

This is probably overkill but I've decided to rewire the entire room with #12 
wire and use a dual ganged 20A breaker. That way there will be a separate 
return for each circuit, and replacement breakers are readily available. I'm 
rapidly running out of room in the breaker panel though, and may have to start 
cruising this file for help on that soon too....
291.960Read them with a meter...some examplesSPEZKO::LEMIEUXThu Mar 18 1993 14:0662
>>That's interesting, and I think I picture what you're saying but how can
>>    you tell if they're on different legs w/out a scope?

	Measure between the two or three wires with a volt meter. 

	|Leg A		|Neutral	| Leg B
	|		|		|	
	|		|		|
	
	|---120 volts---|---120 volts---|

	|-----------240 volts-----------|

	(I've left out the ground for clarities sake but the readings from hot
	to ground are supposed to be the same as hot to neutral. and the 
	voltage values I used may or may not apply to every situation)
	 
	If the hot wires read 120 volts to Neutral or ground but read 0 volts
	to each other they are effectively the same leg.  

	If the hot wires read 240 between each other they are on different 
	phases.

	
	On a circuit like the one above, the neutral will never see more current
	than the maximum unbalanced current between the two phase legs.

	Here are some examples:	
	
	|Leg A		|Neutral	| Leg B
	|		|		|	
	| load		|	load	|
	|--//////-------|-----//////----|
	15 amps		0 amps		15 amps
	
	
	
	|Leg A		|Neutral	| Leg B
	|		|		|	
	| load		|	load	|
	|--//////-------|-----//////----|
	18 amps		6amps		12 amps

	


	But as one of the previous noters mentioned if you have both 
hot legs on the same phase and share the neutral this is what you end up with:

	
	|Leg A		|Neutral	| Leg A
	|		|		|	
	| load		|	load	|
	|--//////-------|-----//////----|
	15 amps		30 amps		15 amps



			
	

	
291.961LANDO::OBRIENGive it a TRIThu Mar 18 1993 14:399
>You may be in worse shape than I. At least my fixture has the provisions for 
>completely different cables into each of the functions. 
    
    
    Not really,... I'm done ;-).  (I just ran another wire for the
    common to the box from the GFI that I installed, and cut out another hole
    for another switch box.)
    
    Good luck.
291.962LANDO::OBRIENGive it a TRIThu Mar 18 1993 14:453
    re. .8
    
    Ah, I see now.... Thanks for your explanation.
291.963two circuits (separate neutral) in same box?RGB::SEILERLarry SeilerTue Mar 23 1993 19:5310
Well, I'm now confused.  I have a dual switch box in my garage that has
two separate circuits entering it.  They have separate grounds (both
connected to the metal box, of course) and separate neutral returns.

Is this legal?  Do I have to gang the breakers so that they switch off
together?  Note that I cannot put them on the same circuit without putting 
more lights and switched outlets on one circuit than I think is allowed.

	Thanks,
	Larry
291.964SPEZKO::LEMIEUXTue Mar 23 1993 21:0310
    
    Perfectly OK. You don't have to gang the breakers together.
    
    	The ganged breaker thing applies to a multi-wire branch circuit
    where you have 2 hots, 1 neutral within a cable or conduit and it feeds
    more than 1 device (receptacle, switch, lampholder etc)or equipment
    on a yoke. (By the way this only applies to dwellings)
    
    	I've paraphrased the above from Art 210-4 of NEC. See Art 100
    for a longer description of Multi-wire Branch circuit.
291.884GreenPlug Ideal Voltage ControllerQUARK::LIONELFree advice is worth every centFri Jul 09 1993 18:4280
A new product has started appearing in stores in this area, a line of devices
called "GreenPlug Ideal Voltage Controllers" from a Colorado company called
Green Technologies Inc.  The device plugs into a three-prong wall outlet and
provides a socket of its own, into which you plug an appliance.  There are
three models, each intended to work with a specific type of motorized appliance:
Air Conditioner/Dehumidifier, Refrigerator/Freezer and Washer/Gas Dryer.
(This last can also be used for other motorized appliances such as
attic fans up to 3/4HP.)

The claim for these products is that they reduce power consumption and 
increase product longevity.  They accomplish the former by modifying the
power waveform so that the peak voltage is lower than the nominal 120V; the
actual voltage is varied depending on the load presented; full voltage is
supplied when load suddenly increases, such as a fan or compressor starting
up, and then it ramps back down.  The controller also provides a "soft start",
where the initial voltage ramps up over a period of about a second, rather
than coming on all at once; this supposedly increases motor life.  The
manufacturer claims that motors don't need the full voltage to keep running,
and that they will operate more efficiently and cooler at a lower voltage.

The devices also include a surge protector MOV (only one, I think - across
the hot and neutral lines).  There is a 10-year warranty against defects;
the price is approximately $35.  This is rather steep; the payback period
is 1-5 years, depending on the type of appliance and the frequency of use.

The instructions for the refrigerator/freezer model indicate that you need
to adjust the freezer temperature control (the one that regulates how much
air gets blown from the freezer to the refrigerator) to the warmest setting,
as the fan will be running "more efficiently".

I saw a demonstration setup with a motor that could be run either from
straight AC power or through the GreenPlug.  There was what claimed to be
a wattmeter display for each mode; with the Greenplug, the motor ran quieter,
though apparently at the same speed, and indicated power consumption was
about 20% lower.

The devices are based on technology developed for NASA; I have read about the
concept over the past several years, and it appears to be sound.  So, being
the technology junkie that I am, I sprang for three GreenPlugs; two for
my refrigerator and chest freezer and one for a dehumidifier.

I first tried out the dehumidifier.  The GreenPlug seemed to work as
advertised, in that it started with less of a "jolt" and ran quieter than
with straight wall power.  Performance of the dehumidifier does not seem to
have suffered after several days of use.  So far, so good.

Next I tried the chest freezer.  I plugged it in, turned it on and...  I
heard a low hum from the freezer and then a click as the thermal overload
protector tripped.  I tried the other GreenPlug and got the same result.
Even though the leaflet claimed that they had tested the GreenPlug with
"every type of home appliance", it seems that it just doesn't like my
freezer (a smallish 13CF model that is about three years old.)

I decided not to try the GreenPlug on the refrigerator for now, given that
I would have to roll it out from the wall, and that is enough of a
"production" that I didn't want to do it if I wasn't sure the device would
work.

I did take the GreenPlug from the dehumidifier and tried it out on each of
two window air-conditioners, which given our recent heat wave, have been
getting quite a workout.  They seem to work fine there - the AC units start
up fine and run quieter, but with no apparent loss of performance.

Whether or not I'm actually saving energy is something I'll probably not know
for a long time, but I understand the principles enough to be reasonably
confident that they do what they claim.  Just how long it will take to repay
the considerable investment is another question.

I have since exchanged the two refrigerator/freezer models for
AC/Dehumidifier models so that I can use them on all three units.  (I don't
know what the operational differences are supposed to be between the models;
perhaps it has to do with reaction times for loads, etc.)

I plan on writing to the manufacturer (there's no phone number listed) to
get more information and to try to find out why my freezer doesn't like the
GreenPlug.

Has anyone else tried these?

					Steve
291.885Where did you find these in the Nashua NH area?SPEZKO::LEMIEUXFri Jul 09 1993 19:165
Hi Steve,

	I've been trying to find a vendor for them here in Nashua. Did you get
them locally?

291.886HQ to the rescueCADSYS::FLEECE::RITCHIEElaine Kokernak RitchieFri Jul 09 1993 19:171
I saw them in Home Quarters (Shrewsbury) a few weeks ago, if that helps
291.887QUARK::LIONELFree advice is worth every centFri Jul 09 1993 19:334
Both Home Depot and Builders Square have them.  HD's price is a buck or so
cheaper.  Builders Square had the demo setup I described.

				Steve
291.888I'm From MissouriJUPITR::HILDEBRANTI'm the NRAFri Jul 09 1993 19:348
    I'd like more info before I would use one. Most induction motors become
    inefficient under reduced voltage. The actual curves depend a lot
    on the rotor resistance...which is not changed by external line
    conditioners.
    
    Got any technical info on them? 
    
    Marc H.
291.889AIRBAG::SWATKOFri Jul 09 1993 19:443
Home Depot in Nashua has the motor/meter demo as well.

-Mike
291.890QUARK::LIONELFree advice is worth every centFri Jul 09 1993 19:5615
Re: .4

I'm hoping to get more technical details from the manufacturer.  The
literature they do provide shows that it doesn't just reduce the voltage;
rather, it modifies the waveform so it's no longer sinusoidal.  Exactly
what the motor does with this, I'm not sure, but I've read enough different
articles on the concept, including NASA's use of similar controllers on
the space shuttle, that I was willing to give it a try.

I know that the typical response of an induction motor to low voltage is
much increased current, strain and stalling.  I can tell you that that
DOESN'T happen here (except for my freezer!), so something else is going
on.

					Steve
291.891Power Factor reduction???STRATA::CASSIDYTue Jul 13 1993 07:1710
	    I would have thought that these ran by correcting the current/
	voltage phase shift.  ELI the ICE man:  Voltage leads current in 
	an inductive circuit (motor coil) and vice versa in a capacitive 
	circuit.  When E (voltage) and I (current) are in phase, you have
	maximum efficiency.
	    Part of the Green thing's function must be to reduce the degree
	by which E leads I.

					Tim
291.892timely articleCPDW::PALUSESBob Paluses @MSOTue Jul 13 1993 15:2670
 I copied the following from last Sunday's Homes section of the Worcester
Telegram & Gazette. Maybe someone will want to follow up and post the
additionaly info that's available ?

 Bob


Copied without permission from the Worcester Sunday Telegram 7-11-93
[From the HOMES section]

 Motor Controllers Increase Efficiency


 Dear James T. Dulley: I can't afford new energy efficient appliances now, but
with ever higher electric rates, I need to save. Do those inexpensive "black
box" electronic devices improve appliance efficiency ? J.H


 You are referring to motor controllers for appliances. Plugging your appliances
into inexpensive controllers can make them operate more efficiently than when 
they were new. A controller can reduce electricity usage up to 15%, reduce 
repair calls, and increase appliance life.

 A controller instantaneously monitors the needs of the motor and gives it only
enough power to match the load. You can use them on any appliances that have
motors (refrigerators, freezers, clothes dryers, washing machines, 
dehumidifiers, air conditioners, sump pumps, tools, etc)

 Controllers are particularly effective on old refrigerators because they 
reduce the heat created by the motor. Excess heat not only wastes electricity,
but it also makes the compressor run longer to stay cold.

 Older appliances often have motors that are more powerful than needed. These
motors run 95% of the time at lower output than they were designed for, so
they operate inefficiently and electricity is wasted.

 A controller is a small radio-size device that you plug into any wall outlet.
You just plug the appliance into the outlet built into the the controller. There
is an indicator light to show you it is working.

 I use a controller on my refrigerator. Other than a lower pitched and 
quieter sound of the motor, it operates the same. I move another controller
from outlet to outlet when I am vacuuming or running the washer.

 Most controllers have built in high voltage spike protection. There are many
thousand-plus voltage spikes in your household wiring. One large spike can
easily burn out controls in your appliances. Repeated smaller voltage spikes
can slowly degrade the insulation and electronic components.

 Soft-start is another built-in feature. This allows the current to ramp up 
slowly when the motor (refrigerator compressor) starts up. Soft-start reduces 
energy usage and wear and tear on the motor and components.

 Controller brownout sensors can save a motor from destruction. When voltage
drops during a brown out or storm, a motor may stop running and just hum. In 
this state, in can quickly burn out, if power to it is quickly limited.

 Proper use habits are also important to keep your old appliance at peak 
efficiency. Keep then clean, especially refrigerators and clothes dryers.

 You can write to me for utility bills update # 619 listing manufacturers of
plug in motor controllers, specs, features, prices and efficiency tips for 
using your refrigerator, freezer, clothes dryer, and washer. Please include 
$1.50 and a self addressed stamped business sized envelope.

Write to:  James T. Dulley,
           Cut Your Utility Bills
           c/o The Telegram & Gazette
           20 Franklin St.
           P.O. Box 15012, Worcester Ma. 01615-0012
291.893JUPITR::HILDEBRANTI'm the NRATue Jul 13 1993 15:306
    RE: .8
    
    Read the article in the paper. I still doesn't have the details on just
    how they work. 
    
    Marc H.
291.894diagram from the demo literatureAIRBAG::SWATKOTue Jul 13 1993 17:5317
If I remember correctly, the demo if the GreenPlug at Home Depot has a
diagram showing a regular sine wave and a clipped sine wave.  The clipped
sine wave, instead of varying from 0 to Max and back gets clipped so the Max
to 0 part is not present.  (Crappy ASCII diagram follows - this is from
memory now...).  Presumably this has something to do with it - I dunno
enough about the subject to know it that's how it works or not.

      +++                     +++     vs.    +++                     +++      
    ++   ++   (regular)     ++   ++   !!   ++  +      (clipped)    ++  +      
   +       +               +       +  !!  +    +                  +    +      
  +         +             +         + !! +     +                 +     +      
-+-----------+-----------+-----------+!!+------++++++------++++++------++++++-
              +         +             !!             +     +                  
               +       +              !!              +    +                  
                ++   ++               !!               ++  +                  
                  +++                 !!                 +++    
-Mike
291.895JUPITR::HILDEBRANTI'm the NRATue Jul 13 1993 18:427
    RE: .10
    
    That type of waveform would have a lot of higher order frequencies.
    Those frequencies would not produce useful work...just heat.
    Doesn't sound correct.
    
    Marc H.
291.896If memory serves correctly...STRATA::CASSIDYWed Jul 14 1993 04:2013
      +++                     +++     vs.    +++                     +++      
    ++   ++   (regular)     ++   ++   !!   ++  +      (clipped)    ++  +      
   +       +               +       +  !!  +    +                  +    +      
  +         +             +         + !! +     +                 +     +      
-+-----------+-----------+-----------+!!+------++++++------++++++------++++++-
              +         +             !!             +     +                  
               +       +              !!              +    +                  
                ++   ++               !!               ++  +                  
                  +++                 !!                 +++    

	   That reminds me of the waveform produced by a dimmer or speed 
	control.
291.897SCRJUPITR::DERRICOJBrian Rost Library_Card holderMon Jul 19 1993 06:1018

      +++                     +++     vs.    +++                     +++      
    ++   ++   (regular)     ++   ++   !!   ++  +      (clipped)    ++  +      
   +       +               +       +  !!  +    +                  +    +      
  +         +             +         + !! +     +                 +     +      
-+-----------+-----------+-----------+!!+------++++++------++++++------++++++-
              +         +             !!             +     +                  
               +       +              !!              +    +                  
                ++   ++               !!               ++  +                  
                  +++                 !!                 +++    



  If the second waveform is correct, it's probably controlled by an SCR. It
probably also has an IC that senses and controlls the current.

/J
291.898Kind'a expensive stillVICKI::DODIERFood for thought makes me hungryTue Jul 20 1993 20:335
    	If there is any kind of market for these things, competition will
    drive the cost down fairly quickly. At $35 a pop, the return on
    investment doesn't quite seem worth it.
    
    	Ray
291.899QUARK::LIONELFree advice is worth every centWed Jul 21 1993 01:329
    If the circuit design is patented well enough, that will make ity
    difficult to come out with competing products.  What will drive
    the price down is not enough people willing to pay $35.
    
    I'm back to just one GreenPlug which I have on the dehumidifier 
    (which runs year-round); I switch it to an AC unit for those few
    days we need one.
    
    				Steve
291.872Wall Unit WiringTROOA::STOIKOSConstantly ConfusedWed Aug 11 1993 17:4119
	This question is not about dimmer switches but is about in-line 
wiring.

I have a wall unit which has three separate lights (one in each section).  
Only one of the lights has a outlet plug on it with an in-line switch.
The lights are set up so that each light has two wires attached to it; one has 
a plug and one has a recepticle so that each light can be connected to the 
others so that all can be controlled by the one in-line switch.


Wall
   |
   =<--------switch------light-----=<-----light-----=<-----light-----= 
   |

What I would like to do is to put each light on a separate switch so that any 
one or any other combination of lights can be turned on independently of each 
other.  I would like to use one power supply so I don't have to take up three 
recepticles in the family room just for these lights.
291.873Or get an outlet strip...STRATA::CASSIDYThu Aug 12 1993 03:493
	rep .6

	Put a switch on each light.
291.900lower price for GreenPlugsWRKSYS::SEILERLarry SeilerFri Aug 27 1993 17:5114
    My local Home Quarters (Shrewsbury Mass) is selling GreenPlugs for a
    bit over $36 each.  HOWEVER, Spags is selling them for $28.85.  So I
    bought one at Spags and took it and the receipt to Home Quarters to
    ask for their 10% discount off competitors' prices.  That brings the
    price per GreenPlug down to $26 plus tax -- *much* nicer.  
    
    Unfortunately, the refrigerator/freezer greenplug makes my freezer
    start clicking after it has run for a few seconds.  However, the
    AC version works fine on my AC and dehumidifier.  I also got the
    washer/gas drier plug (one plug can support both machines), but I
    haven't tried that one out yet, nor have I tried my refrigerator.
    
    		Enjoy,
    		Larry
291.901KAOFS::S_BROOKDENVER A Long WayWed Sep 08 1993 03:3617
    The waveform looks like it is a dimmer waveform, except that the
    clipped part of the wafeform is on the LEADING edge of the sinusiod
    after the zero crossing ... this is on the trailing edge, when the
    motor is pushing due to inertia.
    
    This will in fact provide a form of power factor correction, at least
    for that portion of the sinusoid, because the Inductive circuit will
    not be pushing power back into the supply out of phase (the ELI the
    ICE man thing again ... boy my E.Eng. degree is of use again!)
    
    The soft start so called may be a problem with the fridges etc with
    more efficient compressors, especially if the motor stopped on the
    verge of a compression stroke (like stopping your car in front of
    a sleeping policeman ... hard to get over without a LOT of revs!)
    
    Stuart
    
291.902GreenPlug = zero savings for meAIRBAG::SWATKOWed Sep 22 1993 14:4725
Ya, my diagram in one of the previous replies is wrong.  It should be
clipped on the leading edge, not the trailing edge.  I also saw on the
package that it changes the voltage to 106V.

I just bought a GreenPlug for my fridge ($28 from Home Depot).  The fridge
ran okay but I didn't notice any difference in noise, etc other than the
light in the fridge was dimmer.

So I wanted to see how much electricity I was *really* saving so I did a
little empirical experiment, much like their GreenPlug demo.  With
everything electrical shut off in the house (within reason), when the fridge
was running with the GreenPlug installed, I went out to the electric meter
and timed how long to took to do a complete revolution of the "spinner".
Then I came back in and removed the GreenPlug, waited till the fridge came
on again, and timed the electric meter again.  The results...  no
difference.  The GreenPlug was saving no electricity in my case.  I repeated
the experiment a few times and got the same results.

I have an old fridge so maybe it constantly draws a lot of power thus not
allowing the GreenPlug to do its thing.  I dunno.  All I know is that I'm
taking the GreenPlug back for a refund.  Your results may vary - I would be
interested in hearing the results if others do the same experiment.


-Mike
291.903KAOFS::S_BROOKDENVER A Long WayWed Sep 22 1993 15:2211
If the clipping is on the leading edge, this sure isn't going to do a lot
to correct the power factor.  The apparent voltage reduction is due to
reading the chopped waveform with a meter designed to read the RMS voltage
of a sine wave.  The peak voltage remains the same as 115 * 1.414.

On the other hand, it is strange that the power consumed was not reduced.
Was there any possibility that there was other power consumption goin on 
in the house which would mask the effect of the fridge (like an electric
Hot Water tank) ?

Stuart
291.904VERGA::WELLCOMESteve Wellcome PKO3-1/D30Wed Sep 22 1993 16:137
    If the motor is running at or near its design load (and most 
    refrigerator motors probably are, as the load is fixed so it's
    easy to design for), my understanding is that this gizzie won't
    do much of anything.  If, however, you have a motor somewhere
    that is oversized for its load, then this gizzie does reduce
    power consumption.  Or so I've heard.
    
291.905Too small to notice maybe ???VICKI::DODIERCars suck, then they dieWed Sep 22 1993 16:1611
    	My *guess* is that the "spinner" will not change it's speed noticably
    in the test that was done. I think that you'd at least have to run for
    a day or more to see any real difference, and that wouldn't be in the
    "spinner", it would be in the least significant dials/digits.
    
    	There are other factors to account for that make it pretty tough
    to isolate the savings over a day or more, such as whether you have an
    electric hot water heater, electric range, washed laundry/dishes that
    day, how many times you opened the frig and for how long, etc..
    	
    	Ray
291.906AIRBAG::SWATKOWed Sep 22 1993 20:2134
There were no other major electrical appliances running or lights on at the
time I did the tests (my hot water is gas-fired).  What little there was
running (clocks, nightlights, etc) only amounted to a tiny bit of background
noise.  When the fridge was not running, the "spinner" hardly moved at all.

If you have not seen it, the GreenPlug demo in the store has a motor (*with
no load*) hooked up and a standard-looking electric meter.  There are two
buttons on the demo panel.  Pressing the red one activates the motor without
the GreenPlug and the "spinner" on the electric meter spins away like nuts.
Press the green button which diverts power through the GreenPlug and the
"spinner" visibly runs much slower than before, maybe half to 2/3 of the
speed produced by the red button.

My own test yielded no such "spinner speed" difference.  Even timing the
spinner with a stopwatch did not yield a measurable difference.  I timed 1
revolution of the spinner to be 86 seconds with and without the GreenPlug.
Even assuming that if my measurements were too crude and with GreenPlug it
actually took *87* seconds per revolution instead of 86 sec.  (Grabbing
calculator) that comes out to a savings of about 12 spins of the spinner per
day if my fridge motor ran 24 hours per day (which it does not).  Say the
fridge actually runs only 15 min per hour - does 3 spins per day add up to
$30 in a year? I doubt it.

I would suspect what .20 says that my 'ol fridge motor is running near
capacity and (if the GreenPlug is working at all) it senses the motor needs
all the juice it can get so it is passing all voltage straight through.
Whatever the case, the demo in the store had me expecting a visible
difference.  I hoped to measure the before/after power consumption in terms
of percentage.  My reasoning is that if the percentage is too small to
measure for the one appliance in question, then it cannot possibly put a
dent in my electric bill when you figure it's only one of many electrical
appliances, the others of which do not have GreenPlugs attached to them.

-Mike
291.907AIRBAG::SWATKOWed Sep 22 1993 20:4413
Oh, another thing - I was able to measure via the electric meter "spinner"
method the difference between one normal 60 watt light bulb vs.  *two*
60-watt-equivalent compact fluorescent bulbs (actual rating 18 watts each).

The compact fluorescents combined put out a light equivalent of 2 60watt
normal bulbs while using only 2/3 of the power of a single 60watt bulb.
That matches up with the stats given with the compact fluorescent bulbs.

I figured that if I could verify the savings of a couple of light bulbs, I
certainly should be able to detect a difference with the fridge and the
GreenPlug.

-Mike
291.908Different meter type ???VICKI::DODIERCars suck, then they dieThu Sep 23 1993 12:4911
    	The Green plug demo I saw had a digital display indicating the
    power consumed. I forgot what the difference was, but if you can see
    the difference in light bulbs then perhaps your meter is different than
    mine.
    
    	If I watch mine spin without any major electrical device running
    (i.e. dryer, toaster, stove/oven) my spinner makes a rotation about
    once every 7-10 seconds. At a guess, my average consumption is around
    700 KWH per month in the summer.
    
    	Ray
291.909Are you sure everything was unplugged / turned off?TALLIS::KOCHDTN244-7845 If you don't look good, Digital doesn't look good.Thu Sep 23 1993 21:027
>    	If I watch mine spin without any major electrical device running
>    (i.e. dryer, toaster, stove/oven) my spinner makes a rotation about
>    once every 7-10 seconds. At a guess, my average consumption is around
>    700 KWH per month in the summer.
    
     If it only takes 7 seconds to go around, you have a lot going on!  
Just clocks and timers is more like 70 seconds. 
291.910I'll have to checkVICKI::DODIERCars suck, then they dieFri Sep 24 1993 14:465
    	Now you've got me curious. This is just from memory, so I'll have
    to go check now. I know that my average consumption though is around
    700 KWH which amounts to about $85 per month.
    
    	Ray
291.911GreenPlug save any money?ISLNDS::BRENNAN_PTue Nov 02 1993 13:2548
    I got this out of the Nov 1993 Consumer Reports p694.  Typed quickly
    without any review or permision.
    
    "Can a fancy plug cut energy costs?
    
    Two devices recently cought our eye because they claim to significantly
    reduce the amount of electricity used by refrigerators and outher
    household appliances.
    
    Both the GreePlug Electricity Saver $35, and the Energe Buster
    Motordyne, $80 plus shipping, say they can reduce energy consumption up
    t 25 percent a year, an annual saving that could amount to $50 or more
    with an older refrigerator. 
    
    These plug-in devices are line-voltage controllers that switch power to
    an appliance on and off 120 times per second.  Proponents of the volage
    controllers say that reduces the line voltage, hence the amount of
    electricity, hence your utility bill.  The Green Plug (Green
    Technologies, Boulder, Colo.) is meant only for refrigerators or
    freezers.  The Energy Buster ( Condyne Technology, Longwood, Fla.),
    works on any 120 volt induction motor.  We tried the controllers on
    four refrigerators - one brand new; two middleaged ones, aged 14 and
    15; and a 24 year old antique.
    
    We ran our standard energy-consumption tests with and without the
    controllers, then used the data to figure annual running costs and
    savings.
    
    The controllers didn't even come close to a saving of 25 percent a
    year.  The GreePlug turned in the greater saving of the two- 8.6
    percent on the antique, 3.5 percent on one of the middle aged
    refrigerators. At the national average electricity rate, those savings
    amount to about $20 and $4 a year, respectively.  Savings with the
    Energy Buster amounted to 4.7 percent (about $11 a year) at best.
    
    Both controllers actually increased running costs by a few dollars on
    the brand new refrigerator and on one middle aged model.  That's not
    very suprising, given changes appliance manufactures have made to
    improve the performance of their products over the past two decades.
    
    In our view, add-on gadgets to squeeze a little more efficiency out of
    an older refrigerator don't make much sense.  It's better simply to
    replace the old hardware with new.  A new refrigerator could save $80
    to $150 annually, paying for itself in a few years.  Thats a much more
    impressive saving than either the GreenPlug or the Energy Buster
    provide."
    
    
291.912QUARK::LIONELFree advice is worth every centTue Nov 02 1993 13:595
I was annoyed that CU ignored the other two GreenPlug models, in particular
the AC/dehumidifier model which is the only one which I think has a chance of
being useful.

				Steve
291.913Report didn't cover wear and tearISLNDS::BRENNAN_PTue Nov 02 1993 15:064
    Also CU didn't discuss extending life of appliance.  If I can make my
    20 year old frig use less energy and live longer, I can spend major
    money ($500-700) for new frig later? 
    
291.914NOVA::SWONGERDBS Software Quality EngineeringTue Nov 02 1993 17:576
	First of all, testing the wear and tear would be very difficult.
	More important, given the minimal energy savings of the plug and the
	vast savings of a more efficient refrigerator, making your
	20-year-old refrigerator last longer will be a bad deal anyway.

	Roy
291.915Greenplug - cost analysis is never easyISLNDS::BRENNAN_PWed Nov 03 1993 12:3719
    RE .30
    
    I'm sorry, I think I led you to believe I was advocating the use of the
    GreenPlug.  While testing wear and tear would be very difficult, I
    simply wanted to indicate that if it does occur, it may enter into a
    cost analysis.  For me the analysis is further complicated because that
    we plan to put the house on the market in the next 12-18 months and I
    would be hard pressed to come up with the capital for a new
    refrigerator.  Our current Kitchen appliances are not the color we will 
    choose for the next kitchen.  I don't believe I would save enough money
    to cover the cost of capital?  I bought the toy prior to reading the
    Consumer Reports article and did one of those in your head analysis
    where I got a new toy, saved some electricity, and extended the life of
    my frige while spending too much at the hardware store anyway.  If you
    any ideas how I might perform some more precise cost analysis, I'm
    interested.  I expect I could find someone to buy the plug used for
    $15-20.
    
    paul
291.916Any REAL numbers avialable?GNPIKE::MIKELISwar is a crime against humanityWed Nov 03 1993 14:0914
I'm a little surprised that someone here hasn't done an accurate assessment
of how much current the appliances with and without the devices actually draw
using a watt-meter. It would be pretty easy to figure out the savings from 
there.

I think i'll pick up one of those gizmos soon at Spags and do some 
benchmarking experiments on my own. I'd be interested in seeing the 
benefits of using one on my dehumidifier.

I remember seeing plans for a similar device - oh, it must of been 20
years ago in Popular Electronics. Amazing it took so many years to publically
hit the market considering their alleged energy savings.

/james
291.917Every Little Bit May HelpSALEM::GAGERSwap Read Error-You loose your mindWed Nov 03 1993 14:448
    RE:32 
    
    <I remember seeing plans for a similar device - oh, it must of been 20
    <years ago in Popular Electronics.  Amazing it took so many years to
    <publically hit the market considering their alleged energy savings.
    
     Yea, but twenty years ago the cost of electricity didn't make it
    too feasible.  PSNH rates makes you want to try anything.
291.918Noise sourceCIMBAD::CURTISWed Nov 17 1993 19:3410
I wonder how well the switching transients are filtered.
Every once in a while, I enjoy short wave listening, and
AM radio.  The triac/SCR controlled devices can generate
RF interference that can really get on your nerves.  At
least with light dimmers (or other noise sources such as
flourescents and TV's) you can shut them off.  The frig
has a mind of it's own. It's not a good idea to unplug it
for some peaceful SWL'ing.

Chet 
291.824Local code may dictateREFDV1::CALDERAMon Jan 03 1994 21:226
    I have used both and have had electricians use both, they don't mahe
    shallow plastic boxes.  As for "This Old House" they do a lot of shows
    on house in BOSTON proper and I think that there is a code in Boston
    that only allows metal, I heard that I don't know how true it is.
    
    Paul
291.825Fiberglass also availableSTAR::DZIEDZICTony Dziedzic - DTN 381-2438Tue Jan 04 1994 10:4915
    There is another type of box which hasn't been mentioned - fiberglass.
    These are a LOT sturdier than the flimsy blue or gray plastic boxes
    which you can pick up at home centers.  The fiberglass boxes also
    stand up to drywall cutout router bits a lot better than the plastic
    boxes.  These were the type used when the electrician wired our
    house; I also used them when I finished off the basement.  As far
    as Nashua goes, the inspector approves of them; your mileage in
    other cities may vary.
    
    I purchased the fiberglass boxes at M&M Lighting and Electrical
    in Nashua (on Lowell Street, right off Main Street).  They had
    single, double, triple, and quad gang rectangular, and a few
    different sizes of octagonal (round), plus other variations.
    Offhand, I BELIEVE a single rectangular cost about 25 cents, but
    I'm only going from a 2-year-old memory here.
291.826usually dark brown in colorHNDYMN::MCCARTHYBack to BASICsTue Jan 04 1994 13:0012
The fiberglass boxes mentioned in .4 do take a great deal more abuse than the
standard plastic boxes.  The problem with them is, while mounting, if you hit
the box, it shatters.  They usually come with clamps also.  You can also get
many different styles (for example, if you have a very narrow stud cavity you
can get one with a "flag mount" (I belive that is what it was called) where you
nail it to the front of the stud instead of the side.  Comes in very handy in
tight places.

I guess they would stand up better to the drywall cutter, I'll have to test
that out some day :-)

Brian
291.827JUPITR::HILDEBRANTI'm the NRATue Jan 04 1994 16:264
    Maybe I'm out of date, but, I always use the metal boxes. The price
    increase is small, and they are rugged.
    
    Marc H.
291.828SOLVIT::CHACEMy favorite season is getting nearer!Tue Jan 04 1994 17:466
    
      I'm with you, Mark. For most any job the boxes are a tiny fraction of
    the cost. Not only that, my time is waaaay too valuable to mess around
    with small things that I don't have to.
    
    				Kenny
291.829QUARK::LIONELFree advice is worth every centTue Jan 04 1994 18:077
    I used to use plastic boxes all the time, especially the "old work"
    boxes.  But I stopped when my wife complained that they made 
    wallpapering over them difficult (because they stick out too much).
    Now I use metal boxes with either the bend-over wallboard clamps or
    the kind with the built-in screw-tight clamps.
    
    				Steve
291.830I like some things about bothWEDOIT::DEROSACan't see it from my houseMon Jan 10 1994 15:1710
    I've used both metal and plastic. What I don't like about plastic
    boxes is in new construction, there's no room for error in cutting
    the hole in the sheetrock because they seem to be a "tad" bigger 
    than metal boxes. I also like the durability of the metal ones.
    What I do like about the plastic ones is the little extra room 
    you get for wires.  
    For me, it depends on what's available at that time at the store.
     
    
    /BD   
291.831Works especially well on thermostats mountingsBROKE::TAYLORHoliday shoppers wear my brakes outWed Jan 12 1994 15:5411
    The major advantage I see in the fiberglass boxes is that, if you are
    concerned with air infiltration, the boxes can be caulked shut
    (airtight) very easily, since the whole box is already pretty much
    sealed. You poke the wire holes in the box where you need them, remove
    the cable clamp over your wiring, caulk around the wire, replace the
    clamp, and all that's left to do is to run a thin bead of sealant
    around the hole in the wall for the box. You then have a sealed box,
    and leave the infiltration problems to the windows, which already leak
    more than enough.
    
    Mike
291.832clamps?NETRIX::michaudJeff Michaud, PATHWORKS for Windows NTWed Jan 12 1994 17:575
> ... remove the cable clamp over your wiring ... replace the clamp ....

	cable clamp?  I haven't been using any clamps with the plastic
	boxes, I assumed they were only needed on the metal boxes because
	of the sharp edges on the metal cutout????
291.833MIYATA::LEMIEUXWed Jan 12 1994 18:4416
You need them on the plastic boxes also. The clamp keeps the wires in the box
and any potential cable burn back limited to the box. Also helps seal the hole
the cable entered the box from. 

The Metal VS plastic is a religious war. Both types have thier pro's & cons.
Plastic are faster, cheaper and non conductive. Metal are more industructable,
slower to use and are conductive which makes them not as much fun to pull
live devices out of for trouble shooting etc. Both types have thier place.
I wouldn't use plastic boxes in a commercial building they just don't hold
up to the abuse and I wouldn't use metal boxes in a house simply because they
are just too slow to work with and are more costly. The profit margin on houses
is already too low. Although, both types of boxes are perfectly acceptable in
either location by the NEC.

Paul
 
291.834QUARK::LIONELFree advice is worth every centThu Jan 13 1994 00:145
    The plastic boxes have built-in "clamps" which work fairly well,
    but if you bend them too far, they become useless.  The NEC does
    not require separate clamps on plastic boxes with built-in clamps.
    
    				Steve
291.835fiberglass=seperate and may not be requiredHNDYMN::MCCARTHYBack to BASICsThu Jan 13 1994 09:4212
The fiberglass boxes have seperate clamps that are metal and have to be
tightened via a screw.  I've only bought these at electrical supply houses and
they threw them at me after I told them how many boxes I wanted (ie they were
not attached to the box.

Now according to a master electrican I was working with several years ago, the
seperate clamps did not have to be used if there was a staple on the romex(tm)
within 6 inches of the box.  He agreed that this left too much play and either
used the clamps or put staples closer.  Again this is ONLY with the fiberglass
boxes that do not have "pressure" clamps.

bjm
291.836must be a trick someplace..ELWOOD::DYMONThu Jan 13 1994 10:1810
    
    
    I'll second the stapling 6" from the box.   But all the boxes
    i've used have has a square or rectangular hole wiht a pressure
    clip.  You push the wire in and its a real pain to get it back
    out.  
    Now, tell me how you fit a round clamp in square hole.  I'll
    go back and rewire my house.....
    
    JD 
291.837Heres the clamp codeMIYATA::LEMIEUXThu Jan 13 1994 13:0031
Here's the scoop on what nonmetallic boxes need clamps etc.


1990 NEC (I've only got the 90 book in the office I'll verfy with 93 later )

Art 370-7 Conductors entering boxes, conduit bodies, or fittings  

(c)Nonmetallic boxes

I didn't type in the entire paragraph but it goes on to say a bunch of stuff
about knob and tube, flex and other accepted wiring methods and then states:

	"Where nonmetallic sheathed cable is used, the cable assembly, including
the sheath shall extend into the box no less than 1/4inch through a nonmetallic
cable knockout opening. In all instances all permitted wiring methods SHALL be
secured to the boxes." 

"EXCEPTION: Where nonmetallic sheathed cable is used with boxes no larger than
a nominal size 2-1/4 X 4 mounted in walls and where the cable is fastened within
8 inches measured along the sheath andwhere the sheath extends into the box no
less than 1/4 inch securing the cable to the box shall not be required."

**********

What this all means is you must use clamps in all plastic boxes (fiberglass too) 
for all but the small 1 gang boxes where it's allowed not to use the clamps.
If the clamps are thrown in the case but not attached to the box when you buy
them you still have to install them to comply with NEC. The cable has to be
secured (stapled) within 8 inches of the box to comply. (Note that the ruling
for NM cables secured near a box is 12 inches. The rule for plastic boxes
shortens that distance if you plan on not using the clamp in a 1 gang box.) 
291.838MIYATA::LEMIEUXThu Jan 13 1994 13:0410
 
<       But all the boxes
<    i've used have has a square or rectangular hole wiht a pressure
 <   clip.  You push the wire in and its a real pain to get it back
 <   out.  
    

	From your description the boxes you used had the automatic type of 	
	clamps built in. I'll almost bet the 1 gangs didn't have any clamps 	
	present in them. Most don't today.
291.839CSC32::S_BROOKThere and back to see how far it isThu Jan 13 1994 15:455
Just out of curiosity, is there anything in NEC about caulking the
cable outlets ?  Non metallic boxes have only recently arrived in Canada
and the code really only addresses non-metallic conduit boxes.

Stuart
291.840No requirments to seal used openingsMIYATA::LEMIEUXThu Jan 13 1994 16:1415
<Just out of curiosity, is there anything in NEC about caulking the
<cable outlets ?  Non metallic boxes have only recently arrived in Canada

There is a little blurb about closing unused holes with fittings in a non
metallic box but Nothing requires us to caulk around the cable/hole to further
seal it after installation. Wouldn't surprise me to see become a requirement in
the future though. It sounds sensible enough. 

We are required to make sure the box has no gaps greater than 1/8Inch around the
opening it creates in the drywall. It must also be flush with the front surface
if the wall is combustible and no further than 1/4inch recessed if the wall is
non combustible IE drywall, plaster etc. How does the Canadian code handle the
nonmetallics? 

Paul
291.841CSC32::S_BROOKThere and back to see how far it isThu Jan 13 1994 17:1820
>There is a little blurb about closing unused holes with fittings in a non
>metallic box but Nothing requires us to caulk around the cable/hole to further
>seal it after installation. Wouldn't surprise me to see become a requirement in
>the future though. It sounds sensible enough. 

I was actually expecting to see things ANTI-CAULK to be hones, on the grounds
that the caulk, particularly when fresh and gassing off, could be more
flammable !

>We are required to make sure the box has no gaps greater than 1/8Inch around the
>opening it creates in the drywall. It must also be flush with the front surface
>if the wall is combustible and no further than 1/4inch recessed if the wall is
>non combustible IE drywall, plaster etc. How does the Canadian code handle the
>nonmetallics? 

I hadn't seen a recent enough code to deal with non-metallic boxes, although
the round ones do add some interesting twists to grounding, since they DON'T
have a grounding connection, and still use metallic lids!

Stuart
291.842MIYATA::LEMIEUXThu Jan 13 1994 17:3520
<<I was actually expecting to see things ANTI-CAULK to be hones, on the grounds
<<that the caulk, particularly when fresh and gassing off, could be more
<<flammable !

	Thats a good point. 
	A little off the subject but somewhat related is the method thats used 	
	to seal the end caps on Thermaray radiant ceiling panels. They are 	
	approved by UL and I think CSA as well, to use drywall
	compound as the sealing medium. (By the way Thermaray is produced by
	a company called CANray up in New Brunswick Canada). I've also seen 	
	drywall compound used to firestop small drill holes between floors of 	
	buildings too. I suppose if they ever required the gaps to be filled 	
	they would acceptan already used method....merely speculation on 	
	my part, In reality I hope they never go that route. Just one more 	
	operation to perform during a rough-in.  



Paul
291.843CSC32::S_BROOKThere and back to see how far it isThu Jan 13 1994 18:354
The problem with using drywall compound is that it is not airtight and
shrinks too much on drying.  The only advantage is that it is non-flammable.

stuart
291.844MIYATA::LEMIEUXThu Jan 13 1994 18:443
Apparently UL wasn't concerned with the amount of shrinkage in the case of the
radiant panels. They approved both the method and the product. I've installed a
lot of it without any problems. 
291.845Correct outlet height in cellarGIAMEM::PBROUGHOperating within established parametersMon Jan 17 1994 17:427
    	I am finishing my basement, and I want to wire it as well, however
    I don't know what the height is supposed to be for outlets in the
    basement, is it the same height as the rest of the house.
    
    	Another question, I know that I can get this from the store, but I
    want to wire my workshop with a 20 amp circuit, rather than the
    standard 15 amp.  Is the correct gauge 12 for this purpose?
291.846JUPITR::HILDEBRANTI'm the NRAMon Jan 17 1994 18:2210
    RE: .24
    
    I would suggest that if you do not know the answers to those questions,
    that you buy a book on the current code (i.e. wiring simplified) before
    continuing. Your questions indicate a lack of the basic info.
    
    I'm not saying don't do the work...but, you really need to know more
    than what the correct wire size is to do a good job.
    
    Marc H.
291.847NETRIX::michaudJeff Michaud, PATHWORKS for Windows NTMon Jan 17 1994 21:057
	Yes, 12 guage for 20 amp circuit, 14 guage for a 15 amp
	circuit.  Very important is that the breaker be no higher
	amperage than what the thinist guage wire on the circuit
	can handle (ie. even if 99% of the circuit is wired with
	12 guage wire, if you have something wired into the
	same circuit using 14 guage wire, the breaker must not
	be larger than 15 amps).
291.848You didnt hear it hereELWOOD::DYMONTue Jan 18 1994 10:486
    Seem to recall something in here on the subject.....
    But going out on a limb again...  New wiring has
    to be 12g/20a circuits.  and 15"for the floor rings a bell.
    but as always....CONSULT YOUR LOCAL CODE.
    
    JD
291.849MIYATA::LEMIEUXTue Jan 18 1994 13:2812
<<Seem to recall something in here on the subject.....
<<    But going out on a limb again...  New wiring has
<<    to be 12g/20a circuits.  and 15"for the floor rings a bell.

Nothing in NH and Ma. codes require any of the above in general lighting
circuits in a residence. You may may find that there are some building codes
for handicap access that require the outlets and switches be at a certain
heigth from the floor but nothing in NEC.  

<<    but as always....CONSULT YOUR LOCAL CODE.

Good Idea....    
291.850could be a useful safety featureSMURF::WALTERSTue Jan 18 1994 14:4010
    
    If you plan to put any electronics down there, and codes allow it
    you may want to put the power outlets for these at a higher level.
    
    I didn't do this, but on reflection it would have been a good idea
    as all this stuff is up on shelves away from little fingers, but the
    power cables are still in easy reach of the kids.
    
    Colin
    
291.851WRKSYS::SEILERLarry SeilerFri Mar 25 1994 18:1620
    Late entry -- when I was doing my garage I found a place where the NEC
    said that I didn't need any sort of clamp at all in my plastic boxes
    -- not even the pressure clamp that comes on some of them.  However,
    with no clamp I had to staple them within 3".  That's sometimes a pain,
    but it doesn't provide much play inside the box.  
    
    Since I was worried about air infiltration, I caulked the holes shut.
    Boy, that's a lot easier with a plastic box!  But since I didn't know
    how flammable the caulk might be, I first filled in around the wires
    with nonflammable electrician's putty -- cheap stuff, and designed for
    the purpose of plugging a conduit.
    
    Finally, whether you need to place the outlets high in your finished
    basement probably depends on whether your electrical inspector
    considers it living space or basement space.  Definately, you need
    to have outlets high off the group (I think 4'?) in a basement.
    As usual, consult your local code official.
    
    		Enjoy,
    		Larry
291.852MIYATA::LEMIEUXFri Mar 25 1994 22:3212
<Definately, you need
<    to have outlets high off the group (I think 4'?) in a basement.
<    As usual, consult your local code official.

Not as far as NEC is concerned. There are no height requirments for receptacle
locations in NEC for residential wiring. Your local mileage may vary.

I think is a requirement in commercial garages and aircraft Hangers if the
receptacles are not to be rated explosion proof....but I'm not sure on this
one without looking it up. 

Paul
291.853I hope the pro knows the codeVMSSPT::STOA::CURTISDick &quot;Aristotle&quot; CurtisSun Mar 27 1994 22:117
    .30:
    
    I certainly hope the requirement isn't 4' from the floor, or I'm going
    to have to remove all the wallboard before having the electrician
    rework everything he did.
    
    Dick
291.854FREBRD::POEGELGarry PoegelMon Mar 28 1994 13:1613
>>     <<< Note 5195.32 by VMSSPT::STOA::CURTIS "Dick "Aristotle" Curtis" >>>
>>                       -< I hope the pro knows the code >-

>>    I certainly hope the requirement isn't 4' from the floor, or I'm going
>>    to have to remove all the wallboard before having the electrician
>>    rework everything he did.

I had my basement finishing project inspected a few months ago (Hudson,NH).

All the outlets are 16" off the ground but all are on a GFCI.

Garry    
291.855JUPITR::HILDEBRANTI'm the NRAMon Mar 28 1994 13:576
    In an unfinished basement, the general procedure is to run the power to
    the outlets in metal pipe when the line is below grade.
    
    When the area is finished, does the rules change, even if below grade?
    
    Marc H.
291.856MIYATA::LEMIEUXMon Mar 28 1994 14:3721
>In an unfinished basement, the general procedure is to run the power to
>>   When the area is finished, does the rules change, even if below grade?
    
	The wire run in pipe doesn't have anything to do with grade or finish
	of the basement...It has to do with securing the wire and possibly
	protecting it from damage. You could just nail a running board onto
	the concrete wall and secure the wire and the box to it. It's legal
	but it's kludgy but I've seen it done quite a bit.

	So the answer to your question is: You don't have to run conduit for a 	
	finished basement. 

	The only rule that comes into play that mentions below grade space
	directly, is used when determining how many stories a building has. The
	number of stories is a factor in wiring methods. IE, anything over 3 	
	floors, romex isn't allowable.


	Hope this helps

	Paul
291.857SMAUG::FLOWERSIBM Interconnect Eng.Mon Mar 28 1994 17:137
>	The wire run in pipe doesn't have anything to do with grade or finish
>	of the basement...It has to do with securing the wire and possibly
>	protecting it from damage. 

...yup, like the damage of a power tool cutting or ripping into it :-(

Dan
291.858JUPITR::HILDEBRANTI'm the NRAMon Mar 28 1994 17:315
    RE: .35
    
    Thanks...clears up a minor mystery I've had.
    
    Marc H.
291.859WRKSYS::SEILERLarry SeilerMon Apr 04 1994 19:027
    Hmm... NEC does say 4' from the floor in "wet locations".  Inside a
    residence, including in finished rooms in a basement, this isn't a
    problem.  My inspector considers a garage a wet location, however,
    hence 4' off the ground *and* GFCI.  It's all in the interpretation.
    And as usual, the building inspector is always right.
    
    		Larry Seiler
291.993Green Plug Energy SaversVMSSG::DEANETue May 17 1994 15:5510
Anyone have any comments (pros/cons) about an item (sold locally
at Home Depot) called "Green Plug" which claims to save big bucks
in electricity on your washer/dryer, refridgerator, etc? Do these
things work? They are $29 each. Has anybody (Radio ELectronics, for
example) published a schematic for these things? How do they save $$$?

Bottom line: Are they worth it?


Tom Deane
291.994CR wasn't impressed (for what that's worth)9251::BECKPaul Beck, TSEG (HYDRA::BECK)Tue May 17 1994 16:054
Consumer Reports had a column on them in a recent issue (one of the early
pages "briefly noted" type columns) and indicated that they didn't seem to
be worth it. Sometimes they'd save, sometimes not, but (if memory serves)
not enough to recoup their cost.
291.995LEZAH::WELLCOMESteve Wellcome MRO1-1/KL31 Pole HJ33Tue May 17 1994 16:2821
    There's another note in here someplace about them, I think.
    
    My understanding is that they save energy only when the motor is
    running underloaded.  If the motor is pulling its rated load, then
    the savings are minimal, if any.  
    
    Since the load in nearly all appliances can be quite accurately
    predicted (e.g. the load imposed by a refrigerator compressor
    is fixed), the motors can be chosen such that they run at or 
    near their rated capacity, and the greenplugs won't save much, if
    anything. 
    
    Notice that the demo of the greenplug they sometimes have is done
    with a motor running with no load at all.
    
    If you have a situation where the load on a motor changes dramatically,
    so the motor is often running very underloaded for its size, then a
    greenplug might save you something.
    
    My understanding, anyway...not guaranteed correct.....
    
291.996One point of informationZENDIA::ROLLERLife's a batch, then you SYS$EXITTue May 17 1994 16:4279
    I pulled this off the internet a while back.  It's one datapoint, 
    take it for what it's worth.
    
    	Ken
    
    
Article: 23384
Newsgroups: sci.energy,sci.electronics,misc.consumers.house
Path: nntpd.lkg.dec.com!nntpd2.cxo.dec.com!pa.dec.com!decwrl!concert!gatech!holos0!rsiatl!jgd
From: jgd@dixie.com (John De Armond)
Subject: Green Plug 1, Refrigerator 0
Message-ID: <ty94!sr@dixie.com>
Date: Sat, 12 Mar 94 07:46:34 GMT
Organization: Dixie Communications Public Access.  The Mouth of the South.
Keywords: smoke, flames
Lines: 60
Xref: nntpd.lkg.dec.com sci.energy:23384 sci.electronics:81375 misc.consumers.house:66360
 
Back in November I posted some preliminary results of my testing under
actual conditions, a Green Plug with a 1977 yearmodel Hotpoint Model
CTF18C refrigerator and some squirrel-cage fans.  I promised that I
would post the long term tests on the refrigerator when they were
completed.  The long term energy consumption tests were complete in
February but I decided to wait until now to post so as to let a process
I saw developing run to completion.  The process was the destruction of
the compressor in this refrigerator.  The refrigerator fired back by
destroying the green plug.
 
The process started back in January when I started seeing on the
attached recording ammeter an increased duration of starting current.
This increase appeared to be caused by the "soft start" feature (sic) of
the green plug that is supposed to limit inrush current.  At the time I
got the green plug, I thought it foolhardy, because limiting starting
current drags out the starting process which actually subjects the motor
winding to MORE heat.  Shortly after I noted this increased starting
duration, the refrigerator tripped the GFI on the circuit it was plugged
into.  Prime evidence that the winding insulation in the compressor was
degrading.
    
I decided to let this play itself out so I plugged the refrig and green
plug into a non-GFI outlet.  The refrigerator continued maintaining the
temperature setpoint as indicated by the digital thermocouple meter
attached to the refrig.  I noticed, however, that the compressor
overload would occasionally trip on excess temperature.  And the total
current draw continued to creep up as the leakage current continued to
increase.
 
This afternoon the process ended.  I heard the thermostat on the refrig
turn on and a moment later, the green plug erupted in a pleasing ball of
smoke and flame.  I checked resistance between the refrigerator cord
prongs and ground.  Dead short.  I cracked the service fitting on the
compressor and was greeted by what is probably the worst compressor
burnout I've ever seen.  This was a long term roast and not a quick
failure.
 
After I replace the compressor, I plan to open the shell of the old one
to inspect the damage and make sure it wasn't a tight bearing or
something else mechanical.  But based on the electrical history I have,
I'm pretty positive that the green plug took out this refrigerator.  I
plan on sending this device along with a letter asking them to pay for
the compressor to the factory to see what kind of reaction I get.
 
So the final score is this.  The green plug was "saving" electricity
at the rate of about a dollar a month.  Meanwhile, the replacement
compressor will cost me about $80 plus the better part of a day
to replace it and flush all the contamination out of the freon system.
I think that extra buck a month for power without the Plug was a
bargain.
 
John
 
-- 
John De Armond, WD4OQC, Marietta, GA    jgd@dixie.com 
Performance Engineering Magazine.  Email to me published at my sole discretion
 
Tonight, suppose Washington were nuked to atoms.  Ask yourself, would you 
be better or worse off. This graphically frames the role of the federal
government in destroying the American way of life.
    
291.997WRKSYS::MORONEYTue May 17 1994 16:483
Note 5016 is the previous note.

-Mike
291.135how should I wire this ?ICS::STUARTskis + snow = funMon Oct 24 1994 14:2639
I'm about to wire a 3 season porch I just built.

I'll be taking the power from what existed from the original deck which
is as follows....

A switch on the inside for a spot light and constant power to a two plug
outlet. This is on a GFI circuit. I'll have to figure out what else is
on this circuit, I think it's in with the kitchen power.

I will be adding a second switch to control a light/fan and a couple outlets
if the circuit can take them. I'll be moving the spotlight to the end of the
porch and also adding another spotlight both of which will work of the
original switch.

Whats the best way to wire this up ?? I'd like constant power to the
outlets which will be on the same wall as the outside spotlights.

Should I use 3 wire or can I accomplish this with standard 2 wire. ??

crude diagram ....


switches
 ----  _______________________________ ----
|! ! |                                |fan |
 ----                                  ----
  |________________________ ---- ___________________________ ---- 
  |                        |spot|                           |spot|
  |                         -|--                             -|--
  |                          |                                |
  |                          |                                |
  |                         ----                             ----
  ----                     |plug|                           |plug|
 |plug|                     ----                             ----
  ----

thanks for any help...  Randy     223-2248 if it's easy to explain verbally

291.136QUARK::LIONELFree advice is worth every centMon Oct 24 1994 15:525
You'll need some sort of third conductor to carry the switched hot line to
the lights.  Three-conductor w/ground is the easiest way to do this.  The
other "side" of the lights should go to the neutral conductor.

					Steve
291.695Electrical - Buzzing SoundASABET::HUNTLEYMon Nov 07 1994 16:3810
    I installed a new dining room light and it has a buzzing sound from
    the bulb.  I changed bulbs and it still buzzes.  The light is on a
    dimmer and buzzes when it is turned down low; the sound goes away
    when I turn it up to full bright.  The bulb is a G40 150W.  The old
    light did not buzz.  Could I have connected something wrong, the 
    ground?
    
    Any Ideas?
    
    Thanks
291.696Bad dimmer maybeNOTAPC::RIOPELLEMon Nov 07 1994 17:0116
    
    
    Can the light be used with a dimmer ? I've seen some lights that
    specifically say they can not be used with a dimmer.
    
    Maybe you have a bad dimmer. Was this a new dimmer, or an old one ?
    If it's old maybe time for a new one. If it's a new one maybe replace
    it with a switch, and see what happens. 
    
    Dimmers worry me. We have some friends that had a dimmer fail in their
    house ( house was only 6 months old ) came home to meet a fire truck,
    and no house one night after a nice dinner. Faulty dimmer.
    
    We have one in our dining room. I constantly check it.
    
    
291.697QUARK::LIONELFree advice is worth every centMon Nov 07 1994 18:324
    It's common for dimmed bulbs to buzz - a lot may depend on the
    design of the bulb filament.
    
    				Steve
291.698bulb-dependent, not uncommon..TEKVAX::KOPECPackin' ta move..Wed Nov 09 1994 14:003
    Try a different bulb, from a different manufacturer.
    
    ...tom
291.699Cheap voltage regulators don't always workCSLALL::NASEAM::READIOA Smith &amp; Wesson beats four aces, Tow trucks beat Chapman LocksWed Nov 09 1994 15:159
My lights stopped buzzing when I replaced the dimmer switches with 
better-designed units.

A bit more circuitry seems to be the answer.  The cheap ones only had a 
couple of components (transistor, resistor, pot)



291.700My lights are S9+20..TEKVAX::KOPECPackin' ta move..Wed Nov 09 1994 15:226
    I've found some correlation between dimmers that seem to be susceptable
    to bulb-buzzing and the amount of RFI that the dimmer generates. With
    the winter 160-meter Ham season coming 'round, I'm going to have to go
    hunt down all the noisy dimmers in the house 8-(
    
    ...tom
291.701cheap dimmer = major hum problem!WRKSYS::RICHARDSONWed Nov 09 1994 15:2510
    Yup - there was a dimmer in the sanctuary at our synagogue that
    generated so much RF that it was getting into the PA system!  Since
    there wasn't any real good reason for there to be a dimmer there
    anyhow, we replaced it with a real silent mercury switch (I didn't
    think they still made them! - had a lot of trouble finding one) that
    doesn't go THUD if someone has to surreptitiously turn on the switch if
    it has been forgotten.  Probably a better dimmer would have worked as
    well.  Sure sounded awful coming out of the PA speakers...
    
    /Charlotte
291.702More humming lightsCUPMK::WIEGLERThu Nov 10 1994 19:348
    Here's a *somewhat* related problem.  My kitchen ceiling fixture has 4
    florescent bulbs.  It is NOT on a dimmer switch.  But the fixture does
    hum sometimes. What can I do about it, or is that a characteristic of
    florescent lights?  Also, sometimes 2 of the bulbs light first, and
    then, after a few moments, the second two bulbs decide to light also.
    I replaced all 4 bulbs at the same time, but this problem still exists.
    
    	Willy
291.703QUARK::LIONELFree advice is worth every centThu Nov 10 1994 20:196
Humming flourescent lights can sometimes be caused by a dying bulb or by
a dying or poor-quality ballast.  If it's the ballast, you may not be able
to do much - you can buy new ballasts, but the old one is often welded in 
place.

				Steve
291.704Never ran into a ballast that wasnt replaceableCSLALL::NASEAM::READIOA Smith &amp; Wesson beats four aces, Tow trucks beat Chapman LocksFri Nov 11 1994 11:417
I've never seen a ballast that was welded in.  Every one I've replaced was 
either screwed in at both ends or was held in place by a screw on one end 
and a tab on the other.

BTW, if you go out looking at ballasts, make sure you get the right one. 
The info is printed right on the ballast.  i.e. number of bulbs it'll 
handle, the rating of the bulbs and the line voltage.
291.705is there a starter?WRKSYS::RICHARDSONFri Nov 11 1994 15:486
    It could be the starter, too, if the fixture is old enough to have a
    starter - easy to replace.  I never saw a welded-in ballast - I've
    replaced several of them as they got old enough that we couldn't
    tolerate the loud hum, and they all just bolted on.
    
    /Charlotte
291.706ASABET::HUNTLEYMon Nov 14 1994 13:5114
    Dimmer Problem?
    
    Well I changed the dimmer with one of better quality - light still
    buzzes.  I'll probably go back to a regular switch.  The guy at home
    depot thought the light (G40 bulb @ 100 or 150W) is just too large
    a bulb to work with a dimmer  - the filament vibrates at the low light.
    sounds logical - since the buzzing goes away when I turn it up all 
    the way.  I may try a different bulb - the third one! The old light
    didn't buzz because they were very small bulbs.. unlike the large one
    in the new light.
    
    Thanks
    
    Thanks
291.707It *is* possible; keep trying combinationsSSDEVO::JACKSONJim JacksonMon Nov 14 1994 15:042
I had a fixture that used a 150W G40 bulb on a dimmer, and had no problem
with buzzing, so it *is* possible to do it.
291.708ASABET::HUNTLEYMon Nov 14 1994 15:541
    what kind of bulb in .12 - i'll buy one!
291.709How about dimmer brand names?HANNAH::BAYJim BayMon Nov 14 1994 16:149
    Gee, I must buy cheap switches.  I didn't know there was such thing as
    a dimmer (or dimmer/light combo) that DIDN'T buzz.  I figured you had
    to give up peace and quiet for flexible lighting.
    
    Even my X-10 stuff has a high-pitched whine.  I can't hear it, but it
    makes my wife mental.
    
    Jim
    
291.710TARKIN::HARTWELLDave HartwellWed Nov 16 1994 14:336
    What brand/model dimmer works best here
    
    
    
    				/Dave
    
291.919What type of boxes for exterior outlets?ANDREW::OSTROMETP Engineering Mgr.Fri Dec 02 1994 19:0516
    I'm building a house (90% myself), and doing all the electrical work.
    In all the work I've done before, which has been old work, all the
    exterior wiring I've done has been with EMT and watertight boxes,
    etc.  Now, with new construction, my options are greater.  I'd like
    to have a few flush-mounted recepticles and some exterior lights and
    such...
    
    So, my question is -- do I need to use the solid "exterior" type
    boxes, should I use "masonry" type boxes, or can I just use standard
    recepticle, round, square, whatever,  boxes mounted from the outside,
    with normal exterior covers?  I can ask the inspector next week (he's
    only in Tuesday and Thursday mornings), but would like to do most of
    the outside work this weekend.

                                Andy Ostrom
291.920leave wire in wall, so you don't end up between shinglesHNDYMN::MCCARTHYHe's here, but I'm still not readySat Dec 03 1994 22:316
In Quincy, MA, I have installed "old work" boxes from the outside after the
siding was put on and then put watertight covers over them.  So the outlet is
inside the wall.  This was done under a master electrian and was approved by
the inspector - of course, the outlets were GFCI protected....

bjm
291.921Tnanks.ANDREW::OSTROMETP Engineering Mgr.Mon Dec 05 1994 01:2011
>In Quincy, MA, I have installed "old work" boxes from the outside after the
>siding was put on and then put watertight covers over them.  So the outlet is
>inside the wall.  This was done under a master electrian and was approved by
>the inspector - of course, the outlets were GFCI protected....
>
>bjm

        Thanks, this is what I decided to do.

                                Andy Ostrom
291.922QUARK::LIONELFree advice is worth every centMon Dec 05 1994 12:227
If you intend to leave something always plugged into the outlet, don't
use the kind of cover with the spring-loaded flaps.  They're not intended
for "permanent" use.  Instead get a cover which is sort of a clear plastic
dome with slots in the bottom for cords to go through.  These go for about
$15-$20.

					Steve
291.923Thanks.ANDREW::OSTROMETP Engineering Mgr.Mon Dec 05 1994 18:577
    Yup, know about that, thanks...  This weekend was too nice, so I
    worked on siding/roofing, but the outlets go in later this week.
    I think I'm just going to use standard new-work depp boxes, of which
    I have loads.

                                Andy Ostrom
291.1006haunted condo (power problems)KLUSTR::SOUTHY::GardnerSouthie MudsharkThu Dec 08 1994 23:5344
	got a kinda strange problem that started very recently...

	it began with the line conditioner I use for all my
	computer related equipment....I noticed that late at night
	a relay in the box would start clicking away indicating to
	me that over/under voltage conditions must be occuring....

	next it was the X-10 stuff...lights would turn on and off
	by themselves...switches wouldn't work one day and would the
	next...even applicance modules starting behaving eratically....

	then, my DECrouter 250 has started randomly rebooting about
	once every four days...its on the line conditioner, but maybe
	its a little more sensitive then the rest of the stuff ;-)

	now all hell has broken lose...when I came home, the router
	was down *again*....while writing this message the line conditioner
	was at first clicking away and now has gone quiet again....
	the lights in the living room wouldn't turn on at all an hour
	ago and now they work, but only from the mobile control, not
	from the wall switch.....and the tv has turned itself off then
	on five times (its plugged straight into the wall eg no X-10)...
	this last bit worries me abit because it can't be too good
	for the tv...........

	now: I live in a 700 sq.ft. condo in South Boston...2 years
	ago (next month) I did a complete remodeling of the place
	including stripping the old place down to the bare walls...
	at the time, myself and an electrician went over all the
	wiring including installing dedicated 30 amp circuits for
	the computer and A/V stuff and doing all the X-10 stuff....
	(I also took the opportunity to wire the place for ThinWire,
	cable, and audio)....since that time, all had worked perfectly
	until this all started happening....and, no, nothing inside
	these four walls has changed recently....

	so, what to do? I would have called in an electrician already
	but the problems seem of the intermitent variety; I'm afraid
	it won't happen while he/she is here.....and if the problem is the
	power coming into my place, what would I do about it?????

	any advice would be greatly appreciated! help!!!

	_kelley
291.1007one thought to ponder...BIGQ::GARDNERjustme....jacquiFri Dec 09 1994 12:177

    It just started getting really cold lately and you do have and
    old place.  Are you harboring mice or squirrels?  They might be
    have a feast on your wires!  

    justme....jacqui
291.1008LEFTY::CWILLIAMSCD or not CD, that's the questionFri Dec 09 1994 12:329
    Or some of your connections may be getting looser in the main box or
    elsewhere.
    
    Call the electrician ASAP.... If the problem is in your building, you
    have a potential fire hazard...  If something is loose, the electricial
    ought to be able to find it....
    
    CHris
    
291.1009LEZAH::WELLCOMESteve Wellcome MRO1-1/KL31 Pole HJ33Fri Dec 09 1994 14:483
    Are the outlets wired with the push-in connections on the back,
    or with the screw terminals?  The push-in connections are not
    reliable.
291.1010CALL 1 800 GHOST BUSTERSRELYON::MONACOFri Dec 09 1994 15:3421
    Sounds like your problem is across several seperate circuits. So you
    need to go back to where they meet "main box" and work back to the power
    coming from the street. 
    
    Some questions to think about;
    Has there been any work in the area (new building, renovations, buisness..
    .etc) 
    Did the problem first occur after a storm? 
    With cold weather are people cranking up their electic heat?
    Are your neighbors having similar problems?? If so call in the power
    company or building owner. 
    If it's only you than call an electrician in to check your system out. 
    You could also attach line montoring equipment to track the voltage 
    changes over an extended time to see if there is a pattern. (like 
    when the office buiding across the street turns heat on in the morning or
    there is heavy elevator usage.
    
    good luck
    
    Don           
     
291.1011"Exorcise 'em!!"POLAR::PARKERGreat White North!Fri Dec 09 1994 19:067
re: .1 - .4 all make good suggestions.  I am leaning more towards a
priest.  Thats right,  a priest.  Perhaps an exorcism is just the ticket
to get rid of your odd power fluctations.  

Warily yours,


291.1012NETCAD::DESMONDFri Dec 09 1994 20:216
    Re: .5  Exorcism
    
    If you decide to go this route, make sure that you pay promptly for the
    exorcism.  Otherwise, your condo could be...
    
    repossessed.  :-)
291.1013Radio maybe??WMOIS::HARVEYFri Dec 09 1994 20:346

    You might want to make sure someone isn't running an amateur or CB
    radio nearby.
    
    DH
291.1014poltergeist? I may never know...KLUSTR::SOUTHY::GardnerSouthie MudsharkFri Dec 16 1994 10:5625
	I want to thank all those who responded to my basenote...I have
	waited to reply to see what would happen....

	basically, it all stopped just as fast as it started...all is back
	to normal now with the sole exception of one pesky X-10 wall
	switch which has always given me problems, but thats another
	story..........

	my favorite theory is that it was in the street...here in Southie,
	we have some of the oldest underground wiring in the country...
	being located only four blocks from the power plant doesn't appear
	to help this; we have had numerous powerouts etc over the years...

	my second theory is that it was all caused by an over zealous
	Christmas light display which has since self-destructed ;-)

	.4 mentions a line monitor...this sounds like something that
	would come in handy in the event of a reoccurance (repossesion? ;-)...
	where does one find such a device and what do they generally
	cost?

	(btw, .6 was great! laughed quite loudly...)

	thanx again
	_kelley
291.1015southie is KNOWN for that !!!NECSC::DWORSACKFri Dec 16 1994 17:3615
    last winter my sister in-law had a problem, with her heat 
    (only on the first floor) which is where she was. took a few
    days to get anyone to come out to look at her furnace. 
    this was during one of our cold snaps !!
    
    turns out it not only affected the furnace, but other outlets/lights
    were not working in the building.
    
    come to find out one of the hot lines was bad, the other 
    was good. 
    
    power company had to dig up the whole street in front of her
    house to fix it, 1 1/2 day job. i dont understand, phone/cable
    on ugly phone poles in the rear of all the homes, and 
    electric (like you said, OLD at that), underground.
291.998Knob&tube - can we work around it ?PCBUOA::ERSKINEMon Feb 20 1995 17:2218
    
    
    In the process of remodeling our kitchen and bath of our "new"
    old house, circa 1920, we have discovered that the breaker box which
    has new wires going in, actually has the old knob&tube still in 
    operation.  For example, the bathroom light fixture has k&t and
    BX cable, or there could be K&t and new wiring.  I was surprised to
    see the two mixed together.  Is this okay ?  Since the k&t is
    throughout the house, ripping it out (3 stories) would be a nightmare.
    
    If we want to move a light switch with k&t can we create a junction box 
    and move it to a lower/another location ?  Do we just add the new wire
    for the new light switch ?  I had read in note 2309 that there should
    not be more than a 15amp breaker, what if the circuit contains three
    kinds of wiring, (k&t/BX cable and new wiring) ?
    
    rke
    
291.999Only change what you need toHNDYMN::MCCARTHYDisabled Service ButtonTue Feb 21 1995 09:0839
                    -< Knob&tube - can we work around it ? >-
Yes.

>>    BX cable, or there could be K&t and new wiring.  I was surprised to
>>    see the two mixed together.  Is this okay ?  Since the k&t is

It was done all the time.  There was a special connector for the end of the BX
(acutally a trade name I believe) that avoided the need for a junction box and
was used quite often.

>>    If we want to move a light switch with k&t can we create a junction box 
>>    and move it to a lower/another location ?  Do we just add the new wire
>>    for the new light switch ?  

Yes.  There are special connectors that electrical supply houses will have to
bring the K&T wire into a metal junction box - actually I've seen this done two
ways, one with simply putting a rubber grommet in the knock out of the box and
running the wire through that (one wire per knock out) or a special connector
to bring the K&T wires in.

Add the junction box (in an accessable location) and run your new cable from 
the junction to the new switch.

>>    I had read in note 2309 that there should
>>    not be more than a 15amp breaker, what if the circuit contains three
>>    kinds of wiring, (k&t/BX cable and new wiring) ?

Its three kinds of wiring but you ALWAYS pick the amperage of the smallest wire
on the circut.  

I assume by "new wiring" you mean RX?  BX is still used all over the place
(commercial buildings mostly).

One think you will have to check with someone on is what to do with the ground. 
I think what we did in your "moving a switch" situation was to clip the ground
wire so it would not give anyone an idea that it was actually connected to
ground.

bjm
291.436Step-down (120V to 12V) transformer wiringMSE1::SULLIVANWed Apr 26 1995 15:2150
	 I have  a  wiring  question which can be boiled down to, "Can I
     place  a  step-down  (120V  to  12V) transformer in the middle of a
     daisy chained circuit?"

	 I have  a  dining room ceiling light which was controlled by two
     switches  (a  three-way).   We are having a built-in cabinet put in
     which eliminates  one  of  the  switches.   Instead, it will have
     low-voltage  lighting inside.  I want to use the old switch box and
     wiring for power to the low-voltage lights.  And ideally, have the
     one remaining light switch turn on both the ceiling light and the
     low voltage cabinet lights.

	 The power  source  is  into  the light box, then to the switch.
     My question is, can I get this to work with the existing wiring/boxes?
     At this point, I don't think so.

	How can I wire the following if it can be made to work?

			  old switch box	  switch
			+---------------+	+-------+
    bbbbbbbbbbbbbbbbbbbbbbbbbbbbbbbbbbbbbbbbbbbbbbb	| b, w connected
power			|		|	|	|   to screws on
    w2w2+    +w2w2w2w2w2w2w2	    wwwwwwwwwwwwwww	|   simple 2-way
         \  /		|		|	|	|   switch
	  light		|	    rrrrrrrrrrrrrrr	| r not used
			+---w1--b1-------+	+-------+
			    w1	b1
			    w1	b1
			    w1	b1
			    w1	b1
			 +--------------+
			 |transformer	|-->w+b to low voltage light
			 +--------------+

    With a "daisy chain" (w connected to b1, w1 connected to w2), the
    low voltage light works but not the ceiling light.

    If I connect w+r to the common screw on the switch, connect w to b1,
    r to w2, and w1 to ground, it works.  However, I obviously would not
    do this unless I was looking to seriously shorten the life of the
    house or one of the occupants.
  
    I can not pull a new wire between the light and the old switch box.
    I can get one between the old switch and the remaining switch.

    I can also probably get power directly to the switch (this is my plan B)

						    Thanks,
							Mark
291.437you have a need for feed..TEKVAX::KOPECwe're gonna need another Timmy!Fri Apr 28 1995 18:3341
    The transformer wires just like a light, and lights wire in parallel.
    
    you're SOL. You don't have the wires you need. You need an unbroken
    neutral to the transformer, in the current situation.
    
    
    If you can get power to the switch box where the transformer is:
    
    1. Connect all whites together at the transformer box.
    2. connect the black feed to the black leading to the switch.
    3. connect the black lamp lead and the black transformer lead to
       the red lead from the switch.
    4. Disconnect and cap the feed at the lamp. 
    5. connect the lamp to the black and white from the transformer
       box in the usual way.
    6. Disconnect and cap the white wire at the switch. (*)
    7. Connect the one of (black|red) to the "common" switch terminal,
       connect the other to either of the non-common switch terminals.
    
    so you end up with:
    
        +-----black------+----------red-------+
        |                |                    |
      lamp          transformer             switch
        |                |                    |
        +-----white------+--wh-+ +---black----+
                               | |
                               w b
                               h k
                               | |
                              feed
    
    You can do essentially the same thing if you can get power to the
    switch box, using the white wire to bring the neutral to the other
    white wires at the transformer.
    
    (*) Given the spare non-white conductor, you really shouldn't use the
    white for non-neutral.. if you do, wrap a piece of black electrical
    tape around each end.
    
    ...tom
291.438Thanks for the confirmationMSE1::SULLIVANMon May 01 1995 13:446
Thanks Tom,  you confirmed my suspicions.  I can get a new power lead to
the switch.  In fact I located the spot and drilled up from the basement
last night.  All set to pull the new wire.

							Mark

291.711General Electrical Circuit Questions...IKE22::EIKENBERRYJohn (Ike) EikenberryThu Sep 07 1995 18:5949
    Hi -
    
        I've read through several notes relating to circuits and didn't
    find a note that seemed appropriate, so I'm starting a new note. 
    Moderator, please feel free to move this note if I overlooked a better
    place.
    
    Last night, my wife & I managed to trip a circuit breaker two times. 
    After a little experimenting, we identified all of the items on the
    circuit and to say that I was somewhat surprised was an understatement. 
    The items we noted (there may be more) were: microwave in the kitchen,
    all kitchen lights, at least one outlet in the family room, porch
    light, and the 4 spotlights around the house.  Somehow this doesn't
    seem reasonable and perhaps doesn't even meet code.
    
    My plan is to break up this circuit into n circuits (n to be determined
    after more investigation).  Thinking about the project raised a few
    questions which I'm hoping that the notes-readers here can help with:
    
    --	When would someone use a 15-amp circuit vs. a 20-amp circuit?  I
    	realize that if you need the power, you would use 20-amp.  Is it
    	just a matter of economy in that 15-amp is cheaper?  Or is there a
    	real reason (e.g., code requires 15-amp circuit so that the builder
    	has to put in more circuits, breaking the electrical map up more)?
    
    --	A few years ago, I heard of a rule of thumb for the number of
    	outlets/lights/devices on a circuit.  At the time, I remember the
    	rule to be assume x amps per duplex outlet, so you should only have
    	15/x duplex outlets on a 15-amp circuit or 20/x for 20-amp.  Can
    	anyone fill in x for me?  What is an average light counted as
    	(75watts/125 volts = .6 amps, count as 3/4amp)?
    
        For permantly wired lights and other items, I can easily calculate
        it out the exact ampers used, but is a slop factor used?  For
        example, the kitchen light is 4 banks of 2 fluroescent lights. 
        Let's say that each light is 40 watts, so total wattage for the
        light fixture is 8x40 = 320watts, about 2.5 amps.  So for this
        circuit, do I set aside just the 2.5 amps or something like 4 just
        in case someone down the road wants a bigger light (and therefore
        won't have to worry about having to upgrade the circuit)?
    
    --	Lasstly, and this may answer all of the above questions, is the
     	NEC (National Electrical Code) book available to a mere mortal like
     	me?  If so, where does one get it?  Barnes & Noble?
    
    thank you for your information,
    	Ike
    
                                        
291.712QUARK::LIONELFree advice is worth every centThu Sep 07 1995 19:159
The only reason to run 15A is if you're a cheapskate and putting in 14GA
wire.  Since the savings is minimal, I see little point.  The NEC requires
20A for some circuits (small appliance circuits in a kitchen).

You can buy the National Electrical Code book at any electrical supply store
(since you're in Nashua, try Ralph Pill, where I got mine).  It has answers
to most everything you asked here.

				Steve
291.713Wiring Simplified as NEC reference alternativePASTA::DEMERSThu Sep 07 1995 19:268
    I find the "Wiring Simplified" book to be a nicely condensed version of
    the NEC for what I need to do.
    
    Current version is based on the '93 NEC and Spag's has it for $3.99.  I
    did notice that this new version has much better diagrams than older
    versions.
    
    Chris
291.714MKOTS3::WTHOMASThu Sep 07 1995 19:275
    Re: Slop factor
    
    I seem to recall a 150% slop factor for motor/compressor-type stuff on a
    circuit  (ie. 6 amp rated window a/c should count as 9 for "startup"
    current). 
291.715PCBUOA::TARDIFFDave TardiffThu Sep 07 1995 20:2813
        <<< Note 5669.0 by IKE22::EIKENBERRY "John (Ike) Eikenberry" >>>

	Unless you're rewiring all the devices, you won't be able
to upgrade to a 20 amp line, as that would require 12 gauge wire,
as opposed to the probably 14 you've got in there now.  The breaker's
job is to protect the wire from melting - putting in a larger breaker
on a circuit that you didn't wire personally, and KNOW what's out there,
is just as bad as the old replace-the-fuse-with-a-penny trick.  
	Alternatively, just make sure your smoke detectors are working...

	Probably your simplest fix is to run a new 20 amp line for the
microwave and leave the rest alone.  As long as you're not running any
heating devices in the outlets, you'll be ok.
291.716SHRMSG::BUSKYFri Sep 08 1995 12:1119
    As a previous reply stated, you can't just pop in a bigger breaker
    to solve your problem. A 15 amp breaker is used to protect 14
    gauge wire, a 20 amp breaker is ued to protect 12 gauge wire. 

    As far as breaking up a circuit, you'll have to do a little
    detective work to figure out how to easily do it and accomplish
    the goal. While just running a new line to a high amperage device
    on the circuit, such as the microwave, you have to consider what
    to do with the existing circuit wires currently feeding the
    microwave and the rest of the outlets or fixtures down the
    line.

    If most of the devices are daisy chained, one feeding the next,
    you can map out the circuits and try to find a point some where
    in the middle where you can end the current line, and run a new
    line to the next device to feed it and the other outlets and
    fixtures down the line.

    Charly
291.717DSSDEV::RICESun Sep 10 1995 18:1824
The basic answers to your questions are:

- 1.5A per duplex receptacle
- 80% general load factor, i.e. 12A max on 15A circuit
- Use 14 GA 15A circuits in general
- Use 12 GA 20A circuits in kitchen and work areas.
- Separate large applicances onto their own circuit

As far as always using 20A circuits....
- It really isn't wise to provide more power to a point than you need.
- You may need more 15A circuits than you would 20A; So its likely to be the
  same cost wise.
- If something does trip a circuit, you loose fewer things with the 15A
  circuits.
- Remember appliance/lighting that you use in the receptacle are UL approved for
  15A circuits generally.  This can sometimes make a safety difference.
- If you do generally use 20A circuits, the entire circuit is supposed to handle
  the 20A.  This includes the actual duplex receptacle, a 20A one doesn't even
  look like a 15A one.

From what you've described the problem just sounds like you need to find another
circuit to plug your microwave into.

-Tim
291.718NETRIX::michaudJeff Michaud, That GroupSun Sep 10 1995 23:2112
> - If you do generally use 20A circuits, the entire circuit is supposed to handle
>   the 20A.  This includes the actual duplex receptacle, a 20A one doesn't even
>   look like a 15A one.

	This last sentence is a little confusing.  One does not need
	20A receptacles because the circuit is 20A's.  A standard
	duplex outlet receptacle has 15A outlets, but is rated for
	20A feed through.

	You only need a 20A outlet if the applicance has a 20A plug
	(as far as I know, or all of the homes I've been don't meet
	code :-)
291.719DSSDEV::RICEMon Sep 11 1995 12:4217
RE: .7  

Although it has been allowed in the past they have been "recommending" for
awhile now that you always use the screw connections and not "feed through" a
receptacle.  You may already see this as code in some communities; MA for
instance.

Also, I did say "generally", as in "should".  The point being, don't make a mess
by using 20A circuits where you don't need them. ;-)  If you want to 'err on the
side of safety then use the 12GA wire on a 15A circuit; You "should" not be
using 15A anything on a 20A circuit.

The code has lots of "shall" and "should" with alot of "good workmanship"
sprinkled in ;-)

Sorry if this was confusing,
-Tim
291.720NETRIX::michaudJeff Michaud, That GroupMon Sep 11 1995 14:1911
> Although it has been allowed in the past they have been "recommending" for
> awhile now that you always use the screw connections and not "feed through" a
> receptacle.

	"feed through" from use my of the word does not have anything to
	do with using the quick connect holes vs. the screw connections.
	"feed through" simply means "non-terminal receptacle" (ie. daisy
	chaining).

	Either I'm completely messing up the terminology or you haven't
	been in the trade for a while :-))
291.721WAHOO::LEVESQUEsunlight held together by waterMon Sep 11 1995 14:585
    I think the point he's making is that if you are going to have a switch
    or receptacle that you will be daisy chaining you ought to use the
    screw connections for both wires as opposed to using the scew
    connection for one and the quick connection for the other (thus forcing
    all the current to flow through the switch or receptacle.)
291.722Thanks for the info...IKE22::EIKENBERRYJohn (Ike) EikenberryMon Sep 11 1995 15:2710
    Thanks for all of the information.  I think I'll take the easier route
    and just run a line to microwave.  I have 200amp service which isn't
    even close to being used and lots of space in the circuit box, so just
    running a dedicated line is no big deal.
    
    Also, I'll go get the NEC, sounds like a useful reference.
    
    Thanks again,
    	Ike
    
291.723DSSDEV::RICEMon Sep 11 1995 15:5028
Sorry I confused you again by making two points when you thought I was making
one.

Point 1:
Do not "feed through" means that you do not feed the next receptacle from
another.

Point 2:
Always use the screw connections and never use the quick connect ones.

Now they relate because people use a duplex receptacle to make connections; Yes,
they are not supposed to do that.  When they do that then they are doing a "feed
through" the duplex receptacle.  They are relying on the receptacle to carry
current as RE:-.1 has correct.

So I'll assume you never use the quick connects anylonger.  Now there are two
receptacles in a duplex receptacle, duh I know.  There is a metal break-away tab
connecting the two for each leg.  Unless you break this tab there should never
be more than one wire connected to each leg.  The tab is good for when you want
to switch one half of the duplex receptacle. 

If you want to make wiring connections then use pig-tails.  Also, don't forget
to clamp your grounds ;-)

-Tim

P.S. I haven't been away from the trade, I just don't rely on it to pay any
bills.  Also, there are too many Electricians in my family already ;-)
291.724NETRIX::michaudJeff Michaud, That GroupMon Sep 11 1995 16:085
> If you want to make wiring connections then use pig-tails.

	Isn't this code anyways, at least for neutral and ground wires?
	The idea being that this minimizes the chances of the neutral
	connection being broken while the hot isn't??
291.725QUARK::LIONELFree advice is worth every centMon Sep 11 1995 17:073
Yes, it is.  I just found out about it myself.  

			Steve
291.726SHRMSG::BUSKYMon Sep 11 1995 17:105
> I think I'll take the easier route and just run a line to microwave.  

    And what will you do with the line that's currently running to the
    microwave outlet and possibly the line leaving that box that's
    feeding the next box down the line?
291.727Breaking up a circuit - questions....IKE22::EIKENBERRYJohn (Ike) EikenberryTue Oct 10 1995 16:5918
    re: -.1
    
    Thankfully the outlet servicing the microwave is the end of the chain. 
    So, I'll break the chain one before and run a new wire to service the
    microwave.
    
    As a side question, is it best to remove unused wire from behind the
    walls?  That's probably confusing.  Maybe a diagram will help. 
    Currently I have one end of the circuit as below.
    
           ---a---- overhead lights -----b------ microwave outlet
    
    My goal is to run a new wire to the microwave outlet, thus making wire
    b not used.  Can I leave wire b in place with caps or should I pull
    wire b out of the wall and ceiling (perhaps easier said than done)?
    
    	thanks!
    		Ike
291.728What are some wire snaking gotcha's?IKE22::EIKENBERRYJohn (Ike) EikenberryTue Oct 10 1995 17:0113
    New question for the guru's out there...
    
    Does anyone have tips/guidelines for snaking new wires through the
    house?  The list of projects that involve running new wires is growing
    (move switch, new switch, new lights, etc.) - yes, probably growing
    faster than I'll be able to get to them.  One of the joys of owning a
    house :-).  I currently have a wire snake and the long drill bits, just
    what are some of the gotcha's/tips/etc that people have in their back
    pockets...
    
    			Thanks,
    				Ike
    
291.729WAHOO::LEVESQUEsunlight held together by waterTue Oct 10 1995 17:4315
    >       ---a---- overhead lights -----b------ microwave outlet
    
    >My goal is to run a new wire to the microwave outlet, thus making wire
    >b not used.  Can I leave wire b in place with caps or should I pull
    >wire b out of the wall and ceiling (perhaps easier said than done)?
    
     If your wire was run properly, it'll be tacked down just outside the
    boxes (and possibly other places along its length.) Removing the wire in
    these circumstances more or less requires that you make a mess of the
    wall. Seems unnecessary. I would probably just disconnect the feed from
    the overhead lights and push the unused wire through the hole in the
    box (put a piece of tape over the hole so when the box is opened people
    will know nothing belongs there.) Then disconnect the wire at the
    microwave outlet and push it through the hole. Now run your new wire to
    the microwave outlet. 
291.730New question - wires in dining room confusing...IKE22::EIKENBERRYJohn (Ike) EikenberryMon Oct 16 1995 17:1841
    
    Thanks for the info in the last many replies - extremely helpful.  
    
    On to a new & different question for the gurus here...
    
    When my wife and I started work on our dining room (painting et al), I
    took down the old chandelier to ensure that it wouldn't get paint
    splattered.
    
    Now here is where I made the blunder - I forgot to mark which wires
    were attached to what.  So, I'm here to ask for help.
    
    The junction box for the chandelier has 3 sets of wire-nutted wires:
    
     	--  A single black wire.  My assumption is that this is the "Hot"
     	    lead for the chandelier.
    
        --  Two white wires twisted together.  Hot neutral for the
            chandelier?
    
        --  Two black wires and 1 white wire twisted together.
    
    Here is where my questions come in:
    
    1)  Using a voltmeter, I can test to see if the single black wire is
        controlled by the dining room switch.  Will this tell me what I
        need to know or is there a different test I should do?
    
    2)  How can I tell which wire set is the hot-neutral for the
        chandelier?
    
    3)  Lastly, is having 2 black wires and 1 white wire twisted together
        part of NEC code?  As someone who has learned that black is "hot",
        white is "hot neutral" and green is "ground" - seeing a black and
        white wire twisted together looks like a short, but it isn't.
        What would the combination be used for?	
    
    
           Thanks in advance for your help,
    				Ike
    
291.731Easy fix.....BITZEE::CLAYIndecision may or may not be my problemMon Oct 16 1995 18:2110
     1)    The single black wire is the hot to the lamp.
     2)    The two whites are the neutral to the lamp.
     3)    The two blacks and one white is the unswitched hot line and the
    white is being used to feed the switch. (Perfectly legal)
    
    If you still want to test with a meter..... put the meter between the
    single black and the two whites and this will turn on and off with the
    switch.
    
     
291.7322155::michaudJeff Michaud - ObjectBrokerWed Oct 18 1995 20:046
>      3)    The two blacks and one white is the unswitched hot line and the
>     white is being used to feed the switch. (Perfectly legal)

	though I believe in this case doesn't code say that this *hot*
	white wire should be marked as hot (usually be wrapping a piece
	of black electrical tape around the white sheating)??
291.733not in this caseHNDYMN::MCCARTHYA Quinn Martin ProductionWed Oct 18 1995 22:3618
>>	though I believe in this case doesn't code say that this *hot*
>>	white wire should be marked as hot (usually be wrapping a piece
>>	of black electrical tape around the white sheating)??

Nope.  Not required when used as a swtich leg.  In any other situtations you
are required somehow (usually via electrial non-white/grey tape) to mark a
normally white or grey colored wire (I mean the insulation around the wire!).

As I mention in my three-way diagram - this method lets an electrian who looks
at the connections later on easily know which is the switch leg.  

The same is true when using a dark (black/blue/red etc) wire for a neutral or
ground - it must be taped with white/grey or green (for ground).  I did this
when I replaced my electric stove with a gas one.  I used the second black leg
as the neutral and put white tape around it and use the greatly oversized for a
15A line feed.

bjm
291.978Flickering LightBRAT::MCCRACKENWed Nov 22 1995 10:577
    We have an outside light, on a timer, which flickers.  The 
    others don't do this.  Is the wiring wrong, not enough power, 
    what would be causing this?  How do we fix it?  
    
    Thanks in advance,
    Linda
    
291.979SMURF::WALTERSWed Nov 22 1995 12:145
    
    Is it a mechanical timer or just a photocell switch?
    
    If the latter, then the problem may be that light from the lamp itself
    is bouncing back into the photocell causing a feedback loop. 
291.980BRAT::MCCRACKENWed Nov 22 1995 15:173
    It is a mechanical timer.....please help it is driving me crazy!
    
    
291.9812155::michaudJeff Michaud - ObjectBrokerWed Nov 22 1995 15:285
> It is a mechanical timer.....please help it is driving me crazy!

	Have you tried changing the bulb, or making sure the bottom
	contact in the socket is raised high enough to contact the
	bulb?
291.982You need to do some workZENDIA::ROLLERLife member of the NRAWed Nov 22 1995 15:3115
    Is the bulb screwed in tightly?  If it's loose, the heat generated
    could cause it to move and break the connection, cooling down it would
    remake the connection and start all over again.  
    
    Could it be the bulb itself?  Did you try another bulb in that socket?
    
    Is it the timer?  Can the timer be removed from the circuit?  Is there
    a bypass switch on the timer?  If so, did you try turning it on
    manually?  If you did, did the problem go away?  
    
    You need to attack the problem systematically, eliminating one variable
    at a time.  This will get you to the problem component eventually, but
    you have to do some work.
    
    Ken
291.734Done & working, here is final circuit layout...SEND::EIKENBERRYJohn (Ike) EikenberryMon Nov 27 1995 17:5938
    Thnaks for the help on the last electrical question I posted - the
    dining room lamp is up and working.  
    
    Just for future people who may find this set of notes, I'll try to make
    a diagram to help out
    
         black ----------O---------------------- black to next item in
    			 |			       circuit
                         |
         white ----------+----------------o----- white
     			 |    		  |
    			 |    		  |
    			 |-white	  |
    			 |	          |-Neutral from light
    			 |__  _______###__|
                            \    ^    ^
    			    ^    ^    lamp
                            ^    ^
                            ^    Black wire
                            ^
                            dimmer switch
    
    So, in the junction box for the light, I had three sets of wires
    
    	1) Black-Black-White: The hot source, hot going to the next
    			      thing in the circuit, and a white wire
    			      going to the switch.
    
        2) white-white:       the neutral and the neutral going on in 
    			      the circuit
    
    	3) black:	      The wire returning from the switch
    
    So, as noted earlier in the notesfile, the lamp went between the single
    black wire and the two white wires.
    
    		Thanks again!
    			Ike
291.735Don't do that.NETCAD::COLELLAMon Nov 27 1995 18:4514
     >     <<< Note 5669.8 by DSSDEV::RICE >>>
     >
     >    If you want to 'err on the
     >    side of safety then use the 12GA wire on a 15A circuit;
     >    
    
    I thought this was considered bad practice (and rejected by Inspectors),
    because you can now fake out future electricians into thinking 
    it's a 20A ckt.  I think 14 guage has proved itself to be safe when 
    the rules are followed.
    
    
    
    
291.983WRKSYS::WEISSMon Nov 27 1995 21:041
    Is it a standard incandescent bulb or fluorescent?
291.736DSSDEV::RICETue Nov 28 1995 14:369
RE: .24

I agree.

You can do it but it would send "smoke signals" to an inspector.  He'd then look
harder and probably find other screw-ups that are illegal ;-)

Of course, the code is written to allow the inspector room to be more stringent.
There isn't anything "wrong" with putting a 15A fuse on a 20A circuit.
291.984NUBOAT::HEBERTCaptain BlighTue Nov 28 1995 16:177
We had four 60W incandescent bulbs in the fixture over a bathroom sink
that flickered and bugged me. They were all noname, and made in Europe
(Hungary, I think), and the problem was self-correcting. None of them
lasted more than about three months. When I replaced them with name bulbs
the flickering ceased. 

Art
291.969step-up transformer purchase ?PATE::POUNDERFri Dec 08 1995 16:159
    I'm looking for a 120->240V step-up transformer but have had no success
    in finding one. I brought over a TV set and a VCR ( only reason was
    that my kids have 100+ pre-recorded tapes, Disney etc, and I didn't
    want to pay megabucks for conversion ) and only need to drive these 2
    pieces from the transformer so it needn't be a monster !  Can anyone
    help direct me to some electrical supplier(s) where I can purchase
    this?
    
    Trevor
291.970SMURF::SWARDCommon sense is not that commonFri Dec 08 1995 16:334
    Look for a 240-110 Tranformer and run it backwards. You only get half
    the rated power but it should be easier to find..
    
    /Peter
291.971Thanks...PATE::POUNDERFri Dec 08 1995 17:404
    Thanks....given the power reqmts for a TV and VCR are low I wouldn't
    see this as a problem anyway.
    
    Trevor
291.972PCBUOA::TARDIFFDave TardiffFri Dec 08 1995 18:3816
	Won't you also have trouble with cycles?  Isn't Europe
50hz versus our 60hz?  While this doesn't matter much for a resistance
heater or too much for a tool motor, I wouldn't be surprised if it 
mattered a great deal for electronics.  On second thought...maybe not.
Our PC power supplies have a switch for 120/240...so maybe that's all
it takes.  Still got the manuals?  Perhaps your stuff has switches too.

	If existing tapes in PAL/SECAM (European, I believe) versus
our NTSC (or whatever) is your problem, I think you can get VCRs that
take both formats.  This, of course, may also cost a bundle...but then
you'll also be able to watch stuff you get here, not to mention broadcast
TV....if you really want to.

	You might also check out a higher-end electronics store for
advice.  I'm sure they get this sort of question often, and may have
various priced solutions.
291.9732155::michaudJeff Michaud - ObjectBrokerFri Dec 08 1995 19:4311
> 	If existing tapes in PAL/SECAM (European, I believe) versus
> our NTSC (or whatever) is your problem, I think you can get VCRs that
> take both formats.  This, of course, may also cost a bundle...but then
> you'll also be able to watch stuff you get here, not to mention broadcast
> TV....if you really want to.

	I would imagine such a VCR for use here would convert PAL to
	NTSC for output to a NTSC TV.  As such I think you'd lose alot
	as PAL is higher definition (much crisper, I can't wait til we
	get HDTV or Digital TV!).  Then again, if this is for the kids
	they probably don't care ....
291.974clocks will be offSMURF::WALTERSFri Dec 08 1995 20:2819
    
    The only thing that seems to get screwed up by the 50/60 cycles
    problem are internal clocks.  Most of my 240v stuff from the
    UK was switchable to 110 so I never needed a transformer, but
    the clocks are no longer accurate. If you are just playing tapes,
    it should not be a problem. 
    
    There are a few VCRs that convert to NTSC and they range from about
    $600 to $2000 depending on what features you want.  Hunt stocks low-end
    multistandard VCRs in Ma and Great Northern Video in Concorde NH has the
    high-end Panasonic stuff.  If you also have a PAL camcorder,
    this could be a way to go.
    
    Regards,
    
    Colin
       
    
      
291.975Tell the kids it's broken !PATE::POUNDERMon Dec 11 1995 13:4418
    From what I can determine there should be no problem with "playing
    only" tapes. Both the TV and VCR were brought across with me for this 
    purpose only. The format shouldn't be an issue. I know I can't receive
    programs on the TV, but as I said...I'm only using it for tape playing.
    I think the answer to the frequency question is that the time clocks
    will run "out of whack" but the internal electronics critical for
    viewing tapes should be OK...they should generate their own clocks for
    timing ( internally ).  Yes I checked both machines and no,
    unfortunately they are not switchable between 110 & 240V.  I think
    because of the format difference where the machines are completely
    incompatable, they assume no-one would be dumb enough to bring them
    from UK to USA ;-)
    
    Assume that running a transformer "in reverse" will work ?  i.e. that
    there won't be some safety feature that blocks attempts to shove a
    supply onto the connections designed to be the "output".
    
    Trevor
291.985Light Switch--Need help pleasePOWDML::GILDERMon Dec 11 1995 14:4919
    Could I please have help with my bathroom light?
    
    First of all, I am the worse chicken in the western hemisphere
    when it comes to electrical stuff. Scenario is, my 1956 house
    has 1955-early 56 wiring.  On Saturday, I went to turn off the
    light upon leaving room. --Conservationist that I am...
    
    The switch went down but lights didn't go off.  There is a little
    illumination on the switch that acts as sort of a "hi folks, I'm 
    the light switch" for the dark.  That illumination is out when light
    is in the on position.
    
    If I repeat the motion several times the light eventually goes out.
    
    What kind of problem do I have?  Is it fixable by a whimp?
    
    Thanks
    
    Adriane Gilder 
291.986answerPOWDML::GILDERMon Dec 11 1995 15:056
    A friend just informed me that I have a major potential fire hazzard.
    I gotta get a new switch in there pronto.
    
    I'm leaving this entry in as the possibility it will help others.
    
    Adriane
291.987Watch out...VICKI::DODIERSingle Income, Clan'o KidsMon Dec 11 1995 15:1512
    	Hate to be the bearer of bad news, but it may not be quite as easy
    as just replacing the switch. If the wiring is that old, you may have a
    situation where the insulation around the wires themselves is old,
    dried out, and brittle.
    
    	I came across something like this when I tried to replace a light
    fixture in an old cottage for a relative. Moving the wire, even
    slightly, made the insulation crack and fall off the wire. Perhaps 
    you'll be luckier, or perhaps that's why the switch does nothing
    (i.e. wires shorted together). :-(
    
    	Ray
291.988if you are worried - find someone to helpHNDYMN::MCCARTHYA Quinn Martin ProductionMon Dec 11 1995 15:3916
>>    If I repeat the motion several times the light eventually goes out.

Most likly a bad switch.
    
>>    What kind of problem do I have?  


>>Is it fixable by a whimp?

Could be real simple, could be a nightmare.... if you are a wimp about touching
electrial anything - than it is most likly going to be a nightmare - that's
just the way it works...  If you are scared to even open the main panel cover
than find someone to help you out.  At best, its a 2 minute job, at worst,
maybe 15-30 minutes.

bjm
291.989thanks I'm all setPOWDML::GILDERTue Dec 12 1995 11:097
    Thanks to everyone who answered here and directly to me.  Last
    night a kind soul came by to fix the problem.  Someone I'd not met
    before but is now a nice friend to have.
    
    Looking forward to other types of helpful hints in this conference.
    
    Adriane
291.990TP011::KENAHDo we have any peanut butter?Tue Dec 12 1995 13:051
    Was it just a broken switch?
291.991yes to -.1POWDML::GILDERTue Dec 12 1995 18:5610
    -.1
    
    I think the answer to the question is yes.  I think that the 40 year 
    old switch decided to be this week's p.i.t.a.
    
    Everything has worked fine since my "knight in shining armor" left.
    Now all I have to do is sit back and wait for the next crisis.
    
    Mods:  thank you for managing such a worthwhile project as this
    conference.
291.9922155::michaudJeff Michaud - ObjectBrokerTue Dec 12 1995 21:115
> Mods:  thank you for managing such a worthwhile project as this conference.

	I don't believe this conference has any "active" moderators any
	more .... (should instead thank the original moderators whomever
	they were ... :-)
291.96CSLALL::NASEAM::READIOA Smith &amp; Wesson beats four aces, Tow trucks beat Chapman LocksThu Dec 28 1995 16:2220
291.97SUBSYS::DONADTFri Dec 29 1995 14:413
    RE .7
    Better call Active first. I think they closed the Westboro store a few
    years ago. Still open in Woburn though.
291.612Auto-transformer solutionSMURF::PRWSY1::WOODSThu Jan 04 1996 17:437
    
    Most of the larger electonic supply houses (Newark Electonics, for
    example) carry setup down auto-transformers specifically for this purpose.
    
    You are probably looking at around $90-$120 for a unit which will
    supply about 7 amps at 115 volt from a 230 volt input.  BTW, they
    weigh about 15-20 pounds.  
291.1000Blowing adjacent circuit breakerROCK::MUELLERMon Jan 15 1996 19:5331
I've got a strange problem ...

I'm renovating a bathroom/hallway in my basement and re-doing the wiring myself.
This bathroom, hallway, and a misc room are all on a 20 Amp circuit.  My
addition and garage run off of a separate, 15 Amp circuit, who's breaker happens
to be directly above the one for the bathroom/hallway/misc room in the box.  The
15 Amp breaker is one which has a "test" button right on the breaker.  The 20
Amp breaker is a normal breaker.  I just installed some track lighting (3-lamp,
halogen, I forget the wattage, but each light has it's own transormer to drop
the voltage to the bulbs) on the 20 Amp circuit.

If there are no major appliances running on the 15 Amp circuit (ie: no lights,
but TV/VCR is OK), and I turn the track light on the 20 Amp circuit on, the 15
Amp circuit blows (yes, you read this right, the adjacent circuit blows, not the
one with the track light!).  If there is a major applicance running on the 15
Amp circuit, I can flip the track light switch 'till I'm blue in the face, and
it won't trip the 15 Amp circuit.  I can make this happen over and over again.

Anyone ever seen this?  Any ideas where to look?  Could poor/bad/non-existant
grounding cause such a problem?  I have not looked into the circuit breaker box
yet, but my home inspector (I recently bought the house) said that the wiring
was a mess in that box.

BTW: The house was built in 1967/68.  The addition/garage was put on in early
1970's.  House and addition have grounded wire throughout.

Any input would be appreciated.

Thanks,

Rob
291.100119096::BUSKYTue Jan 16 1996 11:0411
> addition and garage run off of a separate, 15 Amp circuit, who's breaker happens
> to be directly above the one for the bathroom/hallway/misc room in the box.  The

    Maybe heat from the 20AMP breaker is rising up and causing the
    15AMP breaker, you did say above it, to trip. Breakers do get warm
    during normal use and I believe that it is this heat, or over
    heating that causes them to trip. 

    Try relocating the breakers to see if the problem goes away.

    Charly
291.1002I doubt that it's the heatROCK::MUELLERTue Jan 16 1996 12:019
>    Maybe heat from the 20AMP breaker is rising up and causing the
>    15AMP breaker, you did say above it, to trip. Breakers do get warm

Nah ... the 20 Amp circuit could be completely off (and, thus, cold) when I turn
on the track light for the first time, and the 15 Amp will still blow.

Sorry, but heat doesn't seem to be the culprit.

-Rob
291.1003Sound like a ground fault..BITZEE::CLAYIndecision may or may not be my problemTue Jan 16 1996 12:156
    It seem to me that the breaker is triping out because of ground fault
    and not overload. The cause of the problem could be a loose neutral or
    you could have the lights on the same neutral as the garage/addition.
    Are you replaceing existing lights or as it a new instalation?
    
    Don
291.1004some replacement, some newROCK::MUELLERTue Jan 16 1996 12:3312
I'm replacing some existing wiring, but have added a new light and a bathrooom
exhaust fan as well as re-wired a 4-way switch to a 3-way switch (I didn't need
the extra switch anymore).  All of this was on the 20 Amp circuit. I never
touched the 15 Amp circuit. The halogen track lighting is on a standard 2-way
switch on the 20 Amp circuit.

I think I'll have to open up the circuit breaker box and have a look inside. 
I'll check the neutral wires.

Thanks,

Rob
291.1005one or more of these circuits is GFCI, right?REGENT::POWERSTue Jan 16 1996 14:009
There's a "test" button right ON the 15amp breaker?
Doesn't this mean that that breaker is a GFCI breaker?

I can think of scenarios where breakers on OPPOSITE legs can affect 
one another more easily than I can think of scenarios that would make
adjacent breakers on the same leg affect one another, but I'm guessing that the
GFCI nature of the 15amp circuit is key here.

- tom]
291.1016EVMS::MORONEYOperation Foot BulletTue Jan 16 1996 18:0320
re .1921:

The breaker which keeps tripping is almost certainly a GFCI breaker.

I'll _guess_ that either the place is incorrectly wired with the neutral
being shared between the two circuits, or there is a high resistance
connection between a switched hot of the 20A circuit and the GFCI
circuit.  The GFCI circuit must have its own neutral to the GFCI
breaker itself.  If you open up the panel you'll see the GFCI breaker
has the hot AND the neutral leading to it, and it has a short wire to
the "real" neutral bus.  The GFCI breaker measures the difference in
current in the hot and neutral.  If not the same there's a problem and
it trips.

re .1926:

The "adjacent" breaker is almost certainly using the opposite
"hot" leg of the feed.  It becomes obvious when you look how
the breakers are connected in a box.  But this isn't really
relevant.
291.1017same difference :-)2155::michaudJeff Michaud - ObjectBrokerTue Jan 16 1996 21:526
> The GFCI breaker measures the difference in
> current in the hot and neutral.  If not the same there's a problem and
> it trips.

	In other words there should be zero (or whatever the threashold is)
	difference between current flowing on both legs of the circuit?
291.1018looks like I forgot a sentence...EVMS::MORONEYOperation Foot BulletTue Jan 16 1996 23:596
re .1938:

Yes the _difference_ in current should be 0.  I think they "allow"
something like 20mA before they trip.  It's not that much.

-Mike
291.101920 mA is too highSSDEVO::JACKSONJim JacksonWed Jan 17 1996 13:447
20mA can kill you under the right circumstances.  I believe the trip is for
less than 4 mA.

My high school electronics class had an interesting sign on the wall:

	"At 10 mA you can't let go.  At 100 mA you're dead.  Don't make
	 an ash of yourself"
291.1020RE.1931 : call the power companyDUNKLE::MCDERMOTTChris McDermottWed Jan 17 1996 14:046
I had a similar low current/voltage problem that manifested itself by the all
the lights in the house dimming whenever a heavy load, like the electric dryer,
came on line.  The problem was the power line comming into the house.  It had
burnt itself out such that most of the current was passing through only small
number of conductor strands that hadn't burnt away.  The power company came out
and replaced the cable - problem solved.
291.1027water in service panel!11666::CLEMENTSmells like NirvanaMon Jan 29 1996 12:2228
    Discovered a weird (to me) problem on Friday nite during our heavy
    rainstorm.  I had a water leak inside my electric serice panel.  I
    removed the front cover and discovered water was entering the panel
    thru the mainline feed cable.  The water is travelling "inside" the cable
    and dripping out of the cable where the cable casing ends.  This is the
    main house feed that is on the 100amp breaker.  From there it just
    drips all over the service panel wires and collects on the bottom of
    the box where it drips out of crevices.
    
    The service to my house is bolted on the side near the roof, from there
    a cable (about 6') travels down to the meter box, then another cable
    leaves the meter box for about 18" and enters the house into the
    basement.  The meter itself had a lot of moisture inside it, the bottom
    of the meter box had a punchout, I tapped it open to see if water was
    inside there, but there was not any.  I am thinking maybe the water is
    entering thru the casing of the cable.  This cable is 30 years old.  I
    wrapped eletric tape around the end that comes out of the meter
    yesterday.  There is putty around the point where the cable enters and
    exits the meter and enters the house (thru the elbow).  
    
    Anyone ever experience this?  Any ideas on where the water could be
    coming in?  I assume that the cable coming out of the meter is
    different from the cable coming into the meter (not continuous), so I
    wrapped the end closest to the leak first to see if this makes a
    difference, but will not know until the next rainstorms...
    
    Thanks!  Mark
    
291.102819096::BUSKYMon Jan 29 1996 12:3713
>    Anyone ever experience this?  Any ideas on where the water could be
>    coming in?  I assume that the cable coming out of the meter is

    Yep, more often than not, the water enters through the so-called
    weather head! Once inside the outerjacket of the cable, it follows
    it just like a pipe right into your main panel!

    The weather head "seal" is usually just a clamp and cover around
    the cable. Wind blow rain can find it's way in there. Maybe some
    putty up there might help. But be careful up there near the
    service cable to feed cable clamps.

    Charly
291.1029weather head?11666::CLEMENTSmells like NirvanaMon Jan 29 1996 14:496
    Charly,
    
    This is where the street feed connects to my house?  I noticed some
    kind of little box up there, is that the weather head?  I'll take a
    closer look next weekend, maybe I can seal it up with putty or some
    sprayfoam???   Thanks, Mark
291.1030Create a "Drip Loop"BINKLY::CLAYIndecision may or may not be my problemMon Jan 29 1996 15:2127
    Try looping the wires going to the weather head down so the water
    follows the wires and drips off and doesn't flow down inside the
    outer sheathing of the cable.
    Hope this helps....
    
    Don
    
         conection to the house
       /                            main feedersferom street
      /                            /
     Xmmmmmmmmmmmmmmmmmmmmmmmmmmmmmmmmmmmm
              x
    |wh       x
    |w x     x
    |w  x   x
    |w   xx
    |w      \
    |w       \
    |w        \drip loop
    |w
    |w
    |w      /meter 
    |w     /
    |---- /
    |    |
    |    |
    |____|
291.103119096::BUSKYMon Jan 29 1996 15:3727
>     This is where the street feed connects to my house?  I noticed some
>     kind of little box up there, is that the weather head?  I'll take a

    Exactly! If you've got "flat" entrance cable going up the side of
    the house, the weather-head is usually a clamp-on "box" maybe 3"
    by 3" or so and probably has a mounting slot for a screw to fasten
    the weather-head to the side of the house. 

    It covers the end of the cable where the sheathing stops but the
    two feed wires and loose ground wires continue out and are
    connected to the street feed. The "box" is more like a hood over
    the cable. Very easy for wind blown rain to enter, especially if
    it's mounted parallel to a shallow roof line.

    Once the water enters the sheathing, it travels right down the
    cable, into the meter box. If your meter box has a wire in the top
    and out the bottom, the water probably "sticks" to the ground
    wires, which usually feed straight down to a pair of connecting
    blocks, and then re-enter the sheathed cable and make it's way
    down to the main panel.

    I've since replaced my feed cable with steel conduit up the side
    of the house. This type of arrangement seems to have a more
    weather tight type of weather-head. It's also mounted vertically
    and less susceptible to wind blown rain.

    Charly
291.1032Its like, you were there!11666::CLEMENTSmells like NirvanaMon Jan 29 1996 16:0517
>    Once the water enters the sheathing, it travels right down the
>    cable, into the meter box. If your meter box has a wire in the top
>    and out the bottom, the water probably "sticks" to the ground
>    wires, which usually feed straight down to a pair of connecting
>    blocks, and then re-enter the sheathed cable and make it's way
>    down to the main panel.
    
    Yes you have described my meter, and indeed the water seems to be
    traveling down the strands of ground wire and not the two feed wires!
    
    Thanks for all the help and ideas!  Hard to tell without looking at it
    if I will do this, but do you see any problem with using spray-on
    insulation foam where the wires enter the weather-head, or would I be
    better off using a putty.  I'd rather try putting something in there
    instead of trying to re-arrange the configuration of the wiring.
    
    Mark
291.103319096::BUSKYMon Jan 29 1996 16:5813
>    if I will do this, but do you see any problem with using spray-on
>    insulation foam where the wires enter the weather-head, or would I be
>    better off using a putty.  I'd rather try putting something in there

    Putty is typically used, like you might find where the cable
    enters the meter box. Although I suppose that some type of
    expanding foam might have a better chance of filling all of the
    nooks and crannies where the wires exit the cable sheath. Problems
    with this? I don't know???

    Charly


291.1034call MA Electric?11666::BWHITEMon Jan 29 1996 17:466
    Mark...maybe MA Electric will take care of this....I thought that they 
    are responsible for the wiring up to the meter....I know that when I
    had my electric service upgraded, they came and replaced the wire from
    the weather head to the meter at no charge....
    
    Ben
291.103519096::BUSKYMon Jan 29 1996 18:4027
>     Mark...maybe MA Electric will take care of this....I thought that they 
>    are responsible for the wiring up to the meter....I know that when I

    Not quite... above ground, they're responsible up to the
    connection between the feedwire from the pole and your wires just
    beyond the weatherhead that we've been discussing.

    They also own the meter itself, but you own the meter box and
    wiring to and from it.

    In an underground situation, you own the wires underground and up
    the side of the pole as well.

    I don't know what the rules are for an underground service in a
    development where they have underground feed wires as well.
    Probably somewhere inside of the ground level distribution boxes.

    Keep in mind, these rules are for the state of Massachusetts.
    Your milage will vary in other states. 

    There are also several communities in Mass that have local
    municipal electric companies (not Mass Electric or Boston Edison).
    I think that most of them also follow the rules listed above but I
    don't know for sure.

    Charly

291.1036Mass electric. just dont take NO...ANGST::DWORSACKMon Jan 29 1996 19:2730
    RE: Mass electric.
    
    whenever it would rain hard, or blow from a direction, i would get
    water in my box in the basement. turned out it was running down
    the wires starting at the point where the wires would enter the
    connector where the drip loop should be. turns out i did all i could
    (not much) but the large ground cable was not long enough to get 
    a loop. 
    
    i called and someone came out to look at it. (i didnt ever know they 
    were there) i expected someone to at least knock on the door and
    ask to see where it was leaking.
    
    so i called and they said they had been there. i said come out again
    and talk to me about it. i thought it was THEIR problem. i finally got
    to talk to a field supervisior and he would send someone. 
    
    FINALLY a nice guy comes out and i tell the story. yep, he says,
    water will work down that braided ground cable like it was running
    downhill. i asked real nice if he could put some kind of "extention"
    piece on it. sure he said , but you mind if i drive my truck over 
    your lawn.. hell, i would have done anything to get this fixed for
    free...!! i even had him put some kind of cover on the wires
    rubbing against a tree. (a tree i couldnt cut down, since it had
    the electric wires on one side, and tele on the other... :-(
    
    just dont take NO for a answer. request someone come out and talk
    to you..!!!
    
    jim
291.1037SMURF::MSCANLONa ferret on the barco-loungerMon Jan 29 1996 21:006
    I had the same situation you describe about 2 winters
    ago.  Called PSNH, they came out and fixed it.  Never
    got a bill for it.  This is, of course, New Hampshire.
    Don't know about Massachusetts.
    
    Mary-Michael
291.1038MA Electric11666::CLEMENTSmells like NirvanaTue Jan 30 1996 13:0810
    Well, MA Electric came out this morning.  That was fast, within 1 hour
    of calling them and asking them to look at it and install a drip loop.
    Turns out we already have a drip loop.  He said the weather head box
    should be replaced, it is not at the correct angle, and that we should
    of course have an electrician do this.  I still need to get up there
    and take a good first hand look at it.  Maybe I can still get away with
    sealing the box, or perhaps I can move the angle of the box myself if
    there is just a screw holding it onto the house.  
    
    Mark
291.1039the weather head angle?11666::CLEMENTSmells like NirvanaWed Jan 31 1996 12:0333
    Got a better look at the weather box this morning (from the ground).  
    This box is a lot smaller than I thought it would be (maybe 2"x2"), it
    looks a bit rusted and instead of the box being horizontal, it is at
    a 45 degree angle.  Is it suppose to be angled?  How difficult is it to
    replace this box, and how dangerous is it.  I have done wiring inside a
    service panel before, but messing with the main feed is new to me.
    
    Here is an attempt to draw the roof line and angle of the box...
                                       
    
                       / <--- roof line
                     /
                   /
                 / /\ <--- top of box
               /    /
             /    /
                 / <--- cable leaving bottom of box
    
    
    I am thinking that perhaps it should be more like this...????
    
    
                       / <--- roof line
                     /
                   /
                 / ___ <--- top of box
               /   | |
             /      /
                   / <--- cable leaving bottom of box
    
    
    
    
291.1040adding a 2nd light to 2 switchesAKOCOA::STUARTRSkiers have bigger mogulsWed Mar 06 1996 14:4636
    
    
I installed a light in the stairwell going down to the basement. I 
needed this because when I finished the basement and enclosed part
of the stairway it made it dark.(no light at bottom of stairs)

I have a switch at the top of the stairs and in the garage that works
a light in the basement but only lights part of the bottom stairs.

I installed track lighting in place of the existing light with no
problem, works off the switch fine.

I installed the new light right above the switch at the top of the 
stairs running the wire from the switch to the new box.

The switch has the white and red wire from the other switch connected
to it and the black wire from the downstairs light. The black wire
from the other switch and the white wire from the downstairs light
are tied off together. So I connect the black wire from the new
light to the switch where the black wire from the other light is
and the white wire from the new light to the white and black wires
that are tied off. NOT !

When the downstairs light is off, the new light is on and visa-versa.

So I'm scratching my head and taking a load of crap from the wife at
this point.

I tried a couple other OBVIOUS combinations but the result is always
the same.
    
Any ideas ??? This looked soooo easy !

Randy
    

291.1041MAET11::SEGERThis space intentionally left blankWed Mar 06 1996 15:4317
If i've read this correctly, it sounds like you're saying you have a 3-way 
switch and want to add an addional light.

If you look in the box you're trying to connect the second light to, are there
2 cables or one?  If one, it's a 3-wire one (henve the red wire) and all it
really does is connect to the other switch.  I think what happens is the 
switches switch the HOT wire between the red and the black depending on their
positions.  IN this case, connecting your light to one of these may give the
unusual results you're seeing.  

If you want both lights to work off the same switch, you'll need to connect it
to the SECOND cable, which must be in the other switch box , OR connect it to
the second light.

I think...

-mark
291.1042a general diagramHNDYMN::MCCARTHYA Quinn Martin ProductionWed Mar 06 1996 15:595
If it helps check out:

http://hndymn.zko.dec.com/three_way.html

bjm
291.1043WLDBIL::KILGOREStop Global Whining!Wed Mar 06 1996 16:0221
    
    If you're positive that the cable that feeds the downstairs lights
    is coming from the upstairs box, just tie the new cable to it, black to
    black and white to white.
    
    The second possibility, if there are two cables into the upstairs
    box, is that the two-wire cable is an unswitched feed and the three-wire
    goes to the garage switch (and another cable connects the garage
    switch to the lights). In that case, tie the white wire from the new
    light to the white of the unswitched feed, and the black from the new
    light to the wire that currently connects to the center pole of the
    switch. (A three-way switch connects either of two wires on the
    "outside" poles to a third wire on the "center" pole; it's pretty easy
    to figure out which is the center pole with an ohmeter; turn off the
    power and disconnect the switch first. :-)
    
    The third possibility, if there is only one three-conductor wire coming
    to the upstairs switch, is that you just can't run a wire from that
    switch to the new light. (In this configuration, there is no neutral
    wire available at the upstairs switch.)
    
291.1044Run new light wires to existing lightFOUNDR::DODIERSingle Income, Clan'o KidsWed Mar 06 1996 16:2414
    	It's hard to know exactly what you have without seeing it. You'd
    need to know which box the power feeds into, and where the light is in
    relation to the switches, and so forth to be able to explain to us what
    you actually have. I don't think that's nessecary though.
    
    	The bottom line is, a light takes only two wires, a hot and a
    neutral. Depending on where the light is in relation to the switches,
    the wires going to the existing light may not be black and white.
    
    	The easiest way to do this is to run the wires for the new light to
    the two wires going to the existing light. This assumes that you can
    get the wires back to the way that they were originally connected.
    
    	Ray
291.1045ODIXIE::ZOGRANAtlanta, Home of the WS ChampsWed Mar 06 1996 18:088
    How do I re-wire a light switch to have all of the outlets in a room
    always remain "on"?  I just set up a PC in a room with all of the
    outlets working off of one light switch, and I'm afraid of the kids
    turning the switch on and off.  Leaving the outlets hot wouldn't be a
    problem.
    
    Dan
    
291.1046Easiest way...HELIX::WELLCOMESteve Wellcome MRO1-1/L31 Pole HJ33Wed Mar 06 1996 18:176
    Do you need the light switch for anything else (like an overhead
    light)?  
    
    Easiest thing would be to take out the switch, join the wires with
    a wire nut, and put on a blank cover plate.
    
291.1047ThanksODIXIE::ZOGRANAtlanta, Home of the WS ChampsWed Mar 06 1996 18:314
    I don't need the switch for anything else.  By connecting the wires I
    assume that you mean black to black and white to white?
    
    Dan
291.1048Should only be two shielded wires connected to the switchVAXCPU::michaudJeff Michaud - ObjectBrokerWed Mar 06 1996 18:5213
> I don't need the switch for anything else.  By connecting the wires I
> assume that you mean black to black and white to white?

	If the power feed comes into the box, as well as the wires going
	to the light (or in your case the outlets) then the whites should
	already be connected together (as should be all the grounds).

	In any case, assuming the switch is a 1-way switch, there should
	be only two wires connected to it (not counting a possible bare
	cooper ground wire to a green screw on the switch), those two
	wires, regardless of color, are the two wires you want to
	connect together with a wire nut (after you've turned the breaker
	off :-).
291.1049WLDBIL::KILGOREStop Global Whining!Wed Mar 06 1996 19:0419
    
    All your outlets, both top and bottom in each duplex fixture, are
    controlled by the switch???
    
    It's fairly common to have a number of outlets switch-controlled, but
    it's also fairly common to have only one outlet in each duplex
    controlled in this manner, while the other outlet is unswitched.
    
    If this is your situation, just remove the duplex you want unswitched,
    detach the three wires, cap the red wire, replace the duplex with a
    new one (the original duplex has a connector between top and bottom
    outlets broken off, allowing them to work separately), reattach the
    black, white and ground wires, and reinstall.
    
    If you really have only a two-wire switched connection to the outlets
    (which is somewhat strange), remove the switch, disconnect the two
    wires and connect them together, and replace the switch plate with a
    blank cover.
    
291.1050I'll try some things that were mentionedAKOCOA::STUARTRSkiers have bigger mogulsThu Mar 07 1996 11:0314
re; adding a light .....

Thanks for the responses. I was assuming the other wire in the box
went to the light, but now that you mention it, it could go anywhere.
This weekend I'll disconnect it and if the existing light still works
I'll have my answer. I can't get another wire from the existing light
to the upstairs switch. I might be able to get a wire from the garage
switch to upstairs though. Should keep me busy this weekend.

I'll update things next week.

Randy

291.1051???FOUNDR::DODIERSingle Income, Clan'o KidsThu Mar 07 1996 14:029
    re: 1050
    
    > I can't get another wire from the existing light to the upstairs switch.
    
    	You don't need to get a wire from the existing light to the
    upstairs switch (unless you're trying to do something else I missed).
    You need to get a wire from the existing light to the *new light*.
    
    	Ray
291.1052can'tAKOCOA::STUARTRSkiers have bigger mogulsThu Mar 07 1996 15:1815
      <<< Note 291.1051 by FOUNDR::DODIER "Single Income, Clan'o Kids" >>>
                                    -< ??? >-

    re: 1051
    
<    	You don't need to get a wire from the existing light to the
<    upstairs switch (unless you're trying to do something else I missed).
<    You need to get a wire from the existing light to the *new light*.
    
<    	Ray

can't do that either.....

Randy

291.1053Simple 3-way diagramFOUNDR::DODIERSingle Income, Clan'o KidsThu Mar 07 1996 16:4041
    	If that's the case, then your only alternative is to either learn
    how three-way switches operate and then learn how to apply it to your
    particular situation, or get someone who has this knowledge to do it
    for you.
    
    	If you knew which box had the power coming into it and where the
    light was in relation to the power feed wire and switches, then I could
    enter in a simple schematic you might be able to follow. Otherwise, I
    don't see how anyone here will be able to help you without this
    information.
    
    	On the outside chance this will help, here is a simple one light
    schematic with two 3-way switches to ponder -
    	
     blk = black wire
     wht = white wire
      o  = switch or light screw terminal
    		
    		   +-------+       +-------+        +-------+
                   |  box  |       |  box  |        |  box  |  
    		   v       v       v       v        v       v
    			     red
    	blk		o-------------o      blk		wht
    	-------------o	     wht	 o------------olighto----
    feed wires		o-------------o	  			 |
        wht						 	 |
        ---------------------------------------------------------
    		   ^       ^       ^       ^        ^       ^
                   |  box  |       |  box  |        |  box  |  
    		   +-------+       +-------+        +-------+
    
    	A 3-way switch has 3 terminals, one of which is a slightly
    different color than the other two. This can be referred to as the
    point terminal. The switch connects one or the other terminal to the
    point terminal. 
    
    	If you draw them in yourself, and simulate the switching action from 
    one to the other, you'll see how it works and also understand why a 3-way 
    switch cannot be marked on or off like a single-pole (2 terminal) switch.
    	
    	Ray
291.1054HYLNDR::BROWNFri Mar 08 1996 20:1533
    
    off the subject, but... 
    
    I did a similar thing a house ago.  I added an overhead light at the bottom of 
    stairs and made the switch a 3-way.  Initially I found 3 wire in the
    single switch at the top of the stairs which controlled a light at the
    top of the stairs and a utility light in the middle of the basement.  
    
    I initially thought, Great! the electrician ran 3-wire so I can just
    splice in the new switch at the bottom of the stairs and be all set.
    The downstairs light was within 5' of the panel, so what I thought
    had been done was 2 wire to light, three wire to switch (power sent
    up stairs to switch and back down the third leg to the light).
    
    I couldn't get the stupid thing to work.  Power never seemed to be
    where I thought it should be.... Good reason.  Actually power came
    from upstairs! down thru the light at the top landing, down into 
    the switch, then a switched leg went to the down stairs lights, and
    a hot leg went down behind the fuse panel out to the outside/
    downstairs light... also turns out it then loops up into the 1st
    floor to support some lights there.  This is probably all to code,
    but butt ugly.  Power starts from the downstairs panel then first goes
    up to the 2nd floor then works its way back down then up again.
    I ended up dead heading the power as it came down thru the stair 
    landing light and adding another breaker to the panel, cutting the wire
    as it went behind the panel and connected both halves to the new
    breaker.  Then I rewired the all the lights in the basement, at
    least I was then able to remember which leg was powered and from
    which direction.
    
    
    
    from the
291.1055Problem SolvedODIXIE::ZOGRANAtlanta, Home of the WS ChampsMon Mar 11 1996 12:168
    Turned off the breaker and took off the switch.  It had the black wire
    going in and out, so I just unhooked the wires, connected them
    (standard wire connector and tape), popped the power back on and
    replaced the switch (will deal with a plain cover later).  All outlets
    work fine, with no possibility of someone switching he computer off via
    the lightswitch.

    Dan
291.1056avoid tapeHNDYMN::MCCARTHYA Quinn Martin ProductionMon Mar 11 1996 13:339
>>    (standard wire connector and tape), 

Tape?  Why tape?  If the "wire nut" is not covering all exposed copper then
something is wrong. 

Its very rare when tape is needed. - I don't even know where it would be called
for in the code!

bjm
291.1057QUARK::LIONELFree advice is worth every centMon Mar 11 1996 13:365
I always tape my wirenuts to provide additional resistance to the nut twisting
off or the wire popping out.  Similarly, I put tape over the side terminals on
switches and outlets.

				Steve
291.1058VAXCPU::michaudJeff Michaud - ObjectBrokerMon Mar 11 1996 14:109
> I always tape my wirenuts to provide additional resistance to the nut twisting
> off or the wire popping out.

	Why would the nut twist itself off?

> Similarly, I put tape over the side terminals on switches and outlets.

	I do this sometimes too, especially when the devices are inside
	a metal work box...
291.1059Under certain conditionsFOUNDR::DODIERSingle Income, Clan'o KidsMon Mar 11 1996 15:006
    	About the only time I tape anything is if I put an old work box in
    a sheetrock wall using the metal straps (buchanon strips [sp?]). Then
    I'll tape the terminals of a switch or outlet. Not sure if it's
    required for code, but it's a good idea anyway.
    
    	Ray
291.1060hmmm, I wonder when you ARE supposed to use it?HNDYMN::MCCARTHYA Quinn Martin ProductionMon Mar 11 1996 15:196
If the nut is applied correctly it will never loosen up.  I have taped the
sides of devices when installing them in old-work metal boxes but I have never
taped over a wire nut ever since I worked with a master electrian "oh so many
years ago" :-)

bjm
291.1061I give upAKOCOA::STUARTRSkiers have bigger mogulsMon Mar 11 1996 15:5717
I'm gonna call my electrician !

recap; switch upstairs has 2 wires, a 3-way and a 2-way. red and white
of 3-way into switch, black of 2-way into switch, black of 3-way and
white of 2-way tied together. 
after more investigation, switch in garage has only the 3-way wire
that I assume goes to upstairs switch.
I've tried every possible combination of connections with no luck,
the new light goes of when you turn on the downstairs.

Yesterday I disconnected 2-way and the light in cellar does not work
so I assume the 2-way supplies the light. It's probably something
simple that is getting by me.

Randy

291.1062It's not a "simple thing"FOUNDR::DODIERSingle Income, Clan'o KidsMon Mar 11 1996 16:3513
    re:1061
    
    	The 2-way and the 3-way have nothing to do with each other. A 3-way
    is NEVER, under *any* configuration, ever connected to a 3-way. A 3-way
    will only ever be connected to another 3-way in a two switch set-up, or
    a 4-way if more than 2 switches are used to control the same thing.
    
    	If you do not understand 3-way switches, and you can't run the wire
    from the existing light to the new light, then it is not a "simple
    thing". It sounds like you've been lucky that you haven't shorted
    anything out, yet ;-)
    
    	Ray
291.1063ODIXIE::ZOGRANAtlanta, Home of the WS ChampsMon Mar 11 1996 17:094
    re. - The Tape.  It doesn't hurt, and, while the chances of it
    "unwinding" are slim, I had the tape handy and went for it.
    
    Dan
291.1064VAXCPU::michaudJeff Michaud - ObjectBrokerMon Mar 11 1996 18:3511
> re. - The Tape.  It doesn't hurt, and, while the chances of it
> "unwinding" are slim, .....
                  ^^^^

	if you tightened the nut yourself and you give it a little
	pull to make sure it's on, then I'd say the chances are
	less than "slim".  Unless you got polterguists ....

	Also remember that *before* you put on the wire nut, that the
	wires should already be mechanically joined (ie. twisted together)
	and sound....
291.1065Pwiiiiing!SMURF::wolf95.zk3.dec.com::PBECKPaul Beck, WASTED::PBECKMon Mar 11 1996 19:263
I'm getting this mental image of the twisted wires under the wire nut acting as 
a spring, untwisting suddenly and sending the wire nut caroming around the 
inside of the electrical box like a champagne cork...
291.1066WLDBIL::KILGOREStop Global Whining!Mon Mar 11 1996 19:4211
    
    Re .1065:
    
    It has been calculated that if all the potential energy stored in all
    the twisting of wires and wire nutes in an average 2.3-bedroom house
    was converted to kinetic energy simultaneously, the 1.2-gigawatt surge
    would cause a warp in the space-time continuum could destroy the universe
    as we know it.
    
    Of course, that's a worst-case scenario...
    
291.1067ODIXIE::ZOGRANAtlanta, Home of the WS ChampsMon Mar 11 1996 20:086
    I think I triple twisted and duct taped the connections on my air
    shredder.  Shredded air does funny things to non-taped wire
    connections.  Of course I didn't tape my water shredder connections for
    the pool (who does that anymore anyways?).
    
    Dan
291.1068What's that about an Ayer sweater?SMURF::wolf95.zk3.dec.com::PBECKPaul Beck, WASTED::PBECKMon Mar 11 1996 21:582
I don't use wire nuts. I use a wire shredder. You get much better wire-to-wire 
connectivity with a wire shredder.
291.1069getting back to basicsMAET11::SEGERThis space intentionally left blankTue Mar 12 1996 11:3917
hell, I just fill the box with epoxy!

back to the original question (was there really one?) - getting the 2 lights to
work off the two switches, something I have done may help you...

Having turned off the breaker, remove all the switches and expose all the wires
involved.  Now turn the breaker back on and find the HOT wire!  Now try to
figure out where the OTHER wires go.  If you only have 2 reds (which I suspect
you do), they're obviously part of the same cable as are the associated black
and white wires.  If you're lucky, there will only be one or two cables left
and you should be able to determine which end goes with which.  If you can't,
you're dead in the water.

Having verified all this stuff, you should be able to draw out the diagram of
what's connected to what and from there get your switches working.

-mark
291.1070up the creekAKOCOA::STUARTRSkiers have bigger mogulsTue Mar 12 1996 16:3314
I talked to my electrician last night and he confirmed what was already
mentioned here, I have no neutral, I have to get it from the light that
is downstairs. He said it's possible to fix it so the ground wire was
the neutral but he wouldn't do it or tell me how. (I wouldn't anyway)

So, I'll have to figure out how to get a wire from the downstairs
light to the upstairs light. The ceiling of the basement is sheetrocked.
(I know, stupid move... didn't have enough room for a suspended one)

My wife is REAL pleased with this project !

Randy

291.1071ground = netural (sort of)MAET11::SEGERThis space intentionally left blankWed Mar 13 1996 10:3213
>He said it's possible to fix it so the ground wire was
>the neutral but he wouldn't do it or tell me how. (I wouldn't anyway)

as a point of clarification:

	ground wire = neutral (from a functionality perspective)

at least they're run to the same place in the fuse box and are even the same
gauge wire.  I've hear a few explanations in the past why you need both and
usually forget them as quickly as I hear them, though I'm sure someone will
once again remind me in here  8-) 

-mark
291.1072Its in the flow..BITZEE::CLAYIndecision may or may not be my problemWed Mar 13 1996 12:321
    A neutral carries current a ground does not......(or should not)
291.1073QUARK::LIONELFree advice is worth every centWed Mar 13 1996 12:344
The NEC is quite explicit that a ground conductor (bare or green) should never
be used in place of a neutral.

					Steve
291.1074inquiring minds want to knowMAET11::SEGERThis space intentionally left blankWed Mar 13 1996 15:239
re: last couple

I'm not saying that one should use a ground instead of a neutral, all I'm saying
is that from a connectivity perspective, they both go to the same place...

that said, could someone say a few words about WHY this is done the way it is
as I'm sure there's a good reason.

-mark
291.1075WLDBIL::KILGOREStop Global Whining!Wed Mar 13 1996 15:5923
    
    Re .1074:
    
    At the service box, all neutrals and grounds are tied to the same bar,
    which is tied to a good earth ground.
    
    In normal service, the neutral wire completes the current loop with the
    hot wire; the neutral always sits at ground potential, while the hot wire
    swings + and - with respect to it. The ground wire also sits a ground
    potential, but it doesn't conduct current.
    
    The ground wire is meant to complete the current loop *IN AN EMERGENCY*.
    For example, if a hot wire in your washing machine vibrates loose and
    touches the metal enclosure, which is connected to the ground system
    through the ground pin in its power cord, the gound system completes
    the circuit, keeping the enclosure at 0 potential (and popping the
    breaker). Without the backup ground system, the enclosure would quite
    patiently sit at the hot wire potential until you do the next load, at
    which time it would at very least administer a nasty shock.
    
    The ground system is meant to be a backup -- safety via redundancy. It
    can't be a backup if it's being used as a primary conductor.
    
291.1076can't be too careful with electricity...MAET11::SEGERThis space intentionally left blankThu Mar 14 1996 10:5410
ahhh...  that sounds famailiar.

just as a point of clarification for me, many new electrical appliances have
one of the plug prongs enlarged so the plug will only go in one way and any
exposed metal parts are then grounded to that, eliminating the need for the
3rd wire for gound.  Applying that login to your washing machine example, if
a hot wire loosened up and hit the chasis wouldn't it trip the breaker even if
the ground wire weren't attached?

-mark
291.1077only as good as the dyi'er installationHNDYMN::MCCARTHYA Quinn Martin ProductionThu Mar 14 1996 11:095
Yes the polarized plugs are supposed to make two-prong usage safer - but how
many DIY'er know which side of the outlet is supposed to get the hot and which
one gets the neutral???  

bjm
291.1078EVMS::MORONEYwhile (!asleep) sheep++;Thu Mar 14 1996 14:1619
re .1076:

No, the exposed metal is not connected to the neutral in items with the
large plug.  It would be too dangerous to do so.  A break in the neutral
would mean the whole chassis is "live" (in series with the appliance), not
to mention the miswired DYI outlets, and even those with older outlets who
file off the enlargements on the plug!

What they do is, the appliance is designed so in case of a fault contact is
much more likely with the neutral than the live side, decreasing (but not
eliminating) the odds of a zap.  Because of such dependancies I consider this
rather silly.

About the only example I can think of is obsolete, "hot chassis" TVs where
the tubes (told you it was obsolete) are run directly from the rectified power
line, and the circuit ground is directly connected to one side of the power
line, hopefully the neutral.

-Mike
291.1079Why a separate ground wireSSDEVO::JACKSONJim JacksonThu Mar 14 1996 14:418
1) Because current flows in the neutral conductor, it is not at "ground"
   potential at the appliance (IxR voltage drop occurs in the conductor).  A
   separate grounding conductor is always at "ground" potential.

2) As mentioned, if the neutral feed opens, the neutral wire in the
   appliance is now at the full "hot" potential.  If a grounding conductor
   opens, the appliance chassis is now just floating, and it would take a
   second fault to cause a shock potential.
291.1080HDLITE::SCHAFERMark Schafer, Alpha Developer's supportFri Mar 15 1996 15:4313
    "login to your washing machine"
    
    Mark, you got a Netscape[tm] washer/dryer?    :-)
    
    I believe that the small appliances that come with "polarized" plugs
    are built so that the outside surfaces cannot under any circumstances
    become hot.  Plastic parts and "double insulation" are methods of
    achieving it.
    
    You connect the hot wire to the copper colored terminal.  The neutral
    connects to the silver, and ground to green.
    
    
291.1081we have light !AKOCOA::STUARTRSkiers have bigger mogulsMon Mar 25 1996 13:1514
    
We can close the books on .1040

I went out and bought an 18" drill bit and 25' of wire ......
(had to drill up through the 2X10's, subfloor and plate)

Managed to run a wire from the new light to the existing light and it now
works fine off the switch. This sounds much easier than it was !

Now I have to patch the 5" X 5" hole I had to put in the sheetrock to get
the wire across the ceiling to the light.
    
Randy

291.1082NEC requirements for "smart" switches???STAR::BALLISONTue Apr 02 1996 14:5131
    	Has anyone know what the NEC has to say about remote light
    switching in a house???  I'm building a new house and rather and
    directly wiring from switch to fixture, I'm using X-10 based remote
    switches with the actual line being switched in boxes located in the
    basement.  This gets me lots of flexability since I can switch any
    light from just about anyplace.  But if the dedicated computer running
    the show (a timecommander +), goes down, none of the lights will work. 
    (btw, I've had the timecommander running for several months in the
    place I'm currently renting with no blips or crashes of any sort).
    
    	Leviton makes these nice 4 switch modules that live in a single
    box.  Its much nicer looking than having the 3 and 4 wide boxes full of
    switches that show up in newer houses.  Plus you can define "macros"
    where a single switch can do combinations of things (like dim the
    living room lights, brighten the dining room lights and turn off the TV
    at dinner time).
     
    	I thought of fully wiring the switches/lights and then adding yet
    another box for the remote control stuff, but the number of electrical
    boxes got out of hand in a big hurry.
    
    	The local inspector in Mont Vernon NH seems pretty mellow.  I worry
    a bit that he'll be baffled by the whole concept (he doesn't even own
    an answering machine).  The mini NEC guide books don't say much about
    this.  I don't really want to spend $60 for the real thing and then try
    to wade through it to find out the aspects of this in a residential
    application.  I'm sure it has plenty to say about commercial
    application of this sort of technology.
    
    Brian
     
291.10832082::LIONELFree advice is worth every centTue Apr 02 1996 16:117
The NEC doesn't seem to concern itself with remote switching.   But it's
what your inspector will accept that really matters.

I have read of houses with setups like what you describe - all outlets
and "switches' relay-controlled with a junction box in the basement.

				Steve
291.1084EVMS::MORONEYwhile (!asleep) sheep++;Tue Apr 02 1996 17:0611
>I have read of houses with setups like what you describe - all outlets
>and "switches' relay-controlled with a junction box in the basement.

I lived in such a house as a kid.  12 light circuits had 24V switches run off
a doorbell transformer and wired with doorbell type wiring.
These all went to a box in the basement which had a bunch of latching
relays.  Also there were 2 control panels that could turn off or on any or
all of these circuits.

Since the relays were latching relays they actually remembered their state
across power failures just like "real" light switches.
291.1085LEFTY::CWILLIAMSCD or not CD, that's the questionTue Apr 02 1996 21:4316
    My dad wired our house in LI that way... 
    
    It was a GE industrial/commercial wiring system. Relays at each light,
    wired to 110VAC, with 24VAC control wiring to the switches, with
    multiple switches. Works great.
    
    Most inspectors have seen this stuff in commercial buildings. It's even
    covered in the little green code summary book that Spags and others
    sell...
    
    THe X10 stuff is another issue, though. It's just direct switch
    replacement, so it's not too difficult to figure out, but who knows
    what the inspector will say.
    
    Chris
    
291.1086"every habitable room ..."TEKVAX::KOPECwe're gonna need another Timmy!Wed Apr 03 1996 12:044
    as long as there is a switch in the room that will turn on the light
    they will be happy; if not, they probably won't. (sec 270-10(a)).
    
    ...tom
291.1087STAR::BALLISONWed Apr 03 1996 14:3129
    	Well its not quite using the X-10 switch replacements...  The main
    problem with them is that they don't transmit an X-10 message when you
    push them (they only respond to X-10 messages).  The net effect is that
    the control computer doesn't know the state of the light.  
    
    	Leviton makes a small module that does the same thing as the switch
    only it doesn't have a push button.  I'm hiding these critters in
    electrical boxes in the basement (accessable for fixing them in the
    future if they end up with similar reliability as the switches).  One
    problem is that they are very expensive ($40).  I've toyed with just
    using the regular $9 switches hidden in the basement since the function
    is identical.  Anyway, the normal switch location in the entry to each
    room now gets a device with 4 rocker switches that can send X-10
    commands to the central controller, which in turn will send out the
    on/off/dim commands to the "x-10 switches" hidden in the basement.
    
    	So, the part in the code about a switch to control a light at the
    entrance to each room is met.  I was just worried that the NEC might
    frown on the need for a functional computer between the switch and the
    light.  Of course we all have functional computers in our cars,
    microwaves, VCRs, TVs, dishwashers etc..............
    
    	I do worry a bit about what happens if the control computer
    fails...  At $600 its pretty expensive to keep a spare.  I chose the
    one from the largest maker (and used X-10 which is by far the biggest
    home control protocol), so hopefully spares will be available for
    some time to come.
    

291.1088Weird box problem...AKOCOA::ROLLINSfive fuzziesThu Apr 18 1996 21:1528
    We're currently running a 7K Watt generator and bringing power
    into our electric box at 240v. We've been having some problems
    that seem like they are right at the box...when you switch
    on or off one breaker to any circuit it tends to effect the
    other circuits - if I switch off my 30amp breaker to the water
    pump (wired for 240v), the living room circuit shuts down -
    and that is on a totally separate 15amp breaker.
                        
    And the bathroom's 15amp breaker effects the 30amp water pump
    circuit.
    
    Is this normal???  I have no clue what is going on, but am
    wondering if the generator is no longer supplying the full
    240v????
    
    The box looks like this:
    
    
    		Side 1			Side 2
    
    in		main 50amp
    bathroom	15amp			30amp-a Water
    bedroom1	15amp			30amp-b	Pump
    Kitchen	20amp			15amp	Bedroom2
    		empty	
    		empty
    
    Thanks for any help!
291.1089Wiring by Larry, Moe and Curly?EVMS::MORONEYwhile (!asleep) sheep++;Thu Apr 18 1996 22:5110
About the only thing I can think offhand is if the living room circuit
(not on the diagram?) is really wired through half the pump circuit and
one of the pump leads is through the bathroom breaker.

Only other wild guess is check the neutral, but that would lead to other
symptoms.

240V 30A pump circuit?  Must be some pump!

-Mike
291.1090Question and thoughtsFOUNDR::DODIERSingle Income, Clan'o KidsFri Apr 19 1996 14:4421
    re:1088
    
    	When you say the living room circuit shuts down, do you mean the
    breaker trips, or you just lose power to the living room ? If it's the
    latter, then part of the living room must be wired from one of the legs
    coming from the well circuit. 
    
    	The other possibility is that you're losing one of your hot legs
    under load. When the living room shuts down, check to see if you
    actually have power at the living room breaker. If not, see if you 
    dropped the whole leg. I suspect you'd be noticing other problems though 
    if this happened.
        
    	If this is the case, look to see if you have your load as evenly
    distributed as possible across the two legs (bus-bars) at the main
    panel. Obviously, 240v breakers go across both legs, but the remaining
    ones may be unevenly distributed.
    	
    	Ray
    
    BTW - 240v/30a is not that unusual for a deep submersible well pump.
291.1091Electrical - Buzzing Sound - strip light dial switchAPLVEW::DEBRIAEraising two thumbs up in tranquillityWed Aug 07 1996 15:1230
    
    Gee I liked the old organization of the file better. 

    I'm responding to the old string 5458 "Electrical - Buzzing Sound"
    which now is .695...

    I installed two strip lights inside a china kitchen cabinet (I'm just
    finishing a total kitchen rebuild). The lights had plugs on their
    electrical wires that are removable, such that when you snap the plug
    onto the wire, two teeth inside bite into the power and ground lines. 
    There is no grounded prong on the plug, nor is one side of the wire
    marked in any way, nor do the instructions say one side of the wire
    must be power, etc. I connected these two wires directly to power and
    ground in an electrical workbox.

    On the wire, before the strip lights, is a round dial type of switch.
    Rotate half a turn is on, another rotation is off. This switch is
    making a loud buzzing sound that is driving my SO crazy. Before the
    crown moulding goes up and I no longer have access to the workbox,
    I will try reversing the power and ground sides, though it should 
    not make a difference.

    What could be causing this switch to buzz?

    Can I take any other steps other than hacking in a light switch
    somewhere now that the backsplash tiles are up and I have no room for
    one. Any ideas?

    -Erik

291.1092HDLITE::SCHAFERMark Schafer, SPE MROWed Aug 07 1996 15:481
    maybe try replacing the zip-cord switch?  
291.1093eliminated strip light switches from equation altogetherAPLVEW::DEBRIAEraising two thumbs up in tranquillityMon Aug 12 1996 13:548
    
    I found some room for a hidden light switch in a cabinet corner and
    will simply reroute the wire through the light switch, cutting all
    power to both strips and their noisy switches. This works out well
    since reaching for the upper switch inside the cabinet was a pain, and
    since the crown moulding covering the strip wiring went on this
    weekend. For once the task timing was perfect...

291.1094NOTIME::SACKSGerald Sacks ZKO2-3/N30 DTN:381-2085Mon Aug 12 1996 15:3019
We just moved into a first floor flat with no ceiling fixtures in the bedrooms. 
The rooms all have wall switches, which seem to control half of a duplex
outlet.  I'd like to install ceiling fixtures in two or three of the rooms.
Off the top of my head, I've come up with this methodology on fishing the
wires.  I've never run a horizontal wire in a finished ceiling, so I want
to know if I've got the right idea.

1.  Figure out which way the joists run.
2.  Make hole in ceiling where fixture will be installed.
3.  Make small hole at edge of ceiling between same pair of joists that
    the other hole is between (should this hole be in the ceiling or the
    wall or really at the junction of the two?)
4.  Run fish tape from first hole to second.
5.  Turn the corner (go down the wall).  I've always used a length of
    lightweight chain for vertical runs.  Will one length of fish tape
    do this, or should I use this in combination with the chain, or
    do I need two lengths of fish tape?
6.  Depending where I end up, go through the basement and down from the  
    switch.
291.1095AIAG::SEGERThis space intentionally left blankMon Aug 12 1996 16:0514
I've run wires in ceiling, but I've never really figured how to get them through
the walls, short of having to cut holes...

The one thing that's REAL important is whether or not the ceiling is attatched
to strapping.  If it is, the straps run perpendicular to the joists in which
case you need to rotate your thinking 90 degrees.  I suppose if you start by
cutting the hole for the light fixture first, you can then put a mirror up there
and SEE whether or not there is strapping up there.

I'm still not sure how you make the turn to go down the wall without doing any
major excavating.  For example, how do you get a hole in the 2X4's at the top
of the wall studs?

-mark
291.109619584::DZIEDZICTony Dziedzic - DTN 381-2438Mon Aug 12 1996 16:1818
    You may find it easier to cut a pair of holes at the edge of
    the ceiling/wall joint (one on the ceiling, one on the wall);
    space the one on the wall down a few inches from the ceiling
    to clear the top plate of the wall framing.  You may have a
    bit more patching to do, but the additional access will really
    cut down the amount of time you spend blind fishing.  You can
    drill a hole in the top plate via the top of wall access hole.
    
    Pull the cable up from the basement through the top plate, then
    feed it over to the fixture opening.  That way you can get by
    with a single fish tape and/or use your chain method.
    
    You should check where the power feed for the outlet runs before
    planning your installation; the feed could go directly through
    the switch or it could go into the outlet and via a switch loop.
    
    Avoid running wires through exterior walls if you can; less chance
    of insulation obstruction.
291.1097WLDBIL::KILGOREStop Global Whining!Mon Aug 12 1996 16:3121
    
    If the ceiling is strapped, I've found it possible to fish wires
    parallel to either the joists or the strapping.
    
    To go parallel to the strapping, make sure the tape lies flat enough
    to sneak under the joists.
    
    To go parallel to the joists, bend a small length of the end of the
    fish tape back on itself and tape it, to make a small loop. This will
    allow the tape to sneak over the strapping. (I haven't actually done
    this with fish tape, but it works well with my tool of choice -- an
    old 25-foot tape measure with a broken tip.)
    
    --------------
    
    On the other hand, if this were *my* project, and especially in light
    of the ceiling-to-wall transition, which is never pleasant, I would
    consider putting those switched outlets to good use and buying one or
    two of those torchier-style lamps that reflect off the ceiling. Nice,
    crisp, indirect lighting, no tools required!
    
291.109810+ years agoHNDYMN::MCCARTHYA Quinn Martin ProductionMon Aug 12 1996 16:4216
I don't know if its code anymore but the master electrician I used to work for
taught me to make small notches in the wallboard (or plaster/lathe which was
more often the case) at the top of the wall and  on the ceiling.  You then
fished from the center of the room to the hole on the ceiling.  You notched
with a chisel the top wall plate deep enough so the RX cable and a staple could
be put in place.  The cable was then pulled from from light to switch and
placed into the chiseled out top plate, stapled in, small metal plate was put
over it and nailed in place (to prevent nails from hitting the wire), then a 
patch was applied.

>>    Avoid running wires through exterior walls if you can; less chance
>>    of insulation obstruction.

Not in my house, all interior walls have insulation also.

bjm
291.1099NOTIME::SACKSGerald Sacks ZKO2-3/N30 DTN:381-2085Mon Aug 12 1996 17:107
>    On the other hand, if this were *my* project, and especially in light
>    of the ceiling-to-wall transition, which is never pleasant, I would
>    consider putting those switched outlets to good use and buying one or
>    two of those torchier-style lamps that reflect off the ceiling. Nice,
>    crisp, indirect lighting, no tools required!
    
We have two toddlers.  Floor lamps (and even table lamps) are a hazard.
291.1100Swag chain?SSDEVO::JACKSONJim JacksonMon Aug 12 1996 17:208
How about a lamp hung on a swag chain from a ceiling hook? I did this in my
bedroom, which has the switched outlets that you describe.  Run the chain
between ceiling hooks over to the wall, and then down to the outlet.

Now, I'll admit that in my case the hooks were already in the ceiling (as
plant hangers), and putting in a ceiling box is on my "honey do" list.  But
I've managed to put off putting in the ceiling box for two years now,
because the swag solution is "good enough".
291.1101WLDBIL::KILGOREStop Global Whining!Mon Aug 12 1996 18:007
.1099> We have two toddlers.  Floor lamps (and even table lamps) are a hazard.
    
    Well, there's you optimal solution.
    
    Take 5-6 years planning the rewiring job in gruesome detail, at which
    time the problem definition will have changed.
    
291.1102NOTIME::SACKSGerald Sacks ZKO2-3/N30 DTN:381-2085Mon Aug 12 1996 19:313
>How about a lamp hung on a swag chain from a ceiling hook?

My kids are climbers.
291.1103'more power'HNDYMN::MCCARTHYA Quinn Martin ProductionTue Aug 13 1996 10:165
>>>How about a lamp hung on a swag chain from a ceiling hook?
>>
>>My kids are climbers.

Use heavy chain, lag bolts and pad the floor, they will have a blast :-)
291.1104Doorbell blues...ORION::OTTEWed Oct 09 1996 22:2218
291.1105sounds miswired.TEKVAX::KOPECWhen cubicles fly..Wed Oct 09 1996 22:503
291.1106VAXCPU::michaudJeff Michaud - ObjectBrokerWed Oct 09 1996 23:1821
291.1107not uncommonHNDYMN::MCCARTHYA Quinn Martin ProductionThu Oct 10 1996 01:165
291.1108ding, dong, the doorbell's dead...PCBUOA::TARDIFFDave TardiffThu Oct 10 1996 13:5323
291.1109REGENT::POWERSThu Oct 10 1996 14:599
291.1110time for some data collection...ORION::OTTEThu Oct 10 1996 20:483
291.1111110v between hot wire and buried but unused UF cableHANNAH::SCHULLMANDan SchullmanSun Oct 20 1996 19:1325
291.1112run a new lineHNDYMN::MCCARTHYA Quinn Martin ProductionSun Oct 20 1996 22:1311
291.1113SHRMSG::BUSKYMon Oct 21 1996 12:0326
291.1114MSBCS::BROCKSon of a BeechMon Oct 21 1996 12:192
291.1115HANNAH::SCHULLMANDan SchullmanMon Oct 21 1996 14:0425
291.1116SKYLAB::FISHERGravity: Not just a good idea. It's the law!Mon Oct 21 1996 16:4811
291.1117impedance.NPSS::BENZI'm an idiot, and I voteMon Oct 21 1996 19:0118
291.1118EVMS::MORONEYSorry, my dog ate my homepage.Mon Oct 21 1996 21:1424
291.1119lightbulb removal left base behindTLE::PACKED::BLATTThu Dec 05 1996 23:3616
291.1120I like my potatos sliced and fried :-)HNDYMN::MCCARTHYA Quinn Martin ProductionThu Dec 05 1996 23:399
291.1121interestingVAXCPU::michaudJeff Michaud - ObjectBrokerFri Dec 06 1996 01:233
291.1122REGENT::POWERSFri Dec 06 1996 11:5510
291.1123Globe in the way ?FOUNDR::DODIERDouble Income, Clan'o KidsFri Dec 06 1996 11:5615
291.1124Try this with patienceSALEM::LEMAYFri Dec 06 1996 14:4119
291.1125Another WD-40 useSSDEVO::JACKSONJim JacksonFri Dec 06 1996 17:382
291.1126it won't stay plugged inADISSW::HAECKMea culpa, mea culpa, mea maxima culpa!Fri Dec 06 1996 18:158
291.1127MROA::MACKEYFri Dec 06 1996 18:311
291.1128MKOTS3::WTHOMASFri Dec 06 1996 18:333
291.1129ADISSW::HAECKMea culpa, mea culpa, mea maxima culpa!Fri Dec 06 1996 18:452
291.1130VAXCPU::michaudJeff Michaud - ObjectBrokerFri Dec 06 1996 22:0346
291.1131QUARK::LIONELFree advice is worth every centMon Dec 09 1996 10:5410
291.1132STAR::DZIEDZICTony Dziedzic - DTN 381-2438Mon Dec 09 1996 13:018
291.1133ADISSW::HAECKMea culpa, mea culpa, mea maxima culpa!Mon Dec 09 1996 14:363
291.1134SKYLAB::FISHERGravity: Not just a good idea. It's the law!Mon Dec 09 1996 15:4916
291.1135ADISSW::HAECKMea culpa, mea culpa, mea maxima culpa!Tue Dec 10 1996 13:393
291.1136how to add a box to a ganged set?REGENT::POWERSThu Dec 12 1996 12:5319
291.1137no shortcut that I know ofHNDYMN::MCCARTHYA Quinn Martin ProductionThu Dec 12 1996 13:0513
291.1138Without one in hand...???FOUNDR::DODIERDouble Income, Clan'o KidsThu Dec 12 1996 13:3412
291.1139WLDBIL::KILGOREHow serious is this?Thu Dec 12 1996 13:579
291.1140REDZIN::COXThu Dec 12 1996 14:0814
291.1141SKYLAB::FISHERGravity: Not just a good idea. It's the law!Thu Dec 12 1996 15:039
291.1142not too hardUSCTR1::RIDGESteve Ridge @297-6529Thu Dec 12 1996 15:127
291.1143This method has worked for meSTAR::DZIEDZICTony Dziedzic - DTN 381-2438Thu Dec 12 1996 17:1826
291.1144REGENT::POWERSFri Dec 13 1996 12:0818
291.1145cut open the drywall!VAXCPU::michaudJeff Michaud - ObjectBrokerFri Dec 13 1996 14:324
291.1146AIAG::SEGERThis space intentionally left blankMon Dec 16 1996 11:225
291.1147REGENT::POWERSMon Dec 16 1996 12:0327
291.1148QUARK::LIONELFree advice is worth every centMon Dec 16 1996 12:449
291.1149220 extension cord wiringSTAR::SCHENThu Feb 06 1997 19:5913
    
    I am using 12/3 wire to make an extension cord to 
    go from a four_prong_twist_lock outlet to a three_
    prong 220 outlet (looks like a standard 110 but the 
    two blades are perpendicular to each other).   One 
    end will plug into the 220/110 outlet on a generator
    and the other will have a 220 jointer plugged into 
    it.
    
    Can anyone tell me what the correct way to do this
    would be?  (maybe even a nifty ascii diagram !?! )
    
     
291.1150avoid shocking experiences....PCBUOA::TARDIFFDave TardiffThu Feb 06 1997 20:1333
	I think you've got something wired improperly already.
4 connections on one end (the machine?) and only 3 on the other
(outlet?).

	If a device uses 'pure' 220/230/240, then it only needs the
two 'hot' wires, which are 220 volts apart, and a ground wire for
safety.  What's normally called 'neutral' is the center of the transformer,
between the two 'hot' lines, so either extreme to the center 'neutral'
produces 120 volts.  At certain points in a wiring system, the 'neutral'
is connected to the 'ground', making them the same potential - so any
ground to a 'hot' is at most 120 volts.

	An appliance like an electric range will use all 3.  The heating
elements run between the two hots, getting 240 volts.  Lights and timers
and electronics run between the neutral and a hot, getting 110.  The
ground is there for safety, and connects to the metal frame, so if a hot
accidently shorts to the metal, it'll blow the breaker and turn off, instead
of leaving the chassis 'hot' and letting YOU, perhaps, perform the function
of shorting to ground.  SOME OLDER APPLIANCES cheated here, and didn't
use all 4 wires, although all now have to.

	If you're just running an electric motor at 220, then that machines
cord should only have 3 prongs - ground, hot, and hot.  If you're trying
to plug it into an outlet designed for a dryer, say, that also has a ground,
you're going to end up with something not connected.  You'd do better to
install a proper outlet dedicated to the device.  If you're REALLY sure
of what you're doing, and what ANY future user of your work will be as
well, you could make an extension that leaves out the neutral - but right
now you haven't told us enough to be sure of that - I'm just speculating.

	All these sorts of outlets/plugs are keyed for reasons - they
control/specify the max current allowed as well, and using the wrong
ones can get you in big safety trouble.  Please be careful.
291.1151TEKVAX::KOPECConsider a spherical chicken; ..Thu Feb 06 1997 20:5310
    the four-prong outlet has two hots, a neutral, and a ground; you only
    need to connect the two hots and the ground to the three-prong outlet. 
    
    I'd *guess* that the twist-lock plug will have some hints as to which
    wire is what.. the ground is probably a green screw, the hots are
    probably brass, and neutral is probably plated (silvery).  (the same
    will likely be true for the three-prong socket, but that's not really a
    challenge to figure out anyway..)
    
    ...tom
291.1152Thanks!STAR::SCHENFri Feb 07 1997 12:1710
    
    	Thanks for the info.  I checked out the manual for the 
    generator and now know which of the four terminals on the
    220/110 outlet are the ground and the two hots.  (I will be
    NOT connecting anything to the neutral) 
    	Ground goes to ground, but do I need to worry about which
    of the brass terminals the two hots go to?  It seems like it 
    would not make a difference to the end product (running the
    240 jointer).
     
291.1153either way..TEKVAX::KOPECConsider a spherical chicken; ..Mon Feb 10 1997 12:165
    it does not matter which way the hots are connected (it just gives you
    a 180 degree phase shift, but in a single-phase system that doesn't
    matter..)
    
    ...tom
291.1154Works GreatSTAR::SCHENMon Feb 10 1997 16:5416
    Well, I put the ends on the extention cord and fired up the generator.
    The line checked out fine with a meter and I was about to plug in the
    Jointer but decided to put a new power cord on it (the old one was in
    worse shape than my shiny new yellow waterproof extension).
    I was checking out the way the old cord is was wired to the motor and 
    found that the meter read Zero resistance between the Hot terminal on
    the cord and the body (ground) of the machine!!  But there was infinite
    resistance from the body to the ground prong on the cord!
    
    I rewired it and had my wife 'spot me' while I fired everything up for
    the first time and it works great.  We celebrated my still breathing
    by her lecturing me on 'when to hire an electrician'  :-)
    
    Anyone who needs a staight edge, feel free to call !
    
    Thanks for pointers.
291.1155ASIC::RANDOLPHTom R. N1OOQWed Mar 05 1997 15:478
One of the duplex outlets in the living room is dead. It seems to be the last
one on its particular circuit, i.e. one 14/2 comes into the box and ends at
the outlet.

I flipped every switch on the lower floor, nothing. So now what? How does one
trace the wiring back without opening every box in the house?

(The map of all the house circuits is still on the things to do list)
291.1156WLDBIL::KILGOREBEA; same chattel, new ownerWed Mar 05 1997 16:2332
    re .1155:
    
    Start by making sure that no circuit breakers are tripped (or fuses
    blown).
    
    Carefully remove the outlet from the box (if you're really
    safety-conscious, turn of the house main breaker first, then remove the
    outlet, then turn the main back on and reprogram the VCR).
    
    With a VOM, check for voltage on the wire to the outlet. If it's there,
    switch off breakers until it goes away. When the line is dead, if it was
    attached to the outlet using the quick connectors in the back, remove it
    and attach it to the screw terminals on the side, then restore power and
    check the outlet. (NEVER use the quick connectors!) If the outlet is still
    dead, or if the wires were already on the screw connectors, replace the
    outlet.
    
    If there's no voltage on the line to begin with, you probably have
    a bad connection at another box, either an outlet or a switch box. If
    you found the wire connected to the dead outlet by quick connectors,
    start by removing the wires from the quick connectors on the other
    outlets in the room and attach them to the screw terminals. (This is
    why you NEVER use the quick connectors -- the connections often go bad,
    and if the outlet was used as a pass-through to the next box,
    everything downline goes dead. Futhermore, as the connection is *going*
    bad, it can develop an increasing resistance that can create a lot of
    heat.)
    
    IF the problem is still there, check the outlet boxes on other rooms,
    starting with anything in proximity to the dead outlet, for bad
    connections.
    
291.1157ASIC::RANDOLPHTom R. N1OOQWed Mar 05 1997 18:1423
The wires are already attached to the screw terminals, and a VOM showed no
juice under any conditions. Also, this particular outlet is sort of by
itself, so there's not really a logical next box to go to, to find the rest
of the circuit:

                  ||        ||           ||
                  ||        ||           ||     ^
                  ++        ++           ||     |
                                         ||     |
           bath       hall      closet   ||   stairs
                                         ||     up
                  ++        ++           ||
                  ||        ||           ||
          --------+|        |+-----------+|
          ---------+        +-----===-----+
                                   ^
                                   |
             living room           +---- dead outlet

All of the breakers looked ok, and I have no reason to believe that this is a
dedicated outlet with it's own breaker or anything... Oh, the ceiling light
in the hall above also is dead - might be a related problem. It's 3-way
switched at both ends of the hall, haven't checked into it yet.
291.1158You can't always "see" a tripped breakerSSDEVO::JACKSONJim JacksonWed Mar 05 1997 22:1015
291.1159ASIC::RANDOLPHTom R. N1OOQThu Mar 06 1997 11:277
> Cycle (off/on) all the breakers.

Yah, I have to do that eventually anyway in order to map out all the
circuits. What the heck, it's free and easy...

I'll be surprised if this guy put only one ceiling light and one outlet on a
breaker, though.
291.1160ah ah ah ah sta-in alive sta-in aliveHNDYMN::MCCARTHYA Quinn Martin ProductionThu Mar 06 1997 12:555
>>What the heck, it's free and easy...

And you get a great strobe effect from all the clocks/VCRs flashing 
12:00 - 12:00 - 12:00
:-)
291.1161TEKVAX::KOPECConsider a spherical chicken; ..Thu Mar 06 1997 13:0528
    FIrst I'd check that 3-way light; might be a backwire-to-screw "splice"
    that went west.. or a bad wirenut somewhere..
    
    
    take your handy outlet-wiring-tester (the things with three lights on
    it), and wander around the house finding any other outlets that are
    dead..
    
    
    It is possible that a "fox and hound" sounder might be sensitive enough
    to trace the wire behind the sheetrock, but I've never tried this
    (that's on my toy list... someday..)
    
    Another tool that everybody should have for these kinds of things is a
    voltage probe.. Fluke makes a nice one (AC-1, about $20), and I think
    Radio Shack has come out with one too.. 
    
    I had to replace the bulb in the halogen floodlight above the driveway,
    but (because the bulb was dead!) I didn't know what breaker it was on..
    but I did know where the wire went up the wall from the garage, so I
    just had my daughter hold the probe against the outside of the NM cable
    and flipped breakers till the probe went off..
    
    it's also handy for when you go help Dad out with a project and he says
    "Yeah, I already killed that circuit.." .. you can sniff the box
    without having to probe the metallic parts of the wires/terminals..
    
    
291.1162skylab.zko.dec.com::FISHERGravity: Not just a good idea. It's the law!Thu Mar 06 1997 15:527
I agree with checking that light first.  In fact, I bet one of the switches is at
the bottom of the stairs and thus not far from the outlet.  That's where I would
start.  That may be where the power feed to the outlet is coming from, and
especially if it is an add-on outlet, that might be a big mess in the 3-way switch
box.

Burns
291.1163check the 3way switchesCPEEDY::BRADLEYChuck BradleyThu Mar 06 1997 20:584
check the three way switches.  when they get old, sometimes some of them can
stop in an intermediate position, neither side hot.

291.1164ASIC::RANDOLPHTom R. N1OOQFri Mar 07 1997 11:084
I started mapping out all the circuits last night. That'll at least give me
someplace to start looking for the next box up the line. The breaker labeled
"smokes/halls/bath" doesn't switch off the smoke detectors (120VAC only, as
far as I know). Great. I wonder which one does?
291.1165Being lazy, I'd try this before pulling the main breakerEVMS::LYCEUM::CURTISDick &quot;Aristotle&quot; CurtisFri Mar 07 1997 11:4411
291.1166kids, don't try this at home..TEKVAX::KOPECConsider a spherical chicken; ..Mon Mar 10 1997 10:2310
    household rubber gloves are not durable enough to be considered
    protection.. they can easily develop a pinhole from little things like
    a burr on a terminal screw where a screwdriver cammed out in the
    distant past..
    
    Thinking you are safe when you aren't is much worse than thinking you
    aren't safe..
    
    
    ...tom
291.1167as .-1 says - don't try this at home (or anywhere)HNDYMN::MCCARTHYA Quinn Martin ProductionMon Mar 10 1997 13:3815
>>    If the nervousness is regarding yourself and not just some interesting
>>    sparking and a tripped breaker, wouldn't a pair of rubber gloves do the
>>    job?

Wow - I never thought of that - Never seen it done either, maybe there is a
reason.

The gloves used by lines people once in a while are much thicker than the 
household type.

Its kind of strange because I trust the rubber coating on my 9" linesman Klein
pliers and that is very thin - never thought about it - but I do toss the pair
out if a nick develops.

bjm
291.1168skylab.zko.dec.com::FISHERGravity: Not just a good idea. It's the law!Mon Mar 10 1997 15:375
You probably don't have to take it out anyway...you can usually reach the
terminal screws with a multimeter probe by just taking of the decorative
cover.  Use great caution, especially if it is in a metal box.

Burns
291.1169PCBUOA::TARDIFFDave TardiffTue Mar 11 1997 19:466
>Its kind of strange because I trust the rubber coating on my 9" linesman Klein
>pliers and that is very thin - never thought about it - but I do toss the pair
>out if a nick develops.

Gee, could I have the next pair instead of the trash?  I use 'em
on cold wiring - I don't mind the rubber flaws.  Or I'll re-dip 'em!
291.1170out of the front line and into the rearHNDYMN::MCCARTHYA Quinn Martin ProductionTue Mar 11 1997 21:285
"out" means - into the "spare" tool box(es).  I think I have four 
sets somewhere in the house.

bjm

291.1171ASIC::RANDOLPHTom R. N1OOQFri Mar 21 1997 11:5221
Well, I finally finished mapping out all my electrical circuits. It turns out
that:

- the breaker labeled "smokes/halls/baths" really does switch the smoke
  detectors after all.
  
- the dead outlet in the living room is ok, it's just wired funny. All of the
  living room outlets except for that one switch the top and not the bottom.
  That particular outlet switches both on when all of the others switch
  off... good for a night light maybe? Can't say I've ever seen this done
  anywhere else.
  Safety note: don't assume anything with electrical stuff. I assumed it was
  dead and got bit by 120V... that's when I realized what was going on... it
  came as a shock, heh, heh.

- somebody never bothered to actually wire any electricity to the hall light
  that doesn't work. In fact, I can't figure out what the heck they were
  thinking when they wired that. It didn't match any concept of a 3-way
  switched light that I've ever seen. The wires are all there, based on some
  probing between boxes with very long leads on the VOM.
  
291.1172HYLNDR::BROWNMon Mar 24 1997 17:0583
    
    I'm curious, I began mapping out the circuits in my house so I could
    turn on some temporary lights (been waiting for the electrician to do
    this the last 4 weeks -- 6 broken appointments later I'm still
    waiting).
    
    Anyway, wire nutted everything (this is new wiring) and began tracing
    the first circuit.
    
    	14-2, 15A (I'm assuming 15A because 14-2 feeders(?))
    	    . switch to (1) recessed light
    	    . switch to (3) recessed lights
    	    . switch to (1) recessed light and (1) hanging light
    	    . switch to (3) outside post lights [future]
    	    . switch to (2) recessed lights
    	    . switch to (4) garage interior lights (future)
    	    . switch to (4) garage exterior flood lights (future)
    	    . switch to (1) hanging light
    	    . switch to (1) recessed light (future)
    	    . switch to (1) flouresent light, closet
    	    . switch to (1) recessed light
    	    . 2 duplex outlets (in mudroom)
    	    . 3 duplex outlets (in pantry/includes freezer)
    	    . 1 duplex outlet for "art light" - high on wall
    
    Its been awhile since I did electrical stuff, but this seems a tad
    excessive for a 15A circuit.  Could I use a 20A or 30A breaker?
    Usually I use 12-2 for 20A and 10-2 feeders for 30A circuits.  Its
    passed inspection and the contractor has paid the rough-in fee
    (although bathroom vents not wired, well pump not wired, and about
    another 2-6 circuits are missing).  This circuit is spread out over 5 
    different rooms (not counting future garage and outside lights).
    Garage is being wired now because there won't be any access without
    lots of hacking and whacking of drywall later.
    
    Is it 10 duplex outlets/lights per 15A circuit?  12A I think is the
    rule for 15A (80%), so 23 lights @ 1.2A + 6 outlets @ 1.2A is more
    like 34.8A or a 50A circuit (40A = 32amp load allowance @80%)?
    
    Assuming it is a 15A circuit, I believe I have to spit the circuit
    four ways to get it under control.  This split is paritally based upon
    logical physical area groupings more than a minimum subset of things.
    I'm suggesting that I split the circuit as follows:
    
    	Existing 14-2:
    	    . switch to (1) recessed light
    	    . switch to (3) recessed lights
    	    . switch to (1) recessed light and (1) hanging light
    	    . switch to (3) outside post lights [future]
    	    . switch to (2) recessed lights
    
    	    [This is 11 lights, upgrade the feeder to 12-2 20A?]
    
    New 10-2 feeder, 20A:
    	    . switch to (4) garage interior lights (future)
    	    . switch to (4) garage exterior flood lights (future)
    
    	    [This is 8 lights, but I can tap the 10-2 to support
    	     a couple of outlets in garage]
    
    New 14-2 feeder, 15A:
    	    . switch to (1) hanging light
    	    . switch to (1) recessed light (future)
    	    . switch to (1) recessed light
    	    . 1 duplex outlet for "art light" - high on wall
    
    New 12-2 feeder, 20A:
    	    . switch to (1) flouresent light, closet
    	    . 2 duplex outlets (in mudroom)
    	    . 3 duplex outlets (in pantry/includes freezer)
    
    	  [6 units of load]
    
    
    This is only the first circuit I've fully mapped (I partially mapped
    another) but I certainly hope I don't have to rewire the whole house!
    [Meanwhile the contractor wants to ignore the whole issue and slap 
    up drywall -- it passed the town inspection and I'm holding things up
    by making an issue of it.]
    
    Any advise?
    
    Bud
291.1173OVRTYM::RANDOLPHTom R. N1OOQMon Mar 24 1997 17:3114
>                     <<< Note 291.1172 by HYLNDR::BROWN >>>

A quick calculation:

22 lamps X 75 watts        (75 watt bulb in each)
= 1650 watts
/ 120V = 14 amps

That's not even including whatever gets plugged into the outlets, or any 100W
bulbs. Make 'em do it right. It's your house that'll go up in flames.

BTW, you probably know this by now, but town inspections are crapola. Must be
a hell of a job if you can get it... 5 minutes per inspection, 5 inspections
per day, 15 minutes to drive to each = about 1 1/2 hours work per day.
291.1174Freezer too ?FOUNDR::DODIERDouble Income, Clan'o KidsMon Mar 24 1997 19:217
    	I think you need 12-2 if you want to use a 20amp breaker. It does
    seem like an awful lot on one breaker, especially a 15amp one. The 
    pantry plugs could likely see some high wattage appliances, and if I
    read your reply right, the freezer could be a significant load (at
    least the start up current anyway).
    
    	Ray
291.117520 AMP IN PANTRYSOLVIT::MCCOYMon Mar 24 1997 21:3631
RE: .1172

> 3 duplex outlets (in pantry/includes freezer)

	See 210-52(b) of the N.E.C.  "In the kitchen, pantry, breakfast room,
	dining room, or similar areas of a dwelling unit, the two or more
	20-ampere small appliance branch circuits required by Section
	220-4(b) shall serve all receptacle outlets covered by Sections
	210-52(a) and (c) and receptacle outlets for refrigeration equipment."


	A separate circuit for the freezer is desirable but not required by
	the N.E.C.

	The house will not go up in flames with too much load, the circuit
	breaker will trip and protect the wiring.  

	While not required by the N.E.C., it would make sense to limit the
	load on any one circuit to 80% of what you would consider the maximum
	load at any given time.

	The number of general purpose receptacles on one circuit in a dwelling
	is not limited by the N.E.C.  In other than dwellings, general purpose
	receptacles are assumed to use 1.5 amps and the sum of the amperage
	can not exceed the 15 or 20 amp circuit rating.  30 amp circuits
	are not allowed for general purpose receptacles. 

	20 amp circuits would allow more load per circuit, but some lighting
	fixtures are labeled "connect to 15 amp circuit only"


291.1176HYLNDR::BROWNTue Mar 25 1997 13:4330
    
    Talked to the building inspector, 1.5A allowance per fixture whether light or
    outlet.  This may be a generalization, but is certainly easy enough to
    apply.  Building inspector said to split the circuit to meet the above
    guideline.
    
    The electrician (finally) showed up this morning, demanded full payment
    by friday at which time he will sue me & place a lien on my house.  (I
    note that he said nothing about the contractor -- guess its easier to 
    sue the future home owner.)  Then he left.  Yup, just what I need.
    
    Meanwhile.  The pantry wiring is 14-2 -- which seems ok for nominal
    outlets such as in bedrooms and such.  However, if a 20A circuit is 
    needed, nay required, for the pantry then do I rewire the outlets
    in that room from 14-2 to 12-2?  The feeder certainly should be 12-2,
    but I've always wired circuits throughout with the same gauge wire.
    
    Also, anyone know a good building inspection firm -- esp. one that
    specializes in electric code?  The contractor and I have agreed that
    it may be easier/better to have a 3rd party access the situation.  That
    way we'll know what, if anything, needs to be fixed.  Then we can get
    an estimate to do those changes and then we'll know how much to
    with hold from the final payment to the electrician (and have backing
    documentation for same).
    
    To top it all off getting all this straightened out so we can
    confidently move onto drywall is really going to mess up the schedule
    big time!  Since I've sold my previous residence and my short term 
    lease on the apartment I moved into runs out in another 2 months I'm
    just about ready for... Nervous?  Nah, scare sh*tless!
291.1177WLDBIL::KILGOREBEA; same chattel, new ownerTue Mar 25 1997 14:1017
    
>    The electrician (finally) showed up this morning, demanded full payment
>    by friday at which time he will sue me & place a lien on my house.
    
    If he's serious, countersue and place a lien on his house. However, I
    can't imagine him demanding payment until after his work is ok'd by
    the inspector.
    
>    Meanwhile.  The pantry wiring is 14-2 -- which seems ok for nominal
>    outlets such as in bedrooms and such.  However, if a 20A circuit is 
>    needed, nay required, for the pantry then do I rewire the outlets
>    in that room from 14-2 to 12-2?  The feeder certainly should be 12-2,
>    but I've always wired circuits throughout with the same gauge wire.
    
    If you change the circuit to 20A, all wire on that circuit has to be
    12-2.
    
291.1178Code questionTALLIS::KOCHKevin Koch TAY1-2 DTN227-4043Wed Mar 26 1997 11:484
     The tab on the madison hanger in an outlet box occasionally touches 
one of the screws on the outlet and pops the breaker.

     Does the code let me put tape over the screw and over the metal tab?
291.1179REGENT::POWERSWed Mar 26 1997 11:5518
>      <<< Note 291.1178 by TALLIS::KOCH "Kevin Koch TAY1-2 DTN227-4043" >>>
>                               -< Code question >-
>
>     The tab on the madison hanger in an outlet box occasionally touches 
>one of the screws on the outlet and pops the breaker.
>
>     Does the code let me put tape over the screw and over the metal tab?

Jeesh, I hope not.
If you've got a situation where something is "occasionally" touching 
something else, you've got too much movement in the box and things need 
to be tightened down.
Put tape over it and the motion will continue, probably wearing the 
tape enough so that eventually there will be a high resistance path
instead of a short, and you won't pop the breaker, you'll start a fire
in the box.

- tom]
291.1180REGENT::POWERSWed Mar 26 1997 11:5710
>                     <<< Note 291.1176 by HYLNDR::BROWN >>>
>
>    
>    Talked to the building inspector, 1.5A allowance per fixture whether light or
>    outlet.  This may be a generalization, but is certainly easy enough to
>    apply.  Building inspector said to split the circuit to meet the above
>    guideline.

Didn't anybody file electrical plans on this job?
Did anybody (you, contractor, or inspector) review them?
291.1181HYLNDR::BROWNWed Mar 26 1997 13:5120
    
    There is a signed project plan which includes required outlets,
    switches, lights, subpanels, etc. descriptions on a room by room
    basis.  This along with a statement requiring wiring to meet all
    applicable NEC and local codes.  Included is floor plan views of
    the lighting plan of record including placement and model numbers.
    
    Its the electrician's job to break these down into circuits -- and 
    we did request one both before, during, and after the electrician 
    declared rough-in complete.  The answer was an emphatic no; he doesn't 
    provide one until after final.
    
    I feel I should be able to trust a licensed electrician to 
    do work that meets code -- and trust is require that subs will
    perform work that meets the plan of record.  I can easily visually
    verify whehter something is missing vs the plan -- its harder for
    me to determine whether it meets code without reading and understanding
    the code myself.  [Why do we have licensing programs if home owners are
    also required to learn the code to protect themselves?]
    
291.1182vaxcpu.zko.dec.com::michaudJeff Michaud - ObjectBrokerWed Mar 26 1997 14:5710
> I feel I should be able to trust a licensed electrician to 
> do work that meets code .....

	Well sadly that is your mistake.  *Never* trust a contractor,
	no matter how trustworthy they sound, or how many recomendations
	and rave reviews your friends gave of a given contractor.  Yes,
	there are honest ones out there, but the problem is you can't
	tell them apart so have to assume the worse.

	Same with auto shops, commisioned sales people, etc
291.1183HYLNDR::BROWNWed Mar 26 1997 15:0411
    
    "Trust but verify" is my motto.
    
    Anyway, I seem to recall hearing/reading somewhere that you don't have
    to be licensed to be an electrician in new hamshire?  Is this true.
    I'm looking for the licensing bureau in new hampshire for licensing
    electricians, plumbers, and other tradesman and can't seem to find
    it in either the phone book or the nh agency web page.
    
    
    
291.1184Well, sort of...FOUNDR::DODIERDouble Income, Clan'o KidsWed Mar 26 1997 15:105
    	I believe a home owner can do electrical work in their own home
    without a licence. They must still pull the permit, submit the appropriate 
    plan, and get the work inspected.
    
    	Ray
291.1185reply -.1 Derry, you MUST have an electricianFOUNDR::SKABOExpect Nothing U never disappointedWed Mar 26 1997 15:239
    reply -.1
    
    	Sorry, in Derry, you MUST have an electrician (registered with NH)
    pull the permit - doing the work is another story.....
    
    	Some other NH tows now also have this in requirement, and ya can't
    get around it!  ;*(  No live free or die....
    
    Tom
291.1186HYLNDR::BROWNWed Mar 26 1997 15:5412
    
    I don't want to do this... just wondering if the electrician is really
    licensed, or has to be.  I found the state agency regulating this
    field:
    
    Electricians Licensing Board
    78 Regional Drive, Building 1
    PO Box 646
    Concord, NH 03302
    Attn: Pamela Olin
    
    
291.1187HYLNDR::BROWNWed Mar 26 1997 15:586
    
    ...and unfortunately there is reciprocity only with Mass., Maine, and
    Vermont.  So I guess renewing my Journeymans License in R.I. won't
    do much good.
    
    
291.1188Live Free or Die Except in DerrySOLVIT::MCCOYWed Mar 26 1997 19:3531
RE: .1185

I was also told by the Derry building inspector that I could not do electrical
wiring or plumbing in my own home.  He said they have already been to court
and won the case.  I don't understand how they can get away with this,
N.H. sate law allows a home owner to do this.  Doesn't state law supersede
town ordinances or the whim of the building inspector.  I wonder if this
really went to court.  What other towns have this restriction?  .1184 is true 
in most other towns, even Nashua.  Maybe Derry can outlaw free speech too.


RE  .1175

My point is the wiring described in .1172 violates the N.E.C. because
pantry receptacles must be on a 20 amp circuit separate from everything
except the receptacles in the kitchen and dining room.  No lights can
be on this circuit.  See N.E.C. 220-4(b) and 210-23(a) Exception.

Also, my interpretation of 210-23(a) is that the sum of the ratings of the
lighting fixtures in .1172 can not exceed 50% of the circuit rating.










291.1189Sounds weirdFOUNDR::DODIERDouble Income, Clan'o KidsWed Mar 26 1997 20:5123
    	Well, I guess I stand corrected, at least in Derry. In talking to the 
    author of .1185 (works in my group), he said you used to be able to do it 
    until they changed building inspectors. Sounds like the new inspector wants 
    to limit his liability.
    
    	As far as the original question, it sounds like if you gave the
    electrician a copy of the appropriate NEC code that he violated, it would 
    shut him up about threatening to sue you. The agreement was that he would 
    do the work per code. 
    
    	Since the electrician wanted to be an ass about it, I'd probably take 
    pictures of his work (document the 15amp wiring in the pantry) and tell 
    him if the work isn't corrected pronto, you'll report him to the local 
    inspector. No licenced worker wants to get a bad name with a local 
    inspector if they can help it. 
    
    	Aside from that, if you don't own the house now, why would you be
    paying for this instead of the contractor ? If it's a house your buying, 
    any liens on the house must be cleared before you can buy it. I would 
    think that he'd be SOL if he waited to collect from you when it's the 
    contractor that owes him the money.
    
    	Ray
291.1190HYLNDR::BROWNMon Mar 31 1997 20:0839
    
    I'm the owner of the land and house as it sits.  The bank gives me the
    money and I give it to the contractor -- that's why the bank makes me
    sign a lien waiver at each withdrawal for the full amount.  The deed 
    and morgage lien are in my name.  
        
    The electrician won't be back.  I have pictures of all his work. 
    I've produced a wiring diagram of the circuit which will be verified by an 
    independent building inspection firm.  The electrician has told the
    contractor that he isn't liable for the wiring since I obviously
    rewired it incorrectly.  He inferred that I connected several circuits
    together so of course its overloaded... except I've accounted for
    all wires in all boxes and there is only one feeder into the circuit.
    In addition, the line side had already been twisted together and wire
    nutted in most boxes.  But anyway, it now comes down to him saying I 
    rewired his work to make him look bad and me saying I didn't.  This sub
    is the contractor's responsibility and therefore liability and in that 
    there is no dispute.
    
    Personal opinion is that the electrician has about 3 jobs too many at
    present (hence the reason he was showing up ~1 day/week only after we
    called and called and called) and was doing work a little too quickly,
    doesn't need the job, and is glad to be gone.  [This is now the 11th or
    12th week of rough-in (started about 1/20) -- at first things went thru 
    ceiling joists, but near the end wires were just laid on top of them.  
    This makes walking in the attic area interesting.  The point being the 
    work changed workmanship levels from beginning to end.]
    
    Wierd don't even began to cover it.  
    
    Someday I'll publish my diary and the pictures I've taken during the 
    project... including the framing piece I'm proudest of; an 18:12 pitch
    round turret roof clad in hand cut/fitted copper foil shingles (fiberglass 
    core, bonded copper foil top) topped with the copper cone I fashioned out 
    of 24" wide 20 oz. copper flashing.  I knew my old commutator irons would 
    come in handy some day!  It took me and my brother-in-law a day and a
    half to erect... and me 4 days to pre-cut all the framing and
    sheathing materials.
    
291.1191ASIC::RANDOLPHTom R. N1OOQWed Apr 02 1997 13:5817
> - the dead outlet in the living room is ok, it's just wired funny. All of the
>   living room outlets except for that one switch the top and not the bottom.
>   That particular outlet switches both on when all of the others switch
>   off... good for a night light maybe? Can't say I've ever seen this done
>   anywhere else.

It turns out I was wrong about this... it worked fine with a single 25 watt
bulb plugged in, but 120 watts of bulbs lit up very dimly. Back to square
one...

I broke down and started opening boxes around the room. I finally found the
other end of the mystery box's romex. Seems he wired it between the switched
hot and the permanent hot in one of the split outlet boxes.

Switch "on" - 120v each side, no light. Switch "off", 120v one side, nothing
on other side, but it got a crappy ground somewhere and lit dimly.
Interesting electrical problem, now fixed.
291.1192New 220 volt circuit11673::SUTERand now for something you'll really like!Wed Apr 09 1997 14:2517
	Just purchased a 220 volt shop appliance which uses a plug that
looks like a standard, three prong 110 plug except one of the flat tines
is turned 90 degrees, like this:

		o
	       - |

	I'm installing a dedicated double breaker for a new 220 circuit
for this appliance, but am unclear on the actual wiring configuration.
Anyone have a "wiring for dummies" diagram for this type of circuit? Also,
I know the amp rating of the machine, but does this plug configuration also
imply a specific Amp rating?

thanks,

Rick
291.1193120VAC versus 220VAC PlugsNETCAD::B_MACARTHURWed Apr 09 1997 16:3511
    Rick,
    
      The plug that you describe is not a 220VAC plug, it's a 120VAC, 20A
    plug (assuming that you're drawing is looking into the end of the
    plug). If it's a drawing looking into the mating receptacle, then it's
    rated for 220VAC, 20A. The 120VAC plug is a 5-20P plug, and if the
    blade that's turned 90 degrees were on the other side, then it's a
    6-20P and it's the 220 variety.
    
    Bob
    
291.1194Please help me get the wiring correct as well..11673::SUTERand now for something you'll really like!Wed Apr 09 1997 16:5720
>    Rick,
>    
>      The plug that you describe is not a 220VAC plug, it's a 120VAC, 20A
>    plug (assuming that you're drawing is looking into the end of the
>    plug). If it's a drawing looking into the mating receptacle, then it's
>    rated for 220VAC, 20A. The 120VAC plug is a 5-20P plug, and if the
>    blade that's turned 90 degrees were on the other side, then it's a
>    6-20P and it's the 220 variety.
>    
    Bob,

	I think I may have been drawing it from a receptable perspective.
This of course is further confirmed by the fact that the new applicance
says 220VAC in big letters right on it. 

thanks,

Rick
    

291.119519466::ARSENAULTWed Apr 09 1997 17:1910
While we're on the subject of unusual plugs...

I have a two speed whole house fan that I want to wire using a plug.
This is because I need to physically move the fan into and out of
place each year. 

The fan has two hot wires (low speed and high speed), a neutral, and
a ground.  

Is there a correct to make this pluggable device?
291.1196my guess..TEKVAX::KOPECTom Kopec W1PFWed Apr 09 1997 18:2135
    re Rick:
    
    (note: do this at your own risk. I'm not an electrician.)
    
    The plug has two "HOT" and a ground wire. If you are using plain old
    12-2 NM cable to wire it:
    
    at the breaker box,
      the bare wire connects to the ground (not neutral,
      if they are different) busbar (it will have other
      bare wires attached to it).
    
      wrap the insulation of the white wire with a couple 
      turns of black electrical tape near the bared end,
      and connect it to one screw on the breaker.
    
      connect the black wire to the other screw on the breaker.
    
    at the outlet:
      The bare wire connects to the green terminal. 
    
      Do the black tape thing to the white wire, and connect it
      to one of the brass terminals.
    
      connect the black wire to the other brass terminal.
    
    For the curious, the dance with the electrical tape is required by
    code; it is an exception to the rule "white wires are always neutral".
    
    I believe that plug config is 20A; it will be marked on the mating
    socket. (if the mating socket says "125V", we have an artwork problem
    here..!)
    
    
    ...tom
291.1197always be careful....PCBUOA::TARDIFFDave TardiffWed Apr 09 1997 19:4225
	The code says something like 'white conductors used for hot
lines must be marked'.  Rather than tape, I prefer to mark by coloring
the last inch or so of white insulation with a permanent black marker,
as I get a cleaner and non-removable marking.  This is most often done
on 'switch loops' used when power runs to a ceiling box, and a length
of 14-2 is used to bring the power down to the switch and back up, so
both the black and white leads are used for 'hot', and should be so marked.

	When you're wiring the 220V-rated receptacle, both of the screws
will be gold colored, since it doesn't matter which 'hot' line goes where.

	I've been wiring up for a device that needs 4 conductors - both
hots (220) plus neutral plus ground.  I'd figured out that what I needed
was a L14-20 (NEMA standard designation) which translates to a twist-lock
4 conductor 20 amp 125/250 volt configuration.  Physically, it's got 4
conductors, in twistlock formation.  So off I went to HD...and found what
I thought was the right thing by looking for twistlock....4 conductors...
yup, says 250 volts...got 3 plugs and 1 receptacle.  When I started to
wire it up, the plugs had gold screws on all 3 non-ground pins...hmmm....
which one gets the neutral?  Turns out I'd bought L15-20 by mistake,
which is 20 amp, 250 volt, 3 PHASE...so you get 3 hots, no neutral...and
they vary the pins a bit so it's not compatible with what I wanted.

	In general, though, for basic 120 stuff - black and red wires go
to gold screws, white goes to silver.
291.1198which direction is white hot?REGENT::POWERSThu Apr 10 1997 12:4120
>	The code says something like 'white conductors used for hot
>lines must be marked'.  Rather than tape, I prefer to mark by coloring
>the last inch or so of white insulation with a permanent black marker,
>as I get a cleaner and non-removable marking.  This is most often done
>on 'switch loops' used when power runs to a ceiling box, and a length
>of 14-2 is used to bring the power down to the switch and back up, so
>both the black and white leads are used for 'hot', and should be so marked.

Since you bring it up, in which direction should the white wire be used
as hot?  I've done this, of course, but never knew ifthere was a convention
or code statement about whether the white should carry hot to the switch
or back from it.
My guess would be that white carries hot to the switch so that black can 
be used to carry hot back to the appliance.  This makes a "natural" connection
of black feeding hot into a box and makes it obvious that the white is lilkely
to be connected to the black hots that come into the distribution box.
But guesses like this don't always turn out true.
Is there a proper choice?

- tom]
291.1199TEKVAX::KOPECTom Kopec W1PFThu Apr 10 1997 14:329
    I *believe* that if you use the marked-white, you can do it any way you
    want.
    
    I *believe* there is a specific wiring required by a NEC exception when
    you do NOT mark the white. I can't remember exactly which way the
    required wiring goes, however (I always end up looking it up.. I don't
    do a lot of switch loops these days..)
    
    ...tom
291.1200PCBUOA::TARDIFFDave TardiffThu Apr 10 1997 15:0156
>Since you bring it up, in which direction should the white wire be used
>as hot?  I've done this, of course, but never knew ifthere was a convention
>or code statement about whether the white should carry hot to the switch
>or back from it.

	I recall that there IS a convention, and depending your inspector,
you might get called on it, but I can't recall which way it goes.

	I think you use the white conductor to RETURN the power to the
fixture - I'm basing this on the memory that that's the only time you
can hook up a black and white wire together, at a light fixture.  I may
be wrong, though...

	Simplified case - power running to a ceiling box and stopping there,
switch loop running down to a single switch.  So, coming in to the ceiling
box you've got a power feed - ground, hot black, neutral white.  You've
also got a black and white and ground from the switch loop, and you've got
a ground and black and white from fixture.

	First, all grounds in the box connect together and to the metal box
itself.  I do this first and tuck 'em down out of the way.  The feed wire
hot/black connects to the switch loop black, making it always hot - normal
so far.  At the switch box, you hook the hot/black to one screw - a simple
switch (single pole, single throw) has only 2 gold screws.  Color the white
end black, and attach it to the other.  This part seems logical to me, since
it's NOT always hot, depending on the switch.  Back at the ceiling, color
the white end black again, and attach it to the fixture black - here's your
abnormal connection.  Now connect the fixture neutral white to the feed
neutral white, and you're done.  If the feed was to continue on to another
location (always hot) you'd just add it's black and whites to that of the
original feed.

	I find that tracing the power flow this way - starting at feed hot
and continueing through to feed neutral - helps me keep it all straight.

	Whether it's correct or not, this way makes sense to me, since the
wires that are ALWAYS hot are all real black.

	A common error is to wire the switch loop and device in the wrong
sequence - power goes from feed to device and THEN to switch and back.
This means that the device feed is ALWAYS hot - you CAN'T shut it off, just
interrupt the return path - not nice at all.  I have a porch light wired
this way (it came that way).  Everything seemed normal - if the light stopped
working when the switch was thrown, ok, bad bulb, replace it, all fixed.
(The risk here is that the fixture feed is always on, so say while you're
on your metal ladder, which is in a puddle, and you're reaching up to unscrew
the bulb, and the glass snaps off and your hand hits the wires inside -
ZAP!  Your body just provided a return path for the hot, and you may be dead.
With a proper switch, turned off, the fixture is cold and you're ok.  Of
course, if you leave the switch on, you run the same risk, and the bulb 
lights up as soon as you put it in.  Not really a good idea, considered.)
Then I installed a auto-timer switch, electronic, in place of the switch.
One day I noticed that the switch itself seemed dead - no glowing leds any
more, and of course no light - ok, bad switch, replace it.  Did so...same
results...replace the bulb, original switch ok again - realized that it
was wired backwards.
291.1201STAR::DZIEDZICTony Dziedzic - DTN 381-2438Thu Apr 10 1997 15:1514
    Convention is that a switch loop receives power on the white wire
    and feeds it to the switched device on the black wire.  The idea
    is that the device will have the "normal" black and white wires,
    and the connection of the white wire to a power source (black) is
    a quick clue that an intentional use of the white wire as a "hot"
    conductor is happening at that point.
    
    SO, at ceiling box, power source black connects to white going to
    switch loop.  Black from switch loop connects to the "usual" (brass)
    terminal on fixture.  Power source white connects to the "usual"
    (nickel) terminal on fixture.
    
    BTW, the NEC uses the term "identified conductor" when using a white
    wire as a hot conductor.
291.1202second thatHNDYMN::MCCARTHYA Quinn Martin ProductionThu Apr 10 1997 15:198
>>    Convention is that a switch loop receives power on the white wire
>>    and feeds it to the switched device on the black wire.  The idea

Amen - written or not, it was the way the people I used to work with did 
things.  It made identifying the switch leg in the ceiling box very easy (along
with other obvious things).

bjm
291.1203skylab.zko.dec.com::FISHERGravity: Not just a good idea. It's the law!Thu Apr 10 1997 16:3217
The other nice thing about this scheme is that if you use a tester on it, the
white wire will always test hot.  If the white wire were only hot when the
switch was on, you might discover it to be cold with a tester, and then proceed
on the assumption that is was neutral.

On another subject:  The ceiling fan.  I don't know what the code says, but the
only way I can think of that I would feel even slightly comfortable with would
be to use two normal 110V plugs with neutral and ground on both and with the low
speed hot on one and high speed hot on the other.  And I'd only feel comfortable
with that if the low speed and the high speed were completely independent, that
is if energizing the low speed with the high-speed unplugged did not make the
high-speed plug pin hot.

I'd really discourage using one of the 220 or 3-phase plugs even if they have
the right number of conductors.

Burns
291.1204220 job all done!KWLITY::SUTERand now for something you'll really like!Fri Apr 11 1997 15:347
	The new 220/20 circuit is installed and working just fine! The new
6.5hp compressor it lotsa fun too!

	thanks for all the help!

Rick
291.1205box size - am I grandfathered?RICKS::WINDNAGLEWed Apr 30 1997 16:5218
I pulled a permit to install ceiling lights in three bedrooms that
currently have a switched outlet instead.

So far I'm working on the first one.  I believe the box at the switch is big
enough as it is, unless MA code really does differ from the NEC and
require me to count each bare wire individually (there are two switches
and three ground wires).

At the switched outlet though the box is too small as it is but I don't
have to make any changes there.  I put a junction box in the attic and
connected the formerly switched red wire to black so it's always on.
Another outlet is daisy chained from this one.  Can I leave this box alone
or do I have to put in a bigger one?

I guess a separate question is whether that junction box in the attic
is ok, especially after I put insulation up there and it gets covered.

/carl
291.1206PCBUOA::TARDIFFDave TardiffWed Apr 30 1997 18:2221
>So far I'm working on the first one.  I believe the box at the switch is big
>enough as it is, unless MA code really does differ from the NEC and
>require me to count each bare wire individually (there are two switches
>and three ground wires).

Last formula I used was count the insulated conductors, add one for ALL
the bare ground wires, add one for internal wire clamps, add one for
the device itself.  This was a few years ago, though.

>I guess a separate question is whether that junction box in the attic
>is ok, especially after I put insulation up there and it gets covered.

The junction box being in the attic is ok - covering it up is NOT,
as far as I know.  In general, it shouldn't require more than a screwdriver
to get access to ALL connections - I don't think searching under insulation
counts.  Might, though.

Especially since you were good enough to get a permit, call the inspector
and ask.  He's the one who'll have to pass it anyway, you might as well
find out what he wants before you do it.
291.1207STAR::DZIEDZICTony Dziedzic - DTN 381-2438Thu May 01 1997 11:224
    The NEC now counts a device (switch, receptacle, etc.) as TWO
    conductors when calculating box capacity.  I suspect this was
    motivated by increased usage of larger devices such as GFCI
    outlets.
291.1208Lights on steps/stairsHYLNDR::BROWNWed May 21 1997 13:3917
    
    Are lights required for stairs?  Simple question but I expect it isn't
    a simple answer.  Common sense would seem to dictate that stairs be
    directly lit so as to avoid accidents.  But what constitutes stairs and what
    constitutes being directly lit.  
    
    The particular case in question is a set of three steps between levels
    of the house.  There are ceiling lights in the lower level about 12' 
    away and ceiling lights in the upper level about 8' away from the
    stairs.  Although a light directly over the steps is on the lighting 
    plan they weren't put in and now the walls and ceiling are closed up.  
    What to do, what to do.
    
    Bud