T.R | Title | User | Personal Name | Date | Lines |
---|
291.1 | Check the neutral coming into your house | SOFCAD::KNIGHT | Dave Knight | Tue Sep 16 1986 11:10 | 7 |
| I had a problem like that many years ago. It turned out that the
neutral line was open at the service feed somewhere. Thus many
appliances had 220 across them and many had 0. This kind of situation
is extremely dangerous (fire hazard, etc. etc.). If you have an
open neutral and your ground connection is VERY good, nothing much
happens. If the ground is bad or becomes bad, things go to hell
in a handbasket fast.
|
291.2 | Neighbor's Short? | USFHSL::PIEPER | | Wed Sep 17 1986 15:35 | 24 |
| I just thought I'd throw a few comments out to maybe draw some
discussion about this one...
My first reaction to this one is to think that the problem is really
at your neighbors house (the one whose water line was disconnected
when you had your problems). There is no reason that I can think
of that there should be a potential difference between his water
line and the water main (the shock the workman got and the sparks
when reconnecting). My theory is that the neighbor's water line
is shorted to a hot wire somewhere in his house. This of course
is not a "dead short" but probably a nick in a wire causing a
high resistance connection. Since ground and neutral are tied together
in the service panel, their ground and neutral being tied to a hot
lead essentially ties your ground and neutral to the same hot lead
(giving you a zero reading on one side and 190 on the other)because
your ground is tied to their ground via the water lines.
just a couple of questions:
Are there any more houses that are serviced from the same transformer
that you are?
Did anyone else have any electronic stuff get damaged?
Joe
|
291.3 | Sounds Familiar | MAXWEL::BROSNIHAN | BRIAN | Wed Sep 17 1986 16:16 | 7 |
| We are also having some water work done on our street. Last
week our neighbors had the fire dept. there because they smelt
smoke and the lights were flickering. After invesigating, the
Mass. electric company said that the water dept. disconnected
their ground wire from the water meter which caused an electrical
surge. From what they told me... a few of thier wires got fried
and the water dept. is liable.
|
291.4 | PROBLEM SOLVED! | DRAGON::SCHIFF | | Fri Sep 19 1986 00:52 | 68 |
| The problem has been solved (I hope)! (.1) had the answer.
The electric company came by my house yesterday morning to install recording
meters on my main service panel. While they were there, they checked the main
circuit breaker box and discovered that the neutral connection was very loose.
This service panel had supposedly been "checked" by the town electrician and an
electrician I had called.
The electric company also checked the connections at my meter and decided that
the neutral there was also bad. This had been discovered the first time they
were at my house and said it probably was not the cause of the problem but I
should have my electrician fix it. My electrician looked at it but had to
order the appropriate parts so he did not fix it. (The wire is aluminum, going
into the box, and the wire exiting from the box and going into my house is
copper. The wires are joined in the meter box with a device which clamps each
piece and serves as a connection. The correct procedure is to apply a special
paste (Penetrox?) on the wires to prevent corrosion. This was not done 17 years
ago when the house was built.)
The electric company removed both wires from the very corroded clamp and the
wire hidden under the clamp was in very poor condition. They cleaned the wires
with a stiff metal brush and then created a fairly solid, but temporary, jump
between them. The jump apparently violates electrical codes for permanent
connections but they are allowed to make them for emergencies. They are also
not supposed to fix any connections belonging to the customer (rather the
customer's electrician is supposed to do this under their direction); however
this can be waved in an emergency if the customer is willing to assume any
liability (which I was). I still have to get my electrician to make a
permanent connection with the proper clamp.
We went back into my house and started the dryer which no longer caused the
lights to dim on start-up. They explained to me that the dimming was
previously caused by the dryer motor (at 110) rather than the dryer heater
resistance (at 220). The "definitive" test they suggested is to run the washing
machine in spin cycle; this worked fine with no lights dimming. They came back
this morning to remove their recording meters and everything appeared fine.
In summary, I have probably had this problem for the five years I lived in the
house. The dynamite blasts for the sewer construction most likely caused
vibrations that made a loose connection(s) much worse. As I understand it, the
grounding load is supposed to be distributed 50-50 between the neutral at the
service panel and the water pipe ground; my corroded/loose neutral connections
threw this into a very unbalanced (20-80?) state. Since I was the only
one in the neighborhood to suffer any damage, the disconnection-reconnection
of my neighbor's ground appears to have further upset this condition but
did not harm his appliances (his lights don't dim so his neutral is probably
fine). Note: dimming lights don't automatically mean you have a poor neutral,
it is also a function of the service rating and distance from the transformer.
Since I have 200 amp service and the transformer is in front of my house,
dimming lights did, in fact, indicate a problem.
The connection at my circuit breakers is something I could check every couple
of years; however, how often do you remove your electric meter to check
the connections there? This problem would not be recognized until you ran into
a problem like mine, or worse yet, a fire.
I also feel that the electric company really did a super job in helping me.
The connections behind the meter and at my service panel are legally my
responsibility, not theirs. They could have just diagnosed a potential
problem and come back after I had fixed it.
I think I'll log off and plug in the rest of my appliances. Ready Kilowatt
and Mr. Light Bulb are my friends, once again!
mike
|
291.5 | Wiring a three-way switch | DSTAR::SMICK | Van Smick | Fri Oct 24 1986 11:16 | 24 |
| I have a basic electrical question.
What is the proper way to wire a light when I want two switches able to
control it? I know this is frequently done -- for instance at the
top and bottom of a stairway. You can turn on the light at the bottom
and turn it off at the top, etc.
------------
-------- | light | --------
|switch| |__________| |swtich|
-------- --------
---------
| power |
| panel |
--------
I have done simple wiring before, but this one eludes me!
Thanks for the help.
VCS
|
291.6 | | LATOUR::KILGORE | Wild Bill | Fri Oct 24 1986 11:35 | 28 |
|
14/3
,----------------------------------------------.
| ------------ |
-------- | light | --------
|switch| 3-way |__________| |swtich| 3-way
-------- | --------
| `-----------------'
| - 14/2 14/2
---------
| power |
| panel |
--------
The logic looks like this:
| 14/2 | 14/3 | 14/2
white---------*-------------------------*--------------------------*----.
|
load
,-*--------black-------*-. |
black------*-' `-*--------black-----------*----'
*---------red--------*
The light is on. If either of the two switches is moved to the red wire,
the circuit is broken. To relight the light, either that switch must be
moved back to the black, or the other switch moved to the red.
|
291.7 | Here It Is | STAR::SWIST | Jim Swist ZKO1-1/D42 381-1264 | Fri Oct 24 1986 11:36 | 12 |
|
o-----(Black)--o
Power (Black)-----------o o-----(black)---LIGHT
o------(Red)---o
(White)------------------------------------------------FIXT
(Tough to draw switches). You need single pole double throw switches.
The left end of the left-hand switch, and the right end of the
right-hand switch as shown above go to the terminal labeled "COMMON"
on each switch.
|
291.8 | | LATOUR::KILGORE | Wild Bill | Fri Oct 24 1986 12:07 | 24 |
| You can also add more switches, as shown below:
white---*--------------------------*-------------------------*---------
(B) (A) (C)
(A) ,-*--------black-------*-. ,-*--------black-------*
black-*-' (C) (B) X (D) ,-*--black
*---------red--------*-' `-*---------red--------*-'
3-way 4-way 3-way
The "3-way" and "4-way" should probably be translated into "3-pole"
and "4-pole". A nornal light switch has two poles, which are either
connected or not. A 3-way (3-pole) switch has three connections, and the
input connection (A) is always connected to one of the output connections
(B or C). The 4-way (4-pole) has four connections; in one position, the
connections are (A-D) and (B-C), and in the other position, the connections
are (A-C) and (B-D).
More 4-way switches can be added to the above circuit, as long as they are
between the 3-ways. I've used the three-switch setup, with the first switch
at the bottom of the stairs, the second at the top, and the third at the
other end of the upstairs hallway - I have yet to see a situation that calls
for more than three.
|
291.9 | THANKS! | DSTAR::SMICK | Van Smick | Fri Oct 24 1986 12:19 | 3 |
| Thanks for the information. I'm all set now!
VCS
|
291.10 | Helpful Book | OOLA::OUELLETTE | Roland, you've lost your towel! | Fri Oct 24 1986 16:20 | 7 |
| Mass Hardware in Acton carries a wonderful little book with all
the wiring help you could ever want. It's called something like
"Electrical wiring for Home and Farm Simplified". The book
claims to conform to the latest national wiring standards and is
in it's 37th edition. For $2.95 you can't go wrong...
R.
|
291.11 | 4-Pole... 'I'll order it for you if...' | NETCOM::HARRIS | Mark Jay Harris, Term Srvr Mktg Mgr | Fri Oct 24 1986 20:12 | 6 |
| The real question is FINDING 4-POLE switches!!! Try it. I have yet
to
find a retailer that carries it IN STOCK!
Mark
|
291.12 | | REGENT::GETTYS | Bob Gettys N1BRM | Sun Oct 26 1986 00:56 | 4 |
| That's the sort of thing that you go to your local
electrical supply house for.
/s/ Bob
|
291.13 | Go to an elec. supplier | DRUID::CHACE | | Mon Oct 27 1986 15:42 | 4 |
| Spag's has (had) four pole switches, as so does Maynard Supply
on Rt.62.
Kenny
|
291.14 | | OOLA::OUELLETTE | Roland, you've lost your towel! | Mon Oct 27 1986 15:46 | 6 |
| re: .5
The book's title is "Wiring Simplified".
It's in its 37th edition.
R.
|
291.15 | 4-pole switches at Spag's still. | CLOUD::SHIRRON | Stephen F. Shirron, 223-3198 | Mon Oct 27 1986 16:58 | 2 |
| I bought a 4-pole switch at Spag's last week ($6.50 or so). I had
to ask at the Electrical Department (they kept them in the back).
|
291.16 | There's lots of variations | BEING::WEISS | Trade freedom for security-lose both | Tue Oct 28 1986 10:58 | 29 |
| By the way, for ease of wiring, you always need a 14-3 wire between the two
switches, but you can run the power into either switch box or the light box,
and if you run the power into a switch box you can run the 14-2 wire to the
light from either switch box. For example, if you run the power to the light:
Switch Switch
+-------+ +--------+
| | White | |
| o-+-----------------------------------------------------+-o |
| o | Red | o |
| | o-+-----------------------------------------------------+-o | |
| | | Black | | |
| | ,-+-----------------------------------------------------+----' |
| | | | | |
+--+--+-+ +---------+ +--------+
| | Black | | Black
| `----------------------+---------+-------- Power in
`-------------------------+---, ,--+--------
White | | | | White
+---+--+--+
| |
Light
With a few minutes and a piece of paper it's easy to figure out the other
variations. Also, note that if you are using 14-3 wire, the circuit should
only be a 15 amp circuit (which most lighting circuits are). If it's on a 20
amp circuit, you should use 12 guage wire.
Paul
|
291.17 | Variation: light between switches | NOVA::PAL | Paul Lemaire | Tue Oct 28 1986 13:08 | 15 |
| Here's the variation for the author's problem (light between the switches).
'W/tape' means White wire with a band of black electrician's tape at both
ends (to signal that this is a 'hot' wire)
B
B o----------------------------------------------o
----------o R o-----|
o----------------------------------------------o |
W W W/tape |
-------------o-------------------| |-------------------------------|
| |
W | | B
light
|
291.18 | Dim Wit? | WFOVX3::CRABTREE | | Thu Oct 30 1986 10:21 | 6 |
|
Now the next question is: "Where do you add a dimmer to any of the
above circuits and do they have 3-way dimmers?"
John
|
291.19 | HELP! ...The story continues. | DSTAR::SMICK | Van Smick | Thu Oct 30 1986 10:39 | 20 |
| As the author of .0:
Thanks for all the help on the wiring. I put in the 14-3 and the
swtiches -- and it works!
PROBLEM:
Even though I put the fluorescent lights on a separate circuit, they
dim when other appliances in the house come on. Why?
This is a 2 year old house. Originally, the basement had standard
incandescent lights on a circuit with the freezer and other appliances.
These lights (as well as others which may or may not have been on the
same circuit) dimmed when some of the appliances started. So, I ran a
new circuit -- complete with a new 15amp circuit breaker to make sure
the new fluorescent lights would not dim. But they do.
Any ideas on what is wrong?
|
291.20 | | VINO::KILGORE | Wild Bill | Thu Oct 30 1986 11:04 | 6 |
| re .13
Yes, 3-way dimmers are available, in most department stores (and
surely Spag's). You put a single dimmer at either end of the
run of switches. Unfortunately, you can only control the brightness
from that end.
|
291.21 | | FURILO::JOHNSON | Peter Johnson | Thu Oct 30 1986 11:41 | 19 |
| Just a piece of info for those of you who have to control/dim lights from
several locations for convenience. I use BSR x10 modules in my house and
with control consoles located in strategic locations I can control circuits
anywhere in the house. Its especially nice at night in a multi-story
house to hit the all-off button and all my lights go off - or in an emergency
you can hit all on and all the lights come on. The original reason I got them
was so my wife could turn the outside floods on from the upstairs master
bedroom. Now were addicted - we can control the whole house from anywhere.
Additionally I have a timer module so I can have any ligths come on at
any time for security or other reasons - like coming home to a house with
some lights on when you drive home in the dark.
As for dimming. Putting devices on a separate service is not necessarily
going to eliminate such a problem. It depends on what your house wiring
and service back at the box looks like. When a large appliance goes
on (one with motors) a large surge current can and does cause a momentary
voltage drop coming into the house. This voltage drop can and does get
reflected on house branch circuits especially if the devices on these
circuits are very voltage sensitive.
|
291.22 | MORE INFO? | DSTAR::SMICK | Van Smick | Thu Oct 30 1986 11:52 | 20 |
| RE: -.1
> It depends on what your house wiring and service back at the box
> looks like.
Can you elaborate on this? This is a new house and I assumed it had
adequate service.
> This voltage drop can and does get reflected on house branch circuits
> especially if the devices on these circuits are very voltage sensitive.
1. Are fluorescent light fixtures "very voltage sensitive"?
2. Are lights on a dimmer switch which have been turned down to a low output
level "very voltage sensitive"?
Do you know of any "cure" for the situation?
Thanks, VCS
|
291.23 | Source for BSR-10 | 6910::GINGER | | Thu Oct 30 1986 14:23 | 13 |
| re .16- the BSR system 10
I agree they are a real great gadget. I didnt buy one because they
were a bit expensive. Last year DAK- a catalog company that sells
electronic stuff was selling the controller for $9.90, plus a couple
bucks shipping. They had the simple controller and the fancy
programmable timer controller and several of the optional device
controllers all at similar savings. I just got a catalog from them
a couple weeks ago and noted they still had them listed. Unfortunately
I threw the catalog out so I cant give you an exact address or current
price.
|
291.24 | Juice lost in sauce! | NETCOM::HARRIS | Mark Jay Harris, Term Srvr Mktg Mgr | Thu Oct 30 1986 14:31 | 20 |
| If you are having a dimming effect on one circuit when an appliance
on a TOTALLY different circuit is switched on... then you have
feeder problems.
1. Check overall box loading. If you approach the box limit
for appliances ACTUALLY in use, then you ned more
AMPS from the street. (Not usually the case as boxes
are typically calculated properly by a good electrician.)
If you DO NEED more amps from the street... look out!
the power company gets real picky about what they can
and can not do, and what it will cost YOU to upgrade!
2. Have a qualified electrician check the MAIN feeder connections.
If you have a dimming effect, power is being lost
somewhere. If the connections are faulty, the actual
joint will take some power (and heat up in the process!)
mark
|
291.25 | I wish the programming was easier | ZEPPO::SULLIVAN | Spontaneity has a time and place | Thu Oct 30 1986 16:50 | 9 |
|
Let me add to the recommendations for the BSR units. I use them
to control several lights/appliances in my house. They are getting
cheaper too. BTW, Radio Shack and Sears sell them under their brand
names. Usually one of them is having a sale (plus DAK). Sears seems
to be the only one who makes a three way wall switch unit.
Mark
|
291.26 | Voltage Sensitive Lights.... | SAVAGE::LOCKRIDGE | | Thu Oct 30 1986 17:35 | 17 |
| RE: .17
> 1. Are fluorescent light fixtures "very voltage sensitive"?
I have several (like six or seven) fluorescent lights in my shop,
a few of which were VERY cheap ones ($9.00 each or something like that).
Those lights are VERY VOLTAGE SENSITIVE. The better lights (in the
range of $20 each) do not show the problem nearly as much. My drill
press and band saw are on the light circuit as they have lights
on them I always forget to turn off. Everytime I start the drill
press, the cheap light just about go out - well, a slight exaggeration,
but they do dim quite a lot. The good ones hardly blink. It probably
depends on the quality of the ballast used. I also have on in my
organ that is "All solid state", which I guess means that it doesn't
have a ballast in it and it hums like hell. A little 60hz noise
I can deal with but this too much!
-Bob
|
291.27 | | FURILO::JOHNSON | Peter Johnson | Thu Oct 30 1986 19:25 | 17 |
|
> It depends on what your house wiring and service back at the box
> looks like.
> Can you elaborate on this? This is a new house and I assumed it had
> adequate service.
I suppose I should ask exactly what is going on which causes your lights
to dim. Large motor devices (like well pumps) draw large surge currents
momentarily so a voltage drop can be seen especially if you are at the
end of the line from where the power source is for your house (power
source being the reduction tranformer). To give an example an RA disk
drive can suck 36 amps at 120 volts. Usually the dimming would/should
be very momentary. What's the service into your house, how far from
distribution tranformer?
-peter
|
291.28 | THE SITUATION | DSTAR::SMICK | Van Smick | Fri Oct 31 1986 10:59 | 31 |
| RE: -1
The service is 100amp, and I do not know how far I am from a
distribution transformer. I am not in a development, nor at the
end of a street, so I would guess that there is a transformer within
a reasonable distance.
As for what is going on, the lights have done a momentary dimming when:
1 This morning I know that the furnace was on (FHA-oil) as well as
the water heater (Elect).
2 Last night I know that the furnace and hot water heater were off,
and the refrigerator kicked in.
3 Night before last (furnance & water heater off) when the large
upright freezer kicked in the lights dimmed momentarily and then
flickered for several minutes.
Based on all the information I have received thus far, I would guess
that the problem is caused by:
a. The cheapness of my lights (Channel $10)
b. The 100amp service my house was wired with
Any other thoughts?
Thanks
VCS
|
291.29 | | RENKO::JOHNSON | Peter Johnson | Fri Oct 31 1986 11:34 | 24 |
|
> a. The cheapness of my lights (Channel $10)
> Any other thoughts?
Forget the flourescents for the moment. What do the incandescents show.
If you can hang an incandescent off the same circuit this will give a
much more reliable indication (visually) of what's happening. The light
from the incandescent will reflect better the volatage fluctuation. If it
dims momentarily (we're talking less than 1/2 second here - and the dimming
is just) then I should think this would be ok. If its much longer or much
dimmer then the service box, feed and branch circuits bear a little closer
inspection. Closer inspection means looking at the mechanical connections
making sure everything is tight can clean. How old are the circuit breakers?
Maybe one is old and is not giving good connection. Turn them on and off
several times to cause contact wiping. Next step would be to look at
actual current draw and voltages. This would require an amp probe and
voltmeter.
-peter
|
291.30 | Check the drops across the connections/breakers. | NETCOM::HARRIS | Mark Jay Harris, Term Srvr Mktg Mgr | Fri Oct 31 1986 12:11 | 29 |
| I too say forget the 'cheapness' of the lights. That should NOT
be an issue.
One trick I learned is as follows: (This MUST be done with caution)
Using a standard AC voltmeter, press one probe into the main feeder
line. (there should be 3 wires coming into your house which produce
basically two separate 'legs' for your breaker box.)
Determine which appliances turning on cause the problem and find
the breaker that is supplying it.
Press firmly one voltmeter probe into the FEEDER lead at the TOP
of the first connection to the box. (Wire is probably 1/2" in diameter
so look for that on the TOP of the box. Press into WIRE not after
connection point!)
Press the other probe into the BREAKER screw connection feeding
the leg in question.
If the appliance kicks on, you should see VERY little voltage
present if everything is ok. (actually ideally ZERO, but in reality
a breaker will take a few volts in the element within it)
IF THE VOLTAGE IS ANYTHING MORE THAN A FEW VOLTS... check connections,
check breakers, check wires that have been nicked, etc.
Mark
(BE CAUTIOUS IF YOU DO THIS!!! LOTSA AMPS IN THAT BOX!)
|
291.31 | Two More Cents | FSTVAX::HARDEN | | Fri Oct 31 1986 16:21 | 28 |
| Your problem sounds very familiar to me. I had the flickering lights
problem for quite some time before isolating it. I suspected the
power company was causing it due to the time of day I noticed it,
early AM. I thought maybe they were throwing some big switches or
something as the demand increased.
I checked with some neighbors as to whether they were experiencing
any of this, of course they weren't, so then I got real curious
and worried about my electric service.
I isolated the problem by waiting until the flickering came up again
and went down to the service panel, took off the cover and just
looked and listened.
What I found was the connection from the main to the circuits was
loose on one leg and the flickering lights was caused by the arcing
across the on again off again gap.
The solution was simple, VERY CAREFULLY, WITH ONE HAND IN YOUR POCKET,
WEARING RUBBER SOLED SHOES, reach in with a screw drive and tighten
the screw.
Loose electrical connections can/will cause fires. God knows how
long this problem existed in my house, it's 40 years old.
Careful and happy hunting,
-boB
|
291.32 | Basic wiring questions | AMULET::FARRINGTON | statistically anomalous | Mon Nov 17 1986 12:23 | 27 |
| A new (Cape-style) house with unfinished 2nd floor & basement...
I am about to embark on wiring the upstairs. My thought was to
use 12/2 wiring for plugs/lights. However, when I examined the
wiring left by the builder for the connections to the power box
(in basement) he used 14/2.
Question - which alternative is recommended ?
1. continue 14/2 usage.
2. install at junction/connection 12/2.
3. reroute 12/2 to the box in basement.
Also, I had hoped to run a separate circuit to the bathroom but
only two circuits are terminated to the 2nd floor. Should I -
1. connect ground-fault plug to the 1st floor plug,
or install a second circuit.
2. split the bathroom between the two circuits.
3. is it worth the effort to drop a third line to the
power box.
Any input would be appreciated; I'm not very confident in this area...
Dwight
|
291.33 | | VINO::KILGORE | Wild Bill | Mon Nov 17 1986 12:43 | 22 |
| Two circuits are enough for the upstairs of a normal-sized cape,
and 14/2 is sufficient, unless you're planning to put a shop or
a 5-kw. ham transmitter up there.
Put the bathroom at the end of one circuit. Place a GFCI/outlet
unit in the first box, then wire the rest of the bathroom (including
light and switch) from the LOAD side of the unit. That way, the
entire bathroom is protected, and only the bathroom.
Use the two circuits so that if one trips, you can still find your
way to the stairs with light from the other (eg, you might want
to supply the hallway light from one circuit, and put an outlet
in the hallway from the other circuit, into which you can plug a
night/emergency light).
To keep voltage drops to a minimum, use the screw connections on
the sides of outlets, and not the slip-in connections on the back.
For more home wiring hints, see "Home Wiring Simplified" (or something
like that, available in electrical dept. at Spag's), or hardcover
books from Readers Digest and Home and Garden, available at libraries
and book stores.
|
291.34 | It depends on the amperage of the circuit | BEING::WEISS | Trade freedom for security-lose both | Mon Nov 17 1986 12:54 | 9 |
| In general, 14 gauge wire is used for 15 amp circuits and 12 gauge wire is used
for 20 amp circuits. If by any chance the 14/2 wire is attached to a 20 amp
breaker, you should probably change the breaker to 15 amp, since I believe that
it's a fire hazard to send 20 amps through 15 gauge wire.
Which you decide to use depends on the size of the circuit, but whichever way
you go, match the wire to the breaker.
Paul
|
291.35 | | ULTRA::PRIBORSKY | Tony Priborsky | Mon Nov 17 1986 13:37 | 23 |
| First, .-1 is right: the 14-gauge wire is for 15-amp max. If
you continue from the drop your builder left you with 12 gauge,
think of the 14 gauge as a fuse (that is, don't do it). The maximum
capacity of the circuit is the smallest capacity item on it - that
is normally the circuit breaker. If you run a 20-amp breaker,
to 14-gauge wire, and then continue with 12 gauge wire, you've got
a 15 amp circuit, and a good chance of a fire. DON'T DO IT.
It may also be against code (the code generally "makes sense" and
this doesn't make sense.)
The recommendation about the GFCI is also correct. You can get
the GFCI outlets at almost any hardware store, and I'm sure Spags
has them too. If you have a dedicated breaker in your panel, and
you can "find" that circuit, then there is ample capacity to handle
one more bathroom (those circuits handle the kitchen (most likely
some but not all, probably the ones around the kitchen counter) and
the other bath. If you can't locate the circuit from upstairs
(I couldn't, it was too far away), the outlet-style ones will be
enough. Also, my inspector exempted the bathroom lights from the
GFCI protection. Also note that connecting the convenience outlet
on a medicine cabinet is against the code. They are generally
two-wire outlets and thus can't be connected to the GFCI to give
the right protection.
|
291.36 | | ULTRA::PRIBORSKY | Tony Priborsky | Mon Nov 17 1986 13:39 | 10 |
| Another recommendation: Do get a permit and have it inspected.
I had to have my inspection before I put up ANY insulation - all
wires must be visible. And, use insulated staples. The books
mentioned earlier describe the maximum number of wires you can have
in any single outlet box or junction box - adhere to them. Make
sure you don't cross your hot/ground (keep the black wire connected
to the black wire throughout) as the final inspection (hot wire
test) will insure that the polarity is correct on all outlets.
They will also test the GFCI, and you must tell the inspector what
outlets are on the load side of any outlet-type GFCI protector.
|
291.37 | Avoid GFCI circuit breakers | ALEX::CONN | Alex Conn, ZKO | Mon Nov 17 1986 13:44 | 7 |
| Another point: Do *not* use a GFCI circuit breaker at the box.
My electrician says they are expensive, often fail to work right
out of the box, and are not worth the trouble. Use the outlet type--
they only cost $10-15 and can be used to protect a number of outlets
in a chain.
Alex
|
291.38 | price question | EXODUS::SEGER | this space intentionally left blank | Mon Nov 17 1986 13:50 | 5 |
| Are you sure on that $10-$15 price tag? I bought one at Spags 5 years
ago for $20 and felt like I got a bargain because everywhere else wanted
over $30! Have prices on something finally come down?
-mark
|
291.39 | | VINO::KILGORE | Wild Bill | Mon Nov 17 1986 14:27 | 21 |
|
re .6
Yes, GFCI outlet devices have come down quite a bit in price. The
one I bought at Spag's eight years ago cost me $27, and now I can
find them for $10 on sale in department stores (even Sears stocks
them at $16). They are a much better buy than the panel GFCI breakers,
and seem to be much less prone to lightning suicide.
re .3
Assuming that the electrician knew his job, there is a 15-amp breaker
at the other end of each 14/2 wire that he ran to the second floor.
Extending the circuit with 12/2 does not violate any code in that
case, as the circuit is still protected in accordance with its
weakest link. For long-haul circuits, it sometimes makes sense to
use a heavier wire than minimum to decrease line voltage drop. However,
I would not classify a normal circuit in a two story house as long
haul, and in any event running 12/2 for the second half would not
gain enough in reduced line loss to justify the cost in materials
and decreased wire counts in the boxes.
|
291.40 | ??? on .1 and quick connects | SWTPEA::COUTURE | | Mon Nov 17 1986 15:04 | 11 |
| I have a question about something that was mentioned in .1.
Is it better to attach the wire to the sides of the outlet,
instead of the quick connects? If so, Why and What are the benefits?
I've always used the quick connects and not have have any problems
but maybe I should start using the sides. I guess quick connect
= Easier + Me taking the easy route..
Thanks
|
291.41 | Use the screw terminals | BEING::WEISS | Trade freedom for security-lose both | Mon Nov 17 1986 16:19 | 23 |
| The problem with the quick connects is that the point of contact to the wire is
quite small. There are (I think) two metal plates angled together like a V,
and the wire slips between them, with the V preventing the wire from being
pulled back out. The only point of contact is where these plates hit the wire,
and that's usually with only an edge of the plate:
\ \ | | / /
\ \ | | / /
\ \ | | / /
\ \| |/ /
\/| |\/
|_|
This is at least an order of magnitude smaller than the contact area of a screw
terminal. I know of at least one case where the connection in a quick connect
has failed altogether. If you think of a large circuit, the current must go
through a series of these to get to the last outlet, and this can cause a
significant voltage drop. It might not be much of a loss to use the quick
connects on the last outlet, but terminating outlets are easy to wire anyway.
It takes a little longer, but I always use the screw terminals.
Paul
|
291.42 | | VINO::KILGORE | Wild Bill | Mon Nov 17 1986 16:46 | 3 |
|
.9 was on the money. I have traced a multitude of wiring problems
to use of the slip-in connects (not in MY house, of course ;-).
|
291.43 | | OOLA::OUELLETTE | Roland, you've lost your towel! | Mon Nov 17 1986 19:39 | 9 |
| re: quick connection stories
I had 2 intermittent open circuits because of them. I think that
quick connections exist so that contractors don't have to pay
electricians to do the job right.
__Never__ use quick connections with Aluminum wire!!!
R.
|
291.44 | While you are still planning ... | PAXVAX::NAYLOR | Mark E. Naylor | Tue Nov 18 1986 01:06 | 8 |
| While you are in the planning stages for the wiring, you may
want to plan for a future room air conditioner. If there is a
window where you think you may install an air conditioner, you
may want to run a separate circuit to an outlet below that window
so that the AC will have its own circuit.
Mark
|
291.45 | AL wire and screws... | SAVAGE::LOCKRIDGE | | Tue Nov 18 1986 18:01 | 16 |
| RE: .11
> __Never__ use quick connections with Aluminum wire!!!
This may be true with fixture for CU wire (which should NEVER be used
with AL wire anyway), but AL fixtures have just that type of
connections - to keep constant pressure on the wire. The problem with
AL wire is that as it oxidizes, it gets smaller in diameter. With a
screw connection, this can lead to a loose and hence dangerous
connection. The 'quick type connection' keeps constant pressure on the
wire as it gradually gets (minutely) smaller.
Just thought you'd like to know.
-Bob
|
291.46 | More free advice | NOVA::PAL | Paul Lemaire | Tue Nov 18 1986 20:45 | 33 |
| The same electrician who told me never to use quick-connects also
told me to avoid wiring through outlets. That is instead of using
the receptacle to splice the circuit like so:
----------------------- ---------------------------
S _____ \ / _____
o / __ \_@__@_/ __ \ to other
u | o o| outlets
r \ -- /-@--@-\ -- /
c ----- / \ -----
e / \
---------------------/ \------------------------
Do it this way:
splice
----------------------\---------------------------------
S _____ \ _____
o / __ \_@__@_/ __ \ to other
u | o o| outlets
r \ -- /-@--@-\ -- /
c ----- / -----
e /
---------------------/---------------------------------
The reasons are:
- If ANY screw works loose in the wire-thru method, you get problems
all the way down the line (no, the gremlins don't loosen them,
you do when you're wallpapering or whatever).
- Those little break-off bars between the screws don't have to
carry the current for the whole circuit.
|
291.47 | More more free advice | CADZOO::HARDING | | Thu Nov 20 1986 16:24 | 18 |
| SInce I just had my final inspection done on my wiring heres
my two cents worth. On several of my outlets I used a type
that you could insert from the back then by tighting the
screw on the side the wire was clamped to the outlet. It
met code but the inspector wasn't pleased. The reason was
that there was more bending of the wire when the outlet
was pushed into the box when it was inserted from the back
then when put on the screw on the side.
Adding a little thought to that one could see that with straight
push in there could be more pressure put on the contact points
causing the wire to pull out. The other is that if one did
not push the wire in far enough or the wire started pulling
out there will be some bare wire showing. This could cause
a intermitten short.
dave
|
291.48 | On wriring sockets | DSSDEV::REINIG | August G. Reinig | Sat Dec 06 1986 18:04 | 24 |
| re .14
First, I find your drawing a little confusing. What do you mean
be source. Wouldn't it be better to label it like so?
black black
----------------------- ---------------------------
_____ \ / _____
/ __ \_@__@_/ __ \
| o o|
\ -- /-@--@-\ -- /
----- / \ -----
white / \ white
---------------------/ \------------------------
Is thre any reason to go through the house and make the changes
in the wiring your friend suggested? Finally, should the splice
go to of the live screws on the outlet or is the power drop over
one of the tabs inconsequential and it's only when power passes
through several tabs that the loss becomes noticeable.
August G. Reinig
|
291.49 | Didn't know there was such a thing | SUPER::MATTHEWS | Don't panic | Sat Dec 06 1986 18:30 | 5 |
| Is there any way to tell whether an existing panel breaker has a
GFCI?
Val
(also doing bathroom wiring)
|
291.50 | Without a GFCI label, assume it's not | ALEX::CONN | Alex Conn, ZKO | Sun Dec 07 1986 01:48 | 5 |
| I believe the panel breakers have the same test feature as the outlets
(you're supposed to push test once a month to see if the ground fault
portion is working properly). I believe that the affected outlets
would be labeled as well. GFCI breakers are rare in most houses. Due
to cost and reliability, most builders opt for the single-outlet types.
|
291.51 | GF breakers | RINGO::FINGERHUT | | Sun Dec 07 1986 20:51 | 2 |
| I have a GFCI breaker. It's as you described.
|
291.88 | Wiring for a motor | BCSE::SPT_LEPAGE | | Mon Dec 08 1986 16:00 | 11 |
| I've recently 'liberated' a motor from a dishwasher we replaced.
I'd like to use this motor for something, since it does work OK.
(I'll probably get something like a belt sander or lathe from AMT,
they sell their tools without motors). Anyway, this motor was wired
to a 110V line, and has 4 wires coming from it - black, white, yellow,
and red. My question, for you electrical types, is how would I
wire this up to a standard 3-prong plug so I can use it? Thanks
in advance for any help.
-Mark LePage
|
291.89 | If its not at least 1/4 HP forget it. | 15476::HARDING | | Mon Dec 08 1986 18:00 | 5 |
| Before you decide to use it for anything check out the HP of the
motor. A lot of diskwasher motors are less then 1/4 HP. If it
is, junk it. Its not worth using. Also some of them are two speed.
dave
|
291.90 | Just a thought... | JOET::JOET | | Thu Dec 11 1986 10:58 | 4 |
| Most (all?) dishwasher motors are bi-directional. One direction pumps
the water through the spray arms, the other pumps it out the drain.
-joet
|
291.91 | Oh yea, the h/p rating | BCSE::SPT_LEPAGE | | Thu Dec 11 1986 11:22 | 6 |
| The point in .1 (horespower rating) is one I had forgotten about.
I took a look at it last night, but can't find any h/p rating on
the plate with the other standard info. The motor will certainly
need to produce 1/2 h/p or more, so maybe this 'project' isn't worth
it. An underpowered tool probably wouldn't be much good.
|
291.98 | Wire through kitchen vent, and cut stud | MIZZEN::DEMERS | Chris DeMers Worksystems | Wed Feb 11 1987 10:57 | 14 |
| The saga continues. After some good replies to my questions on
kitchen subfloors, etc. I am well on my way to a new kitchen. As
part of the "package", the installer is putting in the exhaust vent
from the stove to the outside. When he got to the wall he encountered
a stud (just about dead center) and a wire. Jogging around the
stud would have been difficult because of lack of room, so he cut
it. I guess I can live without one stud. Anyway, the wire is a
different story. He notched the end of one of the vent pieces and
slid it over the wire. Now I have a wire running through the exhaust
vent. Is this legal? Will the wire deteriorate? Should a conduit
surround the wire as it passes through?
Chris
|
291.99 | Doesn't sound too good | LIONEL::BRETSCHNEIDE | Crazy Hawaiian DTN 289-1604 | Wed Feb 11 1987 11:23 | 8 |
| I had the same problem, except that I AM doing it myself. I boxed
in the area which will contain the vent and rerouted the wire.
I can't see how it would or could be legal to have the wire run
through the vent area. There should at least be a grommet over
the wire at each edge of the vent to protect it from chafing on
the edge of the sheet metal. (Just my $.02 worth)
bb
|
291.100 | | VINO::KILGORE | Wild Bill | Wed Feb 11 1987 11:40 | 9 |
| I wonder it it's breaking some obscure code? When wiring is
specifically installed in ductwork (using the ductwork as a convenient
wiring route), the wire must be encased in a metal conduit, or it
must be certified as low-smoke-creating (in case it starts to burn).
Certainly the spirit of the code is not being violated in ypur case
(since the duct only vents to the outside) but you may be inviting a
future technicality hangup.
The point about possible chafing is also well taken.
|
291.101 | Geez, what some jerks will do | BEING::WEISS | Trade freedom for security-lose both | Wed Feb 11 1987 12:43 | 11 |
| In this case, who cares about code? It is certainly not unheard of to have all
the grease that accumulates in the vent catch fire. That's why they have to be
metal. Aside from the fact that such a fire would quickly remove any
insulation from the wires, it can also escape into the wall cavity through the
hole that the jerk cut in the vent. It's plain unsafe, code or not.
Tell him, in no uncertain terms, that his solution is completely unacceptable,
that he has to buy a new vent to replace the one he cut, and he has to either
move the vent or the wire.
Paul
|
291.102 | common sense leads automatically to code | AMULET::YELINEK | | Wed Feb 11 1987 13:23 | 1 |
| Have to agree.....
|
291.103 | Your insurance adjuster won't like it...after the fire | SEESAW::PILANT | L. Mark Pilant | Wed Feb 11 1987 14:15 | 22 |
| The National Electrical Code has a good deal to say about wires
passing through hazardous and harsh environments. (I would certainly
consider an oven/range vent to be a harsh environment.) To comply
with the current code, it is usually necessary to use special cable
and/or supply conduit for the cable to run in.
From your description of what was done, I would say that the work
was in violation of the electrical code. (It might also be useful
to indicate who did this, so that other of us will know to stay
clear.)
I would also second the suggestion that you get the installer to
fix the problem correctly. You should probably also consider
with-holding payment until this problem is fixed. IT IS MOST CERTAINLY
A DANGEROUS SITUATION.
- Mark
BTW: I had the pleasure of reading through all 600 some odd pages
of the 1984 code (1987 version isn't out yet) when I installed a
new service panel in my house. (I went from a 100 amp fuse panel
to a 200 amp breaker panel.)
|
291.104 | | CAD::VANNOY | | Wed Feb 11 1987 15:24 | 8 |
|
I agree. Common sense should tell you, you are
asking for trouble. I usually do my own work when
possible, simply because I sleep better at night know-
ing it's done right. In your case, I wouldn't get
much sleep!
/Derrick
|
291.105 | | VIDEO::DCL | David Larrick | Wed Feb 11 1987 15:46 | 15 |
| I agree with the preceding replies; the installation as stands doesn't
sound safe, and almost certainly doesn't meet code. If you need a specific
code reference, ask for it here and we code-hounds can have a race!
If your contractor doesn't want to fix it, get the town building inspector
and/or wiring inspector involved.
Of course, depending on how your contract is worded, you may have to pay
some extra money to have the wire re-routed properly. The question is
whether the contractor should have reasonably expected to find a wire with
insufficient slack in that wall; it may be a judgement call.
But one reason to pay a pro is so he can take this type of risk, and so
you're sure everything is done safely and to code. Don't settle for
anything less.
|
291.106 | Never time to do it right, always time... | MIZZEN::DEMERS | Chris DeMers Worksystems | Wed Feb 11 1987 16:02 | 22 |
| Well, all's well that...
I confronted the installer and told him that the installation was
sleazeball. He agreed and we worked on a solution. No hard feelings
although I wish he would have filled me in before he made a decision.
We traced the wire and found that it serviced the washer/dryer.
What's strange is that the wire is dedicated (I did an exhaustive
test of all plugs/switches in the house) yet runs up to the second
floor, down through the kitchen wall into the basement and mounts
on the foundation wall. After we convinced ourselves that this
was strange and that the line was indeed dedicated, we clipped the
wire. I'll run a new one downstairs on the floor joists.
This is why I like to do things myself. Unfortunately things like
family, work, time constraints and lack of experience force me to depend on
"professionals". I do go home every night though, look over the
work and say "Is that the way I would have done it?"
Thanks for your replies.
Chris
|
291.107 | 1987 NEC | PAXVAX::NAYLOR | Mark E. Naylor | Wed Feb 11 1987 23:18 | 9 |
| re: .5
The 1987 NEC is out; I have a copy at home. As mentioned in a
previous note, the cost is around $37. However, I found that it
is available in loose-leaf for $24.50.
Mark
|
291.108 | Are fluorescents a fire hazard with old wiring? | HAZEL::THOMAS | No <ESC> from reality | Mon Mar 02 1987 13:49 | 17 |
| After installing a fluorescent light fixture in my kitchen, I noticed a warning
on the box just as I was throwing it away. It essentially says:
WARNING - DANGER OF FIRE. Most homes built before 1985 have wiring rated at
60 degrees C. Consult qualified electrician before installing.
Needless to say, my house is older than that. If there is a real problem,
selling these units for installation in existing homes is ludicrous.
There does not appear to be any temperature marking on the house wiring.
I have since seen other fluorescent fixtures for sale with the same warning
on the box.
What's going on here? Are these things really a fire hazard or are the warnings
the result of an over zealous consumer protection agency run by Ralph Nader?
- Rich
|
291.109 | | CACHE::WHALEN | Why is common sense so uncommon? | Mon Mar 02 1987 14:34 | 12 |
291.110 | | VINO::KILGORE | Wild Bill | Mon Mar 02 1987 15:25 | 24 |
291.111 | Flame seal insulation... | ZENSNI::HOE | | Tue Mar 03 1987 01:41 | 8 |
| wild bill's answer is correct. The wire insulation now requires
the higher temperature. Fiberglas or teflon insulated falls under
the newer code. The fix is to be sure that all wiring *within the
fixture* have the higher temperature rating 90 degree C (which is
almost at boiling temperature).
/cal, an ex electrician who found wiring was too shocking.
|
291.771 | Cleaning up the electrical system of an older house | MORMPS::WINSTON | Jeff Winston (Hudson, MA) | Tue Mar 10 1987 21:12 | 29 |
| We are moving into a place which may need some electrical work - I'm
looking for opinions on what does/doesn't NEED to be fixed, and what
can be done by a DIY'er as opposed to a licensed electrician. The
situation is:
House is 26 years old. Has old style fuses (round screw-in, large
'automobile' type), appears prior owner did some DIY work in the
fusebox. ALL outlets are 2-prong. No outlets in bathrooms (excepting
1 in the light fixture over the mirror, in SOME bathrooms).
Fusebox has 100A coming in, but only 60A service. (Note: my wife uses
1300W hair dryer in the bathroom, and we want to add central A/C)
The EE in me says that the 'RIGHT' things to do are:
1) replace/update fusebox, put in 100A service and breakers.
2) put new service to bathrooms, with GFI
3) put 3 prong outlets everywhere.
Is this all luxury, or a good idea (it does cost $$)?
We also want to:
4) put ceiling fixture boxes in 5 rooms
5) hang a fan from the cathedral ceiling in the living room (can I do
this with ZIP cord?)
6) (maybe) wire external spotlights over garage, out back, etc
Is this DIY or 'electrician' stuff?
thanx /j
|
291.772 | consider 200 amps | CLUSTA::MATTHES | | Wed Mar 11 1987 07:32 | 10 |
| You might consider putting in 200 amp service if you are going to
re-wire. The incremental cost is insignificant compared to wanting
to do it later when you get the arc welder for the garage or some
such. The key word here is RE-WIRE. To go from 2 prong to 3 prong
outlets may mean rewiring the entire house from 2 wire to 3. Can
be done but fishing wires through existing construction can be
painful and the least time consuming.
If you don't put in 200 amp service consider an oversize panel (i.e.
200 amp box) and use a 100 amp main breaker. Change is then minimal.
|
291.773 | Have integrity yourself first | CLUSTA::MATTHES | | Wed Mar 11 1987 07:44 | 21 |
| Just re-read the original note. In Mass. 90 per cent of what you
want to do MUST be done by licensed electrician. If you have the
knowledge or can get a friend to help, you could have an electrician
do the main panel and all the hookups. See if you can strike a
deal with him (or her) that you fish all the wiring. Most electricians
would be willing to do this I expect cause it's a real pain in the
whatsis. It's also very time consuming therefore $$$$$$. You gots
to talk nice though. I once heard of a guy who told the electrician
that he'd hook up the main panel after the electrician had strung
all the wires figuring he'd save himself a day's labor fee. What
the heck all the wires are just dangling there waiting to be dressed
and just 'plugged' into the panel. Well talk to a frien whose wired
houses and he'll tell you that wiring the house is the dog work
and hooking up the panel is the 'gravy'. Well I don't know how
the guy was stupid enough to turn his back on the electrician, msut
have been picking up his tools or something but when he went to
hook up the panel there were no longer any labels on any of the
wires and most if not all were just a tad SHORT.
Moral, when you make a deal with the contractor make an honest one.
What the heck, you expect him to have integrity.
|
291.774 | Wiring | VIDEO::FINGERHUT | | Wed Mar 11 1987 11:21 | 11 |
| > Just re-read the original note. In Mass. 90 per cent of what you
> want to do MUST be done by licensed electrician.
You can do your own wiring in Mass. You don't need a licensed
electrician for any of it.
If your town requires you to have a licensed electrician take out
the electrical permit, then that's probably because your town's
wiring inspector is a licensed electrician and is doing this as
a favor to all the electricians in your area. What town is this?
|
291.775 | more info | ZEN::WINSTON | Jeff Winston (Hudson, MA) | Wed Mar 11 1987 13:14 | 9 |
| Thanks for all the good comments so far......some additional info
I had an electrician look at the job, he tells me that the 3rd wire is
available at all the outlets, just need new sockets.
The town is Sudbury, MA
Extra question: What do you suppose an electrician should charge for
all this, his pre-estimate guess was $1000 - $1500
|
291.776 | You TOO??? | THE780::CHANG | TheFaceOfADragonFlyIsNothingButEyes! | Wed Mar 11 1987 16:39 | 30 |
|
GOSH! Your original note sounds EXACTLY like what we are facing.
Our house is 34 years old, 60amp service, no grounded outlets, old
fabric wrapped wiring, etc...
The estimates that one electrician gave us (another is coming tonight):
Upgrade from 60amp to 100 -- $700
Upgrade from 60amp to 150 -- $870
Upgrade from 60amp to 200 -- $1100 <-- We're thinking about putting
in a hottub. (Oh by the
way we are in California,
Bay Area.)
To ground an existing outlet -- $60 each <-- We aren't fortunate enough
to have the third wire there.
To "clean-up" (work done by the previous owner not to code) -- $200
Install bathroom GFI outlets -- $100 each
Install bathroom fan -- $250 (depending on which fan we choose to
use).
My husband also wants to do some of the work himself. He wants
to rewire the whole house! I don't think it's necessary. I sure
will be interested in the future replys to this note.
-Gina
|
291.777 | | BEING::WEISS | Trade freedom for security-lose both | Wed Mar 11 1987 17:23 | 13 |
291.778 | | AUTHOR::WELLCOME | Steve | Wed Mar 11 1987 17:36 | 11 |
| Ditto on .6 . If you have a specific location where a grounded
outlet makes sense (the garage, maybe) think about getting that
done. But the whole house? Not worth the money or trouble.
A GFI in the bathroom is nice, but the slightest bit of common
sense (don't stand in the shower while you unplug the heater with
wet hands) is just as good. I might upgrade the service entrance
to 100 amps with breakers (200 amp if you have or plan on getting
LOTS of appliances) and let it go at that. The wiring you have is
probably perfectly safe, as is. If/when you discover a real need
for additional circuits or grounding, get that done.
|
291.779 | check your code first | COBRA::DUTHIE | | Wed Mar 11 1987 19:51 | 12 |
| When I checked on changing my house in Littleton, Ma. from 60 to
100 amps, I was told that the code required that the entire house
be brought up to current code standards if the main service equipment
was changed. Are you prepared to re-do the entire house to current
code? (your code may vary... check with the town.)
Also, to change an outlet to a GFI is only about a $10 part (on
sale) and isn't much different than just replacing an outlet. Of
course, the GFI requires a grounded circuit to the box it is going
into.
Jim D.
|
291.780 | BTW | MORMPS::WINSTON | Jeff Winston (Hudson, MA) | Wed Mar 11 1987 20:27 | 1 |
| BTW: Mass codes require all new outlets in bathrooms to be GFI
|
291.781 | | VIDEO::DCL | David Larrick | Wed Mar 11 1987 20:40 | 66 |
| re .4, Sudbury: I heard a rumor that Sudbury is one of the most
restrictive towns around, and requires ALL electrical work to be done by a
licensed electrician. Note that this is a rumor only; please double-check
before you base any decisions on this information!
The Maynard wiring inspector told me that legally I wasn't supposed to do
any electrical work, but that he realized I would probably do it whether he
approved or not, so he might as well issue me a permit and perform
inspections. I said "Yes, sir!", and didn't ask him to quote chapter and
verse.
re .0:
I agree with the other replies: it doesn't sound like any of your proposed
work is critically necessary. Do fuses blow often? Do the lights dim when
you plug in the iron?
You're extremely lucky to have grounded wiring in place. Is it in good
condition?
Start by making a circuit map of the house. Find out which circuit serves
each outlet, fixture, and appliance. You can determine a lot by tracing
the wires through the basement, but verify your work by disconnecting the
circuits one-by-one. Then figure the normal and worst-case wattage load
for each circuit.
If there are unused circuits (fuse sockets) in the fuse panel, or if the
existing circuits have excess capacity, you may not need a new panel.
There's nothing inherently inferior or unsafe about fuses; they're just
less convenient than circuit breakers.
> 1300W hair dryer in the bathroom, and we want to add central A/C
A dedicated circuit with GCFI will handle this hair dryer just fine.
Consider gas A/C?
> 1) replace/update fusebox, put in 100A service and breakers.
> 2) put new service to bathrooms, with GFI
> 3) put 3 prong outlets everywhere.
>
>Is this all luxury, or a good idea (it does cost $$)?
Except to power the A/C, about which I know nothing (I'm originally from
the Washington, DC area; New England summers still don't seem hot to me),
sounds like luxury. Given that you have grounded wiring, 3-prong outlets
are easy and DIY if you're reasonably careful, but I'd still install
3-prong only where specifically needed.
> 4) put ceiling fixture boxes in 5 rooms
Now you're talking ceiling demolition/repair or serious fishing or both.
Unless, of course, there's an unfinished attic above. If you want wall
switch too, see the first sentence.
> 5) hang a fan from the cathedral ceiling in the living room (can I do
> this with ZIP cord?)
I'm not sure what you're talking about, but zip cord doesn't sound kosher.
A ceiling fan needs strong mechanical support, usually a metal rod through
which the wiring runs.
> 6) (maybe) wire external spotlights over garage, out back, etc
Worthwhile, probably DIY, perhaps top priority for all this stuff. Parts
suitable for outdoor use are relatively expensive, and you may again be
looking at some serious fishing and/or demolition/repair.
|
291.782 | Nooooooo problem in Sudbury | DRUID::CHACE | | Thu Mar 12 1987 13:18 | 0 |
291.783 | only kidding folks | KELVIN::RPALMER | Half a bubble off plumb | Mon Mar 16 1987 16:19 | 9 |
291.784 | Do you attach grounding tab on adapters? | WMEATH::KEVIN | | Tue Mar 17 1987 12:53 | 5 |
| re .12 I agree with you that it should have been done right; however,
when was the last time you attached the wire pigtail or tab from
a 3 - 2 adapter to the center screw on the outlet? (if the outlet
box isn't grounded, even doing that doesn't give you a grounded
outlet)
|
291.785 | What's the alternative? | WELFAR::PGRANSEWICZ | | Tue Mar 17 1987 15:49 | 15 |
| RE: .12
I am doing exactly that in my house. First, the old 2 prong outlets
have been painted over (why do people do this???) and second, a
lot of the outlets are just worn out and don't hold the plug like
they should. Oh, and third, do they sell 2 prong outlets anymore?
I can't recall seeing any. I've got plenty to do already, so rewiring
the entire house just doesn't come close to the top of the list.
I know this is the "right" way but I just can't see it. Should
I label the outlets "NOT GROUNDED". As a previous note suggested,
I'm not sure I really need grounded outlets except in the kitchen
and bath (which I intend to re-wire).
Phil
|
291.786 | No easy solution... | BEING::WEISS | Trade freedom for security-lose both | Tue Mar 17 1987 17:08 | 17 |
| > Should I label the outlets "NOT GROUNDED"?
A rhetorical question, I assume. Who wants to have little labels on every
outlet? What I suppose you could do, if you were really worried about it, would
be to buy a length of 1/8" metal rod, cut off a bunch of 1/2" pieces, and shove
them into the ground plug holes. That would prevent anyone from inserting a
3-prong plug, and it doesn't detract from the look of it. Of course, if you
sell the house, the poor sap who buys it won't know anything about it until he
tries to use a 3-prong plug. Due to Murphy's law, this person will not have a
3-to-2 prong adapter, and this will occur at 10:05 on a Friday evening when he
absolutely needs to use this tool to finish some job on the guest room, and
relatives are coming first thing in the morning. Still, I suppose it's better
than letting him plug it in thinking it's grounded and getting a nasty
surprise. But I can just see the reply to note 147: "You'll never believe what
the jerk who owned my house did! ...."
Paul
|
291.787 | No ground? | DRUID::CHACE | | Tue Mar 17 1987 17:40 | 13 |
| Are you sure there is no connection to the ground of the fuse box?
If you have armored cable (BX) then the outer metal jacket should
make a connection between the fuse box and the outlet box. If you
have Romex it should have a ground wire that is connected to the
fuse box and the outlet box. I suppose there may be some very old
wiring that is 2 conductor with absolutly no ground, but this should
be very rare. Knob-and-Tubing wiring does not have any ground, but you
would only find this in VERY old houses (75+ years).
If you have armored cable, a simple pigtail from the new outlet
to a screw in the outlet box should give you the ground you need.
Kenny
|
291.788 | How many wires do you have | KELVIN::RPALMER | Half a bubble off plumb | Tue Mar 17 1987 18:01 | 8 |
|
There IS stuff called two wire romex. It isn't armored cable
and contains no ground wire. It is vintage 1930's. My house is
full of the stuff (except in my shiny new kitchen :^) ). Yes I
also have knob and tube wiring, except I've replaced the knobs with
junction boxes. The stuff still looks and works fine, so I'm in
no hurry to replace it. History of wiring tours will be given upon
request.
|
291.789 | | 3D::GINGER | | Wed Mar 18 1987 01:54 | 5 |
| Two wire Romex is not at all rare. It was the only kind in use
from sometime in the 30's until I think late 50's or maybe even
the 60's. Even in the 60's two wire was still being used in some
cases.
|
291.790 | 2 prong REPLACEMENT outlets | HEADS::OSBORN | Sally's VAXNotes Vanity Plate | Wed Mar 18 1987 14:31 | 8 |
| Re: .14
In Massachusetts, you can buy and use two-prong outlets only as
replacements for existing non-grounded service. So, yes, remove
your painted and worn outlets and install unpainted equivalents.
Hmm ... why is the paint stuck so tightly while the lamp won't
stay plugged in due to gravity?
|
291.791 | Electrics observations | BPOV09::SJOHNSON | Steve | Wed Mar 18 1987 15:33 | 47 |
|
Upon doing some rewiring in my 65 year old 2-family I also found
some electrocution kits. :^) (3rd terminal not grounded)
An easy way to check to see if the 3rd terminal is grounded is to
put a voltage checker(light) between ground and one of the other terminals.
I woundn't bother to replace all your 2 prongers with 3's either,
execpt maybe the kitchen (fridge, microwave, or any number of
modern appliances). I would say that mine are about half and half
right now.
I'm planning in putting in an outdoor outlet too, I'll get plenty
of use out of it, mostly when trimming the hedges. Also for electric
starting snow blowers, or any other work outside needing a power
tool.
I guess the previous owner strung an extension cord out a window.
Not for me! You might want to also.
The wiring schematics for older houses will be quite strange too,
as was mine. You'll probably find that each room has one of it's
outlets tied together on one circuit. In other words you may have
to unscrew 2 or 3 fuses to completely shut down power to a room.
When they upgraded the electrical system, they didn't bother to
consolidate one room on one circuit, just added wiring to what was
already there. Nothing wrong with this, just a little inconvenient
until you've generated the schematic for your house.
My unit has a 100 amp service, which serves my needs fine. The rental
unit has a 60 amp service, but is only using 30 amps of it, there
are two empty fuse sockets in the fuse panel. I plan on tapping
these to add some outlets to the rental. They've blown a fuse once,
when they had their hair curler on at the same time as they pushed
down on the toaster. (that's what they said) I put a slo-blo fuse
in there and haven't had a problem since. But this is an indication that
the electrical system in the rental needs some upgrading.
I feel that 60 amp is good enough for an apartment but for an entire
house, maybe not.
Steve
Back in the horse and buggy days each room
was lucky if there was one outlet in it, and some times the whole
house ran off two 20 amp fuses! There weren't too may appliances
on the market then
|
291.792 | My mess. | WELFAR::PGRANSEWICZ | | Wed Mar 18 1987 16:47 | 20 |
| The "original" wiring in my house (built around 1950) is all 2 wire,
non-shielded romex (cloth covered). I'm pretty sure this includes
all kitchen, bathroom and exterior lighting circuits. Some new wiring
was added in the basement for what used to be an apartment. This is
3-wore romex. There must be at least 6-7 sub-panels clustered around
the main panel (there's one there somewhere). I'm pretty sure it's
60-amp service.
I'm planning on upgrading the service to 100-amp and replacing the
thousands of fused, subpanels with breakers. When I redo the bathroom
and kitchen, I'll run new, GFI 12-2 circuits.
Is there anything else I should consider doing? My detached garage
is fed from a single line run from the house. Should there be any
special considerations for this circuit? Has anybody out there
actually replaced their 2-wire romex with 3-wire throughout
the house? Is it difficult? Is it worth it? I'm pretty close
to re-wiring the whole house anyway.
Phil
|
291.793 | | USMRM2::CBUSKY | | Thu Mar 19 1987 11:43 | 5 |
| Outlets in the garage (as well as outside) should be GFI protected
as well. You don't want to zap your self when to step in a puddle
while you're using the electric buffer on your car! :-)
Charly
|
291.794 | No fishing permit required... | JOET::JOET | | Sat Mar 21 1987 02:35 | 15 |
| re: .21
I've redone a few circuits in my house from 2-wire to 2-wire w/ground.
Since you don't have to "fish", it's really less than half the work
of adding a new outlet in old construction.
You have to twist and tape the old and the new together and basically
just pull the old stuff out. Make sure that it's solid wire and not
going through a junction box somewhere.
A little detective work and it'll be OK.
-joet
P.S. 14 gauge pulls a hell of a lot easier than 12.
|
291.795 | pulling stapled wire | CLUSTA::MATTHES | | Sat Mar 21 1987 08:23 | 9 |
| re .23
That's great unless the old wiring is stapled to the studs like
it is in mine. You 'throw away' the old and put in new. I'm told
that this is code in my area to do this (Nashua, NH circa 1969).
Fortunately I'm only making some minor changes, nothing major.
It just goes against the grain to know that wire is lurking in the
walls going to waste.
|
291.796 | Taylor's Rent-A-Gorilla... | JOET::JOET | | Mon Mar 23 1987 12:52 | 8 |
| re: .24
> That's great unless the old wiring is stapled to the studs like it is
> in mine.
Pull REAL hard?
-joet
|
291.118 | Wiring Circuit PLan Question | FRSBEE::PAGLIARULO | | Thu Mar 26 1987 15:55 | 29 |
| I'm bringing power out to a new porch via a circuit that now powers one
upstairs bathroom outlet. I plan on putting a GFI in the bathroom and then
running 14-2 from there to the porch outlets and lights i.e
L--|--|
---|--|--o-----------------o-----------
| | |_______________________ |
| | | | |
| | L-----\ PORCH L |
0 / / \ /0
| / / \ _________________/ |
| | / \ / |
-s-s--------------o--------------------------------------------
| Bath. Outlet |
| HOUSE |
There will be two legs coming off the bathroom outlet box. One leg will go to
the GFI and from there to the first outlet on the right and then continue
around to power all the other outlets. The other leg will go to the inside
porch lights and associated switch leg. Off the left light I want to bring
power to some outside lights and put those on a separate switch.
Before I go through and do all this I want to make sure there is nothing wrong
with my circuit plan. So, can any of you electrical types that are more
familiar with wiring then I am see anything wrong?
Thanks,
George
|
291.119 | Wiring changes | SEESAW::PILANT | L. Mark Pilant | Fri Mar 27 1987 13:55 | 14 |
| It is generally a good idea to have at least one light on a separate
circuit. Having everything on one circuit has the potential for
creating a dangerous situation. If you should happen to trip a
breaker/blow a fuse, you could be left in the dark; which will give
you lots to bang into.
Also, you might run into a problem with the size of the wire currently
serving the bathroom. I would not be at all surprised to find it
as 14-2. Supplying another room off that could lead to problem.
A general rule that I use when running new circuits is to use nothing
smaller than 12-2 for outlets, and usually 14-2 for lights.
- Mark
|
291.120 | | BEING::WEISS | Trade freedom for security-lose both | Fri Mar 27 1987 14:04 | 0 |
291.797 | Too simple to be legal? | CADSYS::BURDICK | Ed Burdick HLO2-2/G13, dtn 225-5051 | Fri Mar 27 1987 17:15 | 8 |
| Would it be legal to just run a new ground wire through whatever route was
convenient? I don't have this problem, because my house is only 6 years old,
but in reading this stuff, it dawned on me that replacing all the wiring seems
like a lot of work compared to just running a ground wire. Dropping a 14
guage single wire (bare or insulated) from the attic or into the basement
might be an easy spot upgrade if it ran to a legal ground. Since the wire
is sitting at ground, it would be pretty hard to make it dangerous.
Or is this a no no for some reason?
|
291.798 | | VIDEO::DCL | David Larrick | Tue Mar 31 1987 13:34 | 33 |
| > < Note 873.14 by WELFAR::PGRANSEWICZ >
>
> I know this is the "right" way but I just can't see it. Should
> I label the outlets "NOT GROUNDED". As a previous note suggested,
> I'm not sure I really need grounded outlets except in the kitchen
> and bath (which I intend to re-wire).
A nit, but an important one: according to code and modern practice, you
not only need grounded outlets in kitchens and baths (and basement, and
outdoors), but those grounded outlets also need GFCI protection.
> ...do they sell 2 prong outlets anymore?
> I can't recall seeing any.
They're hard to come by new. They should be readily available from
renovation and rewiring projects, though.
re .-1
> Would it be legal to just run a new ground wire through whatever route was
> convenient?
The code has some specific requirements for supporting and insulating
single conductors, but I can't remember if they apply to the ground wire.
On the one hand, what you're proposing is weird and nonstandard, and
therefore not a good idea; on the other hand, if it does improve the safety
of your wiring, and you probably wouldn't have gone to the trouble of a
more drastic safety improvement, then it's better than nothing.
Note that you need to connect all of the ground wires to the service panel,
rather than finding a convenient water pipe or other local ground. I'm not
sure exactly what "ground loops" are, but I know they're bad!
|
291.799 | from NEC 1987... | REMEDY::KOPEC | ne1g | Tue Mar 31 1987 15:04 | 38 |
| ok, let's see what the NEC has to say about all this...
Do you only need grounded outlets in the bath and kitchen?
210-7(a) Receptacles installed on 15- and 20- ampere branch
circuits shall be of the grounding type.
Exception: Nongrounding-type receptacles installed in
accordance with 210-7(d), Exception.
Can you leave them ungrounded?
210-7(b) Receptacles and cord connectors having grounding
contacts shall be effectively grounded.
Exception: Ground-fault circuit-interrupter replacement
receptacles installed as permitted by section 210-7(d),
Exception.
so, what do I replace my two-conductor outlets with?
210-7(d) Grounding-type receptacles shall be used as replacements
for existing nongrounding types and shall be connected to a
grounding conductor installed in accordance with [210-7] (c)
above.
Exception: Where a grounding means does not exist in the
receptacle enclosure either a nongrounding or ground-fault
circuit-interrupter type of receptacle shall be used. A
grounding conductor shall not be connected from the
ground-fault circuit-interrupter type receptacle to any outlet
supplied from the ground-fault circuit-interrupter type
receptacle.
[this "shall not be connected", I believe, deals with wire-
through GFI connections downstream..]
...tek
|
291.137 | Simple (?) Wiring Problem | BOOKIE::WIEGLER | | Fri Apr 03 1987 13:09 | 22 |
| I recently moved into a new (actually 7 year old) house. The wiring
is interesting because almost every light is controlled from 2
switches, for convenience I suppose. The previous owners took their
dining room celing fixture with them and I want to hook up my new
one. I have installed numerous celing lights in the past and have
never had any problems until now. The dining room light is controlled
by 2 switches; one is a dimmer and the other is a regular on/off
switch. The ceiling box has three sets of wires feeding into it.
Each set of wires has a black, white, and a copper ground. The
3 copper grounds are all twisted together, but all the other wires
were just left hanging. The fixture that I want to install has
2 wires, 1 black and 1 white. HERE IS THE PROBLEM: I tried to install
the fixture by connecting all the white wires together (the 3 from
the ceiling box and the one from the fixture), and then connecting
all the black wires together. I left the ground wires twisted together
and tucked them up into the box. The result is that the circuit
breaker switches off the first time I use the wall switch.
WHAT AM I DOING WRONG??? GAWD, I FEEL SO STUPID!!!
The wife really wants this light working this weekend, so any help
would be greatly appreciated.
|
291.138 | Insulate the connections? | HEADS::OSBORN | Sally's VAXNotes Vanity Plate | Fri Apr 03 1987 13:29 | 6 |
| You did cover each connection? With the wire nut? With
the black electrical tape?
If the wires were just twisted together and jammed into the box,
they could short against each other and even against the box
itself. (We have been there!)
|
291.139 | | VINO::KILGORE | Wild Bill | Fri Apr 03 1987 13:46 | 37 |
|
The first thing to do is disconnect the wires you connected, get paper
and pencil, pull out the switches in question, and try to make a
diagram of the circuit. An AC voltmeter or circuit testing light will
help in this endeavor. An alternative would be to ask the previous owner.
No red wires, eh? Guess the installer didn't go the normal route,
using 14/3 cable to provide the extra conductor needed for such
a circuit.
Two normal variations of the circuit are shown below. (The switches
can be either dimmers or toggle - circuit is still the same.)
switch switch light
,*-----red------*.
black----*' `*----black-----*
*----black-----* \
/ (load)
white-----*-----------------*----------------*
switch light switch
,*-----red-------*----------------*.
black----*' `*-.
*----black------*----------------* |
|
white-----*---------------* *-------------------'
\ /
(load)
I can't come up with a variation, using an extra 14/2 to replace
the red conductor from the 14/3, that puts three cables in the light
box. Perhaps the results of your circuit testing will help.
You shouldn't feel stupid - the problem is that you're not placing
the blame on the correct party (see the ever popular "Why did they
ever do that?" note in this conference).
|
291.140 | It's a remote switch | BEING::WEISS | Trade freedom for security-lose both | Fri Apr 03 1987 14:20 | 66 |
| I bet I know what is going on. You have three two-conductor wires coming into
the light box. One is the power coming in from the circuit box. Another is
the power going out, continuing on to another light on the same circuit. And
the third is going out to the remote switches. There is a 3-conductor wire
connecting one switch with the other. That means that one of the switch boxes
has the other end of the two conductor wire going out from the light and the
three conductor wire going to the other switch, and the other switch box has
just the three conductor wire. A diagram will probably help:
+---------------+
Black | | Black
Power in -------------+--- ---+---------- Power out
from White | | White to other
Panel -------------+--- ---+---------- lights
| | | |
+------+-+------+
W| |B
| |
+---+-+---+ +---------+
| | | | Black | |
| | +---+----------+-------+ |
| | | Red | | |
| | ---+----------+---\ | |
| +- | White | ---+ |
| \---+----------+--- |
| | | |
+---------+ +---------+
Thus it makes sense that the breaker trips when you hit the switch, because you
are directly connecting the black and white wires. What you want to do is
this: First, wire all three of the black wires together, but don't include the
black wire from the light, just the three black wires coming in. By doing
that, you connect the power in with the power out, and you provide power to thw
switch. Next figure out which of the three wires is the one going to the
switch. It might help to find out which of the switch boxes has the wire
coming in. Then, connect the white wires of the OTHER two wires with the white
wire of the light. Again here, you're connecting power in with power out, and
you're tying in the neutral end of the light with the circuit. All you should
have left at this point is the white wire from the switch and the black wire on
the light. Hook these together, and you're done.
BTW, you might be able to tell which is the switch if the white wire has a
piece of black electrical tape wrapped around it, which indicates that it is
really carrying current. If it's not there, you might do that yourself to save
a future light-changer the same problem you're having.
When you're done, the wiring should look like this: (* is a connection)
Light
| |
W| |B
+------+-+------+
Black | | \ | Black
Power in -------------+--------*------+---------- Power out
from White | | |/ | White to other
Panel -------------+------*-|------+---------- lights
| /| |
+------+-+------+
W| |B
| |
Switch
Good Luck!
Paul
|
291.141 | I bet thats it! | TRACTR::DOWNS | | Fri Apr 03 1987 14:40 | 6 |
| Nice job .3, I second this solution! If fact that is exactly how
I wired all of my three way ceiling lights.
Boy isn't this file great! Anyone out there know what next wednesday's
Mass. megabucks ticket sequence will be?
|
291.142 | One thing to try | STAR::SWIST | Jim Swist ZKO1-1/D42 381-1264 | Fri Apr 03 1987 15:54 | 8 |
| .3 seems likely, but a simple verification is in order. Since there
is an outfeed to some other part of the circuit, then if all wires
are left unconnected, and the circuit breaker is turned on, them
there will be at least one other fixture or outlet which is not
working (probably need the light in question, but maybe anywhere!).
This would be simple to test before proceding with .3
|
291.143 | yes but....... | MRMFG1::C_DENOPOULOS | | Fri Apr 03 1987 16:00 | 10 |
| Not so fast .4, .3 may be right but in an appartment I was in I
had the same situation as .0. There was no 14/3 wire anywhere.
If the downstairs switch was off, the upstaris did nothing. If
the downstaris switch was on, then you could turn the light off
and on again from upstairs. Needless to say, this was a royal pain.If
an electrition did your wiring, then you probably have what .3 had
shown. If the previous owner did, then who knows!!
Chris D.
|
291.121 | | VIDEO::DCL | David Larrick | Fri Apr 03 1987 17:52 | 25 |
| Existing 14/2 wire shouldn't be a problem as long as you don't plan to run
a radial arm saw on the porch - or, for that matter, to vaccuum the porch
while running a hair dryer in the bathroom.
If you do plug in anything on the porch that's likely to trip the GFI,
walking around into the bathroom to reset it could be a pain, especially in
the dark. You might consider a second GFI on the porch itself. If the
porch is weathertight, you don't NEED GFI protection on the porch at all.
You mention adding two legs to the existing bathroom outlet box. Adding
additional wires to an existing box can cause you to exceed the Code-
specified maximum wire count for the box size. These calculations are
certainly detailed, but straightforward once you get the hang of them.
Code considerations aside, trying to work with too many wires crammed into
too small a box is unpleasant work, and increases the likelihood of a
short.
The GFIs I've installed are quite large, and take up most of the space in
the box. You may need to replace the existing bathroom box with a larger
(i.e. deeper) one just to fit the GFI in.
One last parting shot: "a circuit that now powers one upstairs bathroom
outlet" doesn't strike me as a typical configuration, especially for
pre-GFI construction. I'd double-check to make sure the circuit really
does serve just that bathroom.
|
291.122 | What is and What Shall Be | FRSBEE::PAGLIARULO | | Fri Apr 03 1987 19:20 | 21 |
| When I traced all my house circuits last winter I taped a sheet of
paper on the box that said what each fuse runs. When I looked at the
bathroom fuse again I realized that that fuse doesn't run only the
bathroom just yet. Right now it also runs the washer, the gas drier, the
dishwasher, and one kitchen counter outlet! When I wrote the base note I guess
I was thinking of what would be on that circuit when I got all the stuff off
that doesn't belong there. This is the same circuit that had a 30 amp fuse in
the box when we moved in.
After re-evaluating the situation I've decided to run a separate circuit
for the porch. The GFI will be the first oulet on the this circuit. It's this
circuit that will power the bathroom. As I originaly planned, the washer and
drier will get their own circuit as well as the dishwasher. The kitchen
outlet that was on the dishwasher/drier/bathroom/clothes washer circuit will
be wired to one of the other kitchen circuits.
Thanks for all the help.
Oh yeah, one more thing. For a circuit with a clothes washer and gas drier
is it best to use 14-2 or 12-2
|
291.123 | | SEESAW::PILANT | L. Mark Pilant | Fri Apr 03 1987 20:05 | 3 |
| One person's opinion: I'd use the 12-2.
- Mark
|
291.124 | | VIDEO::DCL | David Larrick | Fri Apr 03 1987 20:38 | 8 |
| I used 12/3, two opposite-phase 20A circuits in a single cable, to power
the washer and gas dryer separately. Arguably overkill, and 20A isn't
enough if somebody wants an electric dryer there; but I still like it that
way.
Separate, dedicated circuit for dishwasher too. I think Code requires it
that way, since the dishwasher is built in and hard-wired. The clothing
applicances are plug-connected, so the rules aren't as strict.
|
291.112 | Cross your fingers and hope. | CAD::GREENBERG | Steve HLO2-2/H13 225-6105 | Fri Apr 03 1987 20:51 | 9 |
| I ran into similar problems with an electric radiant cove heater. I didn't
find the electrical supply stores around here too helpful in telling me what
the thermal rating was for the wire they were selling me. I put some wire in
boiling water and it didn't seem to affect the insulation at all.
So far, I have been through one heating season with the heaters installed and
didn't have any problem.
/Steve
|
291.125 | Hmmm | TALLIS::SAMARAS | Advanced Vax Engineering LTN | Sat Apr 04 1987 21:18 | 8 |
| re: .6
Isn't your neutral connection carrying twice as much as it should?
If you can pull 40A from your box with your configuration, isn't
all of the return current flowing through 1 wire????
just wonderin',
...bill
|
291.126 | | VIDEO::DCL | David Larrick | Sun Apr 05 1987 19:02 | 9 |
| > Isn't your neutral connection carrying twice as much as it should?
No, that's the beauty of it. Since the two circuits are opposite in phase,
they cancel rather than adding.
"Worst case" is when one circuit is drawing 20A and the other zero: the
neutral carries 20A, i.e. normal. When both circuits are drawing something,
the neutral carries their difference, and when they match, the neutral
actually carries zero!
|
291.127 | | VIDEO::DCL | David Larrick | Sun Apr 05 1987 19:09 | 2 |
| P.S. This technique is perfectly legal, and is described in some detail in
the Code under the name of "3-wire circuits".
|
291.128 | Not an option | ALIEN::WEISS | Trade freedom for security-lose both | Mon Apr 06 1987 11:18 | 5 |
| As mentioned before, the size wire you use is not an option if it's a 20A
circuit. You HAVE to use 12 gauge wire. You can only use 14 gauge if the
circuit is 15A.
Paul
|
291.129 | a question | TALLIS::SAMARAS | Advanced Vax Engineering LTN | Mon Apr 06 1987 13:16 | 5 |
| What's the likelyhood of getting away with a washer and a fridge
on the same 20A 12-2 circuit? I don't have anymore room in my panel,
and they don't make "double" breakers for Cutler Hammer (yet).
...bill
|
291.130 | | CSSE32::NICHOLS | HERB | Mon Apr 06 1987 15:30 | 2 |
| A dish washer and clothes washer cannot hack the same 12-2 20A circuit
in our house.
|
291.131 | | VIDEO::DCL | David Larrick | Tue Apr 07 1987 12:40 | 20 |
| > What's the likelyhood of getting away with a washer and a fridge
> on the same 20A 12-2 circuit?
I don't think code has any objection to this arrangement as such, although
I wouldn't recommend it.
You're pretty likely to trip the breaker when both appliances demand high
power at the same time. But that's likely to be when you're in the house
and awake, and you can go reset it. Annoying, but not disastrous.
If you're in the habit of leaving the washer running when you go to bed,
plan to wake up to a warm refrigerator once in awhile.
Better would be to put the washer on a circuit with lights and infrequently-
used outlets, and put the fridge with kitchen outlets. (Code requires two
circuits dedicated to kitchen outlets, but the fridge may be on one of these).
Be sure to read the rating plates on both appliances before you decide
anything. If you report those ratings here, you might get more free
advice...
|
291.132 | A Possibly Dumb Question | FRSBEE::PAGLIARULO | | Tue Apr 07 1987 13:29 | 3 |
| When you're running wires between studs that will also have
fiberglass insulation between them do you put the wires behind or in
front of the fiberglass? Does it matter?
|
291.133 | Don't do it | STAR::SWIST | Jim Swist ZKO1-1/D42 381-1264 | Tue Apr 07 1987 15:12 | 20 |
| Ahh, a catch-22 of wiring. Wiring run horizontally has to pass
through holes which must be more-or-less centered in the stud.
Otherwise you run the risk of nail penetration, plus cuts close
to or on the edge will weaken the studs.
However this forces you to compress the insulation either behind
or in front of the wire. The electrical code doesn't care, but
neither is a great idea from an insulating effectiveness point of
view.
You will notice most professional electricians in new houses solve
this problem by not doing it. Wiring on walls to be insulated will
run up from the floor below or down from the attic directly along
the studs, even if this means using a lot more wire. In fact you
will usually see this even on interior walls, since it's a matter
of habit.
If this is a basement wall you are finishing, it is legal (and
saves a lot of drilling) to run the wiring between the back of the
studs and the concrete wall, if you have space there.
|
291.134 | | VINO::KILGORE | Wild Bill | Tue Apr 07 1987 15:25 | 6 |
| re .14:
You could slit the fiberglas batt (but no the facing) where it will
intersect the wire, to allow it to wrap around the wire without
comperssing.
|
291.144 | Simple (?) Wiring Problem - Part 2 | BOOKIE::WIEGLER | | Thu Apr 09 1987 13:42 | 45 |
| Thanks to all of you who responded to my wiring problems described
in note 966. Unfortunately, none of them worked. Rather than restate
the problem, I'll just continue where I left off in that note.
I spent 2 1/2 hours last night climbing the ladder, wiring the light
fixture, going down to the basement, turning the circuit back on,
going upstairs to check the light, finding it still wasn't right,
and then doing it all over again with a different wiring arrangement.
I labelled all the wires to keep track of all the different
combinations. There are 3 sets of wires coming into the ceiling
box. I labelled the black ones A, B, & C and the white ones 1,
2, & 3. The kitchen ceiling light also comes from the same circuit,
so, I believe my dining room box is also a junction box leading
to the kitchen light. The explanation given by Paul Weiss in note
966.3 makes a lot of sense (thanks Paul) and, yes, there is a red
wire running between the 2 wall switches in the dining room, but
not to the ceiling box. However, I tried connecting it up Paul's
way and it still didn't work. I connected all 3 black wires together.
Then I connected 1 white wire to the black wire from the light,
and the other 2 white wires to the white wire from the light. I
tried this in all 3 possible combinations, but the dining room light
never lit. I also tried another suggestion which
was to connect 2 black wires together, 2 white wires together,
and the remaining black and white wires to the light. I tried this
in all 9 possible combinations and I got the following results:
1. The kitchen light worked, dining room light didn't
2. The kitchen light was out, but the dining room lit (although the
dining room switches didn't turn it off, but the kitchen switch
would dim the dining room light)
3. Nothing would light
I'm sure this sounds confusing; I could draw a picture of the wiring
and all the possible combinations I tried, but probably couldn't
do it clearly on the screen. If anyone loves the trill of a challenge
and lives in Manchester, NH, I'm sure I could stock my fridge with
beer and have a LIGHT-WIRING PARTY this weekend.
Now, I know that the previous owner had a working light in that
room, and I guess the next step is that I'll call him up and see
if he can help, but I suspect he's not too knowledgeable about such
things. I am certainly open to any suggestions. The last thing
I want to do is to PAY an electrician to come over and sort it out,
but if I get desperate enough....
|
291.145 | If at first you don't suceed... | YODA::BARANSKI | 1's & 0's, what could be simpler!? | Thu Apr 09 1987 15:13 | 9 |
| The solution!
Rip out all the wires, leaving a wire or string or twine or rope between
the switches and lights to allow you to pull new wires through, and wire
it up in a way that you understand it!
Jim.
|
291.146 | start at the beginning... | WHO::SHOREY | | Thu Apr 09 1987 16:33 | 24 |
| are you getting power to the box? i would think that the first
thing to do would be to hang all three black wires and all three
white wires out of the box, turn on your circuit breaker, and find
out which pair, if any, is live. if you don't have a test light,
now is the time to spring for the $1.29 and get one.
once you have a live pair, one of the other pairs should go to the
kitchen circuit. connect your live pair to one pair (you may turn
off the circuit breaker when doing this) and try the kitchen light.
if it doesn't work, connect your live pair to the other pair and
try the kitchen again.
once you get the kitchen going, connect the black wire from the
remaining pair to the two blacks, connect the white wire from the
remaining pair to the black wire of your new dining room light,
and connect the white wire from the dining room light to the two
whites.
if this doesn't work, you need a new lightbulb or switch!
good luck, and let us know how you make out. i'd love to stop by,
but i'm busy with my own home_work this weekend.
brian (225-7285)
|
291.147 | We'll get it yet | BEING::WEISS | Trade freedom for security-lose both | Thu Apr 09 1987 16:43 | 33 |
| More questions:
You say: "The kitchen ceiling light also comes from the same circuit,
so, I believe my dining room box is also a junction box leading
to the kitchen light." Does this mean that if you don't connect any wires, the
kitchen light won't work?
Other than the 3-conductor wire running between the two dining room switches,
there should be just one 2-conductor wire going to just one of those switches.
Are there any other wires in those switch boxes?
Does the kitchen light have 1 or two switches? You said that the kitchen
switch would dim the dining room light. Do you mean that the kitchen switch is
a dimmer switch and it controlled the dining room light? Or is it a regular
switch, and would dim the dining room light when turned on?
How many wires come into the kitchen light and switch boxes?
If we can't figure it out from your description, there's another way to find
out what's going on. Go spend $2 on a cheap voltage tester. Now separate all
the wires in the box, and go turn on the breaker. *Carefully* try the tester
between each black wire and the ground wires until you find the hot wire. Now
you'll at least know where the power is coming in from. Now open up both
switch boxes, plus the switches and light in the kitchen (don't forget to mark
which wires go where in these boxes - you don't want to make the situation
worse :^)), and get all the wires separated and loose in those boxes. Connect
the known hot wire in the dining room box with another black wire, then go turn
the power on again, and check the other boxes to see where that wire went to.
You can keep doing this until you've identified where all the wires are going,
and then you ought to be able to figure out how to wire it.
Paul
|
291.148 | Reply .4 continued | BOOKIE::WIEGLER | | Thu Apr 09 1987 19:07 | 7 |
| SOMEHOW THE END OF .4 GOT CUT OFF. Here's the rest:
...and wire it according to the suggestion in .2.
If it still doesn't work, I may try replacing the switch and dimmer
and hope that they are the cause of my misery.
I am open to all suggestions until the weekend. Then I'll go home
and try them all. I'll report back to you on Monday.
|
291.149 | | BEING::WEISS | Trade freedom for security-lose both | Thu Apr 09 1987 20:13 | 9 |
| You want to try .4 again? From my terminal, it all got cut off.
Is your kitchen light a flourescent? If so, then maybe when you turned on the
kitchen light and it dimmed the dining room but did not turn on the kitchen,
perhaps it did turn on the kitchen, but the flourescent would not work with the
lower voltage. That would help in figuring it out, because it would mean you
had the two lights in series.
Paul
|
291.150 | Here are some more facts | BOOKIE::WIEGLER | | Thu Apr 09 1987 20:38 | 31 |
| I guess .4 got screwed up so let me enter it again here:
Re questions from .3 and .6:
The kitchen has 2 light switches (neither is a dimmer). When I
said that the kitchen switch dimmed the dining room light, I meant
just that. I couldn't turn off the dining room light, but flipping
the kitchen switch dimmed the dining room light. (Pretty wierd,
huh?)
The kitchen light is not a florescent; it is a track light.
I believe that if I leave all the wires in the dining room box
unattached, then the kitchen light will not work (it won't have
power). I haven't actually tried it, but I will.
There are only the 3 sets of wires going into the dining room box.
No other wires feed into it.
The suggestion made in .2 is basically the same as made by Paul
in 966.3. I do believe that it is the correct way, but for some
reason it did not work. I will get a line tester, identify the
power wires, identify the wires to the kitchen light, and wire
it according to the suggestion in .2. If it still doesn't work,
I may try replacing the switch and dimmer and hope that they are
the cause of my misery.
I am open to all suggestions until the weekend. Then I'll go home
and try them all. I'll report back to you on Monday.
|
291.151 | Look at a book on wiring | BEANCT::VANCLEAVE | | Thu Apr 09 1987 21:46 | 9 |
| With a 3-way switch is important to know where the switch is in relation
to the power feed and the lights. Try looking at the TIME-LIFE
Basic Electricity Book, but be careful, it doesn't show all the
possibilities for this kind of wiring. If you diagram your circuit
and it looks like the one in the book, you're probably ok. By the
way, a wiring diagram of your whole house will be invaluable later
on when you want to add more circuits or check a fuse.
Dave Van Cleave
|
291.152 | Dimmers die like that | CADSE::MCCARTHY | Excellent, more than a match for poor Enterprise. | Thu Apr 09 1987 21:47 | 11 |
| Dimmers have a habbit of kicking the bucket if the circut they are
attached to trips a breaker. If the wiring was incorrect the first
time you turned the switch on, you may have killed the dimmer.
One of the previous replies said that one of your switches for
the dinning room must have a 14-2 AND a 14-3(red) wire. Wire the
box as stated in note 966.3 and then use a single pole switch between
the 14-2 in the switch box. Have you tried this?
Still pretend I'm an electrician every Saturday,
Brian Mac
|
291.153 | Bad dimmer = interesting possibility | BOOKIE::WIEGLER | | Fri Apr 10 1987 14:01 | 10 |
| Thank you Brian Mac (.9). If my dimmer blew when I tripped the
circuit, that would explain a lot. How about if I remove the dimmmer
switch and just connect the wires together (the ones that ran to
the dimmer switch) as a means of bypassing the switch? Then I could
test out the circuit without the dimmer in the way. Does that make
sense? What do I do with the red wire that leads into the dimmer
box?
Boy, this is great. I almost look forward to tackling the wiring
tonight.
|
291.154 | What to do with red | VIDEO::DCL | David Larrick | Fri Apr 10 1987 15:05 | 26 |
| > What do I do with the red wire that leads into the dimmer box?
Here's how a simple 3-way switched circuit looks:
white
-------------------------------------------------+
power |
----+ black LIGHT
| /----------------\ |
+-----/ \-------------------+
black ---------------- black
red
So, if you want to replace one of the switches with a hard-wired connection
for testing purposes, you have two options:
1. Wire black to black, ignore the red. Don't connect that leg to the
circuit at all. The other switch will turn the light on when it
connects to the black leg, off when it connects to the red leg.
2. Wire black to both red and black. Thus both legs are always hot. The
other switch will turn on the light no matter which way it's switched.
Option 1 is most useful for most purposes, including yours. Option 2 is
useful for such applications as determining whether the red wire has
continuity, or determining whether the other switch is working properly.
|
291.155 | Use 3 way as single pole | CADSE::MCCARTHY | Excellent, more than a match for poor Enterprise. | Mon Apr 13 1987 11:37 | 9 |
| You can use a 3-way switch as a single pole switch. There are three
points on the 3-way, one of them is usually a copper color, this
is the point. By taking the wire that is coming from the celling
box to the switch (the 14-2) and connecting one of them (white or
black) to the point terminal and the other to either of the remaining
two terminals you have a single pole switch.
Brian mac
|
291.156 | A HAPPY ENDING | BOOKIE::WIEGLER | | Mon Apr 13 1987 14:13 | 33 |
| Well, here's the final chapter of my story. I went home on Friday
and did the following:
I removed the dimmer switch and wired that box to complete
the circuit without the switch.
Then I used a circuit tester (bought it Friday afternnon at a hardware
store for $1.89) to determine which of the wires coming into the
ceiling box carried power.
I connected the power wires to another set of wires in the ceiling
box to determine which wires led to the kitchen ceiling light.
I then labelled all the wires.
The remaining set of wires going into the ceiling box obviously
went to the wall switches. I then wiring the light according to
the recommendations in notes 992.2, 992.3 and 966.3 and IT WORKED!!
I then danced a little euphoric jig around the house. Apparently,
the dimmer blew when I tripped the circuit breaker in an earlier
wiring attempt (a possibility suggested in note 992.9) so that even
when I did have it wired correctly, it wouldn't work.
I installed a new dimmer switch on Saturday and now everything works
great. Thanks to everyone who responded with suggestions. This
notes file is the greatest.
I do have one more question. When I dim the light, it hums. I
have had this occur with other dimmed lights in the past. Is this
something you learn to live with, or can it be cured? It's not
terribly loud, but it is noticeable.
THANKS AGAIN FOR ALL THE HELP!
|
291.157 | Alls well that ends well | BEING::WEISS | Trade freedom for security-lose both | Mon Apr 13 1987 16:39 | 33 |
| Hooray!!
Glad it worked out. Just goes to show once again that the SUM of the
experience of the people in this file is amazing. I chanced to be the first
person to suggest the correct wiring, but I never would have suspected that
wiring it incorrectly before would have busted the dimmer. Wonderful! Y'learn
sumpin' new ever day.
As to the dimmer, the reason it humms is that the dimmer does not lower the
amplitude of the entire alternating current sine wave, it just clips the wave
at a certain amplitude, so instead of a nice clean sine wave you get something
that looks like this:
___________________ ___________________
/ \ / \
/ \ / \
/ \ / \
\ /
\ /
\___________________/
All those jerky transitions make the filament hum. I imagine it takes a bit
off the life of the bulb, also, but I don't know.
I heard somewhere that if you put a 3-way bulb in the socket, it won't hum, but
I've never tried it. Supposedly something about the way the filament is held
in a three way bulb keeps it from humming. Let us know if you try it and it
works.
Paul
|
291.158 | | PEANO::GLASER | Steve Glaser DTN 226-7646 LKG1-2/A19 | Mon Apr 13 1987 17:25 | 16 |
| If a 3-way doesn't help the humming lamp problem, you might try
either long life lamps (designed for places that are hard to get
to so you don't want to do it very often) or tough lampss (designed
for being mishandled as in trouble lights, etc.).
The humming is coming from the filament vibrating. The tough lamp
has many more filament supports. Both lamps have thicker than normal
filaments. These lamps are more expensive and may not put out as
much light.
If you can't use these lamp (say you need decorator lamps), there
are dimmers available that don't cause the humming problems. They
are much more expensive and usually can't fit in an outlet box but
they are available.
Steveg
|
291.159 | I'll try some other bulbs | BOOKIE::WIEGLER | | Mon Apr 13 1987 18:02 | 7 |
| Interesting information about why the humming occurs. The light
fixture we have looks sort of like an upside down glass bowl (with
ridges in the glass) suspended from a brass chain. Because the
bowl part is clear we have always used a clear bulb in it. It gives
off a beautiful glow (especially when dimmed) but I'll try some
other bulbs, just for the heck of it. Thanks again.
|
291.160 | Hot Hummer Horrifies Homeowner | ERLANG::BD | Brian D. Handspicker | Mon Apr 13 1987 18:24 | 10 |
| Why would the dimmer itself hum? My electricians just finished
installing dimmers for the front hall and living room recessed
lights. The dimmers are side-by-side. The hall dimmer controls
three fixtures without humming. The living room dimmer controls
9 fixtures (@ 25 watts per fixture) and hums and heats.
Is this normal? Is this simply the result of the heavy load
or the result of miswiring?
bd
|
291.161 | hot dimmers | WHO::SHOREY | | Mon Apr 13 1987 19:04 | 21 |
| 9x25 = 225, which seems to be a lot of watts for a dimmer. i think
that the average dimmer is meant to handle one 100 - 150 watt bulb.
you can overload a dimmer quickly by shorting out the wires, in
which case it fails quickly (as we have found out here) or you can
overload it slowly, in which case it fails slowly.
find a dimmer that is meant to handle 225 watts and replace yours
immediately, if not sooner. a hot box in a wall is a fire waiting
to happen.
on dimmers in general - i believe that the more you dim the lights
the more energy is absorbed by the dimmer = more heat dissipated.
they have always scared me, because i have felt very hot walls
when they fail. perhaps newer dimmers are more reliable, but if
it were me i'd still try to come as close as possible with the proper
wattage light bulb, then only dim the lights as little as possible.
correct me if i'm wrong.
brian
|
291.162 | 225 is not too much. | STAR::SWIST | Jim Swist ZKO1-1/D42 381-1264 | Mon Apr 13 1987 19:28 | 19 |
| Re .18
Most ordinary elcheapo dimmers are rated at 500-600 watts. So 225
should be no problem; however, the humming/buzzing problems will
increase with a larger load.
Re: Earlier replies.
It's not my experience that sending square waves through a filament
shortens the life - if it does, then it's more than offset by the
lengthening of life due to lower voltage.
Actually, I find the more annoying problem is that the damn harmonics
from those square waves radiate around the house wiring and introduce
buzz into radios, particularly AM.
Jim
|
291.163 | most timmers chop time, not voltage | PEANO::GLASER | Steve Glaser DTN 226-7646 LKG1-2/A19 | Mon Apr 13 1987 19:50 | 36 |
| Most of the dimmers out there work by cutting the sine wave apart in
time, not voltage.
In other words (or pictures):
|\
| \
| \
| \
| \
| \
_________| \_________ ____________
| /
| /
| /
| /
| /
| /
|/
Where the vertical lines move based on what position you have the
control at. The vertical pulse contains all sorts of high frequency
components. The interference you get in radios, stereos, etc. is
due to tha appearance of this pulse of RF 120 times a second.
The good (expensive) dimmers do things to moderate the rise time of
this pulse. This cuts down on the RF noise, makes the filaments last
longer, and helps with humming problems in filaments and dimmers.
[actually now that the FCC has tightened up the rules on EMI, it may be
that all dimmers do this to some extent.]
Note that the dimmer is just acting as a switch (turning the bulb
off and on 120 times a second). It is not absorbing any energy
as was implied in an earlier reply.
Steveg
|
291.164 | filter..... | NEXUS::GORTMAKER | | Tue Apr 14 1987 02:05 | 8 |
| You can cut some of the interference by installing a .05mfd
ceramic disk capacitor between hot and gound and neutral and ground.
I tried this due to problems with lines on the tv caused by the
dimmer. Worked fine the 1st time. Besure to properly insulate the
leads on the cap with old (wire)insulation scraps and tape.
-j
|
291.165 | Maybe they don't know the words?? | TALLIS::SAMARAS | Advanced Vax Engineering LTN | Tue Apr 14 1987 13:48 | 20 |
| A humming dimmer is not usually a sign that anything is wrong. It
turns out that the semiconductor device in the dimmer that is doing the
switching actually vibrates slightly! This happens 'cause it's
switching 2 or 3 AMPS, 120 times a second. It generates a little
EMF (for you EE types). BTW, the most noise
(electrical and audible) occurs at about the mid brightness setting.
The semiconductor device gets a little warm from all this switching, so
its mounted (riveted) to a heat sink to keep it cool. Usually this is
just the case of the dimmer. Some high power dimmers have "fins" on the
front of them to help remove the heat. If the vibrating semiconductor
device is a little bit loose, or if your dimmer is not fastened into
your electrical box tightly, the sound could be louder. I'd suspect
that a plastic box would make less noise (I'm guessing).
The speed control in an electric drill works the same way. They
"buzz" or hum at slow speeds too.
...bill
|
291.113 | ??? about wattage in fluorescent fixtures | CHAPLN::ROSENTHAL | Out to break Murphy's Law! | Tue Apr 14 1987 15:30 | 14 |
|
I bought a beautiful kitchen light fixture from the Lightolier
catalog for my new house. The fixture required 2 40-watt lamps.
After having it installed, I've found it MUCH too bright and
harsh in my kitchen (I can't remember the type of lamps I
chose, whether they were soft white, or cool white, or whatever).
Can I change the 40-watt lamps to something dimmer, as I would
with a regular fixture, or must I use only 40-watt?
Thanks.
Donna_who_didn't_do_enough_homework_and_now_needs_sunglasses!
|
291.166 | | CLOVAX::MARES | | Tue Apr 14 1987 15:59 | 17 |
| RE: .17
Does ME = ME ?????
yl
e
c
t
r
i
c
i
a
n
Randy
|
291.114 | No, But... | YODA::BARANSKI | 1's & 0's, what could be simpler!? | Tue Apr 14 1987 16:42 | 10 |
| The problem with fluorescent fixtures is that the amount of light they produce
is directly proportionate to their size, or to be exact, their surface area. So,
no, you can't just change to a lower wattage 'bulb'.
However, the above assumes that all other things are equal... There are
a number of different 'bulbs' that put out different light at the same
wattage... You could replace the cover with a smoked cover to dim the light...
etc...
Jim.
|
291.115 | A couple more ideas | VIDEO::DCL | David Larrick | Tue Apr 14 1987 19:10 | 11 |
| > (I can't remember the type of lamps I
> chose, whether they were soft white, or cool white, or whatever).
The tube should say, right on it. Most common, cheapest, and most likely
is cool white. Perhaps what you're reacting to is not the level of light
so much as its harsh, garish quality; if so, switching to soft white or
warm white might well do the trick.
Simplest solution: just remove one of the tubes. It may not look very
good, but it'll be less light.
|
291.167 | Know my Limitations | ERLANG::BD | Brian D. Handspicker | Tue Apr 14 1987 22:09 | 13 |
| Re: .17 - .22
Thank you all for easing my fears. I will rest much
easier now.
Re: .23
This time around I had enough rewiring to warrant hiring
a real electrician. I'll putter. I'll run wire. But
I won't rewire an entire condominum unit while I and 14
other people live in the building. One screw-up and all
of us are without light and heat. I let a pro handle
this one.
|
291.116 | | NEXUS::GORTMAKER | | Wed Apr 15 1987 00:40 | 14 |
| You can also purchase the GE watt-mizer lamps they do have a somewhat
lower lumen output over standard cool white lamps. I belive the
wattage for the watt-mizer lamps is 34 -vs- 40 watts.
Not a big savings but... I would sugggest the warm white or day
light lamps. I use them in every lixture i have and prefer them
for the reduced harshness and how they make colors appear.
BTW-they do run 5-10% higher in price.
-jerry
P.s. Any lighting store worth its name should be able to demo
the various bulbs for you. GE makes about 20 types of 40 watt
lamps all different colors,ect. Get a cataloge for more info.
|
291.168 | Help with Wiring (lighting) | FDCV19::CUMMINGS | | Tue Apr 21 1987 13:33 | 0 |
291.169 | | VINO::KILGORE | Wild Bill | Wed Apr 22 1987 14:27 | 13 |
|
Use whatever routing is more convenient (less cable, less cutting,
fewest cables per box, etc). Three-wire cabling is not neccessary for
what you have in mind.
Do you really need a 20-amp circuit? How big are these lights? A
15-amp circuit will handle 10 150-watt lamps with a capacity margin
of 17% (120v.*15a.=1800w., 10*150w.=1500w., 1500w./1800w.=83%).
And 14ga. wire is so much easier to work with than 12ga. (not to
mention somewhat less expensive).
I would also check the capacity of the dimmers - most are rated
in the 300-600w. range. Make sure they can handle the proposed load.
|
291.170 | 125% of continuous load.. | REMEDY::KOPEC | Eschew Obfuscation! | Wed Apr 22 1987 15:04 | 9 |
| re: is 20 amp circuit really needed:
Normal (code) calculation is 125% of the permanently connected
continuous load.. the continuous load for recess lighting is the
RATING of the fixture. so, if you use 8 fixtures rated at 150W,
the answer is yes, you can get away with 15 amps. 10 fixtures wouldn't
work (16.3 amps min.)
...tek
|
291.117 | Gro-Lux? | Q::ROSENBAUM | Rich Rosenbaum;mail->Boehm::Rosenbaum | Tue Apr 28 1987 17:40 | 12 |
| re .7
Romoving one of the lamps will probably prevent the other from working.
You might try using one "Gro-lux" or "Plant-Gro" bulb. These are
fairly reddish, and have a much lower light output than standard
bulbs. You proably would not like two bulbs of this type, tho.
I would try one Gro-Lux and one Warm white. The Gro-Lux type are
expensive, though - about $10 for 1 4'.
__Rich
|
291.181 | Voltage drop in old wiring | TALLIS::SAMARAS | Advanced Vax Engineering LTN | Tue Apr 28 1987 19:32 | 27 |
| I've been renovating an old house and have run into an electrical
problem. It seems that there is an excessive voltage drop from any of
the existing outlets. Lighting is OK, but whenever a high current
device is used, the lights dim alot. A "smart" device like a microwave
oven, sometimes causes the oven to shut off since it "knows" when the
voltage gets too low. The VCR gets wierd too, when all of the lights
are on. (I haven't measured yet, but it MUST be a 20 or 30 volt drop to
do that)!!
There are some new (<1yr) circuits that are fine. The existing stuff is
classic 1940 BX two wire, with the shield used as the safety ground.
I took the breaker panel apart and everything looked nice and tight.
My question is: Is this old BX stuff inherently high resistance
wire? Was copper rare during the war or something?? So far, I'm
hoping to find a junction box with a loose connection, but I can't
find one. I tightened all of the outlet screws (they were already
pretty tight), but I couldn't see anything funny.
I'm starting to wonder if the BX wire is high resistance stuff.
There is a pretty long run of wire up to the second floor. I'm not
too happy about dissipating all of that power in my wires.
Any info is appreciated,
...bill_who_doesn't_like_old_wiring_anyway
|
291.182 | | VIDEO::DCL | David Larrick | Tue Apr 28 1987 20:30 | 22 |
| First of all, it may just be that your house is under-powered, or that your
circuits are poorly configured. Make a circuit list/diagram of the house,
listing all loads by circuit. You may be surprised at the current some of
your circuits are drawing!
Failing that, it sounds like dirt and corrosion where the existing wires
are connected to the existing outlets, rather than deterioration of the
cables themselves. You'd do well to get a voltmeter and measure the
voltage at every point where you can get at it, i.e. at each outlet along
each circuit. That procedure would help you pinpoint which outlets (and
maybe cables) are in the worst shape, and where your corrective efforts
should begin.
The Old House Journal had an article a few years back with useful
information about debugging old wiring. One technique involves shutting
off all circuits but one, unplugging all loads on that one remaining
circuit, and then checking the electric meter. If the meter moves at all
over a period of an hour or so, you've got a slow current leak in that
circuit somewhere.
All of the above problems are potentially quite serious. As you mention,
the "missing" power is being dissipated as heat somewhere in the house.
|
291.183 | Check your fusistors. | TALLIS::KOCH | Kevin Koch LTN1-2/B17 DTN226-6274 | Wed Apr 29 1987 11:56 | 4 |
| A much more common cause of dimming when the fridge turns on (or
whatever) is old fuses that have developed a resistance. Electricians
call them fusistors. Try replacing your main fuses. It worked for
me.
|
291.184 | | AUTHOR::WELLCOME | Steve | Wed Apr 29 1987 13:51 | 6 |
| Corrosion on the terminals in the outlets, maybe? Or low pressure
on the plug terminals when one is plugged in?
Does the plug heat up on a current-drawing appliance when you plug
it in? If so, changing the outlets might help. Or maybe run an
ignition file into the outlet slots (power off first!!!) to clean
the contacts?
|
291.185 | check neutral lines | WHO::SHOREY | | Wed Apr 29 1987 22:05 | 11 |
| check to make sure that they didn't ground the neutral wire when
they did the original wire.
if neutral is grounded and something is drawing current, ground
potential can actually go up. when ground is above ground (!!!???)
that is like a voltage drop.
i know it sounds screwy, but it really happened in a place where
i used to work. they were having voltage drop problems when lots
of things were on and found that the ground inside the building
was about 10v higher than the ground outside. this too is dangerous...
|
291.171 | LITTLE ADVICE | ANOVAX::GUYDISH | | Thu Apr 30 1987 12:57 | 11 |
| BEING AN ELECTRICIAN FOR A FEW YEARS, MAYBE I CAN HELP WITH ONE
SUGGESTION.
14 GAUGE WIRE WILL BE PLENTY BIG ENOUGH FIRST OFF AND WHEN YOU
RUN THE WIRE, GO TO THE SWITCH FIRST AND THE TO THE LIGHT THE REASON
BEING THAT MOST RECESSED LIGHTS HAVE VERY LIMITED SPACE IN THEIR
JUNCTION BOXES AND THE LESS CONNECTIONS AND WIRE NUTS IN THE BOX,THE
BETTER AND SAFER
JOE
|
291.186 | good ideas | TALLIS::SAMARAS | Advanced Vax Engineering LTN | Thu Apr 30 1987 18:04 | 11 |
| Thanks for the ideas so far. I'm going to check this out this weekend.
BTW, there have been some recent new circuits added to the building
that are absolutely fine. I doubt if there is a problem with the
service entering the building. Also, the sevice box was recently
upgraded to all breakers, so there aren't any fuse panels left. There's
just something funnie going on with the "old" BX stuff. The idea about
ground currents in .4 sounds feasible. I'll get out the "OLD" VTVM and
do some measuring.
thanks so far,
...bill
|
291.198 | HELP WITH WIRING! | VENOM::WATERS | The Legend of the Lakes | Fri May 01 1987 13:52 | 22 |
| I have a wiring question! I think I have the right idea in mind
but when it comes to electricity I'd like to make sure!
I have one heavy duty cord coming off my bench...when plugged
in, it turns my fluorescent lights on and makes the outlets to
my work bench LIVE! I want to put a switch in so I don't have to
plug in the cord...just hit the switch..and BINGO! Now the outlet
that I plug into is mounted right beside the main power boc to the
house! I've mounted the switch box right above this outlet! When
I took the outlet apart last night and found that there is only
a black and white wire coming out of the main box into the outlet!
Where is the ground? Shouldn't it be grounded to the outlet box
it self? Could someone just walk me through this..
I have one cord with three wires coming off the bench..
I have the outlet pulled apart and disconnected from the two B/W
wires coming out of the main box...
The switch box is mounted just above the outlet..What do I do????
The power is turned off..I'm stupid...NOT CRAZY!
John
|
291.199 | A possibility | ARGUS::CURTIS | Dick 'Aristotle' Curtis | Fri May 01 1987 14:22 | 21 |
| I've seen instances where the ground wire was wrapped around the
last inch of outer cable insulation in a tight wrap. This just
happens to be the place where the clamping device in the top (or
bottom) of the box holds the cable firmly in place; the effect
is to make a good connection between the ground wire and the box.
You can determine whether this is the case by loosening the screw
on the clamp and (carefully!) pull the cable out about an inch or
so.
Oh, by the way... (getting set to be beaten about the head and
shoulders here)...
I was thinking of adding a couple of outlets to a room here, and
the outlets have ONE ground screw. The ground wire in my 12-2 looks
rather large for putting two wires on the single screw; is it
legitimate (i.e., according to the Electrical Code) to put one wire
on the screw, and do this wrapping jazz with the other?
Dick
|
291.200 | conduit? | WHO::SHOREY | | Fri May 01 1987 14:50 | 10 |
| is the outlet connected to the box with conduit?
perhaps that is the ground?
also, do you want to run your entire workbench through the switch,
or just the lights? you might be better off to leave the bench
as it is and wire a separate circuit for the lights.
brian
|
291.201 | IT IS CONDUIT! | VENOM::WATERS | The Legend of the Lakes | Fri May 01 1987 15:24 | 10 |
| Brian, I'd like to run everything into the switch! I was going
to run the lights into the regular cellar lights that turn on when
the switch at the top of the stairs is turned on! I don't want
my shop lights coming on everytime the kids take a bag of rubbish
down! And I am putting the switch where it can't be reached! Even
though the kids have been told never to go near my power tools..you
never know what a kid will do!I like the idea that the bench and
machinery is dead when the switch is off! There is conduit coming
from the main box to the outlet! Is that my ground? And if so
how do I ground the switch box?
|
291.202 | | BEING::WEISS | Trade freedom for security-lose both | Fri May 01 1987 17:29 | 0 |
291.203 | Some answers | VIDEO::DCL | David Larrick | Fri May 01 1987 17:57 | 49 |
| Nice guess on the conduit, .2.
re .0 and .3: Yes, the conduit is your ground, and a good one too,
assuming all clamps are properly installed.
The idea is to ground both the box and the device (outlet, switch, etc.).
An old technique was to ground the box (perhaps by conduit clamps or by
the wrapping technique .1 mentions), then assume the ground is properly
transmitted to the device by its mounting screws. Modern Code and modern
practice require that the device be grounded too, by running a ground wire
(usually bare, sometimes green-insulated) to the device's grounding screw.
In your case, you can assume that the existing box is properly grounded by
the conduit and its clamp. There should be a (bare or green) wire running
from a screw driven into the box itself to the device's ground screw; if
there isn't one, you should probably install one. To propogate that ground
to another (new) box, connect the ground wire of your Romex to another
screw driven into the existing box. Use a proper Romex clamp, too. Even
better (but more difficult), use conduit.
N.B. If there are any plastic boxes (as opposed to metal ones) involved,
the answers are different, since there's not much point to grounding a
plastic box.
re .1:
> ...is it
> legitimate (i.e., according to the Electrical Code) to put one wire
> on the screw, and do this wrapping jazz with the other?
The "wrapping jazz" must have been legit once - my father taught me to do
it that way - but it's a no-no now. Note that your scheme would transmit
the ground for the outlet, plus that for any boxes downstream, through the
outlet's mounting screws - risky, especially for #12 wire.
As you seem to recognize, the Code NEVER allows multiple wires under a
single screw, so that's not an answer either.
You're supposed to run a bare wire from the device's ground screw, another
from the box's ground screw, and connect both to the ground wire(s) coming
in from outside the box.
Special topless wire nuts exist that allow you to connect two wires
together, but pass the end of one or both wires on through to attach to
screws. Crimp lugs are even better for this purpose.
If there's only one cable coming into the box, it's also possible to loop
the ground wire around the box's ground screw and end the same wire at the
device's ground screw.
|
291.204 | IS THIS THE RIGHT WAY? | VENOM::WATERS | The Legend of the Lakes | Fri May 01 1987 18:53 | 12 |
| So...this is how I'll do it!
First I'll run the wire coming from my bench to the switch, then
I'll put the w-on one side and b-on the other and screw the g-to
the back of the box. I'm then going to run a short cord running
out of the switch box to the outlet box making the connections to
both the switch and the plug and making a good connection of the
ground wire from box to box the grounding of the outlet box will
be cared over to the switch by making the connection to both boxes!
RIGHT??????!!!!
When I do this tonight I don't want any electricity getting me to
excited!!!!!!!!!!!!
|
291.205 | | VIDEO::DCL | David Larrick | Fri May 01 1987 20:32 | 52 |
| Maybe yes, maybe no; I can't tell for sure. A couple of questions arise
from your description:
> First I'll run the wire coming from my bench to the switch, then
> I'll put the w-on one side and b-on the other and screw the g-to
> the back of the box.
Well...what type of "wire" is it? If it's an extension cord (even a heavy-
duty one), you really shouldn't wire it permanently to anything. You might
prefer to install a switch-controlled outlet into which you can plug your
"wire", or even re-wire the existing outlet so it's controlled by the
switch.
Alternatively, if the existing "wire" is Romex that you've attached a plug
to, your existing installation is illegal (but you'll be fixing that). The
point is that extension cords and permanent wiring are different things,
made of different materials, intended for different purposes, and mixing
them causes problems.
I don't understand how you plan to wire the switch. What's usually done is
to switch the hot (black) side of the circuit, and run the common (white)
side straight through the switch box, unswitched.
..."to the back of the box": on the INSIDE of the box, right?
> I'm then going to run a short cord running
> out of the switch box to the outlet box making the connections to
> both the switch and the plug and making a good connection of the
> ground wire from box to box
The "short cord" must be Romex or other official house-wiring cable of the
proper gauge, NOT a hacked-up extension cord.
Your description of grounding both boxes seems OK.
Be sure you NEVER put two wires under the same screw. In a situation where
you'd like to do so, you should connect those two wires to each other and
to a short jumper wire, using a wire nut. Then attach the other end of the
(single) jumper wire with the screw.
> the grounding of the outlet box will
> be cared over to the switch by making the connection to both boxes!
I don't understand this description at all. You haven't said anything
about the grounding screws on the devices (outlet and switch) themselves.
I can't tell whether you understand how to do the job or not - maybe you
just didn't write very precisely. But I would strongly suggest that you
get a book about wiring (the Time-Life one is probably about right for this
job), and read and understand it thoroughly before you proceed. Too much
is at stake here to fool around, and your NOTEing friends won't be down in
the basement watching you!
|
291.206 | Ask a silly question, get material for 3 more... | ARGUS::CURTIS | Dick 'Aristotle' Curtis | Mon May 04 1987 00:28 | 35 |
| .5:
>The "wrapping jazz" must have been legit once - my father taught me to do
>it that way - but it's a no-no now. Note that your scheme would transmit
>the ground for the outlet, plus that for any boxes downstream, through the
>outlet's mounting screws - risky, especially for #12 wire.
Oh good. Guess who showed me that trick? But I don't understand
your objection. I have a 20A duplex outlet made by Leveton here.
At top and bottom are the little metal tabs with captive screws
that bolt the outlet into the box. Turning it over reveals that
the two metal tabs are part of a metal strip that runs the length
of the outlet, and the metal strip has a wing on the side into
which the ground screw is mounted. So, unless the mounting screws
have some sort of nonconductive finish, they too will be electrically
grounded. But then again, if the box is grounded, the screws will
be too, so what's the difference? (Besides which, I thought I stated
that this would involve the cable clamp in the back of the box,
whose screw would effectively be a ground screw for the box -- oh,
come to think of it, there's TWO such screws in the box, perhaps
using one of them would be legitimate?)
>You're supposed to run a bare wire from the device's ground screw, another
>from the box's ground screw, and connect both to the ground wire(s) coming
>in from outside the box.
>Special topless wire nuts exist that allow you to connect two wires
>together, but pass the end of one or both wires on through to attach to
>screws. Crimp lugs are even better for this purpose.
Sigh. Does Spag's carry these topless wire nuts? Or these crimp
lugs? (Are these vanilla looking things, or multi-wire wombats?)
Dick
|
291.207 | | VIDEO::DCL | David Larrick | Mon May 04 1987 02:33 | 27 |
| Please understand that I was describing the Code (as I remember it from a
big project several months ago, and as the Maynard wiring inspector
enforced it), not my personal opinion.
My interpretation is that the Code wants to separate the functions of
mechanical support and electrial/ground continuity. The idea, I guess, is
that the mechanical support (clamps, mounting screws, etc.) can fail or be
taken apart without loss of ground protection. So even though you have two
mounting screws that happen to provide adequate ground, they don't count
for Code purposes; you still need a separate electrical ground path that
doesn't serve any mechanical function.
Note that the above is my guess; the Code tells you what to do, not why.
For me, the Code's ratio of worthwhile stuff to foolishness is high enough
that I don't bother trying to justify each rule. I just do what it says,
especially if there are likely to be inspectors, other electricians, or
other owners involved.
> Sigh. Does Spag's carry these topless wire nuts? Or these crimp
> lugs? (Are these vanilla looking things, or multi-wire wombats?)
Sorry, I don't know. Crimp lugs are pretty widely available (auto parts
stores and even K-Mart, I think). I was lucky enough to receive a Buchanon
crimping tool as a present, so once I found a source for their special
lugs, I was all set - used very few wire nuts.
|
291.208 | | COBRA::DUTHIE | | Mon May 04 1987 14:50 | 36 |
| Well, I hope you didn't try it yet. If you hook the white wire
to one side of the switch, and the black wire to the other side
of the switch, you will blow your fuse/circuit breaker as soon as
you turn the switch on (if your lucky). You need to put the black
wire from your work bench to one side of the switch, and a black
wire from the other side of the switch to your power supply. The
white wire should pass unbroken through the box where the switch
is, and run directly to the power supply. Your idea to use a plug
between the switch and the original outlet sounds OK, but probably
not to code. What you are doing is basically using an extension
cord that has an on/off switch in it. What I would do is...
Put a short piece of conduit between the new switch box and the
old outlet box. You can buy an offset nipple (is that the right
name?) that is about 3" long with about a 1" offset and is threaded
at both ends. This will ground your new box. Run the black wire
from the outlet strip to one side of the switch. Run a black wire
from the other side of the switch to the black wire on the original
outlet. There should be two screws on each side of the original
outlet, this new wire goes to the unused screw next to the black
wire. Run the white wire from the outlet strip directly to the
screw next to the white wire on the original outlet. Run the green
or bare wire from the outlet strip to a screw in the back of the
switch box.
____
| black black 1 is the fuse box
|----------, ,----------, 2 is the old outlet
| |----| |----| 3 is the new switch
1 | |--2-| |--3-| black
|----------' '---, '------------->
| white | to work bench>
| '-------------------->
---| white
(plus green wire to ground)
Jim D.
|
291.209 | switched outlet? | WHY::SHOREY | | Mon May 04 1987 19:33 | 18 |
| i like the suggestion in .10. there is one other way, those of
you who know the CODE correct me if i'm wrong...
you can wire the switch before the outlet, therefore making a
switched outlet. you could leave the extension cord you have
going to your bench, and use the switch to turn it on and off.
i'm pretty sure it's ok to have a switched outlet.
if you have tools on your bench that draw lots of power, make sure
you get a heavy duty switch. overloading a switch can melt the
contacts together, and someday you might think you're turning the
power off but it'll still be on.
if you don't fully understand what you're doing, read up on it or
find somebody to help. when houses burn due to faulty wiring
claims don't get paid.
brian
|
291.210 | Spag's, strikes again. | WELFAR::PGRANSEWICZ | | Mon May 04 1987 20:47 | 6 |
| RE: .8
Yes, Spags has both the wire nuts and crimp lugs. In the electrical
dept., first find the wire nuts in the bins. Now do a 180 degree
turn and you'll see the crimp lugs on the top shelf.
|
291.211 | I would avoid a switched outlet by a workbench | CADSE::MCCARTHY | Excellent, more than a match for poor Enterprise. | Mon May 04 1987 22:54 | 11 |
| > if you have tools on your bench that draw lots of power, make sure
> you get a heavy duty switch. overloading a switch can melt the
> contacts together, and someday you might think you're turning the
> power off but it'll still be on.
I would not run ANY power tool off a switched outlet (well maybe
a hand drill) but I know I would not like to be around when the
contacts start to melt!
mac
|
291.212 | | VIDEO::DCL | David Larrick | Tue May 05 1987 12:48 | 10 |
| > I would not run ANY power tool off a switched outlet (well maybe
> a hand drill) but I know I would not like to be around when the
> contacts start to melt!
Unnecessary paranoia. If the ratings of the switch, outlet, and wire are
all greater than that of the power tool in question, all will be well. If
the power tool's rating exceeds that of the outlet and/or wire, you're in
trouble whether there's a switch in the circuit or not.
It's just a question of using the proper materials for the job.
|
291.187 | please clarify | TALLIS::SAMARAS | Advanced Vax Engineering LTN | Tue May 05 1987 14:25 | 15 |
| RE: .4
>check to make sure that they didn't ground the neutral wire when
>they did the original wire.
>
>if neutral is grounded and something is drawing current, ground
>potential can actually go up. when ground is above ground (!!!???)
>that is like a voltage drop.
How can a grounded neutral cause a problem? If it's grounded at
the receptical (white to GND), then there would be an additional
return path (I think). At the service panel, isn't neutral tied
to ground there anyway??
..bill
|
291.213 | Maybe unnecessary, but ratings are not my only reason | CADSE::MCCARTHY | Excellent, more than a match for poor Enterprise. | Tue May 05 1987 14:31 | 17 |
|
There is one more reason I never use a switced outlet. Have you
ever been drilling a hole with Milwalkee right-angle drill and had
the power shut off and back on quickly? That sucker has alot of
torque. The drill stops, you say "What the....." and loosen your
grip (still holding the trigger) BAM the power returns and it starts
doing a twist! (Never use the trigger lock by the way!). You then
here in the distance "No Bobby, the other switch."
When you work under unknown conditions (kids in area, or at a
customers house) I try to reduce risk so I make sure that I am using a
constant feed outlet and tell the people to send the kids out to
play.
By the way, if the drill stops now, I let go of it QUICK!
mac
|
291.188 | One point (only) | CADSE::MCCARTHY | Excellent, more than a match for poor Enterprise. | Tue May 05 1987 14:35 | 8 |
| By code, the neutral and ground wires are only supposed to be "common"
(connected) at one point. That point is usually in the breaker
panel.
I am not sure if it would cause a voltage drop but the neutral side
of a circut can carry a load (voltage).
mac
|
291.189 | Ground is for safety, not for any current! | DRUID::CHACE | | Tue May 05 1987 14:38 | 10 |
| The reason is that ground in this case would be carrying current
which it is never supposed to do except in a fault condition. The
ground in house wiring is supposed to be a redundant safety and
not a paralleled conductor. If there is any current flow in the
ground then there will be a voltage on the wire due to normal
resistance. This may or may not cause problems with equipment that
uses ground as a reference. It definitely could cause problems at
other outlets if you had an open neutral in the circuit in question.
Kenny
|
291.214 | I'm all set! | VENOM::WATERS | The Legend of the Lakes | Tue May 05 1987 17:56 | 34 |
| Well, thanks for all your suggestions! I had the scare of my life!
I wired it the way I described and ....boom! I knocked the whole house
out! I am presently in the process of buying the duplex I live in so
instead of messing with it anymore I called the landlord and explained
what I did and that I had no power in the house. He said I probablly
had to reset the breaker for the whole house that was located in the
basement on the other side! He said not to mess with it and he would have
his electician come over to wire it up! Its all set now..works great!
He put a seperate breaker in the box for the bench..the bench wire which is
14 gage wire runs to the switch and then a piece of heavy duty solid wire
runs from the switch box to the outlet box! It looks o.k.! That wire from
my bench comes out of one of the long black bars with five plug outlets.
I never use more than one power tool at a time and the switch installed will
never be on when I'm not in the workshop working. I think I'm all set!
Thanks for all your help and concerns. I learned a good lesson..handyman
or not...when it comes to electricity you better know what your doing!!
John
|
291.215 | Electrical questions - Boston | NEPTUN::BERKSON | | Mon Jun 08 1987 17:46 | 23 |
| A few questions about wiring. This ifor the third floor of a 3 family
house with the breaker box in the basement. It is in Boston and
I'd like the answers to conform to the National and Massachusetts
code.
1. Does the 1987 code require GFCI's in the kitchen?
2. Does the code require two separate small appliance circuits in
the kitchen? Of what capacity?
3. My impression was that these two circuits are required and that
they must/should be GFCI's. Since these circuits are sometimes run
via a three conductor cable, how is the GFCI incorporated? I assume
a standard GFCI wouldn't work here.
4. A dishwasher and disposal will be wired on separate breakers
in the basement. Is there any requirement for there to be an additional
switch for them in the unit?
Thanks.
mitch
|
291.216 | | JOET::JOET | | Mon Jun 08 1987 18:19 | 5 |
| Not to sound like a broken record, but check with the building
inspector. Since he (she?) has the final say, it only makes sense
to see what he's looking for.
-joet
|
291.217 | Would rather not ask the inspector | NEPTUN::BERKSON | | Mon Jun 08 1987 19:12 | 5 |
| Only licensed electricians can do electrical work in Boston. I am
looking for answers which can be had without asking the building
inspector.
mitch
|
291.218 | | BPOV09::SJOHNSON | Hill Street Station... | Mon Jun 08 1987 20:30 | 4 |
|
you can pick up the NEC code book at bookstores for about 25 bucks,
if you'd like something official to use as a guideline.
|
291.219 | Where? | DELNI::OSTROM | Andy Ostrom Networks Mktg. 272-7132 | Mon Jun 08 1987 20:39 | 8 |
| re: .3
Anyone know of a bookstore that HAS the 1987 code. I've been looking and
can't find it anywhere...
Andy Ostrom
|
291.220 | | VIDEO::DCL | David Larrick | Mon Jun 08 1987 22:11 | 42 |
| Disclaimers: the following is my opinion only, and I don't know if Boston
has electrical code provisions of its own, in general or specifically for
rental property.
> 1. Does the 1987 code require GFCI's in the kitchen?
Yes, for outlets that are within some defined distance (six feet?) of the sink.
> 2. Does the code require two separate small appliance circuits in
> the kitchen? Of what capacity?
Yes, at least two, 20A each. Note that a refrigerator is a "small
appliance" for purposes of this rule.
> 3. My impression was that these two circuits are required and that
> they must/should be GFCI's. Since these circuits are sometimes run
> via a three conductor cable, how is the GFCI incorporated? I assume
> a standard GFCI wouldn't work here.
Subtle distinction: the requirement is that the OUTLETS (and, as we've
seen above, only certain outlets) be protected by GFCI - not necessarily
the entire circuit. So one option is to run 3-wire cable to all of the
outlets that don't require GFCI, than use normal 2-wire cable (perhaps
tapped off of a 3-wire circuit) for the outlets near the sink.
You may certainly have GFCI on the entire circuit, either via a
service-panel-mounted GFCI breaker, or via a GFCI outlet in the first box
on the circuit. The problem, as you've noticed, is that the available GFCI
packaging doesn't lend itself to 3-wire circuits. Anybody know about
clever GFCI packaging that's more accomodating (or is there an inherent
restriction that I haven't thought of)?
> 4. A dishwasher and disposal will be wired on separate breakers
> in the basement. Is there any requirement for there to be an additional
> switch for them in the unit?
I've never heard of a dishwasher or a disposal that didn't have some sort
of switch associated with it, so maybe I don't understand your question.
re .4, where to find 1987 code: I don't know for sure, but I would think
that electrical supply houses would be a better bet than bookstores.
|
291.221 | 1987 NEC code book @ Ralph Pill | SEESAW::PILANT | L. Mark Pilant | Tue Jun 09 1987 01:24 | 8 |
| RE: .4
Last time I was in, Ralph Pill in Nashua had a large stack of
1987 NEC code books. They also had a smaller stack of 1984
code books. I'm not sure of the price, but a phone call would
correct that.
- Mark
|
291.222 | no gfi for three wire ckts | REGENT::GETTYS | Bob Gettys N1BRM | Tue Jun 09 1987 12:06 | 10 |
| It would be difficult (if not impossible) to construct a
gfi that would work on a 3 wire circuit (two hots and a neutral)
because of the way in which a gfi works. A gfi senses an
imbalance of current between the hot lead and the neutral lead.
In a three wire circuit, the only time that the current is
guaranteed to be balanced between hot and neutral is when only
one side is in use. ANY current drawn on the opposite side WILL
cause the neutral current to be different from the hot current!
/s/ Bob
|
291.224 | MA code book, outlet type GFIs | VIDEO::GOODRICH | Gerry Goodrich | Tue Jun 09 1987 12:55 | 23 |
|
You don't really want the NEC, Mass has a somewhat stricter
version. I am not sure about the present, but you should
be able to find where to purchase a Mass version by calling
state agencies in Boston. The Mass version was just the
NEC book with a prefix of requirements unique to Mass such
as using insulated staples.
As to 3 wire & GFI's - the only purpose is to save wire.
If you are running 3 circuits (2 utility & dishwasher) just
put the outlets near the sink on the single circuit. Or you
can just run 3 single circuits.
Another approach would be to run the 3 wire circuit to the
kitchen with conventional breakers. Wire one circuit to
the first GFI protected outlet and use a outlet type GFI.
Additional protected outlets may be wired from the outlet
GFI.
If you find the source for the MA code book it might be handy
to post it in a seperate note.
- gerry
|
291.225 | | CRETE::FLANNERY | | Tue Jun 09 1987 18:03 | 3 |
| Walden Books at Searstown Mall in Leominster had them
last month. Might still.
|
291.226 | gfi circuit breaker in main | MORMPS::WINSTON | Jeff Winston (Hudson, MA) | Tue Jun 09 1987 21:12 | 4 |
| interesting thing about GFIs - I just had an electrician put them in
all 3 bathrooms - instead of putting $30 gfi's in each one, he put in
regular outlets, and put them all on a dedicated line with a 'gfi
fuse' in the fusebox - new idea?
|
291.227 | | NEXUS::GORTMAKER | the Gort | Wed Jun 10 1987 01:19 | 10 |
| re.11
No, they have been around for along time...some disagree on the
protection they offer. Square-d is a popular vendor for these type
of GFI's but they only work in Sq-d panels federal pacific makes
them for thier panels.
Anyone out there care to expand on why the panel GFI's are
not used as often?
-jerry
|
291.229 | | VINO::KILGORE | Wild Bill | Wed Jun 10 1987 12:05 | 14 |
| Assuming we're talking about a GFCI panel breaker, as opposed to
a GFCI outlet:
o The breaker is VERY expensive ($65 retail, $40 if you have an
electrician friend). The outlet can be had for $10 on sale at
retail outlets.
o The breaker seems to be much more sensitive to surges (lightning
strikes, etc; I have heard of many breakers destroyed by
near strikes, but the outlets seem to come out ok.)
o The breaker is more suitable for new construction, when you have
some control over the wire routing. The outlet can be popped in
anywhere it's needed, as an afterthought.
|
291.230 | Had 'em... Don't like 'em! | USMRM2::CBUSKY | | Wed Jun 10 1987 13:17 | 17 |
| I had a GFI/breaker in the panel for the bathroom and it it/was a royal
pain in the A**. It had a habit of tripping randomly in the middle of
the night, usually 2-3 times a month with NO set pattern, ie only in
electrical storms or wet nights. I replaced the breaker once to no
avail.
We would discover that it had been tripped usually in the morning after
a shower while trying to plug in a razor or hair dryer. Then it was
either a trip to the basement or a loud cry to some else in the house,
"WOULD SOMEBODY PLEASE GO DOWNSTAIRS AND RESET THE G*D* CIRCUT
BREAKER."
I've since rewired and replaced the bathroom outlet with the more
common GFI/outlet. It has never tripped but if/when it ever does the
reset button is right there.
Charly
|
291.231 | Where to get the various electrical code books | ISBG::POWELL | Reed Powell - LCG Marketing - 297-4261 | Wed Jun 10 1987 14:05 | 22 |
|
To get the NEC code call the NFPA at 800-344-3555. As I've said
in other notes, this is good reading for sleep-less nights, but
for the '87 code they got smart and sell their own version of "What
we meant when we wrote this document" as Audel's and others have
been doing for years. Get that version (includes the straight text,
but with explanatory notes, etc., like a lot of the Tax books do).
For the Mass addendum (it's not a seperate book, just a couple of
pieces of paper mimeographed), call the State Bookstore in boston,
and they will tell you the order number, and you can send them the
$$ - they are quick also (NEC takes credit cards). Or you can go
pickup the Mass stuff yourself (better like climbing hills!).
Does the City of Boston have their own? You say that in Boston
a licensed electrician is required. That means Bostons has different
requirements than Mass, which does not require that (FOR YOUR OWN
SINGLE FAMILY RESIDENCE). If Boston already has one screwey trist,
better check with the city (call the inspector and hand him a line
- he cannot trace the call!) they may have others (GFCIs needed
for alarm clocks, toaster ovens, and portable jackhammers).
|
291.232 | Forget breaker-box GFIs | ALEX::CONN | Alex Conn, ZKO | Wed Jun 10 1987 14:29 | 17 |
| RE: Main box GFIs
When replacing our service after it was ripped out by the hurricane last
year, I asked my electrician about breaker-box GFIs. He flatly stated
that he would not put them in. They often fail right out of the carton
or shortly thereafter and only result in dissatisfied customers and
return trips for him. And they're expensive. If you're in love with
having a GFI at the main box control a whole circuit, wire an outlet GFI
next to the main box and connect the whole circuit in question to the
protected side (make sure the GFI outlet is rated appropriately; some
are rated for 20 amps, others are only for 15).
[Actually, the elecrician when pressed *would* put a breaker-box GFI
in, but the price he felt he would have to charge was approaching the
cost of the panel!]
Alex
|
291.233 | | ULTRA::PRIBORSKY | Tony Priborsky | Thu Jun 11 1987 13:44 | 6 |
| Re: GFCI on a 3-wire/2-circuit setup:
I'm absolutely positive that the data sheet with the Leviton that
I put in recently contained explicit instructions for such a setup.
This GFCI is the one that has screw terminals for all connections
instead of the usual braided wire that you use with twist-locks.
|
291.234 | GFCI breaker | VIDEO::FINGERHUT | | Fri Jun 12 1987 12:47 | 8 |
| This is a different GFCI question:
I have a GFCI breaker. Yesterday it tripped, and now I can't get
it to reset. When I move it all the way to the OFF position, it
doesn't stay there, but goes back to the center. It will stay in
the ON position, but there's no power to the circuit.
Is it dead?
|
291.235 | Hidden Reset | SWSNOD::RPGDOC | Dennis (the Menace) Ahern 223-5882 | Fri Jun 12 1987 19:49 | 4 |
| I've sometimes seen cover plates that cover over the reset button on
the front of a GFI outlet. Unscrew the cover plate (if it's one of
those outdoor outlets with a hinged cover) and press RESET.
|
291.236 | GFI's | VIDEO::FINGERHUT | | Fri Jun 12 1987 20:01 | 17 |
| > I've sometimes seen cover plates that cover over the reset button on
> the front of a GFI outlet. Unscrew the cover plate (if it's one of
> those outdoor outlets with a hinged cover) and press RESET.
I know what you're talking about, but no, that's not what I have.
I have a GFI breaker, not a GFI outlet.
What's the test button do on the breaker anyway? On mine, it doesn't
do anything. Is it supposed to trip the breaker?
I assume the breaker is broken. BTW, that's the second one I've
gone through. I'll be replacing it with GFI outlets (I have 2
outlets each running directly off the breaker, so I assume
I need 2 GFI outlets?)
Now I know why GFI breakers aren't used much..... While it was
working, it tripped very often.
|
291.237 | | VIDEO::DCL | David Larrick | Sun Jun 14 1987 02:23 | 20 |
| re .21
> I'll be replacing [a GFI breaker] with GFI outlets (I have 2
> outlets each running directly off the breaker, so I assume
> I need 2 GFI outlets?)
If you really do have two separate cables running directly from the service
panel to the two outlets, then yes, you need two GFI outlets (barring some
re-wiring).
But if the cables run from the service panel to the first outlet, and then
from the first outlet to the second outlet, then you only need one GFI
outlet, to be installed in place of the existing first outlet.
It is possible (and common) to wire a GFI outlet so that "downstream"
outlets are GFI-protected. It is also possible to wire it so that
downstream outlets are NOT protected - although it makes sense to protect
downstream outlets whether you're required to or not, unless you have some
overwhelming reason for not doing so. Instructions for both styles of
wiring should come with the GFI outlet.
|
291.239 | GFI breaker | VIDEO::FINGERHUT | | Tue Jun 16 1987 15:23 | 16 |
| > BTW was the breaker ever exposed to the weather, perhaps as part of a
>temporary service; or a leak during construction? Did it get itself
>cycled on a regular basis? Can you tell us the brand?
It was never exposed to the weather or used as temporary service.
BTW: The one I did use in my temorary hookup also broke after a
couple months.
> Did it get itself cycled on a regular basis?
What?
> Can you tell us the brand?
Bryant.
|
291.240 | Preventive maintenance for breakers | VIDEO::DCL | David Larrick | Tue Jun 16 1987 17:33 | 7 |
| >> Did it get itself cycled on a regular basis?
> What?
Yup, breakers last longer (and are more likely to be re-settable when they
trip) if they're manually switched off and on periodically. A couple of
times a year is plenty.
|
291.241 | Mass Electric Code at State Book Store. | DELNI::OSTROM | Andy Ostrom Networks Mktg. 272-7132 | Tue Jun 16 1987 21:17 | 17 |
| I stopped by the State Book Store the other day. They no longer publish the
"entire" Electrical Code, but just the changes for Mass. It cost a whopping
$1.25 (might have been $.75, can't remember). I'd be glad to make some copies
for folks -- or if there's enough interest maybe two or three of us could
divvy it up and type it in. Then we could put the parts together and add it
as a note -- it should remain current till 1990.
They also sell lots of other books including a cut-down version of the state
Building Code with only sections 1 and 21. These apply to one and two family
dwellings. The cost was $7.00 and it came in its own loose leaf binder.
Andy Ostrom
BTW -- Good luck getting them on the phone -- I tried 3 or 4 times a day for
a week.
|
291.190 | WILD WIRING | TALLIS::SAMARAS | Advanced Vax Engineering LTN | Tue Jun 30 1987 13:29 | 24 |
| It's been a while, but I finally got this electrical problem solved.
Initially, the problem was excessive voltage drops. After some
investigation, I found 3 outlets with NO ground continuity, and 2 with
backwards polarity. At this point I got suspicious that the previous owner
did something stupid. Sure enough, after 2 whole Saturdays of tracing
circuits, and running up and down to the basement 300 times turning power
off and on, I found the problems. It seems that the previous owner lowered
the kitchen ceiling a few years back. Since there was a light fixture in
that ceiling, he just ran an extension wire from the old ceiling fixture
to the new lowered one. Pretty stupid: reverse polarity, no ground, wire
size too small, loose conections, bare wires. I'm just real happpy I
found it. Luckily, the "old box" was directly above the new one, so I
only had to enlarge the existing opening slightly to do my handy work.
I installed a complete new box at the "new" ceiling level. All of the
wiring in that area now terminates in this new box. I'm happy, everything
works right, and I can use my u-wave in the kitchen!
BTW, I still get a 10V drop in this circuit, but at 10Amps and 200 ft of
wire, 1 ohm ain't too bad.
I guess the previous owner was proud of his wiring. After all it worked
didn't it? :'))
..bill
|
291.191 | Nice work | VIDEO::DCL | David Larrick | Tue Jun 30 1987 13:45 | 8 |
| Congratulations, and thanks for reporting back to us.
A helper and a pair of walkie-talkies or intercoms are indispensable for
that type of work.
Then again, maybe the l - o - n - g walk to and from the breaker box
makes us take enough time to think over the problem thoroughly, encourages
us to make every test count.
|
291.242 | Horizontal T&G boards over electrical boxes? | STAR::SWIST | Jim Swist ZKO1-1/D42 381-1264 | Mon Jul 13 1987 17:15 | 23 |
| I hate writing new notes (2nd one today) but this
electrical/woodworking combo question seems to be new.
How do you install horizontal tongue-and-groove boards over electrical
boxes? This one has me baffled - the 1x8 boards have about a 3/4"
tongue. If I cut out the hole exactly where the box is, then I
can't lower the board onto the one below it because the box is in
the way, and that's the only way you put t&g boards on. If I elongate
the hole by 3/4" such that I can press it over the box rim and clear the
tongue below it before lowering it in place, then the hole is too
big to seat the ears of the outlet/switch nicely against the finish
wood (it's also pretty close to being exposed under the switchplate.
I have the same problem even if I straddle the box over a joint
(upper piece is OK, but lower piece has the same problem).
I suppose I could put the boxes in after the fact (use old-work
boxes with ears), but I'd sure like to do all my rough wiring first.
Is there some standard solution to this problem?
Jim
|
291.243 | Installing T&G around electrical boxes | SEESAW::PILANT | L. Mark Pilant | Mon Jul 13 1987 17:51 | 8 |
| One thing that I have done to install T&G over electrical boxes
is to cut out the desired size opening, then back bevel the edge
parallel to the tongue (or groove as the case may be). There is
usually enough give in the tongue & groove to allow then to engage
while still keeping the exposed surface gap to a minimum. I usually
use about a 15 or 20 degree angle for the bevel.
- Mark
|
291.244 | T&G boards over outlets | VIDEO::FINGERHUT | | Mon Jul 13 1987 18:21 | 6 |
| I had the same problem.
I cut my bottom board to just the right width so that there was
a T&G joint where all my outlets were. If 2 boards meet at the height of
the boxes, you don't have the problem.
|
291.245 | splicing wires in ceilings? | REMEDY::KOPEC | How did I get myself into this?? | Thu Jul 23 1987 14:49 | 21 |
| In order to install some skylights, I need to move a couple
of wires out of the way.. unfortunately, the wires themselves are
too short to be routed any way other than the current routing.
So, I have a couple of choices:
1.) replace the wires from source to destination. This would be
a bear to do; I'd have to remove and rewire 6 nailed-to-the-studs
boxes (some double-gang), snake wires through walls with blocks
in them, etc...
2.) stick some junction boxes up in the rafters and splice. Sounds
rational, but it seems to be a technical violation of the Code
(junction boxes must be accessible without removing any of the
building, 370-19).
I can't believe that Joe Contractor would go through all the hassle
of (1). Do people really do (2) and nobody cares, or is there a
special method of splicing in concealed spaces?
...tek
|
291.246 | Access panel | VIDEO::DCL | David Larrick | Thu Jul 23 1987 15:20 | 5 |
| One possibility is to put the splice boxes behind an access panel. If you'll
be putting fancy trim boards around the indoor skylight opening, make one of
those trim boards removable, and hide the boxes behind that. Or, if you'll
have a light shaft through the attic, you can put the access panel up in a
side wall of the light shaft.
|
291.247 | $8 covers | VIDEO::GOODRICH | Gerry Goodrich | Mon Jul 27 1987 14:47 | 16 |
|
I mounted a smoke detector over my junction box, it looks
like it belongs there. I didn't need another smoke detector
but it solved the cosmetic problem.
This situation may need two splice boxes, two smoke detectors
might look a bit silly, any chance you can have a removable
piece of trim somewhere? In the spirit of the code, a stranger
should be able to find it.
Once I did cheat and covered a splice. I soldered the wires
and carefully insulated them. This was as close as I could
get to an "unspliced" joint.
- gerry
|
291.248 | ex | TALLIS::SAMARAS | Advanced Vax Engineering LTN | Mon Jul 27 1987 18:03 | 11 |
| I recently remodeled a bathroom, and part of the renovation was alot of
rewiring. The electrician said that I'd have to have access to the old box
in the ceiling. I wasn't too pleased about having an access cover in the
middle of my new ceiling, but I went along with it.
Anyhow, a few weeks ago I discovered a wierd wiring problem left over
from the previous owner/hacker. After tracing wires all over the place, I
*needed* to get at the bathroom connection to test the circuit.
I was VERY tempted to bury that box; luckily I didn't. It doesn't bother
me much any more....
|
291.249 | Splices? We don't need no steenking splices! | JOET::JOET | | Tue Jul 28 1987 14:15 | 3 |
| You could always pull another wire of the proper length.
-joet
|
291.250 | the code is for standard construction | NRADM2::MITCHELL | george..ya snooze - ya lose | Wed Jul 29 1987 15:17 | 8 |
|
Add the length of wire needed to get them out of the way,
add the necessary boxes to house the splices, solder the
connections and use "wire nuts" on top, tape them if you wish
and bury them....no problem. Re-running new wiring is out
of the question. you'd be tearing the house down to do it.
___GM___
|
291.251 | this hurts my psyche, but... | REMEDY::KOPEC | Joe Isuzu for President! | Wed Jul 29 1987 15:44 | 16 |
| > and bury them....no problem. Re-running new wiring is out
> of the question. you'd be tearing the house down to do it.
yes, this is exactly the problem; I'd have a few days of sheetrock
work if I wanted to run new wires; the wires are stapled (so I can't
pull a new wire through with the old one), and the walls have blocks
in them, so I can't snake... plus, the boxes are all new-work boxes
that won't come out without a fight (read: rip and patch sheetrock).
I guess I don't feel too bad about doing a concealed splice; it's
not a junction (where I might need to get into test some part of
the circuit), it's just a striaght-thru splice..
time to close my eyes....
...tek
|
291.252 | | AUTHOR::WELLCOME | Steve | Wed Jul 29 1987 17:09 | 5 |
| HOWEVER:
No matter HOW you do it, an inaccessible splice is against the code.
If you still go ahead and make one, at least put it in a box.
|
291.253 | | PHENIX::CONNELL | Ha..I'd like to meet his tailor.. | Wed Jul 29 1987 18:21 | 11 |
| > HOWEVER:
> No matter HOW you do it, an inaccessible splice is against the code.
ALSO:
Should (God forbid) you have a fire, and the splice be (or even
suspected to be) the cause, your insurance could be negated.
Is it worth the risk?
--Mike
|
291.254 | More creative solutions | VIDEO::DCL | David Larrick | Thu Jul 30 1987 12:52 | 32 |
| I'm surprised that none of the preceding suggestions was practical. Here
are a couple more, mostly obvious ones, mostly inspired by Gerry's smoke
detector. Sometimes you gotta do what you gotta do, but I urge you to
think hard one last time about alternatives.
1. Attach a lamp to the workbox, either recessed or hung from the ceiling.
2. A track light power feed. You don't need to install the track light;
having the power feed there makes it look like there used to be track
lighting, or like you're planning for future track lighting.
3. Just a duplex outlet. Good conversation piece. Explain that it's for
Christmas lighting, or for your roof heat cables. (Doesn't have to be
true...).
4. Don't put a switch up there. Code calls for switches to be within some
distance from the floor, something like seven feet.
5. There exist blank box covers that are meant to be unobtrusive in
ceilings, to cover up now-unused boxes or as placeholders for future
lamps etc. The ones I've seen are round and white.
6. Use a regular blank box cover, carefully install it flush with the
ceiling, and paint over it.
It sounds like whatever you do will be near the new skylight. Thus it's
more likely than your average electrical work to be exposed to water
problems, and to structural weirdness as your skylight framing settles
under load. And if you bury this work on the roof side of the attic
insulation, it'll also be exposed to more temperature variation (and,
again, moisture) than usual. My point is that, if I HAD to bury a box
someplace, this is not the location I would choose.
|
291.255 | ALUMINUM WIRING QUESTIONS | VRTMP1::SMICK | Van C. Smick | Tue Aug 25 1987 22:34 | 21 |
| Since there is no note on aluminum wiring, I'll start one.
I have read several notes on the hazards of using aluminum (AL) wiring
in the house. I have not seen anything on AL wires on lamps, appliances
etc.
SPECIFICS:
I have a clear glass lamp and I want to use the "clear" decorative
wiring sold in many hardware stores. After purchasing it and cutting
it to size, I suddenly noticed that the wire is AL. The light
socket has screw connections (one copper, one AL), and the plug
I used is the clip on plug -- which has brass connections.
QUESTIONS
Is there any danger in using AL wire?
Is there any danger in mixing the copper of the light socket and
plug with the AL wire? If so, are there AL light sockets and plugs?
|
291.256 | | STAR::GOLDSTEIN | Andy Goldstein, VMS Development | Tue Aug 25 1987 23:10 | 5 |
| Are you sure the wire is AL? Never heard of aluminum wire being used
in light gauge cord. I'll bet it's tinned or plated copper. Strip some
insulation and scrape the wire with a knife a while. If it turns reddish
it's copper. If it's real soft and stays silvery white, it's AL and I'd
throw it out and get some clear insulation copper wire from Radio Shack.
|
291.257 | | DICKNS::WELLCOME | Steve | Wed Aug 26 1987 22:45 | 2 |
| I'll also bet on the tinned copper. Virtually certain. 99.99999%.
|
291.258 | YEP -- All that glitters is not gold | DSTAR::SMICK | Van C. Smick | Thu Aug 27 1987 11:40 | 1 |
| You were right. Thanks I can sleep easy now.
|
291.172 | More wiring help please | RECKON::GONYEO | | Mon Aug 31 1987 14:41 | 15 |
| I have a situation similar to that described in .0 but I really dont
want to run the power to the switch first (as recommended in .3). The
switch is on a finished wall and there is only one wire going to it now.
My question: what is the correct wiring configuration?
Power Dimmer
Source ================================================== Switch
|| || ||
|| || ||
|-------| |-------| |-------|
| Light | | Light | | Light |
|-------| |-------| |-------|
Thanks. Jim
|
291.173 | simple series hookup | TOOK::CAHILL | Jim Cahill | Mon Aug 31 1987 16:50 | 30 |
| I don't understand your comment about "... there is only one wire
going to it now." I'm assuming you mean one cable, containing three
wires (black for hot, white for neutral, and bare copper for the
ground).
If the wiring is indeed as shown in your diagram, wire each light
up like this (for simpicity, the grounds are not shown; they should
be connected together, as well as to each junction/switch box):
(junction box)
+------------------------------+
>>>===============|------------------------------|===============>>>
(power in from |\ (white neutral wire) /| (power out to
source or pre- | \ / | next light or
vious light) | \ (black hot wire) / | dimmer switch)
| \_________ _________/ |
| | | |
+-------------|---|------------+
| |
<out to light>
At the dimmer switch, just connect the two leads of the switch to
the black and white wires. If the switch has screws instead of
leads, the black wire goes to the brass screw while the white wire
goes to the silver-colored screw.
P.S. I'm assuming your switch can handle the load of the three
lights... you should not!
Jim
|
291.174 | Yes, I know.... | TOOK::CAHILL | Jim Cahill | Mon Aug 31 1987 16:58 | 8 |
| Obviously, the disadvantage of this wiring circuit is that if one
lamp burns out, they all go out (since the blown bulb breaks the
looped circuit to the other two). Because you don't want to or
can't run the power to the switch first, this is the price you have
to pay. Since there's only three lamps on the switch, it shouldn't
take too long to find the burned out bulb.
Jim
|
291.175 | Smells bad | TALLIS::SAMARAS | Advanced Vax Engineering LTN | Mon Aug 31 1987 17:46 | 9 |
| Can you run power to the "last" light box first? Then you could connect
the switch and power the remaining lights from right to left (per your diagram).
I'd avoid series lighting at ALL costs. I'd go to the dentist before I'd
do a series wire. Besides, each light will be 1/3 as bright.
...bill
|
291.176 | a small piece of 14-3 would be required... | 3D::WHITE | Randy White, Doncha love old homes... | Mon Aug 31 1987 18:37 | 36 |
| RE:1047.4
>I have a situation similar to that described in .0 but I really dont
>want to run the power to the switch first (as recommended in .3). The
>switch is on a finished wall and there is only one wire going to it now.
Jim
I assume that what you currently have is this.
Power -------------------------------------------------- Dimmer
Source ---------------------- --------------------------- Switch
| |
| |
|-------|
| Light |
|-------|
If you don't want to rerun the entire leg but can get at the middle
section you could wire it thusly (grounds not shown for clarity):
14-2 14-2
Existing New 14-3 Existing Dimmer
<--| |--> Switch
BLK
Line BLK ---x-------------------------------------x-------- BLK Line
Neutral WHT -----x---------------x----------------
| | WHT |
| --------------|-x-------------|-x---------- WHT Load
| | | | RED | |
| | | | | |
| | | | | |
|-------| |-------| |-------|
| Light | | Light | | Light |
|-------| |-------| |-------|
Good Luck
|
291.177 | | RECKON::GONYEO | | Tue Sep 01 1987 15:52 | 26 |
| Thanks to all that responded. Re .8, one clarification question. Which
WHT wire (the neutral or the load) goes to which wire (WHT or BLK) on
the lights?
14-2 14-2
Existing New 14-3 Existing Dimmer
<--| |--> Switch
BLK
Line BLK ---x-------------------------------------x-------- BLK Line
Neutral WHT -----x---------------x----------------
| | WHT |
| --------------|-x-------------|-x---------- WHT Load
| | | | RED | |
| | | | | |
| | | | | |
|-------| |-------| |-------|
| Light | | Light | | Light |
|-------| |-------| |-------|
Re: .7, could you explain why you do not like this type of wiring? I
do not understand why each light would be 1/3 as bright.
Re: .5 - .8, all assumptions are correct.
Thanks. Jim
|
291.178 | clarifications ... | 3D::WHITE | Randy White, Doncha love old homes... | Tue Sep 01 1987 16:19 | 38 |
| RE:1047.9
Hi Jim,
> Re .8, one clarification question. Which WHT wire (the neutral or the load)
> goes to which wire (WHT or BLK) on the lights?
14-2 14-2
Existing New 14-3 Existing Dimmer
<--| |--> Switch
BLK
Line BLK ---x-------------------------------------x-------- BLK Line
Neutral WHT -----x---------------x----------------
| | WHT |
| x-------------|-x-------------|-x---------- WHT Load
| | RED | | RED | | ^
| | | | | | /
| | | | | | This wire should
WHT | | BLK WHT | | BLK WHT | | BLK have black tape
|-------| |-------| |-------| wrapped around
| Light | | Light | | Light | the white plastic
|-------| |-------| |-------| to indicate it
is a hot line.
>Re: .7, could you explain why you do not like this type of wiring? I
>do not understand why each light would be 1/3 as bright.
.7 illustrates a series connection of lights, like the old christmas
strings. In a series connection with equal loads the total available
voltage will be proportionately divided against the loads. In the
illustration shown 1/3 or approx. 40 volts. The current in this
configuration will be the same for all loads.
In the illustration above the lights are wired in parallel though
each will have its own current draw, they will all have the same
voltage across the load.
Hope this helps - Randy
|
291.179 | LOOKS good now! | TALLIS::SAMARAS | Advanced Vax Engineering LTN | Tue Sep 01 1987 22:36 | 5 |
| RE:.5 and RE:.6 assume series wiring which isn't cool. The last
reccomendation is a parallel connection wich is fine (that's what I'd
do). Each light has a direct shot to the power line.
...bill
|
291.180 | forget series, go with parallel | TOOK::CAHILL | Jim Cahill | Wed Sep 02 1987 13:47 | 6 |
| Re .11
Yup, I agree.... Although a little more complicated, it does avoid
the problems with series wiring.
Jim
|
291.265 | Confused Ground or Grounds for Confusion... | SAWDST::PAQUETTE | Colonial Computing Nut | Wed Nov 25 1987 14:21 | 19 |
| I'm confused about electical grounding!
I have an OLD house that has a NEW 100A service. The feed in has the ground
wire attached to the "GROUND BAR" like what I expect. Some of the house
circuits are TWO wire with NOGROUND and others are THREE wire. On the
THREE WIRE circuits the BLACK (hot) is connected to the circuit breaker but
the WHITE and BARE wire are attached to the same point on the BAR??
Is this some MICKEY_MOUSE wiring setup or what??
I want to splice some THREE wire onto a TWO wire circuit running out of a
light fixture. What do I attach the ground wire to?? The WHITE ??
If I didn't have to face snaking wire around/throught 10" beams, I'd
rewire the whole thing from scratch with THREE wire but....
Can anyone shed light on what's going on here....
-=Dennis
|
291.266 | separate but equal paths to ground | CIMNET::LUNGER | Dave Lunger, 291-7797, MET-1/K2 | Wed Nov 25 1987 14:38 | 13 |
| What you see is correct. The three wire circuit gnds connect to the same point
electrically in your panel. The idea though, is that at the other end
of the circuit the white or neutral wire is your normal path to ground...
there will be current in this wire. The ground wire is a separate (but
basically equal) path to ground for things like chassis, metal parts on
appliances that get handled, etc. This does not carry current. If there
should be a short, the ground wire will safely carry the current to ground.
I believe that GFCI's somehow use this to work... ie: if current goes thru
the ground wire, the circuit trips and/or if current in white wire does
not equal current in black circuit trips... I'm not sure of this, but it
works something along those lines...
|
291.267 | Be Careful | CASSAN::OLSON | C. JOHN OLSON DTN: 297-5344 | Wed Nov 25 1987 14:47 | 14 |
| The tying of the White(AC low) to the Bare Ground wire is common
in three wire house wiring. They are trying to make them at the
same Power Reference Point.
As for connecting or tapping power from a light fixture, be careful.
If the Black(AC High/Hot) is being switched, then you could have
a Amperage problem for the circuit that you are trying to create.
The switch can be your weak link for the circuit. Always verify
your source when tapping into another box.
What are you trying to power off this light fixture??
John
|
291.268 | grounds for confusion | YODA::BARANSKI | Too Many Masters... | Wed Nov 25 1987 15:03 | 63 |
| I've always been confused about electrical service grounding... and I'm supposed
to be an electrical engineer! :-)
The way I understand it, there's this here wire with you on one end, and the
electrical company on the other end. There may also be God only knows howmany
transformers on the wire between you and the electrical company, but I'm
confused enough as it is, so I'll skip that part.
Anyway, you have this here wire from the electrical company, and it's *hot*,
electrically speaking. Now there's a couple of other wires that come into your
house from the electrical company, but basically they are there so that you
think that you are getting more for your money from the electrical company and
electricians.
Only one of the extra wires has any meaning, it's the opposite phase of the
*hot* wire from the electrical company. I think it's the electrons the
electrical company sold you last month, or something. This wire is for when the
electrical company wants to sell you more electricity, and rather then replace
the wire you already have with a bigger one, they give you two wires, and charge
you twices as much by selling you the electrons twice.
One of the other extra wires simply goes out to your telephone pole, and goes
into the ground, in other words, it's grounded. Ah Ha! you say, that's where
the ground is, right? Wrong! There's a half dozen or so grounds, and this is
only the first one. Again, these extra grounds are to make you feel like you are
getting your money's worth. All these grounds go into the ground, and a bunch
of wires tied to a common point all have the same voltage, right?
So then you have two or three or more (I'll forget about the other wires if you
will) wires coming into your house. Now they start putting colors on the wires
to confuse you. They call one wire "white", and one wire "black". The "white"
is supposed to be the *hot* one, but that doesn't mean anything at this point,
because you can get the blue spark fairy to come forth from either one of them,
so just forget about that distinction.
Usually close to where your wire come into your house, there is a fuse or
breaker box. Here they add another wire, and call *it* ground, too. This wire
usually doesn't have any insulation put on it; the electricians save money this
way, and immediately pass the savings on to their bank accounts. This wire
also goes into the ground, so I suppose they have a good reason for calling it a
ground, but what did they do to that perfectly good ground that they had? Nobody
knows, all I can tell you is that it's ruined, forever, and ever.
Now you have three of four or more wires (see above...) that you run all over
your house. Now the electrical code is written by electricians, for
electricians, to make money... that is why the code says that you have to have
an outlet every six feet of wall. Sheeash, you'd think they never heard of
extension cords.
Eventually, all these wires go to a box in the wall that you can stick a plug
into (or your fingers) to get electricity out of the wall. And this plug goes
to a cord that goes to a transformer, and a power supply, and there is another
entirely unassociated ground on the other side of the power supply. This is my
home territory, where I went to school, where the electrons and grounds behave
as the laws of nature and God intended them to.
But wait... there's three more grounds here: ground, chassis ground, and
floating ground!!! AAAAAARRRRRGGGGHHHHhhhhh...... <silence> <except for a few
whimpers>
Jim.
|
291.269 | | DICKNS::WELLCOME | Steve Wellcome (Maynard) | Wed Nov 25 1987 15:49 | 20 |
| Re: .3
>to confuse you. They call one wire "white", and one wire "black". The "white"
>is supposed to be the *hot* one, but that doesn't mean anything at this point,
NO! The **BLACK** wire is hot, the ***WHITE*** is neutral.
Re: .0
Yes, the neutral and ground get tied together at the service entrance,
AND AT THAT POINT **ONLY**!!! Do NOT connect them together anyplace
else. You cannot ground boxes, outlets, etc. on your 2-wire circuits.
According to code, for a 2-wire circuit with no separate ground
wire available, you're supposed to use only 2-prong sockets (without
the hole for the grounding prong on a 3-prong plug). That's to
keep somebody from thinking an applicance with a 3-prong plug is
grounded just because he plugged it into a 3-prong outlet. If you
want a grounded outlet on a circuit that is currently 2-wire, you'll
have to run a new line from the service entrance and rewire that
circuit.
|
291.270 | Ground is ground the world around ??? | TOOK::ARN | | Wed Nov 25 1987 15:59 | 8 |
|
I'm glad someone came out of the closet. I was always embarrassed
that I was an Electrical Engineer and could not explain it either.
I'm convinced it's a secret and they tell you when you get your
electrical license or something.
Tim
|
291.271 | | DICKNS::WELLCOME | Steve Wellcome (Maynard) | Wed Nov 25 1987 16:07 | 29 |
| Re: .0 again
You shouldn't splice 3-wire onto a 2-wire circuit, because you can't
ground it properly. Either go all the way back to the service
entrance with 3-wire, or extend the 2-wire circuit with 2-wire.
You can probably use 3-wire and just clip the ground wire short
so it's obvious that it's not to be used, but I'm not sure about
that.
Is the present wiring BX (armored cable)? If so, the metal armor
may be grounded. HOWEVER, it may not be an acceptable ground
according to the code. If it's BX and IF it has an internal metal
strip inserted inside the sheathing (like a wire, only it's sort
of flat), then you can use the sheathing as a grounding path. If
there is no metal strip, then the sheathing is not acceptable as
a grounding path and you must treat the circuit as a 2-wire circuit.
Assuming the metal strip is there, you should be able to connect
the ground wire of your 3-wire cable to the junction box where you
are making the splice and continue from there. However, I am a
little hazy on the details here, and that may not be correct.
To explain things a bit further, BX cable, by itself, has a relatively
high resistance. It's steel, which is not all that great a conductor
compared to copper, and the spiral construction doesn't provide
a very good ground path exept around and around and around and
around...the spiral. Hence the inserted metal strip; it runs linearlly
inside the armor sheathing and provides a ground path of acceptably
low resistance and good reliability.
|
291.272 | I have seen the light.... | SAWDST::PAQUETTE | Colonial Computing Nut | Wed Nov 25 1987 16:24 | 16 |
|
WOW!!! Thanks for the plentify and rapid response!
There is TWO wire running from the panel to a "pull_chain" light fixture.
A piece of BX cable is spliced to the two-wire coming into the light and
runs to another "pull_chain" light fixture in another room.
I want to replace the OLD fixtures (can't find globes to fit them) with
NEW pull_chain fixtures and since there are only two lights on the entire
20A circuit, I'd like to tap off the line and add 4 outlets (2 in each room)
I think I'll use three-wire for the outlets and tape up the ground for now.
After the holiday crunch, I'll go back and feed new wire from the panel...
-=Dennis
|
291.273 | Is the box big enough? | VIDEO::DCL | David Larrick | Wed Nov 25 1987 16:51 | 6 |
| When you "tap off the line", be sure the box from which you do so is big
enough to hold the additional wires and wire nuts. Cramming too many
things into too small a box is difficult, dangerous, and contrary to Code.
I trust your "20A circuit" uses 12-ga. wire in addition to having a 20A
breaker.
|
291.274 | what the power company gives you | TOOK::CAHILL | Jim Cahill | Wed Nov 25 1987 16:53 | 60 |
| The difference between grounds (chassis, equipment, safety, etc.)
may be confusing, but what it boils down to is this: there should
be only one point in an electrical system where all the grounds are
brought together and joined. This avoids something known as ground
loops.
First, what the wires are.... Most houses have three wires coming
off the pole: two insulated wires and a bare wire. They usually
appeared to be all twisted together, but in some localities may
be seperated. Older houses that do not have 220 volt service have
only one insulated and one bare wire; the reason why will hopefully
become apparent after reading the following. If you measured the
voltage on the bare wire by putting your meter between it and "ground",
it should read close to if not 0 volts. The other two wires contain
110 volts measured relative to the bare wire (meter probes placed one
on the bare wire and one on either of the two other wires). However,
a meter placed between the two insulated wires will read 220 volts.
This is because the voltage is constantly switching back and forth
between positive and negative phases; when one wire is at +110v, the
other is exactly 180 degrees out of phase, or -110v. Remember the
old sine wave??
These three lines are brought through the meter and into a circuit
or fuse box. The bare wire gets connected to a copper bar containing
many connection points, while the two "hot" wires go through a double
(a.k.a. ganged) main breaker. Notice that the bare wire does not
get interrupted by a breaker; this is an important safety feature!!
Once through the main breakers, the two hot lines feed both single
110v circuits and larger capicity 220v circuits.
The larger circuits that feed electric dryers, hot water heaters,
and stoves contain both a red and a black wire (along with one or
two others: a white and possibly a bare). The black wire gets
attached to one of the two insulated feeds from the power company,
while the red wire goes to the other insulated feed. The smaller
110v circuits contain only a black wire, in addition to the white
and bare wires. This can go to either of the above two feeds, but
the system as a whole should balance the load drawn from each feed
as closely as possible (it makes the power company very happy by
causing less wear and tear on their equipment!).
Every electrical circuit contains a white wire. These get connected
to the bar containing the bare feed wire. If the circuit also has
a bare grounding wire, that too gets connected to this bar. This
bar is also attached to a good ground point, either a cold water
pipe coming into the house, a grounding rod driven several feet into
the ground, or a cable that's buried along the foundation.
In the simple case where's there's only one fuse/breaker box, the
white and the bare wires are tied together and grounded. It gets
more complicated when there are multiple fuse/breaker boxes. In
this case, the white and bare wires should not be joined together
in the secondary distribution boxes, but attached to seperate bars
that are isolated from each other. But that's another story.
I hope this clears up the confusion about what the lines coming
from the power company provide you. Sorry if this has been boring
for any other power distribution junkies!
Jim
|
291.275 | fingers engaged before brain.... | TOOK::CAHILL | Jim Cahill | Wed Nov 25 1987 16:59 | 9 |
| > two others: a white and possibly a bare). The black wire gets
> attached to one of the two insulated feeds from the power company,
> while the red wire goes to the other insulated feed.
Least anyone misunderstand what I wrote in .9, the red and black
wires must go through a double breaker (and the main breaker) before
they connect to the main power company's feeds.
Jim
|
291.276 | Like water pressure? | AKOV75::CRAMER | | Wed Nov 25 1987 18:15 | 38 |
| re: .9
I understand, I think, what you, and others have said, I have
just one question left concerning the original scenario.
What is the problem with connecting the ground and neutral (white)
wires to the neutral wire of the existing 2 wire circuit?
It seems that the net effect will be the same.
+-- junction box
V
neutral bar in box - old white ooooooo+oooooooooo new white - fixture
\________________ ground
versus a complete three wire circuit
neutral bar in box -oooooooooooooooooooooooo new white - fixture
\_______________________ ground
With your comment on "ground loops" I can only assume that in the
former circuit the electricity which should go all the way from
the fixture, at the end, to the neutral bar (and thence to ground?)
will "loop" back TOWARD the fixture from the connection at the
junction box, probably because the resistence on the old white
wire is higher than the new white or new ground, depending on which
wire (white or ground) is carrying the current.
And the reason that this doesn't happen in the three wire circuit
is that the neutral bar (aka ground) is the path of LEAST resistence.
Or am I totally lost?
Alan who had an electrician wire the new range outlet
|
291.277 | Do it right, it's more painful to do it over | ARGUS::CURTIS | Dick 'Aristotle' Curtis | Fri Nov 27 1987 02:25 | 18 |
| .8:
If I read the code synopsis book correctly, the minimum acceptable
box for an outlet with 2 12-3 cables (i.e., a daisy-chained set
of boxes) will be the size that's about 3 1/2 inches deep
(approximately the depth of a planed 2 x 4 -- we ran into a bit
of hassle with the screws going a little beyond the 2 x 4, and hitting
foundation). It was an annoyance to discover that I'd bought
about 8 boxes that were too shallow, but at least the ones of the
correct size allow you to fold the wires and push them and the outlet
in without being a Hercules.
If you're getting the boxes at Spag's, look for the deeper of the
two sizes of metal boxes (don't know what the measurements are for
the plastic ones, which I thought I saw recently).
Dick
|
291.278 | Richter's near Nashua?? | FREDW::MATTHES | | Fri Nov 27 1987 10:22 | 4 |
| I've seen the book 'Richter's' touted here and elsewhere in this
file.
Anyone know where I can obtain a copy near Nashua N.H. ??
|
291.279 | grounding. | MRMFG1::J_BORZUMATO | | Mon Nov 30 1987 13:26 | 10 |
| dennis, your 100a service hook is fine. its wired correctly.
you should also find a ground going to the incoming water line.
or perhaps a ground rod. (make sure one of them is there)
we're in the same boat when it comes to old houses. mine
is 100 yrs +????. i have the old "knob and tube" in some places.
my wifes uncle is an electrician, he tells me the knob and tube
is good wiring and to leave it alone, or replace it.
in your last question are you saying you are looking at a light
fixture that has only one wire????
jim
|
291.280 | | DICKNS::WELLCOME | Steve Wellcome (Maynard) | Mon Nov 30 1987 13:59 | 11 |
| Re: .11
>It seems that the net effect will be the same.
Yes, it does, doesn't it? However, doing what you suggest is
absolutely positively NOT permitted by the electrical code.
The problem is "ground loops" as you suggest. I'm somewhat vague
about the exact details of the phenomenon, but I seem to recall
a note in this file someplace that did an excellent job of explaining
ground loops and why they are A Bad Thing To Have.
Do it right, do it according to code; that's what separates competent
do-it-yourselfers from house butcher do-yourself-iners.
|
291.281 | So what is a ground loop? :-) | YODA::BARANSKI | Too Many Masters... | Mon Nov 30 1987 20:02 | 0 |
291.282 | better Nate than lever? | REMEDY::KOPEC | Huh? | Thu Dec 03 1987 18:02 | 25 |
| The reason you can't just connect the white and bare conductors
together is that the voltage drops along the white wire will get
connected to the case of the washing machine that's sitting in a
puddle in your basement (or the case of that electric drill, etc...)
the "equipment grounding conductor" is kept separate to keep these
voltages in line...
(as he scratches the back of his brain) The rules for outlets on
2-wire circuits are:
a.) Can't add a new, non-grounding (2-prong) outlet.
b.) existing non-grounding outlets are to be replaced with
grounding (3-prong) types unless there is no way to provide
the ground (see the BX-discussion a few replies back..)
(you can install a GFCI, but you can't extend a new ground
from it.)
c.) NEVER, EVER install a grounding outlet without a proper
ground. This is serious stuff, here... people have been killed
by violations of this rule.
houses with 2-wire circuits are not fun, unless you are an electrician;
then they pay for your kid's education.
...tek
|
291.967 | Plastic vs Metal boxes | NETMAN::SEGER | this space intentionally left blank | Mon Dec 07 1987 17:35 | 10 |
| I'm surprised this wasn't listed already, unless it's buried under some
unrelated topic as much of this stuff is...
Is there any general opinions about metal vs. plastic boxes? It seems that in
almost any new construction I see that everyone uses plastic, yet SPAGS only
carries metal. In fact, one can get plastic boxes virtually anywhere cheaped
than the metal boxes at Spags. My thought is if plastic is better than metal,
why would Spags even bother carrying the metal?
-mark
|
291.966 | NOT at the FISH & TACKLE counter | CHART::CBUSKY | | Mon Dec 07 1987 18:29 | 19 |
| SPAG'S DOES carry the plastic! But you do have to look for them, they
are hidden, believe it or not, in the ELECTRICAL DEPARTMENT.
They have a trash barrell FULL of the single boxes in the back row near
the door bells. They list for $.33, the same as I've seen in other
stores, but at least they're not MORE. The doubles are in the same row
as some of the metal work boxes (middle row). I don't remember the
prices of them or the availibility of the triple boxes.
I prefer the plastic boxes for new work in the single size.
The double and especially the triple are too flimsy for my liking. My
experience with the triple has been when you mount the box on the stud,
the box does not remain square but rather takes on a trapazodal shape.
The switches and the switch plate then are mounted on a slant and look
like S#%T. I'll stick with the metal boxes for the few places that
require more than a single.
Charly
|
291.965 | | 3D::BOOTH | Stephen Booth | Tue Dec 08 1987 10:16 | 9 |
|
Plastic boxes suck, they are brittle and snap very easy and
I have never seen a pro use one ! If you screw them down too tight
or you nail them in too hard or you tighten the cable clamp too
much and SNAPPPPPPPPPPPPPPPPPP!
-Steve-
|
291.296 | Two appliances on one 220V circuit with toggle switch? | GLIVET::RECKARD | Jon Reckard 264-7710 | Mon Dec 21 1987 11:33 | 7 |
| Can two 220 appliances (range, dryer, (is a dishwasher 220?)) share one
circuit? The arrangement I have in mind would put a toggle switch of some
kind in the loop, enabling one appliance and disabling the other. (This
is in a full-circuit-breaker-box-type-house. And I'm not including any
baseboard heat in the loop.)
It shouldn't be too hard to plan certain non-meal times to use the
dryer - just flick the switch.
|
291.297 | | CHART::CBUSKY | | Mon Dec 21 1987 12:22 | 17 |
|
??? WHY ???
Even if there aren't or weren't any code restrictions it is generally a
not a good idea to do something that is too far from what most people
would consider normal. Future owners (and who ever does the laundry and
cooking in your house) will curse you 'till the day you die and then
some.
Charly
|
291.298 | shared 220v | NSSG::FEINSMITH | | Mon Dec 21 1987 12:23 | 8 |
| Considering that the dryer would have a 30 amp or 40 amp connector,
you're talking quite a large switch(a transfer switch would do the
job quite well, but be rather expensive). A big question would be
the electrical code in your area. Unless the two locations are near
each other, you may be better off running two separate circuits,
once the cost of everything is considered.
Eric
|
291.299 | | ULTRA::PRIBORSKY | Tony Priborsky | Mon Dec 21 1987 12:25 | 4 |
| Someone with the code book handy could comment, but I think these
heavy appliance circuits must be DEDICATED (that is my recollection
of reading the code at the library). DEDICATED means NOT SHARED,
so you can't do it...
|
291.300 | There's gotta be another way | VIDEO::DCL | David Larrick | Mon Dec 21 1987 12:36 | 7 |
|
I agree with the other replies - your proposed scheme is inconvenient, requires
an expensive switch, and is probably contrary to Code. There are likely to be
better ways to share capacity and free up breaker-box slots.
But if you're still considering this option, check with your local wiring
inspector _before_ buying the materials or investing substantial planning time.
|
291.301 | | BSS::HOE | The Rockies lets you come higher. | Mon Dec 21 1987 14:29 | 11 |
| Not all 220VAC appliances are the same. A/C compressors are 220V
only while stoves and dryers uses the neutral for the 110V timer
and lights.
Though some places allows for aluminium wires, get the copper if
you can afford the copper. I had thought about using the 220V line
to the A/C from the old stove plug since I converted over to gas
stove. The cost of the connectors and stuff made running the line
from the C/B box more feesible.
/cal
|
291.302 | Not a real good idea | WORDS::DUKE | | Mon Dec 21 1987 15:15 | 8 |
| The dryer has a 30 amp. plug and the range has a 50 amp. Feeding
the 30 amp. receptacle with a 50 amp. breaker is a code violation.
Feed the 50 amp. w/ a 30 amp. breaker and you risk tripping the
breaker if all of the range units are on. Not a real good idea
at best. Run two separate circuits. You will be much happier in
the long run.
|
291.303 | horse into a camel?? | AIMHI::BERNARD | | Mon Dec 21 1987 16:23 | 14 |
| This little project you have conjured up is really turning a horse
into a camel.
-1 is absolutely right, you are violating basic wiring rules, and
the standard electrical code (for MA I'm sure).
It will take less time, effort and money to just run 2 separate
lines. Otherwise, you will need a switch, heavy duty relay for the
poser, indicator lights, have to run wire to the receptacles anyway.
Enough said
JMB
|
291.304 | Let me try again | GLIVET::RECKARD | Jon Reckard 264-7710 | Tue Dec 22 1987 11:14 | 14 |
| Well! I didn't expect to get my head bit off!
Just kidding. These responses comprise a perfect example of the benefit
of Home_work. Thanks. Now, just one more peep, and I'll be quiet.
We have a 3-family house and inadequate wiring (I mentioned our full circuit
box, I neglected to mention its capacity - 100 amps! - that handles 3 range
circuits, 1 dryer circuit, and one room's electric baseboard, with only two
tripped circuits in 4 1/2 years - one of my first projects was separating two
ranges that shared 1 circuit!). Before we inherited a dryer, one of our tenants
started using the one dryer hookup, in a central hallway. OK with us. And then
I started wondering why couldn't we share the one circuit.
So, adding another circuit is out (unless we add another 100 amps - $$$$).
Sharing a 50-amp device with a 30-amp (or whatever) isn't a factor. And, I'll
check out the dedicated aspect with the town/state codes (NH).
One reply listed 4 or 5 things I'd need, even if it was legal. More info?
|
291.305 | don't be a fool!!! | AIMHI::BERNARD | | Tue Dec 29 1987 16:30 | 32 |
|
I've run into many situations like yours and all of them have scared
the daylights out of me. I was looking at a house once and the owners
had an air conditioner attached to small extension cord. I mentioned
the potential hazard to the owner and they laughed. I was going
to show them how the cord would crack from heat, but when I touched
it, ALL of the insulation fell off in my hand, there was a big spark
and the owner almost fainted.
I know you mentioned that $$$$ was an issue, but 100 amps for 3
families is VERY dangerous. You should get quotes from local
electricians for running 100 amp services for each appartment and
then have a detailed inspection done of the wiring. For me it's
more than $$$$, but's it piece of mind and the safety of my family
and possesions that's important. Electrical fires are very common,
expecially when heating and old or inadequate wiring are involved.
I wouldn't use "only 2 tripped breakers in 4 1/2 years" as a comfort
indicator. What you may have is damaged insulation on the wire that
was sharing 2 ranges. The ranges themselves won't last as long.
Sort of like working in a brownout all the time. The service cable
should be checked. I'll bet it's warm most of the time. Circuit
breakers are supposed to be toggled every 3 months or so to be sure
that they will operate. Do you do that???? Most folks don't.
In short, your initial question didn't even begin to discuss your
real problem. You should fix that before you are reparing fire damage!!
Sorry for any harsh statements, but I've seen situations like yours
turn into tradegies.
JMB
|
291.306 | | PARITY::GALLAGHER | | Mon Jan 04 1988 14:20 | 14 |
|
I agree with all of the replies; you really need to install dedicated
services for each unit, and size your ciruits correctly.
The only thing that might be marginally acceptable (and despite
this, I believe that what I'm going to tell you is against code
regs) is if you had a piece of baseboard heat requiring a 20 amp
230 circuit, as well as something such as say an air conditioning
unit. If you could safely assume that you'd not use either at the
same time -- such as the heat and the AC together, then you could
safely do it. However, I have this situation in my house, and I
have 2 separate circuits. The wire and the breakers are cheap enough,
so I'd certainly encourage you not to compromise your property and
safety. Do it correctly and you won't have to fix it later.
|
291.316 | Grounding a 2-wire Circuit? | DECWET::MCWILLIAMS | Brian @ DECwest, 206.865.8837 | Tue Feb 16 1988 22:41 | 28 |
| I'm doing some minor kitchen remodeling (counters, lights, paint,
etc.) and I'm contemplating adding another outlet to my new
counter space when I take the old counter out. Adding this outlet
will involve extending from one of two existing outlets.
Presently, there exists one outlet already on the counter. It
uses old, 2-wire (ungrounded) wire and shares a 20 amp breaker
with the kitchen overhead light and 4 living room receptacles.
On an adjacent wall is another outlet, on 12 (14?) ga. 3-wire by
itself on a 20 amp breaker. Very virtuous looking.
THE QUESTION:
1. Is it safe/acceptable to add a ground wire to a 3-prong outlet
and ground the receptacle directly to plumbing (under the sink)?
This way, I could extend the old 2-wire outlet and put in grounded
3-way receptacle without going through the hassle involved in
extending from the existing grounded supply on the adjacent wall
outlet.
Thanks for your help,
-Brian
|
291.317 | NO! | AKOV88::CRAMER | | Wed Feb 17 1988 11:08 | 14 |
| I'm not an electrician, but, from perusing this file and talking
to folks who know about such things the answer is a resounding NO!
You should not run a 3 wire from a two wire, in fact it is not
up to code and, therefore, illegal.
Find out if that grounded outlet on the 20A breaker is 12 or 14
ga. wire, 'cause if it is 14 then the breaker is too big for the
wire and unsafe, also.
If I were you I'd have a qualified electrician look at your wiring
given that the house is old and has obviously had some additional
electrical work done.
Alan
|
291.318 | NO! | FANTUM::BUPP | | Wed Feb 17 1988 12:00 | 6 |
| It's interesting how much trouble that can cause if the pipe is
ever replaced with plastic.....
(However, I have done something similar to get a ground-fault
interrupter installed. Don't do as I do, do as I say....)
|
291.319 | Highly illegal | STAR::SWIST | Jim Swist ZKO1-1/D42 381-1264 | Wed Feb 17 1988 12:27 | 7 |
| The real reason is that the Nat'l electrical code requires that
all grounds for circuits emanating from a given main panel be
connected to physical ground at one and only one point. This is
to eliminate any possibility of ground loops - a dangerous phenomenon
caused by potential differences between two different grounds due
to leakages, imperfect conductivity of pipes/earth/etc.
|
291.320 | There's another thing to look out for | PSTJTT::TABER | Eunuchs are a trademark of AT&T | Wed Feb 17 1988 13:11 | 16 |
| I suppose enough people have told you that you shouldn't ground to a
pipe by now. There's another potential problem in your message though:
The Code now requires that the outlets in your kitchen be separate from
the lighting cicuit. (Makes sense -- kitchens are filled with dangerous
things, and if you just popped a breaker 'cause the mixer cord is
frayed, you don't want to stumble around in the dark.) I believe it's
ok for the light to be tied in to the living room circuit, but not the
kitchen outlet.
This isn't a problem in your present situation, because your old wiring
is "grandfathered" in under the new code, but if you go to make changes,
you may be required to bring the whole kitchen into compliance. It
would be a good idea to voluntarily make the change anyway while you're
snaking the wire over from your modern outlet. :-)
>>>==>PStJTT
|
291.321 | Maybe it IS grounded ... | ERLANG::BLACK | | Wed Feb 17 1988 14:36 | 45 |
| In my "old" (1955) house in Seattle, I had the same problem: two
prog outlets in the kitchen, and I wanted to add another outlet
and GFCI. I had already fiddled the wires from the new outlet down
to the basement, and was prepared to run a new grounding wire back
to the panel.
However, when I finally managed to rip out the metal box that housed
the existing outlet, I found that it WAS grounded. The grounding
wire had been installed before the sheetrock, and was attached to
a screw on the OUTSIDE of the box. So, the box WAS grounded, although
I couldn't tell from the inside.
If you have a metal box, you may find the same thing. Get out your
test lamp and see if the box is grounded. If so, rip it out, bring
that grounding wire through the knockout, and you are home.
Now for my problem:
>> The Code now requires that the outlets in your kitchen be separate
>> from the lighting cicuit.
Oh dear! My kitchen has a main light and a small one over the sink.
They used to be on the same circuit, but I recently re-wired the
one over the sink so that it is on a different circuit from the
main light, but on the same circuit as an outlet. I did this (without
a permit, of course) for two reasons:
(1) When I turn off the main light circuit, to work on the living room
or the breakfast room, or something else, it is nice to have at
least the small light over the sink still work.
(2) I wanted to use a pair of three-way switches on the light by
the sink, instead of the existing single switch. Normally that
would mean running three-core cable to replace the two core, which
means ripping out the outlet box, which typically means major repairs
to the wall. However, this switch shared the box with an outlet,
so by using the power supply to the outlet the feed the common side
of the switch, I was able to avoid all that.
My question: have I broken the new code? (Which code introduced
this requirement?) Or is it OK as long as ONE light is on a separate
circuit?
Andrew
|
291.323 | I'm legit | DECWET::MCWILLIAMS | Brian @ DECwest, 206.865.8837 | Wed Feb 17 1988 15:51 | 14 |
| Well, against my nature, I broke down and decided to do the project the right
way ...
I added a new circuit. This required using up my last breaker in the panel,
cutting a hole in the wall for wire-snaking, as well as removing a baseboard so
I could sneak the wire behind it.
But hey, I'm glad I did it. According to code, you're supposed to have
two (2) "small appliance" circuits in a kitchen, separate from the lighting
circuit. That's what I've got now.
-Brian
|
291.324 | Stupid question? | CSSE32::NICHOLS | HERB | Fri Feb 19 1988 01:01 | 6 |
| is there any danger in replacing 2 prong outlets with 3 prong outlets?
Maybe another way of asking the question is: What uses are there
for 3 prong outlets that are dangerous when there are only 2 wires
backing up the 3 prongs?
Just bought a bunch at Spags for 60c and have installed several.
|
291.325 | | QUARK::LIONEL | We all live in a yellow subroutine | Fri Feb 19 1988 02:12 | 6 |
| Re: .8
The danger is if you use an appliance which, for safe operation,
requires the ground pin to be grounded, and something goes wrong...
Steve
|
291.326 | | DICKNS::WELLCOME | Steve Wellcome (Maynard) | Fri Feb 19 1988 11:58 | 7 |
| The basic problem is, if you put in an ungrounded 3-prong outlet,
the outlet is not telling the truth. It's lying to whoever plugs
a 3-prong plug into it.
I can see one danger. You hire a contractor. He plugs his 3-wire
extension cord into one of your outlets, runs the cord outside,
plugs his 3-wire saw into it, pulls the switch, and promptly gets
zapped. He sues you.
|
291.327 | More info | CSSE32::NICHOLS | HERB | Fri Feb 19 1988 13:50 | 7 |
| Thnx for help .10,.11
Called around and discovered that two prong outlets are not made
anymore, are not stocked, and are apparently out of code (in Mass)
One store suggested that a 3 prong outlet can be properly grounded
simply by running appropriate-guage-wire from the ground screw in
the outlet to the back of the junction box. Does that make the outlet
"3-prong-safe"?
|
291.328 | Is the junction box grounded? | ULTRA::BUTCHART | | Fri Feb 19 1988 14:29 | 10 |
| re .11
Only if the junction box itself has been properly grounded. If I remember
correctly, one type of system uses the metal of the electrical conduit that
the wires run through as the ground. (Might be an out-of-date or state
memory though.) This works fine as long as all the junction boxes are
properly connected directly to the conduit and nobody has broken the path
in subsequent renovations.
/Dave
|
291.329 | | VIDEO::DCL | David Larrick | Fri Feb 19 1988 15:01 | 26 |
|
.11> Called around and discovered that two prong outlets are not made
.11> anymore, are not stocked, and are apparently out of code (in Mass)
They won't be easy to find, but they are in fact _required_ by Code when
the box isn't properly grounded. This should only be true when replacing a
defective 2-prong outlet - if you're installing a new box or running a new
cable, it must be properly grounded, and then you must use a 3-prong outlet.
Maybe your fellow NOTErs will have enough 2-prongers lying around for you.
I know I have at least one you can have.
.11> One store suggested that a 3 prong outlet can be properly grounded
.11> simply by running appropriate-guage-wire from the ground screw in
.11> the outlet to the back of the junction box. Does that make the outlet
.11> "3-prong-safe"?
As .12 indicated, this advice is correct only if the box itself is properly
grounded - a dangerous assumption. If the box were properly grounded, you'd
most likely already have a 3-prong outlet there!
_Never_ get this type of advice from a store. The people behind the counter
and answering the phones may know their stock (often they don't even know
that), but they don't know the Code. If they knew the Code, they'd be out
working as electricians and making lots more money.
|
291.330 | Sure its only two wire? | AKOV75::CRAMER | | Fri Feb 19 1988 15:09 | 12 |
| What kind of cable do you have? My house had two pronged outlets
also and, unless you looked carefully, 2 wire cable to match.
BUT, they took the ground wire and wrapped it neatly around the
cable under the cable clamp (holds the cable to the box) grounding
the box. I could then run a pigtail to the box for my new three
prong outlets.
Alan
PS I may still have some two prongs you can have, if necessary.
I'll let them go REAL cheap ;^)
|
291.331 | Source for 2-prong outlets | NEBR::HARRISON | Bob Harrison, CIM Engineering | Fri Feb 19 1988 15:54 | 0 |
291.332 | please, take my outlets | TOOK::CAHILL | Jim Cahill | Fri Feb 19 1988 16:10 | 20 |
| I have about 20 million two-prong outlets, free for the taking
(In fact, I might pay someone to take them out of my sight!).
This is due to the replacement of 90% of the existing outlets in
my house with 3-prongers. And, yes... the new outlets are indeed
grounded. The existing wiring has the ground wire brought out
of the outlet box and attached with a neat little spade lug to
a screw on the outside (i.e., inaccessible within the wall!) of
the box.
.12> Only if the junction box itself has been properly grounded. If I remember
.12> correctly, one type of system uses the metal of the electrical conduit that
.12> the wires run through as the ground. (Might be an out-of-date or state
.12> memory though.) This works fine as long as all the junction boxes are
.12> properly connected directly to the conduit and nobody has broken the path
.12> in subsequent renovations.
You're probably thinking of armored cable, more commonly known by
a trade name: BX cable. Your last point is an important one!
Jim
|
291.333 | Can't use BX shield as ground. | TALLIS::KOCH | Kevin Koch LTN1-2/B17 DTN226-6274 | Fri Feb 19 1988 16:18 | 11 |
| There have been other notes stating that two-wire BX cannot be used
to ground a three prong outlet. The metal shield is not considered a good
enough conductor back to ground.
Yet another earlier note stated that you can put a GFCI on your
two-wire-plus-BX circuit.
I have some 12-2 and 14-2 romex with a much smaller diameter ground
wire. How can it be legal to use this to ground the third prong? If the
third wire is smaller, how can it carry the full load in a hard fault?
|
291.334 | | CSSE32::NICHOLS | HERB | Fri Feb 19 1988 16:23 | 5 |
| thnx for good analysis and advice guys. Will try to determine if
in fact the wiring is 3 wire. (House was built c. 1954)
herb
|
291.335 | | HPSMEG::LUKOWSKI | I lost my A$$ in the '87 CRASH! | Fri Feb 19 1988 16:31 | 26 |
| >They won't be easy to find, but they are in fact _required_ by Code when
>the box isn't properly grounded.
Richter and Schwan's (sp?) Wiring Simplified calls this out.
>Maybe your fellow NOTErs will have enough 2-prongers lying around for you.
True.
I replaced all of the two-prong recepticles in my house with
grounded ones. I saved the ones that appear to be in reasonable enough
shape to be used again and meant to put in a note offering them to
anyone that needed them for the reason stated above. I believe I have
at least a dozen left (maybe more). If anyone needs some/all, let
me know. No warranty/liability is expressed or implied.
> If the box were properly grounded, you'd
>most likely already have a 3-prong outlet there!
I think it really depends on when the house was wired. My house
was built in '55 and ALL of the boxes are properly grounded (or
at least were when they were installed) yet none of the recepticles
were the grounded type. I don't understand this but then again, I
don't know what the code was thirty years ago.
-Jim
|
291.336 | | DICKNS::WELLCOME | Steve Wellcome (Maynard) | Fri Feb 19 1988 16:32 | 12 |
| BX armor can be used as a ground *IF* it has a bonding strip
running along inside it. This is just a thin metal ribbon, running
inside the armor but outside the wire bundle. The armor, by itself,
isn't considered a suitable ground because the spiral-to-spiral
connection isn't very secure, and the only path that has any reliablity
is around and around and around and around and around and around...
following the spiral, which ends up being too high a resistance.
The bonding strip gives a straight-line path, and makes it acceptable.
(Or so the theory goes).
The bonding strip ought to be bent over the end of the BX armor
and clamped under the cable clamp; and don't forget the anti-chafe
bushing.
|
291.337 | | BINKLY::WINSTON | Jeff Winston (Hudson, MA) | Sat Feb 20 1988 03:29 | 2 |
| NHD hardware (and I think some true value stores) sell 2 prong outlets
|
291.338 | | DICKNS::WELLCOME | Steve Wellcome (Maynard) | Mon Feb 22 1988 12:40 | 6 |
| Re: .19
Yes, that seems to have been the code at one time. My parents'
house was built around 1953 and it has grounded boxes with 2-prong
receptacles. I guess the theory was that if a fault developed
in the box and a hot wire touched the box it would blow a fuse,
not just sit there ready to zap somebody.
|
291.339 | Smaller ground wire? | VIDEO::DCL | David Larrick | Mon Feb 22 1988 14:12 | 20 |
|
.17> I have some 12-2 and 14-2 romex with a much smaller diameter ground
.17> wire. How can it be legal to use this to ground the third prong? If the
.17> third wire is smaller, how can it carry the full load in a hard fault?
The ground wire does indeed carry the full load in a hard fault, but
_not_for_very_long_ - just long enough to trip the breaker. At the power
levels 12-2 is used for, it takes a while for the resistance of the smaller
ground wire to generate enough heat to be dangerous.
But the Romex I've used has a ground wire of about the same size as the
other conductors (I think). Is yours some special-purpose product? Does
it have "Type NM" printed or stamped on the outer jacket? ("Type NM", for
"non-metallic", is the Code's name; "Romex" is one brand, and the universal
trade name.)
Not to be insulting, but just covering all the bases: you're comparing the
ground wire's size with the conductor _inside_ the white and black
insulation, right? Of course the "black and white wires" are bigger than
the bare one when you include the insulation!
|
291.340 | | AUTHOR::WELLCOME | Steve Wellcome (Maynard) | Mon Feb 22 1988 15:44 | 7 |
| re: .23 etc.
Yes, I think the ground wire can, by code, be one size smaller than
the other wires, so with 12-gauge insulated wires you can have a
14-gauge ground. (At least this used to be true - haven't checked
the latest book.) I saw, some time ago, some NM wire in which
this was done; most of what I've seen has the ground the same size
as the others though.
|
291.341 | Used to be that way | CADSE::MCCARTHY | CADSE Environment Group | Mon Feb 22 1988 20:05 | 6 |
| A while ago (10+ years) there was ROMEX around with a smaller ground
wire. When they started to produce it with same size ground, they
advertised it as "14-2 Romex with full size ground". I think it
would be hard to buy some now though.
bjm
|
291.342 | nope | SOFCAD::KNIGHT | Dave Knight | Tue Feb 23 1988 10:02 | 1 |
| The '87 code does NOT allow a smaller ground anymore.
|
291.307 | Conversion between 220V plug types possible??? | SUSHI::KMACDONALD | Got any ICE you need climbed? | Tue Mar 01 1988 12:33 | 19 |
| Well, I have a question on a similar-but-dissimilar topic as .0. My
situation is that I'm living in a townhouse now, which has 220V service
in the bsmt. with a plug that looks sorts like:
L
\ /
and I'm thinking of buying a planer, also 220 (230?) V which seems to
come with a plug shaped like:
o
_ _
As I don't want to rewire this townhouse, which I'll only be in for a
few more months, is it possible and/or SAFE (!!!) to somehow make up an
extension/conversion cord to allow the planer to plug into the dryer
circuit, or are these types of circuits incompatible???
ken
|
291.308 | Do it | ALIEN::WEISS | Trade freedom for security-lose both | Tue Mar 01 1988 13:24 | 15 |
| I think it should be fine to make a short conversion cord. The only difference
in the two plugs is amperage. Luckily, the planer is lower amperage than the
outlet - it would clearly be unsafe to do the conversion if it were the other
way around. The planer plug is a 20A plug, I'm not sure the exact amperage of
the outlet, but it's at least 30A, maybe as much as 50A. Make sure you use
wire rated for at least 20A for the cord, and that there is only one outlet on
the cord - if there were two outlets, the cord would have to be rated for the
amperage of the wall outlet since it could take more than 20A.
At first I wasn't sure about the safety of putting the lower amperage planer
on the high amperage line, but then I thought about 18 guage stranded lamp
cords being safely plugged into 20A circuits, and that convinced me it would be
fine.
Paul
|
291.343 | No lights on 2 Kitchen Appliance Circuits | ERLANG::BLACK | | Tue Mar 01 1988 13:41 | 17 |
| I thought that I would answer the question that I asked in .5, since
no-one else has!
I bought a new Richter and Schwann (no, I don't have the real code)
and they are quite explicit: the kitchen must have two 20A circuits
for appliances. These circuits MAY also serve the dinning room,
breakfast room and pantry, , but MUST serve the kitchen. They
MAY have an electric clock recepticle, but MAY NOT have ANY LIGHTS.
The refrigerator MAY use one of these circuits.
So, I disqualified one of my circuits from this provision when I
connected the supplimentary light to it. BUT it turns out that
the refrigerator is on its own 20A circuit, so I DO still have the
two circuits required by the Code.
Andrew
|
291.309 | Use Pigtail, make extension cord | ERLANG::BLACK | | Tue Mar 01 1988 14:13 | 14 |
| Go to the hardware store and buy a "PIgtrail" for a dryer -- about
three feet of flexible cord with the 30A dryer plug molded on the
end. Then put a handybox (one of theose metal boxes with rounded
corners) on the other end, with a cable clamp -- you may hev to
enlarge the knockout to get the cord into the box. Put a 20A socket
into the box, and connect the wires.
Voila - one extension lead. Should cost you ~ $15
I've never seen the 30A plugs on sale other than connected to the
pigtail, but I bet DEC has a source for them!
Andrew
|
291.310 | Don't touch those ... ******** ZAP ******** | SUSHI::KMACDONALD | Got any ICE you need climbed? | Tue Mar 01 1988 16:04 | 5 |
| Thanks, folks! I may get this thing flying, after all. If I make up the
rig Andrew suggested, which wire goes where? I suspect that wiring the
plug improperly could be exciting....
ken
|
291.311 | Manuals, manuals... | 11508::CURTIS | Dick 'Aristotle' Curtis | Tue Mar 01 1988 18:07 | 7 |
| .14:
Some wiring books (Richter & Schwann?) may describe the proper way
to wire various plugs. Come to think of it, the code might, too.
Dick
|
291.312 | | ALIEN::WEISS | Trade freedom for security-lose both | Tue Mar 01 1988 18:28 | 8 |
| Wiring's pretty simple. In the cord from the plug, there'll be three wires.
One of them will either be bare (no insulation) or will have green insulation.
This is the ground. On the outlet, there will be three screws - one will be
in a distinctly different place from the other two and should be green.
Connect the ground wire to this screw, and the two other wires to the other
screws.
Paul
|
291.313 | | NEXUS::GORTMAKER | the Gort | Wed Mar 02 1988 00:02 | 7 |
| Wouldent it be a good idea to change the breaker in trhe panel too?
Seems a 20-30 amp device on a 50 amp feeder could be a tad dangerous
at least to the planer. It would have to draw 50 amps before tripping
the breaker. Or am I missing something?
-j
|
291.314 | | ALIEN::WEISS | Trade freedom for security-lose both | Wed Mar 02 1988 11:27 | 13 |
| > Wouldent it be a good idea to change the breaker in trhe panel too?
> Seems a 20-30 amp device on a 50 amp feeder could be a tad dangerous
> at least to the planer. It would have to draw 50 amps before tripping
> the breaker. Or am I missing something?
I thought that at first too, but then I thought of what would happen to, say, a
clock radio if it really drew all 20 amps that it's circuit would allow. POOF!
I guess the point is that it's common practice to have devices with far less
capacity than the circuit. Think of wiring a shop such that you could run more
than one machine on one circuit - you'd make that circuit 40 amps or so, yet
none of the machines would draw that much.
Paul
|
291.315 | NEC ends at the outlet, sorta | STAR::SWIST | Jim Swist ZKO1-1/D42 381-1264 | Wed Mar 02 1988 11:58 | 16 |
| re: Last couple.
The purpose of the panel breaker is to protect the building and
its internal wiring. If a plugged-in device wishes to protect
itself it may do so by a breaker on the device rated at the device
current (seen on many motors, good stereo equipment, etc). But
it's not required on the device by the NEC.
Failure modes of a device where it draws enough current to become
a hazard but not enough to trip the breaker are considered rare
enough that the NEC doesn't worry about it. The underwriter's lab
has some say in this matter when they UL approve a device - one
of their criteria is the implications of various kinds of failures.
|
291.259 | Another AL-CU connection question | ACUTE::MCKINLEY | | Wed Mar 30 1988 22:46 | 13 |
| I have a similar question. I was hooking up the power for a dishwasher
(Sears) and found what seems to be aluminum wiring. I am hooking 14
guage solid copper wire to 14-16 gauge stranded aluminum (appearing)
wire. The wire appears to be a solid silvery color, i.e. I look at
the end and there is no copper color seen. I guess that this is AL,
not clad CU. I'm using copper wire nuts for the connection. Is there
any problem with this? BTW, the dishwasher runs on 110VAC.
As a more general question, when is there a problem using AL and CU?
The instructions for the dishwasher warn about hooking "stranded copper
wire to solid aluminum wire," exactly the opposite of what I have.
---Phil
|
291.260 | | NEXUS::GORTMAKER | the Gort | Thu Mar 31 1988 01:08 | 7 |
| re-.1 the wire nuts should be rated as AL/CU anything less could/will
be a problem later it is also against code. BTW-most wire nuts are
rated for both but be 100% sure before using them I dont think you
want a fire later on.
-j
|
291.261 | Use an anti-oxidant | SEESAW::PILANT | L. Mark Pilant | Thu Mar 31 1988 13:36 | 5 |
| I would also consider using a dab of anti-oxidant before using the
wire nut. I usually goes by the name NOALOX, or some such thing.
(I don't have my bottle in front of me.)
- Mark
|
291.262 | Thanks | ACUTE::MCKINLEY | | Thu Mar 31 1988 16:29 | 8 |
| Re: -.1,-.2
Thanks for the tips, I'll check the wire nuts to see that they are
rated correctly and look around for the anti-oxidant.
Anyone want to tackle the general AL-CU question?
---Phil
|
291.344 | GFCI to replace 2-prong? | QUARK::LIONEL | We all live in a yellow subroutine | Fri Apr 08 1988 15:54 | 6 |
| The latest Popular Science has an article suggesting the use of
a GFCI outlet to replace a 2-prong outlet, in the absence of a ground
wire. They claimed that this gave some protection against leaks to
ground, but I am very dubious about this. Anyone else care to comment?
Steve
|
291.263 | | VINO::KILGORE | Wild Bill | Fri Apr 08 1988 17:13 | 6 |
| re .7:
I thought it had something to do with the comparitively large
expansion/contraction that AL goes through as normal currents
generate heat, which over time can cause a bad connection, extreme
heat and fire.
|
291.345 | ground current - with no ground?! | DRUID::CHACE | | Fri Apr 08 1988 19:30 | 2 |
| If it's really a two-wire circuit it will need a ground installed
before it can have fault current through it.!
|
291.346 | Ground is NOT necessary | CURIE::DISHMAN | | Fri Apr 08 1988 20:10 | 19 |
|
I've been successful installing GFCI's in two-wire circuits.
According to an electrical consultant (actually, an instructor), GFCI's
work by comparing the current in both sides of the circuit. Any
mismatch triggers them to shut off. A ground is not required.
For some reason, "code" doesn't allow installation of outlets beyond the
ungrounded GFCI.
Assuming this is correct, it substantiates the information in .28, and
provides a measure of protection to ungrounded, two-wire circuits.
Further evidence for the lack of a ground requirement is that it works.
I've installed GFCI's in all exterior locations, some fed only by knob
and tube wiring. I intentionally shorted one to ground (via a long
wire) and, yes, it cut out as hoped.
-Bruce
|
291.264 | The why of it | REGENT::GETTYS | Bob Gettys N1BRM 223-6897 | Mon Apr 11 1988 12:22 | 18 |
| Aluminum and copper have different rates of expansion
and contraction. This causes any connection between them to
eventually work loose. Once it is slightly loose, heat starts to
build up in the joint causing more loosening. And on and on it
goes until the resistance is high enough to cause enough heat to
be generated to cause a problem, like a fire.
The electrical devices (outlets, etc.) which are marked
as aluminum usable use an alloy for their terminals which has a
close enough coefficient of expansion to aluminum so that the
loosening doesn't occur (assuming proper installation). The
NoAlOx (or other preparations) also reduces the problem by
keeping the aluminum from oxidizing and provides a conductive
path to reduce the resistance in the joint. Less resistance
means less heat; thus less expansion and contraction; thus less
problems.
/s/ Bob
|
291.347 | Yes, but.... | AMUSE::QUIMBY | | Mon Apr 11 1988 14:16 | 6 |
| From a theoretical point of view, .30 is right -- the GFCI will
fulfill its ground-fault function without a grounding conductor.
However, the GFCI outlets ceom with three-hole outlets, and it is
probably not acceptable to have what appears to be a grounded outlet
when the ground is not connected.
|
291.348 | | QUARK::LIONEL | We all live in a yellow subroutine | Mon Apr 11 1988 19:21 | 12 |
| I went back and looked at the PS article. It stated that the "code"
(they had a citation which I don't recall) explicitly allows for
a GFCI to replace a two-prong outlet. Says nothing about the
unconnected ground pin. However, the article goes on to say that
you CAN do a feed-through with this method, contradicting what an
earlier reply here said.
I agree that a GFCI is better than nothing, but I would be inclined to
fill in the ground pin with something (silicone sealant?) rather than
allow the possibility of someone depending on that being a ground.
Steve
|
291.283 | Outlet ground tied to common | VIDEO::DCL | David Larrick | Mon Apr 25 1988 14:34 | 53 |
291.284 | Advise and Withdraw | BIMINI::SCHNEIDER | Dennis Schneider | Mon Apr 25 1988 15:30 | 19 |
| David,
1. Given the description, I'd suspect that Neutral and Safety ground have
been bonded elsewhere in the wiring.
I've NEVER seen anyone intentionally strap safety ground to neutral in
in outlet box. One wonders why they bothered to clamp the safety
grounds together.....
2. As far as the ethics/law are concerned, I'd have told my neighbor that
you believed there was a genuine hazard there and let the neighbor
take whatever decisions fell out of that.
Given you were likely not looking at the only instance of crossed
neutral/safety ground, genuinely correcting the hazard would have
been lots of work.
Dennis
|
291.374 | Need advice on old wiring | TOLKIN::ROMANO | It works better if you plug it in | Thu May 19 1988 12:56 | 20 |
| This note is also in REAL_ESTATE.
I'm interested in buying a 118 year old Victorian in Hudson. The
building seems to be very stable and in good shape. It's about
2700 square feet of living space. One sticking point for me is
that over 50% of it still runs on the ancient "ceramic" insulated
wiring from the vintage 20's. The other half has been upgraded
to the metal-sheathed wiring (mental coil) and modern wiring. My
question is how dangerous in the old wiring. The amount that it
will cost to replace is going to be a strong indicator on the price
we are willing to pay for the house. Any rough estimates on
replacement costs for the old wiring... does it need to be done
right away. We would like to run a couple of air conditioners in
some of the floors to branch wiring may be necessary.
Thanks for the information,
-Don-
|
291.375 | | DICKNS::WELLCOME | Steve Wellcome (Maynard) | Thu May 19 1988 13:44 | 4 |
| The official name for that kind of wiring is "knob and tube."
It's basically safe. I wouldn't worry about it. You'll want
to replace it someday, but don't panic in the meantime. After
all, it's been there for a long time already with no problem.
|
291.376 | more.. | TOLKIN::ROMANO | It works better if you plug it in | Thu May 19 1988 13:57 | 9 |
| I'll admit that I'm a little concerned about the hazards of it.
I'm more concerned whether it will be able to meet our needs. I
couple of air conditioners will need to be used... can this wiring
handle it. If we do want to change it (a lot of people have), any
ideas on cost estimates... we just want to know what we're up against.
Thanx,
Don
|
291.377 | As long as they work ... | CIMNET::HARRISON | Bob Harrison, CIM Engineering | Thu May 19 1988 13:58 | 2 |
| I still have two circuits (out of 17 )that are knob and tube in
my 1917 vintage house. No problems ...
|
291.378 | | SPGOPS::FLANNERY | | Thu May 19 1988 14:49 | 12 |
| More important that what kind of wiring it is, check what's
on each circuit and see how many outlets are in the rooms for
the air conditioners. We have a lot of this wiring and the
only problem have is that many of the rooms only have one
outlet. If you want to run an AC off it could present a
problem.
As for cost to replace, if you don't want to rip out the walls
and/or ceilings, its very labor intensive. Took us 8 hours to
snake a new line into the kitchen. To pay someone could get
very expensive.
|
291.379 | Knob and Tube OK, but modify to meet needs | TOOK::ARN | Tim Arn LKG2-2/BB9 226-7572 | Thu May 19 1988 15:40 | 18 |
| The wiring itself is probably OK if noone has seriously overloaded
it in the past creating problems. The problem is that you probably
have a 60 amp service running only 4 - 15 amp circuits throughout
the house. All of the lights for a lot of rooms could be on the
same circuit. Now you want to take two air conditioners which draw
about 30 amps when the compressor kicks in, and put it on the existing
wiring. From experience let me tell you, buy about 10 boxes of slow
blow fuses and have them ready. What I did to solve the problem
was to add a circuit breaker box capable of adding 8 new circuits.
Then, you can string a seperate line to each place you want a air
conditioner or a grounded outlet for hooking up you home computer.
There is nothing wrong with knob and tube wiring, except that it
does not provide a ground at outlets. Mine is still in excellent
shape and is 65 years old. I can't imagine that the previous owner
hasn't added another box! Hasn't the kitchen been remodeled?
Tim
|
291.380 | | HEYDEN::BBARRY | | Thu May 19 1988 15:53 | 8 |
| I do not know MA electrical codes very well, but doesn't the 50% rule
kick in when he adds the additional circuits. The 50% rule says that if
more than 50% of the current electrical capacity is remodeled, upgraded or
added to then the entire system must be upgraded to current code levels.
I know this was the case in Arizona.
Brian
|
291.381 | Do it right!!! | AIMHI::BERNARD | | Thu May 19 1988 16:38 | 39 |
|
Knob and tube was the best way to wire in the "old" days. Those
days also saw lots and lots of house fires started by faulty electical
systems. The major problem with K&T is that there is no ground,
or third wire back to the fuse box to open the circuit in the event
of a short. I've heard of cases and actually ran into one where the
old wiring became frayed inside the box, and everytime something was
plugged in, a spark came out. The fuse never blew.
With today's ever increasing dependence on elecrticity, the last
place to scrimp is in the wiring.
A previous note made a good suggestion to upgrade the service. I know
the MA code doesn't allow K&T wiring to run into a new box. Most
electricians run new wiring to the first junction box and connect
there. I personally have made every effort to replace all K&T that
can be reached without major work.
For your A/C's, I would run dedicated circuits. They tend be be
real noisy (electically) so you may get interferrence on appliances
or blinking lights if they share circuits.
While you're at this project, don't forget to install electric smoke
detectors that are connected together on all floors. I got cheap
at my mothers house and a careless tenant nearly caused a disaster.
I'm installing them this weekend!!.
As for costs, you can usually count on not exceeding $100 per device.
A device would be a plug, light etc.. This sounds like a lot, but
as a previous noter discussed, it can take lots of time for old work
wiring. Get several estimates and references, and make sure that
the inspector does more than a walk through inspection.
Sorry for the long note for a simple question, but I've seen too
many bad things happen due to faulty wiring.
good luck
JMB
|
291.382 | | RAMBLR::MORONEY | The purpose of diplomacy is to prolong a crisis | Fri May 20 1988 00:38 | 6 |
| FWIW:
Until very recently (a couple months ago) there were knob-and-tube circuits in
use in the Mill, carrying 550 volts.
-Mike
|
291.383 | lots of work or $$ for new. | 27958::DONNELLY | Take my advice- Don't listen to me | Fri May 20 1988 04:06 | 26 |
| As stated, the knob and tube is probably ok especially if not overloaded.
The trick here is not over loading it. Unscrew one fuse and go see what
goes out, you can find out the extent of the circuits like this. Most knob
and tube is 14 ga. wire, that means 15 amps max. Hardly suitable for ac.
What I would suggest is putting in new wiring to handle everything except
ceiling lights and some switches to run them. The rational is that light
bulbs will not overload the wire and those fixtures are usually the
toughest to get to.
Adding the new wiring is very expensive if done right. I rewired my
complete house like this and it took me a year. The house is only 1200 sq.
ft. (ok, I didn't work on it 24 hours a day). I called in an electrician
to run the huge 200 amp cable, put up the meter socket, and hook them up to
the wire from the street and my new panel. This took all of 4 hours and
cost about $500. If I had paid for the whole job it would have run over
$5000 I'm sure (lots of outlets and circuits).
Another thing to consider is, are the walls accessable to run wires? I ran
one 3-wire to the attic and then everything top down for the 2nd floor.
This was ok but still lots of work. I've seen lots of surface conduit in
old victorians; gets the job done but doesn't look too great.
I guess there's no simple answer for you. Just don't put in bigger fuses,
the 15 amp ones will blow if they're supposed to.
Craig
|
291.384 | More than 15 Amperes? | ERLANG::BLACK | | Fri May 20 1988 22:19 | 8 |
| I think that 14 guage wire in knob and tube can safely carry more
than 15 amps. 14 guage NM cable can carry 15 amps, but knob and
tube can safely get hotter than NM cable with paper and plastic
in direct contact with the wires.
However, voltage drop may certainly be a problem with 14 guage.
|
291.385 | | RAMBLR::MORONEY | The purpose of diplomacy is to prolong a crisis | Sat May 21 1988 01:40 | 10 |
| re .10:
Open wire *is* rated at a higher current capacity than cable (a wire table I
have rates #14 as able to take 32A continuously as a single, bare open-air
wire), *BUT* try explaining that to your insurance company should your house
burn down and they find 20A fuses for #14 knob-and-tube wiring, even if it
wasn't at fault! Run #14 gauge with 15A breakers/fuses and use its "open-ness"
as a safety factor to make up for its obsolencence, if you keep any of it.
-Mike
|
291.386 | Electric wire thru several 2 x 4's ? | HPSTEK::CURRAN | | Wed May 25 1988 20:20 | 14 |
|
My husband is currently wiring up a new addition. There are
several places in the room where we need to go thru about 4-5
2 x 4's, which is about 6-7.5". Last night my husband was
drilling thru the middle of one of these and broke our new
drill, because of the 16" distance he needs to start with
a small drill then put a larger one in the hole and attach
the drill to it. Seems the larger drill wasn't tightened enough
and it damaged the holders. Is there an easier way to do this ?
Could the 2 x 4's be notched and then covered with metal to
still meet code ? What would be the easiest way to notch them ?
thanks
Karen Curran
|
291.387 | Notches and grooves | VIDEO::DCL | David Larrick | Wed May 25 1988 21:08 | 20 |
| Yes, the Code allows you to install wiring in notches or grooves and then
cover them with metal plates to protect them from nails and other damage.
It goes into some detail about how thick the metal plates need to be. I
was going crazy looking for material that would meet these specs until my
wiring inspector let me in on the secret: just use the box sides that are
left over when you disassemble boxes to gang them.
I used a router to cut a groove along some framing lumber. Repeated passes
with a circular saw (with its blade set to the proper depth of cut) might
be faster for cutting notches. Actually, just cut the notch top and bottom
with the saw, then hit between the cuts with a hammer; a good-sized plug
should pop right out. Neatness doesn't count much, as long as you leave
something sound enough to attach the metal plates to.
Don't notch so deeply that you weaken the structure, especially in multiple
adjacent boards. And don't count on the metal plates for any structural
help; their purpose is to protect the wiring from nails, not to hold the
house up. If you go deeper than, say, 1/3 of the board's width, you should
be drilling holes, not cutting notches.
|
291.388 | | SMURF::WALLACE | Life's a beach, then you dive! | Wed May 25 1988 21:08 | 14 |
| 4-5 2x4's sounds like a supporting post for a beam or a header
which would make me leary of notching it. There are two things
you might do.
1. Notch the 2x4's and then replace the notched out section
with a piece or wood so that the strength of the post is not
impaired. (If in fact it is a supporting post of some kind)
2. There are 90 degree drill attachments that are sold for just
this purpose. It allows you to get into tight places. The
unit goes into the drill chuck like a regular bit, then forms
a tight 90, into which you insert the drill bit.
3. Rent a 90 degree drill.
|
291.389 | Anther way to wire | FRSBEE::DEROSA | because a mind is a terrible thing | Thu May 26 1988 12:36 | 10 |
|
Another way I've seen wiring done is instead of drilling or notching
2x4's, run the wire up into the attic or the space above the ceiling
and then back down to where ever and then up again and so on. This
uses more wire but you don't have to drill so many holes and the
holes you have to drill, you can get at. The good thing about this
is if you want to cut a hole in the walls for something the wires
aren't in the way..
BD
|
291.390 | trouble drilling?? | AIMHI::BERNARD | | Thu May 26 1988 16:59 | 20 |
|
At the risk of sounding out of line, if he can't get holes drilled
in 2x4's, are you sure he should be wiring the house???
I can't imagine why he can't drill a 3/4" hole in studs with a regular
drill set-up. And why can't the smaller drill go through all of
them? Is he pushing too hard, or not pulling the drill out occasionaly
to clear the saw dust? Or is the bit dull?
The previous suggestions of using a 90 degree drill, or going to
the attic or basement are excellent alternatives. Most electricials
I've worked with over the years use notching as a last resort. For
one thing, if you don't also notch for the plate, it will make the
sheet rock bulge in that spot. Not much granted, but it will show.
Also some inspectors are real tough on the depth of the notch. Why
risk having to add more support.
good luck
JMB
|
291.92 | Fried Motor anyone ? | TOOK::ARN | Tim Arn LKG2-2/BB9 226-7572 | Thu May 26 1988 17:40 | 7 |
| Does anyone know where you can buy spools of varnish coated copper
wire for rewinding motors? I've called every electrical supply place
and motor repair shop but noone sells the wire. I'm in N.H., Mass.
Thanks
Tim
|
291.391 | won't fit !! | FREDW::MATTHES | | Thu May 26 1988 17:59 | 8 |
| The problem is that you don't have the normally 14-1/2" between
studs when you encounter 3, 4, or 5 of them together.
The regular drill setup won't fit.
He's probably having a problem because he's going at an angle and
then trying to straighten out once in the stud pocket. This would
put undue sideways pressures on the drill and bit.
|
291.392 | Use Spade bit, series of extenders | ERLANG::BLACK | | Thu May 26 1988 18:11 | 19 |
| I've found a spade bit is better for these jobs than an auger bit.
Because the shank is smaller than the head, to some extent one CAn
straighen out the hole.
You can get 6", 12" and 18" bit extenders for the Irwin spade bits.
Drill the first 6" with the bit, add a 6" extender and drill the
next 6", remove and add the 12" extender, etc.
The first 6" could be a slightly larger diameter, too.
If all else fails, how about removing the stud adjacent to the 6"
pillar, drilling the hole, and putting the adjacent stud back.
Notching should be OK too. The nail plates to cover the notch cost
a quarter each at Ralph Pill's. (I have 10 or so such plates if
you want 'em -- I ended up drilling holes instead!)
Andrew
|
291.93 | | VAXWRK::INGRAM | Larry Ingram | Thu May 26 1988 19:42 | 6 |
| The wire is called "magnet wire". What gauge are you looking for?
the thinner stuff can usally be purchased from electronic supply
houses, not electrical. You could also look in the yellow pages
under wire-insulated or wire products.
Larry
|
291.393 | Just get a long auger bit | HPSVAX::POWELL | Reed Powell HPS Marketing | Fri May 27 1988 00:27 | 26 |
| Notching is certainly a last resort - lots more work to get it flush
with the 2x so the sheetrocking is not a problem. Code says you
can notch up to 1/3 of the width, fyi.
I disagree on the spade vs auger point. What I did when I started
my wiring, after trying a spade bit a couple of times, was to go
out and get a 5/8" x 18" auger bit (costs around $15 at Spags).
I never regretted it. Especially for going through multiple 2xs
in one swipe - the auger would have been a pain in the a**. The
auger pulls itself in nicely.
If the combined depth of the 2xs is real deep, then you end up hitting
it from each side, pointed towards the outside wall (making a sort
of V), and then either pushing the wire through, or maybe having
to fish it through, depending on how well you got the two holes
lined up. I never had to do that though - but then I used 2x6s
and that gave me the necessary additional depth.
I doubt if this is a supporting post or anything. Probably is either
at the corner of an inside partition wall, and the extra 2x are
there to both give nailing surfaces for the wallboard on all sides
and to give a solid surface for the partition to be nailed into,
or else an inside corner along the outside wall, again to give added
nailing surfaces for the wallboard.
|
291.94 | Motor still fried,getting well done | TOOK::ARN | Tim Arn LKG2-2/BB9 226-7572 | Fri May 27 1988 13:53 | 8 |
| I'm looking for 20 gauge. Somebody I called yesterday also suggested
an electronic supply house. Do you know of any good ones off of
495? I didn't look under wire in the yellow pages either. I'll check
it out.
Thanks
Tim
|
291.95 | A couple of places to try | VAXWRK::INGRAM | Larry Ingram | Fri May 27 1988 14:30 | 14 |
| > Do you know of any good ones off of 495? I didn't look under wire in the
> yellow pages either. I'll check it out.
You could try Active electronics in Westboro. It's on Flanders Rd.,
about 1/2 mile west on Rt. 9 from 495. Phone is 366-9684 or 366-
8899. Also, You-Do-It Electronics just off Highland Ave. in Needham.
That is just off Rt. 128 though.
Radio shack sells the stuff too, but the thickest they have is 22
gauge.
Larry
|
291.394 | | HPSTEK::CURRAN | | Fri May 27 1988 17:42 | 25 |
|
Wow, I really pleased to see so many responses.
The 2 x 4's are for supporting beams and headers on either side
of 8' windows. Going to the attic was an alternative and we did
do that in the areas we could. On the end wall this was not possible.
He is most capable of doing the work, you must admit that after
working a 10 hour day, and then working around the house anyone
is likely to have their patience tried.
What we did was bought a 1/2" drill, the one we had was 3/8"
and we bought the Irwin spade bits with the extenders. He's
going to give that a shot this weekend.
He was using just regular drills to begin with.
The auger bit sounds like a good idea, We missed that at Spags
yesterday, are they where the other drill bits are ? On the main
isle ?
I was looking thru the Sears catalog and the have a right angle
attachment for $7.99, perhaps we'll try that with the auger bit.
thanks for the help
Karen
|
291.395 | Using spade drill bits | SEESAW::PILANT | L. Mark Pilant | Fri May 27 1988 19:06 | 12 |
| On comment on the extensions: make sure the set screw is TIGHT.
There is nothing worse than having the set screw loosen up leaving
the spade bit still on the hole. (I had this happen when I was
drilling through 2 4x4s and 1 2x4 nailed together.) Also, remember
to pull the bit out frequently to let the wood chips out. Otherwise
the bit may bind up in the hole.
If I has it to do over again, I would not have used the short (6")
spade bits. I would have located one of the longer auger bits or
an 'electricians' long (18"-24") twist drill of the right diameter.
- Mark
|
291.396 | I use drill extensions only because I'm too cheap to use the right tool | STAR::SWIST | Jim Swist ZKO3-4/U14 381-1264 | Fri May 27 1988 19:55 | 7 |
| Mark's point is well taken. Extension bits are inexpensive but
don't really work all that well. The problem is that they have
to serve the function of the drill chuck but in a space equal to
the smallest spade bit they support (3/8" to 1/2" typically).
Allen-head setscrews just don't cut it given the torque generated
by drilling through 5 2*4's or whatever. If you can get it tight
enough, you'll probably strip the setscrews or your wrench.
|
291.96 | | NEXUS::GORTMAKER | the Gort | Sat May 28 1988 01:47 | 7 |
| An electronic supply house should carry it. Belden is one brand
Carol Cable is another you may have to special order to get a spool
with enough footage to wind a motor depending on gauge most of the
spools I have seen were only 100-200' for 20-32 ga. sizes.
-j
|
291.397 | | BPOV08::SJOHNSON | I've found my Victorian at last!!! | Fri Jun 03 1988 16:29 | 17 |
| re. < Note 2328.10 by STAR::SWIST "Jim Swist ZKO3-4/U14 381-1264" >
> Mark's point is well taken. Extension bits are inexpensive but
> don't really work all that well. The problem is that they have
> to serve the function of the drill chuck but in a space equal to
> the smallest spade bit they support (3/8" to 1/2" typically).
> Allen-head setscrews just don't cut it given the torque generated
> by drilling through 5 2*4's or whatever. If you can get it tight
> enough, you'll probably strip the setscrews or your wrench.
>
I did just that recently, the allen head set screws
stripped, and I went out and bought a longer extension
at Sears. Same thing though, after I use it 15 or 20 times
the screws will strip again I would say.
Steve
|
291.401 | Dead Electric Outlets - HELP! | BLURB::WIEGLER | | Mon Jun 06 1988 13:34 | 26 |
| One evening last week we had a thunder storm. Although we didn't lose power,
our lights did flicker a few times. The following morning 3 electic
outlets in our house were dead. I don't know if the storm had anything
to do with it or not, but I thought it was worth mentioning.
The three dead outlets are all in bathrooms (one outlet in each
bathroom). The outlets are NOT GFI outlets. They are regular outlets,
just like everywhere else in the house (the house is 10 years old and
the only GFI outlet is in the garage).
I checked the cicuit breakers and they are all ON. I even flipped them
all off, and then on again, just to be sure. I used a line tester and
confirmed that there is power at each of the circuit breakers
themselves. I also used the line tester at the outlets (removed the
cover plates and tested at the screw terminals on the outlets) and found
that there is no power at any of the outlets. That is, there doesn't
seem to be power leading in to any of the outlets. As far as I can
tell, there doesn't seem to be anything on this circuit except for these
three outlets (one of which is used for the washing machine).
What do I do now? I'm looking for suggestions.
Obviously, I could call in an electrician, but I usually try to handle
these kinds of problems myself if I can. However, when I run out of
ideas, I will call an electrician (anyone know a good one in Manchester,
NH?)
|
291.402 | Just have to trace circuits | NSSG::FEINSMITH | | Mon Jun 06 1988 13:54 | 7 |
| Its a pain, but you'll need to trace the circuit from the breaker
to the first outlet. You may find a junction box somewhere in between
tat first outlet and the panel which has a very high resistance.
Its a nuisance job, but its probably the only way to find the problem.
Eric
|
291.403 | It still may be that other GFI! | TRACTR::DOWNS | | Mon Jun 06 1988 14:18 | 7 |
| Did you check the GFI that you mentioned in the garage. The garage
GFI may control the three outlets in all the baths. With one GFI
oulet you can easily protect a number of outlets that follow the
GFI in the same circuit. Otherwise you have to start tracing the
circuit as mentioned in .1
Good Luck!
|
291.404 | Ck for Panel GFI | NSSG::FEINSMITH | | Mon Jun 06 1988 14:38 | 6 |
| In ref to .2, the house I had in NY had all the bathrooms and the
one outside outlet on the same GFI (in panel box), so that's probably
a good shot.
Eric
|
291.405 | This could be easier that I thought | BLURB::WIEGLER | | Mon Jun 06 1988 17:32 | 4 |
| Thanks a lot.
I'll check that GFI tonight. That sounds like a very likely suspect.
I didn't realize that one GFI would protect the other outlets on
the same circuit. I'll post the result tomorrow.
|
291.406 | GFI in panel box? | BLURB::WIEGLER | | Mon Jun 06 1988 17:35 | 4 |
| One more thing....
RE: .3
You said you had a GFI in the panel box. What exactly would that
look like? None of my circuit breakers look unusual.
|
291.407 | Make a list | VIDEO::DCL | David Larrick | Mon Jun 06 1988 17:45 | 7 |
| Not to pick on .0, but this episode underscores the importance of having an
accurate electrical map of your house - a list of every electrical outlet,
light, and appliance in the house, what circuit they're on, how much current
they draw, and ideally how the cabling runs.
Making this list while things are working properly is infinitely easier than
trying to figure it out after something fails.
|
291.408 | | REGENT::MERSEREAU | | Mon Jun 06 1988 17:51 | 7 |
| RE: -.1
> Making this list while things are working properly is infinitely
> easier than trying to figure it out after something fails.
For those of you that normally have a properly working system :^}
|
291.398 | Basic grounding questions | LABC::FRIEDMAN | | Mon Jun 06 1988 23:43 | 14 |
|
A basic house wiring question:
The green wire is the ground. I connect this to the recepticle
green screw and also to each metal outlet box? The more connections
to metal conduits and boxes, etc. the better? My reasoning would
be that if a bare hot wire would touch any of the metal then a
short circuit would develop and the circuit breaker will trip.
Otherwise a piece of metal could be electrified and if some
poor grounded soul touched it they would be shocked. Is this
principle correct: all metal that could come in contact with
an electrified wire is best off grounded?
|
291.399 | Other uses also. | CLOSUS::HOE | Colorado's the place to be. | Tue Jun 07 1988 03:37 | 9 |
| There are other needs for grounding; your terminal at home or your
PC might generate RFI or radio frequency noise that radiates to
tvs and radios. Grounding reduces the RFI.
Lightening strikes dissipates better if the ground is within a grid
(cage). multiple ground paths are used to lessen the effect of the
lightening.
cal hoe
|
291.409 | You folks are so smart! | DOODAH::WIEGLER | | Tue Jun 07 1988 12:37 | 7 |
| I went home last night and checked the GFI outlet in the garage
and, sure enough, the button was out. The electrical storm must
have tripped it. I hadn't relaized that it was on the same circuit
as my bathrooms, but when I reset the GFI, all the outlets came
alive again.
Thanks again.
|
291.410 | how to trace the wire | MSEE::CHENG | | Tue Jun 07 1988 12:39 | 5 |
| re: .6
YES, I agree it's one of those things that homeowner SHOULD do.
Now the question. What method do you use to trace how the system
is wired. i.e. to find out where the 1st outlet, 2nd,... etc., without
tearing down the wall.
|
291.400 | | VIDEO::DCL | David Larrick | Tue Jun 07 1988 13:08 | 13 |
| Your reasoning in .0 is good. But there's more to it than that; electricians
and safety experts have built up a significant body of knowledge over the
years on grounding and related electrical subjects.
This body of knowledge is contained in the National Electrical Code. It calls
out the techniques and materials that should be used to achieve safe grounding
in a variety of circumstances.
Thought experiments such as the one in .0 are valuable for understanding why
the Code says what it does; but when it comes to doing the work, don't try to
derive your techniques from first principles. Get a copy of the Code and/or
the various commercial guides to it (as recommended elsewhere in this
conference), and follow it.
|
291.411 | | VIDEO::DCL | David Larrick | Tue Jun 07 1988 16:54 | 25 |
| I thought I remembered existing discussions of circuit-tracing techniques
in this conference, but I can't find them. Can anybody help?
The first step is to make the list of what outlets, lights, applicances,
etc. are on which circuits. This list will give you many clues in tracing
the cabling.
Any cable paths that are exposed in the basement or attic are relatively
easy, although time-consuming and error-prone, to trace. A flashlight, a
helper, and lots of patience are necessary.
If there's a GFCI in the circuit, tripping it will tell you which outlets
are downstream and which are upstream.
It's more work, but you can use the same technique with any electrical box,
by opening it up and disconnecting the wires that go downstream. You need
to use appropriate safety techniques, of course, and be prepared to repair
any wiring you might break, especially in very old work.
A thorough job of cable tracing is sufficiently painful that it's probably
reasonable to put it off until you have a problem - although it may be more
difficult then. The indispensable thing to have is the list of what's on
which circuit, and that's relatively easy to make - even enjoyable if you
make it a family project. The cabling information is a useful-but-optional
adjunct to that list.
|
291.412 | Don't believe every thing you read | LDP::BURKHART | | Wed Jun 08 1988 17:58 | 24 |
| Funny this should come up now. Last night I was working on some
wiring in my basement & garage for auto door openers and shop lights.
Well, I've been lazy and never di a check of what circuits were
connected with what. I figured it was pretty simple as the house
is only 3 years old and all the breakers labeled. So i figure I
can safely add 2 outlets for door openers & 2 fluorescent light
fictures to 3 basement & garage lights 75W; 3 smoke detectors; 1
300W spot light; and 1 15amp GFI outlet. All this on a 15 amp circuit.
Now the fun part; I turn off the circuit to work in the switch
box and while the power is off I decide to take a break and move
the sprinkler in the front yard. I go up stairs and start to head
out the front door but stop first to turn on the front entry way
lights. Guess what? No lights. Turns out in addition to the above
the outside front 2 lights (2 x 60W) and front foyer chandelier
(8 x 40W or 50W) are also on the same circuit. Does not leave much
on the 15 amp circuit for that 1 outlet I have in the garage for
plugging in the powertools.
Good thig I'm adding additional dedicated outlet for powertools.
...Dave
Who will be checking every outlet and light this week.
|
291.413 | I don't trust lables anymore. | TOLKIN::GUERRA | DUMP THE DUKE | Wed Jun 08 1988 20:39 | 11 |
| I don't believe everything I read either. My house is 3 years old
and I bought it with an unfinished second floor. There were two
pairs of wires going up to the second floor, two for heat and two
for lighting/outlets. The ends were dangling in the cellar marked
as north or south sides. When I was finishing the electrical installation
I figured I could electrify the side I was done with (north) so
I proceded to connect the lighting wire to the panel. Much to my
surprise, when I flipped the breaker on I heard a pop and the breaker
tripped. The wires on the south side shorted since they were touching
the junction box. It looks like the electrician that did the original
wiring didn't know north from south.
|
291.414 | Wiring an OLD house (no ground). | DCC::JAERVINEN | Peace thru superior firepower | Thu Jun 23 1988 12:45 | 41 |
| I finally have bought this old (>200 years) house in Chianti
(that's in Italy for those of you who don't drink wine).
The existing electrical wiring seems to be at least as old, if not
from Roman times...
To be frank, seeing the system would cause any US/German/Scandinavian
inspector to die of heart attack (or be electrocuted) immediately.
Nevertheless, ENEL, the State Energy company, connected power without
a whisper...
Basically, in Italy, they bring a two-wire (single phase) system
into the house (live and neutral). But neutral isn't necessarily
quite neutral (this is a rural area and the xformer may be quite
far away) and you are not supposed to ground the neutral at the entry
to the house as would be done here (in Germany) [and in US].
In fact, there's no ground whatsoever in the house. Despite that,
the person who did the wiring used only 3-prong outlets, just leaving
the center (ground) unconnected (probably just to enable him/her
to connect grounded devices easily to any outlet).
So eventually I would like to provide a ground in the system
before it grounds me. I think I should also use GFI's extensively.
I know how things are wired in Germany (I am an EE) but I have never
encountered a system like this. I'd be grateful for any ideas to
make a safe & simple wiring, as well as advice on any pitfalls.
There's a steel water pipe going from the house to a well about
1000 ft away (in fairly wet soil) which should provide a fair ground.
On the other hand, I keep thinking that there's no great need for
a ground if everything is protected by sensitive GFIs... (remember
that there's no code this installation has to conform to - just
has to be reasonably safe). This might be a problem with things
like the water heater which may have some leakage here and there
and make the GFI trip even when no real fault exists. Same thing
might apply to some other appliances.
Any ideas?
|
291.415 | | BEING::WEISS | Trade freedom for security-lose both | Thu Jun 23 1988 13:11 | 17 |
| > -< true ground could develop voltage in your neutral >-
From what I understood of what he said, there already IS current in the
'neutral'. If he connected the ground to it, then if he plugged a grounded
plug of, say, a power drill into a socket, it would charge the case of the
drill, which is probably a bad idea. :^)
I think he's planning on creating a 'ground' for the ground of the plugs that
is separate from the neutral. Different from wiring here in the states, but it
doesn't sound like a bad idea to me. The case of the drill would be connected
to true ground, which is what you want anyway. Course I'm no EE, so I'll defer
to the greater wisdom of nearly anyone, but it seemed like you had missed a
significant piece of what he'd said.
I agree, though, that I'd use GFIs wherever I could.
Paul
|
291.416 | | DCC::JAERVINEN | Peace thru superior firepower | Thu Jun 23 1988 14:13 | 24 |
| re .1,.2: .2 is right - as I said in .0 you are not supposed to
connect neutral and the (yet non-existing) ground together - because
the 'neutral' may not be quite neutral. When I measured the difference
between neutral and the water pipe was just about 2 volts - but
if one of the vineyards hanging on the same 220 volt (three phase)
line switches on a big machine, it might well be mich higher.
Also, if the power company's neutral breaks somewhere between the
transformer and my house, and I connect neutral to ground, then
everybody's power (after my house) would flow through my ground...
In the normal German (and US as far as I know) system all the neutral
and ground wires coming from the outlets are connected at one single
point (the fusebox) and nowhere else, the same point being connected to
a separate ground in the house (about 600 ft of flat galvanized steel
strip is usually used here, buried around the house) and of course the
neutral brought in by the power company.
There's a tendency to use very sensitive (10 mA) GFI's here in
Germany for special purposes though these are not yet approved by
VDE. These should offer quite perfect protection for humans (and
animals) in all circumstances, but may be too sensitive for some
purposes.
|
291.418 | Here's a pointer for you | CALVA::WOLINSKI | uCoder sans Frontieres | Thu Jun 23 1988 15:24 | 13 |
|
The wiring system in Italy sounds alot like the French one.
You might try contacting John Simpson in Valbonne he was the
European Area environmental specialist for a long time and is
extremely knowledgeable in all of the European power systems.
Just say I pointed you in his direction and I'm sure he'll help
out if he can. I know he could be easily bribed with a few bottles
of good Chianti. :-)
-mike
|
291.419 | Hey Maybe Try This! | TRACTR::DOWNS | | Thu Jun 23 1988 16:21 | 9 |
| I'm no electrician but I have done alittle wiring in my day. Why
can't you just drive a normal copper grounding rod into the ground
(usually 6 to 8 feet long) and connect a ground wire, connected
to a common bar and ground all wiring to that, If your going to
rewire the old place anyway.
P.S. I always thought tha inorder for a GFI circuit to work
effectively, you have to have a good ground system already intact
inorder to connect the GFI circuit breaker too????
|
291.420 | | MTWAIN::WELLCOME | Steve Wellcome (Maynard) | Thu Jun 23 1988 16:28 | 13 |
| The fact that neutral floats with respect to ground seems to me
to be basically irrelevant to the way you want to do the wiring.
Except at the main service panel (and ***ONLY*** at the main
service panel), here in the U.S. the neutral is kept strictly
separate from ground. I'd think that you would want to do the
same thing, except with the added premise that the neutral/ground
connection point for you is "somewhere else", outside your house,
and you have nothing at all to do with it, even at the main
service panel. Just keep neutral/ground separate everywhere.
I think your idea of using the water pipe going to the well for
your ground is good. It ought to work just fine.
|
291.421 | | DCC::JAERVINEN | Peace thru superior firepower | Fri Jun 24 1988 09:07 | 4 |
| re .6: A normal GFI doesn't rely on ground for its operation, it
trips based on the difference in current in neutral and live
(I think this has been discussed extensively elsewhere in this file).
|
291.422 | Not as complex as it seems at first | REGENT::GETTYS | Bob Gettys N1BRM 223-6897 | Fri Jun 24 1988 12:17 | 17 |
| I think that the way you want think about this situation
is to consider that the two wires which enter the house are both
hot (think 220volt line here in US with only 220volt equipment
hung from it - thus no neutral needed). Now it becomes obvious
what to do. Wire up the ground to all the desired outlets and
appliances, but NEVER connect it to either of the two "hot"
wires coming into the house.
As for GFI's - use them anywhere that you would normaly
use one (and they do sense on the difference between the two
power carrying conductors) and forget about it otherwise.
Remember that ground is there to keep the case of an appliance
at a potential that would be safe for you to touch when you are
grounded. It performs no other function at an appliance
connection point.
/s/ Bob
|
291.423 | | PSTJTT::TABER | Touch-sensitive software engineering | Fri Jun 24 1988 13:15 | 11 |
| So I went back to Richter & Schwan and looked it up. What I said about
sub-panels was in error, and I've removed it from the file to avoid
confusion to others. (However, what I said IS the way the subpanel in
my house is wired... more work to do, I guess.)
However, there was reason behind my madness, and it's this; if the
neutral is developing voltage with respect to a local ground, then
equipment that uses ground for a reference will have problems. There's
more to grounding than saftey, these days.
>>>==>PStJTT
|
291.439 | Should aluminum house wiring be replaced? | CLT::DOUCETTE | Joanne Shaughnessy | Wed Aug 03 1988 13:18 | 11 |
| My husband and I are in the process of buying a house, and we
just had it inspected and they found aluminum wiring throughout
the house. The house is 17 years old. The inspector recommended
that we have the branch circuitry changed to copper, and that
rewiring was not neccessary.
Has anyone had any experience with this? Is this procedure
satisfactory, and any idea what it costs?
thanks for any advice!
-Joanne
|
291.440 | not an expert but... | NAC::N_MORIN | | Wed Aug 03 1988 13:36 | 8 |
| I am not an expert but I seem to remember that aluminum wire was
found to cause fires if not installed properly. I think the wire
became loose after a period of time. Special procedures had to be
followed to install aluminum properly. Notice that aluminum wire
is not used in houses anymore. It may be in your best interest to
consult with an electrician. Maybe you can use wire replacing as
a bargaining chip to reduce the price. It is supposed to be a buyers
market. Good luck.
|
291.441 | | BEING::WEISS | Trade freedom for security-lose both | Wed Aug 03 1988 13:58 | 5 |
| See also note 1450 for some discussion of aluminum wiring. I left this note
here to address the issue of whether the wiring should be replaced and if so
how to go about it and how much it would cost.
Paul [Moderator]
|
291.442 | | SMURF::WALLACE | Life's a beach, then you dive! | Wed Aug 03 1988 15:17 | 9 |
|
RE: 0
I don't think it's necessary to replace the wire but you should
have an electrician check it out. There is a "goop" used for
aluminum wiring to keep it from corroding and loosening as .1
suggested. Although aluminum wire is no longer used in general
house wiring, 14-2, 12-2, the service entrance cables and most
other big stuff, is still all aluminum.
|
291.443 | should be no problems | MPGS::PARTAIN | Chuck Partain, KA1MWP | Wed Aug 03 1988 17:04 | 14 |
|
the goop is called no-al-ox.
It is a cleaner/deoxidizing compound that keeps the aluminum from
becomming oxidized on the terminals. I have had NO problems for 12
years except I have taken off the mains ands cleaned them with this
stuff.
---------------------------- I DO NOT----------------------------
recommend anyone but an experienced electrician doing this as the
volts/amps are enough to ruin your day.
------------------------------------------------------------------
If it has to be done at all.
chuck
|
291.444 | | POOL::HAMMOND | Charlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684 | Thu Aug 04 1988 18:42 | 15 |
| >< Note 2520.3 by SMURF::WALLACE "Life's a beach, then you dive!" >
>
> ...the service entrance cables and most
> other big stuff, is still all aluminum.
Service Entrance Cables are the ones from the meter box to the
main breaker box, if I recall the code definitions. Or do you mean
the wires from the transformer on the pole to the meter box? In
either case I thing your wrong. I know from first hand observation
that ALL the wires in my meter box are copper. I think this is
general practice. The 'extra care' required for Aluiminum isn't
worth it.
However on the transmission line side of that transformer on the
pole you're almost sure to find Aluminum.
|
291.445 | | HPSMEG::LUKOWSKI | Nat'l apathy week & nobody cares! | Thu Aug 04 1988 19:24 | 13 |
| It may depend on which electric company you are serviced by or
whatever the electrician felt comfortable with. I asked the electrical
inspector about the aluminum wire at my house which is all of the
wire from the pole to the breaker box. He said that it is getting
very uncommon to use copper wire for this cable since it costs so
much more. I'm guessing but I believe the numbers were something
to the effect of $1.10/ft for aluminum and $3.50/ft for copper.
I know that at least part of the wire to my cooking range is aluminum
but I think it is only the ground wire. As was said before, aluminum
wire has been determined to be safe WHEN INSTALLED PROPERLY.
-Jim
|
291.446 | | SMURF::WALLACE | Life's a beach, then you dive! | Thu Aug 04 1988 20:17 | 8 |
|
Price is the key. I have Aluminum entrance service cable from
the pole transformer to the meter box, and from the meter box
to the service circuit box. All the wires from the service
to the house (individual circuits) are copper. When you get
to #4 and larger wire sizes, I think you'll find aluminum to
be more popular. (cheaper)
|
291.447 | Aluminum just has to be used properly | FREDW::MATTHES | | Thu Aug 04 1988 20:24 | 21 |
| re last couple
Right - WHEN INSTALLED PROPERLY.
All the fame (on infame) that AL wire has received has been because
it was used to wire houses and the Al just pushed into the Cu sockets
on outlets. Oxidation, expansion, contraction - high resistance
connection - heat - fire.
I recently installed a subpanel in the garage as well as changed
over from 100 to 200 amp service. The cable from the street is
Al and the cable I used for the subpanel ~75 feet is Al. The Al
is at least 2 sizes larger the Cu I would have needed but is one-third
the cost. The 75' Al cable cost me $93.00. I forget exactly what
the quote was on the Cu but I know I nearly fainted.
Then I got educated on how to install and work with Aluminum. The
problem was when they used it to wire houses, the electricians treated
it the same as they did copper. You can't do that. And as long
as you treat it properly, it's just as safe as copper. And a hell
of a lot cheaper.
|
291.448 | branch circuits and fixtures | RETORT::GOODRICH | Taking a long vacation | Fri Aug 05 1988 14:16 | 17 |
| AL branch wires have 2 problems;
In the 60s they were installed without proper treatment and
with fixtures not suited for AL.
The wires break easily if bent too many times.
New branch wires can be very expensive to install, somewhat
dependent upon the house construction.
I would suggest checking all fixtures to ensure that they
are suited and treated for AL wire. Be very careful not to
bend the wires too many times - they will break.
This may be a job for an electrician.
- gerry
|
291.449 | | POOL::HAMMOND | Charlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684 | Fri Aug 05 1988 17:42 | 25 |
| Continuing a theme from -.1 ...
Yes, if aluminum wiring is installed correctly -- meaning proper
wiring devices and proper installation techniques, which are BOTH
DIFFERENNT from whats used with copper wire -- then it is safe.
But will it stay that way? Aluminum becomes brittle and breaks
easily when it is bent repeatedly and/or sharply. I've never lived
in a home in which switches/outlest/light fixtures haven't been
changed from time to time, either to replace worn out devices or
to modernize. The simple act of disconnecting aluminum wire and
reconnecting it to a new device is usually more than the wire can
safely tolerate. In theory you should be able to do this without
significant flexing of the wire. In pratice it is just about
impossible.
I worked for ALCOA for a while after I got out of college. They
had (surprise!) aluminum wiring and whenever they replaced
anything they cut the wire back and butt spliced a new piece onto
the end, just to avoid this problem.
The price argument is valid for heavier gages of wire, expecially
since these tend to be 're-worked' less often. As for aluminun
anwhere inside the breaker box, well, I might make some limited
exceptions, but I think it is trouble looking for a place to happen.
|
291.466 | questions on rewiring motors for 220 | STEREO::COUTURE | Gary Couture - Govt. Syst. Group - Merrimack NH | Mon Oct 24 1988 16:41 | 15 |
| I am in the process of wiring my new workshop and would like to include
some 220 circuits so I can run my larger tools on 220. Can someone give me a
quick lesson in whats involved in changing a motor to 220 and wiring for it?
- I plan to run 12/3 and use a 20 Amp breaker with probably only 2 boxes to a
breaker.
- I have not looked at the motors closely but I think the re-wiring diagrams
are on them. But do i need to replace the electrical cord??
- what type of outlet and plug do i need?
thanx
|
291.467 | Ck youer instruction booklet | NSSG::FEINSMITH | | Mon Oct 24 1988 18:50 | 8 |
| Check the instructions for the given tool. Many large power tools
can be wired for either 110 or 220v. The type of plug/outlet is
dependent on how much the unit draws and any local codes. A 220v/15A
plug is different from a 20A plug, and even within the same current
ratings, can be multiple styles (ie straight plug in, twist lock,
etc).
Eric
|
291.470 | Do you mean 12/3 wg or 12/2wg? | GWYNED::MCCABE | | Tue Oct 25 1988 14:41 | 5 |
| By the way, most 220v tools do not need a neutral, unless you have
a 100v lighting fixture. 12/2 wg should be fine, tape the white
wire red in the outlet box and breaker panel.
Chris
|
291.365 | Send me the $63 and I will do it for you! | OASS::B_RAMSEY | Bruce Ramsey | Mon Oct 31 1988 22:33 | 13 |
| My dad had the same problem in his house - his wife wanted the couch
in the middle of the room with the lamp next to it. He took a knife
and made a slit in the carpet, drilled a whole thru the flooring
big enough to fit a plug thru and then wired an outlet in the joist
in the basement. He stuck the plug thru the slit in the carpet,
thru the hole in the floor and plugged it into the new outlet.
There is no cover plate at $63 and dog would have to be a REALLY
good aim to be able to make it in the slit in the carpet and into
the outlet on the joist. You could move the outlet 6-10 inches
away from the whole in the floor just as long as the cord from the
lamp would go the distance.
|
291.366 | Don't try this at home, kids | HANNAH::DCL | David Larrick | Tue Nov 01 1988 15:47 | 3 |
| .12 is, of course, in violation of the National Electrical Code. I
hope that the insulation on the lamp cord is in good shape, and that
somebody inspects it frequently.
|
291.367 | | BEING::WEISS | Trade freedom for security-lose both | Tue Nov 01 1988 16:56 | 12 |
| > .12 is, of course, in violation of the National Electrical Code. I
> hope that the insulation on the lamp cord is in good shape, and that
> somebody inspects it frequently.
Could you elaborate, Dave? I know that it's a no-no to run a cord under a
carpet, becuase of the wear of people walking on it and grinding dirt into the
insulation. But if the hole in the floor were clean and smooth with no
projections that could damage the insulation, it seems like the outlet-in-the-
joists solution would work safely. But I don't really know the electric code.
Why is this dangerous and outlawed?
Paul
|
291.368 | | MTWAIN::WELLCOME | Steve Wellcome (Maynard) | Tue Nov 01 1988 16:59 | 5 |
| Re: .13
Can you quote chapter and verse of what part of the code it violates?
It seems as though it's one of those things that *ought* to be in
violation of the code, but I'm not sure it is.
|
291.369 | No Code book here, but I'll work on it... | HANNAH::DCL | David Larrick | Tue Nov 01 1988 19:33 | 9 |
| re .14, .15: I don't have my Code book handy, but I'll look it up and
post the information when I get a chance. The issue is probably that
only permanent wiring may be run through structural members (such as
floors), and lamp cord with a plug on the end is scarcely permanent
wiring.
It also makes sense to plug an appliance into an outlet that's located
in the same room as the appliance, so you can unplug it conveniently
and safely if it develops a short.
|
291.370 | | STROKR::DEHAHN | | Wed Nov 02 1988 13:50 | 8 |
|
I'm with DCL, it's against Code. Temporary wiring can't be installed
under carpeting. And any permanent receptacle must be surrounded
with non combustable material. Thus you need an honest-to-goodness
floor receptacle. It's your insurance loss.
CdH
|
291.371 | | MTWAIN::WELLCOME | Steve Wellcome (Maynard) | Wed Nov 02 1988 14:00 | 7 |
| The permanent receptacle down in the basement on the beam is
certainly legal; it's in a legit box. I'm not sure if lamp
cords, etc. are classed as as "temporary wiring"; I thought temporary
wiring was what you would do at a construction site, etc. until
the real wiring was in: Romex tied together with wire nuts
and dangling off nails driven into ceiling joists, etc. The "under
the carpet" restriction might apply, but this is "through", not "under".
|
291.372 | The last word...maybe! | GWYNED::MCCABE | | Wed Nov 02 1988 16:23 | 11 |
| The real problem here is there is a receptacle in the floor, ie
the female cord cap. In my 1984 code book, 370-17 (b) on floor
boxes, it states "boxes listed specifically for this application
shal be used for receptacles located in the floor". The only
exception is for show windows. You can not run lamp cord, SJ cable
etc, through a wall or floor legally, only conduit, NM cable, BX,
etc. Article 480-8 on flexible cords states " Flexible cords shall
not be used (2) where run through holes in walls, ceilings or floors.
Chris
|
291.373 | | MTWAIN::WELLCOME | Steve Wellcome (Maynard) | Thu Nov 03 1988 11:54 | 2 |
| 480-8 is it! It's illegal. Thanks for hunting that up.
|
291.471 | | POOL::HAMMOND | Charlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684 | Fri Nov 04 1988 17:13 | 21 |
| 1) Check the directions that came with them motor/tool. If you
don't have instructions for converting vrom 110 to 220 you
probably can't do it. i.e. the motor has to be designed to be
convertable -- not all motors are.
2) re .3
> Hopefully you mean *1* box to a breaker, this is 230V right?
> Check the NEC, you are allowed to do multiple boxes to a
> breaker only as an exception around 120V circuits, this is not
> generally allowed.
Could you be more specific, please? I ask because I have two 230
volt outlets and two 110 volt duplex outlets wired to a single 20
amp breaker in my "shop" (read "back of garrage"). Since all the
wiring devices are rated for 20 amps (I think the 230 volt outlets
are actually rate higher) I don't see any way I could overload the
circuit without tripping the breaker (which I could probably do if
I plugged in and ran enough stuff at the same time, but then I
could also do that on a 110 volt circuit). I also don't see any
other hazzard. What's the purpose of this code requirement?
|
291.472 | | MILVAX::HO | | Tue Nov 08 1988 20:33 | 10 |
| re .5
A 230 volt outlet wired to a single 20 amp breaker? Is this possible?
I thought two adjacent breakers ganged together were needed to get
230 volts. Otherwise the circuit is being fed by only one of the
two hot legs in the panel.
- gene
|
291.285 | why 110V not 240V ? | GIDDAY::GILLARD | Eyeless in Gaza | Wed Nov 09 1988 02:03 | 22 |
| Re: .9
> The larger circuits that feed electric dryers, hot water heaters,
> and stoves contain both a red and a black wire (along with one or
> two others: a white and possibly a bare). The black wire gets
> attached to one of the two insulated feeds from the power company,
> while the red wire goes to the other insulated feed. The smaller
> 110v circuits contain only a black wire, in addition to the white
> and bare wires. This can go to either of the above two feeds, but
> the system as a whole should balance the load drawn from each feed
> as closely as possible (it makes the power company very happy by
> causing less wear and tear on their equipment!).
I've been meaning to ask this question for twelve months, and I'd better
ask it now bacause I'm going next week.
Pity an ignorant lad. Why do US domestic electrics use 110 V and have all
this damned tinkering around with load balancing and the like ? Anyone
know why 240 V was not chosen as in most of the rest of the world ?
Just _very_ curious
Henry Gillard - TSC Sydney
|
291.473 | | WILKIE::THOMS | | Wed Nov 09 1988 11:08 | 25 |
| >< Note 2744.6 by MILVAX::HO >
>
>
> re .5
>
> A 230 volt outlet wired to a single 20 amp breaker? Is this possible?
>
> I thought two adjacent breakers ganged together were needed to get
> 230 volts. Otherwise the circuit is being fed by only one of the
> two hot legs in the panel.
>
> - gene
The two hot leg "busses" alternate down the panel on both sides.
Any double pole breaker inserted in the panel will attach to both legs.
A B
B A
A B
B A
Ross
|
291.474 | | MTWAIN::WELLCOME | Steve Wellcome (Maynard) | Wed Nov 09 1988 12:14 | 2 |
| I assume by "single 20-amp breaker" the author must mean one double breaker.
|
291.286 | | MTWAIN::WELLCOME | Steve Wellcome (Maynard) | Wed Nov 09 1988 12:19 | 6 |
| I suppose because for most domestic use, 240 volts is much more
than is necessary; who needs 240 volts to run an electric shaver
or a fan? 120 volts is presumably less dangerous in the case of
accident, too.
My guess.
|
291.287 | As explained to me by a power xmission guy... | BOSTON::SWIST | Jim Swist BXO 224-1699 | Wed Nov 09 1988 12:45 | 32 |
| re: .-1
There isn't enough safety difference between 120 and 240 for that to be
an issue.
The answer to your question is historical.
It goes back to finding the right balance in the simple equation
W = E*I. What you need to run electrical things is power (measured
in watts) - theoretically the volts and amps are irrelevant as long
as when multiplied together they yield the power you need. Practically
speaking, too low a voltage will require too high a current - this
is inefficient to transmit, requires huge transformers, expensive
heavy wire, and heat buildup/fire problems if connections get loose.
Too high a voltage can break down insulation easily, and is difficult
to switch without expensive devices.
I believe the history is that 120V was arrived at in the early days of
power transmission planning as the best balance in the above equation
(some old systems (USA as well as foreign) are still 120V). What
wasn't figured in the equation was the demand for electricity - no one
figured it would find as many applications as it did. Doubling the
voltage was a fairly cheap solution to this problem since the
insulation and switching problems are really not much worse at 240 than
120. The alternative of keeping the voltage the same and doubling the
current would have meant rewiring a large percentage of users and
transmission facilities.
That's the story as I understand it. Upward compatibity, inertia,
and history are all responsible for having both 110 and 240 devices
as well as entire systems.
|
291.288 | | WOODRO::THOMS | | Wed Nov 09 1988 12:46 | 17 |
| >< Note 1742.21 by MTWAIN::WELLCOME "Steve Wellcome (Maynard)" >
>
>
> I suppose because for most domestic use, 240 volts is much more
> than is necessary; who needs 240 volts to run an electric shaver
> or a fan? 120 volts is presumably less dangerous in the case of
> accident, too.
>
> My guess.
I was always told in school etc., that 120v became an industry U.S. standard
at the turn of the century and stuck. Too costly to change. Actually the
higher voltage appliances would be more efficient, motors lighter, less windings
and all that good stuff.
|
291.289 | | BEING::WEISS | Trade freedom for security-lose both | Wed Nov 09 1988 12:53 | 0 |
291.290 | | CRAIG::YANKES | | Wed Nov 09 1988 17:18 | 5 |
|
Besides, when has the US ever worried about being standard? Don't
we still speak in terms of those silly inches and yards?? :-)
-c
|
291.475 | | CHALK::HAMMOND | Charlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684 | Fri Nov 11 1988 17:49 | 23 |
| > <<< Note 2744.7 by WILKIE::THOMS >>>
>
>The two hot leg "busses" alternate down the panel on both sides.
I believe that this is always, or almost always, the case for the
type of breaker box you have in mind. However, there are other
kinds!
I have a six position breaker box in my garage. The breakers run
across the box. The phases follow a pattern something like this:
A B B A A B
(This may not be exactly right since I don't have the box in front
of me to look at, but the point is as follows.) Obviously it is
physically possible to put a two-pole breaker in two positions in
which both poles will contact the same phase. It is highly
unlikely that there is any goo reason to do this; it would almost
certainly violate the code prohibition of conductors in parallel
(or whatever). This box is clearly labeled indicating where
two-pole breakers may and may not be used.
So... Check your box before you plug in two pole breakers.
|
291.291 | | CURIE::BBARRY | | Fri Nov 11 1988 17:57 | 5 |
| < Besides, when has the US ever worried about being standard? Don't
< we still speak in terms of those silly inches and yards?? :-)
Inches/feet/miles is better then inches/feet/ kilometers they use in
Canada.:-)
|
291.476 | Double check please! | WOODRO::THOMS | | Fri Nov 11 1988 19:04 | 5 |
| RE:9 Hmmm, Never run across a panel as you've described. Double check
the panel when you get a chance. If it is as you described, might be an old
panel, but the layout still doesn't make sense.
Ross
|
291.477 | | POOL::HAMMOND | Charlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684 | Mon Nov 14 1988 18:09 | 30 |
| > <<< Note 2744.10 by WOODRO::THOMS >>>
> -< Double check please! >-
>
>RE:9 Hmmm, Never run across a panel as you've described. Double check
>the panel when you get a chance. If it is as you described, might be an old
>panel, but the layout still doesn't make sense.
No need to double check; I know the insides of it. It was used for
our temporary electric service when our house was built. I saved
it when the permanent electric was connected and installed it in
our garage. At that time I had it all apart to install a separate
ground buss and to de-ground the neutral buss. At that time I saw
the actual shape of the power busses. I'll try to draw a
reasonable facsimile below.
.-------------------------------.
| (A)| (A),(B)--Place where
| .----------. .--------' phases A & B
| |.--------.| |.--. connect to buss
|**|| ** ** || ** ** ||**|
=====1====2====3====4====5====6===== ==== -- Bar onto which
`--'| |`--------'| | breakers attach
.--------' `----------' |
|(B) | ** -- Point at which
`-------------------------------' breakers contact buss
NOTE: Neutral and (separate) Ground Buses not shown. There is no
"Main" breaker as this is a distribution panel. (Its fed from a
breaker in the main panel. This may not be real accurate; the
point is the SHAPE of the phase buses.
|
291.478 | What vendor? | WOODRO::THOMS | | Mon Nov 14 1988 18:28 | 6 |
| Again, I've never seen a panel as you've described, doesn't mean that there
aren't any. I've been a part time Master electrician for the past 14 years
and have seen a few odd ball panels. Who is the vendor of this particular
panel?
Ross
|
291.479 | | MISFIT::DEEP | This NOTE's for you! | Mon Nov 14 1988 19:20 | 8 |
| re: .-1 Interesting!
On thing I notice is that if you want to put double breakers in the box,
you are ok as long as you put the double breakers in first, and single
breakers in last. 3 double breakers can be accomodated. Weird, but
functional.
Bob
|
291.480 | | POOL::HAMMOND | Charlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684 | Tue Nov 15 1988 13:23 | 10 |
| RE .12, .13
I'll try to remember to check the brand/model on the box tonight
and post it here. If you'd like to come by in Bedfore NH and see
it your welcome. I assume its a perfectly standard box -- I went
into Seamans Supply (sp?) and asked for a temporary service and
this is what they gave me.
Meanwhile back at .5 -- can you answer the question there?
(under 2)
|
291.481 | Check your load | WOODRO::THOMS | | Tue Nov 15 1988 15:30 | 38 |
| >< Note 2744.14 by POOL::HAMMOND "Charlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684" >
>
>
> RE .12, .13
>
> I'll try to remember to check the brand/model on the box tonight
> and post it here. If you'd like to come by in Bedfore NH and see
> it your welcome. I assume its a perfectly standard box -- I went
> into Seamans Supply (sp?) and asked for a temporary service and
> this is what they gave me.
>
> Meanwhile back at .5 -- can you answer the question there?
> (under 2)
I think the question was (correct me if I'm wrong): Is it o.k. to have multiple
outlets on a 240v brach circuit? The NEC says: Article 210-4 Multiwire
branch circuits (C) Line to Neutral Load. Multiwire branch circuits shall supply
only line to neutral load.
Exception No 1: A multiwire branch circuit that supplies only one utilization
equipment.
Exception No 2: Where all ungrounded conductors of the multiwire branch circuit
are opened simultaneously by the branch circuit overcurrent device.
Exception #2 is the key exception for your example. If you have the circuit
protected by the proper size overcurrent device (circuit breaker) and when
the breaker trips it opens all ungrounded wires (hot), you're o.k..
However, I would be concerned on what load you're placing on that circuit!
Article 430-25 and 210-22 state you must calculate the first (largest) motor
load (if over 1/8hp) at 125% full load current plus the sum of the other loads.
I bet that circuit you're using isn't up to the task of handling all of the
"possible" load. < It must be rated for the sum possible load!
Ross
|
291.482 | circuit protection | WILKIE::THOMS | | Tue Nov 15 1988 16:19 | 20 |
| >< Note 2744.5 by POOL::HAMMOND "Charlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684" >
>
> Could you be more specific, please? I ask because I have two 230
> volt outlets and two 110 volt duplex outlets wired to a single 20
> amp breaker in my "shop" (read "back of garrage"). Since all the
> wiring devices are rated for 20 amps (I think the 230 volt outlets
> are actually rate higher) I don't see any way I could overload the
> circuit without tripping the breaker (which I could probably do if
> I plugged in and ran enough stuff at the same time, but then I
> could also do that on a 110 volt circuit). I also don't see any
> other hazzard. What's the purpose of this code requirement?
You have the attitude that many home electricians have: Hey if I smoke the
wiring by placing too heavy a load on the circuit the breaker will protect me!
You should wire a circuit so the breaker will "never" have to trip due to
overload!
Ross
|
291.483 | | POOL::HAMMOND | Charlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684 | Tue Nov 15 1988 19:45 | 25 |
| > <<< Note 2744.16 by WILKIE::THOMS >>>
>
>You have the attitude that many home electricians have: Hey if I smoke the
>wiring by placing too heavy a load on the circuit the breaker will protect me!
>You should wire a circuit so the breaker will "never" have to trip due to
>overload!
Re: above -- Your admonishment is properly taken, but unneeded. I
DON'T have that attitude. I was trying to understand what might be
wrong with the way my shop is wired. I didn't intend my (possibly
poor choice of) wording to imply undue reliance on a breaker.
Re: .15 -- Thanks for the information. O.K. Both conductors are
controlled by one, two-pole 20 amp breaker, so the circuit is
within code in that regard. Now as to the load -- nothing is hard
wired into this circuit; it has 2-240v outlets and 2-120v duplex
outlets. Some place I have information as to how to rate the 120v
outlets; how do I rate the 240's?
My gut feeling is that I'm well within the limits. Reality is that
the heaviest simultaneous load I place on the circuit is the
radial arm saw plus a dust collecting shop vac. (The 120v outlets
are there for lesser tools, not used simultaneously. But that
doesn't mean that some one, some day... After there are 2 of the
240v outlets!
|
291.484 | Sorry, But... | MAMIE::THOMS | | Tue Nov 15 1988 22:17 | 30 |
| >
> Re: .15 -- Thanks for the information. O.K. Both conductors are
> controlled by one, two-pole 20 amp breaker, so the circuit is
> within code in that regard. Now as to the load -- nothing is hard
> wired into this circuit; it has 2-240v outlets and 2-120v duplex
> outlets. Some place I have information as to how to rate the 120v
> outlets; how do I rate the 240's?
>
> My gut feeling is that I'm well within the limits. Reality is that
> the heaviest simultaneous load I place on the circuit is the
> radial arm saw plus a dust collecting shop vac. (The 120v outlets
> are there for lesser tools, not used simultaneously. But that
> doesn't mean that some one, some day... After there are 2 of the
> 240v outlets!
O.k., Let me put in my last two cents about your shop circuit!
I believe it's in violation of code due to the fact there is
the potential to overload this circuit. In real life, if you have the skill
and the knowledge to do proper wiring methods (good connections, properly
stripped wire, etc.), your circuit will probably never cause you a
problem. However, what if you sell your house to a person that wants to
hook up his 2hp table saw, 3 hp compressor, a drill press and a shop
heater to this circuit? Let's also suppose that the 20 amp breaker fails
to trip at ~ 20 amps. (believe me this happens!)
Personally, I would stick with exception #1 that I quoted out of the NEC.
This recommends one multiwire circuit to one device/load.
Ross
|
291.485 | | POOL::HAMMOND | Charlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684 | Wed Nov 16 1988 16:49 | 26 |
| > <<< Note 2744.18 by MAMIE::THOMS >>>
> -< Sorry, But... >-
>
>O.k., Let me put in my last two cents about your shop circuit!
>I believe it's in violation of code due to the fact there is
>the potential to overload this circuit. ...
I appreciate your opinion and I may in fact change this circuit.
On the other hand you may have knowledge that you aren't sharing.
I'm quite certain that "potential to overload" is not a cause for
any code violation. If it were, every circuit with an outlet on it
would be in violation! (Let alone circuites with muliple, duplex
outlets!)
What I have is a circuit that I'm certain is quite safe the way I
use it. I also don't think that this circuit presents any greater
danger than any of the other, clearly "code legal" circuits in my
house. I had thought it met code requirements, but an earlier note
raised a question about this.
In a previous reply I asked specifically HOW the code requires you
to calculate the load froma 240v outlet. By adding 2x the result
of this calculation plus the load for the 2 110v duplex outlets
I'll know if it meets code or not. Isn't this the correct thing to
do?
|
291.486 | Send mail if you want to continue this argument! | WILKIE::THOMS | | Wed Nov 16 1988 17:47 | 58 |
| >< Note 2744.19 by POOL::HAMMOND "Charlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684" >
>
> I appreciate your opinion and I may in fact change this circuit.
>
> On the other hand you may have knowledge that you aren't sharing.
> I'm quite certain that "potential to overload" is not a cause for
> any code violation. If it were, every circuit with an outlet on it
You're dead wrong! Home circuits are certainly designed "not" to be overloaded!
Why do you think the code requires (2) 20 amp circuits in the Kitchen, (where
the potential to overload is the greatest in a home). Also, don't confuse
living space with shop area, two totally different areas.
> would be in violation! (Let alone circuites with muliple, duplex
> outlets!)
>
> What I have is a circuit that I'm certain is quite safe the way I
> use it. I also don't think that this circuit presents any greater
> danger than any of the other, clearly "code legal" circuits in my
> house. I had thought it met code requirements, but an earlier note
> raised a question about this.
I'm glad you don't wire houses for living. If you wire a problem in, at least
it will be yours.
> In a previous reply I asked specifically HOW the code requires you
> to calculate the load froma 240v outlet. By adding 2x the result
> of this calculation plus the load for the 2 110v duplex outlets
> I'll know if it meets code or not. Isn't this the correct thing to
> do?
I believe I told you how to calculate the load on your shop circuit in one of
my previous replies. There is no formula like X # of amps/outlet (like there is
for living space, 120v circuits). Mulitwire cicuits are sized to the "load".
BTW, I bet any good electrical inspector would fail your circuit due to the
reasons I stated in earlier replies. (I'll re-state : "the potential to overload
the circuit you've described is too great").
Let's suppose you have a 3hp compressor, a 2hp saw, a 1000 watt heater and a
3/4 hp drill press attached.
3hp x 746w /240 x 1.25 = 11.7 amps
2hp x 746w /240 = 6.2
3/4 x 746w /120 = 4.7
1000w /120 = 8.3 (Portable, not fixed)
------------------------------
30.9 amps
This example is basically the equipment I have in my shop.
My table saw is wired 120v. Each piece has it's own dedicated circuit with
the exception of the portable heater which is rarely used.
Ross
|
291.487 | WRONG! | MISFIT::DEEP | This NOTE's for you! | Wed Nov 16 1988 18:50 | 24 |
|
Typical home circuit, with the potential to plug 8 items in...(4 duplex
outlets)...
OK... I plug in my 1500 watt heater, my 1200 watt hair dryer... (that's 2)
Now, I plug in 6 more heaters (because I ran out of oil) ... My wiring
is to code, and I've just exceeded the limit. Of course the breaker
trips (if its working...whens the last time you toggled your breakers?)
What .-2 was trying to say is that it IS POSSIBLE to exceed the limits on
the normal BY THE CODE circuits.
Of course, the above senario is extremely stupid, but it proves the point.
I ran a dedicated 220v circuit for my table saw, and I have two outlets...
one in the garage and one in the cellar. The only thing I own that is
220 is the saw, and it can't be on both outlets at the same time.
When I move, I'll pull one of the outlets and take it with me. If that's
against the codes then the codes are wrong, and I'm not going to worry
about it.
Bob
|
291.488 | I'm glad it's your house | STROKR::DEHAHN | | Wed Nov 16 1988 19:06 | 6 |
|
You should have a seperate circuit for your garage, preferably a
subpanel.
CdH
|
291.489 | | MAMIE::THOMS | | Wed Nov 16 1988 19:08 | 43 |
| >< Note 2744.21 by MISFIT::DEEP "This NOTE's for you! " >
> -< WRONG! >-
>
>
>
>Typical home circuit, with the potential to plug 8 items in...(4 duplex
>outlets)...
>
>OK... I plug in my 1500 watt heater, my 1200 watt hair dryer... (that's 2)
>
>Now, I plug in 6 more heaters (because I ran out of oil) ... My wiring
>is to code, and I've just exceeded the limit. Of course the breaker
>trips (if its working...whens the last time you toggled your breakers?)
Come on give me a break! The code is written to cover most "normal" situations.
Your scenario is absurd.
>What .-2 was trying to say is that it IS POSSIBLE to exceed the limits on
>the normal BY THE CODE circuits.
Yeah and the code is written to make the possible overload conditions minimal!
>Of course, the above senario is extremely stupid, but it proves the point.
The only point you've proven is wiring should be left to professionals that
are licensed by the State.
>I ran a dedicated 220v circuit for my table saw, and I have two outlets...
>one in the garage and one in the cellar. The only thing I own that is
>220 is the saw, and it can't be on both outlets at the same time.
<When I move, I'll pull one of the outlets and take it with me. If that's
>against the codes then the codes are wrong, and I'm not going to worry
>about it.
>
>Bob
Why tell me, why don't you write to the NEC and convince them that you know more
about correct/safe wiring procedure than they do and the code should be changed.
Ross
|
291.490 | Let's lighten up | RGB::SEILER | Larry Seiler | Wed Nov 16 1988 21:23 | 24 |
| re .1-: The point here is that, for 110V circuits, the code does **not**
prevent overloads, it just tries to make them unlikely. Lots of people
pop their circuit breakers, so it isn't fair to say that the code prevents
overloads in all "normal" situations.
The rules for 220V circuits are apparently must more restrictive, but even
they do not seem to totally prevent the possibility of an overload.
So I'd say that, while following the code is important, understanding
the reasons behind the code rules is even more important. That's what
this note used to be about. I'd guess that none of us have houses that
are 100% code compliant (I've found really awful examples in my house),
so it is important to understand which things are really bad (eg, I've taped
over my outlet with hot and neutral reversed until I fix it) and which
aren't as serious (eg, .-2 shouldn't have two 220V outlets on one breaker,
but so long as only one is used at a time, it can be fixed later).
Now, back to business. I'd like to know if one should test circuit
breakers. If so, how? Is physically flipping them enough? How can
I be sure that my 15A breaker is really going to trip if I one day
accidentally put 20A through it?
Larry
|
291.491 | I give up! | WILKIE::THOMS | | Wed Nov 16 1988 21:58 | 52 |
| >< Note 2744.24 by RGB::SEILER "Larry Seiler" >
> -< Let's lighten up >->
>
>re .1-: The point here is that, for 110V circuits, the code does **not**
>prevent overloads, it just tries to make them unlikely. Lots of people
>pop their circuit breakers, so it isn't fair to say that the code prevents
>overloads in all "normal" situations.
I agree to the point that it is always possible to overload a circuit. But
if a circuit is wired to code, an overload is "not" a normal occurrence. A
homeowner would have to do something really stupid!
>The rules for 220V circuits are apparently must more restrictive, but even
>they do not seem to totally prevent the possibility of an overload.
>
>So I'd say that, while following the code is important, understanding
>the reasons behind the code rules is even more important. That's what
>this note used to be about. I'd guess that none of us have houses that
>are 100% code compliant (I've found really awful examples in my house),
I wired my Nashua home in 1982. I had three electrical inspections by an
inspector that overruled the code to be more stringent in certain circuits.
My home passed 100%, no calls. Some of the really awful examples you've
found in your house probably came about from some past homeowner doing
his own wiring. I know and have seen/repaired some truly unbelievable
wiring jobs.
>so it is important to understand which things are really bad (eg, I've taped
>over my outlet with hot and neutral reversed until I fix it) and which
>aren't as serious (eg, .-2 shouldn't have two 220V outlets on one breaker,
>but so long as only one is used at a time, it can be fixed later).
That's o.k. if this homeowner wants to run a circuit (in his own house)
in this manner. But don't tell me the code is wrong because (in this case) the
homeoowner is either unable or unwilling to do a proper job.
>Now, back to business. I'd like to know if one should test circuit
>breakers. If so, how? Is physically flipping them enough? How can
>I be sure that my 15A breaker is really going to trip if I one day
>accidentally put 20A through it?
> Larry
No, flipping the breakers will tell liitle about the breaker. Sometimes a
breaker will go bad and not be able to be reset. (Safe failure).
The only way to test your breakers would be to pull them from the circuit
and set up some kind of test load. Not really feasable.
Again, the key to a safe circuit is to set it up so it's not normally
in an overload condition.
Ross
|
291.493 | | MISFIT::DEEP | This NOTE's for you! | Thu Nov 17 1988 12:30 | 47 |
|
Well! Since my intent was to draw a little heat away from the guy everyone
was beating up on for a simple question, I guess I was successful! 8-)
>>(eg, .-2 shouldn't have two 220V outlets on one breaker,
>>but so long as only one is used at a time, it can be fixed later).
>That's o.k. if this homeowner wants to run a circuit (in his own house)
>in this manner. But don't tell me the code is wrong because (in this case) the
>homeoowner is either unable or unwilling to do a proper job.
First of all, lets remember why the code is there in the first place. It's
to establish a safe set of standards for electricians to use to keep them
from getting sued when your house burns down. It's extra protection for
the insurance companies, because if they can prove your house was not wired
to code, they can get out of paying you.
The code is not BIBLE and is not practical for all occurances. In some it is
inadequate (for my peace of mind) and for others, overkill. I have no problem
sleeping at night with a circuit that runs from my panel in the garage to the
workshop in the cellar, with two 220v outlets on it, knowing that only one
can be used at a time. I wouldn't leave it that way for the next guy who might
own two 220v tools. The code says that I am in violation, and I say that the
code was not written to take into account a person who only owns one 220v
device, and wants to use it in two possible places. I am neither unable
nor unwilling to do a proper job... I have! It just isn't according to the
code, which is not designed for this particular occurance. Thats called
making an intellegent decision, and people are still allowed to do that
once in a while, regardless of the insurance companies, and lawyers, and
inspectors, and I resent the implication that I am an accident waiting to
happen, simply because I use some common sense.
Dismantle SOAPBOX (according to code, of course) 8-)
Now then:
>No, flipping the breakers will tell liitle about the breaker. Sometimes a
>breaker will go bad and not be able to be reset. (Safe failure).
Right, but flipping the breaker WILL tell you if its frozen closed... the most
common failure, usually due to corrosion from high humidity or the elements.
The feel of the breaker as it is toggled can also tell you if it may be
gunking up...(that's a technical term!) 8-)
Now then... what does ALL this have to do with rewiring 220v motors? 8^)
Bob
|
291.494 | | MAMIE::THOMS | | Thu Nov 17 1988 13:05 | 73 |
| >< Note 2744.27 by MISFIT::DEEP "This NOTE's for you! " >
>
>
>
>Well! Since my intent was to draw a little heat away from the guy everyone
>was beating up on for a simple question, I guess I was successful! 8-)
No Bob, I don't feel we were beating up on anyone. It was a disagreement and
I certainly hope no feelings were hurt. However, I was asked about a particular
circuit and I gave my thoughts. I'm open to any argument about safe wiring and
don't profess to know all of the answers. I did work as an Apprentice
electrician, took many hours of classroom on wiring and passed the State exam
to become a Journeyman electrician, than later Master electrician. But then
again, I currently don't work electrical problems daily or even weekly.
>First of all, lets remember why the code is there in the first place. It's
>to establish a safe set of standards for electricians to use to keep them
>from getting sued when your house burns down. It's extra protection for
>the insurance companies, because if they can prove your house was not wired
>to code, they can get out of paying you.
>
>The code is not BIBLE and is not practical for all occurances. In some it is
>inadequate (for my peace of mind) and for others, overkill. I have no problem
The NEC is the Bible for safe wiring. If you want to disregard it in your own
wiring, that's your call.
>sleeping at night with a circuit that runs from my panel in the garage to the
>workshop in the cellar, with two 220v outlets on it, knowing that only one
>can be used at a time. I wouldn't leave it that way for the next guy who might
>own two 220v tools. The code says that I am in violation, and I say that the
>code was not written to take into account a person who only owns one 220v
>device, and wants to use it in two possible places. I am neither unable
>nor unwilling to do a proper job... I have! It just isn't according to the
>code, which is not designed for this particular occurance. Thats called
>making an intellegent decision, and people are still allowed to do that
>once in a while, regardless of the insurance companies, and lawyers, and
>inspectors, and I resent the implication that I am an accident waiting to
>happen, simply because I use some common sense.
>
>Dismantle SOAPBOX (according to code, of course) 8-)
Again, If you want to disregard the code, fine. Just make sure you don't tell
the Municipality you live in about it.
>Now then:
>Right, but flipping the breaker WILL tell you if its frozen closed... the most
>common failure, usually due to corrosion from high humidity or the elements.
>The feel of the breaker as it is toggled can also tell you if it may be
>gunking up...(that's a technical term!) 8-)
>
>Now then... what does ALL this have to do with rewiring 220v motors? 8^)
>Bob
Like I said, flipping the breakers will tell you little about their condition.
One of my college professor's once did a lab experiment for our class. He
randomly picked new breakers and tested them at the rated capacity. If I
remember correctly approx. 10% didn't trip anywhere near their ratings.
This professor was an old time electrical engineer that used to design
many electrical components for Westinghouse, very knowlegable in electrical
equipment.
Ross
|
291.495 | Sizing conductors for motors etc. | WOODRO::BERKNER | Tom Berkner 264-7942 MK01 | Fri Nov 18 1988 19:34 | 44 |
| Last night as a way to waste an evening, I looked up the multiple
receptical problem in the NEC 1987 edition.
In article 210-19 it says:
GENERAL. Branch-circuit conductors shall have an ampacity not less
than the maximun load to be served. In addition, conductors of
multioutlet branch circuits supplying receptacles for cord- and
plug-connected portable loads shall have an ampacity of not less
than the rating of the branch circuit. ...
(FPN):See Part B of Article 430 for minimum rating of motor
branch-circuits ....
220-3. Computation of Branch Circuits. ...
(c)Other loads -- all Occupancies.
(2)Outlet for motor load See Sections 430-22,-24 and 440.
(5)*Other outlets 180 volt-amperes per outlet
For receptacle outlets, eachj single or multiple receptacle shall
be considered at not less the 180 volt-amperes.
[Basically this says to figur 180VA (1.5amps) per outlet regardless
of whether it has 1, 2, 4 or more recepticals included + add the
motor loads as determined in article 430. -tom]
Article 430.24 says:
CONCUCTORS SUPPLYING SEVERAL MOTORS. Conductors supplying two or
mote motors shall have an ampacity equal to the sum of the full-load
current rating of all the motors plus 25 percent of the highest
rated motor in the group.
Where one or motors of the group are used on
short-time, intermitent, periodic, or varying duty, the ampacity
of the conductors shall be computed as follows:
(1)Determine th needed amprere rating for each motor used for other
than continuous duty from Table 430-22(a) Exception. [table says
use 90% of nameplate current rating -tom]
(2)[pertains to continuous duty -tom]
(3)Multiply the largest single motor ampere rating determined from
(1) or (2) above by 1.25. Add all other motor ampere ratings from
(1) and (2) above and select the conductor ampacity for this total
ampere rating.
|
291.496 | | MAMIE::THOMS | | Mon Nov 21 1988 11:34 | 83 |
| >< Note 2744.29 by WOODRO::BERKNER "Tom Berkner 264-7942 MK01" >
> -< Sizing conductors for motors etc. >-
>
> Last night as a way to waste an evening, I looked up the multiple
> receptical problem in the NEC 1987 edition.
>
> In article 210-19 it says:
> GENERAL. Branch-circuit conductors shall have an ampacity not less
> than the maximun load to be served. In addition, conductors of
> multioutlet branch circuits supplying receptacles for cord- and
> plug-connected portable loads shall have an ampacity of not less
> than the rating of the branch circuit. ...
> (FPN):See Part B of Article 430 for minimum rating of motor
> branch-circuits ....
> 220-3. Computation of Branch Circuits. ...
> (c)Other loads -- all Occupancies.
> (2)Outlet for motor load See Sections 430-22,-24 and 440.
> (5)*Other outlets 180 volt-amperes per outlet
> For receptacle outlets, eachj single or multiple receptacle shall
> be considered at not less the 180 volt-amperes.
>
> [Basically this says to figur 180VA (1.5amps) per outlet regardless
> of whether it has 1, 2, 4 or more recepticals included + add the
> motor loads as determined in article 430. -tom]
You're correct in this statement for normal household branch circuits, with
the exception you didn't point out: small appliance branch circuits (kitchen).
However, for the shop question 220.3 (c) (1) Outlet for a specific appliance
or other load except for a motor load................. ampere rating of
appliance ot load served.
and.
(2) Outlet for a motor load................ See Sections 430-22 and 430-24 and
Article 440.
These are the pertinent passages. The 180 volt-amp calculation is for
"occupancies" (branch circuits).
> Article 430.24 says:
>
> CONCUCTORS SUPPLYING SEVERAL MOTORS. Conductors supplying two or
> mote motors shall have an ampacity equal to the sum of the full-load
> current rating of all the motors plus 25 percent of the highest
> rated motor in the group.
>
> Where one or motors of the group are used on
> short-time, intermitent, periodic, or varying duty, the ampacity
> of the conductors shall be computed as follows:
>
> (1)Determine th needed amprere rating for each motor used for other
> than continuous duty from Table 430-22(a) Exception. [table says
> use 90% of nameplate current rating -tom]
Say what??? "Any motor applications shall be considered as continuous duty
unless the nature of the apparatus it drives is such that the motor will
not operate continuously with load under any condition of use." (fine print
on the bottom of 430-22(a)).
I say Exception No. 1: Conductors for a motor used for short time, intermittent,
periodic, or varying duty shall have an ampacity not less than the percentage
of the motor nameplate current rating shown in Table 430-22 (a)
Exception unless the authority having jurisdiction grants special permission
for conductors of smaller size.
Try Varing duty, continuous rated motor!
> (2)[pertains to continuous duty -tom]
>
> (3)Multiply the largest single motor ampere rating determined from
> (1) or (2) above by 1.25. Add all other motor ampere ratings from
> (1) and (2) above and select the conductor ampacity for this total
> ampere rating.
Agreed, I stated this before.
Ross
|
291.497 | | MAMIE::THOMS | | Mon Nov 21 1988 12:59 | 20 |
| I just re-read my last reply (hastily written) and I don't think I gave
enough information. What I wanted to say is the 180 volt/amp branch circuit
calculation is for occupancies, such as living rooms, bed rooms, etc.
Shop loads are a different story, see last note for pertinent articles in the
code.
Tom, The chart you were using, 430-22 (a) is an exception chart for motors
that see varying duty such as elevators, welders, conveyors, etc. Depending
on the application, these motors are either lightly used, intermittent, light
loads or "hammered" on or off with a full load. That's why the charts there.
The lightly loaded, lightly used motors would be rated at less than the full
load current and the on/off heavily loaded motors are rated at a high
percentage.
Tom, if you wanted to try and use that particular chart for a shop application
such as a table saw, the Varying Duty, Continuous rated motor would apply. This
is an overkill for a normal shop circuit and a continuous duty motor.
The motors we were discussing are Continuous Duty and should be rated at 125%
full load current. If multiple motors are on the same circuit, the first/largest
motor is rated at 125% and the next at 100%.
Ross
|
291.498 | | POOL::HAMMOND | Charlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684 | Mon Nov 21 1988 19:26 | 27 |
| In reading the last few replies I could conclude that every outlet
in my shop should be on a separate breaker, and that even this
would be illegal since some yo-yo could plug an overload into that
outlet. Of course that's absurd and of course I don't think anyone
intended that message. (But what difference does it make if set
the saw for 120 vs 220 and plug it in????)
Which comes back to the question I tried to ask at least twice
before and which I'll now re-word, perhaps better:
In a home, 120v outlets are rated at 1.5 amps for purposes of
determining the load on a circuit. What load factor applies in
a "shop" for 120v and 220v circuits which are not dedicated to
specific equipment?
The implicit question here is something like "what is the
difference between what I have and just pluging the saw (set
for 120v) into any of the outlets in my home?
If there's an answer to this in previous replies I can't pick it
out.
BTW using 1.5 amps per 120v outlet and 225% of the nameplate
amperage (figuring a possible second device of the same rating)
from my saw my circuit is loaded to ~18-19 amps, which surely
sounds O.K. to me for a 20 amp circuit. (I did this at home a
couple days ago and don't have the actual figures in front of me.)
|
291.499 | Someone else please | WILKIE::THOMS | | Mon Nov 21 1988 21:17 | 45 |
| >< Note 2744.32 by POOL::HAMMOND "Charlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684" >
>
>
> In reading the last few replies I could conclude that every outlet
> in my shop should be on a separate breaker, and that even this
Listen, you've about got it! Basically you should have separate circuits
for your heavier loads. How many diy out there have plugged in a good size
table saw to a regular 15 amp branch circuit and tripped the breaker when
starting the saw or ripping some thick wet wood? I have and I bet many
have done the same. I recommend running separate circuits to your more
or less fixed equipment (table saw, compressor, drill press, mig welder etc.)
I definitely like to have my 240v circuits, separate.
> would be illegal since some yo-yo could plug an overload into that
> outlet. Of course that's absurd and of course I don't think anyone
> intended that message. (But what difference does it make if set
> the saw for 120 vs 220 and plug it in????)
>
> Which comes back to the question I tried to ask at least twice
> before and which I'll now re-word, perhaps better:
>
> In a home, 120v outlets are rated at 1.5 amps for purposes of
> determining the load on a circuit. What load factor applies in
> a "shop" for 120v and 220v circuits which are not dedicated to
> specific equipment?
>
> The implicit question here is something like "what is the
> difference between what I have and just pluging the saw (set
> for 120v) into any of the outlets in my home?
>
> If there's an answer to this in previous replies I can't pick it
> out.
>
> BTW using 1.5 amps per 120v outlet and 225% of the nameplate
> amperage (figuring a possible second device of the same rating)
> from my saw my circuit is loaded to ~18-19 amps, which surely
> sounds O.K. to me for a 20 amp circuit. (I did this at home a
> couple days ago and don't have the actual figures in front of me.)
Geez Charlie, I don't know how else to tell you. I've quoted code, I've come
flat out and told you in the plain English. I give up, anyone else want to try?
Ross
|
291.501 | How can we make this better? | POOL::HAMMOND | Charlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684 | Tue Nov 22 1988 19:13 | 57 |
| > <<< Note 2744.33 by WILKIE::THOMS >>>
>
>I definitely like to have my 240v circuits, separate.
Beleive it or not, this was apparent from your various replies.
O.K. 'nuff o' this. Lets talk for a moment about some possible
ways to make this situation better.
The garrage has a six position breaker box which is fed from a 50
amp breaker in the main breaker box. At present these are used as
follows: Position 1 -- inside lights in the garrage and enclosed
breezway. Position 2 -- outslide lights. Position 3 & 4 -- the now
infamous shop circuit. Position 5 -- garrage door openers (2).
Position 6 -- outlets in the garrage and breezway (excluding the
"shop"). All of these are 20 amp circuits.
Running additional circuits from the main box is not reasonable
because most of the wiring is inside a wall. Installing a larger
breaker box in the garrage is not reasonable for the same reason,
but adding a second box in the garrage may be reasonable. (see D &
E)
Here's some ideas in order of difficulty -- easiest first.
(A) I could easily eliminate one of the two 240v outlets. Any
future 240V tools would have to take turns.
(B) I could move the 4 110v outlets (2 duplex outlets) to the
circuit which is now used only for the garrage door openers (two
garrage doors). I don't like this idea because (1) simultaneous
use of both garrage doors and some tools could possibly overload
the circuit, and (2) I like to be able to turn off the garrage
door openers independently -- like when I have something leaning
on them.
(C) I could run #10 wire and upgrade the entire circuit to 30 amps.
(D) I could run #10 wire to the shop and install a new breaker box
with a 20 amp 240v and 2 15amp 110v circuits. This would mean that
a shop distribution panel would be attached to a 30 amp circuit in
the garage distribution panel which is, in turn, attached to the
main breaker box. Would this be legal? (I'm not certain that I'm
using the terms "distribution panel" and "breaker box" according
to any NEC definition here.)
(E) I could continue the 50 amp feed from the main breaker box on
to a second box in the garrage and use this to feed several
seperate circuits to the shop. There's enough space next to the
current box for another small (4-6 position) box. (This might
actually be easier than (D) because I could probably still use the
existing circuit for the 240V outlet(s).
I'll appreciate any and all comments on these ideas.
...and since I won't see your replies till after Thanksgiving,
have a happy Thansgiving.
|
291.502 | My 2 cents worth | WILKIE::THOMS | | Wed Nov 23 1988 11:33 | 39 |
| >< Note 2744.35 by POOL::HAMMOND "Charlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684" >
> -< How can we make this better? >-
>
>> <<< Note 2744.33 by WILKIE::THOMS >>>
>>
>>I definitely like to have my 240v circuits, separate.
>
> Beleive it or not, this was apparent from your various replies.
>
> O.K. 'nuff o' this. Lets talk for a moment about some possible
> ways to make this situation better.
>
> The garrage has a six position breaker box which is fed from a 50
> amp breaker in the main breaker box. At present these are used as
> follows: Position 1 -- inside lights in the garrage and enclosed
> breezway. Position 2 -- outslide lights. Position 3 & 4 -- the now
> infamous shop circuit. Position 5 -- garrage door openers (2).
> Position 6 -- outlets in the garrage and breezway (excluding the
> "shop"). All of these are 20 amp circuits.
O.k., Here's what I would do: If you're currently only running (1) 240v tool,
wire in (1) appropriate amperage outlet using position 3 & 4. Combine circuits
1 & 2 to one breaker (#1), Run a new 20 amp circuit off of postion #2 with
(2) duplex outlets in convenient locations. If you add another 240v piece of
equipment, calculate the the "new" load on circuit #3 & 4 and if acceptable,
add a second outlet.
This is the easiest and safest way to redistribute the loads as I see it.
However, You might be able to do something with the lighting and breezeway
circuits. I don't know the area size or number of outlets, number of
outside lights, etc.
Another option might be running a new breezeway circuit from the main service
and in doing this, freeing up sub panel space and allowing you to add another
240v circuit in the future.
Ross
|
291.503 | combine and dedicate | MAMIE::BUTTON | feet on ground,head in twilight zone | Mon Nov 28 1988 13:26 | 5 |
| Combining the 120v circuits is the way to go. Getting the right
conbination so that overhead lights stay on if receptacles pop is
the tricky part. Dedicate your high load 240v circuits.
paul b
|
291.504 | | PEEK::HAMMOND | Charlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684 | Wed Nov 30 1988 13:29 | 14 |
| RE: .36 & .37 -- Thanks.
After thinking about this over turkey, etc., I realized that the
"key" is to combine the 2 lighting circuits to free up a position
for a dedicated 120v outlet circuit in the "shop". I'll also
remove one of th 240v outlets.
What is/are your opinion(s) on those breakers which put two
circuits on one position in the box? I was thinking about useing
one of these for the two lighting circuits. I think they only go
to 15 amps max, but thats no problem -- although wired for 20 amps
(as are all circuits in my house) neither of the lighting circuits
would even come close to 15 amps. (i.e they'd easily fit on a
combined 20 amp circuite.)
|
291.505 | Rathole alarm | HANNAH::DCL | David Larrick | Wed Nov 30 1988 14:27 | 10 |
| <<< Note 2744.39 by HANNAH::DCL "David Larrick" >>>
-< Rathole alarm >-
.38 set off my rathole alarm - rather belatedly for this topic! The double
breaker that fits in a single slot is a subject of sufficient general
interest, and sufficiently unrelated to "rewiring motors for 220", that
I've started a new topic in 2846. Please, let's continue this particular
tangent there.
DCL with moderator hat on
|
291.506 | DISABLING ELECTRIC WIRES | WMOIS::C_GIROUARD | | Wed Dec 28 1988 11:42 | 14 |
| I've looked, but have not been able to find anything in the file.
I am in the process of refinishing my foyer. The contractor put
a small (independently controlled) electric baseboard heater there.
I will be doing some wain's coating (sp?) there. Since I have never
used the heater in its trhee year existence I want the thing out!
The question is can I just cap the wires with wire nuts. Does it
get more complicated if the heater is on a circuit with other things
that I can't disable.
Any suggestions on the best course of action. I want to do the easiest
and safest thing!
Chip
|
291.507 | | STROKR::DEHAHN | | Wed Dec 28 1988 12:22 | 23 |
|
Forget about the easiest or safest way, you should do it by the
Code. That way you're covered if there's a fire.
Remove the power to the circuit by the switch or overcurrent device.
Then remove the wires from the heater. Trace the wires back to the
junction box they originated from. Disconnect and remove the wires
from the jbox that go to the heater. Then all you have is a wire
that's disconnected at both ends. If the power for the heater
originates in it's own circuit in the panel, then you have to
disconnect main power, pull the breaker, and replace it with a blank
breaker cover.
If you plan to use the heater, or that circuit, in the future, then
you can remove the wires to the heater, and install a junction box
in the area. Install the wires in the jbox with the proper hardware,
wire nut the ends (a little tape over the nuts won't hurt), and
close up the box with the proper cover.
Both ways are safe and should be legal in your area.
CdH
|
291.508 | ALTERNATIVE | WMOIS::C_GIROUARD | | Wed Dec 28 1988 16:19 | 4 |
| Thanks. Maybe I will put an outlet there as an alternative as there
isn't one now.
Chip
|
291.509 | is it 110 or 220? | NSSG::FEINSMITH | I'm the NRA | Wed Dec 28 1988 16:59 | 5 |
| Just make sure if the feed is 110v or 220v before installing an
outlet (hint-usually a 220 feed uses black and red wires for the
hot).
Eric
|
291.510 | THANKS | WMOIS::C_GIROUARD | | Thu Dec 29 1988 10:00 | 3 |
| Will do and thanks.
Chip
|
291.511 | Three wires for split outlet | POLAR::PENNY | For the Benefit of Mr. Kite | Thu Jan 05 1989 19:21 | 20 |
| I don't know about the States, but here in Canada you can't take
a two wire 220 volt feed and split it into two 110 volt lines *without*
a white neutral(sp?) wire.
Heaters are usually 220 volt, two wire. (Two conductors (red/black)
and a bare ground wire). Otherwise you'd be drawing twice the power
(current) through the line. (Read WIRE HEAT and breaker load -
you can only load your breaker to 80% of its rating. (Canada again)).
You would need a *large* breaker 30 : 40 Amp instead of 15 : 20
Amp. Now, split receptacles are allowed (usually manditory (X3)
for kitchen counter outlets). You need a three wire feed
(black/red/white) with a bare ground. Black and red are HOT lines,
white is neutral. The black and red wires go on the brass colored
terminals of the outlet, (AFTER BREAKING OFF THE TAB THAT CONNECTS
THE BRASS COLORED SCREWS "PLATE" TOGETHER!). You'll see it sort of
between the screws. The white wire is secured to the silver colored
screws, without breaking the tab on that side. Ground (bare) goes
to the green ground screw on the outlet.
IF A SPLIT OUTLET IS NOT INSTALLED THIS WAY, IT IS ILLEGAL.
|
291.512 | | TRITON::CONNELL | Down on Toidy-toid 'n Toid Avenue | Fri Jan 06 1989 11:36 | 11 |
| >< Note 2897.5 by POLAR::PENNY "For the Benefit of Mr. Kite" >
> I don't know about the States, but here in Canada you can't take
> a two wire 220 volt feed and split it into two 110 volt lines *without*
> a white neutral(sp?) wire.
Wouldn't it be easier to just swap the double pole breaker in the box
to a single pole, 20 amp one? (then put a blank cover over the exposed
opening that remains). Assuming that there is no other 220v device on
the circuit, this would allow the use of a standard 110v outlet.
--Mike
|
291.351 | | MYVAX::DIAMOND | No brag, Just fact. | Wed Jan 11 1989 16:43 | 21 |
|
I looked through keywords and did a dir/title and couldn't find
anything that is exactly what I want so instead of starting a new
note, I figured this was as good a place as any.
Does anyone know if I can get or where I can get a double switch,
one of which is a dimmer switch??? Places like Grossmans dosn't carry
anything like it.
-----
| |
| > | <------ Switch (normal)
| |
-----
| |
| > | <------ Switch (dimmer)
| |
-----
Mike
|
291.352 | | VINO::GRANSEWICZ | Which way to Tahiti? | Wed Jan 11 1989 17:21 | 10 |
|
I've never seen such a beast. I've seen the double regular switch
only. I think dimmer switches are usually considerably larger than
a regular switch and it may be physically impossible to have such
an arrangement. If one does exist, it'll probably cost $100 since
its probably a very demand item.
Good luck with the search.
Phil
|
291.353 | Gerry Rig it, so to speak | AKOV13::FULTZ | ED FULTZ | Wed Jan 11 1989 17:25 | 7 |
| Have you thought of putting a regular and a dimmer switch together
yourself? You would need the appropriately sized box and may have
trouble finding a switch cover to fit, but it would probably be
cheaper than trying to find a combination switch.
Ed..
|
291.354 | | VINO::KILGORE | Wild Bill -- DECintact Engineering | Wed Jan 11 1989 18:23 | 7 |
| If you have to fit everything into a single box, I think your out
of luck. Dimmers can dissipate considerable heat (depending on the
load), and I doubt anyone has crammed two of those toasters into
the space of a single box.
If you can use a double box, a normal double switch cover will work
with both rotary and the newer up-n-down dimmers
|
291.355 | put them side by side ??\ | FREDW::MATTHES | half a bubble off plumb | Wed Jan 11 1989 18:24 | 3 |
| Do they have to be one above the other ???
Side by side is a piece of cake.
|
291.356 | tried and could not find it (2 months ago) | CADSE::MCCARTHY | Illegitimi Non Carborundum | Wed Jan 11 1989 20:46 | 8 |
| When I was working on a job in the south shore area the home owner
changed her mind several times on what she wanted to be switched,
dimmed, outlet etc. We ended up trying to find the device in
question and after trying three different elect. supply houses
we gave up. Each one said "the don't make it". We knew it was
a long shot anyway.
bjm
|
291.357 | Oh Well | MYVAX::DIAMOND | No brag, Just fact. | Wed Jan 11 1989 21:27 | 10 |
|
Side by side is what I was trying to stay away from. The switch
is located in the bathroom surrounded by tile. To put another switch
in I'd have to cut the tile, not an easy task and at the some time
make it look nice. I had never heard of that kind of switch either,
but then again, I'm not an EE or electrician. It was a long shot
I have to admit, but it was worth a try. Looks like I'll have to
cut the tile.
Mike
|
291.358 | combination dimmer and regular switch | VIDEO::FINGERHUT | | Wed Jan 11 1989 22:43 | 4 |
| Maybe there's a way you can re-configure a rotary dial dimmer switch
so that turning the dial dims one light, and pushing the rotary
dial turns the second light on or off.
|
291.359 | a device that is close in function | CADSE::MCCARTHY | Illegitimi Non Carborundum | Thu Jan 12 1989 09:08 | 14 |
|
Reply .24 got me thinking of a single gang device that the
Casablanka (sp??) (the Calf. ceiling fan company) make to control
BOTH the fan and the light kit on it. It look very much like a
dimmer but it has two knobs (similar to a car radio). One is a
three position unit for the fan the other is a push-on/off, turn
to dim control for the light kit on the fan. Depending on how
the motor speed control portion handles the voltage it may be
possible to get a three position dimmer and a full range dimmer
into a single gang box.
I don't know if this would work. This device does exist
and is UL listed.
bjm
|
291.360 | | VINO::KILGORE | Wild Bill -- DECintact Engineering | Thu Jan 12 1989 10:39 | 5 |
| re .24:
I'll bet the three-position control is just a rotary switch to turn
on the different windings of a three-speed fan, and would not provide
a dimming effect.
|
291.361 | I've seen those...they should work ok. | MISFIT::DEEP | Bring out yer dead...(clang!) | Thu Jan 12 1989 12:48 | 6 |
|
If re: .25 is correct, than it would probably work for Mike's application.
.23 is a good idea, but of course, it would be against the code. 8^)
Bob
|
291.362 | Don't know what code would say about this one. | LYCEUM::CURTIS | Dick "Aristotle" Curtis | Thu Jan 12 1989 16:40 | 10 |
| .23, .26:
Perhaps what .23 has in mind is something like what you see for car
headlights, or the reverse of a common car radio control: the knob
rotates, and at one stop it also throws a switch, with a second switch
controlled by push/pull on the knob.
No, I haven't seen such a beast. Sorry!
Dick
|
291.363 | double switch w/dimmer | BAGELS::MONDOU | | Thu Jan 12 1989 18:13 | 10 |
| re: 1729.16 , request for a double switch w/dimmer
I replied directly to the author but thought I would also enter
the info here in case anyone else is looking for the same switch.
I have seen a switch of this type in an electrical store in
New Hampshire, near the Pheasant Lane mall. I don't remember
the name of the store or the manufacturer of the switch, but if
anyone is interested, contact me and I'll find out the next time
I am in the area.
|
291.364 | | MYVAX::DIAMOND | No brag, Just fact. | Fri Jan 13 1989 18:56 | 21 |
|
re .28
Well I went to that store at lunch (happened to be in the area)
and they don't have the switch. Maybe they did at one time but not
now.
As for the other switch some of you are talking about, I saw something
like that at Builders Square. One was a three position fan and the
other was a full dimmer for a light. Now my question is will this
work in my situation. What I need the switch for is to hook up a
exhaust fan for my mother's house. She has one switch there right
now that is a dimmer which controls the light. Every exhaust fan
I've looked at says to only hook it up to a timer switch or a standard
on/off switch - nothing about being able to use a variable control
switch. Does anyone know if these fans can be used with a variable
control switch???? When I installed the fan on my woodburning stove
the directions warned me from using it with a variable control switch.
Are these fans built the same way????
Mike
|
291.513 | Wire Color Counts | POLAR::PENNY | For the Benefit of Mr. Kite | Mon Jan 23 1989 20:15 | 6 |
| RE: .6
You would still have the wire coloring to contend with. In Canada,
you may do what you mentioned, IF, you properly color code the wires.
In effect, put white tape over the red wire where it enters the
"outlet" box AND the main panel. dep
|
291.424 | "3-wire" circuit | VINO::GRANSEWICZ | Which way to Tahiti? | Thu Mar 16 1989 19:08 | 16 |
|
I'll ask this here since my house is reasonably old, has several
2 wire circuits and the question isn't worth a brand new note.
I'll be replacing my 7 fuse boxes with a breaker panel soon and
have come across some wiring I'll need help with. I have what I
believe is called a "3-wire" circuit. It's basically a 220 line
but it's not used as 240. It's used as 2 110 circuits.
My questions are:
Is this a common practice today?
What type of breaker should be used for this beast? 2 singles
or 1 double?
|
291.425 | xref | HANNAH::DCL | David Larrick | Thu Mar 16 1989 20:43 | 3 |
| I know there are multiple existing discussions of 3-wire circuits
someplace in this conference, but the only one I could find was in
topic 931, beginning at reply 6.
|
291.426 | 3-wire connection at service panel | VINO::GRANSEWICZ | Which way to Tahiti? | Fri Mar 17 1989 12:30 | 7 |
|
RE: .12
Thanks for pointing to 931 but it doesn't address my main question
which is how is a 3-wire circuit connected in the service panel?
Do I use 2 singles, a double or doesn't it matter?
|
291.427 | | MAMIE::THOMS | Ross - 264-6457 | Fri Mar 17 1989 12:50 | 14 |
| >< Note 2412.11 by VINO::GRANSEWICZ "Which way to Tahiti?" >
-< "3-wire" circuit >-
> have come across some wiring I'll need help with. I have what I
> believe is called a "3-wire" circuit. It's basically a 220 line
> but it's not used as 240. It's used as 2 110 circuits.
In older homes it used to be common practice to snake /3 romex (to the attic)
and use it for two circuits, sharing a common neutral. If this is the case
in your scheme, use two separate breakers.
Ross
|
291.428 | See the Code for 3-wire rules | HANNAH::DCL | David Larrick | Fri Mar 17 1989 13:43 | 19 |
| The Code has some specific provisions regarding 3-wire circuits, and I
would suggest that you read and heed them. Under some circumstances
you do need to use a double breaker (two breakers in a double-size
package, with their handles mechanically connected together so they
turn off together).
I think the rule is something like:
- If the two circuits are both present in any outlet box or switch box,
they must be connected by a double breaker
- If the two circuits split apart in a workbox (and so are never both
present in any outlet box or switch box), they may be connected by
single breakers
The idea is to avoid the situation where someone wants to work on an
outlet, switches off a breaker that appears to turn off that outlet,
and gets shocked anyway by the other circuit in the outlet box.
Presumably people expect this sort of thing in work boxes.
|
291.429 | | NSSG::FEINSMITH | I'm the NRA | Fri Mar 17 1989 13:54 | 26 |
| One thing to remmeber is to have each of the hots attached to a
different leg of the 220 feed into the panel (different bussbar).
The reason for this is that there is only one neutral, and as long
as the two hots are out of phase with each other, the neutral won't
be overloaded. Normally, with full size breakers, the bussbar the
breaker attaches to will alternate on each side top to bottom:
A B
|------- (breaker)
|---- (breaker)
|------- .
|---- .
|------- .
|---- .
However, on panels that support the half size breakers, two adjacent
breakers can be attached to the same bussbar and cause problems.
Eric
|
291.430 | | VINO::GRANSEWICZ | Which way to Tahiti? | Fri Mar 17 1989 18:42 | 14 |
|
Alright! Now we're getting somewhere. As far as I can tell, the
2 circuits are only in the ceiling light where they then split off.
Richter's also got into the whys of putting the different legs of
the circuit on different legs of the bussbar. I don't believe it's
connected that way now though. I got a typical 4 circuit fuse box
with the 2 large pullout cartridges above. If the numbering of
the fuses is 1, 2, 3, 4 then the legs were connected to 3 & 4.
This sounds like it was connected wrong but what are the consequences
of this situation? Everything has been working properly with no
blown fuses.
|
291.431 | Be careful here - some things are not obvious | REGENT::GETTYS | Bob Gettys N1BRM 235-8285 | Fri Mar 17 1989 19:31 | 14 |
291.432 | it's probably wrong. | TFH::DONNELLY | Take my advice- Don't listen to me | Sat Mar 18 1989 01:22 | 27 |
| > Richter's also got into the whys of putting the different legs of
> the circuit on different legs of the bussbar. I don't believe it's
> connected that way now though. I got a typical 4 circuit fuse box
> with the 2 large pullout cartridges above. If the numbering of
> the fuses is 1, 2, 3, 4 then the legs were connected to 3 & 4.
> This sounds like it was connected wrong but what are the consequences
> of this situation? Everything has been working properly with no
> blown fuses.
if I was you i'd double check this out. the consequences are fire. ok, so
it's working so far. with breakers not popping and safety factors you
simply have not loaded things up enough to melt plastic. but basically, if
3 & 4 are on the same leg, you have two separate circuits, both with a
15 (20?) amp fuse, pushing up to 30 (35, 40?) amps back through the same
single nuetral wire. take the cover plate off the box. behind you can
trace the wires from the big cartridge fuses to the plug fuses. if one
cartridge fuse leads to both fuses of your 3-wire circuit, it's wrong.
just switch one of them with one of the circuits coming from 1 or 2. i
suppose it's possible for one cartridge to feed fuses 1 & 3, and the other
2 & 4, so do check.
craig
btw, it's times like this when it's helpful to have found out what runs off
what fuses. then you can understand why the load has been low enough to
not cause problems so far. like the air conditioner was on one circuit and
the furnace was on the other. :^)
|
291.433 | "Outlet" <> outlet | HANNAH::DCL | David Larrick | Sat Mar 18 1989 17:47 | 14 |
| .17> Alright! Now we're getting somewhere. As far as I can tell, the
.17> 2 circuits are only in the ceiling light where they then split off.
A nit, but perhaps an important one: the term "outlet", as used in the
Code (and in .15) includes lighting fixtures as well as receptacles for
plugs. So if the circuits split in a box that also has a ceiling light
attached to it, that box is technically an outlet box. To conform to Code,
the two circuits must be on the same double breaker.
I don't know whether the equivalent of a double breaker exists in fuse
technology.
But if the two hot wires are indeed on the same leg, you've got bigger
problems than technical Code violations. Please check this out right away.
|
291.434 | | VINO::GRANSEWICZ | Which way to Tahiti? | Mon Mar 20 1989 13:39 | 17 |
|
Thanks for all the help and info.
Well, the 7 old fuse boxes are history and I now have a 100 amp
breaker panel for my main service panel!
I currently have the 3-wire circuit on 2, single pole 15 amp breakers
and they are on seperate legs. Do 15 amp double poe breakers exist?
I don't recall seeing them on the list at Spag's so maybe they are
not a common item.
Another question:
I replaced the BX wire to the furnace with Romex. Hell, it was
a short run and while I was having sooo much fun ripping out wires
;-) I figured I do it. Does the wiring to the furnace have to be
in conduit? If it does, then how much it (same area protected by
firecode sheetrock?)?
|
291.435 | Furnace wiring | VINO::GRANSEWICZ | Which way to Tahiti? | Wed Mar 22 1989 14:52 | 13 |
|
Let me explain the situation in more detail:
The old power source to the furnace was BX cable which went in above
the firecode sheetrock to the thermal switch right above the furnace.
However, the cable exited the sheetrock through a 1" square hole.
To me, the fire protection offered by the sheetrock appears to be
compromised. Should I instead run the power feed through EMT conduit
to the thermal switch and seal up the 1" hole? The wire to the
shutoff upstairs is also just stapled to the firecode sheetrock.
I would think that that wire should also be in conduit. Or am I
going overboard here?
|
291.292 | what about extending 2 wire on non-outlet circuits | REGENT::POWERS | | Tue Apr 18 1989 17:22 | 20 |
| I have an extend-the-2-wire grounding question that is skirted over
here and in 1980.* and 1992.*.
My brother has a 50/60-ish year old house, two wire circuits, some knob
and tube, some BX (also one legged, that is, 110 only).
I've been helping him out by adding outside lighting fixtures for him.
One was a motion detecting yard light, the other a new porch light.
The Question: What should one do with the grounding wire in the new boxes
and fixtures? I had been clamping them together and to the boxes, hoping
for local integrity. Of course, there is no safety ground for this
local circuit to connect to, so am I compounding the problem by connecting
boxes together? Some boxes are, of course, switches (with metal boxes
and covers) so safety is a consideration. Should I actively AVOID wiring
the bare wire to the fixtures so shorts at the fixture will NOT propagate
to other areas of the circuit? Of course, I know better than to connect
ground and neutral. (That's the one message conference members here continue
to beat into one another's heads! Rightfully so, since it's so hard
to justify it on simple first principles.)
- tom powers]
|
291.293 | | WILKIE::THOMS | Ross - 264-6457 | Tue Apr 18 1989 18:30 | 25 |
| RE:-1 The code says: 250-50 (exception) For replacement of nongrounding-type
receptacles with grounding-type receptacles and for branch-circuit extentions
^^^^^^^^^^^^^^^^^^^^^^^^^
only in existing installations that do not have an equipment grounding conductor
in the branch circuit, the grounding conductor of a grounding-type receptacle
outlet shall be permitted to be grounded to a water pipe which is bonded in
accordance with Section 250-80(a).
Also take a look at Article 210-7, (c) and (d).
210-7 (d) (exception): Where a grounding means does not exist in the receptacle
enclosure either a nongrounding or a ground-fault circuit-interrupter type
of receptacle shall be used. A grounding conductor shall not be connected from
the ground-fault circuit-interrupter receptacle to any outlet supplied from
the ground-fault circuit-interrupter-type receptacle.
"Don't wire in a grounding type device on a ungrounded system!" It's o.k.
to use a non-grounding device or add a ground. But don't provide false security
of an apparent grounding-type device.
Ross
|
291.294 | | WOODRO::THOMS | Ross - 264-6457 | Tue Apr 18 1989 19:35 | 11 |
| RE:27 I re-read your note and assume you're not connecting any
receptacles to your extension. However the rule still applies, keep
the circuit two wire or upgrade to a true 3 wire with a grounding conductor.
If you connect your extension like a 3 wire, what would keep some future
unsuspecting homeowner from adding a grounding type receptacle on that
particular branch? Also by staying 2 wire, (assuming the upgrade to three wire
isn't practical), if you should have a short to metal,
at least the short would be isolated from the rest of the circuit.
Ross
|
291.295 | | WOODRO::THOMS | Ross - 264-6457 | Tue Apr 18 1989 20:04 | 8 |
| Also... read article 250-33. Other Conductor Enclosures. Exeception No. 1:
Metal enclosures for conductors added to existing installations of open wire,
knob-and-tube wiring, and nonmetallic-sheathed cable, which do not provide an
equipment ground, if in runs of ***less than 25 ft*** (7.62 m), if free from
^^^^^^^^^^^^^^^^^^^^^
probable contact with ground, grounded metal, metal lath, or other conductive
material, and if guarded against contact by persons shall not be required to
be grounded.
|
291.514 | Need a "Banana" (inductive amplifier) | MISFIT::DEEP | Set hidden by moderator | Mon Jun 12 1989 13:35 | 19 |
|
Back in the dark ages of Data Communication, before the world got smart
and started using Ethernet, we used to use a device for tracing particular
cables out of a bundle.
I think it was some for of inductive amplifier. You would connect a tone
generator (supplied as part of the set) on the ends of the wire, and then
trace along walls, cable troughs, etc., listening for the tone with the
receiver end (jokingly called the "banana" because of its yellow color and
shape). You could detect the tone without touching the cable...as much
as 1/2 foot away.
WARNING! USE ONLY ON UNLOADED (READ DISCONNECTED FROM BREAKER PANEL)
WIRES!
Your local telecomm people will probably have one... maybe you could borrow
it. They still live in the dark ages! 8^)
Bob
|
291.515 | | OASS::B_RAMSEY | Beautiful Plumage the Norweigen Blue | Mon Jun 12 1989 17:30 | 6 |
| If you have access to the attic or cellar above and below the wall,
look for wires coming and going. You can often get a feel for the
location of wires by where they enter/exit the wall and by looking
at what electrical services are provided on the wall(lights, swithes,
outlets, etc.)
|
291.516 | | BEING::MCCULLEY | RSX Pro | Mon Jun 12 1989 17:52 | 12 |
| re .3 - I have access to either attic or cellar, but not both, since
the situations are on the first and second floors of my two-story
home. In fact the particular cases that most concern me both concern
what my educated guess thinks/hopes might be horizontal runs involving
outlets, switches and lights in a fairly small area of the room(s).
The item described in .1 sounds like it's close to what I want,
it's probably the same principal as .2 except using the 60-Hz field
instead of coupling an induced tone into the cable. Anybody able
to give me a lead on the sort of gizmo described in .1?
Thanks!
|
291.517 | Ask a good metal-detector hobbyist! | POLAR::MACDONALD | | Mon Jun 12 1989 20:12 | 9 |
| Find someone who has a metal detector for locating coins and metal
underground and ask them to find a buried wire for you. Nothing
pleases these hobbyists more than a challenge like this; a good
operator will be able to do the job within minutes, distinguishing
between wires, nails, and outlet boxes.
Every respectable neighbourhood has at least one.
Bernie
|
291.518 | | NEXUS::GORTMAKER | Whatsa Gort? | Tue Jun 13 1989 08:41 | 6 |
| Carol cable used to market a device used for locating wireing hidden
in walls. It worked very much like a stud sensor except it picked
up the 60hz and used it to create a signal(audible). Sorry I forget
the name.
-j
|
291.519 | Tracing is not that hard | KACIE::POWELL | Reed Powell HPS Marketing | Tue Jun 13 1989 13:29 | 11 |
| You will probaby have more luck tracing the wiring from the attic than
you think - when houses are wired, horizontal runs are usually rare -
vertical runs are a lot easier and faster, so that is what they do in
most cases. Orienting yourself is the hardest part (ie, sitting in
the attic saying "what the &*@ am I above?), but all that really takes
is having someone on the floor below tapping on the ceiling, or
listening to your tapping.
I was doing exactly waht you are, and this worked out fine in my case.
|
291.520 | Wire tracing methods | RGB::SEILER | Larry Seiler | Tue Jun 13 1989 14:05 | 34 |
| If you have access to both the attic and the cellar, it should be
possible to figure out a lot of it even without metal detectors.
Here's a couple rules that I discovered in the two houses in which
I have traced wires -- I appreciate knowing if they are more general.
1) First step, of course, is to find out which outlets are on which
breakers. Then apply the following steps to each breaker individually.
2) Look for outlets (on the same breaker) in similar positions on
different floors. It's a good bet that the wire runs vertically.
3) Look for outlets (on the same breaker) around the walls in the
same room, or on opposite sides of the same wall. If you can't
find the wire running between them in the basement or attic, it
probably runs inside the wall, at the level of the outlets.
4) Outlets added after initial construction will be wired more
obscurely, but they're easier to find, since they almost certainly
go directly up into the attic (from the second floor) or directly
down into the basement (from the ground floor). You may have to
dig in the insulation to find them all.
5) Another simple trick is to take the covers off the outlets to
see whether the outlet is at the end of a run, or whether there
are wires both in and out -- or maybe 3 or more wires. Note that
a wire out of a box could go to a light, instead of to another outlet.
6) If you find a junction box (or outlet with multiple wires)
and you can't figure out which branch heads for the breaker box,
disconnect it and see which wires/outlets you've just disabled.
And be careful of those bare wires when you turn the breaker back on.
Enjoy,
Larry
|
291.521 | induction pick-up | SICVAX::SCHEIBEL | U can Teach A new dog UL TRIX | Tue Jun 13 1989 18:14 | 10 |
| Besides the methods in .8 something I have had moderate succes with is
using an amplifier and a telephone pickup coil. (available at rat-snack
for about 15 bucks) plug a load into the outlet like a light bulb hold
the coil to the wall and listen in the amplifier's speaker for the 60
cycle hum. This works sometimes it has a lot to do with the composition
of the wall and how close the wire runs to the surface.
Good luck,
Bill
|
291.522 | Modern vs. historical wiring techniques | HANNAH::DCL | David Larrick | Wed Jun 14 1989 15:40 | 22 |
| .7> when houses are wired, horizontal runs are usually rare -
.7> vertical runs are a lot easier and faster, so that is what they do in
.7> most cases.
Depends on the age of the house. Modern wiring is done .7's way. Back
when labor (even skilled labor) was cheap and wire was expensive, it was
more common to go to the trouble of drilling through lots of framing
members to save a few feet of wire. So the older the house, the more
likely you are to find runs through walls, diagonal runs through
joists, etc.
To the excellent list in .8, I would add: consider the framing
complexity of windows, doors, bays, stairwells, etc. Such things
require substantial pieces of lumber (headers, sills, cripples, etc.),
which limit the possible routes that wiring can take to get from one
place to another. It also helps to know the history of any additions
and/or electrical upgrades to the house.
This won't help you much now, but: whenever you open up a wall, take
photographs of its innards before you close it up again - and leave the
photos behind when you sell the house. They're invaluable for answering
questions about framing, plumbing, wiring, insulation...
|
291.523 | Draper make one | IOSG::CARLIN | Dick Carlin IOSG | Fri Jun 16 1989 09:03 | 14 |
| Sorry about the late reply but there is indeed such a gadget. I have
just bought one for $15 made by Draper (do they distribute in the US?).
It detects wires, pipes etc. I wanted to locate the wires for a servant
bell system. These (the wires, not the servants) are buried in the
walls, running through lead conduits.
It also detects ac power, flowing or not.
I'm very impressed with it, hope you can find one over there.
Cheers
Dick
|
291.524 | impressed, you say? | TLE::THORSTENSEN | | Thu Jun 22 1989 16:21 | 4 |
| Is it just a metal detector? Will it also work as a stud finder?
The stud finder I have is useless... maybe the Draper product would
solve multiple 'finding' pproblems.
|
291.525 | Very impressed | IOSG::CARLIN | Dick Carlin IOSG | Fri Jun 23 1989 16:45 | 11 |
| Sorry, it's pretty versatile but locating studs is something it won't
do. It's a metal/field detector.
Right next to it in the shop was a stud detector made by Black and
Decker. Is that the one you've got? - in which case I'll bear your
negative recommendation in mind. I was tempted to buy it to avoid
having to poke piano wire through the walls to locate studs.
Dick
|
291.526 | Yes, Metal detectors will work | FRIEZE::MEANEY | JIM | Mon Jun 26 1989 19:05 | 19 |
291.527 | May help.... | VICKI::DODIER | | Tue Jun 27 1989 17:12 | 14 |
| You should be able to get a good idea of where a run is by looking
at where the wire enters the room from the cellar/attic AND turning
off breakers and seeing what outlets/lights went off. This will
also tell you how much is on the line already so you can decide
if you want to use it or not.
Secondly, you should be able to remove the cover and the
switch/outlet (and if your real lucky the box itself), which will give
you an idea of where the wire is coming from/going to.
Ray
BTW - If your adding/changing wiring in a bathroom keep in mind that you
need a ground fault breaker or outlet.
|
291.528 | Cheap Radio | CURIE::BBARRY | | Tue Aug 01 1989 19:26 | 20 |
| You can buy electric wire finders. They essentially amount to SCR
circuit to generate pulses and a amplitute modulator hooked upto a
speaker to detect the pulses. You can easily do the samething with
a lightbulb, dimmer switch and cheap transistor radio. Plug the
light in through the dimmer and pass the transistor radio in the
general vacinity of the wire. As you get closer to the wire the
clicking becomes louder.
The transistor radio picks up the magnetic field created by the
change in current in the wire. The magnetic field is proportional to
the change in current, so the SCR is used to quickly pull the
current to zero. Sometimes just the normal 60Hz AC is adequate to
generate a detectable pulse.
I have some Radio Shack books at home that show how to build everything
that is needed. I'll draw the circuit in here when I get a chance.
It probably is nothing more then aa triac and a few pots to adjust
sensitivity.
Brian
|
291.529 | Frozen screws in Electrical box | POWDAH::PEREZ | | Thu Aug 10 1989 18:19 | 11 |
| Does anybody out there know how I can loosen the screws that
hold the white/ground wires to the busbar in a circuit breaker
box. They all seem to be frozen in place.
What I am trying to do is add another circuit in my house,
(remodeling the ole kitchen) and most of the existing screws
are stuck. Also it seems like a good time to remove the old
circuits from the panel.
adTHANKSvance
Dick -
|
291.530 | | CLOSUS::HOE | Sammy sit! Dad needs a breath! | Fri Aug 11 1989 15:49 | 8 |
| Dick,
After turning off the main braker, try squirting some penetrating
oil into the screws. Most of the time, the screws are gulled in
position. Sometimes, an over zealous electrician may have
stripped or cross threaded the screws.
Cal
|
291.531 | | VLNVAX::HEDERSTEDT | T.B.S. | Fri Aug 11 1989 16:00 | 6 |
|
Try a hand impact tool with the CORRECT size screwdriver blade. This
has always worked for me. Sometimes a little heat applied will help
to break the bond between the screw and the bonding bar.
Wayne
|
291.532 | More queries! | POWDAH::PEREZ | | Mon Aug 14 1989 13:12 | 16 |
| re: .1
Thanks Cal.
I'll try the oil. (Probably in combination with Wayne's reply.)
re: .2
Thanks Wayne.
Will a small "tap" on the end of a screwdriver suffice in the absence
of a hand impact tool?
How does one apply heat to a particular screw safely?
Question:
What is the white stuff around the bar? My suspicions are similar to
the white stuff around my car battery. Is this safe? At least as the
house is concern?
Dick - :-)
|
291.533 | An answer, and another question | TOKLAS::FELDMAN | Week 5: insulation and inspection | Mon Aug 14 1989 17:11 | 26 |
| re: .3
While a small tap on a screwdriver may help, and probably won't hurt,
it's not the same as a hand impact tool. A hand impact tool is design
to convert the linear energy of the hammer blow into rotational energy.
You hold the tool tightly in the direction you want the screw to turn,
and hit it with a hammer. An internal wedge transmits the force of the
blow into turning force on the tool's bit. It sounds like a reasonable
idea in this case, so long as you don't get carried away. Remember,
only some of the force is converted to rotational; the rest is the same
as a solid hammer blow against the screw.
Along the same lines:
Is there an easy way to remove a plastic clamp from the service box? I
want to remove the cables that were left from our electric heaters when
we converted to oil. The wedge holding the cable in the clamp is
positioned facing a neighboring clamp, so there's no room to simply
pull out the wedge, and I'm not sure I could get it out, anyway. The
clamp is in the back row, making it difficult to get in there with
pliers, to hold down the latches and pull the clamp out. I'm perfectly
willing to destroy the clamp and replace it with a metal one, but I'm
not sure if there's an easy way to do that without electrocuting
myself.
Gary
|
291.534 | DeOx | DYO780::SCHAFER | Brad - back in Ohio. | Mon Aug 14 1989 18:49 | 22 |
| RE: .3 (oxidization)
Probably not a problem (read: dangerous) ... but to avoid that in the
future, use some DeOx (elec conn lubricant) - the stuff is designed
primarily for split-bolt wire unions, but works well on breakers
and panel screws.
RE: .4 (to destroy or not to destroy)
What kind of clamp, and what size wire? Clip mounting or threaded with
a nut? If the former, I'd destroy it. If the latter, the nut should
be 'toothed' - you can use a screwdriver/hammer to get the thing to
come out. Either way, a good pair of diagonals can be used to cut the
screws that secure the wire pinch - UNLESS the screws are on the inside
of the box. In that case, shoot the electrician. 8-)
An aside - given the nature of the oil market (and assuming that the
wire is in decent shape), you might be better off putting the loose end
of the old wire in a box and cap it off. You might want to use it
again.
-b
|
291.535 | | TOKLAS::FELDMAN | Week 5: insulation and inspection | Mon Aug 14 1989 19:09 | 15 |
| re: .5
It's a plastic clamp that's clip mounted. It looks as though you push
it in from the outside, and it locks in place. Similarly, once the
cables are inside the clamp, it looks like you push a plastic wedge in
from the side to hold the cable, and the wedge locks in place. In
other words, the whole thing seems to be designed to be
permanent/non-reusable.
I will dead-end the old heater wires in a separate box, just for
posterity. I just want to get the wires out of the service box, to
make things neater for when we finish wiring the addition, and to avoid
having to punch another knockout.
Gary
|
291.536 | WD-40 might be safer than oil? | VMSDEV::HAMMOND | Charlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684 | Thu Aug 17 1989 19:28 | 7 |
| I'm not sure I like the idea of spreading oil around inside a
cirucit breaker box. I suspect it could have a detrimental effect
if it got on/in the breakers themselves. I'd use WD-40 instead.
Its safe for use on electical stuff.
If you DO use oil, keep it to a minimum only where neded. (i.e. on
the neutral or ground bus.) Wipe it off when done.
|
291.537 | | VLNVAX::HEDERSTEDT | T.B.S. | Fri Aug 18 1989 16:10 | 8 |
| I use a BIG soldering iron to get the heat on the bar. Works for me!
I am not big on the idea of oil in a breaker box. WD-40 or a electrial
contact cleaner are better ideas! If possible,highly recommened!,kill
the juice to the panel before you start to work on the bus bar.
Wayne
|
291.538 | Part of a circuit showing only 80V | CECV03::SADLER | Ask a glass of water! | Mon Oct 09 1989 14:29 | 38 |
|
A neighbour of mine called last night with a problem which he thought
I'd be able to help with, but it beats me... can someone help?
He's installing a bathroom fan, and has tapped into a cable in the
roof, and connected the fan across it as shown in the diagram below.
The fan doesn't run and putting a meter across the terminals at
the fan shows 80 volts. What's wrong?
-------o-------- black
|
|
-------(-----o-- white
| |
| |
| |
------ -------
| |
| |
| | --
switch fan 80 v across here
| | --
| |
| |
------------------
All suggestions gratefully received, I'm a recent 'import' from
the UK and I don't understand this 120v system very well.
Thanks,
Andy
|
291.539 | Bad connection is my guess | MOOV00::S_JOHNSON | Park Ave in Beautiful Worcester | Mon Oct 09 1989 14:50 | 31 |
|
-------o-------- black --
| Whats voltage here??
| --
-------(-----o-- white
| |
| |
| |
------ -------
| |
| |
| | --
switch fan 80 v across here
| | --
| |
| |
------------------
See if you have 120 at the source; if so, then either the wiring is bad,
(maybe a bad connection) or the switch or fan is bad. Try removing them
from the circuit one at at time (bypass them with a jumper) to see if
the 120 comes back.
My guess is a bad connection or bad switch; the fan itself wouldn't cause
a voltage drop like that, the fuse would blow due to overcurrent. Double
check all conections. You're using wirenuts for connections, aren't you?
Steve
|
291.540 | Tapped the wrong cable | WJO::MARCHETTI | Mama said there'd be days like this. | Mon Oct 09 1989 14:53 | 33 |
|
The other 40v is across some other load.
It appears that your neighbor tapped into a switch cable. I've added
to your drawing to illustrate what is going on. As long as the switch
is open, the fan will be in series with whatever load the switch is
meant to control (probably a light fixture). If you close that switch,
the fan won't work at all, and there will be 0 volts across it.
I suspect that this wouldn't work in the UK either. 8^)
Bob
P.S. Does your neighbor do his own plumbing too?
black
----------o-------- black---------- load ------
| |
swtch | source
| | white
---------(-----o-- white ---------------------
| |
| |
| |
------ -------
| |
| |
| | --
switch fan 80 v across here
| | --
| |
| |
------------------
|
291.541 | 2 volts for you, 1 for me, ... | ASD::DIGRAZIA | | Tue Oct 10 1989 19:47 | 33 |
|
I agree with .2, though load is probably "downstream" of
"swtch", and downstream of the white tap:
----------o-------- black----------------------
| |
swtch | source
| |
---------(-----o-- white ---------load--------
| |
| |
| |
------ -------
| |
| |
| | --
switch fan 80 v across here
| | --
| |
| |
------------------
Let's see, 40V is 1/2 of 80V, so the load is about 1/2 the
resistance of the fan. Very crudely, it's about double the
fan's wattage (or is it 4 times the fan's wattage? Hmmm...).
So some device with twice (or four times) the fan's wattage is
under suspicion. (If the fan isn't turning at 80V, does it make
sense to estimate resistance/impedance for a stopped motor, versus
some unknown load?)
Regards, Robert.
|
291.542 | Don't get zapped!!! | OPUS::CLEMENCE | | Tue Oct 17 1989 02:59 | 35 |
|
WARNING
You are assuming that the white lead is netural or unswitched.
Take the enhancment to the drawing below. This would be to code for mass.
----------o-------- black-----------+ +--white---
| | +--load--+
swtch | source
| |
---------(-----o-- white --------------o-------black---
| | ^
| | wirenut
| |
------ -------
| |
| |
| | --
switch fan 80 v across here
| | --
| |
| |
------------------
Your assumption of the load value is twice the wattage. To
find the switch that it is connected into..... you should place the meter
across the fan and turn on the fan switch. You should then try switching other
switches in the house and observe for voltage changes.
Be carefull that you don't get zapped....
Bill
|
291.192 | Resistance of wire? | ULTRA::WITTENBERG | Secure Systems for Insecure People | Tue Nov 07 1989 15:11 | 7 |
| Does anyone have a table showing resitance of wire (ohms/ft) for
various gauges? Since some of what I'm doing is low voltage and
low current, I'd appreciate numbers for wire from 10 to 20 gauge.
At this point even a few values would help. Please state whether
the resistance is for one or both legs of the circuit. Thanks.
--David
|
291.193 | Here are a few | VINO::DZIEDZIC | | Tue Nov 07 1989 17:19 | 8 |
| Assuming copper (!) wire, this is the resistance in Ohms per
1000 feet. If you have two legs then sum them (i.e., a 20
foot run of 2-wire cable is 40 feet as far as voltage drop
is concerned).
#10: 0.9989 #12: 1.588 #14: 2.525
#16: 4.016 #18: 6.385 #20: 10.15
|
291.194 | | ULTRA::WITTENBERG | Secure Systems for Insecure People | Wed Nov 08 1989 21:36 | 6 |
| Thanks for the information. The bicycle light system I just bought
uses 22ga. copper for a 5 ft. run carrying 1 amp. (at 6 volts). So
about 2% of the power goes into the wires. I'm going to upgrade it
probably to 16 ga.
--David
|
291.195 | not saying you shouln't make the change, though. | NOVA::FISHER | Pat Pending | Thu Nov 09 1989 07:40 | 7 |
| re:.14: Your bike lighting system uses 22 ga strand wire doesn't it?
The numbers in .13 are for solid. I think someone told me a long time
ago that strand wire has the same resistance as the next higher guage
of solid wire so the 22 ga strand is about the same as 20 ga solid.
-- Until you get a bunch of strands broken :-).
ed
|
291.196 | | ULTRA::WITTENBERG | Secure Systems for Insecure People | Thu Nov 09 1989 13:20 | 5 |
| Yup, they use speaker wire. It's stranded wire. Even if I use the
resistance for 20 ga., I'm still loosing over 1%, and batteries
are a lot heavier than the wiring, so it's worth conserving power.
--David
|
291.197 | divergence from "home owner topic" | NOVA::FISHER | Pat Pending | Thu Nov 09 1989 17:19 | 4 |
| I reduce the voltage drop by shortening the distance from the battery
to the light. 1 ft is good but it means putting a cage up front.
ed
|
291.737 | Sizing wirenuts | REGENT::MOZER | H.C.C. ;-) | Thu Nov 30 1989 11:51 | 17 |
|
I did a DIR/TITLE="wirenut" and didn't find anything, therefore
this new NOTE. If there is something somewhere else, please
point me to it and/or move this note there. Thanks!
I have a question regarding wirenut sizes/capabilities.
I need to be able to connect 2 #10 and 2 #14 solid copper conductors
together inside a junction box. All I have seen (and currently
have a box of) are red "large" wirenuts. The box says they are
capable of 2 #10 and 1 #16 or #18 and 2 #10's alone are tough to
"wrap"..
Does anyone know if a larger one is made and, if so, where in the
Central MA area I can get some (preferably 6 or so)?
Joe
|
291.738 | | WILKIE::THOMS | Ross @285-3151 | Thu Nov 30 1989 13:27 | 6 |
| >< Note 3617.0 by REGENT::MOZER "H.C.C. ;-)" >
> -< Sizing wirenuts >-
Go to an electrical supply outlet that carries "Ideal" wirenuts and
buy the grey colored.
Ross
|
291.739 | | CIMNET::LUNGER | Dave Lunger, 291-7797, MET-1/K2 | Thu Nov 30 1989 13:57 | 8 |
| another possibility since you already have reds; and greys are a car-ride
away....
use 2 wire nuts to connect them, putting 2 #10's on one, and 2 #14's on
the other, and connect them with another length of #14, leaving you with
2 #10's and 1 #14 on one, and 3 #14's on the other. The latter may be
a yellow connector (check box; i'm not sure). You could also use a #12
as the short length between the wirenuts.
|
291.740 | Great info, thanks!! | REGENT::MOZER | H.C.C. ;-) | Thu Nov 30 1989 16:14 | 6 |
|
Thanks for the responses!! Definitely gives me way(s) to do it!
I will let you know which way I do it and how it works out!
Joe
|
291.741 | How big is the box? | TALLIS::KOCH | Kevin Koch LTN1-2/H09 DTN226-6274 | Fri Dec 01 1989 12:15 | 6 |
| >use 2 wire nuts to connect them, putting 2 #10's on one, and 2 #14's on
>the other, and connect them with another length of #14, leaving you with
>2 #10's and 1 #14 on one, and 3 #14's on the other.
This will work but will have a drastic effect on the number of 'wires'
in the box. You've added two more wire nuts and an extra piece of wire.
|
291.742 | It's a 4" incher | REGENT::MOZER | H.C.C. ;-) | Fri Dec 01 1989 14:52 | 7 |
|
Right now it's a 4" square box, but I've already decided that I
NEED to get a 4" one with front and back open to double the depth
of the box based on a single 4" square one got filled last night
with 4 "red" wirenuts joining 2 pcs. of #10/3 with ground.
Joe
|
291.743 | Two-Piece wire nuts. | POLAR::MACDONALD | | Mon Dec 04 1989 15:59 | 16 |
| There are wire nuts available which can easily handle several larger
wires, and the space they occupy is about 1/2 bigger than the
larger standard wire nuts you are probably using.
These larger ones come in two pieces, an inside brass hollow cylinder
(sleeve-like) which can have an opening of about 1/4 inch into which
you slip the wires to be joined (no twisting); they are held inside
this cylinder by a large flat set-screw in the side wall. The
set-screw is tightened and clamps the wires.
This brass cylinder, with the wires clamped inside, has one end
threaded over which you screw the plastic insulator completing the
junction. It really does not look different than the standard twist-
the-wire-and-screw-on-the-nut type. Any good electrical supplier should
have them, but you probably won't find them at the local hardware.
|
291.744 | Sounds a bit shaky to me, unless its ground. | JAZZ::WHITE | Randy White, Doncha love old homes... | Thu Dec 07 1989 15:55 | 14 |
| RE:< Note 3617.2 by CIMNET::LUNGER "Dave Lunger, 291-7797, MET-1/K2" >
>use 2 wire nuts to connect them, putting 2 #10's on one, and 2 #14's on
>the other, and connect them with another length of #14, leaving you with
>2 #10's and 1 #14 on one, and 3 #14's on the other. The latter may be
>a yellow connector (check box; i'm not sure). You could also use a #12
>as the short length between the wirenuts.
Huh, depends on what your doing, but I'm not sure this is code.
I'd go with the larger wire nuts or insulated splices. But if you
do use this method be sure that you keep the 10's together in one
wire nut because of ampacity.
- Randy
|
291.924 | Surge/Spike Protection | SOLAR1::FERREIRA | | Thu Jan 11 1990 10:58 | 18 |
| Mr. Moderator, I have looked thru the other notes listed under 1111.34/.35.36
and didn't find anything for surge/spike protection. If I've overlooked a
better place for this note please feel free to redirect.
I have a new home therefore new electrical system. When I arrived home
yesterday I found that we had experienced a 2 hr. power failure sometime
during the day. The resulting damage consisted of tripping (2) GFI panel
circuits, a remote control ceiling fan, an electric garage door opener and
one of the PC boards in our new TV. I will be calling Mass Electric to voice
my concerns and losses. What I would like to do is protect my home from a
reoccurance of same. I do not have any lightning protection nor surge/spike
protection in the house, I didn't think either would be necessary. I know
hind-sight is 20-20 :-)..... Anyway, does anyone know what, where how I can
protect my; house from this sort of loss/disruption in the future..
We are located in Westford Ma with power supplied by Mass Electric. 200A
service and it's all circuit breakers.
Thanks in advance Frank
|
291.925 | Not your average power outage!! | POLAR::MACDONALD | | Thu Jan 11 1990 11:29 | 20 |
| Sounds like you had more than a simple power outage, the results you
describe are serious - I had the same symptoms when I had lightning
hit my underground telephone cable.
I would lodge a serious complaint with the local Power Co. that you
experienced a major surge or transient which caused the described
damage, and first ask them to identify what happened (something of
this magnitude should have been known). Since you are in a new house
assume it may happen again, you may be on a power network with major
industrial loading - which can cause this type of disruption; I could
be wrong but it is worth asking about.
With regard to some form of protection, the standard hardware variety
"surge eliminator" or "noise reducer" probably would not do the job;
these are designed for reducing noise and such from appliances that
otherwise would interfere with you TV. To do the job properly, your
incoming power line should be monitored for disruptions and then the
protective device sized accordingly. A good Power Co. could provide
some assistance/guidance regarding this.
|
291.926 | | QUARK::LIONEL | Free advice is worth every cent | Thu Jan 11 1990 14:23 | 7 |
| You can buy a voltage surge protector from DEC through the Employee Purchase
Plan - I think it works out to under $100. This is wired into your breaker
box and protects the whole house. I know several people who have done this,
and the DEC unit provides a lot more protection than the individual outlet
types.
Steve
|
291.927 | Thanks and Specific questions | SOLAR1::FERREIRA | | Thu Jan 11 1990 14:40 | 6 |
| Thanks Steve,
Do you happen to know how I can contact one of them and ask some
installation specifics?
Frank
|
291.928 | | QUARK::LIONEL | Free advice is worth every cent | Thu Jan 11 1990 19:21 | 7 |
| Re: .3
You won't get any installation help from DEC! I suggest asking in
ELECTRO_HOBBY. Or send mail to Vernon Miller (OPAMP::VMILLER) - I
know he's done this.
Steve
|
291.929 | plus 2 months to get fixed | DEMING::TADRY | | Fri Jan 12 1990 16:55 | 17 |
| The same thing happen to me in Sterling, Home of Sterling Flicker and
Flash, a tree limb fell on one of the main feeder lines during a
snow storm. Why was the limb that close to a feeder.... Anyway, 2
T.V. sets, Stanley Garage door opener (The Sears was fine) VCR
and 1 GFI bit the dust. Metropolitan covered the claim, I had to
pay the deductable. They only pay to a certain point then they
have to review it, I think it was $700.00 worth of repair and I
came close. Check with your insurance co. I found out they would
have paid to have the garage door opener and my large tv removed for
the repair, no big deal. I didn't know my GFI was bad until it started
tripping once a day then more frequently. If you suspect their bad,
have them replaced. I wasn't the only one who had damage and we got
no satisfaction from the power company. I put surge protectors on
all the outlets that had equipment that was damage due to the surge.
Good Luck,
Ray
|
291.745 | Light Dimmer Switch & Ground Connections | CSC32::S_JOHNSON | Lifetime Member of Aye Phelta Thi | Mon Jan 29 1990 13:08 | 12 |
| This might have been mentioned elsewhere, but I could not find it anywhere.
I replaced a dimmer switch on our house. When I took the old one off, I
noticed there were three wires coming out of the switch. The new one did not
have the three wires so I just hooked up the black and white wires to the ones
coming out of the box. I don't remember doing anything to the bare ground
wire. Should I have? The box is plastic and the house is fairly new (8 yrs
old).
Thanks for any and all replies.
scott
|
291.746 | 3-way/2-way selection? | REGENT::POWERS | | Tue Jan 30 1990 12:00 | 4 |
| I'd guess that you had a three-way dimmer in the box and you replaced it with
a two way. It sounds like your installation is a single switch installation,
so the third wire on the old dimmer can float, as long as it it taped so
it won't short to something.
|
291.747 | One more time for me | CSC32::S_JOHNSON | Lifetime Member of Aye Phelta Thi | Wed Jan 31 1990 16:11 | 10 |
| Does that mean, it is ok to leave the bare ground wire not attached to
anything? The bare ground wire I'm referring to is coming out of the
box. The old switch had metal plate on it that dimmed the lights if
you kept your finger on it after awhile. The new switch has a dial on
it that you turn to dim the lights.
Should I tape the bare ground wire coming out of the box or just leave
it hanging?
scott
|
291.748 | grounded frame | NYEM1::MILBERG | Barry Milberg | Thu Feb 01 1990 01:58 | 7 |
| The last dimmer I bought (a GE) mentioned in the instructions that if
the old switch was grounded (with a bare wire to the green screw) that
you should ground the frame of the dimmer by attaching the bare wire to
the front (metal) frame.
-Barry-
|
291.749 | Intended for nonmetallic boxes | SHRFAC::BOUDREAU | | Thu Feb 08 1990 05:18 | 10 |
| The reason that there is a ground wire coming out of the dimmer
is if it is installed in a nonmetallic box, all exposed metal parts
of the dimmer must be grounded. To do this you should tie it to
the branch circuit ground in the box. If you have a metal box and
the dimmer is mounted on a metal plate, (most are) and the metal
plate will be mounted to the box the disregard the ground wire coming
out of the dimmer.
CB
|
291.750 | Ground connections | CSCMA::LEMIEUX | | Thu Feb 08 1990 13:07 | 17 |
|
Always connect the ground wire coming from the dimmer to, 1)
the ground wire run with the other circuit conducters, 2) if the
box is a metal box connect the groung wire to a ground screw that
is then screwed into the metal box. As long as the metal box is
properly grounded.
If you don't do the above you are depending on the mounting
screws for the ground connection, which is not allowed by NEC, also
if you were to remove the switch from the box with the power on for
trouble-shooting purposes, the switch would no longer be grounded
which would allow the metal parts of the switch to possibly become live....
I think you can see what the results would be....
|
291.751 | DEFINE QUALIFIED_PERSON NOT::EVERYONE | SHRFAC::BOUDREAU | | Fri Feb 09 1990 04:19 | 38 |
| RE-1
There may be some confusion on this topic. Are we talking about
Grounding type receptacles, or general purpose snap switches
(dimmers)??
First of all the NEC requires that metal enclosures for switches to be
grounded. (380-12) However it does NOT require the YOKE (strap) of the
switch to be bonded other than the mechanical connection to the
grounded box (yes the mounting screws are an approved method, in fact
you can use the mounting screws to ground a receptacle when there is
direct metal contact to the yoke of the receptacle). Now remember, the
ground of the receptacle is going to serve some type of portable or
cord connected equipment, and therefore should have excellent
integrity. However, the yoke of a switch is *really* only grounding the
strap and at worst the metal face plate. Remember that the face plate
is only held on by the 6-32 screws and you are depending on them to
provide an adequate ground. The only way that the yoke of the switch
could become energize is 1) faulty wiring, 2) a wire coming off of the
device (see #1), or as you had stated 3) a QUALIFIED person working on
it. Now if this *qualified* person should work on this device while
energized, he/she is aware of the hazards involved (art #100), and if
they are uncomfortable with this situation they should shut that
circuit down.
The intention of the green wire coming out of the dimmer, was to ground
the yoke (strap) of the switch when mounted in a nonmetallic box. The
same goes for the green screw on some snap switches. They are only
required when the switch enclosure is not grounded (nonmetallic).
If you are not satisfied with this information I ask you to print
the article #'s that support your theory. Remember an inspector
cannot reject your work unless he/she can point out the *violation*
in the code.
CB
|
291.752 | Clarification of .5 | CSCMA::LEMIEUX | | Tue Feb 13 1990 13:14 | 11 |
| Hi,
RE.6
After a quick review of what I wrote in .5 I agree
with what you have pointed out in .6. I was thinking non-metallic
boxes but not writing what I was thinking. :')
Sorry for any confusion caused by my reply.
Paul L.
|
291.753 | leave this space blank | SHRFAC::BOUDREAU | | Wed Feb 14 1990 02:55 | 5 |
| No problem.
That's why we all use NOTES, for discussion.
CB
|
291.52 | Knob/Tube to Romex Connection? | MFGMEM::S_JOHNSON | Say it, don't spray it! | Thu Feb 15 1990 15:10 | 23 |
|
I need to connect some new romex wiring to an existing 2 wire (knob and tube)
circuit. The romex, will be 14-2 with ground. If the old wiring was easily
accessible, I'd rip it all out and replace it. But it goes between the
1st and 2nd floors, and I don't want to rip the floor up to replace the wiring,
which does not necessarily need replacing.
I must connect these two types of wire in a junction box, of course.
The question is: What tyoe of junction box must be used? The two wire system
wires are enclosed in a (somewhat) flexible tube, presumably to protect against
mechanical damage. This needs to enter the junction box and meet code, and
be connected to the romex.
Is there special junction box for this application?
Then what do I do with the ground wire on the romex? Just ground the box?
Thanks
Steve
|
291.754 | Log Home Wiring | DNEAST::DEE_ERIC | | Tue Feb 20 1990 11:13 | 18 |
|
If you have ever wired a log home, perhaps you can advise me.....
How do you wire the outside walls of a log home?
Do you do the same pre-planning that a post and beam requires, and
avoid outside wall wiring where ever possible?
Do you wire the outside walls by installing the boxes in the logs, and
lead the wires between the logs. Do you route out the logs and provide
a path for the wires?
If so, is there a danger of pinching a wire or driving a spike through
the wires?
Any information you can share or lead me to will be appreciated.
Eric
|
291.755 | I did it | TOOK::SWIST | Jim Swist LKG2-2/T2 DTN 226-7102 | Tue Feb 20 1990 15:05 | 26 |
| I wired a log home from top to bottom.
1) First of all you AVOID wiring in the outside walls where possible.
You may have to get an electrical inspector to agree, for example, that
an outlet on an interior wall 6" from an exterior wall is just as good
as an outlet on an exterior wall 6" from the same interior wall.
2) Yes, you have to preplan outside wall wiring and drill each course
of logs as the walls go up. A (serious) router with a (serious) bit is
needed to make box openings unless you have years to do it with a
drill/chisel or other such means.
3) Outlets near the floor are relatively tolerable to deal with. Ones
higher up like light switches or kitchen counter outlets are the pits.
The wire has to pass through many courses of logs and it always seems
to catch on something no matter how well the access hole is lined up
and cleaned out.
4) For places where appearance is not a consideration, think about
using wiremold or some on-wall wiring system (if you think wiremold
is attractive, think about using it on ALL outside walls :-). I
did this where the through-log wiring would have been ridiculous. It's
also the ONLY alternative for after-the-fact wiring on outside walls.
I love my log home and most of building it was great fun; however, I
would have to say that wiring the outside walls was NOT fun.
|
291.756 | Some suggestions | VMSDEV::HAMMOND | Charlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684 | Tue Feb 20 1990 19:34 | 30 |
| For outlets around the exterior perimeter I offer two suggestions:
1) Put the outlets in the floor -- run the wires between the floor
and the ceiling of the floor below.
2) Use an extra large/thick "baseboard" to create a wiring raceway
around the perimeter.
For switches and lamps mounted in/on the perimeter wall you can
often build a vertical wiring raceway that ends up looking much
like a post. Alternately, put the lamps and switches in/on
interior partition walls near where they intersect the perimeter
walls.
*THE* key to wiring in a log home or a post and beam home is
advance planning. In a conventionally framed home (i.e. "2-by"
construction) you don't need to think about wiring until the
house is fully framed. Wire can be run through the wall cavities
before installing insulation and sheetrock. But in a log home or a
post and beam home the wiring has to be planned in advance so that
wire can be run during construction.
If you're not doing the work yourself -- maybe even if you are --
you might want to look at different electricians till you find one
who has wired this type of building. Better to profit from his
experience that to pay for the learning experience of someone who
has never done this type of job.
Also -- Is it a "kit home"? If so the kit supplier probably has
information including mistakes to watch out for.
|
291.757 | SUSHI::LOG_HOMES | OASS::RAMSEY_B | Put the wet stuff on the red stuff | Tue Feb 20 1990 20:23 | 4 |
| You might also want to post this in SUSHI::LOG_HOMES. That conference
caters to all aspects of Log Home building and maintenance.
Hit keypad 7 to add SUSHI::LOG_HOMES to your notebook.
|
291.758 | Planning is EVERYTHING | SHRFAC::BOUDREAU | | Thu Feb 22 1990 02:58 | 12 |
| I have wired a log home before. If you have proper planning,
it really isn't all that bad. Make sure that you bore your holes
using an auger bit (the home I was involved with the homeowner used
a flat bit and the chips fell into the next lower course). Also
clean your holes after *every* drilling. With proper planning you
can place your receptacles and switches where you want them. I feel
that in the long run you will appreciate the added convenience of
having your receptacles and switches where they *should* be and not
where they were easy to install.
Cary
|
291.759 | Planning sounds like the answer | DNEAST::DEE_ERIC | | Thu Feb 22 1990 12:06 | 20 |
|
Re: all
Thanks for the good replies - I'm in the planning stage right now, and
will do my own construction when I've finally decided upon what I want.
I have plans for a house that I like, but haven't decided on stick, log,
or post & beam, so I'm weighing all the alternatives. I'm leaning to log
or post & beam.
Pre-planning sounds like a must - so I'll give that part more
consideration. I like the idea of wide baseboards, wiring in floors
or upright support logs(posts). The prospect of boring long holes to
get fixtures/outlets where I want them seems like a reasonable place
to put some extra energy.
I'll search the LOG HOME conference too, and cross post the request if
the subject has not been covered yet.
I appreciate all the ideas,
Eric
|
291.760 | | DICKNS::WELLCOME | Steve Wellcome (Maynard) | Fri Mar 02 1990 14:07 | 3 |
| Comment: aren't in-the-floor outlets against code now? Even if
they aren't, I'd avoid them. They fill up with crud, and there's
no way to get it out if a vacuum cleaner doesn't work.
|
291.863 | Looking for hi-tech switches | NITMOI::PESENTI | Only messages can be dragged | Mon Mar 05 1990 23:01 | 14 |
| Does anyone know of any "hi-tech" switch/dimmer suppliers. I've seen
the Stanley remote control set ups, but I'm looking for something that
is more flexible than that.
I would like to have multi point dimmer control (>2 points) for some
lighting. Also, it would be nice to have a lot of switches at a given
point without them taking up too much room.
I've checked a couple of lighting stores, and they seem to go for
lo-tech traditional switches. Should I be investigating electrical
supply stores? Or U Do It Electronics? Or what?
-JP
|
291.864 | | QUARK::LIONEL | Free advice is worth every cent | Tue Mar 06 1990 14:05 | 8 |
| Try the ATSE::X-10 conference for info on the BSR X-10 system. The Stanley
Lightmaker system is just a tiny subset of X-10 (but isn't compatible with
other X-10 devices). There's a lot more out there.
If you have a recent DAK catalog, look at the descriptions of the X-10
devices there.
Steve
|
291.865 | Low voltage switching? | EUCLID::PAULHUS | Chris @ MLO6B-2/T13 dtn 223-6871 | Wed Mar 07 1990 18:05 | 20 |
| An in-between (between traditional switches and the X-10 systems)
is low-voltage (24V) switching of relays. I just ordered half a grand's
worth yesterday. You come off your panel right into a relay cabinet.
Each relay can be connected to any number of switches. Relays are
available with pilot light contacts for remote switches with pilot
lights. Two switches can be put into a standard outlet box (that would
normally hold one switch, or a duplex outlet). There are high narrow
switch plates that hold up to three switches and you can put 3 or 4
switches in a double-width box.
some rough prices: relays $20 to $28 each
switches 5 to 10 each
cabinet with transformer, rectifier, relay mounts
about $150
These are available from GE. Source in E. Mass is G.E. Supply in
Woburn.
Obviously, you don't want to use these when you don't need multiple
switches separated by long distances (3-way stuff works fine, thank
you). But, if you have some situations with 3 or more switching
locations, some over 100' from the device, I think this is the way to
go. - Chris
|
291.866 | Radio Shack | VMSDEV::HAMMOND | Charlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684 | Wed Mar 07 1990 19:20 | 1 |
| RADIO SHACK sells X-10 type controls. They frequently have sales.
|
291.53 | Knob&tube to Romex, or Romex to knob&tube? | HANNAH::DCL | David Larrick | Wed Mar 07 1990 20:48 | 22 |
| I've used regular boxes for this application. The "somewhat flexible" sleeve
fits nicely in both types of Romex clamps (integral and external).
Re ground: if you're replacing knob and tube starting from the service panel,
and re-attaching an old knob and tube run to the new run of Romex, then you're
fine just to ground the junction box - the knob and tube won't be grounded, but
it's no worse off than it was before.
But if you're tapping a new Romex run off of an existing knob and tube run,
then your new Romex run won't have a ground. Your options in this case, it
seems to me, are:
1. Use ungrounded Romex, ungrounded outlets, etc. The Code makes an exception
to its usual grounding requirements in cases like this, but the materials may
be hard to come by.
2. String a ground wire from your service panel to your junction box.
Logically, you're converting the knob and tube run into a grounded circuit.
3. String a ground wire from a conveniently-located grounded circuit. Not as
good as the other options because of potential ground loops and crosstalk,
but better than nothing. (Electrical junkies please confirm this opinion!)
|
291.54 | | VMSDEV::HAMMOND | Charlie Hammond -- ZKO3-02/Y05 -- dtn 381-2684 | Thu Mar 08 1990 19:16 | 22 |
| >2. String a ground wire from your service panel to your junction box.
> Logically, you're converting the knob and tube run into a grounded circuit.
>
>3. String a ground wire from a conveniently-located grounded circuit. Not as
> good as the other options because of potential ground loops and crosstalk,
> but better than nothing. (Electrical junkies please confirm this opinion!)
My reading leads me to believe that there are problems with
running a seperate ground wire. I have been told that a seperate
ground wire will NOT be accepted in new work; it must be part of
the cable the contains the neutral and hot wires. I think that the
problem is that there is no other way to be sure -- well,
reasonably sure -- that you will have a good ground and that it
will stay good. Of course, a grounded type outlet iln which the
ground prong is NOT properly grounded is a disaster waiting to
happen.
My advice? Run an entierly new, properly grounded circuit. don't
attempt to add a ground to an existing circuit.
Another good piece of advice is to check with a licensed
electrician or with a building inspector.
|
291.55 | One is needed, more are ACCEPTABLE | GENRAL::HUNTER | from SUNNY Colorado, Wayne | Tue Mar 13 1990 18:01 | 19 |
| Take this as COLORADO code and might be different back your way:
A separate ground wire MAY be run to EACH circuit IF it returns to
the grounding stud in the breaker panel. This separate ground must run
NEAR TO or with the existing wire for safety purposes. If the wire is
inside a conduit, a separate ground wire MUST also be enclosed WITHIN
the conduit. The conduit itself is NOT adequate for grounding
purposes.
As a sidelight to the above statement of facts, you MAY run as many
ground leads as you wish as long as you have ONE continuous grounding
wire attaching to the ground lug of the breaker panel. For VERY HIGH
FREQUENCY equipment, it is ADVANTAGEOUS to run a GROUNDED GRID for the
equipment and keep the ground impedance LOW. So, in this type of stated
case, you will have one ground wire (LONG) inside the conduit or in the
vicinity of the original wire in ADDITION to an entire grid of wide,
flat, LARGE bars or etc. to drain the high frequency signals. The
single wire meets the code of providing a grounding path for safety, and
the grid grounds the radio frequency.
|
291.56 | question on dryer plug style | DRIVE::HANAM | Hike with a Husky | Tue Apr 17 1990 21:12 | 25 |
| A basic question -
I have an electric clothes dryer that is marked 3 wire, 120/240 60
cycle.
And an outlet that is marked 125/250.
Are these compatible? The dryer plug is slightly different than the
outlet; like this -
outlet dryer
\ / \ /
| |
-+ (like a backwards L)
I'm hoping that a new cord on the dryer will save me a call to an
electrician, but don't want to change anything that would be
dangerous.
Thanks for your advice and experience.
Mike
|
291.57 | 220, 221 whatever it takes | OASS::RAMSEY_B | Put the wet stuff on the red stuff | Tue Apr 17 1990 21:35 | 11 |
| One configuration is for a Dryer and the other is for an electric
range/stove. You can change the pigtail (the cord on the appl.) or you
can change the outlet. Check the rating of the fuse before using the
applicance on that outlet. You probably only need a 30 amp fuse for a
dryer and a 50 amp for a range. Check the documentation with your
dryer. Don't change the fuse from 30 to 50 unless the wire is rated
for that load. It is ok to go from 50 to 30.
Either someone switched the pigtail on your appl. or the outlet was
used for a different appl.
|
291.58 | DRYER OUTLET INFO | CSCMA::LEMIEUX | | Tue Apr 17 1990 22:04 | 40 |
|
Amperage rating is the key to your question.
All appliances have an amperage rating and need to be fed by
a circuit that is suitable for that appliance. You need to determine
what the amperage draw for you dryer is an then determine which
receptacle applies in your situation. That information can be found
on the nameplate attached to the appliance where you found the voltage
rating.
The appliance cord with the backwards L at the bottom may be
the correct configuration for the dryer, if it was designed to be run
on a 30 amp 120/240 circuit. The receptacle with this configuration is
known as a NEMA 10-30R and is rated at 30 amps at 120/240 volts.
The other receptacle you have drawn is known as a NEMA 10-20R
or a NEMA 10-50R depending which side the larger blade socket is
located on. They are rated at 20 amps and 50 amps in that order.
at 120/250 volts.
In either case, the receptacle that is currently installed is
probably not the correct one for the purpose. I would consider
having someone look at it if you are not comfortable with trying to
determine if the wire size is adequate, and if it is fused correctly
for the wire and dryer ampacities.
None of the above would be correct if this dryer outlet were
being fed from a sub-panel in either a multitenant building or
a mobile home. These types of installations would require a 4 wire
receptacle that has a seperate ground wire and associated blade
socket. You would then have to have a 4 wire appliance cord to match
this. The type of receptacle that would satisfy this requirement
would be a NEMA 14-30R.
I hope this helps you out,
PL
|
291.59 | | DRIVE::HANAM | Hike with a Husky | Wed Apr 18 1990 15:50 | 5 |
|
thanks to both of you for your detailed replies. I've called an
electrician friend and he'll be coming over to look at things.
thanks, and i'm happy i didn't just swap cords.
|
291.761 | | FSTTOO::BEAN | Attila the Hun was a LIBERAL! | Thu Apr 19 1990 17:08 | 16 |
| My wife and I will start building our NorthEastern Log Homes kit later
this summer. Wiring is a big concern I have. The NELH homes I have
seen use door jams for channels for some of the light switch and
exterior wiring.
I though of "in-floor" outlets, too. Commonly used in computer rooms,
etc. I don't think there are restrictions against them. Cleaning can
be a problem if they are in a traffic area...but, removal and
maintenance is easy. Problelm with them is carpeting. They are a pain
in the A#* if you have to put carpet around them.
Our kit dealer suggested cutting the box hole into the second tier of
logs (that'd put the bottom of the outlet about 12 inches above floor).
That way you only drill two logs for each outlet.
tony
|
291.762 | | NITMOI::PESENTI | Only messages can be dragged | Fri Apr 20 1990 11:53 | 8 |
| My old roomie did a lot of research before buying her log home. The one she
bought uses a wood stove for heat, with an electric backup. All of her outlets
are built into the electric baseboards. If you are not going to have electric
heat, you could set up some wooden baseboard enclosures, and run all your wiring
thru them. For wall wiring, it depends a lot on the finish for your walls.
Rounded, chinked logs would be difficult. However, her home uses a lot of
surface type wiring, except instead of metal channels, they are wooden, to match
the walls and ceilings. Looks nice, and is barely noticeable.
|
291.763 | Timber-frame/stress skin wiring & plumbing | SEESAW::PILANT | L. Mark Pilant, VMS Security | Fri Apr 20 1990 17:06 | 12 |
| You might also want to check out Tedd Benson's book "The Timber-Frame
Home" and the June/July 1988 (number 47) issue of Fine homebuilding.
These two primarily deal with wiring and plumbing in timber-frame homes
and stress skin panels, but there are probably some ideas you could
use.
Another thought would be to check with Jim Swist (a fellow HOME_WORK
noter). He fairly recently finished a log home he was building. He
could probably give you some good hints and gotchas.
- Mark
|
291.60 | Outlet near chimney? | SALEM::PAGLIARULO_G | | Mon May 07 1990 11:27 | 12 |
| I need to move an outlet. The most convenient place to move
it to (for use - not wiring) is in the wall that contains the chimney.
the chimney is only used for the gas water heater and furnace and
I'm talking about an outlet on the second floor. Now, intuition
tells me that there's no way that this is allowed in "THE CODE"
but I figured I'd ask.
Can I do it?
Thanks,
George
|
291.465 | | QUARK::LIONEL | Free advice is worth every cent | Tue May 22 1990 15:30 | 14 |
| I am having the same problem. My house is 24 years old and most of the
wiring has some sort of fabric outer insulation. I haven't yet looked to
see if it has a temperature rating printed on it.
I called an electrical distributor and asked about a sort of heat shield as
was described in .5. I was told that these did not exist in the US, and that
my only choice was to rewire the box with newer wire. Sigh. I can't find
anything in the NEC either that would allow a heat shield.
Actually, there was one alternative - use lower wattage bulbs. The fixtures
I have use two 40W bulbs. In some cases, two 25s would be ok, but elsewhere
no. Augh....
Steve
|
291.61 | what made this outlet short? | LEZAH::QUIRIY | Christine | Mon Jun 25 1990 18:17 | 27 |
|
Here's my story: I just moved into an apartment. I made the mistake
of looking behind/under the stove, saw how filthy the floor was and
decided to wash it.
The outlet for the stove is mounted on the floor along the wall.
Instead of using the mop for this area, I got down on my hands and
knees and used a sponge and was very careful not to slosh water at
the outlet. However, the tile that the outlet "sits" on was loose
-- or it loosened when the water hit it/seeped under. After the
floor was dry, I plugged in the stove. After a little while (a
minute? a half minute?) I heard zzzzt! After a lot of unproductive
running around, I unplugged the plug and when I did that, there was
more zzzzzt-ing and a small whisp of smoke. (I was sure the house
was going to go...)
This happened Friday and the stove's still unplugged, though I did
turn the main breaker back on (couldn't find a separate breaker for
the stove). Is it OK to plug the stove back in, or could there be
a problem here? I can't say for certain that NO water got into the
prong-slots, but I doubt it. This house is OLD, it's had 4 owners
in the last 9 years, and I've not yet been impressed that the
current owner is the conscientous sort.
Thanks,
Christine
|
291.62 | What I'd do | RGB::SEILER | Larry Seiler | Mon Jun 25 1990 21:05 | 16 |
| If it were me, I'd unscrew the outlet cover (with the power to it turned
off, of course) and look inside. If I saw any blackened insulation, I
would close the cover again and call the owner to let him know (as nicely
but firmly as possible) that he's got to get an electrician out on an
emergency basis because the stove isn't safe to operate. If he gives
trouble about that, I would *immediately* call the town hall and ask who
I could talk to about a landlord who doesn't provide an operable stove
or safe wiring.
After what you described, If I opened the box and didn't see any blackened
insulation, I'd be very surprized! I'm also surprized that it took that
long for the arcing to start. Could the cord to the stove, or something
inside the stove, possibly have been wet?
Luck,
Larry
|
291.63 | Old aluminum wiring? | SSDEVO::JACKSON | James P. Jackson | Mon Jun 25 1990 21:17 | 23 |
291.64 | Get owner involved now | DDIF::MCCARTHY | Coming to you from Pink Flamingo Land | Tue Jun 26 1990 10:42 | 6 |
| An apartment? I would suggest leaving it alone, call the landlord and
tell him/her to come down right away. Most likey they do not want the
place to burn down. Even if they are the "slum loards" type, all you
have to do is threaten him with the health department or city housing
authority (if such exists). If in MA, I don't think you can rent an
apartment without a working stove.
|
291.764 | Orange outlets and Hospital wiring? | MEIS::FONSECA | I heard it through the Grapevine... | Tue Jun 26 1990 19:58 | 19 |
| I was in the General Doroit Auditorium in the mill yesterday,
and noticed the the outlets installed at desk level in the arena
for members of the audience were colored orange. Each outlet also had
a small inverted green triangle symbol.
What did this indicate? GFCI or spike protection?
A related question:
How are hospitals wired? I was on a hospital tour recently, and noticed that
many of the outlets were colored or had tiny symbols attatched.
I suspect that for certain applications in a hospital, it doesn't
matter if a circuit is starting to overload, you want that lif-support
system to keep running. How do they deal with this?
Thanks,
-Dave
(Want to make sure that intensive care addition to my house is wired correctly
:-)
|
291.765 | | NOTIME::SACKS | Gerald Sacks ZKO2-3/N30 DTN:381-2085 | Tue Jun 26 1990 20:58 | 3 |
| I would guess that in a hospital, only certain outlets are hooked up to
emergency power. When the generator kicks in, you don't really need the
TVs to work.
|
291.766 | | QUARK::LIONEL | Free advice is worth every cent | Tue Jun 26 1990 21:02 | 4 |
| The green dot or triangle indicates a special grounding requirement. I'd
have to look at the NEC to see what it is. You should too.
Steve
|
291.767 | | VLNVAX::HEDERSTEDT | T.B.S. | Wed Jun 27 1990 00:16 | 10 |
| The green sticker means the outlet has a "safty" ground. The normal
ground in your house socket attaches to the ground prong of the outlet
and the metal box (if you have a metal box) the outlet resides in.The
Hospital has two seperate ground wires.One for the ground prong of the
outlet and the other attaches to the metal box and frame of the outlet
It is a added safty feature. Hospital's have their own special spec on
wiring and its own grade of electrical parts.
Wayne
|
291.65 | | LEZAH::QUIRIY | Christine | Wed Jun 27 1990 02:13 | 9 |
|
re: .39-.41
Thanks for all the replies! I haven't lived in an (old) apartment for
10 years and am relearning how to react in this sort of "emergency".
The outlet (and wiring to it) will be replaced tomorrow.
CQ
|
291.768 | Isolated ground for computers | CSCMA::LEMIEUX | | Wed Jun 27 1990 12:45 | 17 |
|
Hi,
What you have seen there is an "ISOLATED GROUND"
receptacle. Designated by the green triangle on the face of the
device. It is used to supply an isolated ground to a computer load
to minimize the possibility of the introduction of noise etc into
the computer.
The Hospital grade wiring devices will have a green circle on
the face and serve a completely different purpose than the "IG"
types for computer loads.
Did this help any?
PL
|
291.769 | more information | RAMBLR::MORONEY | How do you get this car out of second gear? | Wed Jun 27 1990 16:13 | 10 |
| The new computer wiring of the Mill is "clean" power. The computer recepticles
are fed off a separate breaker panel that has a separate feed from the other
loads. Lights and normal outlets have their own breaker panel separate from
the computer loads.
I don't know if the "isolated ground" is simply from being separate feeds back
to the feed that supplies the breaker panels (and maybe further, I don't know)
or if they're grounded in some special way.
-Mike
|
291.770 | The code... | HDLITE::FLEURY | | Wed Jun 27 1990 16:33 | 60 |
| RE: a few
The following is from the 1987 NEC book.
Article 517 covers health care facilities which includes in-home care.
517-11. Grounding of Recepticles and Fixed Electrical Equipment.
In areas used for patient care, the grounding terminals of all
recepticles and all noncurrent-carrying conductive surfaces of fixed
electrical equipment likely to become energized that are subject to
personal contact, operating at over 100 volts, shall be grounded by an
insulated copper conductor. The grounding conductor shall be sized
according to Table 250-95 and installed in metal reaceways with the
branch-circuit conductors supplying these recepticles or fixed
equipment.
Exception No. 1: Metal recaeways are not required where Type MC
cable, Type MI cable, or Type AC cable with an insulated grounding
conductor is used.
Exception No. 2: Metal faceplates shall be permitted to be
grounded by means of a metal mounting screw(s) securing the faceplate
to a grounded outlet box or grounded wiring device.
Exception No. 3: An equipment grounding conductor enclosed in the
sheath of a nonmetallic-sheathed cable assembly installed in accordance
with the limitations of Sections 336-2, 336-3, and 336-4 sdhall be
permitted to be used in accordance with Parts C and D of this article.
517-13. Recepticles with Insulated Grounding Terminals.
Recepticles with insulated grounding terminals as permitted in
Section 250-74, Exception No. 4, shall be identified; such
identification shall be visible after installation.
(FPN): Care is important in specifying such a system with
recepticle insulated grounds since the grounding impedance is
controlled only be the grounding wires and does not benefit
functionally from any parallel grounding paths.
================================================
250-74. Connecting Recepticle Grounding Terminal to Box.
An equipment bonding jumper shall be used to connect the grounding
terminal of a grounding-type recepticle to a grounded box.
Exception No. 4: Where required for the reduction of electrical
noise (electromagnetic interference) on the grounding circuit, a
receptical in which the grounding terminal is purposely insulated from
the recepticle mounting means shall be permitted. The recepticle
grounding terminal shall be grounded by an insulated equipment
grounding conductor run with the circuit conductors. This grounding
conductor shall be permitted to pass through one or more panelboards
without connection to the panelboard grounding terminal as permitted in
Section 384-27, Exception No. 1, so as to terminate directly at an
equipment grounding conductor terminal of the applicable derived system
or service.
(FPN): Use of an isolated equipment grounding conductor does not
relieve the requirement for grounding the raceway system and outlet
box.
|
291.450 | How much more for all coper everywhere? | SNDPIT::SMITH | Smoking -> global warming! :+) | Wed Aug 08 1990 02:10 | 7 |
| If you are building a new home, is it worth starting out with copper
wire everywhere (including the feed from the road)? I know aluminum is
cheaper for the main feed and any runs to subpanels (and I'm
considering several subpanels), but how much more can copper cost when
you are starting from scratch?
Willie
|
291.451 | | CSC32::GORTMAKER | whatsa Gort? | Wed Aug 08 1990 03:26 | 7 |
| By the time you spend the extra time and money buying recipticles and switches
rated for Cu/Al the copper would be cheaper. Al is best used for the service
drop and copper for the rest. I worked in a electrical supply warehouse before
joining DEC and the smallest aluminum wire we carried was 2/0 a tad overrated
for a 20A outlet.
-j
|
291.452 | Go with Copper, AL is just not worth it | HNDYMN::MCCARTHY | What will I do when the day is 1.5 hr longer? | Wed Aug 08 1990 10:29 | 9 |
| I don't think you can use AL for anything under 30A runs (dryer). Back
in the late 60's/ early 70's (I think that was the time frame) there
was AL Romex available in 12/14 guage. I never installed it but had to
play with it in a few junction boxes. You had to be very careful not
to nick the wire because a few twists after the nick and it would break
off. Never mind the fact that it could not handle the load, it was
just a bitch to work with.
bjm
|
291.453 | What about the drop from the street? | SNDPIT::SMITH | Smoking -> global warming! :+) | Wed Aug 08 1990 12:09 | 7 |
| OK, is it worth paying extra for copper from the street as well, or can
you 'assume' (and we know what happens when you assume boys and girls,
you burn your house down) that an aluminum drop is OK and is properly
done? The only alumimum feeds I've seen have had some of the strands
cut off to allow them to fit into their clamps... :+{
Willie
|
291.454 | Aluminum OK for feeds. | HDLITE::FLEURY | | Wed Aug 08 1990 15:25 | 7 |
| re: .-1
For the extra cost (probably > 2X), I would say that copper for the
feed is not worth it. As long as there is NO-Ox on the junctions at
the meter socket and panel, you shouldn't have a problem.
Dan
|
291.455 | Cost more to run. | ISLNDS::CALCAGNI | A.F.F.A. | Thu Aug 16 1990 16:46 | 9 |
|
Is aluminum still legal in MASS? I thought due to all the problems
in the 60's it wasn't.
However I do know that it costs a lot more to have Aluminum wiring
in a house vs copper, something to do with resistance.
Cal.
|
291.456 | Only for the big stuff, I don't think they make 12/2 RX in AL | EVETPU::MCCARTHY | Sorry Mike but I'm leaving. | Fri Aug 17 1990 00:44 | 15 |
| >> Is aluminum still legal in MASS? I thought due to all the problems
>> in the 60's it wasn't.
Yes it is, but only for large item like ranges, service entrances
and maybe dryers.
>> However I do know that it costs a lot more to have Aluminum wiring
>> in a house vs copper, something to do with resistance.
Al cost more? I don't think so, not with the price of copper.
Given a one-to-one price per foot for same gauge wire, AL would cost more
because you are required to oversize the AL wire for the breaker it is on.
Ie if you could get away with #12 copper, you would have to use #10 AL.
|
291.457 | resistance of Al and Cu | RGB::SEILER | Larry Seiler | Fri Aug 17 1990 01:24 | 19 |
| >> However I do know that it costs a lot more to have Aluminum wiring
>> in a house vs copper, something to do with resistance.
I presume that you mean Al has a higher resistance than copper (true),
and hence you get more voltage drop with aluminum than with copper,
thus losing electrical energy to heating up your wires.
Well, I don't think so. I believe that the codes required larger
conductors for Al house wiring than for copper house wiring, thus
equalizing the resistance per length. That's certainly the case for
service conductors. You can get a copper service conductor if you want
to, but copper costs maybe 3 times as much at the same allowed amperage.
Of course, if connections between the aluminum house wiring and the
receptacles loosen, that raises the resistance and wastes energy.
Eventually, that can cause a fire, which will definately cost more!
Enjoy,
Larry
|
291.458 | Actually. | ISLNDS::CALCAGNI | A.F.F.A. | Fri Aug 24 1990 16:51 | 13 |
|
Re 18.
That's correct. Aluminum does have more resistance.
I've lived in houses with Aluminum wiring throughout, and moved
to a copper wired house. Same heat same number of appliances and
fixtures, well the new house had more lights.
The Copper wired house cost me less to run.
Cal
|
291.800 | Is rewiring needed here? | OAXCEL::KAUFMANN | A Great Cloud of Witnesses | Wed Aug 29 1990 16:49 | 21 |
| I'm a novice at electrical work, and was wondering if anyone could
help me out.
I have an older home in Sudbury. It was built in 1936, originally
as a vacation cottage for Walthamites who spent their summers in
the country.
Over the years, the house has been added on to, and it is now best
described as a modified Cape, 3 BRs, 1 bath.
My question concerns the wiring: almost all the lights in our home
flicker. We have circuit breakers, but the wiring appears to be
old -- it's wrapped in cloth.
Do we need to replace the wiring? If so, will it need to be done
by an electrician? How long (in terms of days) does rewiring take?
How much 'damage' is done to walls and ceilings during rewiring?
Any comments are appreciated.
Bo
|
291.801 | Get some books and videos | ULTRA::SEKURSKI | | Wed Aug 29 1990 18:24 | 21 |
|
In my town your not even suppossed to pull the wire if your not
an electrician.
I'm in the process of adding on a family room and did the wiring
myself. My uncle is an electrician and he checked my work then I
had the inspector approve everything.
It's suprisingly easy but *very* time consuming if your a novice.
I found the Time Life books very helpful along with the books you
find at Grossmans. I couldn't have done any of the work without
the hometime videos also. It's really nice to stop and rewind then
play again a demonstration you didn't quite catch the first time.
Mike
----
P.S. I could of done without the 5 minute Chevy commerial....
|
291.802 | | MFGMEM::S_JOHNSON | Chicago | Thu Aug 30 1990 16:05 | 16 |
|
I've added 8 circuits to my 94 year old house, and am in the process of
adding 3 more for a new 3/4 bath/laundry room I'm installing on the 1st
floor off the kitchen. The books you mentioned are good, "Sunset" books
are good also.
But my best "practical" wiring experience came from completely wiring our
kitchen, with 6 circuits, with the help of my father in law who is
a master electrician. Techniques on drawing out your wiring
plans, in what order to run the wires to which devices, rough wiring
installation, finish wiring techniques,, etc. Also consult your wiring
inspector for wiring tips. Even though the one in Upton, MA is a stickler,
he's very helpful in helping you to do the job right, and informing you
of these little tricks, that probably won't be found in books.
steve
|
291.459 | | KAOFS::S_BROOK | It's time for a summertime dream | Tue Sep 18 1990 13:07 | 23 |
| The type of wire would not affect the cost of electricity in your
house. If anything the possible higher resistance joints of Al would
actually LOWER the amount of electricity used.
The Power Equation tells you this ...
P = V**2
----
R
V remains constant @ 117 (nominal) therefore ...
Increasing the resistance in the circuit will lower the total power
used.
What will happen is that the appliance will use less power (because the
voltage across its terminals has been reduced) and the remaining
slightly reduced power will be dissipated in the terminals, junctions
etc.
Therefore, if your copper wired house uses less total electricity, then
there is definitely some other reason for it.
Stuart
|
291.460 | Ai wiring is not going to save electricity | OPUS::CLEMENCE | | Thu Sep 20 1990 12:08 | 33 |
| RE:. 20
I am sorry to tell you this, but, AI wiring will not LOWER
the cost of power used. In fact it would likely increase it.
Most electic devices will draw more electricity at a lower
voltage than it would at its proper voltage. They operate at a lower
efficiency. Also for devices with motors, the life of the moter would
be shortened.
> V remains constant @ 117 (nominal) therefore ...
> Increasing the resistance in the circuit will lower the total power
> used.
This would hold true if most appliances reistance would remain the
same at the same voltage. Take a 100 watt light bulb. Its resistance
at 1 volt is about .5 ohms, but at full voltage it is about 145 ohms.
> What will happen is that the appliance will use less power (because the
> voltage across its terminals has been reduced) and the remaining
> slightly reduced power will be dissipated in the terminals, junctions
> etc.
This statement is correct that the remaining power will be dissipated
in the terminals, juctions. The power dissipated is HEAT! A fire hazzard.
> Therefore, if your copper wired house uses less total electricity, then
> there is definitely some other reason for it.
The reason is simple. Your appliances work at best efficiency with
full power going to them. I.E. Less electricity.
Bill
|
291.461 | | KAOFS::S_BROOK | Originality = Undetected Plagiarism | Fri Sep 28 1990 21:05 | 48 |
| > I am sorry to tell you this, but, AI wiring will not LOWER
> the cost of power used. In fact it would likely increase it.
I have a very hard time believing this (and currently live in an
Aluminium wired house)
> Most electric devices will draw more electricity at a lower
> voltage than it would at its proper voltage. They operate at a lower
> efficiency. Also for devices with motors, the life of the moter would
> be shortened.
Not necessarily true, not necessarily true and not necessarily true to
each of the 3 points in this paragraph. The first is explained below.
The second is a nonsense ... an electric heater for example will
dissipate all the power it consumes ... it may not dissipate 1500 watts
anymore, but it will still be 100% efficient. The third is not
necessarily true either ... unless the load is close to the maximum
power rating of the motor, at which point you'll get an increase in
its power factor.
> This would hold true if most appliances reistance would remain the
> same at the same voltage. Take a 100 watt light bulb. Its resistance
> at 1 volt is about .5 ohms, but at full voltage it is about 145 ohms.
Light bulbs in particular work on a very non-linear temperature vs
resistance scale, and the major part of that non-linearity occurs
before the bulb lights. Once the bulb lights, the resistance increases
dramatically and the difference in resistance between a 117V bulb
operating at 100 V vs 120 V is almost negligible.
Most other electrical devices do not have this non-linearity.
Aluminium wiring when the proper size is used and the joints are made
correctly will introduce negligible power drop. So, even accounting
for a few joints with increased resistancce, and a few devices with
lower resistance, the overall net effect should be negligible.
> in the terminals, juctions. The power dissipated is HEAT! A fire hazzard.
That is why Aluminium wiring has been eliminated, and why it is
recommended that you ensure that all Al junctions are tight and
the fittings are CU/AL rated. But, don't be alarmist, otherwise
Al would not be used for main feeds ... that's high current, and
a slight increase in resistance on any connection due to oxidation
could be an instant brown-out.
Stuart
|
291.462 | | RAMBLR::MORONEY | Shhh... Mad Scientist at work... | Sat Sep 29 1990 00:14 | 25 |
| re .22:
There are a few cases where high resistance in the feed can cause higher
power consumption. Consider the case of a 100% efficient electric water
heater. To produce a certain amount of hot water, it must consume a
certain amount of power. Now if there's higher resistance in the feed,
the voltage at the water heater is reduced. Therefore, to produce the
same amount of hot water, it must stay "on" longer. You use more electricity
since you use the amount of electricity the water heater uses (same in both
cases) PLUS the amount heating the wires (the resistance in the feed)
This does not hold true for things that stay on a certain length of time
regardless of the applied voltage, such as light bulbs.
I believe light bulbs are pretty close to being a constant current load
when in the range where they give off light (that is, their resistance
is approximately proportional to the voltage)
_If properly installed_ (and connections are good) the resistance of the
wires should be independant of whether aluminum or copper is used. This
is because a larger wire size is used to compensate for the higher resistivity
of aluminum. Ever wonder why the aluminum feed in the main breaker box is so
huge?
-Mike
|
291.463 | | KAOFS::S_BROOK | Originality = Undetected Plagiarism | Mon Oct 01 1990 13:28 | 36 |
| >There are a few cases where high resistance in the feed can cause higher
>power consumption. Consider the case of a 100% efficient electric water
>heater. To produce a certain amount of hot water, it must consume a
>certain amount of power. Now if there's higher resistance in the feed,
>the voltage at the water heater is reduced. Therefore, to produce the
>same amount of hot water, it must stay "on" longer. You use more electricity
>since you use the amount of electricity the water heater uses (same in both
>cases) PLUS the amount heating the wires (the resistance in the feed)
OK, I'll buy this argument ... but ... during the 8 heating months, the
excess heat is going into your house, reducing your overall heating
bill slightly. During the 4 cooling months, it is increasing your
cooling bill. Overall difference ... negligible.
Having been involved with stage lighting and prolonging the life of
the expensive projector bulbs they use (and the dimmers), I was
concerned about this, and what I found was that the resistance of
a light bulb increases dramatically from cold until it starts to
give off "white" light, at which point it increases only slightly
to normal working temperature.
Anyway, after all this discussion, a noticeable difference in power
consumption would have to be explained in other ways ...
for example our furnace blower fan in our current house stays on
distinctly longer to extract more heat from the furnace which increases
consumption. A single degree difference in heating level can produce
a noticebale difference in consumption, especially with electric heat.
There are too many variables in the heating / cooling system (like
weather, inaccurate thermostats, different comfort levels between
two houses etc) which could have a big impact on electricity
consumption to accurately say that there was a difference due to
Al rather than Cu wire.
Stuart
|
291.464 | | RAMBLR::MORONEY | Shhh... Mad Scientist at work... | Mon Oct 01 1990 14:37 | 19 |
| re .24:
> OK, I'll buy this argument ... but ... during the 8 heating months, the
> excess heat is going into your house, reducing your overall heating
> bill slightly. During the 4 cooling months, it is increasing your
> cooling bill. Overall difference ... negligible.
Don't forget that electricity is more expensive than gas or oil, so if you have
a non-electric house, a large increase in the electric bill will be offset by
a smaller decrease in gas/oil usage.
Actually, if there's enough resistance in the wires to make a difference in
the heating bill, your house will have burnt down anyway...
I don't believe that resistance of Al wiring would make a difference in the
resistance in the circuit, since a 20A branch circuit would be wired with
12 gauge copper or 10 gauge aluminum, which both have about the same resistance.
-Mike
|
291.66 | whats enough? | SNAX::HURWITZ | | Tue Oct 16 1990 23:54 | 25 |
| Basic question...
What rating wire should be calculated to use x amount of wattage on x
amount of amps?
(for instance) The cords that my track lighting came with are 18 gauge
which I thought wouldn't handle the 8 75watt lights total on the
3 track sections. The cord (18 gauge) says right on it that it can
handle no more than 1675 watts! Ya right. I want to hardwire this
track light series with romex to a wall dimmer and want to make sure
there is room for the other mistery outlets on this circut. (I know
that one was sent to an outlet in the bathroom by the previous owner.)
Whats the best easy-read wiring book? Whats the best way to calculate
how much room is left on a circut with it still being safe? (i.e.
if 14-2 romex is used and there is a 15 amp breaker and the total
wattage is only 600 watts then this uses about 7 amps at 120 volts.)
Right? So is this "half" safe? I would assume so. I would not assume
revving my car to the red line was safe though, but would assume that
half way to the red line would be normal usage. So is half way to the
total rated AMPs of the circut normal use? I do plan on checking/finding
the other outlets from this circut (some how).
do I know what I'm even asking?
Steve....................................................................
|
291.67 | | ODIXIE::RAMSEY | Take this job and Love it! | Wed Oct 17 1990 12:26 | 10 |
| Well it depends...
There are several charts in the NEC handbook which address this issue.
It depends on the number of outlets how you determine the usage. For
instance, if you only have 1 outlet on a circuit, figure 100% usage.
If two outlets 90%, 4 outlets 80% usage, etc. This is from memory so
don't go with these numbers.
Check out the NEC handbook at your local library for real specific
details.
|
291.68 | what else is on the circuit? | BPOV06::RIDGE | Trouble w/you is the trouble w/me | Wed Oct 17 1990 15:19 | 13 |
| re. -2
I am not an electrician. Here is what I would do to plan what I needed.
A 15 amp circuit of 120 volts gives a total of 1800 watts available.
(apms x volts = watts) For safety, and I think required by code, you
plan on 80% maximum useage. So that leaves you with 1440 watts.
(1800 x .8)
Then it is important to find out what else is already on this circuit.
You need to know what is on the circuit to be able to tell how much
light the track lighting can be allowed to add to the circuit.
I believe that 14-2 wire is used in 15 amp applications and 12-2 wire
is used for 20 amp applications.
|
291.69 | | VMSDEV::HAMMOND | Charlie Hammond -- ZKO3-04/S23 -- dtn 381-2684 | Wed Oct 17 1990 19:24 | 15 |
| re: << Note 574.43 by SNAX::HURWITZ >>>
> What rating wire should be calculated ...
Just so that you understand, the size wire to use in hardwired
installations is not based directly on the load on the curcyut,
but on the size of the breaker that protects that circuit. Yes, of
coures, the breaker has to be heavy enough for the load, and maybe
thats really what you asking. But please understand that if you
have a 20amp breaker then you must use # 12 wire or heavier (# 14
or heavier for 15 amps), and this is true even if you only load
the circuit with 1 or 2 amps.
Different rules apply for the wire sizes that are used in plug-in
lamps and small appliances.
|
291.70 | | TLE::FELDMAN | Larix decidua, var. decify | Wed Oct 17 1990 20:24 | 11 |
| re: .43
Are you saying 8 75 watt bulbs on each of three sections, for a total of 24
bulbs? That's a lot of track lighting, which deserves a dedicated 20 amp
circuit if you insist on putting it all on one circuit.
If you mean there are only 8 bulbs total, then that's only 600 watts total, or
5 amps. I don't know the numbers by heart, but I'd imagine an 18 gauge wire
can handle 5 amps (on a plug; don't use 18 gauge for a hardwired installation).
Gary
|
291.71 | only 8 bulbs total and one more question | SNAX::HURWITZ | | Wed Oct 17 1990 23:59 | 51 |
| These are the 2 things that I'm planning to do.
a. go to the library and try to find that NEC code book. Hopefully
its not too hard to understand.
b. The circut is a 15 amp circut so I will use 14-2 wire to hardwire
the 3 tracks in series and then to the wall dimmer:
/-----T R A C K-------------------------------\
| ^ |
| <-14/2 ^ |----> |
| | 2 heads here 14/2 |
T T
R R
A <----4 heads here 2 heads here ----> A
C C
K K
\\-----down wall to
dimmer here
Total heads = 8. Total watts if using 75 watt bulbs = 600 = 5 amps
out of a 15 amp line. Plenty of light and plenty of "room" for the
other outlets. BTW of the 8 outlets in the room only 3 are used now.
I just have some figuring to do on the amps used by the other stuff on
that line and I have to find the other paths this line takes in the
house.
One more question....... (I really could use a good basic wiring book)
What does it mean when you say wire in series? I assume that I
should wire the tracks as follows:
from -hot-(black)--------*terminal-on-track*---------------
track#1 14/2 wire to track#2
-white--------------*terminal-on-track*----------------
and so on to form a loop. Is this in series? Or is the following in
series? :
*-terminal-on-track-*
| _________________|
| |
from -hot-(black)-------* *--------------------------------- to track#2
track#1
-white----------------------------------------------------------
Steve...................................................................
|
291.72 | | RAMBLR::MORONEY | Shhh... Mad Scientist at work... | Thu Oct 18 1990 00:24 | 14 |
| I don't really follow your series/parallel diagrams, but you wire 120V
electrical in parallel. This means for something like the tracklights,
connect all the black wires together, and connect all the white wires together.
I'd guess for lighting tracks they may not be marked to black and white,
call one rail black and the other white.
Be sure you know what you're doing before wiring, you don't want to burn
your house down.
Possible "gotcha" with the dimmer: many dimmers can handle only 300 watts or
so. Be sure to get one large enough (be sure to allow for the time when
someone replaces the bulbs with higher wattage bulbs, too)
-Mike
|
291.73 | Not a big enough circuit? | ULTRA::WITTENBERG | Secure Systems for Insecure People | Thu Oct 18 1990 14:23 | 8 |
| Check the code book carefully. I think you're going to have too
many outlets on that circuit. If memory serves, you have to count
each outlet as 1.5 amps, so you've got 12 amps in outlets, and 5
amps in your lights puts you over the max. allowed. Also, if they
are considered "continuous duty" you are allowed even less power
draw per circuit.
--David
|
291.74 | | TLE::FELDMAN | Larix decidua, var. decify | Thu Oct 18 1990 15:30 | 11 |
| If you're looking for basic reading, don't bother with the code book. It reads
like a cross between legalese and a software spec, written by a committee for
which clarity was never considered a priority.
In addition to the usual Time-Life, Sunset, and similar books, there's a very
good basic wiring book available at Spag's and sources. I've forgotten the
name, but I learned about it by reading other notes in this conference, so I'm
sure you could find it by doing some searching. It's a thin (1/4 to 1/2 inch)
medium sized (6 by 8 or 7 by 9) book that sells for $5 or less.
Gary
|
291.75 | you need a basic wiring book | BPOV02::RIDGE | Trouble w/you is the trouble w/me | Thu Oct 18 1990 15:39 | 32 |
| Series vs Parallell I do not know but:
re .48 Provided these are the same track-light, not two diferent
units.
_______________________
| _________________ |
from -hot-(black)--------*|terminal on track| |______________
track#1 14/2 wire | | to track#2
-white--------------*|terminal op track| ----------------
||_________________| |
|______________________|
OR: I would preferr to show it using your second diag with one
minor change:
*-terminal-on-track-*
| _________________|
| |
from -hot-(black)-------*->--------------------------------- to track#2
track#1 |
-white---------------*-------------------------------------------
So, as someone already stated, all white wires are connected,
and all black wires are connected.
(the > in the diagram means that there is no connection at
that point)
hope this helps
Steve
|
291.76 | thats it! | SNAX::HURWITZ | | Thu Oct 18 1990 23:29 | 11 |
| re -1
Thats exactly what I was asking and what I needed to know.
Maybe by next year this time I'll be replying with the answers instead
of the questions.
Thanks all.
Steve.........(off to Spags to find that wiring book and a 800 watt
dimmer if one exsists.)
|
291.930 | possible solution? | CSOA1::MCCULLOUGH | | Mon Oct 22 1990 19:42 | 21 |
| My inlaws are currently renovating an older house they bought. The
house is about 20-25 yrs old. They hired a licensed electrician to come
in and do some rewiring including the installation of a new service
entrance in the garage. Since new wiring was also being run from the
pole, the electrician put the new service on the back wall of the
garage while the new wires came in the front. No problem.
Then the inspector comes to inspect the wiring. Says they have to
remove the already installed wiring in the garage and install a FUSE
box where the wires enter the garage, and then rerun the wires to the
service box. The inspector said that this fuse box was to protect the
service box, with main breakers etc. from a power surge, so that in the
event of a surge the fuses would protect the breakers.
I'm not sure if this inspector is for real or if there is a new code
requiring the additional fuse box.
Any ideas?
Mike
|
291.931 | Sound like you need disconnect | CSCMA::LEMIEUX | | Mon Oct 22 1990 22:13 | 31 |
|
I am not sure if I completely understand what you are saying
but I'll give it a try....Do the wires coming from the utility
enter the front of the building? and continue on to the rear of
the building through the interior walls to the breaker panel in
the rear? Does this sound like the scenerio?
If so there must be a disconnect switch that is either
fused or breaker type where the wire enters the building interior
in the front. You cannot have unprotected service entrance wires
running around inside the building.
From that point on the cable from the disconnect switch to the panel
will have to contain the phase conductors, a neutral and the ground
because the breaker panel at the rear of the building is now a sub-panel.
The neutral to ground bond will have to be in the disconnect switch.
along with the grounding conductor to the cold water pipe and the
ground rod. There must not be a neutral to ground bond in the
sub-panel.
As for the inspector using surge protection as the reason for
fuses, I think he was probably just mixing terms and meant that
the wires running in the building must be protected for over current.
As I stated I was not completely sure of what you were really
asking so if you could post a little diagram here we might be able
to help you out a little better.
Paul L
|
291.932 | Not all that unusual | STAR::DZIEDZIC | | Tue Oct 23 1990 10:20 | 6 |
| Sounds like my (new) neighbor's (new) house. Their service
drop is on the front corner of the garage, but their panel
is near the middle of the basement (garage at basement level).
They have a service disconnect switch right inside the garage
where the feed from the meter enters the garage, and a standard
panel in the basement.
|
291.933 | Cutoff required if more than 5' from meter. | HDLITE::FLEURY | | Tue Oct 23 1990 10:56 | 12 |
| RE: .7
The code requires a cutoff switch as described in .8 whenever the main
panel is farther than 5' from the meter. This cutoff can be either a
breaker or knife switch designed for this. Usually, you will see a
breaker in this type of application.
Once this is done, the main cutoff becomes the "main" panel and the
other panel is wired like a sub-panel. The connection should be made
with SER cable (3-wires w/g) rather than SEU (2-wires w/g).
Dan
|
291.934 | clear as mud | CSOA1::MCCULLOUGH | | Tue Oct 23 1990 12:27 | 28 |
| Maybe there is some logic here.
The new wires entering the building are coming in the front while the
breaker box is in the back, distance of about 20 feet. I can see that
without a switch, fuse or breaker box where the wires enter the house
they would be unprotected to the breaker box. So this makes sense now.
If the breaker box was installed close to the point of entry it would
have been a different story.
ceiling
wires|_________________________________________________________|
======|=======================================================--|
entry | ^ | |
point | |_ wants fuse box here | |
| new breaker box --|
| |
|
front of garage back of garage
Mike
|
291.935 | RE: .7 "Licensed"? | MVDS02::LOCKRIDGE | Artificial Insanity | Tue Oct 23 1990 15:27 | 12 |
| re: .7
> My inlaws are currently renovating an older house they bought. The
> house is about 20-25 yrs old. They hired a licensed electrician to come
^^^^^^^^
Gee, being licensed assured that the electrician was up-to-date with
the codes, huh. One would expect that a licensed electrician would be
required to keep current, or isn't that a requirement after obtaining
the license? (This is both a facetious and at the same time serious
question).
-Bob
|
291.936 | works as advertised | CLUSTA::GLANTZ | Mike 227-4299 @TAY Littleton MA | Tue Oct 23 1990 15:41 | 5 |
| Yes, they're required to take refresher courses (a certain number of
hours, I forget exactly how much). These cover mainly changes and
additions to the code. If you're interested and live in the Greater
Maynard area, the Asabet Valley Regional Vocational School in Marlboro
offers these courses.
|
291.937 | FYI | CSCMA::LEMIEUX | | Tue Oct 23 1990 16:47 | 22 |
|
All that is required to renew your electrical licensce is 15 hours
continueing education for every new code release...which equates to
15 hours every three years. It is probably not enough but that is
the way it is today in all of the New England states.
The diagram you posted as I requested does indeed explain
your situation and my solution/explaination along with the other
ones posted here are correct. This installation needs a disconnect
at the point of entry and the correct style cable running to the
sub-panel.
As this situation shows, as with any profession there are those
who know what they are doing and those that do not. It's funny that
the only ones who get written about are the ones who do not, which
tends to make it appear that there are a lot more electricians who
don't know what they are doing than there are that do.
Signed,
An electrician
|
291.938 | | VMSDEV::HAMMOND | Charlie Hammond -- ZKO3-04/S23 -- dtn 381-2684 | Tue Oct 23 1990 18:16 | 10 |
| The requirement that the service entrance cutoff must be "near"
the point where the service enters the building is not new. This
was a requirement six years ago when we build our house and had
then been on the books long enough to make it into consumer
oriented wiring books. I don't recall that "near" was defined as
five feet or left to the inspector's discretion, so the "5 foot
rule" may be relatively new.
But I agree that a "licensed" electrician should have known better
than to expect to get away with a 20 foot run.
|
291.939 | No distance specified in NEC | CSCMA::LEMIEUX | | Tue Oct 23 1990 19:41 | 12 |
|
Charlie is correct, there is no footage specified by the NEC. Refer
to Article 230-70 (a). which explains where the disconnecting means
shall be placed. It must be placed either outside the building
structure or inside nearest the point of entrance of the service
conductors.
If you have a copy of the NEC "handbook" it even
goes on to explain that NEC does not dictate the distance, but leaves
it up to the local authority having jurisdiction to specify a distance
if they want to.
|
291.940 | What kind of problems does an outside disconnect invite? | VAXADA::G::MORRIS | Greg Morris | Tue Oct 23 1990 22:27 | 12 |
|
I will be building a house and was planning on structuring the basement so
I could eventually create a large finished room down there. A lot of finished
basements I've seen have some sort of funny little door in the finished wall
to hide the main breaker panel. I was hoping to avoid this by locating the
main panel in the portion of the basement that will be left unfinished.
It is unlikely that location will be "near" the meter.
Having a cutoff inside would require some sort of access door in the finished
wall which kind of defeats the purpose of locating the main panel far away in
the first place. I haven't seen a cutoff on the outside of a house. How
unusual is that? Any other way to solve this problem?
|
291.941 | Here are just a few options | WMOIS::BOUDREAU_C | | Wed Oct 24 1990 01:02 | 22 |
| RE-1
It is possible to buy meter sockets with Main breakers in them.
This is most common on multiple gang sockets, but they are available in
single gang configurations. You could also install a main disconnect
outside in a seperate encloser. There is a drawback however, they
connot be locked in the on position, and must be readily assable. This
means that they are open to tampering by strangers, or anyone who wants
to. This may prove to create a much worse situation.
The only other option you have, is to run the conductors from the
meter socket to the panel on the OUTSIDE of the house. This could be an
eyesore if done incorrectly. However, with a little imagination it can
be very inconsipuous.
Why not go all the way and go under ground, with the meter socket
away from the house. The bottom line here is HOW MUCH DO YOU WANT TO
SPEND???
Just my $0.025
CB
|
291.942 | outside is normal in some places | REGENT::GETTYS | Bob Gettys N1BRM 235-8285 | Wed Oct 24 1990 12:42 | 10 |
|
Interesting side note - My aunt and uncle live in
Arkansas and where they live, it is REQUIRED that the main
cutoff be outside at the meter and ACCESSABLE. The rationale is
for the fire department to be able to cut the power to the house
quickly and safely in case of fire. Their breaker panel is
located in a closet (actually the washer and dryer are there
also) just off the kitchen in the center of the house.
/s/ Bob
|
291.943 | Outside disconnects common | CSCMA::LEMIEUX | | Wed Oct 24 1990 13:44 | 12 |
|
Some areas in Colorado also use outside disconnects
and panelboards. I worked in the Breckenridge/Frisco area of Colorado
in the late 70's early 80's and we installed many panelboards and
disconnects outside without any problems at all when done correctly.
I think the only time that locking the disconnect is a problem
is a multi-tennant situation. If it is your own home you can lock
anything you want as far as the code is concerned. As for locking
breakers in the on position, it does not affect their operation
they will still trip as required. If the disconnect were fused
it still would not be a problem.
|
291.944 | Found the paragraph about locking | CSCMA::LEMIEUX | | Wed Oct 24 1990 14:21 | 10 |
|
In addition to my previous reply I found the only reference
to locking a service entrance overcurrent device. It is ART. 230
-92 in the NEC. But as I said before multi tennant situations differ.
It say's as long as the branch circuits on the load side are
in an accessible location, and are of lower ampacity than the service
entrance over current device you can lock the service over current
device.
|
291.945 | Common Practice in Atlanta | ODIXIE::RAMSEY | Take this job and Love it! | Wed Oct 24 1990 18:59 | 22 |
| We had our service upgraded from 60 to 150 about 18 months ago. The
meter is outside and there is a ~15ft run inside the house before it
reaches the main fuse panel. The local inspector required that there
be a shutoff located outside between the meter and the fuse panel. The
meter had to be moved anyway because it was located inside the car port
and the offended various safety rules. The new meter box is about 24
inches tall. The meter itself is located near the top half and the
bottom half has a hinged cover. Under the cover is a main breaker
switch. The hinged cover has a slot which fits over a eye shaped
protrusion so that the cover can be locked. Aparently very common with
new construction.
As to the fire department actually using it to shutoff the power...
As a member of a the local fire department, I can say that our
departments policy is that we are fire fighters, not electricans. We
do not turn off any electricity, we have to wait for the power company.
This is a safety caution from the viewpoint of they know better how to
handle electrical problems, and the process of flipping off a fuse can
cause small arcs at other terminals and fuses inside the structure.
Any gas leak and you have just created a means to ignite it. But none
of this has anything do to with the topic at hand :^)
|
291.946 | SERVICE DISCONNECT | WMOIS::BOUDREAU_C | | Wed Oct 24 1990 20:40 | 27 |
| RE 21,22
Locking the main disconnect. The article that you mentioned had to
do with the "over current protection". We are talking about the SERVICE
DISCONNECT. Art 230-70a states, "LOCATION. The service disconnecting
means shall be installed at a readily accessible location either
outside of a building or structure, or inside nearest the point of
entrance of the service conductors."
By definition (see art 100), Accessible means "Admitting close
approach: not guarded by LOCKED doors, elevation or other EFFECTIVE
means."
Readily Accessible means, "Capable of being reached quickly for
operation, renewal, or inspections, without requiring those to whom
ready access is requisite to climb over or remove obstacles or to
resort to portable ladders, chairs, ect.."
My conclusion is as I stated before, that the SERVICE DISCONNECT
cannot be locked in the on position. Breaker locks must be removed in
order to OPEN the circuit. As you stated, the breaker will still trip
internally, when locked in the on position. But the locks (effective
means) must be removed to disconnect the service.
CB
|
291.947 | Many interpretations of NEC | CSCMA::LEMIEUX | | Thu Oct 25 1990 12:56 | 24 |
|
RE .23
A perfect example of why no 2 individuals involved in
this trade can agree on a particular article in NEC....it usually
can be twisted any way that you want it to be. In the end, if the
local inspector lets you lock the disconnect, it's OK to do so
by code although it is probably not the best thing to do.
I was pointing out another option or way of interpreting the
particular rules pertaining to the situation in the original question
and not trying say that my interpretation was the only one that
is viable. Sorry if I came across that way. I have been in this
business too long to think that my interpretation is the only correct
one. When performing this type of work you interpret the code
according to the training and past experience you have and adjust
accordingly when you encounter an inspector who differs from your
point of view, within reason. Obviously if the inspector is having
me do something that is a blatant safety problem I would certainly
question his method.
|
291.77 | I apologize if I'm teaching my grandmother... | LYCEUM::CURTIS | Dick "Aristotle" Curtis | Thu Oct 25 1990 14:21 | 47 |
| .52 has two circuits which are both wired in parallel; the only
difference is how they were sketched.
.48 has one parallel circuit, followed by one series circuit.
Parallel is what you want. If you were to wire the lights in series,
they would be (a) be very dim, (you could say that they were dividing
between them the 120 volts that each should have), and (b) if one
burned out or was removed, it would break the circuit and none would
light.
To make it somewhat more obvious:
-hot----------------+---------------+---------------+---------------+
| | | |
| | | |
@ @ @ @
| | | |
| | | |
-white--------------+---------------+---------------+---------------+
In a parallel circuit, each light (@) or other load gets the full
voltage applied to the circuit, and the total current is the sum of
the current consumed by each load.
-hot----------------@---------------@---------------@---------------@-+
|
|
-white----------------------------------------------------------------+
In a series circuit, the voltage is "shared" by the various loads, and
none is actually getting the full voltage. In this case, if the four
lights were all the same wattage, they'd each be using 1/4 the voltage;
your 75 watt bulbs would look mighty dim.
There may be some application for this kind of thing when you are
wiring a house, but I don't know of any.
Don't forget that the switch goes in the "hot" side of the circuit;
dimmers will normally have instructions that you can follow.
Dick
|
291.948 | | SALEM::LAYTON | | Thu Oct 25 1990 15:48 | 6 |
| If the goal is to shut the power off to the house, and the meter is
outside, wouldn't it be easiest to simply break the plastic Electric
company seal, and yank the meter? You could lock the main disconnect,
inside or out.
Carl (definitely not a firefighter or electrician or wiring inspector).
|
291.949 | | QUARK::LIONEL | Free advice is worth every cent | Thu Oct 25 1990 16:41 | 11 |
| Re: .25
Yanking the meter creates an incredible electrocution hazard, as you
have the main feed unprotected and exposed. When a meter is pulled, it
is replaced by an insulating glass plate.
With an outside disconnect, I'd be worried about someone coming along and
maliciously disconnecting power to the house.
Steve
|
291.950 | Pulling meter NOT recomended | WMOIS::BOUDREAU_C | | Thu Oct 25 1990 21:19 | 9 |
|
RE-1
I agree, also the meter is not an approved disconnecting method. It
is used as such in emergency situations. A problem does arise if the
meter is pulled under a heavy load. This could cause one to draw an
arc, which could "jump" across the LINE side of the meter. This is the
most serious possible situation. The result could be disastrous. For
this reason, a MAIN disconnect is required.
|
291.951 | no twisting here | WMOIS::BOUDREAU_C | | Thu Oct 25 1990 21:54 | 18 |
| RE 24
I agree the not all interpretations of the code are the same.
However, I try to interpret it as it was intended, and not necessarily
as it can make my job easier. If the main disconnect was intended to be
able to be locked in the ON position, it would be stated (as it was
stated that the over current protection devise can be locked on). Since
it is not stated, I would conclude that it not an option. This theory
is backed up by the phrase, "readily accessible".
As an electrician, you must know that if you give inaccurate, or
poor advice, you could be found liable if some one gets injured by
following the advice as given them. I know that I am not willing to
risk neither my master's, nor journeyman's licenses. Thus, I give
advice as I see fit, and as a lawyer may interpret the code. Anyone
else can do as they please.
CB
|
291.867 | in-line dimmer switch ? | MSEE::CHENG | | Fri Mar 01 1991 14:37 | 6 |
| I bought a crystal table lamp last night. The lamp comes with one of
those cheapo in-line switch on the power cord. I would like to replace
it with a dimmer-switch. Is thare a in-line dimmer-switch out in the
market ? Where can I find it ?
|
291.868 | | MSESU::HOPKINS | Give PEACE a chance | Fri Mar 01 1991 16:28 | 4 |
| I just bought an extention cord with an in-line dimmer switch. I'm not
sure if that's what you're looking for. It's made by G.E. and I bought
it at K-Mart.
|
291.869 | | QUARK::LIONEL | Free advice is worth every cent | Fri Mar 01 1991 16:40 | 4 |
| You can get inline dimmers that hook in just like an inline
switch. Check most any place that sells electrical supplies.
Steve
|
291.870 | or Wolfer's | ENABLE::GLANTZ | Mike 227-4299 DECtp TAY Littleton MA | Fri Mar 01 1991 16:42 | 6 |
| You can also find a wide selection of high-quality stuff like this (if
K-mart's GE isn't good enough) at any good lighting store. One which
comes to mind as having an excellent selection is Wolfer's in (I
think) Brighton. They have some really incredible lighting control
stuff -- the sort of stuff you see advertised in Architectural Digest
and installed in $5-million homes.
|
291.871 | Try Somerville Lumber | 3149::YEE | | Fri Mar 01 1991 21:31 | 6 |
| I bought a couple at Somerville Lumber...works well. Made by GE, I
think, clamps in-line with the cord. It has a slide on the side and
comes in dark brown. There is also a cheaper switch (2 position
rotary)... available also at Somerville lumber.
Ed
|
291.543 | Electrical code violation - report it? | STAR::DZIEDZIC | | Fri Mar 08 1991 11:24 | 28 |
291.544 | Newly built house | STAR::DZIEDZIC | | Fri Mar 08 1991 14:13 | 2 |
| BTW, to clarify, the house in .0 is newly built, so I'm quite sure
the crockery was done by the electrician used by the builder.
|
291.545 | | FLOWER::HILDEBRANT | I'm the NRA | Fri Mar 08 1991 14:33 | 4 |
| I would report it....the "electrican" could cause future harm to others
and should be stopped.
Marc H.
|
291.546 | | KOALA::DIAMOND | No brag, Just fact. | Fri Mar 08 1991 16:30 | 6 |
|
I'd also report, but it probably won't do any good. The local building
inspector would have to take part of the blame also. He was supose to
inspect the house!!!
Mike
|
291.547 | | VMSDEV::HAMMOND | Charlie Hammond -- ZKO3-04/S23 -- dtn 381-2684 | Fri Mar 08 1991 17:59 | 12 |
| Whether or not to report the violation is pretty much up to you
and how you feel about such things. It might be more bother to
report it than its worth, or you might think its an important
thing.
On the other hand you should get this fixed. Having a box broken
open to make room for more wires than allowed is not a marginal
violation -- its a real danger. Fixing it right may mean cutting
the wall open to install a large/deepr box. That means $s to
re-drywall, re-plaster, re-paint, etc. The builder should do this
at no charge to you. And if the builder is reputable he may just
decide not to deal with this electrician again.
|
291.548 | Makes my skin crawl. | XK120::SHURSKY | Stuntman for Wile E. Coyote. | Fri Mar 08 1991 18:18 | 4 |
| Oooooh, just think of all the things this guy did in your walls you haven't
found yet! I couldn't resist.
Stan
|
291.549 | Builder first, inspector second | WMOIS::BOUDREAU_C | | Fri Mar 08 1991 18:54 | 13 |
| I would contact the builder and ask/request that the problem be
fixed. Also tell him that you will not pay to fix something that was
wrong in the first place.
You said that you were doing some work there with a permit. I would
mention it to the wire inspector (if he will be coming) and see what he
says. Sometimes we (electricians) get inspections before we really
should (not quite finished but close enough). This is common practice
if you are a local (your reputation has allot to do with it). However,
this situation can change if you start doing shabby or unacceptable
work.
Cary
|
291.558 | What type of wire inside conduit? | JUPITR::DICK | | Fri Mar 08 1991 23:51 | 12 |
| Looks like I will be wiring my shop using conduit, since it runs
outside of the walls it will give me the option of easy electrical
relocation as the shop takes shape. I won't have to snake wires through
the walls and insulation.
The question is what kind of wire to use in the conduit ?? I see both
solid and stranded copper that appear to meet code. What are the pros
and cons of each ?
Harold Dick
JUPITR::DICK
|
291.559 | A few pros and cons | STAR::DZIEDZIC | | Sat Mar 09 1991 17:10 | 17 |
| Solid wire is typically stiffer than stranded wire for a given
size, but the stranded wire has a slightly larger cross-sectional
area. Stranded wire is often easier to pull through long runs of
conduit.
Other than solid/stranded, another factor in conduit wiring is the
wire type. The NEC allows more type THHN/THWN wires in a given
size of conduit than type T/TW wires. That can make a difference
in what size conduit you use. You'll have to get the complete dope
from tables in the NEC, but as an example, with 1/2-inch conduit,
and number 14 wires, the code allows 9 T/TW wires, or 13 THHN/THWN
wires.
Making connections at devices (switches/receptacles) is a little
harder using stranded wire. Some inspectors don't like it for this
reason. (A good reason to check with your local inspector first.)
|
291.560 | the pull is easier, the final connection is more work | DDIF::MCCARTHY | Well Norm, lets go take a look. | Sun Mar 10 1991 14:03 | 13 |
| >> Making connections at devices (switches/receptacles) is a little
>> harder using stranded wire. Some inspectors don't like it for this
>> reason. (A good reason to check with your local inspector first.)
I also thought that you had to use spade type crimp-on ends making the
connections to non-SPEC grade devices (switches, recep..) (ie stranded wire
under a screw is not allowed).
Pulling stranded wire through is A GREAT DEAL easier especally if you have any
bends to pull through.
Brian
|
291.550 | Inspector stopped by today | STAR::DZIEDZIC | | Tue Mar 12 1991 16:19 | 14 |
| The inspector stopped by today for my rough electrical inspection
and looked at the box. He was a little pissed the electician
didn't replace the box when he broke the side (the couple of
extra wires in the box didn't bother him too much). He thought
that perhaps a single pole switch was originally installed at
that point, and that he flagged that as a violation; apparently
there is a change in the 1990 code requiring switches at all
entrances and exits to a (room? basement?). (We got off on a
tangent and I didn't get the exact details of the code change;
perhaps someone else might be able to elaborate on it.)
He suggested I call the electrician and tell him to fix it; if
the guy gives me any guff I should call the inspector back and
he'll "politely remind him" to fix it.
|
291.551 | | HPSTEK::MONACO | | Tue Mar 12 1991 16:22 | 12 |
| If this is a Newly constructed house in Mass you may have some legal
clout. I belive but I'm not positive that Contractors/builders are
required to fix problems for a period of one year.
We are on our third home and I have dealt with a number of contractors
and tradesmen. I have had good luck with them fixing problems that have
occured or were discovered after several months.
Check with your builder first and by all means DOCUMENT all conversations
and letters to be on the safe side.
Don
|
291.552 | its your money | ELWOOD::DYMON | | Wed Mar 13 1991 09:49 | 5 |
| Look at it this way. Your paying for it. You might as
well get it done right. You wouldnt buy a new car with
one flat tire now would you?????????????
JD
|
291.561 | pulling and bends | WORDS::DUKE | | Thu Mar 14 1991 10:56 | 20 |
|
> Pulling stranded wire through is A GREAT DEAL easier
> especally if you have any bends to pull through.
There are restrictions in NEC on the number of bends
between pull/junction boxes. Unless things have changed
recently, the limit it 360 degrees of bends. Sounds like a
lot of bends, but it adds up fast when you consider all of
the little offsets and saddles to get around things. The
closer one gets to the max number of conductors the harder it
is to pull regardless of the number of bends.
If you have never worked with EMT or other conduit, be
prepared to make a few pieces of spaghetti. Once you get the
hang of it, it is almost fun.
Peter Duke
|
291.562 | that hard ?? | FREDW::MATTHES | half a bubble off plumb | Fri Mar 15 1991 11:49 | 6 |
|
Do you mean making spaghetti by pulling the insulation off the wires ??
By the way, what about the use of soap or vaseline ??
-f
|
291.563 | I thought the code said no to soap/vasline. | EVETPU::IMPINK::mccarthy | Well Norm, lets go take a look. | Fri Mar 15 1991 14:11 | 4 |
| I think soap and vaseline are against code. There is a product out
there that is UL approved.
Brian
|
291.564 | Not wire damage | WORDS::DUKE | | Fri Mar 15 1991 15:13 | 28 |
|
> Do you mean making spaghetti by pulling the insulation off
> the wires ??
No, not damage to the wires. I was thinking of my first
attempt at bending EMT and how easy it was to make things
like offset (especially at boxes) go in the wrong direction.
For a shop or garage, it sure beats all that drilling. Makes
adding a new circuit in the future MUCH easier unless the
pipe is full.
If you happen to be in Merrimack or near by, I have 1/2
and 3/4 inch benders you are welcome use.
I spoke with one of the contract electricians here (MKO).
He stated that many inspectors require crimp lugs on stranded
wire for devices that have only screw connections. If the
conductors are passing through a box, another alternative is
to wire nut in taps of solid wire for connection to the
device. This type of arrangement is generally prefered to
using the bond strap (between screws) on the device. This
also avoids opening the circuit to replace the device. More
important in commmercial than residential.
Peter Duke
|
291.565 | Wire Lube | ESDNI4::FARRELL | Black Pearl Express Trucking, LTD. | Mon Mar 18 1991 12:41 | 15 |
| <<< Note 4158.5 by EVETPU::IMPINK::mccarthy "Well Norm, lets go take a look." >>>
-< I thought the code said no to soap/vasline. >-
I think soap and vaseline are against code. There is a product out
there that is UL approved.
Brian
> Most Electrical Supply houses carry "Wire Lube". Comes in a 1qt bottle
>and resembles a grayish paste.
>
>Runs about $5 - $7 a bottle
>
>/Joe
|
291.566 | "Duck Butter...." | RAVEN1::GHOOPER | Parrotheads Make Great Lovers! | Tue Mar 19 1991 02:17 | 5 |
| There is a product that is used. It is commonly called "soap" by a lot
of electricians, but it is not actually soap. We used to call it "duck
butter". Can't remember the actual brand name.
-Hoop-
|
291.567 | real slippery stuff | EVETPU::MCCARTHY | Well Norm, lets go take a look. | Tue Mar 19 1991 02:21 | 6 |
| We used to call it lube, and usually had the color of Mellow-Yellow. We
usually only used it for underground services and if you got it on your hands
you might has well take five minutes off and clean your hands because you can't
get a grip on ANYTHING!
bjm
|
291.568 | IDEAL wire pulling lube | CSCMA::LEMIEUX | | Tue Mar 19 1991 11:33 | 11 |
|
Hi,
A brand that comes to mind is made by IDEAL, wire pulling
lubricant. You can buy it in a can like paint or a squeeze bottle.
It's cheap and save lots of labor and avoids lots of damage to the
wire and to the conduit if the conduit is PVC.
I have a name for it also....but I can't use it here :')
Paul
|
291.553 | Code change? | FDCV06::MARINO | | Wed Mar 20 1991 18:26 | 9 |
| Can someone clarify the 1990 code change about switches to entrances
and exits. We just built a new house, and there is now switch next
to the door leading to the bulkhead, sort of confused me.
Also, is a requirement to have circuit breaker outlets in bathrooms,
or can they use any type of outlet.
thx! :^)
|
291.569 | Can you flare the end for several inches, by a small amount? | LYCEUM::CURTIS | Dick "Aristotle" Curtis | Wed Mar 20 1991 19:25 | 9 |
| I've a question about working the conduit.
I have a mechanical, not electrical, application for which I thought
that the conduit would be fine; alas, the inside diameter is small by
a very small amount. Is it possible to make 1/2" conduit expand, by
a small amount, for a length of 4 or 3 inches? Or is it either
impossible, or a dicey thing that's likely to spoil the stock?
Dick
|
291.570 | | RAVEN1::GHOOPER | You help me more by not giving in.. | Thu Mar 21 1991 09:01 | 3 |
| They sell conduit stretchers at the same place as they do grid squares.
-Hoop-
|
291.554 | Depends on what you have around... | HNDYMN::MCCARTHY | Well Norm, lets go take a look. | Thu Mar 21 1991 09:52 | 12 |
| >> Also, is a requirement to have circuit breaker outlets in bathrooms,
>> or can they use any type of outlet.
May I assume you mean GFI protected outlets? If so, Yes. There are
several ways of doing this, a GFI receptacle or a "normal" receptacle provided
that it is GFI protected. The second part can be done by having the receptacle
wired into the "load" side of a GFI receptacle. someplace else in the house or it
can be on a GFI breaker. If you have more than one bathroom it is common that
one will have a GFI receptacle and the second will be wired to the load side of
this, hence protecting it.
Brian
|
291.571 | Don't suppose anyone would be willing to lend one for a night... | LYCEUM::CURTIS | Dick "Aristotle" Curtis | Thu Mar 21 1991 13:13 | 3 |
| Great! Would you know if they're expensive?
Dick
|
291.572 | | NOTIME::SACKS | Gerald Sacks ZKO2-3/N30 DTN:381-2085 | Thu Mar 21 1991 13:27 | 1 |
| What's a grid square?
|
291.555 | GFI | FDCV07::MARINO | | Thu Mar 21 1991 18:06 | 6 |
| RE .11
We have 1 1/2 baths the upstairs has a "GFI" breaker, (the kind
with the reset button/test button. But the downstairs bathroom
only has what looks like a regular outlet.
|
291.556 | Test it to see if it is protected. | XK120::SHURSKY | <DETOUR> Easy Street under repair. | Thu Mar 21 1991 18:53 | 9 |
| The one with the regular outlet may be protected by the other GFI outlet (refer
to .11). To test it, press the "TEST" button the GFI outlet, run down stairs
and plug something into the other outlet. If the something works then that GFI
is not protecting the downstairs outlet. Try this with any other GFI outlets
in the house. If none of the GFI outlets disables the downstairs bath outlet,
then I wouldn't use the hair dryer while standing in a puddle of water in the
downstairs bath. %-{
Stan
|
291.573 | Ever been 'Snipe' hunting? | RAVEN1::GHOOPER | You help me more by not giving in.. | Mon Mar 25 1991 05:09 | 10 |
| RE: -1
A "conduit stretcher" is an old gag that is played on new
electricians' helpers and "grid squares" is an old gag played on new
recruits right out of boot-camp.
"......go fetch me a box of 'grid squares', Private, and don't come
back with out 'em....."
-Hoop-
|
291.574 | | WMOIS::VAINE | The Silver Bullet | Mon Mar 25 1991 10:31 | 4 |
| you get those things the same place you get right and left ground
straps.......
lynn
|
291.575 | | SALEM::LAYTON | | Mon Mar 25 1991 12:54 | 3 |
| ...and fetch me a bucket of steam...
...from the sea locker...
|
291.576 | | KENT::KENT | Peter Kent - SASE, 223-1933 | Mon Mar 25 1991 15:31 | 1 |
| ...and clean the contacts on the SCRs.
|
291.577 | Abrasives might serve me -- and .12 obviously has a source... | LYCEUM::CURTIS | Dick "Aristotle" Curtis | Mon Mar 25 1991 16:27 | 8 |
291.578 | Likewise ... '.. relative bearing grease ..' | AHIKER::EARLY | Bob Early, Digital Services | Mon Mar 25 1991 16:42 | 11 |
|
During a stint at an Environmental Research and Survey Company, we
were "on the river" near Albany, NY with "in situ" (in place) water
direction and speed meters, and the diving supervisor sent the
conract technician for a can of "relative bearing grease" ...
Would probably work as well during an Orienteering Meet..
Bob
|
291.579 | Sorry, son, fresh out...try the hanger across the field | ULTNIX::taber | Bitingly cold. Extra Dry. Straight up with a twist. | Tue Mar 26 1991 11:27 | 4 |
| ...20 yards of flight line....a bucket of propwash (rotorwash if you
work on helicopters)...
brings back memories.
|
291.580 | | RAVEN1::GHOOPER | You helped me more by not givin' in.. | Wed Mar 27 1991 01:45 | 9 |
| RE: .16
Ha! I haven't heard that in a long time!
RE: .19
Watch it, buddy! :-)
-Hoop-
|
291.581 | Water Hammer | MEIS::TOWNSEND | Erik S. Townsend (DTN) 247-2436 | Wed Mar 27 1991 12:24 | 12 |
| A typical scenario in a volunteer firefighter-candidate's oral exam:
Examiner: "Let's see, on Engine #5, which compartment is the Water
Hammer stored in, and what is it used for?"
Usual Ans: "Uh, I think its in the left rear compartment and its
used uh, I think to blow water through a door..."
(For the uninitiated, Water Hammer is not a device but an undesirable
phenomenon which can destroy a pump if proper action is not taken)
ET
|
291.582 | bit buckets | PCOJCT::MILBERG | I was a DCC - 3 jobs ago! | Wed Mar 27 1991 20:51 | 9 |
| Surprised that with all us kumpooter types, no one has mentioned the
infamous
"bit bucket"
which - in the days of paper tape or card puches - DID exist!
-Barry_who_is_old_enough_to_remember_and_young_enough_to_remember-
|
291.583 | My sides hurt! | EPOCH::JOHNSON | If we build it, they will come. | Wed Mar 27 1991 23:26 | 6 |
| Does this discussion have anything to do with when we used to send guys back
aft on a carrier for a 'bucket of steam' or 'twenty feet of chow line' or a
dozen 'relative bearings'?
How about left- and right-headed nails (not to mention ceiling- and
corner-nails)?
|
291.584 | Don't forget the wind shifters | SEESAW::PILANT | L. Mark Pilant, VMS Security | Thu Mar 28 1991 00:00 | 4 |
| How about the infamous left and right handed wind shifters. These
are great for directing smoke from a campfire.
- Mark
|
291.585 | | QUARK::LIONEL | Free advice is worth every cent | Thu Mar 28 1991 12:25 | 3 |
| Or the classic left-handed monkey wrench.
Steve
|
291.586 | polka-dot paint | CLOSET::VAXUUM::T_PARMENTER | Brain thieves! | Thu Mar 28 1991 12:26 | 1 |
| skyhook
|
291.587 | old swabbies never | BTOVT::CACCIA_S | the REAL steve | Thu Mar 28 1991 14:06 | 2 |
| aboard a carrier you would also have needed a pad-eye swab.
|
291.588 | The way this note is going,.... seems appropriate. | MARX::SULLIVAN | We have met the enemy, and they is us! | Thu Mar 28 1991 15:35 | 7 |
|
Has anyone found the best price for an air shredder now that Spags
doesn't carry them anymore.
:-)
|
291.589 | | ULTNIX::taber | Bitingly cold. Extra Dry. Straight up with a twist. | Thu Mar 28 1991 15:51 | 2 |
| Wadda mean they don't carry them anymore? They're right next to the
conduit stretchers, by the flight line over by the left-hand ground straps...
|
291.590 | :-) | NOVA::FISHER | It's Spring | Mon Apr 01 1991 14:40 | 4 |
| Well, now that we can't get any work done 'cause nobody can find the
necessary equipment, let's all go on a snipe hunt....
ed
|
291.591 | how short? | NOVA::FISHER | It's Spring | Mon Apr 01 1991 14:41 | 3 |
| Anybody got a diagram of a short circuit?
ed
|
291.592 | Oh those werethe days | CSDNET::DICASTRO | Quantity time! | Mon Apr 01 1991 19:04 | 5 |
| And of course, no Saturday at the garage would be complete without
sending the apprentice to the juck yard/parts store for a VW radiator.
|
291.593 | Oh NO!! - not the air shredder!! | FREDW::SYSTEM | half a bubble off plumb | Tue Apr 02 1991 13:21 | 6 |
|
I kneeeeew someone would mention an air shredder. Frankly, I'm
suprised that it's not a code requirement that the air in the conduit
has to be shredded in order to pass inspection.
How does the inspector do that without it all leaking out ??
|
291.594 | the jokes on you...... | CSC32::J_KALINOWSKI | Forget NAM?....NEVER! | Wed Apr 03 1991 15:00 | 15 |
|
RE: .27
LEFT and RIGHT hand monkey wrenches DO exist as well as
crescent wrenches. I have both kinds and they have both been
around for about 70 years.
Either one of the left handed wrenchs will have left hand
threads so that the natural motion of thumb and index finger
OF THE LEFT HAND will accomplish the same task (opening or closing
the jaws) as a right hand wrench would do. If you shop at "REAL"
plumbing supply stores or auto parts stores they can show you both
kinds. You don,t find real tools at K-MART.
-john
|
291.595 | Don't forget Metric! | CSCMA::DENCE | | Thu Apr 04 1991 15:02 | 1 |
| YEP! And they ALL come in metric sizes!!!
|
291.596 | That reminds me of a story..... | AUNTB::SIMON | | Fri Apr 05 1991 13:00 | 3 |
| in those days of propwash...you could also be sent for a buffer
amplifier to make the buffer run better when buffing the barracks
floor....
|
291.557 | resolution? | ULTRA::WITTENBERG | Secure Systems for Insecure People | Fri May 17 1991 19:52 | 6 |
| So, did the electrician fix it?
Also, did you talk to the builder to let him know what the
electrician did?
--David
|
291.597 | Line for 60amp circuit | DATABS::ROYAL | | Thu Jun 06 1991 18:22 | 12 |
|
I need to extend a dedicated 60 amp circuit (2 30amp breakers) for my
dryer. I need to extend the line about 6 feet (hence move the existing
recepticle with it). What I'm planning on doing is simply using a 4"
metal junction box and 6 feet or so of new wire to run from the junction
box to where I want the dryer recepticle to reside. My problem is that
I don't know what kind of wire to buy and I can't find any indication
on the existing line.
Thanks in advance.
-- Phil
|
291.598 | | CSC32::GORTMAKER | Whatsa Gort? | Fri Jun 07 1991 03:18 | 4 |
| The wire is probably either 10/3G or 8/3G the 10/3g is a flat cable
the 8/3g will be round. Hope this helps you identify what you have.
-j
|
291.599 | I may have some. | SMURF::PINARD | | Fri Jun 07 1991 11:56 | 4 |
| 10-3 +G doesn't have to be flat...
I'll check this weekend to see if I have a small piece hanging
around...
Jean
|
291.600 | 220v 30amp | DATABS::ROYAL | | Fri Jun 07 1991 13:21 | 6 |
|
Thanks. Ya, what I hadn't realized is that this line is really a 220
volt 30 amp line, hence 2 30amp breakers are needed. I have some 10-3
plus ground wire hanging around.
-- Phil
|
291.601 | Cu or Al wire? | CXCAD::RSMITH | Randy Smith, CX01-1/Q11, DTN 522-6712 | Wed Jun 12 1991 13:51 | 12 |
|
I realize this message is after the fact, but there are a couple of
points which may not be clear to everyone. Yes, 10 gauge is rated at
30 amps for both Cu and Al. However, there are different rules for
dealing with Cu and Al splices. Cu-Cu splices are made with a wire nut.
Al-Al splices are made with a wire nut and an anti-oxidizing compound.
I don't have my NEC (National Electrical Code) book handy, but I believe
Cu-Al splices with a wire nut are not allowed. It wasn't clear in the
original message whether Cu or Al wire was being used.
-- Randy
|
291.602 | Table 310-16 | WMOIS::BOUDREAU_C | | Wed Jun 12 1991 20:02 | 6 |
| #10 AL may be rated for 30 amps. But if you look at the obelisk
note you will see that the over current protection shall not exceed 25
amperes.
CB
|
291.603 | It's a double breaker, not two singles | POLAR::PENNY | Find me in my field of grass | Wed Jun 12 1991 20:52 | 12 |
| Re: .3
This is a 220 Volt, 30 Amp line, but the "two" breakers should be "ganged"
together at the toggle. (The thing you flip when a breaker trips.) This
is a double breaker, usually riveted together on the body portion.
There should be a steel rod going through both toggles and held in with
a small circlip at each outside edge. This is for safety. ie: When one
"hot" side trips, it mechanically pulls the other hot side off in
conjunction. So, if it trips, it's FULLY tripped off on both busses.
(Red AND Black). 8/3 wire should be used as you're driving a motor, a
resistance heating element, (and a timer). The farther from the main
panel you are, wire guage goes up. 8/3 is sufficient in most homes
unless your run is around 80 or so feet. dep
|
291.604 | note 9, table 310-16 | CXCAD::RSMITH | Randy Smith | Thu Jun 13 1991 13:51 | 10 |
| Re: .5
Yes, Al #10 is initially rated at 25 Amps. But, NEC also says:
"Where the standard ratings and settings of overcurrent devices do not
correspond with the ratings and settings allowed for conductors, the
next higher standard rating and setting shall be permitted."
Since 25 Amp 2 pole breakers are not made and the closest breaker is
30 Amp, then Al #10 can be upgraded to 30 Amp capacity.
-- Randy
|
291.605 | | FLOWER::HILDEBRANT | I'm the NRA | Thu Jun 13 1991 15:49 | 4 |
| Well....I know what the table says,but,I would go with the "lower"
standard rating,not the "higher". Al and Cu just are not the same.
Marc H.
|
291.606 | "I don't have one in the truck" is NO excuse!! | WMOIS::BOUDREAU_C | | Thu Jun 13 1991 20:03 | 7 |
| Randy,
Just because one doesn't carry a 2 pole 25 amp breaker doesn't mean
that it isn't available. They are available. Most electrical
manufactures make them. Not all wholesalers stock them.
CB
|
291.78 | | LEZAH::KILFOYE | | Fri Jun 14 1991 12:24 | 16 |
|
This may have been answered before, but... I would like to convert an
existing two prong receptacle to a three-prong grounded receptacle.
The problem is that wire running from the box is older two-wire romex
cable with no third ground wire. Is it okay for me to simply ground
the receptacle by installing a ground wire from the receptacle to the
metal outlet box? I'm not planning on running new cable from the
circuit breaker box to the outlet, so that's out. If I can't do it
this way, should I just stay with the ungrounded two-prong receptacle?
I also need to install an ceiling fan and I plan to wire it with a
wall switch to a receptable. Once again, there is no third wire at the
receptacle.
Thanks,
Chuck
|
291.79 | Already here | ODIXIE::RAMSEY | Put the Environment First | Fri Jun 14 1991 12:32 | 3 |
| See note 3637 for information about 2-prong to 3 prong upgrade. Last
count had over 45 replies.
|
291.607 | | CXCAD::RSMITH | Randy Smith | Tue Jun 18 1991 14:15 | 5 |
| Re - 9
Oops...my mistake.
-- Randy
|
291.608 | Rough estimate for electrical work | KAHALA::PALUBINSKAS | | Mon Jul 01 1991 14:13 | 5 |
| Need to have approximately 6 electrical wall plugs, 3 ceiling light
fixtures and an 8 foot electric baseboard heater installed in basement.
Could someone give me some type of estimate which I should expect to
pay ? Thanks Janet.
|
291.609 | More information needed | SASE::DUKE | | Wed Jul 10 1991 10:34 | 23 |
|
> Need to have approximately 6 electrical wall plugs, 3 ceiling
> light fixtures and an 8 foot electric baseboard heater
> installed in basement. Could someone give me some type of
> estimate which I should expect to pay ? Thanks Janet.
Not much to go on here. Is the area finished ie dry
wall, trim, paint, etc? If it is, the job is considerably
more difficult and takes much more time and care. Is there
space for new circuits in the existing electrical panel? How
large is the area? How far to the electrical panel? All
three lights on one switch or individual switches? Three way
switches? Is this a DYI job? Lots of this things to be
considered before anyone could make much of a guess.
Not trying to rain on the parade, but more information is
needed.
Regards,
Peter Duke
|
291.610 | | QUARK::LIONEL | Free advice is worth every cent | Wed Jul 10 1991 12:54 | 5 |
| Why not call in an electrician (or three) and ask for an estimate? They're
free. There are too many variables to account for without actually seeing
the job to be done.
Steve
|
291.611 | | EVMS::PAULKM::WEISS | Trade freedom for security-lose both | Wed Jul 17 1991 11:21 | 5 |
| At the request of the author, I moved the note about buying the fixer-upper and
its replies to note 634, which is titled "Should we buy this fixer-upper?"
Paul
[Moderator]
|
291.613 | How do I know wiring is 20 amp v.s. 15 amp?
| NODEX::BRASS | | Mon Jul 22 1991 16:09 | 11 |
| Hi,
I am having trouble running my air conditioner in the upstairs
of my house(condo/townhouse). The upstairs runs on a 15 amp fuse and the
ac draws a lot of power sometimes and blows the fuse. My downstairs runs
on a 20 amp fuse, and I am considering useing a long extension cord or
something to run the ac off the downstairs. How do I know the downstairs wiring
is 20 amp and the previous owner did not just put a 20 amp fuse in place of
a 15. Is it normal to have the upstairs wired 15 amp and the downstairs 20 amp
I would think they would be the same. Also if anyone has any ideas about the
ac problem they would also be apreciated, the ac is a sears 10,500 btu.
Bob
|
291.614 | Don't do it! | ELWOOD::LANE | | Mon Jul 22 1991 16:48 | 9 |
| 15 amp circuits are wired with 14 gauge wire; 20 amp circuits use 12 gauge.
Do _NOT_ run your air conditioner using a long extension cord. It's an
excellent way to burn your house down. There are a lot of reasons why
this won't work and shouldn't be done. The first that comes to mind is
the generally poor connectors the extension cords use. They overheat
under heavy loads.
Mickey.
|
291.615 | | QUARK::LIONEL | Free advice is worth every cent | Mon Jul 22 1991 16:49 | 8 |
| Don't do it. The long extension cord can't handle the power draw.
Anyway, to answer your question, you'd have to look at the size of wire
used for the circuit. If it's 14-guage, it's a 15-amp maximum circuit.
If it's 12-guage, 20 amps is allowed. You may be able to see the size
stamped on the sheath of the cable as it enters the fuse box.
Steve
|
291.616 | | GIAMEM::S_JOHNSON | Ban all guns | Mon Jul 22 1991 17:15 | 8 |
| If it's a 15 amp circuit and the AC keeps blowing fuses, try a 15 amp
slo-blo fuse. They're designed to withstand the tempoarary surge in current
when a motor kicks in (in your case, the AC's compressor)
My Panasonic 8000 BTU does the same thing, when plugged into a 15 amp 110 volt
circuit.
Steve
|
291.617 | What does NEC say about wire size within circuits | SEURAT::NEWMAN | Chuck Newman, 297-5499, MRO4-1/H16, Pole J13 | Mon Jul 22 1991 17:33 | 25 |
291.618 | Extension cord idea is out :-( | NODEX::BRASS | | Mon Jul 22 1991 17:40 | 10 |
| Thats a bummer about the extension, I thought those big long orange extensions
were suppose to be able to handle a lot of power, but I am NOT going to take the
chance with my house.
I tried the slow blow fuse idea last year and still blew the fuse. Do they
have different types of slow blow fuses, maybe some slower than others?
For now I run the ac through a power strip with its own 15 amp circuit breaker
that saves on fuses and trips down stairs to change them :-)
Bob
|
291.619 | | FSDB45::FEINSMITH | Politically Incorrect And Proud Of It | Mon Jul 22 1991 17:49 | 16 |
| RE: .4, the SMALLEST guarge wiring in a run is what the fuse/cb is
sized to. Generally, the inspectors will not OK a mixture of wire and
of you had a 12/14/12 which was protected by a 20 A fuse, its plain
dangerous and illegal.
RE: .5, perhaps you have something on that circuit besides the A.C.
I don't know what your 8000 BTU machine draws, but a 9500 in my shop is
rated 12 amps. First see what else in on the circuit. If nothing is on
it, you might want to check the connections at each outlet on the
string. Often, electricians use the push in terminals at the outlets.
These may loosen with time, causing a voltage drop. You also might want
to meter the circuit with the a/c compressor kicks in, to see what the
voltage drop is. A final possibility is a defect in the a/c itself
causing it to draw too much current.
Eric
|
291.620 | | QUARK::LIONEL | Free advice is worth every cent | Mon Jul 22 1991 18:09 | 9 |
| My bedroom AC unit is 8000BTU and it is on a 15A circuit. The lights dim
when the compressor kicks in, but I've only blown the fuse once and
I think I had some other things going on that circuit. Still, at 8 amps or
more, you're better off if you can put it on a legitimate 20A circuit.
Another thing you might try is the screw-in circuit breakers that
replace the fuse. They seem to be more tolerant of surges.
Steve
|
291.621 | Put in a dedicated circuit | VMSDEV::HAMMOND | Charlie Hammond -- ZKO3-04/S23 -- dtn 381-2684 | Mon Jul 22 1991 18:58 | 8 |
| The best thing to do is to install a dedicated, 20Amp circuit for
your air conditioner. The most difficult part of this is finding
a way to get the wire from the fuse or circuit breaker box to the
location of the air conditioner. If you'd be willing to run a
small conduit up the outside of the building even this would be
fairly easy. An experienced electrician should be able to do this
in two or three hours maximum. (Of course, there could be
difficulties that I'm not anticipating.)
|
291.622 | | CHIEFF::MACNEAL | ruck `n' roll | Mon Jul 22 1991 19:16 | 3 |
| Have they stopped selling those heavy gray extension cords designed for
appliance useage? Finding one long enough to go to the first floor
might be a problem.
|
291.623 | | QUARK::LIONEL | Free advice is worth every cent | Mon Jul 22 1991 19:25 | 6 |
| Re: .9
They still sell them, but they tend to be 3 feet long. I have seen
14-gauge 50-foot cords, but I would not recommend running an AC from one.
Steve
|
291.624 | while we're on the subject of a dedicated circut... | SNAX::HURWITZ | | Mon Jul 22 1991 23:19 | 7 |
| Anyone have a guess as to how much a dedicated circut/outlet for an
8amp AC would cost to have put in. The main box in the basement is
probably 25' from where the line would enter the floor above. Looks
like it would be easy but I don't have the know how to wire it into the
big box?
Steve.......
|
291.625 | It isn't enough for wiring to be safe when installed | RGB::SEILER | Larry Seiler | Tue Jul 23 1991 16:12 | 20 |
| I've heard it said that one should *never* use 12-gauge wire on a 15amp
circuit, for precisely the reason cited in .4. Someone (including the
original installer) can come along years later, see a 15A fuse/breaker
attached to 12 gauge wire, and conclude that it's safe to upgrade to a
20A fuse/breaker, not knowing (or unable to discover) that there's a
piece of 14 gauge wire hidden in a wall somewhere in the circuit.
We tend to concentrate on the problem of installing wiring that is safe.
A far tougher problem is installing wiring that will *stay* safe through
decades of use and modification. Part of staying safe is doing things in
such a way that it's easy to tell whether one is doing the right thing.
Consistency, such as using consistent wiring sizes, helps a lot.
Of course, it would be long-term safe to use a 15A breaker if *all* of the
wiring on the circuit is 12 gauge. But in that case, why not just use a
20A breaker? And if the reason to use 12 gauge is because of voltage drop
in a big house, it might be a better solution to put in a subpanel.
Enjoy,
Larry
|
291.626 | | KAOFS::S_BROOK | The U word makes me c-sick! | Tue Jul 23 1991 20:27 | 9 |
| On the other hand, my training tells me that if a circuit is
installed with a 15A breaker, then it should remain that way,
even with 12 ga wire, because there is something in that circuit
with a 15 amp rating. Only if I can trace the entire circuit and
be satisfied that it qualifies for 20A should the breaker be
upgraded. It would make far more sense if the codes were written
that way instead of the more illogically restrictive way they are now.
Stuart
|
291.860 | 220V/120V lines with 3-wire SE cable | LANDO::DROBNER | VAX 6000-500 Systems Engineering | Thu Sep 05 1991 14:13 | 39 |
| This topic seems to be a appropriate place for this;
I am looking for some advice on specific code requirements -
I am doing some bathroom remodeling (new window, tile floor, etc) and
adding a whole house attic fan.
I need to get power to the fan (120V at 8Amps steady on high).
I have a unused piece of wire that currently runs from the circuit breaker
box located in the basement to the bathroom upstairs. This wire is currently
not USED - it is not connected in the CB box and ends in a junction box in
the bath. This wire is 6/2 with a bare GND, AL, SE (service entrance cable).
Now you may think that this is pretty strange!! - It was going to be used to
power a sauna heater in the bathroom which was never installed.
So what I would like to do is add another piece of wire from the junction
box in the bath up to the attic.
Now come the questions -
1) Do I run this as 240V line from CB box - and in the attic add a sub-panel
and pull 120V off of one side.
I think I can NOT do this since I only have 2 Hots and a GND, I
am missing the neutral wire. (SE cable is 3 wire - to do this I
would need 4 wire cable - 2 Hots, 1 neutral, and GND.
2) Do I run this as a 120V line from CB box - (on a 20AMP breaker)?
Need to mark the end of the cable to white from black or red
that is in the CB box.
3) If I do run this as a 120V line can I change the wire size at the junction
box in the bathroom to 12 gauge (with appropriate AL-CU cable connectors).
I think this is also NOT allowed.
Thanks/Howard
|
291.861 | not aluminum!!! | SALISH::ROBERTS_JO | Life IS fair in the Pacific NW. | Fri Sep 06 1991 12:10 | 13 |
| When you use the term AL do you mean you have aluminum wire? If so, I
would try to get power from somewhere else. The aluminum expands and
contracts and over time has a loose connection with more resistance
creating heat and poor connections and more resistance and more heat
and...get the picture? It can burn you.
If you do use it, just get some white tape to put on the red wire. Now
you have a black - hot, white - neutral, and bare - ground. If you must
splice to make the wire reach, better use more aluminum. And make sure
you have a good tight connection - and check it in a year or so and
tighten it up again. If you connect copper with the aluminum, buy some
good insurance.
|
291.862 | | WLDBIL::KILGORE | Digital had it Then! | Fri Sep 06 1991 13:15 | 6 |
|
re .25:
You should stop at point 1. With no neutral, there's no acceptable
way to tap 120 off the feed.
|
291.349 | Change two prong to three prong outlets | NODEX::BRASS | | Tue Nov 12 1991 14:08 | 5 |
| HI,
I want to change my outlets, I have the old two prong and they have
a ground wire connected to the box. Can I just connect the ground to the outlet?
Thanks
Bob
|
291.350 | | BGTWIN::dehahn | Ninety eight...don't be late | Tue Nov 12 1991 16:14 | 8 |
|
No.
You must bond the box, ground wire, and ground terminal on the outlet together
using a wire nut. The metal box will have a tapped hole which you can use for
its ground lead.
CdH
|
291.627 | So I WAS right... | JUNCO::CASSIDY | Mission: Repair with care. | Sat Jan 04 1992 02:29 | 11 |
|
All this talk about "black tape on the white wire" got me to
believing my electrical shop teachers had misguided me. They
never mentioned this because we always used Romex and were in-
deed following code. My intention was not to cause people to
lash out in response for my 'supposed' misinformation.
Many thanks to those who helped clarify this... and prove
me right. ;^)
Tim
|
291.1021 | What size circuit? | NICCTR::MILLS | | Fri Jan 24 1992 02:11 | 40 |
| This is the closest note I've seen on the subject I'm interested in.
I've done ton's of DIY wiring and I'm pretty proud and pretty sure I've
done it right. I've had the same problem as the base note and I think
it was good advise.
My problem is this. I'm trying to install a large backup electric
heater for a oil furnace that is not always dependable. I wanted to
stick with something that was under 20amps if possible. Because of
cost. I Looked through one brochure and they seemed to go from #14 wire
recommended to #10 (and skipped #12). But that made sense since no AMP
ratings were in the 12-18 amp range. Another brochure listed a portable
that pulled 16.67amps @240v that specfied the 20 amp outlet (the kind with
one blade that goes across but 240v) but did not specify wire gauge.
I also found another brochure that listed a 16.67 amp unit. I figured
that this was a magic number (as high a powered unit you can fit on a
20 amp circuit). I'm getting their keep reading :-). Finally I decided
on a unit that listed it at 16.67 amps and recommened #10 wire. I
assumed the #10 was a misprint (in brochure) and when I received the
unit the specs say #10 wire but do not specify how many amps (except in
brochure, maybe 16.67 was a misprint?).
I've always assumed (for both 120v or 240v 2 wire or 3 wire) that
#14 for 15amp circuits
#12 for 20amp circuits
#10 for 30amp circuits
If it draws 16.67 (@240v) why do they spec #10 wire. If you had to wire
a 240 16.67amp load circuit what wire do think would be needed? I've
always used 10-3 for 30amp!! 240v dryers. I don't think it's to handle a
surge since heating elements come up smooth and the motor is very
small. Should I use 10-2 and 30amp breaker or 12-2 and 20amp breaker. I
also had to buy contact relays (for low voltage control) which are
pretty expensive for higher amperage (20 going to 30). I beleive there
is a rule that says your load should not exceed ~85% (not sure on
exact number) of a circuit. 16.67 amps comes out to 83% of 20amps. So
20 amps seems to make sense. But using #10-2 on 20amp breaker doesn't
make sense to me. The unit is 4000watts @240v which can be coverted to
amps but I forget how.
|
291.1022 | #10 vs. #12 | RGB::SEILER | Larry Seiler | Fri Jan 24 1992 15:57 | 25 |
| My best understanding is:
You don't need to use #10 wire to a 20A outlet.
So if it can plug into a 20A outlet, you can use #12 wire.
But heater loads are supposed to be only 80% of max rating.
So if it really draws >16A, why does it have a 20A plug?
My guess would be that #10 is recommended because it will have less
voltage drop than #12 -- and for >16A of current, that's a consideration.
However, I just got my garage inspected, and all of my electric baseboard
heaters use #12 wire. Of course, none of the circuits exceed 16A, which
is about 15 feet of baseboard heater. I'm thinking of putting 16' of
heater on some of the circuits, but that isn't the way I've got it set
up now. I'll only turn them on when I'm working out there in the winter,
and that's not going to be very often.
Luck,
Larry
PS -- Watts divided by Volts equals Amps: 4000/240 = 16.67A. Of course,
the line voltage may be more or less than 240V...
|
291.1023 | So 80% is the number | NICCTR::MILLS | | Sun Jan 26 1992 03:21 | 20 |
| Thanks for your excellent reply.
When you say "voltage drop is a consideration" do you mean efficientcy
or danger.
The number 80 something always stuck in my head. So you say it's 80,
Is that code? Hmmmm 80% applys to just heaters?
I called the manufacturer and they said #10 and 20 amp breaker.
I called an electric supply house and asked them what I needed #12 and 20amp
I called mass electric and they asked an electrician and said #12 and 20amp
I was going to go with #12 until I read your reply and stated the 80%
figure. I guess I'm right on the edge and different people have
different opinions. Another reason why I don't like using #10 is it
"labels" the line as 30amp. In 10 years when I'm gone somebody will
probably try to plug a dryer in it.
Does the 80% apply to the wire or breaker or both? In other words
should I use 25-30amp breaker since I exceed 80% of 20amps.
|
291.1024 | 16 is a "magic" number | REGENT::GETTYS | Bob Gettys N1BRM 235-8285 | Sun Jan 26 1992 15:02 | 31 |
| The radio club that I belong to just had some new wiring
added for a linear (power amp) at the town CD headquarters and
the job of deciding exactely what to do and babysitting the
electrician while it was done fell to me. What we ended up with
is three long 20 amp 120v circuits running from the emergency
generators main panel back to the room. The electrician had some
interesting info - some of which I knew without knowing I did -
some nice to know. One piece was the 16 amps as the max steady
load on a 20 amp circuit. The other was using #10 for a long run
on a 20 amp circuit (these runs were about 150 feet!). Something
else - one of the circuits was outfitted for a twist lock
recptacle which is a 30 amp receptacle. This became legal
because of the use of #10 wire which is the minimum for a 30 amp
circuit. (We wanted the circuit to be dedicated and unusable for
anything else!) The only 20 amp item on the circuit is the
breaker itself. (Dictated by the fact that there wasn't a 30 amp
one available - old and non-standard boxes cause problems!)
In the process of doing this - it was discovered that
the current wiring to the CD rooms was done incorrectly. I'm
sure we all know the trick of running a pair of 120v circuits
with three wires (two hots and a neutral) by using the opposite
sides of the distibution (the current in the neutral will be
the current drawn by one side minus the current drawn by the
other). This had been wired that way but the hots were BOTH
taken from the same side of the distribution! Now if the two
circuits had full current drawn the neutral would be carrying
TWICE its rated current!!! And this was supposedly installed by
competent electricians!!!!!!
/s/ Bob
|
291.1025 | some of them just don't check.... | TLE::MCCARTHY | DECTPU | Sun Jan 26 1992 16:06 | 16 |
| >> other). This had been wired that way but the hots were BOTH
>> taken from the same side of the distribution! Now if the two
was most likly caused by:
>> one available - old and non-standard boxes cause problems!)
It was most likly assumed that every-other spot was on a different leg of the
220 service. When dealing with older boxes that assumption is not always true.
Fuse style panels led themselves to this type of error very easily. The old
Federal Pacific had SEVERAL different styles of plug in modules, you had to
make sure were were on different legs of the service.
bjm
|
291.628 | Electrified plumbing | CUPMK::PHILBROOK | Customer Publications Consulting | Tue Jan 28 1992 18:37 | 23 |
| I'm experiencing what I believe to be a very unique problem, that's why
I started a new note.
As of this morning we seem to have an electrified tub faucet. We have a
Symmons Temptrol unit and the lever that controls the tub/shower flow
is electrified when the water is on and I'm standing in the tub. When
the water is off, no problem. When the water is on and I'm not standing
in the tub, no problem.
I'm not talking a simple case of static electricity build-up here, this
thing is truly electrified -- serious voltage! I'm not the least bit
handy and know nothing about electricity short of it being the stuff
that makes lights go on. I've checked the water pipes in the basement
and behind the tub wall and there are no electrical wires touching the
pipes.
Last night the motor in our furnace blew. They oil company came by and
replaced the motor but that's the extent of recent electrical work --
with the exception of the installation of a new water heater back on
November 12th. Any ideas? I'm shocked!
Thanks,
Mike
|
291.629 | | FLOWER::HILDEBRANT | I'm the NRA | Tue Jan 28 1992 18:58 | 6 |
| Any idea of the voltage present? Do you have a VOM to measure, say
from the water to ground?
Maybe a problem in the water heater with a defective element?
Marc H.
|
291.630 | | CUPMK::PHILBROOK | Customer Publications Consulting | Tue Jan 28 1992 19:01 | 9 |
| No, no idea -- I don't have a voltage meter.
If it's the water heater, why is the problem only with the tub and not
the bathroom and kitchen sinks?
Is this a job for a plumber or an electrician?
Thanks,
Mike
|
291.631 | | CSC32::S_MAUFE | hottub and chains weather | Tue Jan 28 1992 19:05 | 8 |
|
perhaps you have a leak to ground and the other sinks etc are connected
via plastic pipe?
I'd put a meter on the electrified spot and start pulling the plugs of
appliances until the electric goes away.
Simon
|
291.632 | | CUPMK::PHILBROOK | Customer Publications Consulting | Tue Jan 28 1992 19:44 | 9 |
| I called the water company and they suggested it was a grounding
problem. Next I called an electrician and they suggested a grounding
problem as well. They also suggested that the motor going on my furnace
may have been linked to this problem (the furnace is only 6 years old
so it's unlikely the motor would burn out that soon).
At $45/hour, an electrician is on his way. Oy vey!
Mike
|
291.633 | | RAMBLR::MORONEY | Is the electric chair UL approved? | Tue Jan 28 1992 20:38 | 6 |
| I'd guess a grounding problem as well, or an open neutral.
Question: Do your lights dim when a major appliance (fridge, furnace) kicks
in? Do any lights get _brighter_ when a major appliance kicks in?
-Mike
|
291.634 | Just curious. | WMOIS::BOUDREAU_C | | Tue Jan 28 1992 22:07 | 5 |
| RE.4
At $45/HR did you get one electrician or one electrician and an
apprentice??
|
291.635 | solved | CUPMK::PHILBROOK | Customer Publications Consulting | Tue Jan 28 1992 22:10 | 22 |
| Well, $67.00 later, the mystery is solved.
It was a grounding problem. A rather bizzarre turn of events, however.
Turns out the furnace, which the former owners of the house had
installed 7 years ago, was never grounded. The copper pipe supplying
the oil feed to the furnace runs under the cement basement floor over
to the oil tank. The oil tank's filler pipe was touching the sewer pipe
which in turn was feeding back to the bathtub's drain pipe. As a result
of the furnace being ungrounded, and the whole system coming in contact
with the water pipes, the copper drain pipe on the tub was charged with
120 volts! The electrician said that if there weren't as much PVC on
the tub's assembly as there is, we could likely have been electrocuted!
So, the problem was patched by installing a grounding clip and copper
wire between the copper water pipe and the copper waste pipe on the
tub.
Now we have to prepare to shell out major bucks to have the service
upgraded to 100 amps and have everything in the house grounded.
Thanks for all the tips.
Mike
|
291.636 | | CUPMK::PHILBROOK | Customer Publications Consulting | Tue Jan 28 1992 22:11 | 4 |
| >Question: Do your lights dim when a major appliance (fridge, furnace) kicks
>in? Do any lights get _brighter_ when a major appliance kicks in?
Yup.
|
291.637 | | CUPMK::PHILBROOK | Customer Publications Consulting | Tue Jan 28 1992 22:13 | 9 |
| > At $45/HR did you get one electrician or one electrician and an
>apprentice??
It was one guy -- it was quoted at $45 because it was technically after
hours. He ended up charging me $60 for 90 minutes work plus about $7 for
parts. 90% of the time he spent here was just investigating and trying
to track down the problem.
Mike
|
291.638 | had the same problem | RAMBLR::MORONEY | Is the electric chair UL approved? | Tue Jan 28 1992 22:24 | 19 |
| re .8:
>>Question: Do your lights dim when a major appliance (fridge, furnace) kicks
>>in? Do any lights get _brighter_ when a major appliance kicks in?
>
> Yup.
It looks like you have an open neutral. The neutral wire is supposed to carry
the difference in current between the hot legs back to the pole transformer.
If the neutral line is open (broken) the current flows through whatever
ground it finds through the ground to the ground stake at the pole transformer.
The "good" news is, depending on where the break is, it might be the electric
company's problem and they'll fix it for nothing.
I'm suprised the electricians didn't spot this. The ground clamp just treats
a symptom, you still have a problem.
-Mike
|
291.639 | | KAOFS::S_BROOK | | Wed Jan 29 1992 12:52 | 13 |
| There is definitely still a problem that has now been masked. An
open ground on something like the furnace should NOT have made the
furnace electrically hot. The ground is there for safety to take
fault currents to ground instead of through you! Yes there are
some induced charges possible on the furnace, but not sufficient to
give you a shock.
Now there is a fault current running permanently to ground and which
you are possibly paying for. A lifted neutral may or may not cause
the problems you experienced. It sounds like this electrician did
half a job.
Stuart
|
291.640 | | 6602::MACNEAL | ruck `n' roll | Wed Jan 29 1992 13:11 | 5 |
291.641 | | CUPMK::PHILBROOK | Customer Publications Consulting | Wed Jan 29 1992 13:20 | 29 |
| >It looks like you have an open neutral. The neutral wire is supposed to
The electrician mentioned that we have only a grounded neutral, but
nothing else. He also remarked that he was hoping it was a PSNH problem
so that I wouldn't have to pay anything, but apparently it was not. The
thing that disturbed me was he had to call to the main office to check
on something twice -- seems he didn't quite know how to take care of the
problem himself...
>The "good" news is, depending on where the break is, it might be the
>electric company's problem and they'll fix it for nothing.
So should I call PSNH? What do I tell them? I don't speak electricity
very fluently...
>I'm suprised the electricians didn't spot this. The ground clamp just
>treats a symptom, you still have a problem.
Yes, he said it was just a patch and that we really needed to ground
the furnace and the rest of the house. He could have grounded the
furnace for me but he didn't have the right size wire in the truck! So
he went on his merry way. Am I still dealing with a potential problem
here that could be risky and dangerous?
This was Stellos Electric, by the way, a rather reputable firm in the
Nashua area. Although, the guy was pretty young and a little cautious.
Thanks for all the help.
Mike
|
291.642 | | CUPMK::PHILBROOK | Customer Publications Consulting | Wed Jan 29 1992 13:21 | 6 |
| > If you're going for the upgrade, spend a little more and go to 200
>amps.
Isn't this overkill for a 5-room ranch? (No garage, either).
Mike
|
291.643 | | CUPMK::PHILBROOK | Customer Publications Consulting | Wed Jan 29 1992 13:24 | 14 |
| > Now there is a fault current running permanently to ground and which
>you are possibly paying for.
What do you mean I'm paying for a ground?
>A lifted neutral may or may not cause the problems you experienced.
>It sounds like this electrician did half a job.
So, should I call the main office back and argue? I have no concept of
what he might have done right and what he might have done wrong, or
what he should have done instead.
Thanks,
Mike
|
291.644 | | 6602::MACNEAL | ruck `n' roll | Wed Jan 29 1992 13:47 | 16 |
291.645 | | CUPMK::PHILBROOK | Customer Publications Consulting | Wed Jan 29 1992 14:01 | 17 |
| > Depends on what kind of toys you're running. If you have a workshop
>with table saws and the like, a kitchen with a microwave oven and small
>appliances, an airconditioner or two, TV/stereo/VCR/etc., electric
>dryer, electric hot water heater, electric stove, the power
With the exception of the workshop power tools, we have all that stuff.
>I opted for the 200 amp service when I upgraded mine from 60 amps. My
Can you give me a ballpark for the cost of doing this? I have no
concept of what this might cost. Is it closer to $1000 or $5000?
Maybe we would be better off with 200. Thanks for giving me something
to think about.
Mike
|
291.646 | | KAOFS::S_BROOK | | Wed Jan 29 1992 14:32 | 19 |
| re .15
What I meant was that if there is a leakage fault somewhere that
electrified the metalwork of your furnace and through other contacts,
your waste stack, there was negligible current flowing. Now that it
has been grounded, there is likely a current flowing to ground that
is consuming power that you'll be paying for.
If the problem really is a floating neutral then this is not the same,
but on the other hand, I would not normally expect the difference
between neutral and ground even with a floating neutral to be
sufficient to give you a shock -- a tingle yes, a shock no. In this
case though, you wouldn't be paying for leaked power.
Unfortunately, if you have a house with ungrounded wiring, the only
way to ensure safety and fix problems like this is to get the house
rewired. Mega $ I'm afraid!
Stuart
|
291.647 | | RAMBLR::MORONEY | Is the electric chair UL approved? | Wed Jan 29 1992 14:39 | 37 |
| re .13:
> >The "good" news is, depending on where the break is, it might be the
> >electric company's problem and they'll fix it for nothing.
>
> So should I call PSNH? What do I tell them? I don't speak electricity
> very fluently...
Tell them that you believe the neutral feed to your house may be broken,
or you have an open neutral, describe how lights get dim and others get
brighter when the refrigerator kicks in, describe the "shocking" experience
in the tub, tell them you had an electrician over and what he did and you
don't think he actually fixed the problem. I don't know what PSNH will do
if they determine the problem is not with their wiring, nor do I know exactly
where their responsibility ends (probably "their" side of the meter box).
You may want to look at the electrical feed to your house. You may not be
able to spot anything but then again it might be something obvious, a broken
wire. Look where the wires attach to your house, look where it attaches to
the pole. If you have the type of wire where there are 2 black wires wrapped
around an aluminum bare wire, look at the connections to the bare wire.
> nothing else. He also remarked that he was hoping it was a PSNH problem
> so that I wouldn't have to pay anything, but apparently it was not.
If he found the problem, he should have either fixed it then, or at least told
you what and where the exact problem is and tried to schedule a fix if he
didn't have the wiring/parts, or called PSNH if he determined it was PSNH's
problem.
While you need a good ground, you really need to get the neutral fixed.
You could always bite the bullet and get the service upgrade now, since when
the feed to your house, the meter, service entrance feed and fusebox are
replaced, the problem will be fixed since it's in there somewhere.
-Mike
|
291.648 | | KAOFS::S_BROOK | | Wed Jan 29 1992 14:42 | 12 |
| Having read back through these notes, since the problem was the
connection through the pipes to the bath waste from the furnace, and
the furnace was recently worked on AND the problem appears to have
started with the replacement of the furnace motor ...
I would say quite categorically that there is something wrong with
either the furnace motor, or its installation. A floating neutral
should not ever put 120 Volts between local neutral and ground, except
in nearly no load conditions ... ie no electrical appliances working.
And if it did, you'd likely be blowing electrical equipment like crazy.
Stuart
|
291.649 | | KEYBDS::HASTINGS | | Wed Jan 29 1992 15:02 | 44 |
| I'd suggest popping into an electrical supply or good hardware store.
You can pick up a socket tester. This is a device with three prongs and
three lights that you plug into an electrical outlet. Depending on the
condition of the socket different lights will light up. This is a very
fast and easy way to check your house electric system.
If my house had bad grounds, as this device will tell you, I would be
concerned about the saftey of anyone operating any device plugged into
any of the defective sockets. BTW this device goes for around $5.
Getting Technical -
(I am NOT an electrician - treat the following accordingly!)
There shoud be three wires in your house electric system. One is the
hot wire and supplies the electricity, the other two are Neutral and
Ground. The Neutral is sort of a return path for the electricity and is
grounded by the power company. The Ground wire is a wire literally to
the ground at your house. This is often accomplished by driving a
copper stake into the ground next to your house (usually near the power
meter) and attaching the house ground to it.
There is an important difference between Neutral and Ground.
Despite the fact that they are both "grounded" they are grounded in
different places. This can cause a potential difference between them.
As a safety measure most appliances and tools have their outermost
cases and parts connected to Ground. This way no matter what happens
inside the appliance/tool you won't get zapped.
if an appliance is not grounded properly, ie: someone breaks off
that pesky third prong, you might get a potential difference between
the case of the appliance and a true ground. We once had a refirgerator
that did this. If you touched the metal trim on the refrigerator whil
touching the stainless steel sink you would get a bit of a tingle. The
best I can describe this is that the metal felt "fuzzy" is you stroked
it lightly. This condition was caused by a "ground loop", of difference
between the Neutral onthe refrigerator and Ground that natrually
existed in the copper pipe plumbed sink.
To sum this all up:
The hot wire is there to provide you electricity
Neutral is there to complete the circuit.
Ground is there to protect you.
Mark
|
291.650 | | 6602::MACNEAL | ruck `n' roll | Wed Jan 29 1992 15:07 | 4 |
291.651 | | RAMBLR::MORONEY | Is the electric chair UL approved? | Wed Jan 29 1992 15:07 | 29 |
| re .20:
> I would say quite categorically that there is something wrong with
> either the furnace motor, or its installation. A floating neutral
> should not ever put 120 Volts between local neutral and ground, except
> in nearly no load conditions ... ie no electrical appliances working.
> And if it did, you'd likely be blowing electrical equipment like crazy.
Not necessarily. It may be that the old furnace was grounded better than
the new one, replacing it revealed the problem. By grounded I mean the
ground wire to the box *and* a ground to earth (through the water pipes?).
If you have an open neutral and a bad ground you *will* see a voltage between
neutral and ground. It won't be 120 volts but it can be noticeable.
My own case is a good example. I had an open neutral (in the box), and
I noticed some serious blinking when the furnace kicked in. Investigation
showed a 10-15 volt spike between neutral and a water pipe when the furnace
kicked in. But the neutral was grounded directly to a water pipe, supposedly.
Connecting a temporary wire to a good ground and running it along the "ground"
wire revealed sparks!. It turns out that from moisture and carrying current
for nn years caused the ground clamp to corrode where it attached to the pipe,
and if I had almost everything in the house off, except a 120 volt heater, a
piece of corroded wire at the clamp would glow red!! In this case the current
path for almost 15 amps was from hot through the heater, to neutral back to the
box, through the ground wire to clamp to water pipe.
Needless to say, I took care of this.
-Mike
|
291.652 | | KEYBDS::HASTINGS | | Wed Jan 29 1992 16:28 | 28 |
| re: .22
Yes, older homes do not have the ground wire. That is why I said
*should* instead of "would". You will be much safer to get rewired. But
how much safer depends on the appliances that you are using. Many have
plastic housings, (hair dryers, some electric tools, etc...) and pose a
minimal risk. You can further reduce your risk by doing common sense
things like not standing in water when you use and electrical
appliance.
One other risk of 2-wire houses is to your electronics. If you have
been wise enough to buy a surge/spike protector for your computer of
whatever, the protection will be eliminated if the ground is not there.
Since one furnace motor burned out prematurely I would be concerned
that it would happen again until the real problem was solved. If your
Neutral is floating and the motor is completing it's circuit through
the ground, you may have a resultant low voltage condition on the
motor, as well as other appliances in the house. This condition may not
be severe enough to prevent "normal" operation, but it will drastically
shorten the life of electric motors.
Fortunately this is easy to check. Simply place a meter on the
input electrical lines to the furnace motor and verify the proper
operating voltage there. If this condition that I have suggested here
is present, instead of seeing an A/C voltage of 110-120v you might see
90v or so.
Mark
|
291.653 | | KEYBDS::HASTINGS | | Wed Jan 29 1992 16:30 | 7 |
| after I entered my last reply I realized that I had left one other
thing out.
A bad Neutral might also cause and *over* voltage on your electrical
equipment. (Also not good!)
|
291.654 | | CUPMK::PHILBROOK | Customer Publications Consulting | Wed Jan 29 1992 18:04 | 38 |
| I spoke with PSNH who advised I call back Stellos and chat with a
Supervisor. I did and he assured me that everything was done properly
and safely and he's offered to have the city inspector come out to look
things over and put my mind at ease. Apparently the electrician who
came to my house last night is one of Stellos' top foremen. He said
the neutral in the house is properly grounded. Of course, my lack of
education in the arena of electricity leads me to misinterpret things
and after the feedback I got here and what PSNH told me, I've been
quite concerned. But I now feel a lot better.
Before he has the inspector come out, however, he's going to talk with
the guy who did the work and make sure everything's looking good. I
obviously want to be sure the entire system is safe, but I don't want a
city inspector condemning my house, either.
He told me we should upgrade to 150 amps and that will cost somewhere
around $800.00 excluding any extras like installing additional outlets
and fixtures and grounding appliances which may not already be
grounded. So, we're going to start saving our pennies.
The one thing the supervisor felt should be done that they will come
back out to do is to ground the furnace to the electrical box. Once
that's done, he feels everything will be perfectly safe. We're
operating under the assumption, for the time being, that all the major
appliances are properly grounded because the former owners had the
kitchen remodeled 6 or 7 years ago and would have had to get all the
new appliances hooked up properly and inspected. Considering that we
have an electric water heater, electric dryer, dishwasher,
refrigerator, furnace, and so on, there's got to be 220 in the house
and it has to be properly wired.
Thank you very much to all who helped me here and offline. I appreciate
all the time you all took to coach me on this. I hope to be back here
one day soon giving advice to others about upgrading electrical
service!
Cheers,
Mike
|
291.655 | | VERGA::WELLCOME | Steve Wellcome (Maynard) | Wed Jan 29 1992 18:26 | 7 |
| Don't bother with 150 amps - go to 200. The incremental cost should
be minimal. A 150 amp service entrance is an oddball - hardly
anybody uses it. A friend of mine installed one in his house, and
has ever since wondered why he chose it over the more standard 200.
(Not that a 150 amp service entrance will be any problem, if you
choose it, but I can't think of any compelling reason why you'd
want to.)
|
291.656 | | MANTHN::EDD | Press END or pay! {argh} | Wed Jan 29 1992 18:28 | 5 |
| You may want to shop that service upgrade gig around to a few
electricians. I've recently obtained estimates for a service upgrade
ranging from $350 to $550...
Edd
|
291.657 | Miswired furnace motor? | HDECAD::THOMAS | Stop, look and listen | Wed Jan 29 1992 18:47 | 5 |
| Seems to me the oil company miswired the motor when they replaced it.
I'd bet they connected one side of the motor to furnace ground instead
of the neutral return wire.
Everything was fine 'till they changed the motor, right?
|
291.658 | | KAOFS::S_BROOK | | Wed Jan 29 1992 19:15 | 21 |
| re .29
Exactly my point.
Also a floating neutral would have given a small voltage ground to
neutral not the 120V that the electrician implied!
If the electrician reckons the neutral is NOT floating, then there
is definitely something wrong with your furnace motor!
Even on an ungrounded piece of electrical equipment, you should not
get more than a stray electromagnetically induced charge. That would
dissipate the moment the electricial tried to measure it. If there
was a voltage on the furnace / bathtub, there is something wrong
with the furnace.
Simple
Stuart
|
291.659 | | CUPMK::PHILBROOK | Customer Publications Consulting | Wed Jan 29 1992 19:19 | 16 |
| > Seems to me the oil company miswired the motor when they replaced it.
>I'd bet they connected one side of the motor to furnace ground instead
>of the neutral return wire.
That's a possibility. The electrician checked all the furnace wiring,
however, and aside from the furnace not being grounded, he said
everything was fine.
>Everything was fine 'till they changed the motor, right?
True. I'm going to ask the electrician if there's a possibility the
motor was installed improperly and if so I'll go back to the oil
company and get them to pay the electrician's bill!
Thanks,
Mike
|
291.660 | ex | KAOFS::S_BROOK | | Wed Jan 29 1992 19:20 | 2 |
| Or maybe it was a faulty motor ...
|
291.661 | | CUPMK::PHILBROOK | Customer Publications Consulting | Wed Jan 29 1992 19:21 | 11 |
| > You may want to shop that service upgrade gig around to a few
>electricians. I've recently obtained estimates for a service upgrade
>ranging from $350 to $550...
Are those reputable, licensed electrician's estimates? The last thing I
need is to get an amateur in here, save a few bucks, and end up with a
sub-standard job. After what we've been through this week, I'd be more
comfortable paying top price for top quality.
Thanks,
Mike
|
291.662 | | MANTHN::EDD | Press END or pay! {argh} | Wed Jan 29 1992 19:25 | 5 |
| > licensed, reputable...?
Yep.
Edd
|
291.663 | Don't assume anything | 6602::MACNEAL | ruck `n' roll | Wed Jan 29 1992 19:46 | 14 |
291.664 | | 6602::MACNEAL | ruck `n' roll | Wed Jan 29 1992 19:48 | 6 |
291.665 | kinda | NICCTR::MILLS | | Wed Jan 29 1992 20:08 | 8 |
| Polarized plugs are not to prevent housing from being hot. Neither side
should go to the housing (just ground if it's 3 wire) and nothing if
it's 2 wire. It is however safer for lamps and such because the hot
will be switched instead of neutral and thereby prevent a jolt when
changing a bulb (no hot socket).
I think polarized plugs take care of interference (or other) problems in
electronic equipment also.
|
291.666 | Another zap | NICCTR::MILLS | | Wed Jan 29 1992 20:31 | 26 |
| Note, there are to many replies to this note and I don't have
time to read them all. But.
I had a related problem recently. My wife said she was getting a jolt
from a switch box. I kinda ignored it thinking it was static. But she
persisted. So I checked it out. I put a load (coil type) tester on it
(between ground mount plate of each switch) and got nothing but the
neon bulb in the tester did flash. I touched each switch and got zapped
(sorta line a phone wire zap). I put my multi meter on it (essentually
no load) and got 82volts !!!. So I took the box apart and low a behold
the "certified" electrian wired both grounds from the two leads coming
in independently to each switch ground !!!. All grounds should be tied
together otherwise you can get a potential between grounds. Even
moisture can case a hot lead to leak to the ground wire. If it's truely
ground it will sink it. The leak (where ever it was) was so small it
could supply enough volts to jolt you but no real current (could not
drive the load tester). Connecting the ALL grounds together in several
boxes fixed alot of mysterous jolts and strange ground fault trips.
P.S. I think every circuit in a house should have ground fault.
The ground fault was trying to tell me something before my
wife got zapped. It would also catch a lot (certainly not all)
of wiring errors that even certified electrians make.
I'm pretty sure this reply will keep this HOT note alive for another day or
two :-).
|
291.667 | | 6602::MACNEAL | ruck `n' roll | Wed Jan 29 1992 20:48 | 9 |
291.1026 | | SOLVIT::THOMS | Ross 285-3151 | Thu Jan 30 1992 11:45 | 10 |
|
Read N.E.C. Article 424-3. It states that electric space heating equipment
should be on a circuit rated for 125% of the heater rating.
4000 watts / 240v * 1.25 = 20.8 amps Hence the 30 amp circuit.
Ross
|
291.668 | | KAOFS::S_BROOK | | Thu Jan 30 1992 14:58 | 16 |
| re .36
Not quite ... Polarised plugs were introduced to ensure in general
becaused most appliances only switch one conductor, that the
"hot" lead is switched, and in the case of lamps, that moreover,
the hot wire connects to the button on the bulb base rather than
the screw thread. The housings of appliances are never never never
connected electrically to anything except ground, or in the case of
electronic equipment, the chassis while not grounded is capacitively
connected to neutral where you then may develop a very small voltage
with negligible power.
Housings are never connected directly to either of the two "power"
conductors ... live or neutral.
Stuart
|
291.669 | polarize does not make housing safer | NICCTR::MILLS | | Thu Jan 30 1992 17:32 | 4 |
| Right .-1. That's what I meant by a hot socket when changing a bulb.
Re: .-2 polarizing the plug would NOT prevent the housing from getting
hot if the insulation wore away. The only thing that would help insure
that to not happen is a 3 wire with ground going to housing.
|
291.968 | Ahhh someone with the book !!! | NICCTR::MILLS | | Thu Jan 30 1992 18:10 | 11 |
|
Thankyou for looking that up :-). I'm convince to use #10 wire. But...
Do they differentiate the "Wire" from the "Breaker" or is it implied
that the entire circuit (wire and breaker) be of the rating. This is
what stumped me. The manuafacturer said 30 amp wire (#10) but 20 amp
breaker. What I'm worried about is that if the heater malfunctions
(shorts) and it's on a 30 amp breaker that wiring and controls within
the heater get fried.
Thanks again...
|
291.670 | You still have a problem to fix | JVAX::JOHNSON | | Wed Feb 19 1992 15:56 | 32 |
| I also think the guy concerned about the furnace was right.
The electrician measured 120 volts at the plumbing - this is
not just a bad or elevated neutral problem.
Grounding the drain to the water pipes solves the shock problem
- everything in the shower is at the same voltage. However, the
current you felt in the shower is now flowing directly to ground.
The power going to the furnace should not connect to the frame of
the furnace. It should be totally insulated from the furnace frame.
Since the furnace frame and the associated piping was made live,
there is something wrong with this insulation. The proper way to
diagnose this is to disconnect the furnace circuit (both phase and
neutral) somewhere between the furnace and the main panel, and to
test for this leakage path using a megger or hypot tester. Working
his way through the loads (burner, igniter, thermostat transformer,
circulating pump) the electrician should be able to finally find the fault.
My guess it is with the circulator or its wiring, which was replaced
at the same time the problem arose.
Until the problem is resolved, there will continue to be a risk
to those working on or near the furnace (since it still is not grounded
except through contact with the sewer line. There is also the
potential for the leakage current to overheat the faulty connection
resulting in a fire risk (although proper wiring according to the
code and UL listing of the pump should prevent it from propagating).
The clearing of the fault and the grounding of the furnace should
be a separate consideration from that of replacing the main panel.
It seems you need the electrician again, but he should fix the source
of the problem, not just apply a bandaid.
Bob
|
291.803 | Can DIY replace fuse box with CB panel ? | MSEE::CHENG | | Fri Apr 17 1992 15:14 | 24 |
| I am planning to upgrade the electrical system in my house. The house
is a 2-family house. Each unit has a 60A fuse box and most outlets are
2 wire ( no ground ). This is what I plan to do :
. change the fuse box to circuit breaker, 100A each
. update the service from 60A to 100A each, this may mean bring in
200A service to the house and split them halp for each apartment.
. re-wire just a few outlet to accomodate air conditioning and power
hungry appliance, but not re-wire the whole house
. finish basement and completely re-wire the basement.
I want to do this in three stages. The first stage is changing the two fuse
boxs to circuit breaker. My brother-in-law is a licence electrician in
New York City and he is currently out of work. He's kind enough to
offer free help to install the new circuit breaker panels. My question
is, is it legal for a DIY ( actually in this case a out of state
license electrician ) to install the CB panel ? Do I have to
acknowledge the city about this ? Do I need to get a permit for doing
this ?
Once this is done, I then will hire a MASS electrician to bring in new
( higher ) 200A service. And the other stuff I plan to do.
|
291.804 | | QUARK::LIONEL | Free advice is worth every cent | Fri Apr 17 1992 16:30 | 5 |
| Call your community's electrical inspector and ask. You will probably
have to get a permit for the work, and will almost certainly have to have it
inspected afterward.
Steve
|
291.805 | its not yours to touch - pull a permit | TLE::MCCARTHY | He's the Other Brian this month | Fri Apr 17 1992 17:16 | 10 |
| In most cities / towns in MA, for electrical work, they do not care who does
the work as long as it is done to code (or there interpretation of the code
and a permit is pulled).
When he goes to install the new panels, he will have to pull the electrical
meter - since that is the property of the electric company that services your
house, you better pull a permit. They can get VERY nasty when that little
plastic tag has been tampered with.
Brian J.
|
291.806 | | GIAMEM::S_JOHNSON | | Fri Apr 17 1992 17:39 | 9 |
| re <<< Note 873.57 by TLE::MCCARTHY "He's the Other Brian this month" >>>
>They can get VERY nasty when that little
>plastic tag has been tampered with.
Just curious, what are the repurcussions of doing this, have you seen them
first hand?
SJ
|
291.807 | Only Mass lic elect. is allow to do | MSEE4::CHENG | | Fri Apr 17 1992 17:47 | 19 |
|
Just finished talking to the electrical inspector in Medford ( that's
where I live ). The following was what he told me :
. ONLY Mass licensed electrician is allowed to do the work ( change to
CB panel ). Since my in-law is lisc in NY not in Ma, he can't do the
work.
. this job requires a permit from the city
. the eletrician will have to notify the electrical company before the
work is started
. city elect inspector will inspect the work after it is done
They sure don't allow you to save some money by DIY even if you know
what you're doing but without the license ( Mass license I should say ).
|
291.808 | | MANTHN::EDD | Real programs in DCL? .NOT.! | Fri Apr 17 1992 18:26 | 10 |
| re: first hand knowledge of missing meter tag...
I've seen what they do, and it's not pretty.
They come to your house, even while you're NOT THERE, and they...
...put on a new tag!
Edd
|
291.809 | Hmm, I did electrical work without a problem... | HDLITE::FLEURY | | Sat Apr 18 1992 14:17 | 15 |
| RE: .59 ( I think)
I hate to correct an inspector, but... I believe you asked the wrong
question. As the homeowner, you are allowed to do any electrical work
you want ON YOUR OWN HOME. I suspect that you mentioned that you would
be assisted by a NY licensed electrician. That makes a difference.
You are no longer doing the work yourself, therefore you need a permit
and license for the work.
I have done electrical work in both NH and Ma without a problem given
that I contact the local inspector first with the plans and contact the
electic company BEFORE I do the work. I have not had any problems at
all.
Dan
|
291.810 | | NOTIME::SACKS | Gerald Sacks ZKO2-3/N30 DTN:381-2085 | Mon Apr 20 1992 14:24 | 5 |
| re .61:
In MA, the rules vary from town to town. For instance, in Boston, you can't
do electrical work on your own house (unless you're a licensed electrician,
of course).
|
291.811 | | KAOFS::S_BROOK | | Mon Apr 20 1992 15:49 | 15 |
| The assumption was also there that an out of state licensed electrician
was helping and therefore "being paid" ... If you are paying someone to
help, then he must therefore be locally licensed. Never mind North
American free trade, it appears that free trade doesn't exist between
states of the U.S. or Canadian provinces.
Also, in many areas, if you as a householder, pull a permit to do
electrical work or plumbing (which I understand you cannot do in Mass
anyway), you must do the work yourself. NO ASSISTANTS. That way if
there are problems, you as householder cannot shirk your responsibility
by saying ... "Joe Blow did that bit ... I'll sue him". Licensed
electricians have insurance to cover this; your neighbour or friend
doesn't.
Stuart
|
291.812 | Local code differs | ELWOOD::DYMON | | Wed Apr 22 1992 19:41 | 11 |
|
Ahhhh, better check with you local on how they work things. I did
most my inside work without a permit. The service needed a permit
requiring a license number and the Electrican had to have insurance.
Seeing we pulled the meter,(100A to 200A), the local had to call
in a "D" number to the E co., because after the blue tag on the
meter came a turn off power move.
Nothing is ever cheep or short and simple.....
JD
|
291.813 | and he was only doing LITTLE stuff | TLE::MCCARTHY | Over 50 copies sold | Thu Apr 23 1992 11:50 | 8 |
| In MA, if you are doing eletrical work for someone, you have to show the owner
proof of insurance OR they have to sign a paper that releases liability. This
law was passed about two years ago. When you go to pull the permit you have to
show the town/city the proof of insurance or the letter from the person you are
doing the work for. For a one-man electrical business, the insurance was
running somewhere around 7-11 hundred dollars a year.
bjm
|
291.814 | | RGB::SEILER | Larry Seiler | Fri Apr 24 1992 17:29 | 14 |
| Mass law allows homeowners to do their own electrical work, if they pull
a permit. Some towns have more restrictive rules, but mine doesn't. I
don't see that it is necessary to tell the inspector whether I had friends
help me do my own electrical work (though I'd tell him if he asked -- and
he's no dummy, I'm sure he knows). However, I take full responsibility
for all DIY work done on my house. If I'm not prepared to take that
responsibility, I hire someone to do the job -- I'm paying both for their
work and for their insurance coverage. I suggest that you not accept
help with a DIY project unless you intend to end the project understanding
just what was done and why -- which is actually the way I like to approach
everything that is done to my house.
Enjoy,
Larry
|
291.817 | multiple recepticles, 1 fuse | MILPND::BENHAM | | Thu May 21 1992 12:36 | 17 |
| I rent an older apartment that was built evidently when they didn't
thing electricity was going to take off. Most rooms have only one
electrical outlet in it and some don't have any. The whole upstairs
and cellar seem to be on one circuit and the whole down stair (living
room, dining room and kitchen) seem to be on another.
Here is my problem. In my bedroom I have a clock radio that I like
to set for one hour when I'm falling asleep. In my daughters room
which is back to back with my room she has a fan. When she puts
the fan on I get nothing but static over the radio and you can't
listen to it. From what I have been told all the electricity going
into the apartment from the street is being used, so that I can't
put a new outlet leading to a new fuse in. (I hope that made sense)
Anyone have any suggestions or know of any product that could help?
Thanks
Carole
|
291.818 | | WLDBIL::KILGORE | ...57 channels, and nothin' on... | Thu May 21 1992 13:26 | 9 |
|
1) Better electronics stores will carry an intereference filter that you
can plug into the wall outlet, then plug your radio into it. Might be
worth a try...
2) Pull rank!
This wouldn't perchance be an AM station, would it?
|
291.819 | | MILPND::BENHAM | | Thu May 21 1992 15:57 | 5 |
| ref -1
2) it's hard to pull rank when it's hot out.
and yes it is an AM station.
|
291.820 | | VERGA::WELLCOME | Steve Wellcome PKO3-1/D30 | Thu May 21 1992 16:08 | 8 |
| Quite likely the problem is not the house wiring, the problem may
be the fan itself. It may be broadcasting RF interference, in
which case a well-grounded copper screen cage around the fan would
help. Lots of other people no doubt know much more about that stuff
than I do though.
One quick thing to try: turn the radio (or fan) plug over in the
outlet and see if that helps any.
|
291.821 | | KEYBDS::HASTINGS | | Thu May 21 1992 16:46 | 3 |
| another thing to try. Move either the fan or the radio or both to
opposite sides of their rooms. Put as much distance between them as
possible. Is this a fairly old fan? A newer one may create less static.
|
291.822 | | WLDBIL::KILGORE | ...57 channels, and nothin' on... | Thu May 21 1992 21:13 | 7 |
|
With an AM station, you're probably picking up the noise through the
antenna, so an interference filter on the plug might not do too much
good.
AM is much-much-much more prone to noise of this type than FM.
|
291.823 | | RAMBLR::MORONEY | Is the electric chair UL approved? | Thu May 21 1992 21:51 | 11 |
| AM radios pick up lots of noise through the power line as well. MAYBE a power
filter on the line cord of the fan, radio or both may help, maybe not
(especially if the AM station is weak) I think Radio Shack has a clip-on
ferrite thingy that may help. I'm not sure if they're good enough for
AM suppression. If you try them, install the one on the fan as close to the
motor as possible.
Try a different fan, one with an induction (brushless) motor, these shouldn't
cause interference.
-Mike
|
291.815 | | INNA::STJOHN | | Wed Jul 22 1992 12:29 | 4 |
| You can do the work yourself if and only if it is your residence. Multi-family
(which in your case it is a 2 family, whether or not you live there) you must
have a Mass licensed person. No options or questions permited. Key is
Multi-family.
|
291.816 | | INNA::STJOHN | | Wed Jul 22 1992 12:29 | 4 |
| You can do the work yourself if and only if it is your residence. Multi-family
(which in your case it is a 2 family, whether or not you live there) you must
have a Mass licensed person. No options or questions permited. Key is
Multi-family.
|
291.671 | Electrical Problem.. | AIDEV::HOLLAND | | Tue Aug 18 1992 13:48 | 15 |
|
I need some advice...
I have a track lighting, with 3 spot lights on it, and a
dimmer to adjust light, The dimmer is the rotary type, with
push on/off.
The problem is that if the light has been on, if you touch the
dimmer switch plate, its hot..
any clue what this could be?
Ken Holland
|
291.672 | | QUARK::LIONEL | Free advice is worth every cent | Tue Aug 18 1992 14:15 | 4 |
| This is normal, though it may be your lamps draw more current than the dimmer
is rated for.
Steve
|
291.673 | How warm is it? | MANTHN::EDD | Nimis capsicum | Tue Aug 18 1992 15:45 | 4 |
| Agreed. The energy that would have gone to the lights is disappated
as heat.
Edd
|
291.674 | | QUARK::LIONEL | Free advice is worth every cent | Tue Aug 18 1992 15:53 | 13 |
| Re: .2
Well, not really. Most dimmers use a switching triac that alters the duty cycle
of the current going to the lamp; this is more efficient (and also works better)
than putting a variable resistor in series. There are some losses involved,
though, and this can make a dimmer warm. Most inexpensive dimmers are rated
for 600W, though I would feel uncomfortable about pushing them that high. You
can get heavy duty dimmers rated for 1000W or more.
If a dimmer is getting hot to the touch, I would say that it is either
defective or underrated for the use.
Steve
|
291.675 | | AIDEV::HOLLAND | | Tue Aug 18 1992 17:39 | 4 |
|
Its hot to touch! I was worried about a potential fire
hazard. I think I'll replace it with a 1000w dimmer
|
291.676 | Pull all but one bulb...still hot? | RESYNC::D_SMITH | | Tue Aug 18 1992 18:19 | 5 |
| Or reduce bulb wattage, then turn your dimmer up to achieve th same
intesity.
Dave'
|
291.677 | | TUXEDO::YANKES | | Tue Aug 18 1992 20:41 | 10 |
|
Wait, *3* spot lights are exceeding the capacity of a (presumed to
be...) 600w dimmer? I have track lights and went for the largest sized
bulbs the heads were rated for -- and that was only 75 watts per. If
you're really exceeding 200 watts per bulb, I sure hope you are using a
different kind of track light head than we have... ;-) I suspect that
you just have a faulty dimmer switch.
-craig
|
291.678 | Electical Outlets Needed. | DEMON::RHODAN::DIROCCO | | Mon Sep 28 1992 17:12 | 14 |
| Hi,
Moderator, please move this note if there is a better spot for
it....
Electric outlets, or lack of them in my old house is presenting
a problem. How difficult is it to add more outlets? Is ripping
holes in the wall and snaking wires as bad as it sounds??? Argh.
Any experience out there with this type of thing? I would
appreciate some thoughts on this.
Thanks,
Deb
|
291.679 | | VERGA::WELLCOME | Steve Wellcome PKO3-1/D30 | Mon Sep 28 1992 17:27 | 12 |
| >> Is ripping
>> holes in the wall and snaking wires as bad as it sounds???
Yes.
Every job like this is unique, there is no way to tell ahead of
time what you are going to run into. There are some other notes
in here somewhere, I'm sure, that talk about techniques for
fishing wires, etc. Ingenuity and a devious mind help a lot.
An unfinished attic directly above or an unfinished cellar
directly below help a lot too.
|
291.680 | | MANTHN::EDD | Please turn out the lights... | Mon Sep 28 1992 18:21 | 5 |
| ...and adding outlets may only change the problem.
Make sure your circuits will support the anticipated load.
Edd
|
291.681 | At what expense??? | ROULET::CASSIDY | Aspiring conservationist | Tue Sep 29 1992 03:14 | 13 |
| > Is ripping holes in the wall and snaking wires as bad as it sounds??? Argh.
> Any experience out there with this type of thing? I would
> appreciate some thoughts on this.
I think in some situations it's far better to call in a
professional. An electrician would cost you some bucks but
would also know what needs to be done... and then deal with
all the headaches involved. Not that I always listen to my
own good advice.
Tim
|
291.682 | get a stud finder | TOOLS::COLLIS::JACKSON | All peoples on earth will be blessed through you | Tue Sep 29 1992 12:36 | 19 |
| Usually difficult.
I just added two more electrical outlets; one in the
garage and one in the kitchen. Garage was simple, kitchen
was a royal pain (had to take out a lot of tile, rip out
the plaster board, drill several holes, run a wire all the
way to the fuse box (did not go off an existing run but
added a new run) and then have to repair everything which
included ordering new tile (since some tile broke).
Personally, I would not choose to hire it out because I'm
sure it would cost a ton of money. The simple job (in the
garage) I would not hire out because it's easy and rewarding.
One thing I can see, between this and the soap dish in the
bathtub which came out, I'm learning how to tile and grout
expertly. :-)
Collis
|
291.683 | | WLDBIL::KILGORE | Bill -- 227-4319 | Tue Sep 29 1992 12:43 | 4 |
|
Look on it as an opportunity to become intimately acquainted with the
construction details of your home...
|
291.684 | Frustrating but very rewarding | DUSTER::MCDONOUGH | | Tue Sep 29 1992 16:30 | 23 |
| I did this in my house and some areas were more difficult than others.
My house was build around 1860 and is a two story two family. For the
first floor, for each new circuit, I ran a wire from the box to the
first outlet through the basement. I popped off the baseboard (6 inch)
and then ran the wires to the next outlet(s) along the baseboard. I
most areas I was able to fish the wire behind grooves in the 2x4's.
Those I couldnt fish behind, I drilled through.
The second floor, I used a snake to go from the attic to the basement
and then pulled up lines. This was not a fun task so I left a string
in place incase I ever have to do it again. I then fished down to
where the first outlet of the circuit was to go. From there, I went
around the baseboard to the next outlet. I some places I hit
stops in the walls and changed where the first outlet went.
I only had to do it this way in 2 rooms since we were remodeling the
entire house and all the other rooms we had gutted to the studs, but
just doing it for those 2 rooms made me appreciate new contruction!
When the frustration factor got too high, usually with the lights on
the first floor, I just banged holes and patched them with plaster later.
Good luck...Rhonda
|
291.685 | Go slowly | KAYAK::GROSSO | Prevent & Prepare or Repent & Repair | Tue Sep 29 1992 17:29 | 46 |
| These replies were great! Gosh this note brought back memories. I've
completely rewired two 100 year old homes and these replies captured the
spirit of the effort. I have a few points I'll add.
If you opt for an electrician, decide what work you really need the electrician
to do. I was lucky for on both my homes, the circuit box and feed had been
upgraded, so I could just run the wires. A large part of the job does involve
electrical work. If you want the electrician to connect the wires to the
box, that's 10 minutes of work. Mounting the box and snaking the wire through
the house without destroying wallpaper/tiles/plaster/etc can take up to 3 hours
for one outlet. Consider doing that yourself if you're at all handy.
Essentially hire the electrician to do only what you can't.
If you opt to let an electrician do the whole job, then be sure you're hiring
one who respects/loves old homes. I've seen some horrible things done in
an effort to save time. A half hour of smashing holes to save three hours of
snaking that leaves 8+++ hours of repair/patch/repaint/repapering.
There are plenty of fine books with lots of hints, tricks and pointers as to
how to get wires through a house. In retrospect, I guess it must have been
fun cause I did it twice. You do get very intimate with the house and learn
lots of its secrets. If you're really going to upgrade the wiring and put
new outlets on all the walls, then you may consider what I did. I ran a feed
to the attic with a subpanel and then wired the second floor down from there.
That saved lots of wire and hassle dragging each wire back down to the basement
and also makes it trivial if I ever divide the house into a two family.
Looking back I think I wish I'd had a better idea of all that was in store for
the house. I painstakingly snaked wires to get outlets exactly where I
wanted them and then two years later lifted floor boards as part of a heating
system upgrade that would have made rewiring trivial. Planning ahead is hard
but can save lots of effort.
One last bit of advice. Try to live in an old house for a while before jumping
in and "fixing". I read this advice in an old house book and its wonderful
advice. Actually, the author suggests a year. Live in the house for all its
seasons before you do anything. Those big old drafty windows which you hate
all winter, make the house the nicest on the block in the summer. That tree
blocking your view might give shade where you'll really appreciate it. And
remember, people have lived there a 100 years without the improvements you
think the house needs, maybe you can too. But by living with it first, you'll
be doing only the improvements the house really needs, and might be able to
coordinate them to your financial advantage.
-Bob
|
291.686 | Updated service... | DEMON::RHODAN::DIROCCO | | Tue Sep 29 1992 17:49 | 25 |
| Snifff...snif...that last reply almost brought a tear to my eye!
My house was build somewhere between 1832 and 1850, the historical
society is a little fuzzy on the dates, but it is obviously 'ol-d'.
Fortunaley, the electical has been updated by a previous owner, so
adding outlets or switches would basically be just a matter of
snaking and wiring, and patching some holes.
I think adding a sub panel in the attic is a good idea, something
my husband and I didn't think of. I do think the panel in the
cellar is becoming pretty full.
Living in the house for a year is a good suggestion, we have been
there for 7 months. Next year we are leaning heavily on re-doing
the heat system for the house, so it may be better to wait on some
of this stuff, but I think we may be able to add an outlet or two
in our bedroom, (which has 1 outlet in the entire room), because I
am going to put up new wallpaper. The walls are in good shape though,
so no need to tear them down. I guess we'll survive if all of you
did.
.7 mentioned some good books on doing this, any titles??
Thanks,
Deb
|
291.687 | | SITBUL::ALINSKAS | | Tue Sep 29 1992 18:00 | 7 |
| I always wondered what people ment when they said "snake a wire". In the
past I always used a 10 gauge aluminum wire which I thought worked fine.
The last wiring job I did, I bought an electrician's snake. This is like the
best tool ever invented. I needed to snake wire in an outside wall stuffed
with insulation. The aluminum wire did not work at all. Not even close!
With the snake it took a few seconds. The snake went right where I wanted
it. THis is definitelt a tool to have if you plan on doing somw wiring!
|
291.688 | The "yellow book" | SSDEVO::JACKSON | Jim Jackson | Tue Sep 29 1992 18:01 | 4 |
| I find the Reader's Digest "yellow book" to be an excellent source of ideas.
There's a section on how to run wires. I don't recall the exact title,
something like "The Readers Digest Do-It-Yourself Guide". There's also a
"blue book", a Fix-It-Yourself Guide.
|
291.689 | It's lots of fun!!! | ESKIMO::CASSIDY | Aspiring conservationist | Wed Sep 30 1992 03:58 | 8 |
|
Snaking wires is an art form. A good electrician can do some
amazing things with one. I've gotten my hands dirty and have had
some success with snakes, but only due to stubborn persistance.
If you opt to do your own electrical work, get ready for a trying
experience.
Tim
|
291.690 | | JUPITR::HILDEBRANT | I'm the NRA | Wed Sep 30 1992 11:01 | 7 |
| One idea....learn about the construction technique used for your
home. If post and beam...study pictures about the method before
you start.
If its balloon framing or Western framing, learn about that method too.
Marc H.
|
291.80 | | RAMBLR::MORONEY | Is the electric chair UL approved? | Thu Oct 22 1992 17:04 | 5 |
| What is the formula for the size box needed for wiring? Or to put it another
way, what size box would I need for a junction box for 5 14/2+ground Romex
lines?
-Mike
|
291.81 | | STAR::DZIEDZIC | | Fri Oct 23 1992 23:32 | 12 |
| Number 14 wires require 2.0 cubic inches per wire; number 12
wires require 2.25 cubic inches per wire. The last time I
read the NEC, you counted ALL grounding wires as ONE wire
(I believe this may have changed recently?); you count each
"device" (switch/outlet/etc.) mounted inside the box as ONE
wire. There are lots of twists regarding wires which run
"through" a box (as in conduit wiring).
IF the "all grounding wires count as ONE" rule is still valid,
you'd have (5*2)+1 wires (11), times 2.0 cubic inches per,
for a total of 22 cubic inches. Most boxes these days have
the cubic inch capacity stamped inside.
|
291.82 | | QUARK::LIONEL | Free advice is worth every cent | Fri Oct 23 1992 23:51 | 3 |
| The 1990 NEC still counts all grounding conductors as one.
Steve
|
291.83 | BIG box... | LUDWIG::CASSIDY | Aspiring conservationist | Mon Oct 26 1992 01:25 | 5 |
| Don't know where you're at, but Mass. code counts all grounds
individually (=15 #14 wires). Or so I was recently told by a
friend who's an electrician. Can't help with the correct box
size.
Tim
|
291.84 | | VERGA::WELLCOME | Trickled down upon long enough | Mon Oct 26 1992 10:41 | 3 |
| ...and isn't there something about each cable clamp counting as a wire?
|
291.85 | Help | JUPITR::HILDEBRANT | I'm the NRA | Mon Oct 26 1992 12:06 | 5 |
| In the installation book for a hot air gas furnace, it states that the
wire bringing power to the furnace should be "type T wire or
equivalent". What is that?
Marc H.
|
291.86 | Adding Outlets for garage door openers | ROULET::HUI | | Wed Oct 28 1992 15:46 | 34 |
| I am planning to add a couple of outlets in the ceiling of my garage to operate
2 new garage door openers. I have 2 line coming into the garage (One for
outside lights and One for the garage lights and 2 existing Outlets (See
Below).
[ ] <--Outside Outlet
S= Light Switches |
inside the |
Familty Room [ ] <--Inside Outlet
|
|
S-------------+ |
S-----------+ | | 0 = Ceiling Lights
| | |
| | |
| +-------O--------------O
|
| { } { }
|
|
|
| { } = New Outlets location
|
| X = Outdoor Lights
X-------------------------------------X
My Question is where should I wire the new outlets from for the garage door
openers? Do I have to bring in a new line (I have a 200 A Panel)? Can I just
tie it into the light fixture? What do I have to watch out for to complete this
job. This just look to ease for me to paid a certified electrician or should I?
Dave
|
291.87 | | VMSDEV::HAMMOND | Charlie Hammond -- ZKO3-04/S23 -- dtn 381-2684 | Tue Nov 03 1992 18:36 | 35 |
| >I am planning to add a couple of outlets in the ceiling of my garage to operate
>2 new garage door openers. I have 2 line coming into the garage (One for
>outside lights and One for the garage lights and 2 existing Outlets (See
>Below).
...
>My Question is where should I wire the new outlets from for the garage door
>openers? Do I have to bring in a new line (I have a 200 A Panel)? Can I just
>tie it into the light fixture? What do I have to watch out for to complete this
>job. This just look to ease for me to paid a certified electrician or should I?
How much power do the openers take? Since you *WILL* -- not often,
perhaps, but sometimes -- run both at once you need to have a
heavy enough supply to do this safely. If you have other
lights/outlets on the same line, it will have to be heavy enough
to handle both openers AND all the other lights/outlets. If you
have access to the panel and there is space for another breaker it
is almost certainly a good idea to run a separate line for these
openers. This also makes it easy to switch them off when you go on
vacation nor anytime you want to be sure the doors don't open or
close. (Much easier than unplugging!)
As for "what to watch out for" -- you have to watch out for
everything that a certified electrician would look out for.
Without seeing your garage, it seems like this is a very easy,
straight forward job. On the other hand, if you don't know how to
tell apart the ground, neutral and hot wires, perhaps you should
think twice.
If you aren't certain of the code requirements and the "how to",
spend the $ for a pro. If the panel is in the garage and the wire
can be run on the surface this is about a 1 hour job -- probably
less that $50, as a guess. If the pannel is somewher else, or if
wires have to be fished through the walls, it might run to twice
that much. (Caution! I haven't hired an electrician in some time,
so these $ could be off.)
|
291.874 | Making outlets stick out | MR4DEC::BMCWILLIAMS | Improvise if you have to ... | Wed Nov 04 1992 12:57 | 11 |
| Anyone know of any tricks for making electrical wall receptacles (outlets)
stikck out of their boxes farther so the faceplate fits better?
I just moved about 8 outlets in my kitchen and seem to have set some of the
boxes in a little too deep. It's too late the move the boxes (sheetrock is
up), but can I, say, add washers behind the mounting screws to make the outlet
stick out farther?
Or am I the only person ever to set a receptacle in too deep? ;-)
Brian
|
291.875 | Use the Ears | JUPITR::HILDEBRANT | I'm the NRA | Wed Nov 04 1992 13:07 | 6 |
| The mounting "ears" on the duplex outlet will reference the actual
surface, not the box. In this way, the outlet will be flush to the
wall. Have you kept the ears on? They can be removed if you want the
outlet to be flush to the box instead.
Marc H.
|
291.876 | | MR4DEC::BMCWILLIAMS | Improvise if you have to ... | Wed Nov 04 1992 13:18 | 4 |
| RE. .1:
Some jerk (me) must have cut the openings in the wallboard too big, so the
"ears" evidently don't touch the wall ... :-(
|
291.877 | | NOTIME::SACKS | Gerald Sacks ZKO2-3/N30 DTN:381-2085 | Wed Nov 04 1992 13:29 | 1 |
| Use small washers under the screws. Or stick bits of cardboard there.
|
291.878 | feature on some boxes | DAVE::MITTON | Token rings happen | Wed Nov 04 1992 15:04 | 20 |
| This be moot, depending on your actual boxes, but...
some metal box types allow you to move the box in/out relative to
their mounting tabs. Look for a screw head in the obvious place.
Crude ASCII drawing follows:
|
L-|-
+---|---+
| ^ |
| |
| |
| |
+---|---+
--|-
|
FWIW: Dave.
|
291.879 | | QUARK::LIONEL | Free advice is worth every cent | Wed Nov 04 1992 15:15 | 6 |
| You can buy plastic spacers designed to solve just this problem. I've seen
them at home supply stores. And no, you're not the only one to do this!
You can also get box extenders, but they won't work in all cases.
Steve
|
291.880 | some other options | EVETPU::MCCARTHY | but I kept rolling off the couch | Thu Nov 05 1992 09:17 | 15 |
| Don't use cardboard - if things, for some reason, get hot in there, cardboard
is flammable.
Somewhere in this conference someone mentioned using the 49 cent cheap plastic
boxes and slicing off the front inch or so. This gives you the added value of
still having the side terminals covered.
The tabs that bend off on the upper and lower corners of the outlet make good
spacers - and it sounds like in your case they aren't doing what they should -
holding the box against the wall.
Creating a "spring" by coiling 14g wire around an small screwdriver or the tip
of needle-nose pliers.
bjm
|
291.881 | I use air... | RANGER::PESENTI | Only messages can be dragged | Thu Nov 05 1992 10:32 | 4 |
| All I do is loosen the outlet mounting screws, then tighten the faceplate
screw to pull the outlet forward. Works great. The outlet IS a bit spongy
(gives a little) as you plug stuff in, but I've never had any problems cracking
the faceplate.
|
291.882 | it happened to me.... | WFOV12::KOEHLER | Personal_Name | Thu Nov 05 1992 11:48 | 4 |
| re last few. Acrtually you should have the outlet tight inside the
box. Otherwise the wiring might loosen and cause a short.
Jim
|
291.883 | | SPEZKO::LEMIEUX | | Thu Nov 05 1992 17:19 | 41 |
| Hi,
There is a little more to this subject than just securing the outlet
to keep it from being pushed in or loose fitting.
The NEC requires that the box if installed in noncumbustible materials
(gypsum board,plaster etc.) have the front edge of the box be no
further back from the finished surface than 1/4". If its installed in
cumbustible materials (wood paneling, wainscoting, etc) then the front
edge of the box must be installed flush with the finished surface.
(this applies to boxes in walls or ceilings)
See Art 370-10
The method that I have used to satisfy this rule and the inspectors
is to use the sheetmetal "add-a-depth" rings. These sit on the finished
surface but extend back into the existing box and surround the device
your trying to secure. Some even come with longer screws so that you
don't have to but them seperately. They are designed for the purpose.
They may even come in plastic these days but I haven't seen them myself.
If your afraid of possible shorts aginst the sheetmetal simply wrap
some elec. tape around the receptacle so that the termination screws
are covered. (You'll see this done a lot on jobs that were done with
metal boxes especially in commercial work.)
Try any well stocked electrical supply, they should have them.
Another related NEC article requires that the plaster surrounding the
box have no gaps greater than 1/8" at the edge of the box....You should
see the discussions this one causes when the inspector tells the
electrician to fix the plaster around the boxes or he won't pass the
job. Of course the plasterers are nowhere to be found at this point in
the job :')
See art 370-11
Later
Paul
|
291.976 | Hummmmm | LANDO::OBRIEN | Give it a TRI | Tue Dec 01 1992 20:43 | 16 |
| Hi,
I just installed a 3-way dimmer switch and noticed that there is a
slight humming noise at the bulbs(75w reflective type). I did not
notice the noise w/ the regular on/off switch.
Is this the filament in the bulb(cheap bulbs?) or possibly a bad/cheap
3-way dimmer? I can get the brand name if that would help.
thank you
regds,
John
p.s. If this is discussed elsewhere, sorry for the duplication and
could you point me to the right note?
|
291.977 | 1111.35 = 3217... | LUDWIG::CASSIDY | Aspiring conservationist | Wed Dec 02 1992 03:26 | 10 |
| John,
Note 1111 contains a directory for all the notes in this con-
ference. Typing DIR 1111.* will allow you to scan the directory
easily. Note 3217 has information pertaining to your situation.
Buying a higher quality dimmer could reduce, or even eliminate
the buzzing noisee. Or you could turn on a radio to drown it out.
8^)
Tim
|
291.691 | Surface-Run Wiring? | ASD::DICKEY | | Thu Dec 17 1992 15:07 | 19 |
|
Does anyone have experience with surface mounted wiring (e.g., conduit
or raceways)? I have some Knob & Tube wiring in the ceilings of my
house which my insurance company wants me to replace.
Running new wiring through the walls/ceilings seems to be impossible
without putting holes in the walls/ceilings. I'm disinclined to do
that since this space is currently occupied by a renter. Eventually,
(when the renter moves out) I would like to redo the interior and
I expect to rewire correctly at that time, so the surface-run wiring
would be somewhat temporary (though these tenants aren't likely to
move out in the next couple of years, at least). For this reason
I'm looking for a cost-effective alternative.
I hope to run the wiring myself and only bring in the electrician to
hook up the new wiring to the panel.
Any suggestions or insights would be appreciated,
Rich
|
291.692 | do it right the first time. | ELWOOD::DYMON | | Thu Dec 17 1992 15:44 | 8 |
|
You might want to do it a room at a time..... It would say
you from doing it twice...
Heck, its only a renter...wire up a bunch of new boxes and give
them 100 extention cords!!! :):):):)
Sparky
|
291.693 | | VERGA::WELLCOME | Steve Wellcome PKO3-1/D30 | Thu Dec 17 1992 16:49 | 8 |
| If you use Wiremold (brand) surface-mount wiring, you may be amazed
at how much the stuff costs. You may decide that doing the job
that way, only to discard it later when you do it "right," is
too much a waste of money.
What does your insurance company have against knob-and-tube wiring?
My understanding is that it's very safe, albeit unsigtly and without
a separate ground wire.
|
291.694 | Conservative Insurance Co. | ASD::DICKEY | | Thu Dec 17 1992 19:45 | 25 |
|
My insurance company is very conservative (which is generally fine
by me as it means lower premiums).
My home inspector said that as long as the knob & tube was accesible
so it could periodically (e.g., annually) inspected, he didn't feel
there was a problem. This implies that if hidden, he would feel it
is a problem.
When the inspection was done, my understanding was that the only
knob & tube was exposed (in the basement). I was told that the
upstairs was re-wired. I had the electrician in to replace the
exposed wiring (as required by my insurance company), and while he
was doing this discovered that most of the upstairs had been
rewired, but not 4 of the overhead light fixtures (in one area of
the first floor). The electrician replace everything he could get
at easily, but I'm left with the problem of the wiring in the
ceiling.
Now that I think of it, the two lights on the back porch could
just be done with BX or Conduit on the surface. This would only
leave two overhead lights for which a more expensive solution is
needed.
Rich
|
291.952 | One fixture, 2 circuits. Legal? | MSD05::ORR | | Mon Mar 15 1993 18:46 | 37 |
|
The closest I could find to this question is #4076, but I
thought this specific situation different enough to enter separately.
If covered eleswhere, please point me to it.
Question #1.
I'm installing a new bathroom ceiling fixture which has 4
separate functions (light/heat/exhaust/night light) and says it
demands a separate 20A circuit. The fixture itself has knockouts for 4
separate #14 cables, one for each function, that come from a cluster
of 4 switches to be mounted on the wall (fed by the 20A line). That's
easy enough but I'd really rather tie the "light" section of this
fixture into another existing circuit that controls the vanity lights.
Electrically that's easy. I'll just take the proper cable that enters the
fixture and run it to the vanity circuit. But is that legal? That
would leave one physical light fixture fed by two separate breakers.
If you didn't know that, you could turn one off (the vanity circuit,
for example) and leave the rest of the fixture live, possibly
resulting in a maintenance hazard.
Question #2.
Along the same lines, even if I wanted to wire that fixture in
the more conventional way, could I still place the control switches
(which are on their own 20A circuit) in the same box cluster as the
switches controlling the rest of the bathroom? Again, we have a
cluster of wall mounted boxes (in this case 3 wide) being fed by two
separate circuits. Kill one and the cluster still has power - another
possible maintenance hazard.
Are either of these situations legal (here in Mass.)?.....
|
291.953 | | ASD::DICKEY | | Mon Mar 15 1993 18:56 | 7 |
|
I don't know about the code, but a book I have that describes
this type of wiring strongly suggests that the handles for
the two circuit breakers in question be tied together (giving
the effect of a double breaker).
Rich
|
291.954 | Yep, thought of that..... | MSD05::ORR | | Mon Mar 15 1993 19:50 | 17 |
|
The problem is that the existing wiring to the rest of the bath
is all #14 and deeply buried within the walls etc. So one of the
breakers would have to be 15A and the other 20A. I'm sure I could
fabricate or steal such a bar from other dual breakers, but then I
thought I'd have to physically tie the two breaker bodies together
just like they do on standard dual units. That's a lot harder and
presents a replacement problem down the road for whoever owns the
place when one of these breakers die. I know that I could rewire the
whole bath with #12 wire, but that's a time consumer that I'd hoped to
avoid.
|
291.955 | Looks familiar... | LANDO::OBRIEN | Give it a TRI | Wed Mar 17 1993 20:38 | 30 |
| This is bizarre. Practically the same situation happened to me this
weekend. In our bathroom, we previously had a LIGHT in the tub, and a
FAN/HEATER outside the tub. We put in a skylight, which got rid of the
ceiling supporting the FAN/HEATER, so I decided to put a 3-funtion unit
inside the tub; FAN/LIGHT/NIGHTLIGHT.
The original FAN/HEATER was on one circuit, the LIGHT on another. I
said, OK, I'll use the pre-existing switches so that:
LIGHT = LIGHT
FAN = FAN
HEAT = NIGHTLIGHT
Hooked up all the switchboxes, and all that was left was the
FAN/LIGHT/NIGHTLIGHT unit. Well, they designed the LIGHT/NIGHTLIGHT
(in the unit), such that they had the same COMMON/RETURN(...BUMMER...)
and the FAN had a different COMMON/RETURN wire.
So, I could NOT hook it up like planned since my initial desire was to
have the LIGHT and NIGHTLIGHT on different circuits. From what I
understand, you can NOT have one return for two different circuits!
So, I guess you have to see how your unit is designed. You may already
know all the above stuff.... I don't know if there is any code saying
that it MUST be on the same circuit(unless the unit happens to only
have one common wire).
regds,
John
|
291.956 | if you think about it - it DOES make sense | 20438::MCCARTHY | but I kept rolling off the couch | Thu Mar 18 1993 09:56 | 19 |
| >> From what I
>> understand, you can NOT have one return for two different circuits!
Did that surprise you?
Doesn't it make sense? You could end up having 2 appliances drawing 20 amps (-
the 15%) on different 20A (110) circuts "returning" on a single 12g wire -
this means that 12g wire is taking 40A worth of load (assuming of course that
the two circuts are on the same leg of the 220 service). Can you say overheat?
I knew you could :-)
My mention of "the same leg of the 220 service" is the exception to using the
same common line. You can run two 110 circuts in a 12-3 or 14-3 RX (gee is
that a trademark???) as long at the two circuts are on different legs of the
220 service. Because AC is a "wave" each leg "peaks" at a different time
and this means that the most current that will ever be drawn at a single time
is at the apex of either leg - and the other leg is at zero at that time.
bjm
|
291.957 | | TOOK::SWIST | Jim Swist LKG2-2/T2 DTN 226-7102 | Thu Mar 18 1993 12:02 | 5 |
| Electricity 101.
Kirchoff's current law: The current in a loop is the same anywhere in
the loop. It does not get "used up" by passing through a load.
|
291.958 | | LANDO::OBRIEN | Give it a TRI | Thu Mar 18 1993 12:21 | 16 |
| *>> From what I
*>> understand, you can NOT have one return for two different circuits!
*
*Did that surprise you?
No, not at all. That's why I was bummed out when I saw the config of
the fan/light/nightlight wiring....
>My mention of "the same leg of the 220 service" is the exception to using the
>same common line. You can run two 110 circuts in a 12-3 or 14-3 RX (gee is
>that a trademark???) as long at the two circuts are on different legs of the
That's interesting, and I think I picture what you're saying but how can
you tell if they're on different legs w/out a scope?
|
291.959 | I guess I won't chance it.... | MSD05::ORR | | Thu Mar 18 1993 12:41 | 10 |
| RE: .3
You may be in worse shape than I. At least my fixture has the provisions for
completely different cables into each of the functions.
This is probably overkill but I've decided to rewire the entire room with #12
wire and use a dual ganged 20A breaker. That way there will be a separate
return for each circuit, and replacement breakers are readily available. I'm
rapidly running out of room in the breaker panel though, and may have to start
cruising this file for help on that soon too....
|
291.960 | Read them with a meter...some examples | SPEZKO::LEMIEUX | | Thu Mar 18 1993 14:06 | 62 |
| >>That's interesting, and I think I picture what you're saying but how can
>> you tell if they're on different legs w/out a scope?
Measure between the two or three wires with a volt meter.
|Leg A |Neutral | Leg B
| | |
| | |
|---120 volts---|---120 volts---|
|-----------240 volts-----------|
(I've left out the ground for clarities sake but the readings from hot
to ground are supposed to be the same as hot to neutral. and the
voltage values I used may or may not apply to every situation)
If the hot wires read 120 volts to Neutral or ground but read 0 volts
to each other they are effectively the same leg.
If the hot wires read 240 between each other they are on different
phases.
On a circuit like the one above, the neutral will never see more current
than the maximum unbalanced current between the two phase legs.
Here are some examples:
|Leg A |Neutral | Leg B
| | |
| load | load |
|--//////-------|-----//////----|
15 amps 0 amps 15 amps
|Leg A |Neutral | Leg B
| | |
| load | load |
|--//////-------|-----//////----|
18 amps 6amps 12 amps
But as one of the previous noters mentioned if you have both
hot legs on the same phase and share the neutral this is what you end up with:
|Leg A |Neutral | Leg A
| | |
| load | load |
|--//////-------|-----//////----|
15 amps 30 amps 15 amps
|
291.961 | | LANDO::OBRIEN | Give it a TRI | Thu Mar 18 1993 14:39 | 9 |
| >You may be in worse shape than I. At least my fixture has the provisions for
>completely different cables into each of the functions.
Not really,... I'm done ;-). (I just ran another wire for the
common to the box from the GFI that I installed, and cut out another hole
for another switch box.)
Good luck.
|
291.962 | | LANDO::OBRIEN | Give it a TRI | Thu Mar 18 1993 14:45 | 3 |
| re. .8
Ah, I see now.... Thanks for your explanation.
|
291.963 | two circuits (separate neutral) in same box? | RGB::SEILER | Larry Seiler | Tue Mar 23 1993 19:53 | 10 |
| Well, I'm now confused. I have a dual switch box in my garage that has
two separate circuits entering it. They have separate grounds (both
connected to the metal box, of course) and separate neutral returns.
Is this legal? Do I have to gang the breakers so that they switch off
together? Note that I cannot put them on the same circuit without putting
more lights and switched outlets on one circuit than I think is allowed.
Thanks,
Larry
|
291.964 | | SPEZKO::LEMIEUX | | Tue Mar 23 1993 21:03 | 10 |
|
Perfectly OK. You don't have to gang the breakers together.
The ganged breaker thing applies to a multi-wire branch circuit
where you have 2 hots, 1 neutral within a cable or conduit and it feeds
more than 1 device (receptacle, switch, lampholder etc)or equipment
on a yoke. (By the way this only applies to dwellings)
I've paraphrased the above from Art 210-4 of NEC. See Art 100
for a longer description of Multi-wire Branch circuit.
|
291.884 | GreenPlug Ideal Voltage Controller | QUARK::LIONEL | Free advice is worth every cent | Fri Jul 09 1993 18:42 | 80 |
| A new product has started appearing in stores in this area, a line of devices
called "GreenPlug Ideal Voltage Controllers" from a Colorado company called
Green Technologies Inc. The device plugs into a three-prong wall outlet and
provides a socket of its own, into which you plug an appliance. There are
three models, each intended to work with a specific type of motorized appliance:
Air Conditioner/Dehumidifier, Refrigerator/Freezer and Washer/Gas Dryer.
(This last can also be used for other motorized appliances such as
attic fans up to 3/4HP.)
The claim for these products is that they reduce power consumption and
increase product longevity. They accomplish the former by modifying the
power waveform so that the peak voltage is lower than the nominal 120V; the
actual voltage is varied depending on the load presented; full voltage is
supplied when load suddenly increases, such as a fan or compressor starting
up, and then it ramps back down. The controller also provides a "soft start",
where the initial voltage ramps up over a period of about a second, rather
than coming on all at once; this supposedly increases motor life. The
manufacturer claims that motors don't need the full voltage to keep running,
and that they will operate more efficiently and cooler at a lower voltage.
The devices also include a surge protector MOV (only one, I think - across
the hot and neutral lines). There is a 10-year warranty against defects;
the price is approximately $35. This is rather steep; the payback period
is 1-5 years, depending on the type of appliance and the frequency of use.
The instructions for the refrigerator/freezer model indicate that you need
to adjust the freezer temperature control (the one that regulates how much
air gets blown from the freezer to the refrigerator) to the warmest setting,
as the fan will be running "more efficiently".
I saw a demonstration setup with a motor that could be run either from
straight AC power or through the GreenPlug. There was what claimed to be
a wattmeter display for each mode; with the Greenplug, the motor ran quieter,
though apparently at the same speed, and indicated power consumption was
about 20% lower.
The devices are based on technology developed for NASA; I have read about the
concept over the past several years, and it appears to be sound. So, being
the technology junkie that I am, I sprang for three GreenPlugs; two for
my refrigerator and chest freezer and one for a dehumidifier.
I first tried out the dehumidifier. The GreenPlug seemed to work as
advertised, in that it started with less of a "jolt" and ran quieter than
with straight wall power. Performance of the dehumidifier does not seem to
have suffered after several days of use. So far, so good.
Next I tried the chest freezer. I plugged it in, turned it on and... I
heard a low hum from the freezer and then a click as the thermal overload
protector tripped. I tried the other GreenPlug and got the same result.
Even though the leaflet claimed that they had tested the GreenPlug with
"every type of home appliance", it seems that it just doesn't like my
freezer (a smallish 13CF model that is about three years old.)
I decided not to try the GreenPlug on the refrigerator for now, given that
I would have to roll it out from the wall, and that is enough of a
"production" that I didn't want to do it if I wasn't sure the device would
work.
I did take the GreenPlug from the dehumidifier and tried it out on each of
two window air-conditioners, which given our recent heat wave, have been
getting quite a workout. They seem to work fine there - the AC units start
up fine and run quieter, but with no apparent loss of performance.
Whether or not I'm actually saving energy is something I'll probably not know
for a long time, but I understand the principles enough to be reasonably
confident that they do what they claim. Just how long it will take to repay
the considerable investment is another question.
I have since exchanged the two refrigerator/freezer models for
AC/Dehumidifier models so that I can use them on all three units. (I don't
know what the operational differences are supposed to be between the models;
perhaps it has to do with reaction times for loads, etc.)
I plan on writing to the manufacturer (there's no phone number listed) to
get more information and to try to find out why my freezer doesn't like the
GreenPlug.
Has anyone else tried these?
Steve
|
291.885 | Where did you find these in the Nashua NH area? | SPEZKO::LEMIEUX | | Fri Jul 09 1993 19:16 | 5 |
| Hi Steve,
I've been trying to find a vendor for them here in Nashua. Did you get
them locally?
|
291.886 | HQ to the rescue | CADSYS::FLEECE::RITCHIE | Elaine Kokernak Ritchie | Fri Jul 09 1993 19:17 | 1 |
| I saw them in Home Quarters (Shrewsbury) a few weeks ago, if that helps
|
291.887 | | QUARK::LIONEL | Free advice is worth every cent | Fri Jul 09 1993 19:33 | 4 |
| Both Home Depot and Builders Square have them. HD's price is a buck or so
cheaper. Builders Square had the demo setup I described.
Steve
|
291.888 | I'm From Missouri | JUPITR::HILDEBRANT | I'm the NRA | Fri Jul 09 1993 19:34 | 8 |
| I'd like more info before I would use one. Most induction motors become
inefficient under reduced voltage. The actual curves depend a lot
on the rotor resistance...which is not changed by external line
conditioners.
Got any technical info on them?
Marc H.
|
291.889 | | AIRBAG::SWATKO | | Fri Jul 09 1993 19:44 | 3 |
| Home Depot in Nashua has the motor/meter demo as well.
-Mike
|
291.890 | | QUARK::LIONEL | Free advice is worth every cent | Fri Jul 09 1993 19:56 | 15 |
| Re: .4
I'm hoping to get more technical details from the manufacturer. The
literature they do provide shows that it doesn't just reduce the voltage;
rather, it modifies the waveform so it's no longer sinusoidal. Exactly
what the motor does with this, I'm not sure, but I've read enough different
articles on the concept, including NASA's use of similar controllers on
the space shuttle, that I was willing to give it a try.
I know that the typical response of an induction motor to low voltage is
much increased current, strain and stalling. I can tell you that that
DOESN'T happen here (except for my freezer!), so something else is going
on.
Steve
|
291.891 | Power Factor reduction??? | STRATA::CASSIDY | | Tue Jul 13 1993 07:17 | 10 |
|
I would have thought that these ran by correcting the current/
voltage phase shift. ELI the ICE man: Voltage leads current in
an inductive circuit (motor coil) and vice versa in a capacitive
circuit. When E (voltage) and I (current) are in phase, you have
maximum efficiency.
Part of the Green thing's function must be to reduce the degree
by which E leads I.
Tim
|
291.892 | timely article | CPDW::PALUSES | Bob Paluses @MSO | Tue Jul 13 1993 15:26 | 70 |
| I copied the following from last Sunday's Homes section of the Worcester
Telegram & Gazette. Maybe someone will want to follow up and post the
additionaly info that's available ?
Bob
Copied without permission from the Worcester Sunday Telegram 7-11-93
[From the HOMES section]
Motor Controllers Increase Efficiency
Dear James T. Dulley: I can't afford new energy efficient appliances now, but
with ever higher electric rates, I need to save. Do those inexpensive "black
box" electronic devices improve appliance efficiency ? J.H
You are referring to motor controllers for appliances. Plugging your appliances
into inexpensive controllers can make them operate more efficiently than when
they were new. A controller can reduce electricity usage up to 15%, reduce
repair calls, and increase appliance life.
A controller instantaneously monitors the needs of the motor and gives it only
enough power to match the load. You can use them on any appliances that have
motors (refrigerators, freezers, clothes dryers, washing machines,
dehumidifiers, air conditioners, sump pumps, tools, etc)
Controllers are particularly effective on old refrigerators because they
reduce the heat created by the motor. Excess heat not only wastes electricity,
but it also makes the compressor run longer to stay cold.
Older appliances often have motors that are more powerful than needed. These
motors run 95% of the time at lower output than they were designed for, so
they operate inefficiently and electricity is wasted.
A controller is a small radio-size device that you plug into any wall outlet.
You just plug the appliance into the outlet built into the the controller. There
is an indicator light to show you it is working.
I use a controller on my refrigerator. Other than a lower pitched and
quieter sound of the motor, it operates the same. I move another controller
from outlet to outlet when I am vacuuming or running the washer.
Most controllers have built in high voltage spike protection. There are many
thousand-plus voltage spikes in your household wiring. One large spike can
easily burn out controls in your appliances. Repeated smaller voltage spikes
can slowly degrade the insulation and electronic components.
Soft-start is another built-in feature. This allows the current to ramp up
slowly when the motor (refrigerator compressor) starts up. Soft-start reduces
energy usage and wear and tear on the motor and components.
Controller brownout sensors can save a motor from destruction. When voltage
drops during a brown out or storm, a motor may stop running and just hum. In
this state, in can quickly burn out, if power to it is quickly limited.
Proper use habits are also important to keep your old appliance at peak
efficiency. Keep then clean, especially refrigerators and clothes dryers.
You can write to me for utility bills update # 619 listing manufacturers of
plug in motor controllers, specs, features, prices and efficiency tips for
using your refrigerator, freezer, clothes dryer, and washer. Please include
$1.50 and a self addressed stamped business sized envelope.
Write to: James T. Dulley,
Cut Your Utility Bills
c/o The Telegram & Gazette
20 Franklin St.
P.O. Box 15012, Worcester Ma. 01615-0012
|
291.893 | | JUPITR::HILDEBRANT | I'm the NRA | Tue Jul 13 1993 15:30 | 6 |
| RE: .8
Read the article in the paper. I still doesn't have the details on just
how they work.
Marc H.
|
291.894 | diagram from the demo literature | AIRBAG::SWATKO | | Tue Jul 13 1993 17:53 | 17 |
| If I remember correctly, the demo if the GreenPlug at Home Depot has a
diagram showing a regular sine wave and a clipped sine wave. The clipped
sine wave, instead of varying from 0 to Max and back gets clipped so the Max
to 0 part is not present. (Crappy ASCII diagram follows - this is from
memory now...). Presumably this has something to do with it - I dunno
enough about the subject to know it that's how it works or not.
+++ +++ vs. +++ +++
++ ++ (regular) ++ ++ !! ++ + (clipped) ++ +
+ + + + !! + + + +
+ + + + !! + + + +
-+-----------+-----------+-----------+!!+------++++++------++++++------++++++-
+ + !! + +
+ + !! + +
++ ++ !! ++ +
+++ !! +++
-Mike
|
291.895 | | JUPITR::HILDEBRANT | I'm the NRA | Tue Jul 13 1993 18:42 | 7 |
| RE: .10
That type of waveform would have a lot of higher order frequencies.
Those frequencies would not produce useful work...just heat.
Doesn't sound correct.
Marc H.
|
291.896 | If memory serves correctly... | STRATA::CASSIDY | | Wed Jul 14 1993 04:20 | 13 |
|
+++ +++ vs. +++ +++
++ ++ (regular) ++ ++ !! ++ + (clipped) ++ +
+ + + + !! + + + +
+ + + + !! + + + +
-+-----------+-----------+-----------+!!+------++++++------++++++------++++++-
+ + !! + +
+ + !! + +
++ ++ !! ++ +
+++ !! +++
That reminds me of the waveform produced by a dimmer or speed
control.
|
291.897 | SCR | JUPITR::DERRICOJ | Brian Rost Library_Card holder | Mon Jul 19 1993 06:10 | 18 |
|
+++ +++ vs. +++ +++
++ ++ (regular) ++ ++ !! ++ + (clipped) ++ +
+ + + + !! + + + +
+ + + + !! + + + +
-+-----------+-----------+-----------+!!+------++++++------++++++------++++++-
+ + !! + +
+ + !! + +
++ ++ !! ++ +
+++ !! +++
If the second waveform is correct, it's probably controlled by an SCR. It
probably also has an IC that senses and controlls the current.
/J
|
291.898 | Kind'a expensive still | VICKI::DODIER | Food for thought makes me hungry | Tue Jul 20 1993 20:33 | 5 |
| If there is any kind of market for these things, competition will
drive the cost down fairly quickly. At $35 a pop, the return on
investment doesn't quite seem worth it.
Ray
|
291.899 | | QUARK::LIONEL | Free advice is worth every cent | Wed Jul 21 1993 01:32 | 9 |
| If the circuit design is patented well enough, that will make ity
difficult to come out with competing products. What will drive
the price down is not enough people willing to pay $35.
I'm back to just one GreenPlug which I have on the dehumidifier
(which runs year-round); I switch it to an AC unit for those few
days we need one.
Steve
|
291.872 | Wall Unit Wiring | TROOA::STOIKOS | Constantly Confused | Wed Aug 11 1993 17:41 | 19 |
| This question is not about dimmer switches but is about in-line
wiring.
I have a wall unit which has three separate lights (one in each section).
Only one of the lights has a outlet plug on it with an in-line switch.
The lights are set up so that each light has two wires attached to it; one has
a plug and one has a recepticle so that each light can be connected to the
others so that all can be controlled by the one in-line switch.
Wall
|
=<--------switch------light-----=<-----light-----=<-----light-----=
|
What I would like to do is to put each light on a separate switch so that any
one or any other combination of lights can be turned on independently of each
other. I would like to use one power supply so I don't have to take up three
recepticles in the family room just for these lights.
|
291.873 | Or get an outlet strip... | STRATA::CASSIDY | | Thu Aug 12 1993 03:49 | 3 |
| rep .6
Put a switch on each light.
|
291.900 | lower price for GreenPlugs | WRKSYS::SEILER | Larry Seiler | Fri Aug 27 1993 17:51 | 14 |
| My local Home Quarters (Shrewsbury Mass) is selling GreenPlugs for a
bit over $36 each. HOWEVER, Spags is selling them for $28.85. So I
bought one at Spags and took it and the receipt to Home Quarters to
ask for their 10% discount off competitors' prices. That brings the
price per GreenPlug down to $26 plus tax -- *much* nicer.
Unfortunately, the refrigerator/freezer greenplug makes my freezer
start clicking after it has run for a few seconds. However, the
AC version works fine on my AC and dehumidifier. I also got the
washer/gas drier plug (one plug can support both machines), but I
haven't tried that one out yet, nor have I tried my refrigerator.
Enjoy,
Larry
|
291.901 | | KAOFS::S_BROOK | DENVER A Long Way | Wed Sep 08 1993 03:36 | 17 |
| The waveform looks like it is a dimmer waveform, except that the
clipped part of the wafeform is on the LEADING edge of the sinusiod
after the zero crossing ... this is on the trailing edge, when the
motor is pushing due to inertia.
This will in fact provide a form of power factor correction, at least
for that portion of the sinusoid, because the Inductive circuit will
not be pushing power back into the supply out of phase (the ELI the
ICE man thing again ... boy my E.Eng. degree is of use again!)
The soft start so called may be a problem with the fridges etc with
more efficient compressors, especially if the motor stopped on the
verge of a compression stroke (like stopping your car in front of
a sleeping policeman ... hard to get over without a LOT of revs!)
Stuart
|
291.902 | GreenPlug = zero savings for me | AIRBAG::SWATKO | | Wed Sep 22 1993 14:47 | 25 |
| Ya, my diagram in one of the previous replies is wrong. It should be
clipped on the leading edge, not the trailing edge. I also saw on the
package that it changes the voltage to 106V.
I just bought a GreenPlug for my fridge ($28 from Home Depot). The fridge
ran okay but I didn't notice any difference in noise, etc other than the
light in the fridge was dimmer.
So I wanted to see how much electricity I was *really* saving so I did a
little empirical experiment, much like their GreenPlug demo. With
everything electrical shut off in the house (within reason), when the fridge
was running with the GreenPlug installed, I went out to the electric meter
and timed how long to took to do a complete revolution of the "spinner".
Then I came back in and removed the GreenPlug, waited till the fridge came
on again, and timed the electric meter again. The results... no
difference. The GreenPlug was saving no electricity in my case. I repeated
the experiment a few times and got the same results.
I have an old fridge so maybe it constantly draws a lot of power thus not
allowing the GreenPlug to do its thing. I dunno. All I know is that I'm
taking the GreenPlug back for a refund. Your results may vary - I would be
interested in hearing the results if others do the same experiment.
-Mike
|
291.903 | | KAOFS::S_BROOK | DENVER A Long Way | Wed Sep 22 1993 15:22 | 11 |
| If the clipping is on the leading edge, this sure isn't going to do a lot
to correct the power factor. The apparent voltage reduction is due to
reading the chopped waveform with a meter designed to read the RMS voltage
of a sine wave. The peak voltage remains the same as 115 * 1.414.
On the other hand, it is strange that the power consumed was not reduced.
Was there any possibility that there was other power consumption goin on
in the house which would mask the effect of the fridge (like an electric
Hot Water tank) ?
Stuart
|
291.904 | | VERGA::WELLCOME | Steve Wellcome PKO3-1/D30 | Wed Sep 22 1993 16:13 | 7 |
| If the motor is running at or near its design load (and most
refrigerator motors probably are, as the load is fixed so it's
easy to design for), my understanding is that this gizzie won't
do much of anything. If, however, you have a motor somewhere
that is oversized for its load, then this gizzie does reduce
power consumption. Or so I've heard.
|
291.905 | Too small to notice maybe ??? | VICKI::DODIER | Cars suck, then they die | Wed Sep 22 1993 16:16 | 11 |
| My *guess* is that the "spinner" will not change it's speed noticably
in the test that was done. I think that you'd at least have to run for
a day or more to see any real difference, and that wouldn't be in the
"spinner", it would be in the least significant dials/digits.
There are other factors to account for that make it pretty tough
to isolate the savings over a day or more, such as whether you have an
electric hot water heater, electric range, washed laundry/dishes that
day, how many times you opened the frig and for how long, etc..
Ray
|
291.906 | | AIRBAG::SWATKO | | Wed Sep 22 1993 20:21 | 34 |
| There were no other major electrical appliances running or lights on at the
time I did the tests (my hot water is gas-fired). What little there was
running (clocks, nightlights, etc) only amounted to a tiny bit of background
noise. When the fridge was not running, the "spinner" hardly moved at all.
If you have not seen it, the GreenPlug demo in the store has a motor (*with
no load*) hooked up and a standard-looking electric meter. There are two
buttons on the demo panel. Pressing the red one activates the motor without
the GreenPlug and the "spinner" on the electric meter spins away like nuts.
Press the green button which diverts power through the GreenPlug and the
"spinner" visibly runs much slower than before, maybe half to 2/3 of the
speed produced by the red button.
My own test yielded no such "spinner speed" difference. Even timing the
spinner with a stopwatch did not yield a measurable difference. I timed 1
revolution of the spinner to be 86 seconds with and without the GreenPlug.
Even assuming that if my measurements were too crude and with GreenPlug it
actually took *87* seconds per revolution instead of 86 sec. (Grabbing
calculator) that comes out to a savings of about 12 spins of the spinner per
day if my fridge motor ran 24 hours per day (which it does not). Say the
fridge actually runs only 15 min per hour - does 3 spins per day add up to
$30 in a year? I doubt it.
I would suspect what .20 says that my 'ol fridge motor is running near
capacity and (if the GreenPlug is working at all) it senses the motor needs
all the juice it can get so it is passing all voltage straight through.
Whatever the case, the demo in the store had me expecting a visible
difference. I hoped to measure the before/after power consumption in terms
of percentage. My reasoning is that if the percentage is too small to
measure for the one appliance in question, then it cannot possibly put a
dent in my electric bill when you figure it's only one of many electrical
appliances, the others of which do not have GreenPlugs attached to them.
-Mike
|
291.907 | | AIRBAG::SWATKO | | Wed Sep 22 1993 20:44 | 13 |
| Oh, another thing - I was able to measure via the electric meter "spinner"
method the difference between one normal 60 watt light bulb vs. *two*
60-watt-equivalent compact fluorescent bulbs (actual rating 18 watts each).
The compact fluorescents combined put out a light equivalent of 2 60watt
normal bulbs while using only 2/3 of the power of a single 60watt bulb.
That matches up with the stats given with the compact fluorescent bulbs.
I figured that if I could verify the savings of a couple of light bulbs, I
certainly should be able to detect a difference with the fridge and the
GreenPlug.
-Mike
|
291.908 | Different meter type ??? | VICKI::DODIER | Cars suck, then they die | Thu Sep 23 1993 12:49 | 11 |
| The Green plug demo I saw had a digital display indicating the
power consumed. I forgot what the difference was, but if you can see
the difference in light bulbs then perhaps your meter is different than
mine.
If I watch mine spin without any major electrical device running
(i.e. dryer, toaster, stove/oven) my spinner makes a rotation about
once every 7-10 seconds. At a guess, my average consumption is around
700 KWH per month in the summer.
Ray
|
291.909 | Are you sure everything was unplugged / turned off? | TALLIS::KOCH | DTN244-7845 If you don't look good, Digital doesn't look good. | Thu Sep 23 1993 21:02 | 7 |
| > If I watch mine spin without any major electrical device running
> (i.e. dryer, toaster, stove/oven) my spinner makes a rotation about
> once every 7-10 seconds. At a guess, my average consumption is around
> 700 KWH per month in the summer.
If it only takes 7 seconds to go around, you have a lot going on!
Just clocks and timers is more like 70 seconds.
|
291.910 | I'll have to check | VICKI::DODIER | Cars suck, then they die | Fri Sep 24 1993 14:46 | 5 |
| Now you've got me curious. This is just from memory, so I'll have
to go check now. I know that my average consumption though is around
700 KWH which amounts to about $85 per month.
Ray
|
291.911 | GreenPlug save any money? | ISLNDS::BRENNAN_P | | Tue Nov 02 1993 13:25 | 48 |
| I got this out of the Nov 1993 Consumer Reports p694. Typed quickly
without any review or permision.
"Can a fancy plug cut energy costs?
Two devices recently cought our eye because they claim to significantly
reduce the amount of electricity used by refrigerators and outher
household appliances.
Both the GreePlug Electricity Saver $35, and the Energe Buster
Motordyne, $80 plus shipping, say they can reduce energy consumption up
t 25 percent a year, an annual saving that could amount to $50 or more
with an older refrigerator.
These plug-in devices are line-voltage controllers that switch power to
an appliance on and off 120 times per second. Proponents of the volage
controllers say that reduces the line voltage, hence the amount of
electricity, hence your utility bill. The Green Plug (Green
Technologies, Boulder, Colo.) is meant only for refrigerators or
freezers. The Energy Buster ( Condyne Technology, Longwood, Fla.),
works on any 120 volt induction motor. We tried the controllers on
four refrigerators - one brand new; two middleaged ones, aged 14 and
15; and a 24 year old antique.
We ran our standard energy-consumption tests with and without the
controllers, then used the data to figure annual running costs and
savings.
The controllers didn't even come close to a saving of 25 percent a
year. The GreePlug turned in the greater saving of the two- 8.6
percent on the antique, 3.5 percent on one of the middle aged
refrigerators. At the national average electricity rate, those savings
amount to about $20 and $4 a year, respectively. Savings with the
Energy Buster amounted to 4.7 percent (about $11 a year) at best.
Both controllers actually increased running costs by a few dollars on
the brand new refrigerator and on one middle aged model. That's not
very suprising, given changes appliance manufactures have made to
improve the performance of their products over the past two decades.
In our view, add-on gadgets to squeeze a little more efficiency out of
an older refrigerator don't make much sense. It's better simply to
replace the old hardware with new. A new refrigerator could save $80
to $150 annually, paying for itself in a few years. Thats a much more
impressive saving than either the GreenPlug or the Energy Buster
provide."
|
291.912 | | QUARK::LIONEL | Free advice is worth every cent | Tue Nov 02 1993 13:59 | 5 |
| I was annoyed that CU ignored the other two GreenPlug models, in particular
the AC/dehumidifier model which is the only one which I think has a chance of
being useful.
Steve
|
291.913 | Report didn't cover wear and tear | ISLNDS::BRENNAN_P | | Tue Nov 02 1993 15:06 | 4 |
| Also CU didn't discuss extending life of appliance. If I can make my
20 year old frig use less energy and live longer, I can spend major
money ($500-700) for new frig later?
|
291.914 | | NOVA::SWONGER | DBS Software Quality Engineering | Tue Nov 02 1993 17:57 | 6 |
| First of all, testing the wear and tear would be very difficult.
More important, given the minimal energy savings of the plug and the
vast savings of a more efficient refrigerator, making your
20-year-old refrigerator last longer will be a bad deal anyway.
Roy
|
291.915 | Greenplug - cost analysis is never easy | ISLNDS::BRENNAN_P | | Wed Nov 03 1993 12:37 | 19 |
| RE .30
I'm sorry, I think I led you to believe I was advocating the use of the
GreenPlug. While testing wear and tear would be very difficult, I
simply wanted to indicate that if it does occur, it may enter into a
cost analysis. For me the analysis is further complicated because that
we plan to put the house on the market in the next 12-18 months and I
would be hard pressed to come up with the capital for a new
refrigerator. Our current Kitchen appliances are not the color we will
choose for the next kitchen. I don't believe I would save enough money
to cover the cost of capital? I bought the toy prior to reading the
Consumer Reports article and did one of those in your head analysis
where I got a new toy, saved some electricity, and extended the life of
my frige while spending too much at the hardware store anyway. If you
any ideas how I might perform some more precise cost analysis, I'm
interested. I expect I could find someone to buy the plug used for
$15-20.
paul
|
291.916 | Any REAL numbers avialable? | GNPIKE::MIKELIS | war is a crime against humanity | Wed Nov 03 1993 14:09 | 14 |
| I'm a little surprised that someone here hasn't done an accurate assessment
of how much current the appliances with and without the devices actually draw
using a watt-meter. It would be pretty easy to figure out the savings from
there.
I think i'll pick up one of those gizmos soon at Spags and do some
benchmarking experiments on my own. I'd be interested in seeing the
benefits of using one on my dehumidifier.
I remember seeing plans for a similar device - oh, it must of been 20
years ago in Popular Electronics. Amazing it took so many years to publically
hit the market considering their alleged energy savings.
/james
|
291.917 | Every Little Bit May Help | SALEM::GAGER | Swap Read Error-You loose your mind | Wed Nov 03 1993 14:44 | 8 |
| RE:32
<I remember seeing plans for a similar device - oh, it must of been 20
<years ago in Popular Electronics. Amazing it took so many years to
<publically hit the market considering their alleged energy savings.
Yea, but twenty years ago the cost of electricity didn't make it
too feasible. PSNH rates makes you want to try anything.
|
291.918 | Noise source | CIMBAD::CURTIS | | Wed Nov 17 1993 19:34 | 10 |
| I wonder how well the switching transients are filtered.
Every once in a while, I enjoy short wave listening, and
AM radio. The triac/SCR controlled devices can generate
RF interference that can really get on your nerves. At
least with light dimmers (or other noise sources such as
flourescents and TV's) you can shut them off. The frig
has a mind of it's own. It's not a good idea to unplug it
for some peaceful SWL'ing.
Chet
|
291.824 | Local code may dictate | REFDV1::CALDERA | | Mon Jan 03 1994 21:22 | 6 |
| I have used both and have had electricians use both, they don't mahe
shallow plastic boxes. As for "This Old House" they do a lot of shows
on house in BOSTON proper and I think that there is a code in Boston
that only allows metal, I heard that I don't know how true it is.
Paul
|
291.825 | Fiberglass also available | STAR::DZIEDZIC | Tony Dziedzic - DTN 381-2438 | Tue Jan 04 1994 10:49 | 15 |
| There is another type of box which hasn't been mentioned - fiberglass.
These are a LOT sturdier than the flimsy blue or gray plastic boxes
which you can pick up at home centers. The fiberglass boxes also
stand up to drywall cutout router bits a lot better than the plastic
boxes. These were the type used when the electrician wired our
house; I also used them when I finished off the basement. As far
as Nashua goes, the inspector approves of them; your mileage in
other cities may vary.
I purchased the fiberglass boxes at M&M Lighting and Electrical
in Nashua (on Lowell Street, right off Main Street). They had
single, double, triple, and quad gang rectangular, and a few
different sizes of octagonal (round), plus other variations.
Offhand, I BELIEVE a single rectangular cost about 25 cents, but
I'm only going from a 2-year-old memory here.
|
291.826 | usually dark brown in color | HNDYMN::MCCARTHY | Back to BASICs | Tue Jan 04 1994 13:00 | 12 |
| The fiberglass boxes mentioned in .4 do take a great deal more abuse than the
standard plastic boxes. The problem with them is, while mounting, if you hit
the box, it shatters. They usually come with clamps also. You can also get
many different styles (for example, if you have a very narrow stud cavity you
can get one with a "flag mount" (I belive that is what it was called) where you
nail it to the front of the stud instead of the side. Comes in very handy in
tight places.
I guess they would stand up better to the drywall cutter, I'll have to test
that out some day :-)
Brian
|
291.827 | | JUPITR::HILDEBRANT | I'm the NRA | Tue Jan 04 1994 16:26 | 4 |
| Maybe I'm out of date, but, I always use the metal boxes. The price
increase is small, and they are rugged.
Marc H.
|
291.828 | | SOLVIT::CHACE | My favorite season is getting nearer! | Tue Jan 04 1994 17:46 | 6 |
|
I'm with you, Mark. For most any job the boxes are a tiny fraction of
the cost. Not only that, my time is waaaay too valuable to mess around
with small things that I don't have to.
Kenny
|
291.829 | | QUARK::LIONEL | Free advice is worth every cent | Tue Jan 04 1994 18:07 | 7 |
| I used to use plastic boxes all the time, especially the "old work"
boxes. But I stopped when my wife complained that they made
wallpapering over them difficult (because they stick out too much).
Now I use metal boxes with either the bend-over wallboard clamps or
the kind with the built-in screw-tight clamps.
Steve
|
291.830 | I like some things about both | WEDOIT::DEROSA | Can't see it from my house | Mon Jan 10 1994 15:17 | 10 |
| I've used both metal and plastic. What I don't like about plastic
boxes is in new construction, there's no room for error in cutting
the hole in the sheetrock because they seem to be a "tad" bigger
than metal boxes. I also like the durability of the metal ones.
What I do like about the plastic ones is the little extra room
you get for wires.
For me, it depends on what's available at that time at the store.
/BD
|
291.831 | Works especially well on thermostats mountings | BROKE::TAYLOR | Holiday shoppers wear my brakes out | Wed Jan 12 1994 15:54 | 11 |
| The major advantage I see in the fiberglass boxes is that, if you are
concerned with air infiltration, the boxes can be caulked shut
(airtight) very easily, since the whole box is already pretty much
sealed. You poke the wire holes in the box where you need them, remove
the cable clamp over your wiring, caulk around the wire, replace the
clamp, and all that's left to do is to run a thin bead of sealant
around the hole in the wall for the box. You then have a sealed box,
and leave the infiltration problems to the windows, which already leak
more than enough.
Mike
|
291.832 | clamps? | NETRIX::michaud | Jeff Michaud, PATHWORKS for Windows NT | Wed Jan 12 1994 17:57 | 5 |
| > ... remove the cable clamp over your wiring ... replace the clamp ....
cable clamp? I haven't been using any clamps with the plastic
boxes, I assumed they were only needed on the metal boxes because
of the sharp edges on the metal cutout????
|
291.833 | | MIYATA::LEMIEUX | | Wed Jan 12 1994 18:44 | 16 |
| You need them on the plastic boxes also. The clamp keeps the wires in the box
and any potential cable burn back limited to the box. Also helps seal the hole
the cable entered the box from.
The Metal VS plastic is a religious war. Both types have thier pro's & cons.
Plastic are faster, cheaper and non conductive. Metal are more industructable,
slower to use and are conductive which makes them not as much fun to pull
live devices out of for trouble shooting etc. Both types have thier place.
I wouldn't use plastic boxes in a commercial building they just don't hold
up to the abuse and I wouldn't use metal boxes in a house simply because they
are just too slow to work with and are more costly. The profit margin on houses
is already too low. Although, both types of boxes are perfectly acceptable in
either location by the NEC.
Paul
|
291.834 | | QUARK::LIONEL | Free advice is worth every cent | Thu Jan 13 1994 00:14 | 5 |
| The plastic boxes have built-in "clamps" which work fairly well,
but if you bend them too far, they become useless. The NEC does
not require separate clamps on plastic boxes with built-in clamps.
Steve
|
291.835 | fiberglass=seperate and may not be required | HNDYMN::MCCARTHY | Back to BASICs | Thu Jan 13 1994 09:42 | 12 |
| The fiberglass boxes have seperate clamps that are metal and have to be
tightened via a screw. I've only bought these at electrical supply houses and
they threw them at me after I told them how many boxes I wanted (ie they were
not attached to the box.
Now according to a master electrican I was working with several years ago, the
seperate clamps did not have to be used if there was a staple on the romex(tm)
within 6 inches of the box. He agreed that this left too much play and either
used the clamps or put staples closer. Again this is ONLY with the fiberglass
boxes that do not have "pressure" clamps.
bjm
|
291.836 | must be a trick someplace.. | ELWOOD::DYMON | | Thu Jan 13 1994 10:18 | 10 |
|
I'll second the stapling 6" from the box. But all the boxes
i've used have has a square or rectangular hole wiht a pressure
clip. You push the wire in and its a real pain to get it back
out.
Now, tell me how you fit a round clamp in square hole. I'll
go back and rewire my house.....
JD
|
291.837 | Heres the clamp code | MIYATA::LEMIEUX | | Thu Jan 13 1994 13:00 | 31 |
| Here's the scoop on what nonmetallic boxes need clamps etc.
1990 NEC (I've only got the 90 book in the office I'll verfy with 93 later )
Art 370-7 Conductors entering boxes, conduit bodies, or fittings
(c)Nonmetallic boxes
I didn't type in the entire paragraph but it goes on to say a bunch of stuff
about knob and tube, flex and other accepted wiring methods and then states:
"Where nonmetallic sheathed cable is used, the cable assembly, including
the sheath shall extend into the box no less than 1/4inch through a nonmetallic
cable knockout opening. In all instances all permitted wiring methods SHALL be
secured to the boxes."
"EXCEPTION: Where nonmetallic sheathed cable is used with boxes no larger than
a nominal size 2-1/4 X 4 mounted in walls and where the cable is fastened within
8 inches measured along the sheath andwhere the sheath extends into the box no
less than 1/4 inch securing the cable to the box shall not be required."
**********
What this all means is you must use clamps in all plastic boxes (fiberglass too)
for all but the small 1 gang boxes where it's allowed not to use the clamps.
If the clamps are thrown in the case but not attached to the box when you buy
them you still have to install them to comply with NEC. The cable has to be
secured (stapled) within 8 inches of the box to comply. (Note that the ruling
for NM cables secured near a box is 12 inches. The rule for plastic boxes
shortens that distance if you plan on not using the clamp in a 1 gang box.)
|
291.838 | | MIYATA::LEMIEUX | | Thu Jan 13 1994 13:04 | 10 |
|
< But all the boxes
< i've used have has a square or rectangular hole wiht a pressure
< clip. You push the wire in and its a real pain to get it back
< out.
From your description the boxes you used had the automatic type of
clamps built in. I'll almost bet the 1 gangs didn't have any clamps
present in them. Most don't today.
|
291.839 | | CSC32::S_BROOK | There and back to see how far it is | Thu Jan 13 1994 15:45 | 5 |
| Just out of curiosity, is there anything in NEC about caulking the
cable outlets ? Non metallic boxes have only recently arrived in Canada
and the code really only addresses non-metallic conduit boxes.
Stuart
|
291.840 | No requirments to seal used openings | MIYATA::LEMIEUX | | Thu Jan 13 1994 16:14 | 15 |
| <Just out of curiosity, is there anything in NEC about caulking the
<cable outlets ? Non metallic boxes have only recently arrived in Canada
There is a little blurb about closing unused holes with fittings in a non
metallic box but Nothing requires us to caulk around the cable/hole to further
seal it after installation. Wouldn't surprise me to see become a requirement in
the future though. It sounds sensible enough.
We are required to make sure the box has no gaps greater than 1/8Inch around the
opening it creates in the drywall. It must also be flush with the front surface
if the wall is combustible and no further than 1/4inch recessed if the wall is
non combustible IE drywall, plaster etc. How does the Canadian code handle the
nonmetallics?
Paul
|
291.841 | | CSC32::S_BROOK | There and back to see how far it is | Thu Jan 13 1994 17:18 | 20 |
| >There is a little blurb about closing unused holes with fittings in a non
>metallic box but Nothing requires us to caulk around the cable/hole to further
>seal it after installation. Wouldn't surprise me to see become a requirement in
>the future though. It sounds sensible enough.
I was actually expecting to see things ANTI-CAULK to be hones, on the grounds
that the caulk, particularly when fresh and gassing off, could be more
flammable !
>We are required to make sure the box has no gaps greater than 1/8Inch around the
>opening it creates in the drywall. It must also be flush with the front surface
>if the wall is combustible and no further than 1/4inch recessed if the wall is
>non combustible IE drywall, plaster etc. How does the Canadian code handle the
>nonmetallics?
I hadn't seen a recent enough code to deal with non-metallic boxes, although
the round ones do add some interesting twists to grounding, since they DON'T
have a grounding connection, and still use metallic lids!
Stuart
|
291.842 | | MIYATA::LEMIEUX | | Thu Jan 13 1994 17:35 | 20 |
|
<<I was actually expecting to see things ANTI-CAULK to be hones, on the grounds
<<that the caulk, particularly when fresh and gassing off, could be more
<<flammable !
Thats a good point.
A little off the subject but somewhat related is the method thats used
to seal the end caps on Thermaray radiant ceiling panels. They are
approved by UL and I think CSA as well, to use drywall
compound as the sealing medium. (By the way Thermaray is produced by
a company called CANray up in New Brunswick Canada). I've also seen
drywall compound used to firestop small drill holes between floors of
buildings too. I suppose if they ever required the gaps to be filled
they would acceptan already used method....merely speculation on
my part, In reality I hope they never go that route. Just one more
operation to perform during a rough-in.
Paul
|
291.843 | | CSC32::S_BROOK | There and back to see how far it is | Thu Jan 13 1994 18:35 | 4 |
| The problem with using drywall compound is that it is not airtight and
shrinks too much on drying. The only advantage is that it is non-flammable.
stuart
|
291.844 | | MIYATA::LEMIEUX | | Thu Jan 13 1994 18:44 | 3 |
| Apparently UL wasn't concerned with the amount of shrinkage in the case of the
radiant panels. They approved both the method and the product. I've installed a
lot of it without any problems.
|
291.845 | Correct outlet height in cellar | GIAMEM::PBROUGH | Operating within established parameters | Mon Jan 17 1994 17:42 | 7 |
| I am finishing my basement, and I want to wire it as well, however
I don't know what the height is supposed to be for outlets in the
basement, is it the same height as the rest of the house.
Another question, I know that I can get this from the store, but I
want to wire my workshop with a 20 amp circuit, rather than the
standard 15 amp. Is the correct gauge 12 for this purpose?
|
291.846 | | JUPITR::HILDEBRANT | I'm the NRA | Mon Jan 17 1994 18:22 | 10 |
| RE: .24
I would suggest that if you do not know the answers to those questions,
that you buy a book on the current code (i.e. wiring simplified) before
continuing. Your questions indicate a lack of the basic info.
I'm not saying don't do the work...but, you really need to know more
than what the correct wire size is to do a good job.
Marc H.
|
291.847 | | NETRIX::michaud | Jeff Michaud, PATHWORKS for Windows NT | Mon Jan 17 1994 21:05 | 7 |
| Yes, 12 guage for 20 amp circuit, 14 guage for a 15 amp
circuit. Very important is that the breaker be no higher
amperage than what the thinist guage wire on the circuit
can handle (ie. even if 99% of the circuit is wired with
12 guage wire, if you have something wired into the
same circuit using 14 guage wire, the breaker must not
be larger than 15 amps).
|
291.848 | You didnt hear it here | ELWOOD::DYMON | | Tue Jan 18 1994 10:48 | 6 |
| Seem to recall something in here on the subject.....
But going out on a limb again... New wiring has
to be 12g/20a circuits. and 15"for the floor rings a bell.
but as always....CONSULT YOUR LOCAL CODE.
JD
|
291.849 | | MIYATA::LEMIEUX | | Tue Jan 18 1994 13:28 | 12 |
| <<Seem to recall something in here on the subject.....
<< But going out on a limb again... New wiring has
<< to be 12g/20a circuits. and 15"for the floor rings a bell.
Nothing in NH and Ma. codes require any of the above in general lighting
circuits in a residence. You may may find that there are some building codes
for handicap access that require the outlets and switches be at a certain
heigth from the floor but nothing in NEC.
<< but as always....CONSULT YOUR LOCAL CODE.
Good Idea....
|
291.850 | could be a useful safety feature | SMURF::WALTERS | | Tue Jan 18 1994 14:40 | 10 |
|
If you plan to put any electronics down there, and codes allow it
you may want to put the power outlets for these at a higher level.
I didn't do this, but on reflection it would have been a good idea
as all this stuff is up on shelves away from little fingers, but the
power cables are still in easy reach of the kids.
Colin
|
291.851 | | WRKSYS::SEILER | Larry Seiler | Fri Mar 25 1994 18:16 | 20 |
| Late entry -- when I was doing my garage I found a place where the NEC
said that I didn't need any sort of clamp at all in my plastic boxes
-- not even the pressure clamp that comes on some of them. However,
with no clamp I had to staple them within 3". That's sometimes a pain,
but it doesn't provide much play inside the box.
Since I was worried about air infiltration, I caulked the holes shut.
Boy, that's a lot easier with a plastic box! But since I didn't know
how flammable the caulk might be, I first filled in around the wires
with nonflammable electrician's putty -- cheap stuff, and designed for
the purpose of plugging a conduit.
Finally, whether you need to place the outlets high in your finished
basement probably depends on whether your electrical inspector
considers it living space or basement space. Definately, you need
to have outlets high off the group (I think 4'?) in a basement.
As usual, consult your local code official.
Enjoy,
Larry
|
291.852 | | MIYATA::LEMIEUX | | Fri Mar 25 1994 22:32 | 12 |
| <Definately, you need
< to have outlets high off the group (I think 4'?) in a basement.
< As usual, consult your local code official.
Not as far as NEC is concerned. There are no height requirments for receptacle
locations in NEC for residential wiring. Your local mileage may vary.
I think is a requirement in commercial garages and aircraft Hangers if the
receptacles are not to be rated explosion proof....but I'm not sure on this
one without looking it up.
Paul
|
291.853 | I hope the pro knows the code | VMSSPT::STOA::CURTIS | Dick "Aristotle" Curtis | Sun Mar 27 1994 22:11 | 7 |
| .30:
I certainly hope the requirement isn't 4' from the floor, or I'm going
to have to remove all the wallboard before having the electrician
rework everything he did.
Dick
|
291.854 | | FREBRD::POEGEL | Garry Poegel | Mon Mar 28 1994 13:16 | 13 |
|
>> <<< Note 5195.32 by VMSSPT::STOA::CURTIS "Dick "Aristotle" Curtis" >>>
>> -< I hope the pro knows the code >-
>> I certainly hope the requirement isn't 4' from the floor, or I'm going
>> to have to remove all the wallboard before having the electrician
>> rework everything he did.
I had my basement finishing project inspected a few months ago (Hudson,NH).
All the outlets are 16" off the ground but all are on a GFCI.
Garry
|
291.855 | | JUPITR::HILDEBRANT | I'm the NRA | Mon Mar 28 1994 13:57 | 6 |
| In an unfinished basement, the general procedure is to run the power to
the outlets in metal pipe when the line is below grade.
When the area is finished, does the rules change, even if below grade?
Marc H.
|
291.856 | | MIYATA::LEMIEUX | | Mon Mar 28 1994 14:37 | 21 |
| >In an unfinished basement, the general procedure is to run the power to
>> When the area is finished, does the rules change, even if below grade?
The wire run in pipe doesn't have anything to do with grade or finish
of the basement...It has to do with securing the wire and possibly
protecting it from damage. You could just nail a running board onto
the concrete wall and secure the wire and the box to it. It's legal
but it's kludgy but I've seen it done quite a bit.
So the answer to your question is: You don't have to run conduit for a
finished basement.
The only rule that comes into play that mentions below grade space
directly, is used when determining how many stories a building has. The
number of stories is a factor in wiring methods. IE, anything over 3
floors, romex isn't allowable.
Hope this helps
Paul
|
291.857 | | SMAUG::FLOWERS | IBM Interconnect Eng. | Mon Mar 28 1994 17:13 | 7 |
| > The wire run in pipe doesn't have anything to do with grade or finish
> of the basement...It has to do with securing the wire and possibly
> protecting it from damage.
...yup, like the damage of a power tool cutting or ripping into it :-(
Dan
|
291.858 | | JUPITR::HILDEBRANT | I'm the NRA | Mon Mar 28 1994 17:31 | 5 |
| RE: .35
Thanks...clears up a minor mystery I've had.
Marc H.
|
291.859 | | WRKSYS::SEILER | Larry Seiler | Mon Apr 04 1994 19:02 | 7 |
| Hmm... NEC does say 4' from the floor in "wet locations". Inside a
residence, including in finished rooms in a basement, this isn't a
problem. My inspector considers a garage a wet location, however,
hence 4' off the ground *and* GFCI. It's all in the interpretation.
And as usual, the building inspector is always right.
Larry Seiler
|
291.993 | Green Plug Energy Savers | VMSSG::DEANE | | Tue May 17 1994 15:55 | 10 |
| Anyone have any comments (pros/cons) about an item (sold locally
at Home Depot) called "Green Plug" which claims to save big bucks
in electricity on your washer/dryer, refridgerator, etc? Do these
things work? They are $29 each. Has anybody (Radio ELectronics, for
example) published a schematic for these things? How do they save $$$?
Bottom line: Are they worth it?
Tom Deane
|
291.994 | CR wasn't impressed (for what that's worth) | 9251::BECK | Paul Beck, TSEG (HYDRA::BECK) | Tue May 17 1994 16:05 | 4 |
| Consumer Reports had a column on them in a recent issue (one of the early
pages "briefly noted" type columns) and indicated that they didn't seem to
be worth it. Sometimes they'd save, sometimes not, but (if memory serves)
not enough to recoup their cost.
|
291.995 | | LEZAH::WELLCOME | Steve Wellcome MRO1-1/KL31 Pole HJ33 | Tue May 17 1994 16:28 | 21 |
| There's another note in here someplace about them, I think.
My understanding is that they save energy only when the motor is
running underloaded. If the motor is pulling its rated load, then
the savings are minimal, if any.
Since the load in nearly all appliances can be quite accurately
predicted (e.g. the load imposed by a refrigerator compressor
is fixed), the motors can be chosen such that they run at or
near their rated capacity, and the greenplugs won't save much, if
anything.
Notice that the demo of the greenplug they sometimes have is done
with a motor running with no load at all.
If you have a situation where the load on a motor changes dramatically,
so the motor is often running very underloaded for its size, then a
greenplug might save you something.
My understanding, anyway...not guaranteed correct.....
|
291.996 | One point of information | ZENDIA::ROLLER | Life's a batch, then you SYS$EXIT | Tue May 17 1994 16:42 | 79 |
| I pulled this off the internet a while back. It's one datapoint,
take it for what it's worth.
Ken
Article: 23384
Newsgroups: sci.energy,sci.electronics,misc.consumers.house
Path: nntpd.lkg.dec.com!nntpd2.cxo.dec.com!pa.dec.com!decwrl!concert!gatech!holos0!rsiatl!jgd
From: jgd@dixie.com (John De Armond)
Subject: Green Plug 1, Refrigerator 0
Message-ID: <ty94!sr@dixie.com>
Date: Sat, 12 Mar 94 07:46:34 GMT
Organization: Dixie Communications Public Access. The Mouth of the South.
Keywords: smoke, flames
Lines: 60
Xref: nntpd.lkg.dec.com sci.energy:23384 sci.electronics:81375 misc.consumers.house:66360
Back in November I posted some preliminary results of my testing under
actual conditions, a Green Plug with a 1977 yearmodel Hotpoint Model
CTF18C refrigerator and some squirrel-cage fans. I promised that I
would post the long term tests on the refrigerator when they were
completed. The long term energy consumption tests were complete in
February but I decided to wait until now to post so as to let a process
I saw developing run to completion. The process was the destruction of
the compressor in this refrigerator. The refrigerator fired back by
destroying the green plug.
The process started back in January when I started seeing on the
attached recording ammeter an increased duration of starting current.
This increase appeared to be caused by the "soft start" feature (sic) of
the green plug that is supposed to limit inrush current. At the time I
got the green plug, I thought it foolhardy, because limiting starting
current drags out the starting process which actually subjects the motor
winding to MORE heat. Shortly after I noted this increased starting
duration, the refrigerator tripped the GFI on the circuit it was plugged
into. Prime evidence that the winding insulation in the compressor was
degrading.
I decided to let this play itself out so I plugged the refrig and green
plug into a non-GFI outlet. The refrigerator continued maintaining the
temperature setpoint as indicated by the digital thermocouple meter
attached to the refrig. I noticed, however, that the compressor
overload would occasionally trip on excess temperature. And the total
current draw continued to creep up as the leakage current continued to
increase.
This afternoon the process ended. I heard the thermostat on the refrig
turn on and a moment later, the green plug erupted in a pleasing ball of
smoke and flame. I checked resistance between the refrigerator cord
prongs and ground. Dead short. I cracked the service fitting on the
compressor and was greeted by what is probably the worst compressor
burnout I've ever seen. This was a long term roast and not a quick
failure.
After I replace the compressor, I plan to open the shell of the old one
to inspect the damage and make sure it wasn't a tight bearing or
something else mechanical. But based on the electrical history I have,
I'm pretty positive that the green plug took out this refrigerator. I
plan on sending this device along with a letter asking them to pay for
the compressor to the factory to see what kind of reaction I get.
So the final score is this. The green plug was "saving" electricity
at the rate of about a dollar a month. Meanwhile, the replacement
compressor will cost me about $80 plus the better part of a day
to replace it and flush all the contamination out of the freon system.
I think that extra buck a month for power without the Plug was a
bargain.
John
--
John De Armond, WD4OQC, Marietta, GA jgd@dixie.com
Performance Engineering Magazine. Email to me published at my sole discretion
Tonight, suppose Washington were nuked to atoms. Ask yourself, would you
be better or worse off. This graphically frames the role of the federal
government in destroying the American way of life.
|
291.997 | | WRKSYS::MORONEY | | Tue May 17 1994 16:48 | 3 |
| Note 5016 is the previous note.
-Mike
|
291.135 | how should I wire this ? | ICS::STUART | skis + snow = fun | Mon Oct 24 1994 14:26 | 39 |
|
I'm about to wire a 3 season porch I just built.
I'll be taking the power from what existed from the original deck which
is as follows....
A switch on the inside for a spot light and constant power to a two plug
outlet. This is on a GFI circuit. I'll have to figure out what else is
on this circuit, I think it's in with the kitchen power.
I will be adding a second switch to control a light/fan and a couple outlets
if the circuit can take them. I'll be moving the spotlight to the end of the
porch and also adding another spotlight both of which will work of the
original switch.
Whats the best way to wire this up ?? I'd like constant power to the
outlets which will be on the same wall as the outside spotlights.
Should I use 3 wire or can I accomplish this with standard 2 wire. ??
crude diagram ....
switches
---- _______________________________ ----
|! ! | |fan |
---- ----
|________________________ ---- ___________________________ ----
| |spot| |spot|
| -|-- -|--
| | |
| | |
| ---- ----
---- |plug| |plug|
|plug| ---- ----
----
thanks for any help... Randy 223-2248 if it's easy to explain verbally
|
291.136 | | QUARK::LIONEL | Free advice is worth every cent | Mon Oct 24 1994 15:52 | 5 |
| You'll need some sort of third conductor to carry the switched hot line to
the lights. Three-conductor w/ground is the easiest way to do this. The
other "side" of the lights should go to the neutral conductor.
Steve
|
291.695 | Electrical - Buzzing Sound | ASABET::HUNTLEY | | Mon Nov 07 1994 16:38 | 10 |
| I installed a new dining room light and it has a buzzing sound from
the bulb. I changed bulbs and it still buzzes. The light is on a
dimmer and buzzes when it is turned down low; the sound goes away
when I turn it up to full bright. The bulb is a G40 150W. The old
light did not buzz. Could I have connected something wrong, the
ground?
Any Ideas?
Thanks
|
291.696 | Bad dimmer maybe | NOTAPC::RIOPELLE | | Mon Nov 07 1994 17:01 | 16 |
|
Can the light be used with a dimmer ? I've seen some lights that
specifically say they can not be used with a dimmer.
Maybe you have a bad dimmer. Was this a new dimmer, or an old one ?
If it's old maybe time for a new one. If it's a new one maybe replace
it with a switch, and see what happens.
Dimmers worry me. We have some friends that had a dimmer fail in their
house ( house was only 6 months old ) came home to meet a fire truck,
and no house one night after a nice dinner. Faulty dimmer.
We have one in our dining room. I constantly check it.
|
291.697 | | QUARK::LIONEL | Free advice is worth every cent | Mon Nov 07 1994 18:32 | 4 |
| It's common for dimmed bulbs to buzz - a lot may depend on the
design of the bulb filament.
Steve
|
291.698 | bulb-dependent, not uncommon.. | TEKVAX::KOPEC | Packin' ta move.. | Wed Nov 09 1994 14:00 | 3 |
| Try a different bulb, from a different manufacturer.
...tom
|
291.699 | Cheap voltage regulators don't always work | CSLALL::NASEAM::READIO | A Smith & Wesson beats four aces, Tow trucks beat Chapman Locks | Wed Nov 09 1994 15:15 | 9 |
|
My lights stopped buzzing when I replaced the dimmer switches with
better-designed units.
A bit more circuitry seems to be the answer. The cheap ones only had a
couple of components (transistor, resistor, pot)
|
291.700 | My lights are S9+20.. | TEKVAX::KOPEC | Packin' ta move.. | Wed Nov 09 1994 15:22 | 6 |
| I've found some correlation between dimmers that seem to be susceptable
to bulb-buzzing and the amount of RFI that the dimmer generates. With
the winter 160-meter Ham season coming 'round, I'm going to have to go
hunt down all the noisy dimmers in the house 8-(
...tom
|
291.701 | cheap dimmer = major hum problem! | WRKSYS::RICHARDSON | | Wed Nov 09 1994 15:25 | 10 |
| Yup - there was a dimmer in the sanctuary at our synagogue that
generated so much RF that it was getting into the PA system! Since
there wasn't any real good reason for there to be a dimmer there
anyhow, we replaced it with a real silent mercury switch (I didn't
think they still made them! - had a lot of trouble finding one) that
doesn't go THUD if someone has to surreptitiously turn on the switch if
it has been forgotten. Probably a better dimmer would have worked as
well. Sure sounded awful coming out of the PA speakers...
/Charlotte
|
291.702 | More humming lights | CUPMK::WIEGLER | | Thu Nov 10 1994 19:34 | 8 |
| Here's a *somewhat* related problem. My kitchen ceiling fixture has 4
florescent bulbs. It is NOT on a dimmer switch. But the fixture does
hum sometimes. What can I do about it, or is that a characteristic of
florescent lights? Also, sometimes 2 of the bulbs light first, and
then, after a few moments, the second two bulbs decide to light also.
I replaced all 4 bulbs at the same time, but this problem still exists.
Willy
|
291.703 | | QUARK::LIONEL | Free advice is worth every cent | Thu Nov 10 1994 20:19 | 6 |
| Humming flourescent lights can sometimes be caused by a dying bulb or by
a dying or poor-quality ballast. If it's the ballast, you may not be able
to do much - you can buy new ballasts, but the old one is often welded in
place.
Steve
|
291.704 | Never ran into a ballast that wasnt replaceable | CSLALL::NASEAM::READIO | A Smith & Wesson beats four aces, Tow trucks beat Chapman Locks | Fri Nov 11 1994 11:41 | 7 |
| I've never seen a ballast that was welded in. Every one I've replaced was
either screwed in at both ends or was held in place by a screw on one end
and a tab on the other.
BTW, if you go out looking at ballasts, make sure you get the right one.
The info is printed right on the ballast. i.e. number of bulbs it'll
handle, the rating of the bulbs and the line voltage.
|
291.705 | is there a starter? | WRKSYS::RICHARDSON | | Fri Nov 11 1994 15:48 | 6 |
| It could be the starter, too, if the fixture is old enough to have a
starter - easy to replace. I never saw a welded-in ballast - I've
replaced several of them as they got old enough that we couldn't
tolerate the loud hum, and they all just bolted on.
/Charlotte
|
291.706 | | ASABET::HUNTLEY | | Mon Nov 14 1994 13:51 | 14 |
| Dimmer Problem?
Well I changed the dimmer with one of better quality - light still
buzzes. I'll probably go back to a regular switch. The guy at home
depot thought the light (G40 bulb @ 100 or 150W) is just too large
a bulb to work with a dimmer - the filament vibrates at the low light.
sounds logical - since the buzzing goes away when I turn it up all
the way. I may try a different bulb - the third one! The old light
didn't buzz because they were very small bulbs.. unlike the large one
in the new light.
Thanks
Thanks
|
291.707 | It *is* possible; keep trying combinations | SSDEVO::JACKSON | Jim Jackson | Mon Nov 14 1994 15:04 | 2 |
| I had a fixture that used a 150W G40 bulb on a dimmer, and had no problem
with buzzing, so it *is* possible to do it.
|
291.708 | | ASABET::HUNTLEY | | Mon Nov 14 1994 15:54 | 1 |
| what kind of bulb in .12 - i'll buy one!
|
291.709 | How about dimmer brand names? | HANNAH::BAY | Jim Bay | Mon Nov 14 1994 16:14 | 9 |
| Gee, I must buy cheap switches. I didn't know there was such thing as
a dimmer (or dimmer/light combo) that DIDN'T buzz. I figured you had
to give up peace and quiet for flexible lighting.
Even my X-10 stuff has a high-pitched whine. I can't hear it, but it
makes my wife mental.
Jim
|
291.710 | | TARKIN::HARTWELL | Dave Hartwell | Wed Nov 16 1994 14:33 | 6 |
| What brand/model dimmer works best here
/Dave
|
291.919 | What type of boxes for exterior outlets? | ANDREW::OSTROM | ETP Engineering Mgr. | Fri Dec 02 1994 19:05 | 16 |
|
I'm building a house (90% myself), and doing all the electrical work.
In all the work I've done before, which has been old work, all the
exterior wiring I've done has been with EMT and watertight boxes,
etc. Now, with new construction, my options are greater. I'd like
to have a few flush-mounted recepticles and some exterior lights and
such...
So, my question is -- do I need to use the solid "exterior" type
boxes, should I use "masonry" type boxes, or can I just use standard
recepticle, round, square, whatever, boxes mounted from the outside,
with normal exterior covers? I can ask the inspector next week (he's
only in Tuesday and Thursday mornings), but would like to do most of
the outside work this weekend.
Andy Ostrom
|
291.920 | leave wire in wall, so you don't end up between shingles | HNDYMN::MCCARTHY | He's here, but I'm still not ready | Sat Dec 03 1994 22:31 | 6 |
| In Quincy, MA, I have installed "old work" boxes from the outside after the
siding was put on and then put watertight covers over them. So the outlet is
inside the wall. This was done under a master electrian and was approved by
the inspector - of course, the outlets were GFCI protected....
bjm
|
291.921 | Tnanks. | ANDREW::OSTROM | ETP Engineering Mgr. | Mon Dec 05 1994 01:20 | 11 |
|
>In Quincy, MA, I have installed "old work" boxes from the outside after the
>siding was put on and then put watertight covers over them. So the outlet is
>inside the wall. This was done under a master electrian and was approved by
>the inspector - of course, the outlets were GFCI protected....
>
>bjm
Thanks, this is what I decided to do.
Andy Ostrom
|
291.922 | | QUARK::LIONEL | Free advice is worth every cent | Mon Dec 05 1994 12:22 | 7 |
| If you intend to leave something always plugged into the outlet, don't
use the kind of cover with the spring-loaded flaps. They're not intended
for "permanent" use. Instead get a cover which is sort of a clear plastic
dome with slots in the bottom for cords to go through. These go for about
$15-$20.
Steve
|
291.923 | Thanks. | ANDREW::OSTROM | ETP Engineering Mgr. | Mon Dec 05 1994 18:57 | 7 |
|
Yup, know about that, thanks... This weekend was too nice, so I
worked on siding/roofing, but the outlets go in later this week.
I think I'm just going to use standard new-work depp boxes, of which
I have loads.
Andy Ostrom
|
291.1006 | haunted condo (power problems) | KLUSTR::SOUTHY::Gardner | Southie Mudshark | Thu Dec 08 1994 23:53 | 44 |
| got a kinda strange problem that started very recently...
it began with the line conditioner I use for all my
computer related equipment....I noticed that late at night
a relay in the box would start clicking away indicating to
me that over/under voltage conditions must be occuring....
next it was the X-10 stuff...lights would turn on and off
by themselves...switches wouldn't work one day and would the
next...even applicance modules starting behaving eratically....
then, my DECrouter 250 has started randomly rebooting about
once every four days...its on the line conditioner, but maybe
its a little more sensitive then the rest of the stuff ;-)
now all hell has broken lose...when I came home, the router
was down *again*....while writing this message the line conditioner
was at first clicking away and now has gone quiet again....
the lights in the living room wouldn't turn on at all an hour
ago and now they work, but only from the mobile control, not
from the wall switch.....and the tv has turned itself off then
on five times (its plugged straight into the wall eg no X-10)...
this last bit worries me abit because it can't be too good
for the tv...........
now: I live in a 700 sq.ft. condo in South Boston...2 years
ago (next month) I did a complete remodeling of the place
including stripping the old place down to the bare walls...
at the time, myself and an electrician went over all the
wiring including installing dedicated 30 amp circuits for
the computer and A/V stuff and doing all the X-10 stuff....
(I also took the opportunity to wire the place for ThinWire,
cable, and audio)....since that time, all had worked perfectly
until this all started happening....and, no, nothing inside
these four walls has changed recently....
so, what to do? I would have called in an electrician already
but the problems seem of the intermitent variety; I'm afraid
it won't happen while he/she is here.....and if the problem is the
power coming into my place, what would I do about it?????
any advice would be greatly appreciated! help!!!
_kelley
|
291.1007 | one thought to ponder... | BIGQ::GARDNER | justme....jacqui | Fri Dec 09 1994 12:17 | 7 |
|
It just started getting really cold lately and you do have and
old place. Are you harboring mice or squirrels? They might be
have a feast on your wires!
justme....jacqui
|
291.1008 | | LEFTY::CWILLIAMS | CD or not CD, that's the question | Fri Dec 09 1994 12:32 | 9 |
| Or some of your connections may be getting looser in the main box or
elsewhere.
Call the electrician ASAP.... If the problem is in your building, you
have a potential fire hazard... If something is loose, the electricial
ought to be able to find it....
CHris
|
291.1009 | | LEZAH::WELLCOME | Steve Wellcome MRO1-1/KL31 Pole HJ33 | Fri Dec 09 1994 14:48 | 3 |
| Are the outlets wired with the push-in connections on the back,
or with the screw terminals? The push-in connections are not
reliable.
|
291.1010 | CALL 1 800 GHOST BUSTERS | RELYON::MONACO | | Fri Dec 09 1994 15:34 | 21 |
| Sounds like your problem is across several seperate circuits. So you
need to go back to where they meet "main box" and work back to the power
coming from the street.
Some questions to think about;
Has there been any work in the area (new building, renovations, buisness..
.etc)
Did the problem first occur after a storm?
With cold weather are people cranking up their electic heat?
Are your neighbors having similar problems?? If so call in the power
company or building owner.
If it's only you than call an electrician in to check your system out.
You could also attach line montoring equipment to track the voltage
changes over an extended time to see if there is a pattern. (like
when the office buiding across the street turns heat on in the morning or
there is heavy elevator usage.
good luck
Don
|
291.1011 | "Exorcise 'em!!" | POLAR::PARKER | Great White North! | Fri Dec 09 1994 19:06 | 7 |
| re: .1 - .4 all make good suggestions. I am leaning more towards a
priest. Thats right, a priest. Perhaps an exorcism is just the ticket
to get rid of your odd power fluctations.
Warily yours,
|
291.1012 | | NETCAD::DESMOND | | Fri Dec 09 1994 20:21 | 6 |
| Re: .5 Exorcism
If you decide to go this route, make sure that you pay promptly for the
exorcism. Otherwise, your condo could be...
repossessed. :-)
|
291.1013 | Radio maybe?? | WMOIS::HARVEY | | Fri Dec 09 1994 20:34 | 6 |
|
You might want to make sure someone isn't running an amateur or CB
radio nearby.
DH
|
291.1014 | poltergeist? I may never know... | KLUSTR::SOUTHY::Gardner | Southie Mudshark | Fri Dec 16 1994 10:56 | 25 |
| I want to thank all those who responded to my basenote...I have
waited to reply to see what would happen....
basically, it all stopped just as fast as it started...all is back
to normal now with the sole exception of one pesky X-10 wall
switch which has always given me problems, but thats another
story..........
my favorite theory is that it was in the street...here in Southie,
we have some of the oldest underground wiring in the country...
being located only four blocks from the power plant doesn't appear
to help this; we have had numerous powerouts etc over the years...
my second theory is that it was all caused by an over zealous
Christmas light display which has since self-destructed ;-)
.4 mentions a line monitor...this sounds like something that
would come in handy in the event of a reoccurance (repossesion? ;-)...
where does one find such a device and what do they generally
cost?
(btw, .6 was great! laughed quite loudly...)
thanx again
_kelley
|
291.1015 | southie is KNOWN for that !!! | NECSC::DWORSACK | | Fri Dec 16 1994 17:36 | 15 |
| last winter my sister in-law had a problem, with her heat
(only on the first floor) which is where she was. took a few
days to get anyone to come out to look at her furnace.
this was during one of our cold snaps !!
turns out it not only affected the furnace, but other outlets/lights
were not working in the building.
come to find out one of the hot lines was bad, the other
was good.
power company had to dig up the whole street in front of her
house to fix it, 1 1/2 day job. i dont understand, phone/cable
on ugly phone poles in the rear of all the homes, and
electric (like you said, OLD at that), underground.
|
291.998 | Knob&tube - can we work around it ? | PCBUOA::ERSKINE | | Mon Feb 20 1995 17:22 | 18 |
|
In the process of remodeling our kitchen and bath of our "new"
old house, circa 1920, we have discovered that the breaker box which
has new wires going in, actually has the old knob&tube still in
operation. For example, the bathroom light fixture has k&t and
BX cable, or there could be K&t and new wiring. I was surprised to
see the two mixed together. Is this okay ? Since the k&t is
throughout the house, ripping it out (3 stories) would be a nightmare.
If we want to move a light switch with k&t can we create a junction box
and move it to a lower/another location ? Do we just add the new wire
for the new light switch ? I had read in note 2309 that there should
not be more than a 15amp breaker, what if the circuit contains three
kinds of wiring, (k&t/BX cable and new wiring) ?
rke
|
291.999 | Only change what you need to | HNDYMN::MCCARTHY | Disabled Service Button | Tue Feb 21 1995 09:08 | 39 |
| -< Knob&tube - can we work around it ? >-
Yes.
>> BX cable, or there could be K&t and new wiring. I was surprised to
>> see the two mixed together. Is this okay ? Since the k&t is
It was done all the time. There was a special connector for the end of the BX
(acutally a trade name I believe) that avoided the need for a junction box and
was used quite often.
>> If we want to move a light switch with k&t can we create a junction box
>> and move it to a lower/another location ? Do we just add the new wire
>> for the new light switch ?
Yes. There are special connectors that electrical supply houses will have to
bring the K&T wire into a metal junction box - actually I've seen this done two
ways, one with simply putting a rubber grommet in the knock out of the box and
running the wire through that (one wire per knock out) or a special connector
to bring the K&T wires in.
Add the junction box (in an accessable location) and run your new cable from
the junction to the new switch.
>> I had read in note 2309 that there should
>> not be more than a 15amp breaker, what if the circuit contains three
>> kinds of wiring, (k&t/BX cable and new wiring) ?
Its three kinds of wiring but you ALWAYS pick the amperage of the smallest wire
on the circut.
I assume by "new wiring" you mean RX? BX is still used all over the place
(commercial buildings mostly).
One think you will have to check with someone on is what to do with the ground.
I think what we did in your "moving a switch" situation was to clip the ground
wire so it would not give anyone an idea that it was actually connected to
ground.
bjm
|
291.436 | Step-down (120V to 12V) transformer wiring | MSE1::SULLIVAN | | Wed Apr 26 1995 15:21 | 50 |
|
I have a wiring question which can be boiled down to, "Can I
place a step-down (120V to 12V) transformer in the middle of a
daisy chained circuit?"
I have a dining room ceiling light which was controlled by two
switches (a three-way). We are having a built-in cabinet put in
which eliminates one of the switches. Instead, it will have
low-voltage lighting inside. I want to use the old switch box and
wiring for power to the low-voltage lights. And ideally, have the
one remaining light switch turn on both the ceiling light and the
low voltage cabinet lights.
The power source is into the light box, then to the switch.
My question is, can I get this to work with the existing wiring/boxes?
At this point, I don't think so.
How can I wire the following if it can be made to work?
old switch box switch
+---------------+ +-------+
bbbbbbbbbbbbbbbbbbbbbbbbbbbbbbbbbbbbbbbbbbbbbbb | b, w connected
power | | | | to screws on
w2w2+ +w2w2w2w2w2w2w2 wwwwwwwwwwwwwww | simple 2-way
\ / | | | | switch
light | rrrrrrrrrrrrrrr | r not used
+---w1--b1-------+ +-------+
w1 b1
w1 b1
w1 b1
w1 b1
+--------------+
|transformer |-->w+b to low voltage light
+--------------+
With a "daisy chain" (w connected to b1, w1 connected to w2), the
low voltage light works but not the ceiling light.
If I connect w+r to the common screw on the switch, connect w to b1,
r to w2, and w1 to ground, it works. However, I obviously would not
do this unless I was looking to seriously shorten the life of the
house or one of the occupants.
I can not pull a new wire between the light and the old switch box.
I can get one between the old switch and the remaining switch.
I can also probably get power directly to the switch (this is my plan B)
Thanks,
Mark
|
291.437 | you have a need for feed.. | TEKVAX::KOPEC | we're gonna need another Timmy! | Fri Apr 28 1995 18:33 | 41 |
| The transformer wires just like a light, and lights wire in parallel.
you're SOL. You don't have the wires you need. You need an unbroken
neutral to the transformer, in the current situation.
If you can get power to the switch box where the transformer is:
1. Connect all whites together at the transformer box.
2. connect the black feed to the black leading to the switch.
3. connect the black lamp lead and the black transformer lead to
the red lead from the switch.
4. Disconnect and cap the feed at the lamp.
5. connect the lamp to the black and white from the transformer
box in the usual way.
6. Disconnect and cap the white wire at the switch. (*)
7. Connect the one of (black|red) to the "common" switch terminal,
connect the other to either of the non-common switch terminals.
so you end up with:
+-----black------+----------red-------+
| | |
lamp transformer switch
| | |
+-----white------+--wh-+ +---black----+
| |
w b
h k
| |
feed
You can do essentially the same thing if you can get power to the
switch box, using the white wire to bring the neutral to the other
white wires at the transformer.
(*) Given the spare non-white conductor, you really shouldn't use the
white for non-neutral.. if you do, wrap a piece of black electrical
tape around each end.
...tom
|
291.438 | Thanks for the confirmation | MSE1::SULLIVAN | | Mon May 01 1995 13:44 | 6 |
| Thanks Tom, you confirmed my suspicions. I can get a new power lead to
the switch. In fact I located the spot and drilled up from the basement
last night. All set to pull the new wire.
Mark
|
291.711 | General Electrical Circuit Questions... | IKE22::EIKENBERRY | John (Ike) Eikenberry | Thu Sep 07 1995 18:59 | 49 |
| Hi -
I've read through several notes relating to circuits and didn't
find a note that seemed appropriate, so I'm starting a new note.
Moderator, please feel free to move this note if I overlooked a better
place.
Last night, my wife & I managed to trip a circuit breaker two times.
After a little experimenting, we identified all of the items on the
circuit and to say that I was somewhat surprised was an understatement.
The items we noted (there may be more) were: microwave in the kitchen,
all kitchen lights, at least one outlet in the family room, porch
light, and the 4 spotlights around the house. Somehow this doesn't
seem reasonable and perhaps doesn't even meet code.
My plan is to break up this circuit into n circuits (n to be determined
after more investigation). Thinking about the project raised a few
questions which I'm hoping that the notes-readers here can help with:
-- When would someone use a 15-amp circuit vs. a 20-amp circuit? I
realize that if you need the power, you would use 20-amp. Is it
just a matter of economy in that 15-amp is cheaper? Or is there a
real reason (e.g., code requires 15-amp circuit so that the builder
has to put in more circuits, breaking the electrical map up more)?
-- A few years ago, I heard of a rule of thumb for the number of
outlets/lights/devices on a circuit. At the time, I remember the
rule to be assume x amps per duplex outlet, so you should only have
15/x duplex outlets on a 15-amp circuit or 20/x for 20-amp. Can
anyone fill in x for me? What is an average light counted as
(75watts/125 volts = .6 amps, count as 3/4amp)?
For permantly wired lights and other items, I can easily calculate
it out the exact ampers used, but is a slop factor used? For
example, the kitchen light is 4 banks of 2 fluroescent lights.
Let's say that each light is 40 watts, so total wattage for the
light fixture is 8x40 = 320watts, about 2.5 amps. So for this
circuit, do I set aside just the 2.5 amps or something like 4 just
in case someone down the road wants a bigger light (and therefore
won't have to worry about having to upgrade the circuit)?
-- Lasstly, and this may answer all of the above questions, is the
NEC (National Electrical Code) book available to a mere mortal like
me? If so, where does one get it? Barnes & Noble?
thank you for your information,
Ike
|
291.712 | | QUARK::LIONEL | Free advice is worth every cent | Thu Sep 07 1995 19:15 | 9 |
| The only reason to run 15A is if you're a cheapskate and putting in 14GA
wire. Since the savings is minimal, I see little point. The NEC requires
20A for some circuits (small appliance circuits in a kitchen).
You can buy the National Electrical Code book at any electrical supply store
(since you're in Nashua, try Ralph Pill, where I got mine). It has answers
to most everything you asked here.
Steve
|
291.713 | Wiring Simplified as NEC reference alternative | PASTA::DEMERS | | Thu Sep 07 1995 19:26 | 8 |
| I find the "Wiring Simplified" book to be a nicely condensed version of
the NEC for what I need to do.
Current version is based on the '93 NEC and Spag's has it for $3.99. I
did notice that this new version has much better diagrams than older
versions.
Chris
|
291.714 | | MKOTS3::WTHOMAS | | Thu Sep 07 1995 19:27 | 5 |
| Re: Slop factor
I seem to recall a 150% slop factor for motor/compressor-type stuff on a
circuit (ie. 6 amp rated window a/c should count as 9 for "startup"
current).
|
291.715 | | PCBUOA::TARDIFF | Dave Tardiff | Thu Sep 07 1995 20:28 | 13 |
| <<< Note 5669.0 by IKE22::EIKENBERRY "John (Ike) Eikenberry" >>>
Unless you're rewiring all the devices, you won't be able
to upgrade to a 20 amp line, as that would require 12 gauge wire,
as opposed to the probably 14 you've got in there now. The breaker's
job is to protect the wire from melting - putting in a larger breaker
on a circuit that you didn't wire personally, and KNOW what's out there,
is just as bad as the old replace-the-fuse-with-a-penny trick.
Alternatively, just make sure your smoke detectors are working...
Probably your simplest fix is to run a new 20 amp line for the
microwave and leave the rest alone. As long as you're not running any
heating devices in the outlets, you'll be ok.
|
291.716 | | SHRMSG::BUSKY | | Fri Sep 08 1995 12:11 | 19 |
| As a previous reply stated, you can't just pop in a bigger breaker
to solve your problem. A 15 amp breaker is used to protect 14
gauge wire, a 20 amp breaker is ued to protect 12 gauge wire.
As far as breaking up a circuit, you'll have to do a little
detective work to figure out how to easily do it and accomplish
the goal. While just running a new line to a high amperage device
on the circuit, such as the microwave, you have to consider what
to do with the existing circuit wires currently feeding the
microwave and the rest of the outlets or fixtures down the
line.
If most of the devices are daisy chained, one feeding the next,
you can map out the circuits and try to find a point some where
in the middle where you can end the current line, and run a new
line to the next device to feed it and the other outlets and
fixtures down the line.
Charly
|
291.717 | | DSSDEV::RICE | | Sun Sep 10 1995 18:18 | 24 |
| The basic answers to your questions are:
- 1.5A per duplex receptacle
- 80% general load factor, i.e. 12A max on 15A circuit
- Use 14 GA 15A circuits in general
- Use 12 GA 20A circuits in kitchen and work areas.
- Separate large applicances onto their own circuit
As far as always using 20A circuits....
- It really isn't wise to provide more power to a point than you need.
- You may need more 15A circuits than you would 20A; So its likely to be the
same cost wise.
- If something does trip a circuit, you loose fewer things with the 15A
circuits.
- Remember appliance/lighting that you use in the receptacle are UL approved for
15A circuits generally. This can sometimes make a safety difference.
- If you do generally use 20A circuits, the entire circuit is supposed to handle
the 20A. This includes the actual duplex receptacle, a 20A one doesn't even
look like a 15A one.
From what you've described the problem just sounds like you need to find another
circuit to plug your microwave into.
-Tim
|
291.718 | | NETRIX::michaud | Jeff Michaud, That Group | Sun Sep 10 1995 23:21 | 12 |
| > - If you do generally use 20A circuits, the entire circuit is supposed to handle
> the 20A. This includes the actual duplex receptacle, a 20A one doesn't even
> look like a 15A one.
This last sentence is a little confusing. One does not need
20A receptacles because the circuit is 20A's. A standard
duplex outlet receptacle has 15A outlets, but is rated for
20A feed through.
You only need a 20A outlet if the applicance has a 20A plug
(as far as I know, or all of the homes I've been don't meet
code :-)
|
291.719 | | DSSDEV::RICE | | Mon Sep 11 1995 12:42 | 17 |
| RE: .7
Although it has been allowed in the past they have been "recommending" for
awhile now that you always use the screw connections and not "feed through" a
receptacle. You may already see this as code in some communities; MA for
instance.
Also, I did say "generally", as in "should". The point being, don't make a mess
by using 20A circuits where you don't need them. ;-) If you want to 'err on the
side of safety then use the 12GA wire on a 15A circuit; You "should" not be
using 15A anything on a 20A circuit.
The code has lots of "shall" and "should" with alot of "good workmanship"
sprinkled in ;-)
Sorry if this was confusing,
-Tim
|
291.720 | | NETRIX::michaud | Jeff Michaud, That Group | Mon Sep 11 1995 14:19 | 11 |
| > Although it has been allowed in the past they have been "recommending" for
> awhile now that you always use the screw connections and not "feed through" a
> receptacle.
"feed through" from use my of the word does not have anything to
do with using the quick connect holes vs. the screw connections.
"feed through" simply means "non-terminal receptacle" (ie. daisy
chaining).
Either I'm completely messing up the terminology or you haven't
been in the trade for a while :-))
|
291.721 | | WAHOO::LEVESQUE | sunlight held together by water | Mon Sep 11 1995 14:58 | 5 |
| I think the point he's making is that if you are going to have a switch
or receptacle that you will be daisy chaining you ought to use the
screw connections for both wires as opposed to using the scew
connection for one and the quick connection for the other (thus forcing
all the current to flow through the switch or receptacle.)
|
291.722 | Thanks for the info... | IKE22::EIKENBERRY | John (Ike) Eikenberry | Mon Sep 11 1995 15:27 | 10 |
| Thanks for all of the information. I think I'll take the easier route
and just run a line to microwave. I have 200amp service which isn't
even close to being used and lots of space in the circuit box, so just
running a dedicated line is no big deal.
Also, I'll go get the NEC, sounds like a useful reference.
Thanks again,
Ike
|
291.723 | | DSSDEV::RICE | | Mon Sep 11 1995 15:50 | 28 |
| Sorry I confused you again by making two points when you thought I was making
one.
Point 1:
Do not "feed through" means that you do not feed the next receptacle from
another.
Point 2:
Always use the screw connections and never use the quick connect ones.
Now they relate because people use a duplex receptacle to make connections; Yes,
they are not supposed to do that. When they do that then they are doing a "feed
through" the duplex receptacle. They are relying on the receptacle to carry
current as RE:-.1 has correct.
So I'll assume you never use the quick connects anylonger. Now there are two
receptacles in a duplex receptacle, duh I know. There is a metal break-away tab
connecting the two for each leg. Unless you break this tab there should never
be more than one wire connected to each leg. The tab is good for when you want
to switch one half of the duplex receptacle.
If you want to make wiring connections then use pig-tails. Also, don't forget
to clamp your grounds ;-)
-Tim
P.S. I haven't been away from the trade, I just don't rely on it to pay any
bills. Also, there are too many Electricians in my family already ;-)
|
291.724 | | NETRIX::michaud | Jeff Michaud, That Group | Mon Sep 11 1995 16:08 | 5 |
| > If you want to make wiring connections then use pig-tails.
Isn't this code anyways, at least for neutral and ground wires?
The idea being that this minimizes the chances of the neutral
connection being broken while the hot isn't??
|
291.725 | | QUARK::LIONEL | Free advice is worth every cent | Mon Sep 11 1995 17:07 | 3 |
| Yes, it is. I just found out about it myself.
Steve
|
291.726 | | SHRMSG::BUSKY | | Mon Sep 11 1995 17:10 | 5 |
| > I think I'll take the easier route and just run a line to microwave.
And what will you do with the line that's currently running to the
microwave outlet and possibly the line leaving that box that's
feeding the next box down the line?
|
291.727 | Breaking up a circuit - questions.... | IKE22::EIKENBERRY | John (Ike) Eikenberry | Tue Oct 10 1995 16:59 | 18 |
| re: -.1
Thankfully the outlet servicing the microwave is the end of the chain.
So, I'll break the chain one before and run a new wire to service the
microwave.
As a side question, is it best to remove unused wire from behind the
walls? That's probably confusing. Maybe a diagram will help.
Currently I have one end of the circuit as below.
---a---- overhead lights -----b------ microwave outlet
My goal is to run a new wire to the microwave outlet, thus making wire
b not used. Can I leave wire b in place with caps or should I pull
wire b out of the wall and ceiling (perhaps easier said than done)?
thanks!
Ike
|
291.728 | What are some wire snaking gotcha's? | IKE22::EIKENBERRY | John (Ike) Eikenberry | Tue Oct 10 1995 17:01 | 13 |
| New question for the guru's out there...
Does anyone have tips/guidelines for snaking new wires through the
house? The list of projects that involve running new wires is growing
(move switch, new switch, new lights, etc.) - yes, probably growing
faster than I'll be able to get to them. One of the joys of owning a
house :-). I currently have a wire snake and the long drill bits, just
what are some of the gotcha's/tips/etc that people have in their back
pockets...
Thanks,
Ike
|
291.729 | | WAHOO::LEVESQUE | sunlight held together by water | Tue Oct 10 1995 17:43 | 15 |
| > ---a---- overhead lights -----b------ microwave outlet
>My goal is to run a new wire to the microwave outlet, thus making wire
>b not used. Can I leave wire b in place with caps or should I pull
>wire b out of the wall and ceiling (perhaps easier said than done)?
If your wire was run properly, it'll be tacked down just outside the
boxes (and possibly other places along its length.) Removing the wire in
these circumstances more or less requires that you make a mess of the
wall. Seems unnecessary. I would probably just disconnect the feed from
the overhead lights and push the unused wire through the hole in the
box (put a piece of tape over the hole so when the box is opened people
will know nothing belongs there.) Then disconnect the wire at the
microwave outlet and push it through the hole. Now run your new wire to
the microwave outlet.
|
291.730 | New question - wires in dining room confusing... | IKE22::EIKENBERRY | John (Ike) Eikenberry | Mon Oct 16 1995 17:18 | 41 |
|
Thanks for the info in the last many replies - extremely helpful.
On to a new & different question for the gurus here...
When my wife and I started work on our dining room (painting et al), I
took down the old chandelier to ensure that it wouldn't get paint
splattered.
Now here is where I made the blunder - I forgot to mark which wires
were attached to what. So, I'm here to ask for help.
The junction box for the chandelier has 3 sets of wire-nutted wires:
-- A single black wire. My assumption is that this is the "Hot"
lead for the chandelier.
-- Two white wires twisted together. Hot neutral for the
chandelier?
-- Two black wires and 1 white wire twisted together.
Here is where my questions come in:
1) Using a voltmeter, I can test to see if the single black wire is
controlled by the dining room switch. Will this tell me what I
need to know or is there a different test I should do?
2) How can I tell which wire set is the hot-neutral for the
chandelier?
3) Lastly, is having 2 black wires and 1 white wire twisted together
part of NEC code? As someone who has learned that black is "hot",
white is "hot neutral" and green is "ground" - seeing a black and
white wire twisted together looks like a short, but it isn't.
What would the combination be used for?
Thanks in advance for your help,
Ike
|
291.731 | Easy fix..... | BITZEE::CLAY | Indecision may or may not be my problem | Mon Oct 16 1995 18:21 | 10 |
| 1) The single black wire is the hot to the lamp.
2) The two whites are the neutral to the lamp.
3) The two blacks and one white is the unswitched hot line and the
white is being used to feed the switch. (Perfectly legal)
If you still want to test with a meter..... put the meter between the
single black and the two whites and this will turn on and off with the
switch.
|
291.732 | | 2155::michaud | Jeff Michaud - ObjectBroker | Wed Oct 18 1995 20:04 | 6 |
| > 3) The two blacks and one white is the unswitched hot line and the
> white is being used to feed the switch. (Perfectly legal)
though I believe in this case doesn't code say that this *hot*
white wire should be marked as hot (usually be wrapping a piece
of black electrical tape around the white sheating)??
|
291.733 | not in this case | HNDYMN::MCCARTHY | A Quinn Martin Production | Wed Oct 18 1995 22:36 | 18 |
| >> though I believe in this case doesn't code say that this *hot*
>> white wire should be marked as hot (usually be wrapping a piece
>> of black electrical tape around the white sheating)??
Nope. Not required when used as a swtich leg. In any other situtations you
are required somehow (usually via electrial non-white/grey tape) to mark a
normally white or grey colored wire (I mean the insulation around the wire!).
As I mention in my three-way diagram - this method lets an electrian who looks
at the connections later on easily know which is the switch leg.
The same is true when using a dark (black/blue/red etc) wire for a neutral or
ground - it must be taped with white/grey or green (for ground). I did this
when I replaced my electric stove with a gas one. I used the second black leg
as the neutral and put white tape around it and use the greatly oversized for a
15A line feed.
bjm
|
291.978 | Flickering Light | BRAT::MCCRACKEN | | Wed Nov 22 1995 10:57 | 7 |
| We have an outside light, on a timer, which flickers. The
others don't do this. Is the wiring wrong, not enough power,
what would be causing this? How do we fix it?
Thanks in advance,
Linda
|
291.979 | | SMURF::WALTERS | | Wed Nov 22 1995 12:14 | 5 |
|
Is it a mechanical timer or just a photocell switch?
If the latter, then the problem may be that light from the lamp itself
is bouncing back into the photocell causing a feedback loop.
|
291.980 | | BRAT::MCCRACKEN | | Wed Nov 22 1995 15:17 | 3 |
| It is a mechanical timer.....please help it is driving me crazy!
|
291.981 | | 2155::michaud | Jeff Michaud - ObjectBroker | Wed Nov 22 1995 15:28 | 5 |
| > It is a mechanical timer.....please help it is driving me crazy!
Have you tried changing the bulb, or making sure the bottom
contact in the socket is raised high enough to contact the
bulb?
|
291.982 | You need to do some work | ZENDIA::ROLLER | Life member of the NRA | Wed Nov 22 1995 15:31 | 15 |
| Is the bulb screwed in tightly? If it's loose, the heat generated
could cause it to move and break the connection, cooling down it would
remake the connection and start all over again.
Could it be the bulb itself? Did you try another bulb in that socket?
Is it the timer? Can the timer be removed from the circuit? Is there
a bypass switch on the timer? If so, did you try turning it on
manually? If you did, did the problem go away?
You need to attack the problem systematically, eliminating one variable
at a time. This will get you to the problem component eventually, but
you have to do some work.
Ken
|
291.734 | Done & working, here is final circuit layout... | SEND::EIKENBERRY | John (Ike) Eikenberry | Mon Nov 27 1995 17:59 | 38 |
| Thnaks for the help on the last electrical question I posted - the
dining room lamp is up and working.
Just for future people who may find this set of notes, I'll try to make
a diagram to help out
black ----------O---------------------- black to next item in
| circuit
|
white ----------+----------------o----- white
| |
| |
|-white |
| |-Neutral from light
|__ _______###__|
\ ^ ^
^ ^ lamp
^ ^
^ Black wire
^
dimmer switch
So, in the junction box for the light, I had three sets of wires
1) Black-Black-White: The hot source, hot going to the next
thing in the circuit, and a white wire
going to the switch.
2) white-white: the neutral and the neutral going on in
the circuit
3) black: The wire returning from the switch
So, as noted earlier in the notesfile, the lamp went between the single
black wire and the two white wires.
Thanks again!
Ike
|
291.735 | Don't do that. | NETCAD::COLELLA | | Mon Nov 27 1995 18:45 | 14 |
| > <<< Note 5669.8 by DSSDEV::RICE >>>
>
> If you want to 'err on the
> side of safety then use the 12GA wire on a 15A circuit;
>
I thought this was considered bad practice (and rejected by Inspectors),
because you can now fake out future electricians into thinking
it's a 20A ckt. I think 14 guage has proved itself to be safe when
the rules are followed.
|
291.983 | | WRKSYS::WEISS | | Mon Nov 27 1995 21:04 | 1 |
| Is it a standard incandescent bulb or fluorescent?
|
291.736 | | DSSDEV::RICE | | Tue Nov 28 1995 14:36 | 9 |
| RE: .24
I agree.
You can do it but it would send "smoke signals" to an inspector. He'd then look
harder and probably find other screw-ups that are illegal ;-)
Of course, the code is written to allow the inspector room to be more stringent.
There isn't anything "wrong" with putting a 15A fuse on a 20A circuit.
|
291.984 | | NUBOAT::HEBERT | Captain Bligh | Tue Nov 28 1995 16:17 | 7 |
| We had four 60W incandescent bulbs in the fixture over a bathroom sink
that flickered and bugged me. They were all noname, and made in Europe
(Hungary, I think), and the problem was self-correcting. None of them
lasted more than about three months. When I replaced them with name bulbs
the flickering ceased.
Art
|
291.969 | step-up transformer purchase ? | PATE::POUNDER | | Fri Dec 08 1995 16:15 | 9 |
| I'm looking for a 120->240V step-up transformer but have had no success
in finding one. I brought over a TV set and a VCR ( only reason was
that my kids have 100+ pre-recorded tapes, Disney etc, and I didn't
want to pay megabucks for conversion ) and only need to drive these 2
pieces from the transformer so it needn't be a monster ! Can anyone
help direct me to some electrical supplier(s) where I can purchase
this?
Trevor
|
291.970 | | SMURF::SWARD | Common sense is not that common | Fri Dec 08 1995 16:33 | 4 |
| Look for a 240-110 Tranformer and run it backwards. You only get half
the rated power but it should be easier to find..
/Peter
|
291.971 | Thanks... | PATE::POUNDER | | Fri Dec 08 1995 17:40 | 4 |
| Thanks....given the power reqmts for a TV and VCR are low I wouldn't
see this as a problem anyway.
Trevor
|
291.972 | | PCBUOA::TARDIFF | Dave Tardiff | Fri Dec 08 1995 18:38 | 16 |
| Won't you also have trouble with cycles? Isn't Europe
50hz versus our 60hz? While this doesn't matter much for a resistance
heater or too much for a tool motor, I wouldn't be surprised if it
mattered a great deal for electronics. On second thought...maybe not.
Our PC power supplies have a switch for 120/240...so maybe that's all
it takes. Still got the manuals? Perhaps your stuff has switches too.
If existing tapes in PAL/SECAM (European, I believe) versus
our NTSC (or whatever) is your problem, I think you can get VCRs that
take both formats. This, of course, may also cost a bundle...but then
you'll also be able to watch stuff you get here, not to mention broadcast
TV....if you really want to.
You might also check out a higher-end electronics store for
advice. I'm sure they get this sort of question often, and may have
various priced solutions.
|
291.973 | | 2155::michaud | Jeff Michaud - ObjectBroker | Fri Dec 08 1995 19:43 | 11 |
| > If existing tapes in PAL/SECAM (European, I believe) versus
> our NTSC (or whatever) is your problem, I think you can get VCRs that
> take both formats. This, of course, may also cost a bundle...but then
> you'll also be able to watch stuff you get here, not to mention broadcast
> TV....if you really want to.
I would imagine such a VCR for use here would convert PAL to
NTSC for output to a NTSC TV. As such I think you'd lose alot
as PAL is higher definition (much crisper, I can't wait til we
get HDTV or Digital TV!). Then again, if this is for the kids
they probably don't care ....
|
291.974 | clocks will be off | SMURF::WALTERS | | Fri Dec 08 1995 20:28 | 19 |
|
The only thing that seems to get screwed up by the 50/60 cycles
problem are internal clocks. Most of my 240v stuff from the
UK was switchable to 110 so I never needed a transformer, but
the clocks are no longer accurate. If you are just playing tapes,
it should not be a problem.
There are a few VCRs that convert to NTSC and they range from about
$600 to $2000 depending on what features you want. Hunt stocks low-end
multistandard VCRs in Ma and Great Northern Video in Concorde NH has the
high-end Panasonic stuff. If you also have a PAL camcorder,
this could be a way to go.
Regards,
Colin
|
291.975 | Tell the kids it's broken ! | PATE::POUNDER | | Mon Dec 11 1995 13:44 | 18 |
| From what I can determine there should be no problem with "playing
only" tapes. Both the TV and VCR were brought across with me for this
purpose only. The format shouldn't be an issue. I know I can't receive
programs on the TV, but as I said...I'm only using it for tape playing.
I think the answer to the frequency question is that the time clocks
will run "out of whack" but the internal electronics critical for
viewing tapes should be OK...they should generate their own clocks for
timing ( internally ). Yes I checked both machines and no,
unfortunately they are not switchable between 110 & 240V. I think
because of the format difference where the machines are completely
incompatable, they assume no-one would be dumb enough to bring them
from UK to USA ;-)
Assume that running a transformer "in reverse" will work ? i.e. that
there won't be some safety feature that blocks attempts to shove a
supply onto the connections designed to be the "output".
Trevor
|
291.985 | Light Switch--Need help please | POWDML::GILDER | | Mon Dec 11 1995 14:49 | 19 |
| Could I please have help with my bathroom light?
First of all, I am the worse chicken in the western hemisphere
when it comes to electrical stuff. Scenario is, my 1956 house
has 1955-early 56 wiring. On Saturday, I went to turn off the
light upon leaving room. --Conservationist that I am...
The switch went down but lights didn't go off. There is a little
illumination on the switch that acts as sort of a "hi folks, I'm
the light switch" for the dark. That illumination is out when light
is in the on position.
If I repeat the motion several times the light eventually goes out.
What kind of problem do I have? Is it fixable by a whimp?
Thanks
Adriane Gilder
|
291.986 | answer | POWDML::GILDER | | Mon Dec 11 1995 15:05 | 6 |
| A friend just informed me that I have a major potential fire hazzard.
I gotta get a new switch in there pronto.
I'm leaving this entry in as the possibility it will help others.
Adriane
|
291.987 | Watch out... | VICKI::DODIER | Single Income, Clan'o Kids | Mon Dec 11 1995 15:15 | 12 |
| Hate to be the bearer of bad news, but it may not be quite as easy
as just replacing the switch. If the wiring is that old, you may have a
situation where the insulation around the wires themselves is old,
dried out, and brittle.
I came across something like this when I tried to replace a light
fixture in an old cottage for a relative. Moving the wire, even
slightly, made the insulation crack and fall off the wire. Perhaps
you'll be luckier, or perhaps that's why the switch does nothing
(i.e. wires shorted together). :-(
Ray
|
291.988 | if you are worried - find someone to help | HNDYMN::MCCARTHY | A Quinn Martin Production | Mon Dec 11 1995 15:39 | 16 |
| >> If I repeat the motion several times the light eventually goes out.
Most likly a bad switch.
>> What kind of problem do I have?
>>Is it fixable by a whimp?
Could be real simple, could be a nightmare.... if you are a wimp about touching
electrial anything - than it is most likly going to be a nightmare - that's
just the way it works... If you are scared to even open the main panel cover
than find someone to help you out. At best, its a 2 minute job, at worst,
maybe 15-30 minutes.
bjm
|
291.989 | thanks I'm all set | POWDML::GILDER | | Tue Dec 12 1995 11:09 | 7 |
| Thanks to everyone who answered here and directly to me. Last
night a kind soul came by to fix the problem. Someone I'd not met
before but is now a nice friend to have.
Looking forward to other types of helpful hints in this conference.
Adriane
|
291.990 | | TP011::KENAH | Do we have any peanut butter? | Tue Dec 12 1995 13:05 | 1 |
| Was it just a broken switch?
|
291.991 | yes to -.1 | POWDML::GILDER | | Tue Dec 12 1995 18:56 | 10 |
| -.1
I think the answer to the question is yes. I think that the 40 year
old switch decided to be this week's p.i.t.a.
Everything has worked fine since my "knight in shining armor" left.
Now all I have to do is sit back and wait for the next crisis.
Mods: thank you for managing such a worthwhile project as this
conference.
|
291.992 | | 2155::michaud | Jeff Michaud - ObjectBroker | Tue Dec 12 1995 21:11 | 5 |
| > Mods: thank you for managing such a worthwhile project as this conference.
I don't believe this conference has any "active" moderators any
more .... (should instead thank the original moderators whomever
they were ... :-)
|
291.96 | | CSLALL::NASEAM::READIO | A Smith & Wesson beats four aces, Tow trucks beat Chapman Locks | Thu Dec 28 1995 16:22 | 20 |
291.97 | | SUBSYS::DONADT | | Fri Dec 29 1995 14:41 | 3 |
| RE .7
Better call Active first. I think they closed the Westboro store a few
years ago. Still open in Woburn though.
|
291.612 | Auto-transformer solution | SMURF::PRWSY1::WOODS | | Thu Jan 04 1996 17:43 | 7 |
|
Most of the larger electonic supply houses (Newark Electonics, for
example) carry setup down auto-transformers specifically for this purpose.
You are probably looking at around $90-$120 for a unit which will
supply about 7 amps at 115 volt from a 230 volt input. BTW, they
weigh about 15-20 pounds.
|
291.1000 | Blowing adjacent circuit breaker | ROCK::MUELLER | | Mon Jan 15 1996 19:53 | 31 |
| I've got a strange problem ...
I'm renovating a bathroom/hallway in my basement and re-doing the wiring myself.
This bathroom, hallway, and a misc room are all on a 20 Amp circuit. My
addition and garage run off of a separate, 15 Amp circuit, who's breaker happens
to be directly above the one for the bathroom/hallway/misc room in the box. The
15 Amp breaker is one which has a "test" button right on the breaker. The 20
Amp breaker is a normal breaker. I just installed some track lighting (3-lamp,
halogen, I forget the wattage, but each light has it's own transormer to drop
the voltage to the bulbs) on the 20 Amp circuit.
If there are no major appliances running on the 15 Amp circuit (ie: no lights,
but TV/VCR is OK), and I turn the track light on the 20 Amp circuit on, the 15
Amp circuit blows (yes, you read this right, the adjacent circuit blows, not the
one with the track light!). If there is a major applicance running on the 15
Amp circuit, I can flip the track light switch 'till I'm blue in the face, and
it won't trip the 15 Amp circuit. I can make this happen over and over again.
Anyone ever seen this? Any ideas where to look? Could poor/bad/non-existant
grounding cause such a problem? I have not looked into the circuit breaker box
yet, but my home inspector (I recently bought the house) said that the wiring
was a mess in that box.
BTW: The house was built in 1967/68. The addition/garage was put on in early
1970's. House and addition have grounded wire throughout.
Any input would be appreciated.
Thanks,
Rob
|
291.1001 | | 19096::BUSKY | | Tue Jan 16 1996 11:04 | 11 |
| > addition and garage run off of a separate, 15 Amp circuit, who's breaker happens
> to be directly above the one for the bathroom/hallway/misc room in the box. The
Maybe heat from the 20AMP breaker is rising up and causing the
15AMP breaker, you did say above it, to trip. Breakers do get warm
during normal use and I believe that it is this heat, or over
heating that causes them to trip.
Try relocating the breakers to see if the problem goes away.
Charly
|
291.1002 | I doubt that it's the heat | ROCK::MUELLER | | Tue Jan 16 1996 12:01 | 9 |
| > Maybe heat from the 20AMP breaker is rising up and causing the
> 15AMP breaker, you did say above it, to trip. Breakers do get warm
Nah ... the 20 Amp circuit could be completely off (and, thus, cold) when I turn
on the track light for the first time, and the 15 Amp will still blow.
Sorry, but heat doesn't seem to be the culprit.
-Rob
|
291.1003 | Sound like a ground fault.. | BITZEE::CLAY | Indecision may or may not be my problem | Tue Jan 16 1996 12:15 | 6 |
| It seem to me that the breaker is triping out because of ground fault
and not overload. The cause of the problem could be a loose neutral or
you could have the lights on the same neutral as the garage/addition.
Are you replaceing existing lights or as it a new instalation?
Don
|
291.1004 | some replacement, some new | ROCK::MUELLER | | Tue Jan 16 1996 12:33 | 12 |
| I'm replacing some existing wiring, but have added a new light and a bathrooom
exhaust fan as well as re-wired a 4-way switch to a 3-way switch (I didn't need
the extra switch anymore). All of this was on the 20 Amp circuit. I never
touched the 15 Amp circuit. The halogen track lighting is on a standard 2-way
switch on the 20 Amp circuit.
I think I'll have to open up the circuit breaker box and have a look inside.
I'll check the neutral wires.
Thanks,
Rob
|
291.1005 | one or more of these circuits is GFCI, right? | REGENT::POWERS | | Tue Jan 16 1996 14:00 | 9 |
| There's a "test" button right ON the 15amp breaker?
Doesn't this mean that that breaker is a GFCI breaker?
I can think of scenarios where breakers on OPPOSITE legs can affect
one another more easily than I can think of scenarios that would make
adjacent breakers on the same leg affect one another, but I'm guessing that the
GFCI nature of the 15amp circuit is key here.
- tom]
|
291.1016 | | EVMS::MORONEY | Operation Foot Bullet | Tue Jan 16 1996 18:03 | 20 |
| re .1921:
The breaker which keeps tripping is almost certainly a GFCI breaker.
I'll _guess_ that either the place is incorrectly wired with the neutral
being shared between the two circuits, or there is a high resistance
connection between a switched hot of the 20A circuit and the GFCI
circuit. The GFCI circuit must have its own neutral to the GFCI
breaker itself. If you open up the panel you'll see the GFCI breaker
has the hot AND the neutral leading to it, and it has a short wire to
the "real" neutral bus. The GFCI breaker measures the difference in
current in the hot and neutral. If not the same there's a problem and
it trips.
re .1926:
The "adjacent" breaker is almost certainly using the opposite
"hot" leg of the feed. It becomes obvious when you look how
the breakers are connected in a box. But this isn't really
relevant.
|
291.1017 | same difference :-) | 2155::michaud | Jeff Michaud - ObjectBroker | Tue Jan 16 1996 21:52 | 6 |
| > The GFCI breaker measures the difference in
> current in the hot and neutral. If not the same there's a problem and
> it trips.
In other words there should be zero (or whatever the threashold is)
difference between current flowing on both legs of the circuit?
|
291.1018 | looks like I forgot a sentence... | EVMS::MORONEY | Operation Foot Bullet | Tue Jan 16 1996 23:59 | 6 |
| re .1938:
Yes the _difference_ in current should be 0. I think they "allow"
something like 20mA before they trip. It's not that much.
-Mike
|
291.1019 | 20 mA is too high | SSDEVO::JACKSON | Jim Jackson | Wed Jan 17 1996 13:44 | 7 |
| 20mA can kill you under the right circumstances. I believe the trip is for
less than 4 mA.
My high school electronics class had an interesting sign on the wall:
"At 10 mA you can't let go. At 100 mA you're dead. Don't make
an ash of yourself"
|
291.1020 | RE.1931 : call the power company | DUNKLE::MCDERMOTT | Chris McDermott | Wed Jan 17 1996 14:04 | 6 |
| I had a similar low current/voltage problem that manifested itself by the all
the lights in the house dimming whenever a heavy load, like the electric dryer,
came on line. The problem was the power line comming into the house. It had
burnt itself out such that most of the current was passing through only small
number of conductor strands that hadn't burnt away. The power company came out
and replaced the cable - problem solved.
|
291.1027 | water in service panel! | 11666::CLEMENT | Smells like Nirvana | Mon Jan 29 1996 12:22 | 28 |
| Discovered a weird (to me) problem on Friday nite during our heavy
rainstorm. I had a water leak inside my electric serice panel. I
removed the front cover and discovered water was entering the panel
thru the mainline feed cable. The water is travelling "inside" the cable
and dripping out of the cable where the cable casing ends. This is the
main house feed that is on the 100amp breaker. From there it just
drips all over the service panel wires and collects on the bottom of
the box where it drips out of crevices.
The service to my house is bolted on the side near the roof, from there
a cable (about 6') travels down to the meter box, then another cable
leaves the meter box for about 18" and enters the house into the
basement. The meter itself had a lot of moisture inside it, the bottom
of the meter box had a punchout, I tapped it open to see if water was
inside there, but there was not any. I am thinking maybe the water is
entering thru the casing of the cable. This cable is 30 years old. I
wrapped eletric tape around the end that comes out of the meter
yesterday. There is putty around the point where the cable enters and
exits the meter and enters the house (thru the elbow).
Anyone ever experience this? Any ideas on where the water could be
coming in? I assume that the cable coming out of the meter is
different from the cable coming into the meter (not continuous), so I
wrapped the end closest to the leak first to see if this makes a
difference, but will not know until the next rainstorms...
Thanks! Mark
|
291.1028 | | 19096::BUSKY | | Mon Jan 29 1996 12:37 | 13 |
| > Anyone ever experience this? Any ideas on where the water could be
> coming in? I assume that the cable coming out of the meter is
Yep, more often than not, the water enters through the so-called
weather head! Once inside the outerjacket of the cable, it follows
it just like a pipe right into your main panel!
The weather head "seal" is usually just a clamp and cover around
the cable. Wind blow rain can find it's way in there. Maybe some
putty up there might help. But be careful up there near the
service cable to feed cable clamps.
Charly
|
291.1029 | weather head? | 11666::CLEMENT | Smells like Nirvana | Mon Jan 29 1996 14:49 | 6 |
| Charly,
This is where the street feed connects to my house? I noticed some
kind of little box up there, is that the weather head? I'll take a
closer look next weekend, maybe I can seal it up with putty or some
sprayfoam??? Thanks, Mark
|
291.1030 | Create a "Drip Loop" | BINKLY::CLAY | Indecision may or may not be my problem | Mon Jan 29 1996 15:21 | 27 |
| Try looping the wires going to the weather head down so the water
follows the wires and drips off and doesn't flow down inside the
outer sheathing of the cable.
Hope this helps....
Don
conection to the house
/ main feedersferom street
/ /
Xmmmmmmmmmmmmmmmmmmmmmmmmmmmmmmmmmmmm
x
|wh x
|w x x
|w x x
|w xx
|w \
|w \
|w \drip loop
|w
|w
|w /meter
|w /
|---- /
| |
| |
|____|
|
291.1031 | | 19096::BUSKY | | Mon Jan 29 1996 15:37 | 27 |
| > This is where the street feed connects to my house? I noticed some
> kind of little box up there, is that the weather head? I'll take a
Exactly! If you've got "flat" entrance cable going up the side of
the house, the weather-head is usually a clamp-on "box" maybe 3"
by 3" or so and probably has a mounting slot for a screw to fasten
the weather-head to the side of the house.
It covers the end of the cable where the sheathing stops but the
two feed wires and loose ground wires continue out and are
connected to the street feed. The "box" is more like a hood over
the cable. Very easy for wind blown rain to enter, especially if
it's mounted parallel to a shallow roof line.
Once the water enters the sheathing, it travels right down the
cable, into the meter box. If your meter box has a wire in the top
and out the bottom, the water probably "sticks" to the ground
wires, which usually feed straight down to a pair of connecting
blocks, and then re-enter the sheathed cable and make it's way
down to the main panel.
I've since replaced my feed cable with steel conduit up the side
of the house. This type of arrangement seems to have a more
weather tight type of weather-head. It's also mounted vertically
and less susceptible to wind blown rain.
Charly
|
291.1032 | Its like, you were there! | 11666::CLEMENT | Smells like Nirvana | Mon Jan 29 1996 16:05 | 17 |
| > Once the water enters the sheathing, it travels right down the
> cable, into the meter box. If your meter box has a wire in the top
> and out the bottom, the water probably "sticks" to the ground
> wires, which usually feed straight down to a pair of connecting
> blocks, and then re-enter the sheathed cable and make it's way
> down to the main panel.
Yes you have described my meter, and indeed the water seems to be
traveling down the strands of ground wire and not the two feed wires!
Thanks for all the help and ideas! Hard to tell without looking at it
if I will do this, but do you see any problem with using spray-on
insulation foam where the wires enter the weather-head, or would I be
better off using a putty. I'd rather try putting something in there
instead of trying to re-arrange the configuration of the wiring.
Mark
|
291.1033 | | 19096::BUSKY | | Mon Jan 29 1996 16:58 | 13 |
| > if I will do this, but do you see any problem with using spray-on
> insulation foam where the wires enter the weather-head, or would I be
> better off using a putty. I'd rather try putting something in there
Putty is typically used, like you might find where the cable
enters the meter box. Although I suppose that some type of
expanding foam might have a better chance of filling all of the
nooks and crannies where the wires exit the cable sheath. Problems
with this? I don't know???
Charly
|
291.1034 | call MA Electric? | 11666::BWHITE | | Mon Jan 29 1996 17:46 | 6 |
| Mark...maybe MA Electric will take care of this....I thought that they
are responsible for the wiring up to the meter....I know that when I
had my electric service upgraded, they came and replaced the wire from
the weather head to the meter at no charge....
Ben
|
291.1035 | | 19096::BUSKY | | Mon Jan 29 1996 18:40 | 27 |
| > Mark...maybe MA Electric will take care of this....I thought that they
> are responsible for the wiring up to the meter....I know that when I
Not quite... above ground, they're responsible up to the
connection between the feedwire from the pole and your wires just
beyond the weatherhead that we've been discussing.
They also own the meter itself, but you own the meter box and
wiring to and from it.
In an underground situation, you own the wires underground and up
the side of the pole as well.
I don't know what the rules are for an underground service in a
development where they have underground feed wires as well.
Probably somewhere inside of the ground level distribution boxes.
Keep in mind, these rules are for the state of Massachusetts.
Your milage will vary in other states.
There are also several communities in Mass that have local
municipal electric companies (not Mass Electric or Boston Edison).
I think that most of them also follow the rules listed above but I
don't know for sure.
Charly
|
291.1036 | Mass electric. just dont take NO... | ANGST::DWORSACK | | Mon Jan 29 1996 19:27 | 30 |
| RE: Mass electric.
whenever it would rain hard, or blow from a direction, i would get
water in my box in the basement. turned out it was running down
the wires starting at the point where the wires would enter the
connector where the drip loop should be. turns out i did all i could
(not much) but the large ground cable was not long enough to get
a loop.
i called and someone came out to look at it. (i didnt ever know they
were there) i expected someone to at least knock on the door and
ask to see where it was leaking.
so i called and they said they had been there. i said come out again
and talk to me about it. i thought it was THEIR problem. i finally got
to talk to a field supervisior and he would send someone.
FINALLY a nice guy comes out and i tell the story. yep, he says,
water will work down that braided ground cable like it was running
downhill. i asked real nice if he could put some kind of "extention"
piece on it. sure he said , but you mind if i drive my truck over
your lawn.. hell, i would have done anything to get this fixed for
free...!! i even had him put some kind of cover on the wires
rubbing against a tree. (a tree i couldnt cut down, since it had
the electric wires on one side, and tele on the other... :-(
just dont take NO for a answer. request someone come out and talk
to you..!!!
jim
|
291.1037 | | SMURF::MSCANLON | a ferret on the barco-lounger | Mon Jan 29 1996 21:00 | 6 |
| I had the same situation you describe about 2 winters
ago. Called PSNH, they came out and fixed it. Never
got a bill for it. This is, of course, New Hampshire.
Don't know about Massachusetts.
Mary-Michael
|
291.1038 | MA Electric | 11666::CLEMENT | Smells like Nirvana | Tue Jan 30 1996 13:08 | 10 |
| Well, MA Electric came out this morning. That was fast, within 1 hour
of calling them and asking them to look at it and install a drip loop.
Turns out we already have a drip loop. He said the weather head box
should be replaced, it is not at the correct angle, and that we should
of course have an electrician do this. I still need to get up there
and take a good first hand look at it. Maybe I can still get away with
sealing the box, or perhaps I can move the angle of the box myself if
there is just a screw holding it onto the house.
Mark
|
291.1039 | the weather head angle? | 11666::CLEMENT | Smells like Nirvana | Wed Jan 31 1996 12:03 | 33 |
| Got a better look at the weather box this morning (from the ground).
This box is a lot smaller than I thought it would be (maybe 2"x2"), it
looks a bit rusted and instead of the box being horizontal, it is at
a 45 degree angle. Is it suppose to be angled? How difficult is it to
replace this box, and how dangerous is it. I have done wiring inside a
service panel before, but messing with the main feed is new to me.
Here is an attempt to draw the roof line and angle of the box...
/ <--- roof line
/
/
/ /\ <--- top of box
/ /
/ /
/ <--- cable leaving bottom of box
I am thinking that perhaps it should be more like this...????
/ <--- roof line
/
/
/ ___ <--- top of box
/ | |
/ /
/ <--- cable leaving bottom of box
|
291.1040 | adding a 2nd light to 2 switches | AKOCOA::STUARTR | Skiers have bigger moguls | Wed Mar 06 1996 14:46 | 36 |
|
I installed a light in the stairwell going down to the basement. I
needed this because when I finished the basement and enclosed part
of the stairway it made it dark.(no light at bottom of stairs)
I have a switch at the top of the stairs and in the garage that works
a light in the basement but only lights part of the bottom stairs.
I installed track lighting in place of the existing light with no
problem, works off the switch fine.
I installed the new light right above the switch at the top of the
stairs running the wire from the switch to the new box.
The switch has the white and red wire from the other switch connected
to it and the black wire from the downstairs light. The black wire
from the other switch and the white wire from the downstairs light
are tied off together. So I connect the black wire from the new
light to the switch where the black wire from the other light is
and the white wire from the new light to the white and black wires
that are tied off. NOT !
When the downstairs light is off, the new light is on and visa-versa.
So I'm scratching my head and taking a load of crap from the wife at
this point.
I tried a couple other OBVIOUS combinations but the result is always
the same.
Any ideas ??? This looked soooo easy !
Randy
|
291.1041 | | MAET11::SEGER | This space intentionally left blank | Wed Mar 06 1996 15:43 | 17 |
| If i've read this correctly, it sounds like you're saying you have a 3-way
switch and want to add an addional light.
If you look in the box you're trying to connect the second light to, are there
2 cables or one? If one, it's a 3-wire one (henve the red wire) and all it
really does is connect to the other switch. I think what happens is the
switches switch the HOT wire between the red and the black depending on their
positions. IN this case, connecting your light to one of these may give the
unusual results you're seeing.
If you want both lights to work off the same switch, you'll need to connect it
to the SECOND cable, which must be in the other switch box , OR connect it to
the second light.
I think...
-mark
|
291.1042 | a general diagram | HNDYMN::MCCARTHY | A Quinn Martin Production | Wed Mar 06 1996 15:59 | 5 |
| If it helps check out:
http://hndymn.zko.dec.com/three_way.html
bjm
|
291.1043 | | WLDBIL::KILGORE | Stop Global Whining! | Wed Mar 06 1996 16:02 | 21 |
|
If you're positive that the cable that feeds the downstairs lights
is coming from the upstairs box, just tie the new cable to it, black to
black and white to white.
The second possibility, if there are two cables into the upstairs
box, is that the two-wire cable is an unswitched feed and the three-wire
goes to the garage switch (and another cable connects the garage
switch to the lights). In that case, tie the white wire from the new
light to the white of the unswitched feed, and the black from the new
light to the wire that currently connects to the center pole of the
switch. (A three-way switch connects either of two wires on the
"outside" poles to a third wire on the "center" pole; it's pretty easy
to figure out which is the center pole with an ohmeter; turn off the
power and disconnect the switch first. :-)
The third possibility, if there is only one three-conductor wire coming
to the upstairs switch, is that you just can't run a wire from that
switch to the new light. (In this configuration, there is no neutral
wire available at the upstairs switch.)
|
291.1044 | Run new light wires to existing light | FOUNDR::DODIER | Single Income, Clan'o Kids | Wed Mar 06 1996 16:24 | 14 |
| It's hard to know exactly what you have without seeing it. You'd
need to know which box the power feeds into, and where the light is in
relation to the switches, and so forth to be able to explain to us what
you actually have. I don't think that's nessecary though.
The bottom line is, a light takes only two wires, a hot and a
neutral. Depending on where the light is in relation to the switches,
the wires going to the existing light may not be black and white.
The easiest way to do this is to run the wires for the new light to
the two wires going to the existing light. This assumes that you can
get the wires back to the way that they were originally connected.
Ray
|
291.1045 | | ODIXIE::ZOGRAN | Atlanta, Home of the WS Champs | Wed Mar 06 1996 18:08 | 8 |
| How do I re-wire a light switch to have all of the outlets in a room
always remain "on"? I just set up a PC in a room with all of the
outlets working off of one light switch, and I'm afraid of the kids
turning the switch on and off. Leaving the outlets hot wouldn't be a
problem.
Dan
|
291.1046 | Easiest way... | HELIX::WELLCOME | Steve Wellcome MRO1-1/L31 Pole HJ33 | Wed Mar 06 1996 18:17 | 6 |
| Do you need the light switch for anything else (like an overhead
light)?
Easiest thing would be to take out the switch, join the wires with
a wire nut, and put on a blank cover plate.
|
291.1047 | Thanks | ODIXIE::ZOGRAN | Atlanta, Home of the WS Champs | Wed Mar 06 1996 18:31 | 4 |
| I don't need the switch for anything else. By connecting the wires I
assume that you mean black to black and white to white?
Dan
|
291.1048 | Should only be two shielded wires connected to the switch | VAXCPU::michaud | Jeff Michaud - ObjectBroker | Wed Mar 06 1996 18:52 | 13 |
| > I don't need the switch for anything else. By connecting the wires I
> assume that you mean black to black and white to white?
If the power feed comes into the box, as well as the wires going
to the light (or in your case the outlets) then the whites should
already be connected together (as should be all the grounds).
In any case, assuming the switch is a 1-way switch, there should
be only two wires connected to it (not counting a possible bare
cooper ground wire to a green screw on the switch), those two
wires, regardless of color, are the two wires you want to
connect together with a wire nut (after you've turned the breaker
off :-).
|
291.1049 | | WLDBIL::KILGORE | Stop Global Whining! | Wed Mar 06 1996 19:04 | 19 |
|
All your outlets, both top and bottom in each duplex fixture, are
controlled by the switch???
It's fairly common to have a number of outlets switch-controlled, but
it's also fairly common to have only one outlet in each duplex
controlled in this manner, while the other outlet is unswitched.
If this is your situation, just remove the duplex you want unswitched,
detach the three wires, cap the red wire, replace the duplex with a
new one (the original duplex has a connector between top and bottom
outlets broken off, allowing them to work separately), reattach the
black, white and ground wires, and reinstall.
If you really have only a two-wire switched connection to the outlets
(which is somewhat strange), remove the switch, disconnect the two
wires and connect them together, and replace the switch plate with a
blank cover.
|
291.1050 | I'll try some things that were mentioned | AKOCOA::STUARTR | Skiers have bigger moguls | Thu Mar 07 1996 11:03 | 14 |
|
re; adding a light .....
Thanks for the responses. I was assuming the other wire in the box
went to the light, but now that you mention it, it could go anywhere.
This weekend I'll disconnect it and if the existing light still works
I'll have my answer. I can't get another wire from the existing light
to the upstairs switch. I might be able to get a wire from the garage
switch to upstairs though. Should keep me busy this weekend.
I'll update things next week.
Randy
|
291.1051 | ??? | FOUNDR::DODIER | Single Income, Clan'o Kids | Thu Mar 07 1996 14:02 | 9 |
| re: 1050
> I can't get another wire from the existing light to the upstairs switch.
You don't need to get a wire from the existing light to the
upstairs switch (unless you're trying to do something else I missed).
You need to get a wire from the existing light to the *new light*.
Ray
|
291.1052 | can't | AKOCOA::STUARTR | Skiers have bigger moguls | Thu Mar 07 1996 15:18 | 15 |
| <<< Note 291.1051 by FOUNDR::DODIER "Single Income, Clan'o Kids" >>>
-< ??? >-
re: 1051
< You don't need to get a wire from the existing light to the
< upstairs switch (unless you're trying to do something else I missed).
< You need to get a wire from the existing light to the *new light*.
< Ray
can't do that either.....
Randy
|
291.1053 | Simple 3-way diagram | FOUNDR::DODIER | Single Income, Clan'o Kids | Thu Mar 07 1996 16:40 | 41 |
| If that's the case, then your only alternative is to either learn
how three-way switches operate and then learn how to apply it to your
particular situation, or get someone who has this knowledge to do it
for you.
If you knew which box had the power coming into it and where the
light was in relation to the power feed wire and switches, then I could
enter in a simple schematic you might be able to follow. Otherwise, I
don't see how anyone here will be able to help you without this
information.
On the outside chance this will help, here is a simple one light
schematic with two 3-way switches to ponder -
blk = black wire
wht = white wire
o = switch or light screw terminal
+-------+ +-------+ +-------+
| box | | box | | box |
v v v v v v
red
blk o-------------o blk wht
-------------o wht o------------olighto----
feed wires o-------------o |
wht |
---------------------------------------------------------
^ ^ ^ ^ ^ ^
| box | | box | | box |
+-------+ +-------+ +-------+
A 3-way switch has 3 terminals, one of which is a slightly
different color than the other two. This can be referred to as the
point terminal. The switch connects one or the other terminal to the
point terminal.
If you draw them in yourself, and simulate the switching action from
one to the other, you'll see how it works and also understand why a 3-way
switch cannot be marked on or off like a single-pole (2 terminal) switch.
Ray
|
291.1054 | | HYLNDR::BROWN | | Fri Mar 08 1996 20:15 | 33 |
|
off the subject, but...
I did a similar thing a house ago. I added an overhead light at the bottom of
stairs and made the switch a 3-way. Initially I found 3 wire in the
single switch at the top of the stairs which controlled a light at the
top of the stairs and a utility light in the middle of the basement.
I initially thought, Great! the electrician ran 3-wire so I can just
splice in the new switch at the bottom of the stairs and be all set.
The downstairs light was within 5' of the panel, so what I thought
had been done was 2 wire to light, three wire to switch (power sent
up stairs to switch and back down the third leg to the light).
I couldn't get the stupid thing to work. Power never seemed to be
where I thought it should be.... Good reason. Actually power came
from upstairs! down thru the light at the top landing, down into
the switch, then a switched leg went to the down stairs lights, and
a hot leg went down behind the fuse panel out to the outside/
downstairs light... also turns out it then loops up into the 1st
floor to support some lights there. This is probably all to code,
but butt ugly. Power starts from the downstairs panel then first goes
up to the 2nd floor then works its way back down then up again.
I ended up dead heading the power as it came down thru the stair
landing light and adding another breaker to the panel, cutting the wire
as it went behind the panel and connected both halves to the new
breaker. Then I rewired the all the lights in the basement, at
least I was then able to remember which leg was powered and from
which direction.
from the
|
291.1055 | Problem Solved | ODIXIE::ZOGRAN | Atlanta, Home of the WS Champs | Mon Mar 11 1996 12:16 | 8 |
| Turned off the breaker and took off the switch. It had the black wire
going in and out, so I just unhooked the wires, connected them
(standard wire connector and tape), popped the power back on and
replaced the switch (will deal with a plain cover later). All outlets
work fine, with no possibility of someone switching he computer off via
the lightswitch.
Dan
|
291.1056 | avoid tape | HNDYMN::MCCARTHY | A Quinn Martin Production | Mon Mar 11 1996 13:33 | 9 |
| >> (standard wire connector and tape),
Tape? Why tape? If the "wire nut" is not covering all exposed copper then
something is wrong.
Its very rare when tape is needed. - I don't even know where it would be called
for in the code!
bjm
|
291.1057 | | QUARK::LIONEL | Free advice is worth every cent | Mon Mar 11 1996 13:36 | 5 |
| I always tape my wirenuts to provide additional resistance to the nut twisting
off or the wire popping out. Similarly, I put tape over the side terminals on
switches and outlets.
Steve
|
291.1058 | | VAXCPU::michaud | Jeff Michaud - ObjectBroker | Mon Mar 11 1996 14:10 | 9 |
| > I always tape my wirenuts to provide additional resistance to the nut twisting
> off or the wire popping out.
Why would the nut twist itself off?
> Similarly, I put tape over the side terminals on switches and outlets.
I do this sometimes too, especially when the devices are inside
a metal work box...
|
291.1059 | Under certain conditions | FOUNDR::DODIER | Single Income, Clan'o Kids | Mon Mar 11 1996 15:00 | 6 |
| About the only time I tape anything is if I put an old work box in
a sheetrock wall using the metal straps (buchanon strips [sp?]). Then
I'll tape the terminals of a switch or outlet. Not sure if it's
required for code, but it's a good idea anyway.
Ray
|
291.1060 | hmmm, I wonder when you ARE supposed to use it? | HNDYMN::MCCARTHY | A Quinn Martin Production | Mon Mar 11 1996 15:19 | 6 |
| If the nut is applied correctly it will never loosen up. I have taped the
sides of devices when installing them in old-work metal boxes but I have never
taped over a wire nut ever since I worked with a master electrian "oh so many
years ago" :-)
bjm
|
291.1061 | I give up | AKOCOA::STUARTR | Skiers have bigger moguls | Mon Mar 11 1996 15:57 | 17 |
|
I'm gonna call my electrician !
recap; switch upstairs has 2 wires, a 3-way and a 2-way. red and white
of 3-way into switch, black of 2-way into switch, black of 3-way and
white of 2-way tied together.
after more investigation, switch in garage has only the 3-way wire
that I assume goes to upstairs switch.
I've tried every possible combination of connections with no luck,
the new light goes of when you turn on the downstairs.
Yesterday I disconnected 2-way and the light in cellar does not work
so I assume the 2-way supplies the light. It's probably something
simple that is getting by me.
Randy
|
291.1062 | It's not a "simple thing" | FOUNDR::DODIER | Single Income, Clan'o Kids | Mon Mar 11 1996 16:35 | 13 |
| re:1061
The 2-way and the 3-way have nothing to do with each other. A 3-way
is NEVER, under *any* configuration, ever connected to a 3-way. A 3-way
will only ever be connected to another 3-way in a two switch set-up, or
a 4-way if more than 2 switches are used to control the same thing.
If you do not understand 3-way switches, and you can't run the wire
from the existing light to the new light, then it is not a "simple
thing". It sounds like you've been lucky that you haven't shorted
anything out, yet ;-)
Ray
|
291.1063 | | ODIXIE::ZOGRAN | Atlanta, Home of the WS Champs | Mon Mar 11 1996 17:09 | 4 |
| re. - The Tape. It doesn't hurt, and, while the chances of it
"unwinding" are slim, I had the tape handy and went for it.
Dan
|
291.1064 | | VAXCPU::michaud | Jeff Michaud - ObjectBroker | Mon Mar 11 1996 18:35 | 11 |
| > re. - The Tape. It doesn't hurt, and, while the chances of it
> "unwinding" are slim, .....
^^^^
if you tightened the nut yourself and you give it a little
pull to make sure it's on, then I'd say the chances are
less than "slim". Unless you got polterguists ....
Also remember that *before* you put on the wire nut, that the
wires should already be mechanically joined (ie. twisted together)
and sound....
|
291.1065 | Pwiiiiing! | SMURF::wolf95.zk3.dec.com::PBECK | Paul Beck, WASTED::PBECK | Mon Mar 11 1996 19:26 | 3 |
| I'm getting this mental image of the twisted wires under the wire nut acting as
a spring, untwisting suddenly and sending the wire nut caroming around the
inside of the electrical box like a champagne cork...
|
291.1066 | | WLDBIL::KILGORE | Stop Global Whining! | Mon Mar 11 1996 19:42 | 11 |
|
Re .1065:
It has been calculated that if all the potential energy stored in all
the twisting of wires and wire nutes in an average 2.3-bedroom house
was converted to kinetic energy simultaneously, the 1.2-gigawatt surge
would cause a warp in the space-time continuum could destroy the universe
as we know it.
Of course, that's a worst-case scenario...
|
291.1067 | | ODIXIE::ZOGRAN | Atlanta, Home of the WS Champs | Mon Mar 11 1996 20:08 | 6 |
| I think I triple twisted and duct taped the connections on my air
shredder. Shredded air does funny things to non-taped wire
connections. Of course I didn't tape my water shredder connections for
the pool (who does that anymore anyways?).
Dan
|
291.1068 | What's that about an Ayer sweater? | SMURF::wolf95.zk3.dec.com::PBECK | Paul Beck, WASTED::PBECK | Mon Mar 11 1996 21:58 | 2 |
| I don't use wire nuts. I use a wire shredder. You get much better wire-to-wire
connectivity with a wire shredder.
|
291.1069 | getting back to basics | MAET11::SEGER | This space intentionally left blank | Tue Mar 12 1996 11:39 | 17 |
| hell, I just fill the box with epoxy!
back to the original question (was there really one?) - getting the 2 lights to
work off the two switches, something I have done may help you...
Having turned off the breaker, remove all the switches and expose all the wires
involved. Now turn the breaker back on and find the HOT wire! Now try to
figure out where the OTHER wires go. If you only have 2 reds (which I suspect
you do), they're obviously part of the same cable as are the associated black
and white wires. If you're lucky, there will only be one or two cables left
and you should be able to determine which end goes with which. If you can't,
you're dead in the water.
Having verified all this stuff, you should be able to draw out the diagram of
what's connected to what and from there get your switches working.
-mark
|
291.1070 | up the creek | AKOCOA::STUARTR | Skiers have bigger moguls | Tue Mar 12 1996 16:33 | 14 |
|
I talked to my electrician last night and he confirmed what was already
mentioned here, I have no neutral, I have to get it from the light that
is downstairs. He said it's possible to fix it so the ground wire was
the neutral but he wouldn't do it or tell me how. (I wouldn't anyway)
So, I'll have to figure out how to get a wire from the downstairs
light to the upstairs light. The ceiling of the basement is sheetrocked.
(I know, stupid move... didn't have enough room for a suspended one)
My wife is REAL pleased with this project !
Randy
|
291.1071 | ground = netural (sort of) | MAET11::SEGER | This space intentionally left blank | Wed Mar 13 1996 10:32 | 13 |
| >He said it's possible to fix it so the ground wire was
>the neutral but he wouldn't do it or tell me how. (I wouldn't anyway)
as a point of clarification:
ground wire = neutral (from a functionality perspective)
at least they're run to the same place in the fuse box and are even the same
gauge wire. I've hear a few explanations in the past why you need both and
usually forget them as quickly as I hear them, though I'm sure someone will
once again remind me in here 8-)
-mark
|
291.1072 | Its in the flow.. | BITZEE::CLAY | Indecision may or may not be my problem | Wed Mar 13 1996 12:32 | 1 |
| A neutral carries current a ground does not......(or should not)
|
291.1073 | | QUARK::LIONEL | Free advice is worth every cent | Wed Mar 13 1996 12:34 | 4 |
| The NEC is quite explicit that a ground conductor (bare or green) should never
be used in place of a neutral.
Steve
|
291.1074 | inquiring minds want to know | MAET11::SEGER | This space intentionally left blank | Wed Mar 13 1996 15:23 | 9 |
| re: last couple
I'm not saying that one should use a ground instead of a neutral, all I'm saying
is that from a connectivity perspective, they both go to the same place...
that said, could someone say a few words about WHY this is done the way it is
as I'm sure there's a good reason.
-mark
|
291.1075 | | WLDBIL::KILGORE | Stop Global Whining! | Wed Mar 13 1996 15:59 | 23 |
|
Re .1074:
At the service box, all neutrals and grounds are tied to the same bar,
which is tied to a good earth ground.
In normal service, the neutral wire completes the current loop with the
hot wire; the neutral always sits at ground potential, while the hot wire
swings + and - with respect to it. The ground wire also sits a ground
potential, but it doesn't conduct current.
The ground wire is meant to complete the current loop *IN AN EMERGENCY*.
For example, if a hot wire in your washing machine vibrates loose and
touches the metal enclosure, which is connected to the ground system
through the ground pin in its power cord, the gound system completes
the circuit, keeping the enclosure at 0 potential (and popping the
breaker). Without the backup ground system, the enclosure would quite
patiently sit at the hot wire potential until you do the next load, at
which time it would at very least administer a nasty shock.
The ground system is meant to be a backup -- safety via redundancy. It
can't be a backup if it's being used as a primary conductor.
|
291.1076 | can't be too careful with electricity... | MAET11::SEGER | This space intentionally left blank | Thu Mar 14 1996 10:54 | 10 |
| ahhh... that sounds famailiar.
just as a point of clarification for me, many new electrical appliances have
one of the plug prongs enlarged so the plug will only go in one way and any
exposed metal parts are then grounded to that, eliminating the need for the
3rd wire for gound. Applying that login to your washing machine example, if
a hot wire loosened up and hit the chasis wouldn't it trip the breaker even if
the ground wire weren't attached?
-mark
|
291.1077 | only as good as the dyi'er installation | HNDYMN::MCCARTHY | A Quinn Martin Production | Thu Mar 14 1996 11:09 | 5 |
| Yes the polarized plugs are supposed to make two-prong usage safer - but how
many DIY'er know which side of the outlet is supposed to get the hot and which
one gets the neutral???
bjm
|
291.1078 | | EVMS::MORONEY | while (!asleep) sheep++; | Thu Mar 14 1996 14:16 | 19 |
| re .1076:
No, the exposed metal is not connected to the neutral in items with the
large plug. It would be too dangerous to do so. A break in the neutral
would mean the whole chassis is "live" (in series with the appliance), not
to mention the miswired DYI outlets, and even those with older outlets who
file off the enlargements on the plug!
What they do is, the appliance is designed so in case of a fault contact is
much more likely with the neutral than the live side, decreasing (but not
eliminating) the odds of a zap. Because of such dependancies I consider this
rather silly.
About the only example I can think of is obsolete, "hot chassis" TVs where
the tubes (told you it was obsolete) are run directly from the rectified power
line, and the circuit ground is directly connected to one side of the power
line, hopefully the neutral.
-Mike
|
291.1079 | Why a separate ground wire | SSDEVO::JACKSON | Jim Jackson | Thu Mar 14 1996 14:41 | 8 |
| 1) Because current flows in the neutral conductor, it is not at "ground"
potential at the appliance (IxR voltage drop occurs in the conductor). A
separate grounding conductor is always at "ground" potential.
2) As mentioned, if the neutral feed opens, the neutral wire in the
appliance is now at the full "hot" potential. If a grounding conductor
opens, the appliance chassis is now just floating, and it would take a
second fault to cause a shock potential.
|
291.1080 | | HDLITE::SCHAFER | Mark Schafer, Alpha Developer's support | Fri Mar 15 1996 15:43 | 13 |
| "login to your washing machine"
Mark, you got a Netscape[tm] washer/dryer? :-)
I believe that the small appliances that come with "polarized" plugs
are built so that the outside surfaces cannot under any circumstances
become hot. Plastic parts and "double insulation" are methods of
achieving it.
You connect the hot wire to the copper colored terminal. The neutral
connects to the silver, and ground to green.
|
291.1081 | we have light ! | AKOCOA::STUARTR | Skiers have bigger moguls | Mon Mar 25 1996 13:15 | 14 |
|
We can close the books on .1040
I went out and bought an 18" drill bit and 25' of wire ......
(had to drill up through the 2X10's, subfloor and plate)
Managed to run a wire from the new light to the existing light and it now
works fine off the switch. This sounds much easier than it was !
Now I have to patch the 5" X 5" hole I had to put in the sheetrock to get
the wire across the ceiling to the light.
Randy
|
291.1082 | NEC requirements for "smart" switches??? | STAR::BALLISON | | Tue Apr 02 1996 14:51 | 31 |
| Has anyone know what the NEC has to say about remote light
switching in a house??? I'm building a new house and rather and
directly wiring from switch to fixture, I'm using X-10 based remote
switches with the actual line being switched in boxes located in the
basement. This gets me lots of flexability since I can switch any
light from just about anyplace. But if the dedicated computer running
the show (a timecommander +), goes down, none of the lights will work.
(btw, I've had the timecommander running for several months in the
place I'm currently renting with no blips or crashes of any sort).
Leviton makes these nice 4 switch modules that live in a single
box. Its much nicer looking than having the 3 and 4 wide boxes full of
switches that show up in newer houses. Plus you can define "macros"
where a single switch can do combinations of things (like dim the
living room lights, brighten the dining room lights and turn off the TV
at dinner time).
I thought of fully wiring the switches/lights and then adding yet
another box for the remote control stuff, but the number of electrical
boxes got out of hand in a big hurry.
The local inspector in Mont Vernon NH seems pretty mellow. I worry
a bit that he'll be baffled by the whole concept (he doesn't even own
an answering machine). The mini NEC guide books don't say much about
this. I don't really want to spend $60 for the real thing and then try
to wade through it to find out the aspects of this in a residential
application. I'm sure it has plenty to say about commercial
application of this sort of technology.
Brian
|
291.1083 | | 2082::LIONEL | Free advice is worth every cent | Tue Apr 02 1996 16:11 | 7 |
| The NEC doesn't seem to concern itself with remote switching. But it's
what your inspector will accept that really matters.
I have read of houses with setups like what you describe - all outlets
and "switches' relay-controlled with a junction box in the basement.
Steve
|
291.1084 | | EVMS::MORONEY | while (!asleep) sheep++; | Tue Apr 02 1996 17:06 | 11 |
| >I have read of houses with setups like what you describe - all outlets
>and "switches' relay-controlled with a junction box in the basement.
I lived in such a house as a kid. 12 light circuits had 24V switches run off
a doorbell transformer and wired with doorbell type wiring.
These all went to a box in the basement which had a bunch of latching
relays. Also there were 2 control panels that could turn off or on any or
all of these circuits.
Since the relays were latching relays they actually remembered their state
across power failures just like "real" light switches.
|
291.1085 | | LEFTY::CWILLIAMS | CD or not CD, that's the question | Tue Apr 02 1996 21:43 | 16 |
| My dad wired our house in LI that way...
It was a GE industrial/commercial wiring system. Relays at each light,
wired to 110VAC, with 24VAC control wiring to the switches, with
multiple switches. Works great.
Most inspectors have seen this stuff in commercial buildings. It's even
covered in the little green code summary book that Spags and others
sell...
THe X10 stuff is another issue, though. It's just direct switch
replacement, so it's not too difficult to figure out, but who knows
what the inspector will say.
Chris
|
291.1086 | "every habitable room ..." | TEKVAX::KOPEC | we're gonna need another Timmy! | Wed Apr 03 1996 12:04 | 4 |
| as long as there is a switch in the room that will turn on the light
they will be happy; if not, they probably won't. (sec 270-10(a)).
...tom
|
291.1087 | | STAR::BALLISON | | Wed Apr 03 1996 14:31 | 29 |
| Well its not quite using the X-10 switch replacements... The main
problem with them is that they don't transmit an X-10 message when you
push them (they only respond to X-10 messages). The net effect is that
the control computer doesn't know the state of the light.
Leviton makes a small module that does the same thing as the switch
only it doesn't have a push button. I'm hiding these critters in
electrical boxes in the basement (accessable for fixing them in the
future if they end up with similar reliability as the switches). One
problem is that they are very expensive ($40). I've toyed with just
using the regular $9 switches hidden in the basement since the function
is identical. Anyway, the normal switch location in the entry to each
room now gets a device with 4 rocker switches that can send X-10
commands to the central controller, which in turn will send out the
on/off/dim commands to the "x-10 switches" hidden in the basement.
So, the part in the code about a switch to control a light at the
entrance to each room is met. I was just worried that the NEC might
frown on the need for a functional computer between the switch and the
light. Of course we all have functional computers in our cars,
microwaves, VCRs, TVs, dishwashers etc..............
I do worry a bit about what happens if the control computer
fails... At $600 its pretty expensive to keep a spare. I chose the
one from the largest maker (and used X-10 which is by far the biggest
home control protocol), so hopefully spares will be available for
some time to come.
|
291.1088 | Weird box problem... | AKOCOA::ROLLINS | five fuzzies | Thu Apr 18 1996 21:15 | 28 |
| We're currently running a 7K Watt generator and bringing power
into our electric box at 240v. We've been having some problems
that seem like they are right at the box...when you switch
on or off one breaker to any circuit it tends to effect the
other circuits - if I switch off my 30amp breaker to the water
pump (wired for 240v), the living room circuit shuts down -
and that is on a totally separate 15amp breaker.
And the bathroom's 15amp breaker effects the 30amp water pump
circuit.
Is this normal??? I have no clue what is going on, but am
wondering if the generator is no longer supplying the full
240v????
The box looks like this:
Side 1 Side 2
in main 50amp
bathroom 15amp 30amp-a Water
bedroom1 15amp 30amp-b Pump
Kitchen 20amp 15amp Bedroom2
empty
empty
Thanks for any help!
|
291.1089 | Wiring by Larry, Moe and Curly? | EVMS::MORONEY | while (!asleep) sheep++; | Thu Apr 18 1996 22:51 | 10 |
| About the only thing I can think offhand is if the living room circuit
(not on the diagram?) is really wired through half the pump circuit and
one of the pump leads is through the bathroom breaker.
Only other wild guess is check the neutral, but that would lead to other
symptoms.
240V 30A pump circuit? Must be some pump!
-Mike
|
291.1090 | Question and thoughts | FOUNDR::DODIER | Single Income, Clan'o Kids | Fri Apr 19 1996 14:44 | 21 |
| re:1088
When you say the living room circuit shuts down, do you mean the
breaker trips, or you just lose power to the living room ? If it's the
latter, then part of the living room must be wired from one of the legs
coming from the well circuit.
The other possibility is that you're losing one of your hot legs
under load. When the living room shuts down, check to see if you
actually have power at the living room breaker. If not, see if you
dropped the whole leg. I suspect you'd be noticing other problems though
if this happened.
If this is the case, look to see if you have your load as evenly
distributed as possible across the two legs (bus-bars) at the main
panel. Obviously, 240v breakers go across both legs, but the remaining
ones may be unevenly distributed.
Ray
BTW - 240v/30a is not that unusual for a deep submersible well pump.
|
291.1091 | Electrical - Buzzing Sound - strip light dial switch | APLVEW::DEBRIAE | raising two thumbs up in tranquillity | Wed Aug 07 1996 15:12 | 30 |
|
Gee I liked the old organization of the file better.
I'm responding to the old string 5458 "Electrical - Buzzing Sound"
which now is .695...
I installed two strip lights inside a china kitchen cabinet (I'm just
finishing a total kitchen rebuild). The lights had plugs on their
electrical wires that are removable, such that when you snap the plug
onto the wire, two teeth inside bite into the power and ground lines.
There is no grounded prong on the plug, nor is one side of the wire
marked in any way, nor do the instructions say one side of the wire
must be power, etc. I connected these two wires directly to power and
ground in an electrical workbox.
On the wire, before the strip lights, is a round dial type of switch.
Rotate half a turn is on, another rotation is off. This switch is
making a loud buzzing sound that is driving my SO crazy. Before the
crown moulding goes up and I no longer have access to the workbox,
I will try reversing the power and ground sides, though it should
not make a difference.
What could be causing this switch to buzz?
Can I take any other steps other than hacking in a light switch
somewhere now that the backsplash tiles are up and I have no room for
one. Any ideas?
-Erik
|
291.1092 | | HDLITE::SCHAFER | Mark Schafer, SPE MRO | Wed Aug 07 1996 15:48 | 1 |
| maybe try replacing the zip-cord switch?
|
291.1093 | eliminated strip light switches from equation altogether | APLVEW::DEBRIAE | raising two thumbs up in tranquillity | Mon Aug 12 1996 13:54 | 8 |
|
I found some room for a hidden light switch in a cabinet corner and
will simply reroute the wire through the light switch, cutting all
power to both strips and their noisy switches. This works out well
since reaching for the upper switch inside the cabinet was a pain, and
since the crown moulding covering the strip wiring went on this
weekend. For once the task timing was perfect...
|
291.1094 | | NOTIME::SACKS | Gerald Sacks ZKO2-3/N30 DTN:381-2085 | Mon Aug 12 1996 15:30 | 19 |
| We just moved into a first floor flat with no ceiling fixtures in the bedrooms.
The rooms all have wall switches, which seem to control half of a duplex
outlet. I'd like to install ceiling fixtures in two or three of the rooms.
Off the top of my head, I've come up with this methodology on fishing the
wires. I've never run a horizontal wire in a finished ceiling, so I want
to know if I've got the right idea.
1. Figure out which way the joists run.
2. Make hole in ceiling where fixture will be installed.
3. Make small hole at edge of ceiling between same pair of joists that
the other hole is between (should this hole be in the ceiling or the
wall or really at the junction of the two?)
4. Run fish tape from first hole to second.
5. Turn the corner (go down the wall). I've always used a length of
lightweight chain for vertical runs. Will one length of fish tape
do this, or should I use this in combination with the chain, or
do I need two lengths of fish tape?
6. Depending where I end up, go through the basement and down from the
switch.
|
291.1095 | | AIAG::SEGER | This space intentionally left blank | Mon Aug 12 1996 16:05 | 14 |
| I've run wires in ceiling, but I've never really figured how to get them through
the walls, short of having to cut holes...
The one thing that's REAL important is whether or not the ceiling is attatched
to strapping. If it is, the straps run perpendicular to the joists in which
case you need to rotate your thinking 90 degrees. I suppose if you start by
cutting the hole for the light fixture first, you can then put a mirror up there
and SEE whether or not there is strapping up there.
I'm still not sure how you make the turn to go down the wall without doing any
major excavating. For example, how do you get a hole in the 2X4's at the top
of the wall studs?
-mark
|
291.1096 | | 19584::DZIEDZIC | Tony Dziedzic - DTN 381-2438 | Mon Aug 12 1996 16:18 | 18 |
| You may find it easier to cut a pair of holes at the edge of
the ceiling/wall joint (one on the ceiling, one on the wall);
space the one on the wall down a few inches from the ceiling
to clear the top plate of the wall framing. You may have a
bit more patching to do, but the additional access will really
cut down the amount of time you spend blind fishing. You can
drill a hole in the top plate via the top of wall access hole.
Pull the cable up from the basement through the top plate, then
feed it over to the fixture opening. That way you can get by
with a single fish tape and/or use your chain method.
You should check where the power feed for the outlet runs before
planning your installation; the feed could go directly through
the switch or it could go into the outlet and via a switch loop.
Avoid running wires through exterior walls if you can; less chance
of insulation obstruction.
|
291.1097 | | WLDBIL::KILGORE | Stop Global Whining! | Mon Aug 12 1996 16:31 | 21 |
|
If the ceiling is strapped, I've found it possible to fish wires
parallel to either the joists or the strapping.
To go parallel to the strapping, make sure the tape lies flat enough
to sneak under the joists.
To go parallel to the joists, bend a small length of the end of the
fish tape back on itself and tape it, to make a small loop. This will
allow the tape to sneak over the strapping. (I haven't actually done
this with fish tape, but it works well with my tool of choice -- an
old 25-foot tape measure with a broken tip.)
--------------
On the other hand, if this were *my* project, and especially in light
of the ceiling-to-wall transition, which is never pleasant, I would
consider putting those switched outlets to good use and buying one or
two of those torchier-style lamps that reflect off the ceiling. Nice,
crisp, indirect lighting, no tools required!
|
291.1098 | 10+ years ago | HNDYMN::MCCARTHY | A Quinn Martin Production | Mon Aug 12 1996 16:42 | 16 |
| I don't know if its code anymore but the master electrician I used to work for
taught me to make small notches in the wallboard (or plaster/lathe which was
more often the case) at the top of the wall and on the ceiling. You then
fished from the center of the room to the hole on the ceiling. You notched
with a chisel the top wall plate deep enough so the RX cable and a staple could
be put in place. The cable was then pulled from from light to switch and
placed into the chiseled out top plate, stapled in, small metal plate was put
over it and nailed in place (to prevent nails from hitting the wire), then a
patch was applied.
>> Avoid running wires through exterior walls if you can; less chance
>> of insulation obstruction.
Not in my house, all interior walls have insulation also.
bjm
|
291.1099 | | NOTIME::SACKS | Gerald Sacks ZKO2-3/N30 DTN:381-2085 | Mon Aug 12 1996 17:10 | 7 |
| > On the other hand, if this were *my* project, and especially in light
> of the ceiling-to-wall transition, which is never pleasant, I would
> consider putting those switched outlets to good use and buying one or
> two of those torchier-style lamps that reflect off the ceiling. Nice,
> crisp, indirect lighting, no tools required!
We have two toddlers. Floor lamps (and even table lamps) are a hazard.
|
291.1100 | Swag chain? | SSDEVO::JACKSON | Jim Jackson | Mon Aug 12 1996 17:20 | 8 |
| How about a lamp hung on a swag chain from a ceiling hook? I did this in my
bedroom, which has the switched outlets that you describe. Run the chain
between ceiling hooks over to the wall, and then down to the outlet.
Now, I'll admit that in my case the hooks were already in the ceiling (as
plant hangers), and putting in a ceiling box is on my "honey do" list. But
I've managed to put off putting in the ceiling box for two years now,
because the swag solution is "good enough".
|
291.1101 | | WLDBIL::KILGORE | Stop Global Whining! | Mon Aug 12 1996 18:00 | 7 |
| .1099> We have two toddlers. Floor lamps (and even table lamps) are a hazard.
Well, there's you optimal solution.
Take 5-6 years planning the rewiring job in gruesome detail, at which
time the problem definition will have changed.
|
291.1102 | | NOTIME::SACKS | Gerald Sacks ZKO2-3/N30 DTN:381-2085 | Mon Aug 12 1996 19:31 | 3 |
| >How about a lamp hung on a swag chain from a ceiling hook?
My kids are climbers.
|
291.1103 | 'more power' | HNDYMN::MCCARTHY | A Quinn Martin Production | Tue Aug 13 1996 10:16 | 5 |
| >>>How about a lamp hung on a swag chain from a ceiling hook?
>>
>>My kids are climbers.
Use heavy chain, lag bolts and pad the floor, they will have a blast :-)
|
291.1104 | Doorbell blues... | ORION::OTTE | | Wed Oct 09 1996 22:22 | 18 |
291.1105 | sounds miswired. | TEKVAX::KOPEC | When cubicles fly.. | Wed Oct 09 1996 22:50 | 3 |
291.1106 | | VAXCPU::michaud | Jeff Michaud - ObjectBroker | Wed Oct 09 1996 23:18 | 21 |
291.1107 | not uncommon | HNDYMN::MCCARTHY | A Quinn Martin Production | Thu Oct 10 1996 01:16 | 5 |
291.1108 | ding, dong, the doorbell's dead... | PCBUOA::TARDIFF | Dave Tardiff | Thu Oct 10 1996 13:53 | 23 |
291.1109 | | REGENT::POWERS | | Thu Oct 10 1996 14:59 | 9 |
291.1110 | time for some data collection... | ORION::OTTE | | Thu Oct 10 1996 20:48 | 3 |
291.1111 | 110v between hot wire and buried but unused UF cable | HANNAH::SCHULLMAN | Dan Schullman | Sun Oct 20 1996 19:13 | 25 |
291.1112 | run a new line | HNDYMN::MCCARTHY | A Quinn Martin Production | Sun Oct 20 1996 22:13 | 11 |
291.1113 | | SHRMSG::BUSKY | | Mon Oct 21 1996 12:03 | 26 |
291.1114 | | MSBCS::BROCK | Son of a Beech | Mon Oct 21 1996 12:19 | 2 |
291.1115 | | HANNAH::SCHULLMAN | Dan Schullman | Mon Oct 21 1996 14:04 | 25 |
291.1116 | | SKYLAB::FISHER | Gravity: Not just a good idea. It's the law! | Mon Oct 21 1996 16:48 | 11 |
291.1117 | impedance. | NPSS::BENZ | I'm an idiot, and I vote | Mon Oct 21 1996 19:01 | 18 |
291.1118 | | EVMS::MORONEY | Sorry, my dog ate my homepage. | Mon Oct 21 1996 21:14 | 24 |
291.1119 | lightbulb removal left base behind | TLE::PACKED::BLATT | | Thu Dec 05 1996 23:36 | 16 |
291.1120 | I like my potatos sliced and fried :-) | HNDYMN::MCCARTHY | A Quinn Martin Production | Thu Dec 05 1996 23:39 | 9 |
291.1121 | interesting | VAXCPU::michaud | Jeff Michaud - ObjectBroker | Fri Dec 06 1996 01:23 | 3 |
291.1122 | | REGENT::POWERS | | Fri Dec 06 1996 11:55 | 10 |
291.1123 | Globe in the way ? | FOUNDR::DODIER | Double Income, Clan'o Kids | Fri Dec 06 1996 11:56 | 15 |
291.1124 | Try this with patience | SALEM::LEMAY | | Fri Dec 06 1996 14:41 | 19 |
291.1125 | Another WD-40 use | SSDEVO::JACKSON | Jim Jackson | Fri Dec 06 1996 17:38 | 2 |
291.1126 | it won't stay plugged in | ADISSW::HAECK | Mea culpa, mea culpa, mea maxima culpa! | Fri Dec 06 1996 18:15 | 8 |
291.1127 | | MROA::MACKEY | | Fri Dec 06 1996 18:31 | 1 |
291.1128 | | MKOTS3::WTHOMAS | | Fri Dec 06 1996 18:33 | 3 |
291.1129 | | ADISSW::HAECK | Mea culpa, mea culpa, mea maxima culpa! | Fri Dec 06 1996 18:45 | 2 |
291.1130 | | VAXCPU::michaud | Jeff Michaud - ObjectBroker | Fri Dec 06 1996 22:03 | 46 |
291.1131 | | QUARK::LIONEL | Free advice is worth every cent | Mon Dec 09 1996 10:54 | 10 |
291.1132 | | STAR::DZIEDZIC | Tony Dziedzic - DTN 381-2438 | Mon Dec 09 1996 13:01 | 8 |
291.1133 | | ADISSW::HAECK | Mea culpa, mea culpa, mea maxima culpa! | Mon Dec 09 1996 14:36 | 3 |
291.1134 | | SKYLAB::FISHER | Gravity: Not just a good idea. It's the law! | Mon Dec 09 1996 15:49 | 16 |
291.1135 | | ADISSW::HAECK | Mea culpa, mea culpa, mea maxima culpa! | Tue Dec 10 1996 13:39 | 3 |
291.1136 | how to add a box to a ganged set? | REGENT::POWERS | | Thu Dec 12 1996 12:53 | 19 |
291.1137 | no shortcut that I know of | HNDYMN::MCCARTHY | A Quinn Martin Production | Thu Dec 12 1996 13:05 | 13 |
291.1138 | Without one in hand...??? | FOUNDR::DODIER | Double Income, Clan'o Kids | Thu Dec 12 1996 13:34 | 12 |
291.1139 | | WLDBIL::KILGORE | How serious is this? | Thu Dec 12 1996 13:57 | 9 |
291.1140 | | REDZIN::COX | | Thu Dec 12 1996 14:08 | 14 |
291.1141 | | SKYLAB::FISHER | Gravity: Not just a good idea. It's the law! | Thu Dec 12 1996 15:03 | 9 |
291.1142 | not too hard | USCTR1::RIDGE | Steve Ridge @297-6529 | Thu Dec 12 1996 15:12 | 7 |
291.1143 | This method has worked for me | STAR::DZIEDZIC | Tony Dziedzic - DTN 381-2438 | Thu Dec 12 1996 17:18 | 26 |
291.1144 | | REGENT::POWERS | | Fri Dec 13 1996 12:08 | 18 |
291.1145 | cut open the drywall! | VAXCPU::michaud | Jeff Michaud - ObjectBroker | Fri Dec 13 1996 14:32 | 4 |
291.1146 | | AIAG::SEGER | This space intentionally left blank | Mon Dec 16 1996 11:22 | 5 |
291.1147 | | REGENT::POWERS | | Mon Dec 16 1996 12:03 | 27 |
291.1148 | | QUARK::LIONEL | Free advice is worth every cent | Mon Dec 16 1996 12:44 | 9 |
291.1149 | 220 extension cord wiring | STAR::SCHEN | | Thu Feb 06 1997 19:59 | 13 |
|
I am using 12/3 wire to make an extension cord to
go from a four_prong_twist_lock outlet to a three_
prong 220 outlet (looks like a standard 110 but the
two blades are perpendicular to each other). One
end will plug into the 220/110 outlet on a generator
and the other will have a 220 jointer plugged into
it.
Can anyone tell me what the correct way to do this
would be? (maybe even a nifty ascii diagram !?! )
|
291.1150 | avoid shocking experiences.... | PCBUOA::TARDIFF | Dave Tardiff | Thu Feb 06 1997 20:13 | 33 |
| I think you've got something wired improperly already.
4 connections on one end (the machine?) and only 3 on the other
(outlet?).
If a device uses 'pure' 220/230/240, then it only needs the
two 'hot' wires, which are 220 volts apart, and a ground wire for
safety. What's normally called 'neutral' is the center of the transformer,
between the two 'hot' lines, so either extreme to the center 'neutral'
produces 120 volts. At certain points in a wiring system, the 'neutral'
is connected to the 'ground', making them the same potential - so any
ground to a 'hot' is at most 120 volts.
An appliance like an electric range will use all 3. The heating
elements run between the two hots, getting 240 volts. Lights and timers
and electronics run between the neutral and a hot, getting 110. The
ground is there for safety, and connects to the metal frame, so if a hot
accidently shorts to the metal, it'll blow the breaker and turn off, instead
of leaving the chassis 'hot' and letting YOU, perhaps, perform the function
of shorting to ground. SOME OLDER APPLIANCES cheated here, and didn't
use all 4 wires, although all now have to.
If you're just running an electric motor at 220, then that machines
cord should only have 3 prongs - ground, hot, and hot. If you're trying
to plug it into an outlet designed for a dryer, say, that also has a ground,
you're going to end up with something not connected. You'd do better to
install a proper outlet dedicated to the device. If you're REALLY sure
of what you're doing, and what ANY future user of your work will be as
well, you could make an extension that leaves out the neutral - but right
now you haven't told us enough to be sure of that - I'm just speculating.
All these sorts of outlets/plugs are keyed for reasons - they
control/specify the max current allowed as well, and using the wrong
ones can get you in big safety trouble. Please be careful.
|
291.1151 | | TEKVAX::KOPEC | Consider a spherical chicken; .. | Thu Feb 06 1997 20:53 | 10 |
| the four-prong outlet has two hots, a neutral, and a ground; you only
need to connect the two hots and the ground to the three-prong outlet.
I'd *guess* that the twist-lock plug will have some hints as to which
wire is what.. the ground is probably a green screw, the hots are
probably brass, and neutral is probably plated (silvery). (the same
will likely be true for the three-prong socket, but that's not really a
challenge to figure out anyway..)
...tom
|
291.1152 | Thanks! | STAR::SCHEN | | Fri Feb 07 1997 12:17 | 10 |
|
Thanks for the info. I checked out the manual for the
generator and now know which of the four terminals on the
220/110 outlet are the ground and the two hots. (I will be
NOT connecting anything to the neutral)
Ground goes to ground, but do I need to worry about which
of the brass terminals the two hots go to? It seems like it
would not make a difference to the end product (running the
240 jointer).
|
291.1153 | either way.. | TEKVAX::KOPEC | Consider a spherical chicken; .. | Mon Feb 10 1997 12:16 | 5 |
| it does not matter which way the hots are connected (it just gives you
a 180 degree phase shift, but in a single-phase system that doesn't
matter..)
...tom
|
291.1154 | Works Great | STAR::SCHEN | | Mon Feb 10 1997 16:54 | 16 |
| Well, I put the ends on the extention cord and fired up the generator.
The line checked out fine with a meter and I was about to plug in the
Jointer but decided to put a new power cord on it (the old one was in
worse shape than my shiny new yellow waterproof extension).
I was checking out the way the old cord is was wired to the motor and
found that the meter read Zero resistance between the Hot terminal on
the cord and the body (ground) of the machine!! But there was infinite
resistance from the body to the ground prong on the cord!
I rewired it and had my wife 'spot me' while I fired everything up for
the first time and it works great. We celebrated my still breathing
by her lecturing me on 'when to hire an electrician' :-)
Anyone who needs a staight edge, feel free to call !
Thanks for pointers.
|
291.1155 | | ASIC::RANDOLPH | Tom R. N1OOQ | Wed Mar 05 1997 15:47 | 8 |
| One of the duplex outlets in the living room is dead. It seems to be the last
one on its particular circuit, i.e. one 14/2 comes into the box and ends at
the outlet.
I flipped every switch on the lower floor, nothing. So now what? How does one
trace the wiring back without opening every box in the house?
(The map of all the house circuits is still on the things to do list)
|
291.1156 | | WLDBIL::KILGORE | BEA; same chattel, new owner | Wed Mar 05 1997 16:23 | 32 |
| re .1155:
Start by making sure that no circuit breakers are tripped (or fuses
blown).
Carefully remove the outlet from the box (if you're really
safety-conscious, turn of the house main breaker first, then remove the
outlet, then turn the main back on and reprogram the VCR).
With a VOM, check for voltage on the wire to the outlet. If it's there,
switch off breakers until it goes away. When the line is dead, if it was
attached to the outlet using the quick connectors in the back, remove it
and attach it to the screw terminals on the side, then restore power and
check the outlet. (NEVER use the quick connectors!) If the outlet is still
dead, or if the wires were already on the screw connectors, replace the
outlet.
If there's no voltage on the line to begin with, you probably have
a bad connection at another box, either an outlet or a switch box. If
you found the wire connected to the dead outlet by quick connectors,
start by removing the wires from the quick connectors on the other
outlets in the room and attach them to the screw terminals. (This is
why you NEVER use the quick connectors -- the connections often go bad,
and if the outlet was used as a pass-through to the next box,
everything downline goes dead. Futhermore, as the connection is *going*
bad, it can develop an increasing resistance that can create a lot of
heat.)
IF the problem is still there, check the outlet boxes on other rooms,
starting with anything in proximity to the dead outlet, for bad
connections.
|
291.1157 | | ASIC::RANDOLPH | Tom R. N1OOQ | Wed Mar 05 1997 18:14 | 23 |
| The wires are already attached to the screw terminals, and a VOM showed no
juice under any conditions. Also, this particular outlet is sort of by
itself, so there's not really a logical next box to go to, to find the rest
of the circuit:
|| || ||
|| || || ^
++ ++ || |
|| |
bath hall closet || stairs
|| up
++ ++ ||
|| || ||
--------+| |+-----------+|
---------+ +-----===-----+
^
|
living room +---- dead outlet
All of the breakers looked ok, and I have no reason to believe that this is a
dedicated outlet with it's own breaker or anything... Oh, the ceiling light
in the hall above also is dead - might be a related problem. It's 3-way
switched at both ends of the hall, haven't checked into it yet.
|
291.1158 | You can't always "see" a tripped breaker | SSDEVO::JACKSON | Jim Jackson | Wed Mar 05 1997 22:10 | 15 |
291.1159 | | ASIC::RANDOLPH | Tom R. N1OOQ | Thu Mar 06 1997 11:27 | 7 |
| > Cycle (off/on) all the breakers.
Yah, I have to do that eventually anyway in order to map out all the
circuits. What the heck, it's free and easy...
I'll be surprised if this guy put only one ceiling light and one outlet on a
breaker, though.
|
291.1160 | ah ah ah ah sta-in alive sta-in alive | HNDYMN::MCCARTHY | A Quinn Martin Production | Thu Mar 06 1997 12:55 | 5 |
| >>What the heck, it's free and easy...
And you get a great strobe effect from all the clocks/VCRs flashing
12:00 - 12:00 - 12:00
:-)
|
291.1161 | | TEKVAX::KOPEC | Consider a spherical chicken; .. | Thu Mar 06 1997 13:05 | 28 |
| FIrst I'd check that 3-way light; might be a backwire-to-screw "splice"
that went west.. or a bad wirenut somewhere..
take your handy outlet-wiring-tester (the things with three lights on
it), and wander around the house finding any other outlets that are
dead..
It is possible that a "fox and hound" sounder might be sensitive enough
to trace the wire behind the sheetrock, but I've never tried this
(that's on my toy list... someday..)
Another tool that everybody should have for these kinds of things is a
voltage probe.. Fluke makes a nice one (AC-1, about $20), and I think
Radio Shack has come out with one too..
I had to replace the bulb in the halogen floodlight above the driveway,
but (because the bulb was dead!) I didn't know what breaker it was on..
but I did know where the wire went up the wall from the garage, so I
just had my daughter hold the probe against the outside of the NM cable
and flipped breakers till the probe went off..
it's also handy for when you go help Dad out with a project and he says
"Yeah, I already killed that circuit.." .. you can sniff the box
without having to probe the metallic parts of the wires/terminals..
|
291.1162 | | skylab.zko.dec.com::FISHER | Gravity: Not just a good idea. It's the law! | Thu Mar 06 1997 15:52 | 7 |
| I agree with checking that light first. In fact, I bet one of the switches is at
the bottom of the stairs and thus not far from the outlet. That's where I would
start. That may be where the power feed to the outlet is coming from, and
especially if it is an add-on outlet, that might be a big mess in the 3-way switch
box.
Burns
|
291.1163 | check the 3way switches | CPEEDY::BRADLEY | Chuck Bradley | Thu Mar 06 1997 20:58 | 4 |
|
check the three way switches. when they get old, sometimes some of them can
stop in an intermediate position, neither side hot.
|
291.1164 | | ASIC::RANDOLPH | Tom R. N1OOQ | Fri Mar 07 1997 11:08 | 4 |
| I started mapping out all the circuits last night. That'll at least give me
someplace to start looking for the next box up the line. The breaker labeled
"smokes/halls/bath" doesn't switch off the smoke detectors (120VAC only, as
far as I know). Great. I wonder which one does?
|
291.1165 | Being lazy, I'd try this before pulling the main breaker | EVMS::LYCEUM::CURTIS | Dick "Aristotle" Curtis | Fri Mar 07 1997 11:44 | 11 |
291.1166 | kids, don't try this at home.. | TEKVAX::KOPEC | Consider a spherical chicken; .. | Mon Mar 10 1997 10:23 | 10 |
| household rubber gloves are not durable enough to be considered
protection.. they can easily develop a pinhole from little things like
a burr on a terminal screw where a screwdriver cammed out in the
distant past..
Thinking you are safe when you aren't is much worse than thinking you
aren't safe..
...tom
|
291.1167 | as .-1 says - don't try this at home (or anywhere) | HNDYMN::MCCARTHY | A Quinn Martin Production | Mon Mar 10 1997 13:38 | 15 |
| >> If the nervousness is regarding yourself and not just some interesting
>> sparking and a tripped breaker, wouldn't a pair of rubber gloves do the
>> job?
Wow - I never thought of that - Never seen it done either, maybe there is a
reason.
The gloves used by lines people once in a while are much thicker than the
household type.
Its kind of strange because I trust the rubber coating on my 9" linesman Klein
pliers and that is very thin - never thought about it - but I do toss the pair
out if a nick develops.
bjm
|
291.1168 | | skylab.zko.dec.com::FISHER | Gravity: Not just a good idea. It's the law! | Mon Mar 10 1997 15:37 | 5 |
| You probably don't have to take it out anyway...you can usually reach the
terminal screws with a multimeter probe by just taking of the decorative
cover. Use great caution, especially if it is in a metal box.
Burns
|
291.1169 | | PCBUOA::TARDIFF | Dave Tardiff | Tue Mar 11 1997 19:46 | 6 |
| >Its kind of strange because I trust the rubber coating on my 9" linesman Klein
>pliers and that is very thin - never thought about it - but I do toss the pair
>out if a nick develops.
Gee, could I have the next pair instead of the trash? I use 'em
on cold wiring - I don't mind the rubber flaws. Or I'll re-dip 'em!
|
291.1170 | out of the front line and into the rear | HNDYMN::MCCARTHY | A Quinn Martin Production | Tue Mar 11 1997 21:28 | 5 |
| "out" means - into the "spare" tool box(es). I think I have four
sets somewhere in the house.
bjm
|
291.1171 | | ASIC::RANDOLPH | Tom R. N1OOQ | Fri Mar 21 1997 11:52 | 21 |
| Well, I finally finished mapping out all my electrical circuits. It turns out
that:
- the breaker labeled "smokes/halls/baths" really does switch the smoke
detectors after all.
- the dead outlet in the living room is ok, it's just wired funny. All of the
living room outlets except for that one switch the top and not the bottom.
That particular outlet switches both on when all of the others switch
off... good for a night light maybe? Can't say I've ever seen this done
anywhere else.
Safety note: don't assume anything with electrical stuff. I assumed it was
dead and got bit by 120V... that's when I realized what was going on... it
came as a shock, heh, heh.
- somebody never bothered to actually wire any electricity to the hall light
that doesn't work. In fact, I can't figure out what the heck they were
thinking when they wired that. It didn't match any concept of a 3-way
switched light that I've ever seen. The wires are all there, based on some
probing between boxes with very long leads on the VOM.
|
291.1172 | | HYLNDR::BROWN | | Mon Mar 24 1997 17:05 | 83 |
|
I'm curious, I began mapping out the circuits in my house so I could
turn on some temporary lights (been waiting for the electrician to do
this the last 4 weeks -- 6 broken appointments later I'm still
waiting).
Anyway, wire nutted everything (this is new wiring) and began tracing
the first circuit.
14-2, 15A (I'm assuming 15A because 14-2 feeders(?))
. switch to (1) recessed light
. switch to (3) recessed lights
. switch to (1) recessed light and (1) hanging light
. switch to (3) outside post lights [future]
. switch to (2) recessed lights
. switch to (4) garage interior lights (future)
. switch to (4) garage exterior flood lights (future)
. switch to (1) hanging light
. switch to (1) recessed light (future)
. switch to (1) flouresent light, closet
. switch to (1) recessed light
. 2 duplex outlets (in mudroom)
. 3 duplex outlets (in pantry/includes freezer)
. 1 duplex outlet for "art light" - high on wall
Its been awhile since I did electrical stuff, but this seems a tad
excessive for a 15A circuit. Could I use a 20A or 30A breaker?
Usually I use 12-2 for 20A and 10-2 feeders for 30A circuits. Its
passed inspection and the contractor has paid the rough-in fee
(although bathroom vents not wired, well pump not wired, and about
another 2-6 circuits are missing). This circuit is spread out over 5
different rooms (not counting future garage and outside lights).
Garage is being wired now because there won't be any access without
lots of hacking and whacking of drywall later.
Is it 10 duplex outlets/lights per 15A circuit? 12A I think is the
rule for 15A (80%), so 23 lights @ 1.2A + 6 outlets @ 1.2A is more
like 34.8A or a 50A circuit (40A = 32amp load allowance @80%)?
Assuming it is a 15A circuit, I believe I have to spit the circuit
four ways to get it under control. This split is paritally based upon
logical physical area groupings more than a minimum subset of things.
I'm suggesting that I split the circuit as follows:
Existing 14-2:
. switch to (1) recessed light
. switch to (3) recessed lights
. switch to (1) recessed light and (1) hanging light
. switch to (3) outside post lights [future]
. switch to (2) recessed lights
[This is 11 lights, upgrade the feeder to 12-2 20A?]
New 10-2 feeder, 20A:
. switch to (4) garage interior lights (future)
. switch to (4) garage exterior flood lights (future)
[This is 8 lights, but I can tap the 10-2 to support
a couple of outlets in garage]
New 14-2 feeder, 15A:
. switch to (1) hanging light
. switch to (1) recessed light (future)
. switch to (1) recessed light
. 1 duplex outlet for "art light" - high on wall
New 12-2 feeder, 20A:
. switch to (1) flouresent light, closet
. 2 duplex outlets (in mudroom)
. 3 duplex outlets (in pantry/includes freezer)
[6 units of load]
This is only the first circuit I've fully mapped (I partially mapped
another) but I certainly hope I don't have to rewire the whole house!
[Meanwhile the contractor wants to ignore the whole issue and slap
up drywall -- it passed the town inspection and I'm holding things up
by making an issue of it.]
Any advise?
Bud
|
291.1173 | | OVRTYM::RANDOLPH | Tom R. N1OOQ | Mon Mar 24 1997 17:31 | 14 |
| > <<< Note 291.1172 by HYLNDR::BROWN >>>
A quick calculation:
22 lamps X 75 watts (75 watt bulb in each)
= 1650 watts
/ 120V = 14 amps
That's not even including whatever gets plugged into the outlets, or any 100W
bulbs. Make 'em do it right. It's your house that'll go up in flames.
BTW, you probably know this by now, but town inspections are crapola. Must be
a hell of a job if you can get it... 5 minutes per inspection, 5 inspections
per day, 15 minutes to drive to each = about 1 1/2 hours work per day.
|
291.1174 | Freezer too ? | FOUNDR::DODIER | Double Income, Clan'o Kids | Mon Mar 24 1997 19:21 | 7 |
| I think you need 12-2 if you want to use a 20amp breaker. It does
seem like an awful lot on one breaker, especially a 15amp one. The
pantry plugs could likely see some high wattage appliances, and if I
read your reply right, the freezer could be a significant load (at
least the start up current anyway).
Ray
|
291.1175 | 20 AMP IN PANTRY | SOLVIT::MCCOY | | Mon Mar 24 1997 21:36 | 31 |
| RE: .1172
> 3 duplex outlets (in pantry/includes freezer)
See 210-52(b) of the N.E.C. "In the kitchen, pantry, breakfast room,
dining room, or similar areas of a dwelling unit, the two or more
20-ampere small appliance branch circuits required by Section
220-4(b) shall serve all receptacle outlets covered by Sections
210-52(a) and (c) and receptacle outlets for refrigeration equipment."
A separate circuit for the freezer is desirable but not required by
the N.E.C.
The house will not go up in flames with too much load, the circuit
breaker will trip and protect the wiring.
While not required by the N.E.C., it would make sense to limit the
load on any one circuit to 80% of what you would consider the maximum
load at any given time.
The number of general purpose receptacles on one circuit in a dwelling
is not limited by the N.E.C. In other than dwellings, general purpose
receptacles are assumed to use 1.5 amps and the sum of the amperage
can not exceed the 15 or 20 amp circuit rating. 30 amp circuits
are not allowed for general purpose receptacles.
20 amp circuits would allow more load per circuit, but some lighting
fixtures are labeled "connect to 15 amp circuit only"
|
291.1176 | | HYLNDR::BROWN | | Tue Mar 25 1997 13:43 | 30 |
|
Talked to the building inspector, 1.5A allowance per fixture whether light or
outlet. This may be a generalization, but is certainly easy enough to
apply. Building inspector said to split the circuit to meet the above
guideline.
The electrician (finally) showed up this morning, demanded full payment
by friday at which time he will sue me & place a lien on my house. (I
note that he said nothing about the contractor -- guess its easier to
sue the future home owner.) Then he left. Yup, just what I need.
Meanwhile. The pantry wiring is 14-2 -- which seems ok for nominal
outlets such as in bedrooms and such. However, if a 20A circuit is
needed, nay required, for the pantry then do I rewire the outlets
in that room from 14-2 to 12-2? The feeder certainly should be 12-2,
but I've always wired circuits throughout with the same gauge wire.
Also, anyone know a good building inspection firm -- esp. one that
specializes in electric code? The contractor and I have agreed that
it may be easier/better to have a 3rd party access the situation. That
way we'll know what, if anything, needs to be fixed. Then we can get
an estimate to do those changes and then we'll know how much to
with hold from the final payment to the electrician (and have backing
documentation for same).
To top it all off getting all this straightened out so we can
confidently move onto drywall is really going to mess up the schedule
big time! Since I've sold my previous residence and my short term
lease on the apartment I moved into runs out in another 2 months I'm
just about ready for... Nervous? Nah, scare sh*tless!
|
291.1177 | | WLDBIL::KILGORE | BEA; same chattel, new owner | Tue Mar 25 1997 14:10 | 17 |
|
> The electrician (finally) showed up this morning, demanded full payment
> by friday at which time he will sue me & place a lien on my house.
If he's serious, countersue and place a lien on his house. However, I
can't imagine him demanding payment until after his work is ok'd by
the inspector.
> Meanwhile. The pantry wiring is 14-2 -- which seems ok for nominal
> outlets such as in bedrooms and such. However, if a 20A circuit is
> needed, nay required, for the pantry then do I rewire the outlets
> in that room from 14-2 to 12-2? The feeder certainly should be 12-2,
> but I've always wired circuits throughout with the same gauge wire.
If you change the circuit to 20A, all wire on that circuit has to be
12-2.
|
291.1178 | Code question | TALLIS::KOCH | Kevin Koch TAY1-2 DTN227-4043 | Wed Mar 26 1997 11:48 | 4 |
| The tab on the madison hanger in an outlet box occasionally touches
one of the screws on the outlet and pops the breaker.
Does the code let me put tape over the screw and over the metal tab?
|
291.1179 | | REGENT::POWERS | | Wed Mar 26 1997 11:55 | 18 |
| > <<< Note 291.1178 by TALLIS::KOCH "Kevin Koch TAY1-2 DTN227-4043" >>>
> -< Code question >-
>
> The tab on the madison hanger in an outlet box occasionally touches
>one of the screws on the outlet and pops the breaker.
>
> Does the code let me put tape over the screw and over the metal tab?
Jeesh, I hope not.
If you've got a situation where something is "occasionally" touching
something else, you've got too much movement in the box and things need
to be tightened down.
Put tape over it and the motion will continue, probably wearing the
tape enough so that eventually there will be a high resistance path
instead of a short, and you won't pop the breaker, you'll start a fire
in the box.
- tom]
|
291.1180 | | REGENT::POWERS | | Wed Mar 26 1997 11:57 | 10 |
| > <<< Note 291.1176 by HYLNDR::BROWN >>>
>
>
> Talked to the building inspector, 1.5A allowance per fixture whether light or
> outlet. This may be a generalization, but is certainly easy enough to
> apply. Building inspector said to split the circuit to meet the above
> guideline.
Didn't anybody file electrical plans on this job?
Did anybody (you, contractor, or inspector) review them?
|
291.1181 | | HYLNDR::BROWN | | Wed Mar 26 1997 13:51 | 20 |
|
There is a signed project plan which includes required outlets,
switches, lights, subpanels, etc. descriptions on a room by room
basis. This along with a statement requiring wiring to meet all
applicable NEC and local codes. Included is floor plan views of
the lighting plan of record including placement and model numbers.
Its the electrician's job to break these down into circuits -- and
we did request one both before, during, and after the electrician
declared rough-in complete. The answer was an emphatic no; he doesn't
provide one until after final.
I feel I should be able to trust a licensed electrician to
do work that meets code -- and trust is require that subs will
perform work that meets the plan of record. I can easily visually
verify whehter something is missing vs the plan -- its harder for
me to determine whether it meets code without reading and understanding
the code myself. [Why do we have licensing programs if home owners are
also required to learn the code to protect themselves?]
|
291.1182 | | vaxcpu.zko.dec.com::michaud | Jeff Michaud - ObjectBroker | Wed Mar 26 1997 14:57 | 10 |
| > I feel I should be able to trust a licensed electrician to
> do work that meets code .....
Well sadly that is your mistake. *Never* trust a contractor,
no matter how trustworthy they sound, or how many recomendations
and rave reviews your friends gave of a given contractor. Yes,
there are honest ones out there, but the problem is you can't
tell them apart so have to assume the worse.
Same with auto shops, commisioned sales people, etc
|
291.1183 | | HYLNDR::BROWN | | Wed Mar 26 1997 15:04 | 11 |
|
"Trust but verify" is my motto.
Anyway, I seem to recall hearing/reading somewhere that you don't have
to be licensed to be an electrician in new hamshire? Is this true.
I'm looking for the licensing bureau in new hampshire for licensing
electricians, plumbers, and other tradesman and can't seem to find
it in either the phone book or the nh agency web page.
|
291.1184 | Well, sort of... | FOUNDR::DODIER | Double Income, Clan'o Kids | Wed Mar 26 1997 15:10 | 5 |
| I believe a home owner can do electrical work in their own home
without a licence. They must still pull the permit, submit the appropriate
plan, and get the work inspected.
Ray
|
291.1185 | reply -.1 Derry, you MUST have an electrician | FOUNDR::SKABO | Expect Nothing U never disappointed | Wed Mar 26 1997 15:23 | 9 |
| reply -.1
Sorry, in Derry, you MUST have an electrician (registered with NH)
pull the permit - doing the work is another story.....
Some other NH tows now also have this in requirement, and ya can't
get around it! ;*( No live free or die....
Tom
|
291.1186 | | HYLNDR::BROWN | | Wed Mar 26 1997 15:54 | 12 |
|
I don't want to do this... just wondering if the electrician is really
licensed, or has to be. I found the state agency regulating this
field:
Electricians Licensing Board
78 Regional Drive, Building 1
PO Box 646
Concord, NH 03302
Attn: Pamela Olin
|
291.1187 | | HYLNDR::BROWN | | Wed Mar 26 1997 15:58 | 6 |
|
...and unfortunately there is reciprocity only with Mass., Maine, and
Vermont. So I guess renewing my Journeymans License in R.I. won't
do much good.
|
291.1188 | Live Free or Die Except in Derry | SOLVIT::MCCOY | | Wed Mar 26 1997 19:35 | 31 |
|
RE: .1185
I was also told by the Derry building inspector that I could not do electrical
wiring or plumbing in my own home. He said they have already been to court
and won the case. I don't understand how they can get away with this,
N.H. sate law allows a home owner to do this. Doesn't state law supersede
town ordinances or the whim of the building inspector. I wonder if this
really went to court. What other towns have this restriction? .1184 is true
in most other towns, even Nashua. Maybe Derry can outlaw free speech too.
RE .1175
My point is the wiring described in .1172 violates the N.E.C. because
pantry receptacles must be on a 20 amp circuit separate from everything
except the receptacles in the kitchen and dining room. No lights can
be on this circuit. See N.E.C. 220-4(b) and 210-23(a) Exception.
Also, my interpretation of 210-23(a) is that the sum of the ratings of the
lighting fixtures in .1172 can not exceed 50% of the circuit rating.
|
291.1189 | Sounds weird | FOUNDR::DODIER | Double Income, Clan'o Kids | Wed Mar 26 1997 20:51 | 23 |
| Well, I guess I stand corrected, at least in Derry. In talking to the
author of .1185 (works in my group), he said you used to be able to do it
until they changed building inspectors. Sounds like the new inspector wants
to limit his liability.
As far as the original question, it sounds like if you gave the
electrician a copy of the appropriate NEC code that he violated, it would
shut him up about threatening to sue you. The agreement was that he would
do the work per code.
Since the electrician wanted to be an ass about it, I'd probably take
pictures of his work (document the 15amp wiring in the pantry) and tell
him if the work isn't corrected pronto, you'll report him to the local
inspector. No licenced worker wants to get a bad name with a local
inspector if they can help it.
Aside from that, if you don't own the house now, why would you be
paying for this instead of the contractor ? If it's a house your buying,
any liens on the house must be cleared before you can buy it. I would
think that he'd be SOL if he waited to collect from you when it's the
contractor that owes him the money.
Ray
|
291.1190 | | HYLNDR::BROWN | | Mon Mar 31 1997 20:08 | 39 |
|
I'm the owner of the land and house as it sits. The bank gives me the
money and I give it to the contractor -- that's why the bank makes me
sign a lien waiver at each withdrawal for the full amount. The deed
and morgage lien are in my name.
The electrician won't be back. I have pictures of all his work.
I've produced a wiring diagram of the circuit which will be verified by an
independent building inspection firm. The electrician has told the
contractor that he isn't liable for the wiring since I obviously
rewired it incorrectly. He inferred that I connected several circuits
together so of course its overloaded... except I've accounted for
all wires in all boxes and there is only one feeder into the circuit.
In addition, the line side had already been twisted together and wire
nutted in most boxes. But anyway, it now comes down to him saying I
rewired his work to make him look bad and me saying I didn't. This sub
is the contractor's responsibility and therefore liability and in that
there is no dispute.
Personal opinion is that the electrician has about 3 jobs too many at
present (hence the reason he was showing up ~1 day/week only after we
called and called and called) and was doing work a little too quickly,
doesn't need the job, and is glad to be gone. [This is now the 11th or
12th week of rough-in (started about 1/20) -- at first things went thru
ceiling joists, but near the end wires were just laid on top of them.
This makes walking in the attic area interesting. The point being the
work changed workmanship levels from beginning to end.]
Wierd don't even began to cover it.
Someday I'll publish my diary and the pictures I've taken during the
project... including the framing piece I'm proudest of; an 18:12 pitch
round turret roof clad in hand cut/fitted copper foil shingles (fiberglass
core, bonded copper foil top) topped with the copper cone I fashioned out
of 24" wide 20 oz. copper flashing. I knew my old commutator irons would
come in handy some day! It took me and my brother-in-law a day and a
half to erect... and me 4 days to pre-cut all the framing and
sheathing materials.
|
291.1191 | | ASIC::RANDOLPH | Tom R. N1OOQ | Wed Apr 02 1997 13:58 | 17 |
| > - the dead outlet in the living room is ok, it's just wired funny. All of the
> living room outlets except for that one switch the top and not the bottom.
> That particular outlet switches both on when all of the others switch
> off... good for a night light maybe? Can't say I've ever seen this done
> anywhere else.
It turns out I was wrong about this... it worked fine with a single 25 watt
bulb plugged in, but 120 watts of bulbs lit up very dimly. Back to square
one...
I broke down and started opening boxes around the room. I finally found the
other end of the mystery box's romex. Seems he wired it between the switched
hot and the permanent hot in one of the split outlet boxes.
Switch "on" - 120v each side, no light. Switch "off", 120v one side, nothing
on other side, but it got a crappy ground somewhere and lit dimly.
Interesting electrical problem, now fixed.
|
291.1192 | New 220 volt circuit | 11673::SUTER | and now for something you'll really like! | Wed Apr 09 1997 14:25 | 17 |
|
Just purchased a 220 volt shop appliance which uses a plug that
looks like a standard, three prong 110 plug except one of the flat tines
is turned 90 degrees, like this:
o
- |
I'm installing a dedicated double breaker for a new 220 circuit
for this appliance, but am unclear on the actual wiring configuration.
Anyone have a "wiring for dummies" diagram for this type of circuit? Also,
I know the amp rating of the machine, but does this plug configuration also
imply a specific Amp rating?
thanks,
Rick
|
291.1193 | 120VAC versus 220VAC Plugs | NETCAD::B_MACARTHUR | | Wed Apr 09 1997 16:35 | 11 |
| Rick,
The plug that you describe is not a 220VAC plug, it's a 120VAC, 20A
plug (assuming that you're drawing is looking into the end of the
plug). If it's a drawing looking into the mating receptacle, then it's
rated for 220VAC, 20A. The 120VAC plug is a 5-20P plug, and if the
blade that's turned 90 degrees were on the other side, then it's a
6-20P and it's the 220 variety.
Bob
|
291.1194 | Please help me get the wiring correct as well.. | 11673::SUTER | and now for something you'll really like! | Wed Apr 09 1997 16:57 | 20 |
| > Rick,
>
> The plug that you describe is not a 220VAC plug, it's a 120VAC, 20A
> plug (assuming that you're drawing is looking into the end of the
> plug). If it's a drawing looking into the mating receptacle, then it's
> rated for 220VAC, 20A. The 120VAC plug is a 5-20P plug, and if the
> blade that's turned 90 degrees were on the other side, then it's a
> 6-20P and it's the 220 variety.
>
Bob,
I think I may have been drawing it from a receptable perspective.
This of course is further confirmed by the fact that the new applicance
says 220VAC in big letters right on it.
thanks,
Rick
|
291.1195 | | 19466::ARSENAULT | | Wed Apr 09 1997 17:19 | 10 |
| While we're on the subject of unusual plugs...
I have a two speed whole house fan that I want to wire using a plug.
This is because I need to physically move the fan into and out of
place each year.
The fan has two hot wires (low speed and high speed), a neutral, and
a ground.
Is there a correct to make this pluggable device?
|
291.1196 | my guess.. | TEKVAX::KOPEC | Tom Kopec W1PF | Wed Apr 09 1997 18:21 | 35 |
| re Rick:
(note: do this at your own risk. I'm not an electrician.)
The plug has two "HOT" and a ground wire. If you are using plain old
12-2 NM cable to wire it:
at the breaker box,
the bare wire connects to the ground (not neutral,
if they are different) busbar (it will have other
bare wires attached to it).
wrap the insulation of the white wire with a couple
turns of black electrical tape near the bared end,
and connect it to one screw on the breaker.
connect the black wire to the other screw on the breaker.
at the outlet:
The bare wire connects to the green terminal.
Do the black tape thing to the white wire, and connect it
to one of the brass terminals.
connect the black wire to the other brass terminal.
For the curious, the dance with the electrical tape is required by
code; it is an exception to the rule "white wires are always neutral".
I believe that plug config is 20A; it will be marked on the mating
socket. (if the mating socket says "125V", we have an artwork problem
here..!)
...tom
|
291.1197 | always be careful.... | PCBUOA::TARDIFF | Dave Tardiff | Wed Apr 09 1997 19:42 | 25 |
| The code says something like 'white conductors used for hot
lines must be marked'. Rather than tape, I prefer to mark by coloring
the last inch or so of white insulation with a permanent black marker,
as I get a cleaner and non-removable marking. This is most often done
on 'switch loops' used when power runs to a ceiling box, and a length
of 14-2 is used to bring the power down to the switch and back up, so
both the black and white leads are used for 'hot', and should be so marked.
When you're wiring the 220V-rated receptacle, both of the screws
will be gold colored, since it doesn't matter which 'hot' line goes where.
I've been wiring up for a device that needs 4 conductors - both
hots (220) plus neutral plus ground. I'd figured out that what I needed
was a L14-20 (NEMA standard designation) which translates to a twist-lock
4 conductor 20 amp 125/250 volt configuration. Physically, it's got 4
conductors, in twistlock formation. So off I went to HD...and found what
I thought was the right thing by looking for twistlock....4 conductors...
yup, says 250 volts...got 3 plugs and 1 receptacle. When I started to
wire it up, the plugs had gold screws on all 3 non-ground pins...hmmm....
which one gets the neutral? Turns out I'd bought L15-20 by mistake,
which is 20 amp, 250 volt, 3 PHASE...so you get 3 hots, no neutral...and
they vary the pins a bit so it's not compatible with what I wanted.
In general, though, for basic 120 stuff - black and red wires go
to gold screws, white goes to silver.
|
291.1198 | which direction is white hot? | REGENT::POWERS | | Thu Apr 10 1997 12:41 | 20 |
| > The code says something like 'white conductors used for hot
>lines must be marked'. Rather than tape, I prefer to mark by coloring
>the last inch or so of white insulation with a permanent black marker,
>as I get a cleaner and non-removable marking. This is most often done
>on 'switch loops' used when power runs to a ceiling box, and a length
>of 14-2 is used to bring the power down to the switch and back up, so
>both the black and white leads are used for 'hot', and should be so marked.
Since you bring it up, in which direction should the white wire be used
as hot? I've done this, of course, but never knew ifthere was a convention
or code statement about whether the white should carry hot to the switch
or back from it.
My guess would be that white carries hot to the switch so that black can
be used to carry hot back to the appliance. This makes a "natural" connection
of black feeding hot into a box and makes it obvious that the white is lilkely
to be connected to the black hots that come into the distribution box.
But guesses like this don't always turn out true.
Is there a proper choice?
- tom]
|
291.1199 | | TEKVAX::KOPEC | Tom Kopec W1PF | Thu Apr 10 1997 14:32 | 9 |
| I *believe* that if you use the marked-white, you can do it any way you
want.
I *believe* there is a specific wiring required by a NEC exception when
you do NOT mark the white. I can't remember exactly which way the
required wiring goes, however (I always end up looking it up.. I don't
do a lot of switch loops these days..)
...tom
|
291.1200 | | PCBUOA::TARDIFF | Dave Tardiff | Thu Apr 10 1997 15:01 | 56 |
| >Since you bring it up, in which direction should the white wire be used
>as hot? I've done this, of course, but never knew ifthere was a convention
>or code statement about whether the white should carry hot to the switch
>or back from it.
I recall that there IS a convention, and depending your inspector,
you might get called on it, but I can't recall which way it goes.
I think you use the white conductor to RETURN the power to the
fixture - I'm basing this on the memory that that's the only time you
can hook up a black and white wire together, at a light fixture. I may
be wrong, though...
Simplified case - power running to a ceiling box and stopping there,
switch loop running down to a single switch. So, coming in to the ceiling
box you've got a power feed - ground, hot black, neutral white. You've
also got a black and white and ground from the switch loop, and you've got
a ground and black and white from fixture.
First, all grounds in the box connect together and to the metal box
itself. I do this first and tuck 'em down out of the way. The feed wire
hot/black connects to the switch loop black, making it always hot - normal
so far. At the switch box, you hook the hot/black to one screw - a simple
switch (single pole, single throw) has only 2 gold screws. Color the white
end black, and attach it to the other. This part seems logical to me, since
it's NOT always hot, depending on the switch. Back at the ceiling, color
the white end black again, and attach it to the fixture black - here's your
abnormal connection. Now connect the fixture neutral white to the feed
neutral white, and you're done. If the feed was to continue on to another
location (always hot) you'd just add it's black and whites to that of the
original feed.
I find that tracing the power flow this way - starting at feed hot
and continueing through to feed neutral - helps me keep it all straight.
Whether it's correct or not, this way makes sense to me, since the
wires that are ALWAYS hot are all real black.
A common error is to wire the switch loop and device in the wrong
sequence - power goes from feed to device and THEN to switch and back.
This means that the device feed is ALWAYS hot - you CAN'T shut it off, just
interrupt the return path - not nice at all. I have a porch light wired
this way (it came that way). Everything seemed normal - if the light stopped
working when the switch was thrown, ok, bad bulb, replace it, all fixed.
(The risk here is that the fixture feed is always on, so say while you're
on your metal ladder, which is in a puddle, and you're reaching up to unscrew
the bulb, and the glass snaps off and your hand hits the wires inside -
ZAP! Your body just provided a return path for the hot, and you may be dead.
With a proper switch, turned off, the fixture is cold and you're ok. Of
course, if you leave the switch on, you run the same risk, and the bulb
lights up as soon as you put it in. Not really a good idea, considered.)
Then I installed a auto-timer switch, electronic, in place of the switch.
One day I noticed that the switch itself seemed dead - no glowing leds any
more, and of course no light - ok, bad switch, replace it. Did so...same
results...replace the bulb, original switch ok again - realized that it
was wired backwards.
|
291.1201 | | STAR::DZIEDZIC | Tony Dziedzic - DTN 381-2438 | Thu Apr 10 1997 15:15 | 14 |
| Convention is that a switch loop receives power on the white wire
and feeds it to the switched device on the black wire. The idea
is that the device will have the "normal" black and white wires,
and the connection of the white wire to a power source (black) is
a quick clue that an intentional use of the white wire as a "hot"
conductor is happening at that point.
SO, at ceiling box, power source black connects to white going to
switch loop. Black from switch loop connects to the "usual" (brass)
terminal on fixture. Power source white connects to the "usual"
(nickel) terminal on fixture.
BTW, the NEC uses the term "identified conductor" when using a white
wire as a hot conductor.
|
291.1202 | second that | HNDYMN::MCCARTHY | A Quinn Martin Production | Thu Apr 10 1997 15:19 | 8 |
| >> Convention is that a switch loop receives power on the white wire
>> and feeds it to the switched device on the black wire. The idea
Amen - written or not, it was the way the people I used to work with did
things. It made identifying the switch leg in the ceiling box very easy (along
with other obvious things).
bjm
|
291.1203 | | skylab.zko.dec.com::FISHER | Gravity: Not just a good idea. It's the law! | Thu Apr 10 1997 16:32 | 17 |
| The other nice thing about this scheme is that if you use a tester on it, the
white wire will always test hot. If the white wire were only hot when the
switch was on, you might discover it to be cold with a tester, and then proceed
on the assumption that is was neutral.
On another subject: The ceiling fan. I don't know what the code says, but the
only way I can think of that I would feel even slightly comfortable with would
be to use two normal 110V plugs with neutral and ground on both and with the low
speed hot on one and high speed hot on the other. And I'd only feel comfortable
with that if the low speed and the high speed were completely independent, that
is if energizing the low speed with the high-speed unplugged did not make the
high-speed plug pin hot.
I'd really discourage using one of the 220 or 3-phase plugs even if they have
the right number of conductors.
Burns
|
291.1204 | 220 job all done! | KWLITY::SUTER | and now for something you'll really like! | Fri Apr 11 1997 15:34 | 7 |
|
The new 220/20 circuit is installed and working just fine! The new
6.5hp compressor it lotsa fun too!
thanks for all the help!
Rick
|
291.1205 | box size - am I grandfathered? | RICKS::WINDNAGLE | | Wed Apr 30 1997 16:52 | 18 |
| I pulled a permit to install ceiling lights in three bedrooms that
currently have a switched outlet instead.
So far I'm working on the first one. I believe the box at the switch is big
enough as it is, unless MA code really does differ from the NEC and
require me to count each bare wire individually (there are two switches
and three ground wires).
At the switched outlet though the box is too small as it is but I don't
have to make any changes there. I put a junction box in the attic and
connected the formerly switched red wire to black so it's always on.
Another outlet is daisy chained from this one. Can I leave this box alone
or do I have to put in a bigger one?
I guess a separate question is whether that junction box in the attic
is ok, especially after I put insulation up there and it gets covered.
/carl
|
291.1206 | | PCBUOA::TARDIFF | Dave Tardiff | Wed Apr 30 1997 18:22 | 21 |
|
>So far I'm working on the first one. I believe the box at the switch is big
>enough as it is, unless MA code really does differ from the NEC and
>require me to count each bare wire individually (there are two switches
>and three ground wires).
Last formula I used was count the insulated conductors, add one for ALL
the bare ground wires, add one for internal wire clamps, add one for
the device itself. This was a few years ago, though.
>I guess a separate question is whether that junction box in the attic
>is ok, especially after I put insulation up there and it gets covered.
The junction box being in the attic is ok - covering it up is NOT,
as far as I know. In general, it shouldn't require more than a screwdriver
to get access to ALL connections - I don't think searching under insulation
counts. Might, though.
Especially since you were good enough to get a permit, call the inspector
and ask. He's the one who'll have to pass it anyway, you might as well
find out what he wants before you do it.
|
291.1207 | | STAR::DZIEDZIC | Tony Dziedzic - DTN 381-2438 | Thu May 01 1997 11:22 | 4 |
| The NEC now counts a device (switch, receptacle, etc.) as TWO
conductors when calculating box capacity. I suspect this was
motivated by increased usage of larger devices such as GFCI
outlets.
|
291.1208 | Lights on steps/stairs | HYLNDR::BROWN | | Wed May 21 1997 13:39 | 17 |
|
Are lights required for stairs? Simple question but I expect it isn't
a simple answer. Common sense would seem to dictate that stairs be
directly lit so as to avoid accidents. But what constitutes stairs and what
constitutes being directly lit.
The particular case in question is a set of three steps between levels
of the house. There are ceiling lights in the lower level about 12'
away and ceiling lights in the upper level about 8' away from the
stairs. Although a light directly over the steps is on the lighting
plan they weren't put in and now the walls and ceiling are closed up.
What to do, what to do.
Bud
|